Post by pernockham on Gateway in China - "Gateway not connected"
CODESYS Forge
talk
(Post)
Trying to communicate (from Europe) with/to a unit located in china, the communication seems blocked/stopped. The edge gateway is installed in a linux environment and was possible to link to my Automation server account using the "Automation service tool". However it seems the unit cannot communicate with the Automation server (a Network scan will give the message "Gateway not connected"). (I have tested the eq. setup with units locally which works.) Anyone having experience situation similar to this and if its possible to make this work? Will a VPN be needed possibly? Other tips?
Last updated: 2025-09-04
Post by reinholdgaylord on CAA File Handling: "Read only" error
CODESYS Forge
talk
(Post)
Hi, sorry for the late reply. After some investigation, the read-only error was being triggered by a FAT-fs filesystem panic on the kernel end, probably caused by unfinished write/reads causing corruption. I found this thread https://forge.codesys.com/forge/talk/Engineering/thread/e637d252b7/geometry dash lite which seems to give a solution of using SysProcess to send the 'sync' command to the console immediately following a write to prevent issues if power is lost or, in my case, if the unit is harshly power cycled. Indeed this seems to resolve the issue bar the worst possible edge cases. Thank you so much!
Last updated: 2025-09-25
Post by ranadheer on Implementation of IEC-104
CODESYS Forge
talk
(Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14
Post by ranadheer on Implementation IEC-104
CODESYS Forge
talk
(Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14
Post by ton on How to create a stopwatch?
CODESYS Forge
talk
(Post)
One i wrote this to measure elepse time When xMeasure is true is starts en when false it stops and time is messured. FUNCTION_BLOCK FB_ElapseTime VAR_INPUT xMeasure: BOOL; END_VAR VAR_OUTPUT xRisingEdge: BOOL; xFallingEdge: BOOL; tElapsed: TIME; ltElapsed: LTIME; ltPrev_Elapsed: LTIME; ltElapsedMax: LTIME; END_VAR VAR xLastValue: BOOL; LTIMEStart: LTIME; LTIMEEnd: LTIME; tonReset: TON:= (IN:= TRUE, PT:= TIME#30S0MS); END_VAR ------------------------------------------- xRisingEdge:= (xLastValue XOR xMeasure) AND xMeasure; xFallingEdge:= (xLastValue XOR xMeasure) AND NOT xMeasure; IF xRisingEdge THEN ltPrev_Elapsed:= ltElapsed; LTIMEStart:= LTIME(); END_IF IF xMeasure OR xFallingEdge THEN LTIMEEnd:= LTIME(); END_IF ltElapsed:= LTIMEEnd - LTIMEStart; ltElapsedMax:= MAX(ltElapsedMax, ltElapsed); tElapsed:= LTIME_TO_TIME(ltElapsed); xLastValue:= xMeasure; tonReset(); IF tonReset.Q THEN tonReset.IN:= FALSE; ltElapsedMax:= LTIME#0NS; END_IF Meaby this will help.
Last updated: 2023-12-09
Post by snhatton on OpC UA server on Raspberry Pi 64 SL runtime
CODESYS Forge
talk
(Post)
Good afternoon, After changing the security settings to: CommunicationPolicy: POLICY_BASICSHA256SHA256 CommunicationMode: ALL Activation: Activated UserAuthentication: ENABLED Then generate a new certificate on the device for the OPC-UA server from Security Agent->Device->OPC UA Server. Restart the runtime using tools->Update Raspberry Pi->Stop->Start for the changes to take effect. It may take a minute for the runtime to start. Initiate the connection from the UA server side. You should see a pop-up asking you to trust the certificate. Click on the button 'Trust Server Certificate'. Next, you should see a certificate in the quarantined folder of the security agent in CODESYS. Click and drag this from quarantined to trusted and then try connecting from UA expert to the device. These steps worked for me and my setup and I hope they can help you!
Last updated: 2023-12-11
Post by manuknecht on Using SMC_MOVTYP.INITPOS without specifying the start position
CODESYS Forge
talk
(Post)
I am using the object SMC_GEOINFO to generate a trajectory and move a system accordingly using the SMC_INTERPOLATOR function block similar to the sample project CNC10_DynamicPath.project. According to the documentation, the movement type INITPOS does not require a start position in the SMC_GEOINFO object, which is confirmed in the documentation of the SMC_GEOINFO object. When using the movement type INITPOS however, the motion will still start from the starting point defined in the SMC_GEOINFO object (0,0,0 if not specified otherwise). Does someone know how to resolve this or is there an example project that makes use of the INITPOS movement type without specifying the starting point? Thanks in advance!
Last updated: 2023-12-15
Post by preimesbergert on Raspberry Pi 4 B HW 1.5 Codesys control 4.10.0 stopps after a few seconds
CODESYS Forge
talk
(Post)
Wanted to play a bit with a raspberry Pi 4 Model B HW 1.5 and Codesys. Regardless of the image (tried 32bit / 64bit version from Raspberry Pi Imager) and with all tested Codesys Control versions (4.2.0, 4.8.0, 4.10.0) and regardless if single core / multicore / 64 bit variant, always is the runtime stopped after about 30sec with the nice message: ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-7, 0x00000BB8, 0xFFFFFFFB) Whats wrong with it?!?!? I read a lot about the issue in topics from 2020-2021 but it always was stated with new Codesys control version issue will be fixed (4.4 for example) but still it is there.
