Search talk: system

 
<< < 1 .. 12 13 14 15 > >> (Page 14 of 15)

Post by trusty-squire on Strange problem with the ‘MC_SetPosition’ function CODESYS Forge talk (Post)
Here, it seems to me that we are getting completely off track with the observed problem. If questions clarifying the details of the installation are problematic, it's best to include those details in the original question then... I had already written this elsewhere. The program before being brought into machines was exhaustively tested in SW emulation and the problem did not occur. Testing the full program in emulation is entirely different from creating a simplified program to isolate the function causing problems in the real world. I would recommend trying it to isolate the issue. The drive and motor have been working fine for about 10 years. In replacing the machine control system, I opted for CoDeSys where before there was something else. But this is not the subject of the problem A simple "yes" is the correct answer to my question here... Anyways, you seem to be a very knowledgeable expert, good luck on your problem!
Last updated: 2025-01-18

Post by george32 on TCP Server CODESYS Forge talk (Post)
Thank you for your advice Rinie, I have tried to follow this example but found one problem.When I disconnect with Hercules the system does not acknowledge the lost of its connection this could result in critical errors. Because of this error I am trying to implement the Syssocket library. With this library I am having a problem which I could not solve. I have the following code: ip_adres : STRING :='0.0.0.0'; port : WORD := 5000; iStep : INT := 1; // Socket information Socket_handler : SysSocket_Interfaces.RTS_IEC_HANDLE; Socket_handler_result : SysSocket_Interfaces.RTS_IEC_RESULT; Socket_adress : SysSocket_Interfaces.SOCKADDRESS; Addres_Convert : SysSocket_Implementation.RTS_IEC_RESULT; // Bind information Bind_handler : SysSocket_Interfaces.RTS_IEC_RESULT; // Listener Information Listener_handler : SysSocket_Interfaces.RTS_IEC_RESULT; Addres_Convert := SysSocket_Implementation.SysSockInetAddr(szIPAddress:= ip_adres,pInAddr:= ADR(Socket_adress.sin_addr)); Socket_adress.sin_family:= SysSocket_Interfaces.SOCKET_AF_INET; Socket_adress.sin_port := SysSocket_Implementation.SysSockHtons(usHost:= port); CASE iStep OF 1: // Create Socket Socket_handler :=SysSockCreate( iAddressFamily :=SysSocket_Interfaces.SOCKET_AF_INET, diType:=SysSocket_Interfaces.SOCKET_STREAM, diProtocol:=SysSocket_Interfaces.SOCKET_IPPROTO_TCP, pResult:=ADR(Socket_handler_result)); IF Socket_handler = SysSocket_Interfaces.RTS_INVALID_HANDLE THEN iStep := 1; ELSE iStep := 2; END_IF 2: Bind_handler := SysSocket_Implementation.SysSockBind( hSocket:=Socket_handler, pSockAddr :=ADR(Socket_adress), diSockAddrSize:=SIZEOF(Socket_adress) ); 3: Listener_handler := SysSocket_Implementation.SysSockListen( hSocket :=Socket_handler, diMaxConnections :=1); END_CASE When I am trying to get this working, the SysSockBind function gives a value of 16#207 which means adress already in use. I find this weird because of the IP-adress of 0.0.0.0. I think I am converting the Ip-adress in the wrong way, but the code does not give a error arround this. So therefore I cannot find the solution to this problem. I hope someone could help me with this problem. Thanks in advance George
Last updated: 2025-02-20

Post by pernockham on Inheritence of struct, CODESYS Forge talk (Post)
Im looking for a way to define predefined version of the same structures through "extends"/inheritance. What I want to do is best shown with an example: TYPE log_item_val_type : ( BOOL_ := 0, INT_, REAL_, STRING_ ); END_TYPE TYPE LOG_DATA_BASE STRUCT val_type : log_item_val_type; (* value, name etc *) ENDSTRUCT ENDTYPE (* this/below is not possible as I understand from the compiler?? *) TYPE LOG_DATA_BOOL extends LOG_DATA_BASE : STRUCT val_type : log_item_val_type := log_item_val_type.BOOL_; END_STRUCT END_TYPE TYPE LOG_DATA_INT extends LOG_DATA_BASE : STRUCT val_type : log_item_val_type := log_item_val_type.INT_; END_STRUCT END_TYPE etc. for LOG_DATA_REAL and ..STRING. The system will not allow me to "re-define" "val_type" however. Instead I must do the work-around of defining four different types with all fields individually defined. The benefit if I could extend the base item would be that Im (more) sure the structures are identical. In usage I can call in a specific type rather use the base type and assign which type. Usage by pointer/ref to log_data_base would also be easier.. (* Usage: *) log_data : log_data_int := (name, value etc.) (* Instead of: *) log_data : log_data_base := (name, value, val_type).. Is this possible to achieve in some way that I have missed?
Last updated: 2025-03-05

Post by struccc on The future and proper use of CAA.BOLT, CAA.SEMA,.. CODESYS Forge talk (Post)
Dear All, Dear CODESYS, I'm curiously following CODESYS transitioning away from the CAA libraries, and I'm mostly in favor of these major changes. Naturally, I'd like to align my current (not end-user) developments accordingly. I'm tracking , reading release notes, ... And want to figure out the future :) Is it possible to hear / read more about the reasons, objectives and scope of these changes? One important element is CAA Types - CAA Types Extern. What is the plan with that? What's the future of CAA.SEMA, CAA.BOLT ? I have never used them (always relied on SysLib*), but they are tempting... Would be useful to have a platform independent "Macro" for this functionality... Is there something in existing or planned ? Are they suitable to be used in low level libraries... For Example IO-Drivers, Components, "to-become system libraries"? CAA.TaskLock, CAA.TaskUnlock ? Well, they don't claim platform independency, so I can't rely on those.... Any up-to-date advise, standard, pattern to follow in new libraries for task and resource locking? Practical set of conditional defines to be used? If this information is not publicly available, can you please send a private message about the proper way to achieve this? I have support agreement, just couldn't get trough with these questions... P.
Last updated: 2025-03-14

