Ethercat Device Scan

2020-01-31
2020-02-03
  • Mino Marangi - 2020-01-31

    Hello,

    I've noticed a problem with ethercat devices scan.
    The system can't find all the devices really present.
    Using twincat, the same group of beckhoff I/Os is recognized and complete.
    In Codesys 3.15.20 I've loaded all the beckhoff XML, but some terminal in codesys are ignored.
    Someone can help me?

    Thanks
    Cosimo

     
  • eschwellinger

    eschwellinger - 2020-01-31

    Hi,
    which plc / which device is it?

    Please check if you loose frames here:
    Addition you need to check the plc logger for more information.

    BR
    Edwin

    IMG: EthercatStatus.png

     
  • Mino Marangi - 2020-02-01

    Hello Edwin,

    the PLC is based on Raspberry Compute module 3, with Codesys Control for Raspberry PI MC SL.
    I've tryed with different ethernet usb dongle and with the onboard ethernet but unsuccessful.
    I've loaded all the updated XMLs files.
    And I haven't found any error from the PLC logger.
    Also I've re-installed the OS, but the problem is the same.
    Using a PC with twincat I can see all the modules.

    I'm loosing my hair...

    Thanks
    Cosimo

    IMG: Annotazione 2020

     
  • Mino Marangi - 2020-02-03

    Hello Edwin,

    I've found the problem.
    One terminal was defective.
    Sorry for the inconvenient.

    Thanks
    Cosimo

     