The profinet controller is not more running.
I did try already a reinstall (with c:\ProgramData\CODESYS\ removed) but it did not change anything
On startup i see the error "Controller Error: PNIO: LMPM signaled an error"
hi,
things to check:
1. WinPCAP is installed
2. How many network adapters does your system have ( should not be more than 6) if more disable some of them..
3. Disable Firewall for the fist tests
Then in your project you have enabled to set the IP of the network which you want to use for profinet.
This need to be enabled by a setting in the config file
[SysSocket]
Adapter.0.Name="ethernet" //this is the name which you see under windows for your network
Adapter.0.EnableSetIpAndMask=1
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
The profinet controller is not more running.
I did try already a reinstall (with c:\ProgramData\CODESYS\ removed) but it did not change anything
On startup i see the error "Controller Error: PNIO: LMPM signaled an error"
hi,
things to check:
1. WinPCAP is installed
2. How many network adapters does your system have ( should not be more than 6) if more disable some of them..
3. Disable Firewall for the fist tests
Then in your project you have enabled to set the IP of the network which you want to use for profinet.
This need to be enabled by a setting in the config file
[SysSocket]
Adapter.0.Name="ethernet" //this is the name which you see under windows for your network
Adapter.0.EnableSetIpAndMask=1
BR
Edwin
Thank you it did work.
Bluetooth did make one more network adapter, disabled it and now it is working again
Hello, I am having the same issue. Where is the Config file you are mentioning?
Thanks
For Control Win plc:
c:\ProgramData\CODESYS\CODESYSControlWinV3x64\xxxxxx\CODESYSControl.cfg