Post by drbuzz on Communication Error (#0) for IFM controller CODESYS Forge talk (Post)
Hi Folks, Every time I use an IFM controller I always seem to run into a problem connecting to it. I get the Communications Error (#0). So I thought I would share some tips and tricks. Once the CANfox Cable (EC2112) cable driver is installed, you can use the yellow app in the sys tray to blink the lights on the cable. Confirm the cable works in the IFM maintenance software by connecting to the controller and reading the information on it. Make sure to download an OS into the controller (the light will go from a fast blink to solid green). In Codesys V2.3, the communication settings for the CR0401 is 250kBaud by default and Node ID 127. What got me, was I needed to reboot the computer after the cable driver install. Also if your application has canbus settings in it which are changed from default, after the controller is power cycled, the new Node ID and Baud will be in effect. I made a handy guide because too much time has been wasted on this. Programming IFM CR0401 Serial/Can Programming Cable • Connect IFM EC2112 CanFox programming cable with connector adapter. • Make sure cable is linked to VM (if using VM). • Install drivers for cable if not installed. o Download from IFM EC2112 site. https://www.ifm.com/ca/en/product/EC2112 • Once Installed, reboot computer. • In system tray, there should be a yellow icon that you can open and check on programming cable. Select the cable in the list and flash the lights to confirm it is working. Maintenance Software • Install IFM Maintenance Tool Software. o Download from IFM Site. https://www.ifm.com/ca/en/download/eco100_MaintenanceTool • Open IFM Maintenance software • Select Basic System • Select CAN cable • It will tell you if you don’t have a cable connected. • Use Wizard if needed. • Read Channel Parameter on the Settings page, or get Identity in the System Information > Identity. • Default Node is 127 on a new unit. Baud is 250kBaud (bits/sec) • Controller information should populate. • Controller green light should be blinking at 5hz (meaning OK but no OS, just bootloader). • Click Software > Load. • Open the OS file. Should match Codesys version selection (for CR0401 this is version 3). o Download OS file from IFM Website. https://www.ifm.com/ca/en/product/CR0401 o It is located at the top of the download under “software for CR0401”. o Select the file and load it… this will take a minute. • Once completed the unit should now have a solid green light o Solid green means the controller has an OS but no application is running. Codesys V2.3 Application • Codesys needs to be downloaded and installed from the IFM website as it has the IFM libraries and license to use the software. o Download from the IFM CR0401 page. o https://www.ifm.com/ca/en/product/CR0401 • Create new application with the correct IFM controller or Open Codesys application. • Keep in mind that the PLC Configuration on the Resources tab can be changed for the CAN communication interface… so changes to node and baud will take effect after the first download and reboot of the controller. • Go to “Online” in the top menu and change “Communication Parameters” o The Local dropdown shows the last configuration used. All other interfaces will show below it and need to be updated when changed or used. o Confirm Node ID is 127 for the first download.  The NodeID will change to whatever the program has after (in my case 125).  Node Send Offset should be default at 1536  Node Recv Offset should be default at 1408  Can bus Baudrate should be 250 kbaud.  Yes to Motorola Byte Order  Block Transfer should be false and note used (60 is default setting).  Can Card Driver should match the systray item which is Sie_USB. • If the system populated the other one, just update and relay the communication parameters. The software will usually bring up the available cable and driver. • Go to “Online” and Login to download. o Press Yes to Download Application. I hope this helps!
Last updated: 2025-03-21

Post by canplum on Codesys 3.5.21 fails to copy file to USB CODESYS Forge talk (Post)
Although I have set in /etc/codesyscontrol/CODESYSControl_User.cfg the [SysFile] PlaceholderFilePath.1=/media/pi, $usb$ PlaceholderFilePath.1.View=1 PlaceholderFilePath.1.Volatile=1 I am not able to copy a file to this directory defined by the placeholder. Neither SysProcess.SysProcessExecuteCommand2 nor SysFileCopy nor FileCopy is working. If I try to copy the same file to /home/pi all is working fine. I also can create and open a different file by using SysFileOpen. I don't understand why the system allows to open (create) and write files into that directory but doesn't allow to copy into it. Obviously there is a rights problem with the USB drive. I have already set the permissions to drwxr-xr-x 2 and the user to pi but without any success. With 3.5.16 I never had such an issue. Is there anybody with some hints how to solve that problem? Cheers, canplum
Last updated: 2025-05-23

Post by canplum on Codesys 3.5.21 kann Datei nicht auf USB kopieren CODESYS Forge talk (Post)
Obwohl ich in der Datei /etc/codesyscontrol/CODESYSControl_User.cfg eingestellt habe die [SysFile] PlatzhalterDateipfad.1=/media/pi, $usb$ PlatzhalterDateipfad.1.Ansicht=1 PlatzhalterDateipfad.1.Flüchtig=1 Ich bin nicht in der Lage, eine Datei in dieses durch den Platzhalter definierte Verzeichnis zu kopieren. Weder SysProcess.SysProcessExecuteCommand2 noch SysFileCopy oder FileCopy funktionieren. Wenn ich versuche, die gleiche Datei nach /home/pi zu kopieren, funktioniert alles einwandfrei. Ich kann auch eine andere Datei mit SysFileOpen erstellen und öffnen. Ich verstehe nicht, warum das System das Öffnen (Erstellen) und Schreiben von Dateien in dieses Verzeichnis erlaubt, aber das Kopieren in dieses Verzeichnis nicht zulässt. Offensichtlich gibt es ein Rechteproblem mit dem USB-Laufwerk. Ich habe bereits die Berechtigungen auf drwxr-xr-x 2 und den Benutzer auf pi gesetzt, aber ohne Erfolg. Mit 3.5.16 hatte ich nie ein solches Problem. Hat jemand einen Tipp, wie man dieses Problem lösen kann? Vielen Dank! canplum
Last updated: 2025-05-23

