  • pawelpol9 - 2023-03-02
    Hi. I searched many forums but couldn't find an answer anywhere. I am trying to connect the Wago pfc200 750-8212 controller to the air handling unit. When I was configuring the MOdbus RTU connection in eCockpit everything worked. When I want to do the same in Codesys I get a message that the port is not working. Maybe the reason is not setting communication via rs485? But I don't know where it is set.
    eschwellinger - 2023-03-02
    If you are on PFC200 SL in the plcshell + restart the device
    Thank you, I changed to rs485 but it still doesn't work.
    Does anyone have any idea why this port is not working? What should be the entry in /etc/CODESYSControl.cfg [SysCom] ?
    PFC side is ok, check your slave side..copy the slave name to the watch window to see the diagnosis of the fb
  • pawelpol9 - 2023-03-03
    The message changes every few seconds.
  • pawelpol9 - 2023-03-04
    The problem with no response within the specified time has disappeared. Instead, the error "Request_crc_fail" appeared. What could be the cause of the checksum error.
    eschwellinger - 2023-03-05
    either wiring or end resistor on RS485