Post by dekelec on Request for IFM ecoPlus21 installation package CODESYS Forge talk (Post)
Hello, I’m looking for the ecoPlus21 development environment used with early IFM controllers (e.g., CR0020_Q firmware). We have an old project created in ecoPlus21 that cannot be opened in CoDeSys 2.3, and IFM no longer provides this software. If anyone still has the ecoPlus21 installer or knows where it can be downloaded, please let me know. It’s needed only for recovery and migration of an existing project. Thanks in advance,
Last updated: 2025-10-17

Post by dgross on Alarm Manager History Message Missing CODESYS Forge talk (Post)
Hi All, I'm using a webvisu on a control Win V3 SoftPLC. My issue is with the Alarm Managers Alarm history. It does create entry's and does also show the latch data. But it only shows the message of the active alarms. In the history the message is empty (also in the .csv Export file). The archiving in the alarm group is checked and the Alarm storage is activated. I'm using the Version V3.5 SP22 Patch 1. Do you have any idea where that comes from?
Last updated: 2026-04-20

Post by drbuzz on Communication Error (#0) for IFM controller CODESYS Forge talk (Post)
Hi Folks, Every time I use an IFM controller I always seem to run into a problem connecting to it. I get the Communications Error (#0). So I thought I would share some tips and tricks. Once the CANfox Cable (EC2112) cable driver is installed, you can use the yellow app in the sys tray to blink the lights on the cable. Confirm the cable works in the IFM maintenance software by connecting to the controller and reading the information on it. Make sure to download an OS into the controller (the light will go from a fast blink to solid green). In Codesys V2.3, the communication settings for the CR0401 is 250kBaud by default and Node ID 127. What got me, was I needed to reboot the computer after the cable driver install. Also if your application has canbus settings in it which are changed from default, after the controller is power cycled, the new Node ID and Baud will be in effect. I made a handy guide because too much time has been wasted on this. Programming IFM CR0401 Serial/Can Programming Cable • Connect IFM EC2112 CanFox programming cable with connector adapter. • Make sure cable is linked to VM (if using VM). • Install drivers for cable if not installed. o Download from IFM EC2112 site. https://www.ifm.com/ca/en/product/EC2112 • Once Installed, reboot computer. • In system tray, there should be a yellow icon that you can open and check on programming cable. Select the cable in the list and flash the lights to confirm it is working. Maintenance Software • Install IFM Maintenance Tool Software. o Download from IFM Site. https://www.ifm.com/ca/en/download/eco100_MaintenanceTool • Open IFM Maintenance software • Select Basic System • Select CAN cable • It will tell you if you don’t have a cable connected. • Use Wizard if needed. • Read Channel Parameter on the Settings page, or get Identity in the System Information > Identity. • Default Node is 127 on a new unit. Baud is 250kBaud (bits/sec) • Controller information should populate. • Controller green light should be blinking at 5hz (meaning OK but no OS, just bootloader). • Click Software > Load. • Open the OS file. Should match Codesys version selection (for CR0401 this is version 3). o Download OS file from IFM Website. https://www.ifm.com/ca/en/product/CR0401 o It is located at the top of the download under “software for CR0401”. o Select the file and load it… this will take a minute. • Once completed the unit should now have a solid green light o Solid green means the controller has an OS but no application is running. Codesys V2.3 Application • Codesys needs to be downloaded and installed from the IFM website as it has the IFM libraries and license to use the software. o Download from the IFM CR0401 page. o https://www.ifm.com/ca/en/product/CR0401 • Create new application with the correct IFM controller or Open Codesys application. • Keep in mind that the PLC Configuration on the Resources tab can be changed for the CAN communication interface… so changes to node and baud will take effect after the first download and reboot of the controller. • Go to “Online” in the top menu and change “Communication Parameters” o The Local dropdown shows the last configuration used. All other interfaces will show below it and need to be updated when changed or used. o Confirm Node ID is 127 for the first download.  The NodeID will change to whatever the program has after (in my case 125).  Node Send Offset should be default at 1536  Node Recv Offset should be default at 1408  Can bus Baudrate should be 250 kbaud.  Yes to Motorola Byte Order  Block Transfer should be false and note used (60 is default setting).  Can Card Driver should match the systray item which is Sie_USB. • If the system populated the other one, just update and relay the communication parameters. The software will usually bring up the available cable and driver. • Go to “Online” and Login to download. o Press Yes to Download Application. I hope this helps!
Last updated: 2025-03-21