Post by struccc on Wish: CODESYSControl.cfg - again CODESYS Forge talk (Post)
Before creating this topic, I was browsing the search results for CodesysControl.cfg - many results, and I remember very well, it's a problematic issue for a long time. To summarize: there were many requests for documentation on this file - the most comprehensive reply is: https://forge.codesys.com/forge/talk/Runtime/thread/ebbf851a3d/#eb85 Hi, not really, this is covered by the manual which you get if you use a runtime toolkit which is not free of charge. Maybe we need to extract the config file part from that documentation if that is possible. BR Edwin I am not sure how much is this relevant, since we buy SL License directly from CODESYS... I think it is a reasonable demand, to get documentation on the configuration entries affecting the documented behaviour of the runtime system and it's components The actual reason I bring up this issue again can be read here: https://forge.codesys.com/forge/talk/Runtime/thread/febad3cc40/#0e12 but mostly my frustration about noticing some new, unknown and undocumented entries in my configuration file. Again. And this happens a lot recently. Just some examples: Changes with SysFile - and mandatory use of IEC path Introduction of Mandatory user management File transfer service now disabled by default SysProcess - allowed commands The above mentioned CmpApp parameters... And finally (Regaridng windows install): With the newer versions, the installation directory (together with the configuration file) tends to hide itself to some super silly location under the roaming profile data of local system account. I am not sure if this change was documented somewhere, but was a very unpleasant one. Someone could please explain the reason and the concept of the introduction of this release specific directories (I am sure, there is a good reason) - how to use them properly? - How to re-introduce user configuration (to preserve configuration data between versions)? - How to do version - to version migrations properly? - How to keep old version of runtime available and ready to start with it's original configuration and application? - ... Therefore, the lack a regularly updated description of CodesysControl .cfg , including all the configuration entries, together with their default values for different runtime versions is really a big deficiency.* This should be done for all components storing or just seeking data from this file... (Maybe there is such thing but I failed to find???) It is regularly causing trouble when introducing a new version (together with the long awaited bug fixes and enhancements), what has changed it's default behaviour for security or other practical reasons. I agree this is very important, and it is logical to change the default options: But it must be documented historically, and make it easily available, so we can prepare better for the upgrade of the runtime. Forge talk is a great source, but not very practical for this kind of documentation purposes... Thanks in advance for CODESYS staff 🙏🙏🙏 (Ps.: It would look rather silly, if some members of the user community prepares this documentation on a Forge Wiki page... Or??? Should we?)
Last updated: 2024-11-21

Post by jst69 on Python script: Launch Codesys, Execute Script, Exit Codesys CODESYS Forge talk (Post)
Dear all: Question about scripting: I am creating a .NET program that is supposed to Open codesys, open template project, export a bunch of pou, then exit codesys. Launch works, Open project works, Export works, But how do i tell codesys to close itself? I can tell windows to terminate codesys, but i would prefer to do it properly. from __future__ import print_function import sys import System proj = projects.primary # We're interested in POU nodes: POUGuid = Guid("6f9dac99-8de1-4efc-8465-68ac443b7d08") # We collect all POU nodes in that list. pous = [] # From the parent node on, we recursively add POU nodes: def CollectPous(node): if node.type == POUGuid: pous.append(node) else: for child in node.get_children(): CollectPous(child) # Now we collect all the leaf nodes. for node in proj.get_children(): CollectPous(node) # We print everything just to know what's going on. for i in pous: print("found: ", i.type, i.guid, i.get_name()) # And now we export the files. for candidate in pous: # We create a list of objects to export: # The object itsself objects = [candidate] # And sub-objects (POUs can have actions, properties, ...) objects.extend(candidate.get_children()) # And the parent folders. parent = candidate.parent while ((not parent.is_root) and parent.is_folder): objects.append(parent) parent = parent.parent # Create an unique file name: if len(sys.argv) == 1: filename = "parent\\%s.export" % (candidate.get_name()) else: filename = "%s\\%s.export" % (sys.argv[1],candidate.get_name()) # print some user information print("exporting ", len(objects), " objects to: ", filename) # and actually export the project. proj.export_xml(objects, filename) proj.close() print ("script finished.") System.exit(0) // Dont work .NET: public static void Export(string path,string proj) { if (checkSettings()) { var p = new System.Diagnostics.Process(); p.StartInfo.FileName = Properties.Settings.Default.CSVersion +"\\CODESYS\\Common\\CODESYS.exe"; p.StartInfo.Arguments = " --Profile=" + qoute(Properties.Settings.Default.CSProfile) + " --culture=en" + " --project=" + qoute(path + "\\" + proj) + " --runscript=" + Properties.Settings.Default.LastOpenProjectPath + "\\INPUT_DATA\\SCRIPT\\Export.py" + " --scriptargs:" + qoute(path) ; p.StartInfo.RedirectStandardOutput = true; p.StartInfo.UseShellExecute = false; p.StartInfo.CreateNoWindow = false; p.Start(); p.StandardOutput.ReadToEnd(); p.CloseMainWindow(); p.Close(); } }
Last updated: 2024-01-16

Post by gallusrrr on usb2can in Codeysy 3.5 Can Gateway CODESYS Forge talk (Post)
Hallo und guten Morgen, Ich danke für die Rückmeldung. ich habe das oben geschriebene durchgeführt und auch festgestellt das mit die Commandos für die Can befehle noch fehlen. (Google angeschmissen und geschaut auch gefunden) sudo apt-get install can-utils (damit auch jemanden anders der Post hilft) Anschließend habe ich das CAN System komplett aufgebaut so das ich mit einen anderen CAN Adapter schauen konnte ob die Nachricht auch ankommt. die Nachricht kommt an :) danach habe ich follgende Ausgabe: pi@Codesys:~ $ sudo ip -s -d link show can0 3: can0: <noarp,up,lower_up,echo> mtu 16 qdisc pfifo_fast state UP mode DEFAULT group default qlen 10 link/can promiscuity 0 allmulti 0 minmtu 0 maxmtu 0 can state ERROR-ACTIVE restart-ms 0 bitrate 250000 sample-point 0.875 tq 250 prop-seg 6 phase-seg1 7 phase-seg2 2 sjw 1 brp 12 gs_usb: tseg1 1..16 tseg2 1..8 sjw 1..4 brp 1..1024 brp_inc 1 clock 48000000 re-started bus-errors arbit-lost error-warn error-pass bus-off 0 0 0 0 0 0 numtxqueues 1 numrxqueues 1 gso_max_size 65536 gso_max_segs 65535 tso_max_size 65536 tso_max_segs 65535 gro_max_size 65536 parentbus usb parentdev 1-1.4:1.0 RX: bytes packets errors dropped missed mcast 3549 819 0 0 0 0 TX: bytes packets errors dropped carrier collsns 32 4 0 0 0 0</noarp,up,lower_up,echo> (Sorry habe kein Speicherplatz im Web um Bilder anzuzeigen..) man kan sehen das die Nachricht abgeht und auch 32 Byte Empfangen worden sind. Die nachricht ist auch am anderen CAN Adapter sichtbar gewesen. Wie bekomem ich den einrichteten Adapter in Codesys rein? das ich den Befehl sudo ip link set can0 up type can bitrate 500000 das ich die Einrichtungs des Can Adapters noch in die Rasperry Start rutine nehmen muss ist mir klar. Ich bedanke mich .
Last updated: 2024-01-18

