Post by john-robinson on Limiting Memory Access of an Array to Within its Bounds
CODESYS Forge
talk
(Post)
Recently we had an issue regarding some simple code to calculate a rolling average. The code indexes from zero to 199 to properly store the current input into a circular buffer which then allows us to calculate a rolling average: VAR input_5s : REAL; outs_arr : ARRAY[0..199] OF REAL; i : USINT := 0; END_VAR ___ //this code runs every five seconds, calculating a rolling average outs_arr[i] := input_5s; i := i + 1; output := OSCAT_BASIC.ARRAY_AVG(ADR(outs_arr), SIZEOF(outs_arr)); IF i >= SIZEOF(outs_arr) THEN i := 0; END_IF There is a simple bug in this code where the index will be set to 0 when it has surpassed the length of the array in bytes (800 in this case) rather than larger than the number of reals in the array (200). The solution here is simple, replacing i >= SIZEOF(outs_arr) with i >= SIZEOF(outs_arr)/SIZEOF(outs_arr[0]). In this example when the index increased to 201 and the line outs_arr[201] := input_5s was called, codesys arbitrarily wrote to the address in memory that is where outs_arr[201] would be if the array was that long. I would like to find a way to wrap the codesys array inside of a wrapper class that checks if an input is within the bounds of an array before writing to that value. I know how I would implement that for a specific array, I could create a method or class that takes an input of an array of variable length, ie. ARRAY[*] OF REAL, but I don't know how to make this for any data type. I am wondering if anyone has ever done anything similar to this, or has any better suggestions to ensure that none of the programmers on this application accidentally create code that can arbitrarily write to other locations in memory.
Last updated: 2024-03-05
Post by drbuzz on Communication Error (#0) for IFM controller
CODESYS Forge
talk
(Post)
Hi Folks, Every time I use an IFM controller I always seem to run into a problem connecting to it. I get the Communications Error (#0). So I thought I would share some tips and tricks. Once the CANfox Cable (EC2112) cable driver is installed, you can use the yellow app in the sys tray to blink the lights on the cable. Confirm the cable works in the IFM maintenance software by connecting to the controller and reading the information on it. Make sure to download an OS into the controller (the light will go from a fast blink to solid green). In Codesys V2.3, the communication settings for the CR0401 is 250kBaud by default and Node ID 127. What got me, was I needed to reboot the computer after the cable driver install. Also if your application has canbus settings in it which are changed from default, after the controller is power cycled, the new Node ID and Baud will be in effect. I made a handy guide because too much time has been wasted on this. Programming IFM CR0401 Serial/Can Programming Cable • Connect IFM EC2112 CanFox programming cable with connector adapter. • Make sure cable is linked to VM (if using VM). • Install drivers for cable if not installed. o Download from IFM EC2112 site. https://www.ifm.com/ca/en/product/EC2112 • Once Installed, reboot computer. • In system tray, there should be a yellow icon that you can open and check on programming cable. Select the cable in the list and flash the lights to confirm it is working. Maintenance Software • Install IFM Maintenance Tool Software. o Download from IFM Site. https://www.ifm.com/ca/en/download/eco100_MaintenanceTool • Open IFM Maintenance software • Select Basic System • Select CAN cable • It will tell you if you don’t have a cable connected. • Use Wizard if needed. • Read Channel Parameter on the Settings page, or get Identity in the System Information > Identity. • Default Node is 127 on a new unit. Baud is 250kBaud (bits/sec) • Controller information should populate. • Controller green light should be blinking at 5hz (meaning OK but no OS, just bootloader). • Click Software > Load. • Open the OS file. Should match Codesys version selection (for CR0401 this is version 3). o Download OS file from IFM Website. https://www.ifm.com/ca/en/product/CR0401 o It is located at the top of the download under “software for CR0401”. o Select the file and load it… this will take a minute. • Once completed the unit should now have a solid green light o Solid green means the controller has an OS but no application is running. Codesys V2.3 Application • Codesys needs to be downloaded and installed from the IFM website as it has the IFM libraries and license to use the software. o Download from the IFM CR0401 page. o https://www.ifm.com/ca/en/product/CR0401 • Create new application with the correct IFM controller or Open Codesys application. • Keep in mind that the PLC Configuration on the Resources tab can be changed for the CAN communication interface… so changes to node and baud will take effect after the first download and reboot of the controller. • Go to “Online” in the top menu and change “Communication Parameters” o The Local dropdown shows the last configuration used. All other interfaces will show below it and need to be updated when changed or used. o Confirm Node ID is 127 for the first download.  The NodeID will change to whatever the program has after (in my case 125).  Node Send Offset should be default at 1536  Node Recv Offset should be default at 1408  Can bus Baudrate should be 250 kbaud.  Yes to Motorola Byte Order  Block Transfer should be false and note used (60 is default setting).  Can Card Driver should match the systray item which is Sie_USB. • If the system populated the other one, just update and relay the communication parameters. The software will usually bring up the available cable and driver. • Go to “Online” and Login to download. o Press Yes to Download Application. I hope this helps!