Post by ggarcia94 on IMAGE DISPLAY ACCORDING TO INPUT VARIABLE CODESYS Forge talk (Post)
Reopening this thread as I need to make a few images visible depending on the value of a variable. However, in the properties of the image I do not have the option to make the image visible (see attached image). I´m using Codesys V3.5 SP19. However, when I use V3.5 SP17 I have the option to make the images visible. Can someone help me achieve this with V3.5 SP19? EDIT: Fixed. Just had to uncheck Support client animations in the Visualization manger settings
Last updated: 2023-09-12

Post by ernesto881124 on ernesto881124 CODESYS Forge talk (Post)
Hello good morning everyone I would like to ask a question, is it possible to directly connect a device that only contains modbus RTU communication through an R-45 connector, directly to the PC? Or would you need an intermediate device to achieve communication? It would be of great help to me because I cannot achieve communication between the Codesys simulator plc and a Fuji Frenic mini VFD, please help me if anyone has had the same experience. Thank you so much
Last updated: 2023-09-13

Post by timvh on When Keyboard Key is in Hold, then Webvisu is extreme slow and latent CODESYS Forge talk (Post)
I'm not really sure what you are trying to do, but maybe you are referring to using the CmpCharDevice library? When you "open" the connection to a device, you can pass flags. What helped me is to set the non-blocking flag. I'm not sure if this is what you are referring to, but maybe it helps: dFlags: DINT := CmpCharDevice.ACCESS_MODE.O_RDONLY + DINT#4000; // see details for flags: http://linux.die.net/man/2/open, + DINT#4000 is for non-blocking hDevice := CmpCharDevice.CDOpen(szFilename, dFlags, Result);
Last updated: 2023-09-20

Post by john-martin on Send file from codesys to...... ftp, cloud, etc CODESYS Forge talk (Post)
Hi everybody, I am looking for a solution to send files, for example, to an ftp or a cloud. I can't use oscat library because 64 bit controller are not supported. Therefore, I see that the IIoT library has some functions that might help me to implement this sending process in codesys. Does anyone have any examples of how to do this? I have spent some days with this issue without success. Best regards.
Last updated: 2023-11-02

Post by timvh on Management of a PLC network from a remote station CODESYS Forge talk (Post)
Maybe the CODESYS HMI is a good solution. https://store.codesys.com/en/codesys-hmi-sl-bundle.html Run this on the remote main control station. In the HMI application you can add the data source manager and to this manager you can add Data sources. A data source has a reference to the PLC you want to connect to and can get access to the variables of the PLC application. You can then use these variables in the visualization of the HMI application.
Last updated: 2023-12-04

Post by mikek10 on Some 'pathetic' errors in SoftMotion program CODESYS Forge talk (Post)
I was answering your last paragraph Meanwhile, I would like to understand why the motion FB instances must still be called even after the Execute is set to FALSE, especially in view of the fact that the next instruction is programmed to abort the previous one, with BufferMode set to 'Aborting'. All these unnecessary FB calls are an unnecessary overhead on the CPU anyway. Is there any precise rule about when to cease calling the various instances? (It should precisely be the 'done' status that says this one has finished its work).
Last updated: 2024-07-18

Post by aliazzz on Unable to deploy Virtual Control SL on ARM64 (Raspberry Pi5) CODESYS Forge talk (Post)
An interesting remark for CODESYS Support. I found this after looking through the Runtime Deploy Tool messages when I connect to an AMD64 architecture Successfully Connected to Target ( {MyIP} - AMD64 ) when I connect to an ARM64 architecture (Raspberry Pi5) Successfully Connected to Target ( {MyIP} - ) As clearly seen in the attached .png, the AMD64 target is detected, while the ARM64 target architecture is not detected (displayed). I assume that this is the reason why the pulldown menu isn't populated correctly.
Last updated: 2024-07-28