Post by testlogic on Sending Sequential Modbus TCP Packets CODESYS Forge talk (Post)
I have a Modbus TCP slave device where I need to do sequential writes to the same register. The register I'm writing to is kind of like a command line, each packet is a command word encoded in Hexadecimal. I am having difficulty implementing this system in CoDeSys 3.5 SP19. I feel like the structure of the program should be something along the lines of (Pseudocode): ModbusTCPSend(Command Register, Command1) ModbusTCPSend(Command Register, Command2) ModbusTCPSend(Command Register, Command3) I have tried to implement this with a rising edge trigger wMot1OPCode := 16#E1; //Stop Motor & Kill Program xMot1SendOP := TRUE; //Send OP on rising edge xMot1SendOP := FALSE; //Reset wMot1OPCode := 16#9E; //Disable Motor xMot1SendOP :=TRUE; //Send OP on rising edge xMot1SendOP := FALSE; //Reset Where "wMot1OPCode" is the IO map for writing to the command register, and "xMot1SendOP" is the rising edge trigger for that modbus channel. However, this doesn't work. The device never responds to the modbus commands. It seems like the trigger variable is switched too quickly for modbus to send the packet. I know the modbus register is working, because I can set the channel to cyclic and the device will respond. However, I can't use this reliably because I need each command to be sent once, in order. Cyclic keeps re-sending the commands and seems like it could miss a command as well if one was sent in-between cycle time. I have also trying using the Application trigger as described by https://faq.codesys.com/pages/viewpage.action?pageId=24510480, but this is also not working for me. See attached picture for my FBD code. This seems like a simple function, I can't tell what I'm doing wrong here. Thanks for the help.
Last updated: 2024-03-06

Post by superjojo2002 on Licensing info not available. CODESYS Forge talk (Post)
I updated the docker container runtime to version 4.11.0.0. and build the container with this "Dockerfile" FROM arm64v8/debian:11.6 RUN apt-get update RUN apt-get install -y wget sudo unzip libusb-1.0-0-dev procps ENV CDS_VERSION "4.11.0.0" ENV EDGE_VERSION "4.11.0.0" ENV URL "https://store-archive.codesys.com/ftp_download/3S/LinuxARM64/2302000039/$CDS_VERSION/CODESYS%20Control%20for%20Linux%20ARM64%20SL%20$CDS_VERSION.package" ENV EDGE_URL "https://store-archive.codesys.com/ftp_download/3S/EdgeGatewayLinux/000120/$EDGE_VERSION/CODESYS%20Edge%20Gateway%20for%20Linux%20$EDGE_VERSION.package" RUN wget --output-document=/tmp/codesys.package $URL && \ unzip -p /tmp/codesys.package '*codemeter*.deb' > /tmp/codemeter.deb && dpkg -i /tmp/codemeter.deb && \ unzip -p /tmp/codesys.package '*codesyscontrol*.deb' > /tmp/codesys.deb && dpkg -i /tmp/codesys.deb RUN wget --output-document=/tmp/edge.package $EDGE_URL && \ unzip -p /tmp/edge.package '*arm64.deb' > /tmp/edge.deb && dpkg -i /tmp/edge.deb EXPOSE 11740 1217 11743 ENTRYPOINT ["/bin/sh", "-c" , "/etc/init.d/codemeter start && /etc/init.d/codemeter-webadmin start && /etc/init.d/codesyscontrol start && /etc/init.d/codesysedge start && tail -f /dev/null"] Now cmu -x" returns root@sensoredge-field-netfield-produktmanagment:/# cmu -x cmu - CodeMeter Universal Support Tool. Version 8.00 of 2023-Nov-28 (Build 5967) for Linux/ARMHF 64-Bit Copyright (C) 2007-2023 by WIBU-SYSTEMS AG. All rights reserved. But still CODESYS development system reports that it needs a dongle and when I click install that "value cannot be null. Parameter name: containerToLicenses" It seems that Codemeter is forced to look for a dongle instead of a CMsoftcontainer. Can you confirm that CODESYS licensing works also when CODESYS is installed in a Docker container?
Last updated: 2024-03-21

Post by leandroct on Error reading files after runtime update from 4.0.0.0 to 4.8.0.0 CODESYS Forge talk (Post)
Since version 19 they changed how file access is handle. There are two solutions: 1. You change where the file is stored (need to go to: /PlcLogic/) 2. You can, if you don´t want to store at PlcLogic, add the following line in the CODESYSControl.cfg under [SysFile]: ForceIecFilePath=0 The CodesysControl.cfg is at C:\ProgramData\CODESYS\CODESYSControlWinV3x64\xxPROJECT_NUMBERxx\ Here the email they sent me: "with the 3.5.19 Version we changed how files are handled. See following issue: CDS-81506 - CODESYS Control SysFile system file access vulnerability. There are two solutions: 1. You change where the file is stored (need to go to: /PlcLogic/) 2. You can, if you don´t want to store at PlcLogic, add the following line in the CODESYSControl.cfg under [SysFile]: ForceIecFilePath=0 Here is the official release-note: [[COMPATIBILITY_INFORMATION]] With the activation of ForceIecFilePath the file access from IEC is now restricted to the configured paths only (file sandbox)! [SysFile] ForceIecFilePath=1 (new default) The standard path is the current directory, the PlcLogic subfolder or a configured path. Every file access outside of this path is configured via PlaceholderFilePath, for example access to temporary files or removable media: [SysFile] PlaceholderFilePath.1=/tmp, $TMP$ PlaceholderFilePath.2=/media/usb, $USB$ PlaceholderFilePath.2.Volatile=1 For more information see our tutorial FilePath & Placeholders. To restore the old behavior ForceIecFilePath may be configured as follows: [SysFile] ForceIecFilePath=0 BUT WE HIGHLY RECOMMEND TO LEAVE THIS SETTING AT ITS NEW DEFAULT VALUE! "
Last updated: 2024-05-07

Post by manuknecht on Maximum dynamic limits of MC_MoveLinearAbsolute and MC_MoveLinearRelative CODESYS Forge talk (Post)
Hello all I use an axis group with two linear axes in a kinematic system. Using MC_MoveLinearAbsolute and MC_MoveLinearRelative, I am trying to realise dynamic movements (set velocity: 1 m/s, set acceleration: 30 m/s^2) with the highest possible jerk, as I want to compare this with a movement with a trapezoidal velocity profile. However, my measurements show that the axes accelerate with a maximum jerk of approx. 800 m/s^3, even if the value in the function block was set to 10,000 m/s^3. I have already increased the dynamic limits of the two axes accordingly (Velocity: 5000 u/s, Acc-/Deceleration: 250'000 u/s^2, Jerk: 100'000'000 u/s^3, where 1 u = 1 mm), but this had no effect. I have checked the input parameters of the function blocks and the VelFactor, AccFactor and JerkFactor factors are all set to the maximum (value 1). Reducing the cycle time has resulted in a higher jerk, but as we are already working with a cycle time of 1 ms, there is nothing more that can be done here. The axes themselves are still a long way from drawing the maximum current, which is why I assume that this should not be a problem either. Are there other factors or parameters that influence the dynamic limits and therefore allow faster movements? The PLC I am using is a Raspberry Pi 4 and Codesys V3.5 SP20 with all libraries up to date. Thanks in advance Manuel
Last updated: 2024-05-08

