IΒ΄m having some problems in the configuration of the Edge Gateway for the connection with the Automation Server. I want to configure my PC as Edge Gateway following the instructions showed in this video: https://www.youtube.com/watch?v=iiPKyyO4M00. The problem is when i want to allow the configuration mode in the Edge Gateway this error appear.
I have restarted the CODESYS IDE, the Gateway, uninstall and download again the Edge Gateway program, but this problem persist. What can i do?
Hi,
check the location of the Gateway.cfg it should be under:
c:\ProgramData\CODESYS\CODESYSGatewayV3\randomnumber\
Check if the Gateway is really in version 3.5.16.20 by versioninfo in the tasktray
Check if you have readwrite access in:
c:\ProgramData\CODESYS\CODESYSGatewayV3\randomnumber\
Which plc do you want to connect?
Sometimes it makes more sense to activate/install the EdgeGateway on plc side ( in case it is a runtime from store this is easily possible...)
BR
Edwin
Last edit: eschwellinger 2020-09-28
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
IΒ΄m having some problems in the configuration of the Edge Gateway for the connection with the Automation Server. I want to configure my PC as Edge Gateway following the instructions showed in this video: https://www.youtube.com/watch?v=iiPKyyO4M00. The problem is when i want to allow the configuration mode in the Edge Gateway this error appear.
I have restarted the CODESYS IDE, the Gateway, uninstall and download again the Edge Gateway program, but this problem persist. What can i do?
Also mark I have installed the version 1.12.0.0 of the CODESYS Automation Server Connector and the CODESYS IDE V3.5 SP16 Patch 2
Hi,
check the location of the Gateway.cfg it should be under:
c:\ProgramData\CODESYS\CODESYSGatewayV3\randomnumber\
Check if the Gateway is really in version 3.5.16.20 by versioninfo in the tasktray
Check if you have readwrite access in:
c:\ProgramData\CODESYS\CODESYSGatewayV3\randomnumber\
Which plc do you want to connect?
Sometimes it makes more sense to activate/install the EdgeGateway on plc side ( in case it is a runtime from store this is easily possible...)
BR
Edwin
Last edit: eschwellinger 2020-09-28