Last updated: 2023-12-21
Post by preimesbergert on Raspberry Pi 4 B HW 1.5 Codesys control 4.10.0 stopps after a few seconds
CODESYS Forge
talk
(Post)
Wanted to play a bit with a raspberry Pi 4 Model B HW 1.5 and Codesys. Regardless of the image (tried 32bit / 64bit version from Raspberry Pi Imager) and with all tested Codesys Control versions (4.2.0, 4.8.0, 4.10.0) and regardless if single core / multicore / 64 bit variant, always is the runtime stopped after about 30sec with the nice message: ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-7, 0x00000BB8, 0xFFFFFFFB) Whats wrong with it?!?!? I read a lot about the issue in topics from 2020-2021 but it always was stated with new Codesys control version issue will be fixed (4.4 for example) but still it is there.
Last updated: 2023-12-21
Post by toby on Ethercat Servo Setup
CODESYS Forge
talk
(Post)
Hi everyone, so a little update to this, I've come back to this project in the new year, and got it working. Yeah!, However, now with the new licensing setup, I need a new SoftMotion license, but it doesn't seem to be compatible with the previous Raspberry Pi SL license. Has anyone had any luck with Raspberry Pi and SoftMotion_Lite? Specifically the licensing of such? My customers new installation needs to be rebooted every 30min which is causing headaches! Another option is to not use the SoftMotion function blocks, and control the EtherCat amplifier directly, but I'm not sure how to do so. Does anyone have a specific example project of how to control a servo without the use of the SoftMotion function blocks? Thanks everyone for any assistance rendered. It's very much appreciated! Toby
Last updated: 2024-01-10
Post by cedriclee on RaspberryPI reconnection error
CODESYS Forge
talk
(Post)
"Hello, I'm Cedric Lee, a PLC engineer based in Korea. I'm reaching out about an ongoing issue with the connection when attempting to control Beckhoff modules using Raspberry Pi with CODESYS for the first time. I use CODESYS to target the Raspberry Pi's IP, install version 4.10.0.0 of the CODESYS Runtime Package, and upon pressing Start in the Runtime, the target connects to the Raspberry Pi. However, within about a minute, an error window appears, stating 'no connection to the device. please rescan your network,' leading to the disconnection of the target. This cycle repeats. I've attached some pictures for your reference. I'm using CODESYS Development System V3, Raspberry Pi 4 Model B (installed as 64-bit), and Beckhoff EK1100 modules. If anyone has a solution to this issue, please help. Your assistance is greatly appreciated."
Last updated: 2024-01-11
Post by davidbo on Does the new license policy means I have to upgrade everything?
CODESYS Forge
talk
(Post)
We have several old project written with 3.5.17 and 3.5.18 and also some older Until now when a customer ordered a product from us. We just installed (we have a tested image) and added a license Now the license policy has changed and we have to buy a License Control Basic S or M However it only works with CODESYS Development System Version 3.5.19.10 or higher Does that mean we have to upgrade all our old products? That is not a simple task as a previous post has explained with weird error messages from CODESYS V3.5. Next we have to do rigorous testing of our applications afterwards. It is very expensive
Last updated: 2024-01-11
Post by yang123 on EtherCAT Can't reconnect to servo drive
CODESYS Forge
talk
(Post)
I am using Ethercat Master 4.6.0.0 and have use the automatic restart slaves feature. But we found of after the Ethercat communication normal and slave drive power-off and power-on the slave can't reconnect sucess. The PLC Log show the drive was al status "6#34 : Invalid DC Timeout Error" and its was reconnection sucess first but seconced later the drive will show the "16#2C : Fatal Sync error" and then drive will can't reconnection. Other slave are reconnect sucess which was link after the can't reconnect's drive the drive was OMRON R88D-1SN
Last updated: 2024-01-23
Post by dhumphries on No source code available
CODESYS Forge
talk
(Post)
Try using an Ethernet/IP scanner instead of an adapter, I'm guessing the 2 devices you're trying to communicate with are adapters, you have to have a scanner somewhere and Codesys should be a scanner. I don't know why you're getting the error, you should be able to use your Ethernet port as an EthernetIP adapter (although I've never had a reason to try,) but it's probably not what you wanted to do, unless you're connecting to another PLC that is a scanner. Good luck configuring the devices you're trying to connect to, it will be a lot easier if you have an .EDS file instead of starting with a generic module, even with an .EDS it can be tricky getting the communication working.