Post by wildcard on Modbus Client Request Not Processed CODESYS Forge talk (Post)
Hi, does anyone has a solution for this issue. I've the same problem. I've implemented a very simple client based on the Modbus Examples and connected the soft PLC to a Modbus Simulator. PROGRAM ModbusClient VAR initDone : BOOL := FALSE; errorID : ModbusFB.Error; client : ModbusFB.ClientTCP; timeout : UDINT := 500000; replyTimeout : UDINT := 200000; aUINT : ARRAY [0..8] OF UINT; clientRequestReadHoldingRegisters : ModbusFB.ClientRequestReadHoldingRegisters; clientRequestsCnt : UINT := 0; clientRequestsProcessCnt : UINT := 0; ipAddress : ARRAY[0..3] OF BYTE := [10,54,0,72]; END_VAR IF NOT initDone THEN initDone := TRUE; client(aIPaddr:=ipAddress, udiLogOptions:=ModbusFB.LoggingOptions.All); client(xConnect:=TRUE, ); clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout); clientRequestReadHoldingRegisters.xExecute := TRUE; clientRequestsCnt := 0; END_IF clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout, xExecute := TRUE); IF clientRequestReadHoldingRegisters.xError THEN clientRequestsCnt := clientRequestsCnt +1 ; errorID := clientRequestReadHoldingRegisters.eErrorID; END_IF clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout, xExecute := NOT clientRequestReadHoldingRegisters.xExecute); When the system is running I do get the following on the logs: 2024-05-13T10:18:07.443Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= Client.RequestProcessed ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2070 state=Error 2024-05-13T10:18:07.443Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2070 change state Error -> None timestamp=63843421226 2024-05-13T10:18:08.444Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2071 change state None -> Init timestamp=63844421420 2024-05-13T10:18:09.444Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2071 change state Init -> Error timestamp=63845421675 But the errorID is jumping between OK and RequestNotProcessed. Any help is very appreciated which gives me a hint what I'm doing wrong. Thanks
Last updated: 2024-05-13

Post by maldus512 on How to adapt Codesys Control SL to custom board CODESYS Forge talk (Post)
Hello everyone, I have been given the task to develop I/O drivers for a custom made, Linux based board to allow for Codesys applications to run and control the hardware. I have successfully installed Codesys Control SL for ARM/Linux and tested it with a simple demo application. Now I should start interfacing the runtime to the actual hardware; I should be able to interact with 2 RS485 serial ports, a few GPIOs and an I2C port, all of which already have the corresponding /dev/ interface in the Linux system. I am having trouble understanding how it should be approached. I have found sporadic references that fail to lead to a really comprehensive documentation. For example: The store page (https://store.codesys.com/en/codesys-control-for-linux-arm-sl-1.html#options) mentions a "runtime package" that should allow "Integration of existing C code" and "Usage of local I/Os", which seems exactly what I need to interact with custom peripherals. I have found no further reference to Codesys-C interpop. The Codesys Help page for the runtime package has a page on the "Development of Drivers" (https://content.helpme-codesys.com/en/CODESYS%20Control/rtsllinuxrbpdriverdevelopment.html) that suggests to either "Implement a function block" or "Implement I/O drivers". Those in turn lead to this page (https://forge.codesys.com/drv/io-drivers/doc/Generic/) which describes briefly an XML schema to describe new devices; unfortunately, it doesn't mention what to do with such a description (i.e. how does the runtime know about it) or how it is in any way connected to the actual hardware. Could anyone give me some pointers? I should also mention I have no prior experience with Codesys, so maybe I'm missing an obvious answer.
Last updated: 2024-08-09

Post by jeffg on ERROR: GetNetLinkSockAndInfoByMac(): could not open netlink socket: Too many open files CODESYS Forge talk (Post)
I just installed codesys runtime on a raspberry pi Cortex-A72 (ARM v8) 64-bit SoC @ 1.5GHz (Compute Module 4) I am running on Codesys control for raspberry pi 64 SL ver 4.13.0 and I keep getting a crash after about five to ten minutes. This program was running fine on a 32bit system with runtime 4.8 previously but they upgraded the panel PC cause it got smashed. Looking at the logs I see this error "ERROR: GetNetLinkSockAndInfoByMac(): could not open netlink socket: Too many open files" at the time of crash. I do have a UDP socket open for a serial to ethernet adapter and im wondering if maybe its opening a bunch of sockets and while receiving messages, Im not sending anything to the device only receiving. Below is the code used for the UDP VAR // Scale Comm fbPeerServer : NBS.UDP_Peer; ipAddress : NBS.IPv4Address; fbReceive : NBS.UDP_Receive; xPeerActiv : BOOL := TRUE; abyReceive : ARRAY [0..255] OF BYTE; sLastValidReceive : STRING(255); udiIndex : UDINT; END_VAR IF xPeerActiv AND NOT fbPeerServer.xBusy THEN ipAddress.SetInitialValue(ipAddress := gvlSettings.sIPAddres); fbPeerServer(xEnable := TRUE, itfIPAddress := ipAddress, uiPort := gvlSettings.uiPort); END_IF fbPeerServer(); fbReceive(xEnable := fbPeerServer.xBusy, itfPeer := fbPeerServer, pData := ADR(abyReceive), udiSize := SIZEOF(abyReceive)); IF fbReceive.udiCount > 0 THEN IF fbReceive.udiCount < SIZEOF(sLastValidReceive) THEN SysMem.SysMemCpy(pDest := ADR(sLastValidReceive), pSrc := ADR(abyReceive), udiCount := fbReceive.udiCount); // Set End of String sLastValidReceive[fbReceive.udiCount] := 0; END_IF END_IF If anyone as seen this I could really use some help figuring it out. I included the Log report
Last updated: 2024-09-19