Post by ivanh on kepware minimun privilege CODESYS Forge talk (Post)
Hello everyone, I’m integrating Codesys with Kepserver using the Kepware driver for Codesys, and I need to configure a user account with the minimum necessary privileges to read and write to the tags on the PLC, without using the internal OPC UA server of Codesys. However, despite not assigning the Modify permission, Kepware still allows writing to the tags. What are the minimum required permissions to ensure that writing is only allowed when necessary, and how can I prevent other permissions from being overridden? Any guidance would be greatly appreciated.
Last updated: 2024-08-12

Post by micik on ERR_OK not recognized CODESYS Forge talk (Post)
Hello, if I try to use ERR_Ok in my code to check whether the file is open correctly or not, I get an error "Identifier ERR_OK not recognized", I can use plain 0 (zero) instead. But in general, is this a proper way to check for success of file operation since the 4th parameter is a poinmter to RTS_IEC_RESULT, and normally I would expect this to be used somehow. _hFile := SysFileOpen(_sFileName, am:=SysFile.ACCESS_MODE.AM_WRITE, ADR(_result)); IF _result <> 0 THEN udDiag := 100; RETURN;
Last updated: 2024-08-17

Post by durallymax on Access Variable Visu Dialog CODESYS Forge talk (Post)
Is there a way to access the variable in the called dialog? Example: Text Field element with PLC_PRG.myVar as Text variable. OnMouseClick configured to write variable with keypad pop-up. OnValueChanged configured to Execute ST RND(PLC_PRG.myVar,2); Rather than change myVar with each copy of this Text Field, is there a way to access whatever the configured text variable is? Generally try to stay away from ST in visu, but was curious regardless.
Last updated: 2024-11-14

Post by garrian on How to write multiple coils (Modbus FC15) CODESYS Forge talk (Post)
Thanks for your reply. I belive it is contiguous, I'm writing to adress 0 to 4. Or, do you mean something else? Well, something is happening. If I on the client set adress 1,2,3 to true, only 1 is set to true on the server side. On the client side, the data is array of word. But on the server side, the coils are array of bool. Holding register is array of word on server side. Can this be a problem? Attached screenshot of how it looks at the server side.
Last updated: 2024-11-17

Post by smartcoco on Opaque NodeId in the OPC UA server CODESYS Forge talk (Post)
This seems to be because when creating 'OPC UA' with 'Communication Manager', the 'IdentifierType' of 'NodeId' cannot be configured as' String 'type. This issue is not an isolated case. For this issue, CODESYS seems to have not provided guidance to users on how to proceed. We can provide feedback on this issue in the 'My Question' section of the 'CODESYS Store' to make CODESYS take it seriously.
Last updated: 2025-01-10

Post by andre-luis on Device diagnosis ( EtherCAT IO card ) CODESYS Forge talk (Post)
Hi, In our project, it is not rare to have I/O cards issues. I wanted to have a way to check their statuses ( Eg. INIT, OP, PREOP, etc.. ) I was trying to use the GetDeviceDiagnosisInfo method from the IoConfig_Globals, but there is no info available on the Web with a simple example; does someone have a link to some tutorial or anything else ? Kind Regards, Andre.
Last updated: 2025-02-06

Post by dogulas on Removing a symbol from the IEC Symbols Editor grid CODESYS Forge talk (Post)
Right now when I make a change to one of the tags in my code, I have to completely remove the IEC Symbol Publishing object from the tree view and re-add it. Then I have to completely re-add every symbol to the grid view by dragging them over. This can be a lot. Surely, this is not the intended behavior. Can anyone tell me how this is supposed to work?
Last updated: 2025-02-11