Last updated: 2024-02-03
Post by alexgooi on Function Blocks and arrays of function blocks
CODESYS Forge
talk
(Post)
Hi Jack, I think you have to look at a FB in a different way. A Function block (Class) can contain its own data. In other words don't define loose data in your GVL, but define a instance of a FB (Object) in your GVL: Example: Function_Block Basic_Class VAR_INPUT Open_Command: BOOL; END_VAR VAR_OUTPUT Opened: BOOL; END_VAR if Open_Command then Opened := TRUE; ELSE Opened := FALSE; END_IF Global Variables Objects: ARRAY[1..100] OF Basic_Class; //Here you ar defining you objects END_VAR In your code you can directly acces the data and couple it to the IO: GVL.Objects[1].Open_Command := %IX0.0; %QX0.0 := GVL.Objects[1].Opened; //To call the code itself use: GVL.Objects[1](); If you want to take this a step further you are also able to add methods and properties to the FB/Class end thereby creating a OOIP program
Last updated: 2024-02-15
Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28
Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28
Post by fless on Warning C0564 when compiling CNC project with variables program
CODESYS Forge
talk
(Post)
Hello, we are porting a CNC project from codesys 3.5.16 to codesys 3.5.19. The project has lots of CNC programs with variables. now we get hundreds of messages like this. [WARNING] CNC Test SP19: TestCNC SPS: PLC Logic: Application: C0564: A reference to uninitialized variable varCNC is used for initialization of TestCNC_D. Accessing the uninitialized variable may result in unexpected behavior. The objects program_name_D are implicit generated by codesys. I see no way to generated them after the variables. Is there a way to correct the initialization order? We know how to suppress this warning. But we need a clean solution as the warning already saved us in a other nonCNC project. Attached a small demo of the problem.
Last updated: 2024-03-21
Post by fless on Warning C0564 when compiling CNC project with variables program
CODESYS Forge
talk
(Post)
Update: We managed to avoid the warnings by changing the order of initialization by adding an attribute to the GVL with the variables. {attribute 'global_init_slot' := '49989'} The variables are initialized right before the regular GVLs (default GVL slot 49990). Note to Codesys: I see the problem, Codesys needs to initialize the CNC objects before the GVLs so they can be used in the GVL. But then you can't use variables from GVLs in CNC programs. Maybe you could disable the warning in your generated CNC objects? At least a note for a workaround would have been nice.
Last updated: 2024-04-02
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
The way I usally tackle this is by syncing only words (then you are able to use the FB above). If you then want to write a Boolean simply type it like this. Value[1].0 := Bool1; Value[1].1 := Bool2; Value[1].2 := Bool3; Uints have the same number of bits than a INT/WORD so these ones will work as well (they are only represented diffrently). A Real will work but you will loose some infomration in the conversion. If you want to keep the information you can convert 2 words to a float with a function (for example with the IEEE-754 standard) . In this way the syncing to the server is very simple and in the Codesys Program you decide what part of the word you want to use.
Last updated: 2024-04-03
Post by tecnocons on Trouble Writing Files to External Paths in CODESYS
CODESYS Forge
talk
(Post)
Hello everyone, I'm encountering an issue in CODESYS regarding writing files to external paths. Despite correctly configuring the placeholder in the CODESYSControl_User.cfg file to allow access to an external folder, CODESYS doesn't seem to write any files, and no errors are reported. The issue on the older versions was absent with no placeholders. I've checked the operating system permissions, and they seem to be in order, but the issue remains. Has anyone faced a similar situation or has any suggestions on how I might resolve this problem? Any help would be greatly appreciated. Thank you in advance for your support. I'm using raspberry PI as a logger. RPI3 Buster Codesys 32bit SL V4.11 Codesys Win64 3.5.20 [SysFile] PlaceholderFilePath.1=/home/pi/scan, $SCAN$
Last updated: 2024-04-09
Post by vernon-laurence on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
The simplest way to do this would be to add a bus coupler dedicated to the expansion IO. The EtherCAT network does not fault when modules connected to the expander are not present. In the image below, nothing below the red line is present in the network - with the network working correctly. In your "base" project, simply include all of the possible modules, and then plug them in as you add pumps to the system. I would also highly recommend against the use of direct addressing. There are other methods to accomplish this, including using the "Optional" checkbox for modules and explicitly addressing them. Although, this would require more upfront work to design the network, and some additional work each time modules were added. https://content.helpme-codesys.com/en/CODESYS%20EtherCAT/_ecat_edt_slave_slave.html
Last updated: 2024-04-09
Post by sachem on Problem retain values Weidmuller UC20-WL2000
CODESYS Forge
talk
(Post)
Good afternoon. I am working with a weidmuller uc20-wl2000 controller, using a codesys license. We made a ladder code to control a process, and it works well, but we want some variables to remain stored even when the controller is turned off. We tried to use retain variables, but at the time of loading the program, when we went offline from the controller, the program was deleted, it did not remain in the controller, and in the same way if we turned off the controller. In addition to this, when we tried to program it again, the program would not stay loaded and began to present errors with the opc-ua communication. What could be causing this problem? How can we maintain the values of the variables without damaging the program or affecting the controller? thank you
Last updated: 2024-04-10
Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20
CODESYS Forge
talk
(Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20
Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20
CODESYS Forge
talk
(Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20