I wonder if there is a possibility to use a certificate for the OPC UA Server used in the CODESYS Runtime.
I tested the Server with the UA OPC UA Client and it worked with no problems.
But if I try to connect it via the WinCC OPC UA channel used in WinCC V7.4 I have no connection although I can browse the variables and add them to my visualization. The OPC Scout of Siemens says: "Connection closed ... missing server certificate".
Maybe somebody could help me with this issue.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Thank you Edwin. I'm sure this helps many problems. I've seen the error myself and many other instances in various forums, not with Codesys but with clients trying to connect.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I'm trying connect through the OPC UA channel , my Pigeon CM3 (OPC Server in Codesys) with Siemens WinCC.
Unfortunately there is no match among the encryption types between the server and the client. My WinCC client does not connect to the server with any encryption types i choose. (see attached pictures).
I Selected the connection type Basic256Sha256 - Sign & Encrypt in the server as explained here: https://help.codesys.com/webapp/_cds_runtime_opc_ua_server;product=codesys;version=3.5.12.0.
Thanks
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
is it possible to ask the Siemens support if in newer versions WinCC supports 'Basic256SHA256' ?
Could not believe that 'Basic256' and 'Basic128Rsa15' are the only options they offer.
Which WinCC version is this exaclty?
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I wonder if there is a possibility to use a certificate for the OPC UA Server used in the CODESYS Runtime.
I tested the Server with the UA OPC UA Client and it worked with no problems.
But if I try to connect it via the WinCC OPC UA channel used in WinCC V7.4 I have no connection although I can browse the variables and add them to my visualization. The OPC Scout of Siemens says: "Connection closed ... missing server certificate".
Maybe somebody could help me with this issue.
Hi,
this is planned for 3.5SP10.
BR
Edwin
Edwin, has this feature been released?
Hi,
yes since 3.5SP12,
see:
https://help.codesys.com/webapp/_cds_ru ... -ua-server
you need to install the Security Agent Plugin from the CODESYS Store(free of chrage):
https://store.codesys.com/catalogsearch ... rity+agent
(would use the shopping cart in CODESYS to do this)
BR
Edwin
Thank you Edwin. I'm sure this helps many problems. I've seen the error myself and many other instances in various forums, not with Codesys but with clients trying to connect.
Hi,
I'm trying connect through the OPC UA channel , my Pigeon CM3 (OPC Server in Codesys) with Siemens WinCC.
Unfortunately there is no match among the encryption types between the server and the client. My WinCC client does not connect to the server with any encryption types i choose. (see attached pictures).
I Selected the connection type Basic256Sha256 - Sign & Encrypt in the server as explained here:
https://help.codesys.com/webapp/_cds_runtime_opc_ua_server;product=codesys;version=3.5.12.0.
Thanks
Hi,
is it possible to ask the Siemens support if in newer versions WinCC supports 'Basic256SHA256' ?
Could not believe that 'Basic256' and 'Basic128Rsa15' are the only options they offer.
Which WinCC version is this exaclty?
BR
Edwin
Hi Edwin,
We are using Tia Portal 14 Service Pack 1.
We are going to ask to the Siemens support if they have some clues.
Thank you
Hi Edwin,
We also tried the new Tia Portal 15. Unfortunately it has the same security policies of Tia 14.
Is it possible to set "None" in both the Tia and the Codesys side ? Siemens has this possibility.
Thanks.
Hi,
in CODESYS none should be possible..
BR
Edwin