Profinet communication issue

Ciprian
2016-06-10
2018-04-24
  • Ciprian - 2016-06-10

    Hi,

    I have problems communicating with Siemens IM 151-3 PN v7.0 using Control Win 3.5.8.4.
    Can you tell me what the codes from "Station Status" means?
    Attached are pictures with Station Status and Diag Data.

    IMG: Status2.png

    IMG: Status1.png

    IMG: DiagData.png

     
  • Quang Loc - 2018-04-17

    Hello,
    I got the same issue but I don't know how to solve it?
    Did you have any solution or the something in order to fix this problem?

    Thanks in advance

     
  • Ciprian - 2018-04-18

    Yes, you can try to increase the Send Clock and the Reduction Ratio.
    Hope this will help you.

     
  • Quang Loc - 2018-04-18

    Thanks for your reply.

    It works, but now I got some problem about the Siemens device. I don't have the file .xml of 6ES7-315-2FJ14-0AB0. I also created by Simatic Manager but it does not work.

    Error: The correct import filter for the file could be not detected.

    hope your help. thanks

    IMG: Capture.PNG

     
  • Ciprian - 2018-04-19

    I don't have Simatic Manager installed but I made a test using TIA Portal. I created an xml file for CPU315F-2 PN/DP + 1 DIx16 and it worked to import in Codesys.

    What version of Codesys are you using?

     
  • radionica - 2018-04-24

    Hi,
    I am using PFC200 and Wago's Profinet modules (five of them). I had to slow down Send Clock ...
    I still have problem with loosing "Online" after downloading new version of application.
    It seems that CPU doesn't have enough time to handle two Ethernet.

     
  • eschwellinger

    eschwellinger - 2018-04-24

    Hi,
    yes I agree that PFC200 is from CPU performance limited to do profinet.
    In this case it is usually better to work for example with Ethercat and 350-354

    BR
    Edwin

     