Post by alex2 on How to uninstall SVN module CODESYS Forge talk (Post)
Hello, At work, I use Codesys V3.5 SP10. I wanted to run some tests with the SVN module, which I kept installed (without actually using it in the end). However, when I tried to launch Codesys today, I was informed that a license was missing. I suspect that this is due to the SVN module. Could you tell me how to uninstall it without launching Codesys? (as i cant proprerly start Codesys without the license) Thank you in advance.
Last updated: 2025-02-25

Post by trusty-squire on How can you get the active frame index from a frame CODESYS Forge talk (Post)
If you are switching a frame based on the "Switch Frame Variable", then just use a variable that is accessible to your program to set your active frame. If you're trying to see which is the active visualization, then use the "CurrentVisu" variable. Note you'll need to enable this by checking it on in the Visualization Manager settings. If it's neither of those, you'll need to be more clear on how you're project is set up.
Last updated: 2025-03-11

Post by trusty-squire on AXIS Rollover CODESYS Forge talk (Post)
In that case, the best thing to do might be to track the offset in a separate variable of your logic, then when you provide target positions, make your target position use the tracked offset as below: ActualTargetPosition := (TargetPosition + MyOffset) MOD 360; Although, upon further reflection, you'll still have the same cycle time issues. You might be able to break your code into multiple tasks to reduce the cycle time, or use an Event task to capture the offset position?
Last updated: 2025-03-12

Post by johnbomb on Ignore Dependencies When Loading Package? CODESYS Forge talk (Post)
I'm trying to load a .package into Codesys 3.5.21, but the package is intended to only work with Codesys 3.5.18.0 and is configured with dependencies on the specific versions of other packages included with 3.5.18.0, and 21 has newer versions so the package will not install. I would like to install the package anyway to try and get things working on a newer Codesys version, since for some reason the installer for .18 errors out and doesn't fully work in my environment, but .21 seems to work fine.
Last updated: 2025-04-01

Post by arwie on Use MC_Home without enabling the drive for homing method 35 CODESYS Forge talk (Post)
Is it possible to use MC_Home without enabling the drive (MC_Power)? On the drive the homing method 35 (Homing on current position) has to be executed. The drive has to stay disabled due to safety. This is explicitly allowed by the drive. Unfortunately MC_Home reports the error SMC_REGULATOR_OR_START_NOT_SET when executed. Are there other options to start homing, if not with MC_Home?
Last updated: 2025-06-25

Post by imdatatas on The default ramp type selection in SoftMotion V4.18.0.0 is Quadratic CODESYS Forge talk (Post)
Dear @gseidel, @tk096, I noticed that with SoftMotion V4.18.0.0, if a new axis is added to the project, the ramp type selection defaults to "Quadratic". In all previous versions, the velocity ramp type selection was "Trapezoidal". This causes some unexpected issues in projects with SoftMotion version V4.18.0.0 for newly created or newly added axes to existing projects. Is it possible to reconsider this situation in the next update and set the velocity ramp type to "Trapezoid" by default again? Best Regards, Imdat
Last updated: 2025-07-22

Post by camjam on BOOL variable in OPC UA and modbus simultaneously CODESYS Forge talk (Post)
I have come across this. The only way i could get it to work would be to define a word that is also the same address as the Bools. eg %MX600.0 through to %MX600.15 would be individually defined in the variables and them have another variable word defined at %MW300. You still need to break out the word in what ever program you are using to read/write the OPCUA tags.
Last updated: 2025-08-18

Post by apurv on Cannot pass array of constant size to a function as a reference CODESYS Forge talk (Post)
I have a Array of constant size defined like this Var Constant MAX_SIZE :UINT := 10; End_var VAR array : ARRAY[0..MAX_SIZE] OF INT; END_VAR Now I want to pass this array to a function by reference, Function fun : INT VAR_IN_OUT CONSTANT MAX_SIZE : UINT; END_VAR VAR_INPUT array : REFERENCE TO ARRAY[0..MAX_SIZE] OF INT; END_VAR but when I run this it gives strange Errors Error : Cannot Convert type 'ARRAY [0..MAX_SIZE] OF INT' to type 'ARRAY[0..MAX_SIZE] OF INT'
Last updated: 2024-01-07