Post by gorditron on I2C Communication with CODESYS Forge talk (Post)
Hello, I have problems with the I2C communication to an ADS7828 AD converter. I don't get any value back from the chip. I use a Kontron chip (ARM 32SC) with Linux as the operating system. I also use the CmpCharDevice library. ADS7828 parameters Address: A1 = 0 / A0 = 0 = SD = 1 = Single End C2 = 0 / C1= 0 / C0= 0 / Channel 0 PD1 = Internal Reference and PD0 = AD Converter ON Here is my code: VAR b_i2cAdr : BYTE := 16#48; (* Standard I2C-Adresse des ADS7828 *) x_Init: BOOL;(* Flag für die Initialisierung *) b_config_byte: BYTE;(* Konfigurationsbyte für den ADS7828 *) ab_cmd_buffer : ARRAY [0..0] OF BYTE; (* Buffer für den Befehl *) ab_data_buffer : ARRAY [0..1] OF BYTE; (* Buffer für die empfangenen Daten *) ui_adc_value_1 : UINT; (* Ausgelesener ADC-Wert *) I2C_Handle: RTS_IEC_HANDLE; (* Handle für das I2C-Device *) di_result_open: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_adr: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_wr_cmd: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_rd_cmd: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_close: DINT;(* Ergebnis der Funktionsaufrufe *) END_VAR //*** Init from the I2C communication port *** IF NOT x_Init THEN I2C_Handle := CDOpen(szFile:= '/dev/i2c-0', dFlags:= O_RDWR, pResult:= ADR(di_result_open)); //* I2C opening * //*** set of the I2C address *** CDIoctl(hFile:=I2C_Handle , dRequest:=1795 , dParameter:=b_i2cAdr , pResult:=ADR(di_result_adr) ); x_Init := TRUE; END_IF (* Hauptlogik *) IF I2C_Handle <> 0 THEN (* Konfigurationsbyte setzen: Single-Ended Kanal 0, interne Referenz *) b_config_byte := 16#8C; (* 10001100b: AIN0, interne Referenz, Single-Ended *) ab_cmd_buffer[0] := b_config_byte; (* Schreiboperation zum Konfigurieren des Chips *) CDWrite(hFile:= I2C_Handle, pbyBuffer:= ADR(ab_cmd_buffer), udCount:= SIZEOF(ab_cmd_buffer), pResult:= ADR(di_result_wr_cmd)); IF di_result_wr_cmd = 0 THEN (* Leseoperation, um den ADC-Wert zu erhalten *) CDRead(hFile:= I2C_Handle, pbyBuffer:= ADR(ab_data_buffer), udCount:= SIZEOF(ab_data_buffer), pResult:= ADR(di_result_rd_cmd)); IF di_result_rd_cmd = 0 THEN (* ADC-Wert aus den Daten extrahieren *) ui_adc_value_1 := SHL(TO_UINT(ab_data_buffer[0]), 8) OR TO_UINT(ab_data_buffer[1]); ELSE (* Fehler beim Lesen der Daten *) ui_adc_value_1 := 0; (* ADC-Wert auf 0 setzen *) END_IF ELSE (* Fehler beim Schreiben der Konfiguration *) ui_adc_value_1 := 0; END_IF END_IF
Last updated: 2024-12-13

Post by s1ack on Wago PFC200 Ethernet / IoDrvEthernet Issue? CODESYS Forge talk (Post)
CODESYS Control for PFC200 4.13.00 CODESYS IIoT Libraries SL 1.11.0.0 Application Based License: CODESYS Control Standard M I have (2) projects with similar code base and both using Wago PFC200. On the second project I am seeing 2 things that I have not been able to resolve: 1) Errors in the log under the Ethernet Item: IoDrvEthernet: [PCI\E1Q51CE62] Could not be found on target! Please check the Ethernet settings. 2) Exception for CPU Load. "Processorload watchdog: plcload=100, maxplcload=95" I have slowed down cyclic tasks on this project, even though on the first project there is actually more code - and it does not exhibit this behavior. In looking at the CPU loading via Linux 'TOP' command there appears to be 20% idle. So plenty of headroom (my opinion). In an effort to troubleshoot I have duplicated the target hardware on my bench. It ran overnight without a CPU load exception. On the test system, I have tried (3) version of the ethernet device. 3.5.16.0 3.5.17.0 and 4.2.0.0 Presently the log does not show the error, but status says the module reports an error. I really do not know if this issue is related to the CPU load exception. The issue does not appear to effect ethernet communications (ModbusTCP or SNMP or Webvisu or PuTTy into Linux Shell). On my test bench I have ModbusTCP slave simulators for all ModbusTCP slaves, but only (1) of the (5) SNMP devices present.
Last updated: 2025-01-21

Post by jeindhoven on Deploying to raspberry pi 5 hangs CODESYS Forge talk (Post)
Yep sure, though now that i think of it, its a pi 4. My bad. The whole ordeal was necessary to use the VGA666 adapter. That needs the old graphical system and GPIO directly on the CPU. Edit: Putty on the virtual development machine connects fine. But i did change the login/pw. The account is still a sudo'er so that should be all right. Edit2: Sorry i get a "Comment rate limit exceeded" from the forum. Then i'll add it as edit here. So i have tried the stock raspberry pi image on a different pi5 (truly 5 this time). Packages updated. Standard password. Same symptoms, no runtime deployed and long hang time. Versions of this pi: pi@raspberrypi:~ $ uname -a Linux raspberrypi 6.12.25+rpt-rpi-2712 #1 SMP PREEMPT Debian 1:6.12.25-1+rpt1 (2025-04-30) aarch64 GNU/Linux pi@raspberrypi:~ $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 12 (bookworm) Release: 12 Codename: bookworm pi@raspberrypi:~ $ apt list --installed | grep openssh-server openssh-server/stable,now 1:9.2p1-2+deb12u6 arm64 [installed,automatic] Attached is the Device information and error text that Codesys comes up with. Edit 3 (Comment rate limit, otherwise it would be a new post) Now i have tried booting an older native Windows 10 machine (no virtualization), and it just works as expected. I have now a raspberry pi 4 and raspberry pi 5 with version 4.16.0.0 of the control application. Windows 10 native: build 19045 (same as virtualised Win 10), same .NET version, same CODESYS version. It seems that running CODESYS virtualized somehow messes with the deployment?
Last updated: 2025-06-23