Last updated: 2025-03-21
Post by egret on Issue with J1939, PGN 65267 (Vehicle Position)
CODESYS Forge
talk
(Post)
I have a J1939 network (ISOBUS) connected to my PLC. I can receive various PGNs such as 65256 (Vehicle Direction/Speed) and 65254 (Time/Date). However, I cannot receive 65267 (Vehicle Position). PGN 65267 (VP) contains SPN 584 (Latitude) and SPN 585 (Longitude). On the network both SPNs return a value of -210 (meaning the CAN message payload is zero in both cases). The conversion settings are the default values and appear to be correct (see attached screenshot). Using a CAN analyser I can see that PGN 65267 (Vehicle Position) is being transmitted over the network with valid (non-zero) data that matches the latitude and longitude coordinates I would expect. I've created a program to read the raw J1939 data and this also returns valid data. It seems that the Codesys J1939 database has a problem with reading PGN 65267 messages. Can anybody else confirm this? I'm using Codesys Version 3.5 SP16 Patch 5.
Last updated: 2023-09-13
Post by moksan on Unconnected_Send Explicit message with Route Path
CODESYS Forge
talk
(Post)
I have been trying out Unconnected_Send Explicit Message with route path.(The Unconnected_Send service shall use the Connection Manager object in each router to forward the message and to remember the return path. Vol 1.3 / 3-5.6.7) However, I could not see the correct path on Wireshark. I want to see the Unconnected_Send Message Service Code as 0x52 and also the last of the message should have the route path. I want to ask some questions about this topic. The IIoDrvEIPAcylicServices Interface has the IoDrvSendUnconnectedMessage Method. And there is a struct (EIP_SendUnconnectedMessage) for this service. But there is no information about how to implement to project, and if it is successful, does it send a message with 0x52 Unconnected_Send Service Code or not? If that is not a solution, how can I set the Unconnected_Send Explicit Message struct on Codesys? Also how can I send explicit message with route path?
Last updated: 2023-10-17
Post by psychoengineer on Cannot Save CSV File on Windows Computer Using CODESYS and Control Win
CODESYS Forge
talk
(Post)
I am currently working on a project using CODESYS and Control Win on a Windows computer. I've encountered an issue where I am unable to save a CSV file. I have followed the standard procedures and used the appropriate file handling functions, but the file is not being created or saved as expected. IF xStartTest THEN sFileName := '\logs.txt'; sFileName := CONCAT(gvl.g_sMainDirectory, sFileName); sFileNameCopy := '\CAAFileCopy.txt'; sFileNameCopy := CONCAT(gvl.g_sMainDirectory, sFileNameCopy); //eWriteState := FILE_OPEN_TRIGGER; xTestDone := FALSE; xError := FALSE; xStartTest := FALSE; END_IF VAR_GLOBAL g_sMainDirectory : STRING := 'C:\LogFiles'; // file path for CSV file END_VAR Despite this, the file does not appear in the specified directory, and no error messages are being generated. I've checked the directory permissions and ensured that the path is correct. Has anyone else experienced a similar issue or have any suggestions on how to resolve this? Any help would be greatly appreciated. Thank you!
Last updated: 2024-07-04
Post by xgongx on What is the insights of IoDrvEtherCAT.DCInSyncWindow?
CODESYS Forge
talk
(Post)
It is well known that you need to increase the value of IoDrvEtherCAT.DCInSyncWindow to solve the "Fieldbus lost synchronicity" issue. In the official document, IoDrvEtherCAT.DCInSyncWindow is explained as the toleration of a certain jitter. But the official document doesn't explain what kind of the jitter is. Is it the jitter of DC sync deviation, master timer or something else? It is very important to know the insights of IoDrvEtherCAT.DCInSyncWindow. For example, if it is the toleration of DC sync deviation, and the official recommending value is 200us for CODESYS SoftMotion. It means maximum of DC sync deviation is 200us. It is unacceptable for some high precision motion control tasks, for example high speed gear task, etc. Increasing the value of IoDrvEtherCAT.DCInSyncWindow will increase the deviation of motor rotation sync if it is the toleration of DC sync deviation. So, would anyone tell me what the insights of IoDrvEtherCAT.DCInSyncWindow is? Thanks.
