Hi,
I need to use digital PWM signal, the current selection is Beckhoff EL2502 2ch PWM module. I added a device description file, but there are only 2 channels in IO MAPPING to adjust the duty option and no option to adjust the frequency.
IhaveconsultedthedocumentationandthefrequencyneedstobewrittenintheCoEcycle.I'm not quite able to understand this problem. I see EL2502 'sstartupParameterswiththePWMsettingsoptiontochangethefrequency,butIneedtochangethefrequencywiththerequirementsinthePLC.IsupposeIcouldbeconfiguringtheExpertprocessdatainEK1100.Idon't quite understand how to relate it to a variable.WhatIwanttodoissimilartoSchneider's FBEL2502ModuleDocumentsat[https://www.beckhoff.com/english/ethercat/el2502.htm](https://www.beckhoff.com/english/ethercat/el2502.htm)Thankyou.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
It looks like this setting can be used.
I don't have a module test yet, if someone has used it, please tell me if I can use it. Does it continue to output?
Thanks.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
I need to use digital PWM signal, the current selection is Beckhoff EL2502 2ch PWM module. I added a device description file, but there are only 2 channels in IO MAPPING to adjust the duty option and no option to adjust the frequency.
It looks like this setting can be used.
I don't have a module test yet, if someone has used it, please tell me if I can use it. Does it continue to output?
Thanks.
Hi,
either map it to the PDO's or send the SDO from your application by SDO send.
http://store.codesys.com/ethercat-example.html
BR
Edwin
Thank you very much.