CODESYS Control for PFC200 SL - missing module

damian177
2020-09-26
2020-09-30
  • damian177 - 2020-09-26

    Hi,
    I using CODESYS Control for PFC200 SL Version: 3.5.16.20
    In Wago PFC200 internal bus I try find 750-623 Wago module (Power Supply; 24 V/5 … 15 VDC) and I can't find it.
    Why ?
    Thanks in advance.

     
  • eschwellinger

    eschwellinger - 2020-09-26

    Hi,
    i think there is no need to add anything for this, other user report they using
    750-602 which is probably similar?
    No processdata for this slices...

    BR
    Edwin

     
  • damian177 - 2020-09-26

    I don't have 750-602. Please find in attachment.

     
  • eschwellinger

    eschwellinger - 2020-09-26

    let me check.. I even do not find module to attach this in eCOCKPIT. ( Maybe I'm wrong - do now know it very well)

    Do you have this in our hands?
    Just plug it an give it a try, expect as I told, if it does not have process data so no need to add anything there probably.

     

    Last edit: eschwellinger 2020-09-28
  • eschwellinger

    eschwellinger - 2020-09-28

    verified... no need to add as module in the device tree!

     
  • annD

    annD - 2020-09-29

    Hi Edwin,
    is the recent 3.5.16.20 runtime compatible with the Wago firmware V030510 (17) on a pfc200 like 750-8212 ?
    In the release notes I can only find firmware 16 with 3.5.16.10
    Thanks a lot.

     
  • eschwellinger

    eschwellinger - 2020-09-29

    yes,FW17 have been tested with 3.5.16.20 should work.

     

    Last edit: eschwellinger 2020-09-29
  • damian177 - 2020-09-30

    Additional question. I can use Runtime PFC200 3.5.16.20 with Firmware Revision 03.01.07(13) in my PFC200 ?

     
  • eschwellinger

    eschwellinger - 2020-09-30

    Hi,
    basically might work, but I would recommend to update to FW17 (tested and even sucurity updates included) -
    you just need to request it on the Wago homepage
    - write the image to an SD card
    - boot from it
    - use the wbm - copy the image to the internal flash

     
  • damian177 - 2020-09-30

    Ok, in FW17 is the same procedure like in FW13 to run serial COM (Modbus Master) on port 1 and run SMS Communiaction on port 4, by:

    add in /etc/CODESYSControl.cfg

    [SysCom]
    Linux.Devicefile.1=/dev/serial
    Linux.Devicefile.4=/dev/ttyRUNTIME66

    ?

     

Log in to post a comment.