Post by t-probst on Strong Private Key Protection for Encryption Certificates CODESYS Forge talk (Post)
Hello, We are trying to implement an automated method of adding of a certificate and private key to the Windows certificate store for encrypting CODESYS projects. We want to do this so that users do not have to deal with details of certificates at all and to prevent user error. We are keen on enforcing strong private key protection since it ensures that a password is required for the certificate to be used to decrypt a CODESYS project. When we add a certificate to the certificate store and enable strong key protection using the Microsoft Management Console Certificates snap-in, it works as expected. However, through this method the user may mistakenly not enable strong private key protection. For the certificates we create programmatically (using Microsoft’s Cryptography Next Generation API in .Net 7) bag attributes are added to the certificate and key by the API. These bag attributes are as follows: Bag Attributes localKeyID: 01 00 00 00 subject=C = xx, ST = xxx, O = xxx, OU = xxx, CN = xxx issuer=C = xx, ST = xxx, L = xxx, O = xxx, OU = xxx, CN = xxx -----BEGIN CERTIFICATE----- [encoded certificate] -----END CERTIFICATE----- After using this certificate with bag attributes to encrypt a CODESYS project, it can’t be decrypted, showing this error: "The specified project could not be loaded. Possible reasons might be: - The project file is corrupted or invalid - The project has been saved with a newer version of the programming system. If this is the case, you can open the project in the corresponding version. Choose "Save as..." with the appropriate storage version, and retry again. - You may not have the necessary permissions to lad the project" We know that the bag attributes are causing the issue because if we manually edit the certificate file to remove them before using the certificate to encrypt a project, the project can be decrypted as expected. However, we are unable to automatically enforce strong key protection using this method. Here is a link to a StackOverFlow question that we have posted recently for this issue: https://stackoverflow.com/questions/76922355/enforcing-strong-private-key-protection-for-x509certificate2-objects-in-net-mod Any help is greatly appreciated.
Last updated: 2023-08-22

Post by martinlithlith on Device User Logon and No device is responding.. Pi4b codesys 3.5 SP19 2 + (64-bit) CODESYS Forge talk (Post)
Hi! Im slowly starting to loose it and i need som help! After a few night of reading up and testing i´m still stuck as a rock and you guys and girls are my last resort for this project. Basic facts; Win 11 Codesys 3.5 SP19 2 + (64-bit) Raspberry pi 4 model b 2 gb Raspian release 11 aarch64 What keeps me up late at night; Username and Password when trying to connect to device and device only beeing connectable for a few seconds. Some of the things I have tried; Username and passord; Credientials from the raspberry Administrator Administrator admin admin Admin Admin administrator administrator Usernames and passwords that I sometimes use (this was a longshot i know, but i was running out of ideas and energy). :) Epand filesystem, activating i2c, spi, 1-wire I can start the gateway and start the runtime. I cant install the edgearm64, arm64 runtime package eventhough I guess i should, i get code [ERROR] Error output: dpkg: error processing archive /tmp/codesysedge_edgearm64_4.8.0.0_arm64.deb (--install): [ERROR] Error output: package architecture (arm64) does not match system (armhf) [ERROR] Error output: Errors were encountered while processing: [ERROR] Error output: /tmp/codesysedge_edgearm64_4.8.0.0_arm64.deb code as a respons. I have tried to Reset Origin Device - no change. I have tried to remove the /etc/CODESYSControl_User.cfg [CmpUserMgr] but i could not find it and i was not sure if i should add it instead but i did not want to mess somthing up. I have tried to create a second gateway with the specific ip if the pi, that did not help. Could it be that i´m currently connected to the pi through WIFI? I can ping the pi and I can connect and control it through VNC. When i scan to select gateway target (scan edge gateway) i find 17-21 devices but can find the pi throug the mac adress. I started of trying to use the "CODESYS Control for Raspberry Pi SL" (I have a license sience earlier) as i read somewhere that this could be used on a Pi4 as well but now i´m trying with the MC SL, no changes, same problem. Right now - gateway version 4.8.0.0 (edgearmHF, armhf), Runtime Package 4.5.0.0 (raspberry, armhf). Any sugestions are very welcome! As mentioned above, theese are some of the things that i have tried/done - but i have been going at this for a while. Best, Martin
Last updated: 2023-09-10

Post by dwpessoa on CNC Jumps G20 - SMC_NCInterpreter and long time to process CODESYS Forge talk (Post)
I am studying and developing a Softmotion+CNC system for a machine that executes multiple pieces. The G code program is written by the machine operator and each cycle execute 1 piece. The programs are large, exceeding 1000 lines and using up to 8 axes (X, Y, Z, A, B, C, P and Q). The machine needs to run cyclically, executing N pieces (selected by the Operator)... so I tested it using Looping and counters (G36 G37 and G20) and it worked, but it takes a long time to process, and the more pieces I need, the longer the processing time and this is totally impracticable. I found this solution which was very good, and for a few cycles it works well, but for 99999 pieces of a program with 1000 lines, it doesn't work very well... Another solution I tested is to maintain the interpolator with an automatic restart, that is, I load the program without looping (without G20) and give it another start as soon as it finishes. This partially resolved it, but there is still a delay in processing SMC_NCInterpreter in each restart :(. Another solution I thought of is to manually create the SMC_GEOINFO structure and then reuse it, avoinding the Interpreter, but reading the documentation and checking the structure filled by standard blocks, I noticed that there doesn't seem to be a "JUMP" function in the structure! In other words, the SMC_NCInterpreter actually keeps copying and copying the program section for each jump (G20)... If I repeat a 10-line program 1000 times, I will have a structure with more than 10000 lines... possibly this is the cause of take so long to process. Has anyone ever had a problem like this? I believe the same thing happens with typical applications with manipulator robots using Codesys in continuous cycles, and I would like to know if there is any solution, or even if I am misinterpreting the G20 question in SMC_GEOINFO. Thanks!
Last updated: 2023-09-20

