Janz-Tech emPC-A-iMX6 runtime randomly dies

AlexD
2021-12-06
2021-12-08
  • AlexD - 2021-12-06

    Hi! I have a project on a Janz-Tec PLC it may work more than 1 month or just for few days. The runtime is hanging (only fresh download help) absolutely randomly.
    I tried to upgrade the Element Collections library to version 3.5.16.0 hopping the problem should be solved but after that the project didn't download (no sufficient memory on plc error).
    Help please

     
  • eschwellinger

    eschwellinger - 2021-12-07

    In such cases first check the plclogger for more information
    cat /tmp/codesyscontrol.log
    and doing the implicit checks with checkbounds would be a good point to start to investigate the application.
    https://faq.codesys.com/pages/viewpage.action?pageId=3538982

     

    Last edit: eschwellinger 2021-12-07
  • AlexD - 2021-12-08

    Hi! I was able to download the project, there was a device description vs runtime mismatch,
    - runtime 3.5.15.30
    - project 3.5.16.0
    (no warning at download!)
    Runtime was updated after second attempt (/opt/janztec/watchog folder delete error)
    Hope no more faults, fingers crossed

     