Im trying to connect to a Phoenix Contact Inline Bus Coupler with Codesys ver 3.5.7.0 on Raspberry Pi2. I am getting these errors in the log:
No local Ethernet/IP Adapter found. Class 1 connection as target not supported.
SetOption unable to set Socket_SO_REUSEPORT
Connection Failure. Extended Status: Invalid network Connection parameter.
I have the Ethernet set up as:
I can connect to the PI and Bus Coupler. I just cant get the PI to talk to the Bus Coupler
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I have a phoenix contact ILB ETH 24 DI16 DIO16-2TX and want to configure it with the same software CODESYS 3.5 on exor PLC. Do I still have to use the EDS file as I am looking at the manufacturer's recommended software to program the contacts and there is no EDS file on the list for this unit. Any reply would be appreciated.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Im trying to connect to a Phoenix Contact Inline Bus Coupler with Codesys ver 3.5.7.0 on Raspberry Pi2. I am getting these errors in the log:
No local Ethernet/IP Adapter found. Class 1 connection as target not supported.
SetOption unable to set Socket_SO_REUSEPORT
Connection Failure. Extended Status: Invalid network Connection parameter.
I have the Ethernet set up as:
I can connect to the PI and Bus Coupler. I just cant get the PI to talk to the Bus Coupler
Hi,
this is only an info - no problem
this is only an info - no problem
this is the Problem.
One question is there a reason why not using the eds file of the PhΓΆnix device?
(-> you are using obvisouly the generic ethernet ip device)
So I would recommend to install the EDS file from your device (from the manufacturer), than it is easy to configure
BR
Edwin
Ok I have the EDS file. How do I install the EDS file into Codesys?
thanks for your help!
I figured it out. VERY COOL!
I have a phoenix contact ILB ETH 24 DI16 DIO16-2TX and want to configure it with the same software CODESYS 3.5 on exor PLC. Do I still have to use the EDS file as I am looking at the manufacturer's recommended software to program the contacts and there is no EDS file on the list for this unit. Any reply would be appreciated.