Post by gustavocsw on MQTT memory leak problem CODESYS Forge talk (Post)
Hello everyone, I'm using the IoT Library to implement the MQTT communication with my local broker server in order to publish and subscribe at specifics topics to share and consume information about my application. But, it seems that are occurring some memory leak problem in a "high" frequency (more than 10 Hz) subscribe process. I follow the same method as in IoT Lib exemples, and at first looks perfect but my PLC was rebooting frequently and when I check its memory usage that was increasing as fast as the subscribe massage was sent. I'm using a WEG PLC410 and a WEG PLC500, and this error occurred in both of them (including in CODESYS Control Win x64). The application sends to the system a message JSON with the float payload Ex. {"data" : 0.8500}, but this happens with a INT, or BOL as well. I use the follow code in my application to find the value: //FindFirstValueByKey VARs PROGRAM JSON_VELO VAR //------Setting the JSON Subscriber to Set the Relay Value jsonDataVelo : JSON.JSONData; jsonByteArrayReaderVelo : JSON.JSONByteArrayReader; xST1okVelo : BOOL; FindFirstValueByKeyVelo : JSON.FindFirstValueByKey; jsonElementVelo : JSON.JSONElement; xDoneReaderVelo : BOOL; xDoneFindVelo : BOOL; //STRING and WSTRING for Subscribe the massage sPayloadJsonVelo : STRING := 'opa'; psPayloadJsonVelo : POINTER TO BYTE := ADR(sPayloadJsonVelo); //wsPayloadJsonRelaySet : WSTRING := "opa"; wsPayloadJsonVelo : WSTRING := STRING_TO_WSTRING('opa'); pwsPayloadJsonVelo : POINTER TO WORD := ADR(wsPayloadJsonVelo); lrVelo : LREAL; xKeepAliveVelo : BOOL; xSetVelo : BOOL; RSSet : RS; LIMPAR : STRING; //Find the msg end sFindVelo : STRING := '}'; psFindVelo : POINTER TO STRING := ADR(sFindVelo); iLenVelo : INT; iSizeVelo : INT := 12; udiContMsg : UDINT; END_VAR // FindFirstValueByKey CODE // Relay Set configuration xSetVelo := MQTT_SUBSCRIBER.RSVelo.Q1; IF xSetVelo THEN xKeepAliveVelo := TRUE; END_IF IF xKeepAliveVelo THEN udiContMsg := udiContMsg + 1; iLenVelo := TO_INT(StrLenA(psPayloadJsonVelo)); iSizeVelo := iLenVelo - TO_INT(MQTT_SUBSCRIBER.udiPayloadSizeVelo); StrDeleteA(psPayloadJsonVelo,iSizeVelo,iLenVelo); wsPayloadJsonVelo := STRING_TO_WSTRING(sPayloadJsonVelo); pwsPayloadJsonVelo := ADR(wsPayloadJsonVelo); //MQTT.ConvertUTF8toUTF16(sourceStart:= ADR(sPayloadJsonVelo), targetStart:= ADR(wsPayloadJsonVelo), dwTargetBufferSize:= TAM, bStrictConversion:= 1); //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := TRUE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := xDoneReaderVelo, wsKey := "data", diStartIndex:= 0, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); IF xDoneFindVelo THEN lrVelo := jsonElementVelo.value.lrValue; //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := FALSE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := FALSE, wsKey := "data", diStartIndex:= 1, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); xKeepAliveVelo := FALSE; GVL.xSetVeloRead := TRUE; END_IF END_IF And this to subscribe at the topic: //SUBSCRIBE VAR: //----------------- Subscribe Velocity ----------------------- MQTTSubscribeVelo : MQTT.MQTTSubscribe;//Variable MQTTSubscriber block -X - function-X wsTopicSubscribeVelo : WSTRING(1024) := "CORE/odometry/GET/data/simp"; // Topic to publish a message sSubscribeMassageVelo : STRING; udiPayloadSizeVelo : UDINT; xSDoneVelo : BOOL; xSErrorVelo : BOOL; xReceiveVelo : BOOL; eSTypeVelo : MQTT.MQTT_ERROR; eSMQTTErrorVelo : MQTT.MQTT_ERROR; RSVelo : RS; udiCont : UDINT; //SUBSCRIBE CODE: MQTTSubscribeVelo( xEnable:= MQTT_CLIENT.xConnection_Broker AND NOT xSErrorVelo AND NOT JSON_VELO.xKeepAliveVelo, pbPayload:= JSON_VELO.psPayloadJsonVelo, udiMaxPayloadSize:= SIZEOF(JSON_VELO.sPayloadJsonVelo), udiPayloadSize => udiPayloadSizeVelo, mqttClient:= MQTT_CLIENT.ClientMQTT, wsTopicFilter:=wsTopicSubscribeVelo, xDone => xSDoneVelo, xError=> xSErrorVelo, xReceived => xReceiveVelo, eMQTTError=> eSMQTTErrorVelo ); RSVelo(SET := xReceiveVelo, RESET1 := JSON_VELO.xKeepAliveVelo);
Last updated: 2024-09-09

Post by alex-at-xana on EThercat Dynamic configuration CODESYS Forge talk (Post)
Hi Everyone, For a fast monitoring system I am using Ethercat oversampling and timestamping inputs. As the customers has a lot of different configurations out in the field, we went for a dynamic Ethercat configuration. Already got the whole detection chain working but now I am stuck since two days in debugging the configuration. Here are my quesitons: I extended the dynamic config example for the EL3632 16#0E303052: //EL3632 pSlave^.SetDCSettings(TRUE,TRUE,80,80,TRUE,4000,0,0); pSlave^.AddSyncManager(16#1000,128,16#26,TRUE,3); pSlave^.AddSyncManager(16#1080,128,16#22,TRUE,2); pSlave^.AddSyncManager(16#1100,0,16#4,TRUE,1); pSlave^.AddSyncManager(16#1110,214,16#20,TRUE,0); pSlave^.AddFMMU(0,214,0,7,16#1110,0,1,1); pSlave^.AddFMMU(0,1,0,0,16#80D,0,1,1); xKnown := TRUE; This leads to a PLL Error for these devices. I double and triple checked the configuraton, but cannot find the issue. There seems to be one difference: the config dialog creates a startup parameter: 16#10F3:16#05, Name: Command_0, Value:0. Bitlen: 16, Stop on fault: false, jumpt at fault: false: next line: 0 a) I do not find information on how to set this in my code. Can you help me there? b) Without trying to set the value, I get a PLL error for these devices in the master log. Is the config wrong? c) Do I need to set the Master to Autoconfigure or Manual? I used autoconfigure for my tests. The stack creates input data addresses for the slaves input data range (pSlaves[i].InputData) which are different from those created when I use the Engineering tools dialogs to configure Ethercat. Specifically, the addresses seem to be aligned at 16 byte boundaries when they are created using the engineering tool, but may appear at uneven addresses when I use the script in dynamic config. I did not try to access ULINT at uneven addresses yet, but I am suspecting this may be a problem. Do I need to manually align the addresses ? Any help is appreciated...
Last updated: 2024-09-10

<< < 1 .. 12 13 14 15 > >> (Page 14 of 15)