Last updated: 2024-07-09
Post by rossanoparis on Clarifications regarding the appropriate runtime system to use
CODESYS Forge
talk
(Post)
Thank you @TimvH It is clear that licences are application based and now thanks to your reply I could understand the meaning of RT systems. The RT called "CODESYS Control for Linux ARM SL" can be deployed on a generic debian based ARM system. The RT called "CODESYS Control for Raspberry Pi MC SL" is more specific for Rasberry HW. Did I understand correctly? Regarding the RT called "CODESYS Virtual Control SL" despite its description it is not clear to me when to use it. It seems that a project created using such RT system can be deployed on any HW. It sound good obviously, as it means that it is possible to realize a completely abstract project from its hardware. The only limit could be represented by the need of using a specific HW or OS feature, in that case a more specific RT system should be chosen. Is my last consideration correct? Regards Rossano
Last updated: 2024-09-26
Post by andrax on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
Hi, Communication with the ADS1115 is actually simple. 1. write config 2. write address pointer 3. read conversation register The ADS1115 works like a multiplexer. This means that you do this individually for each channel that you want to read. e.g: Channel 1: write config > write address pointer > read conversation register Channel 2: write config > write address pointer > read conversation register Channel 3: write config > write address pointer > read conversation register Channel 4: write config > write address pointer > read conversation register then you start again from the beginning You can also omit individual channels or read only one. It doesn't matter. I have written the driver so that I can also use it on the TCA9548. The driver is from Stefan Dreyer. In your case, the driver works and communication with the ADS1115 is running. As you can see, the cfgWrong:=FALSE If you could not write or read data, cfgWrong:=TRUE; This means that either something is wrong with your ADS1115 or you have connected something incorrectly. Question: what voltage do you want to measure?
Last updated: 2024-11-08
Post by kbazzett on "Sequent Microsystems" industrial automation hat raspberry pi
CODESYS Forge
talk
(Post)
Here is a complete list of the Sequent Microsystems Pi hats that work in Codesys. https://github.com/SequentMicrosystems/SM_CODESYS/tree/main/ "For easy install download the .package file and open it on your computer, Codesys installer will know what to do with it." <- This. The Multi I/O Hat fit my needs because of the Analog I/O 4-20ma and RTD. I used a Raspberry Pi 5 and 64b install. The example project is also worth the download. With the sample project open, right click on the Raspberry Pi device and update to whatever you are using (SL, MC, 64b). Enable I2C on the PI. You can jumper the hats Analog Outputs to Inputs and see it function on the Web Visualization. Very Cool! I spent quite a bit of time trying to find this solution so hopefully this update helps others. Here is the video link on how to setup a Raspberry PI as a Codesys PLC https://youtu.be/RPoPscbo3Kc?si=Th4-n-mQ6g5fdHj8
Last updated: 2024-12-05
Post by cihangur on OpC UA server on Raspberry Pi 64 SL runtime
CODESYS Forge
talk
(Post)
Hello everyone, I wanted to write here because it is a similar and the most up-to-date topic. I want to connect to CoDeSys Win V3 x64 - 3.5.19.50 with OPC UA using WinCC Advanced V17. (Or to a PLC with CoDeSys Version 4.10.0.0) My settings are exactly the same as the previous comment. I even tried many different settings. I can access all CoDeSys OPC UA variables via TIA Portal IDE and add them to my HMI tags. When WinCC RT Advanced is started, it gives a warning that the connection could not be established and does not update the variables. I can connect to Inovance AM600 using CoDeSys Target version 3.5.11.50. (The same version Win x64 is also connected.) However, a security setting in the current versions prevents me. I would be very happy if those who have up-to-date experience on this issue and find a solution share it. The CoDeSys Security Settings which I can access variables with TIA Portal: CommunicationPolicy: POLICY_BASICSHA256SHA256 CommunicationMode: ALL Activation: Activated UserAuthentication: ENABLED Server Certificate: Valid until 2034 Greetings.
Last updated: 2024-12-06
Post by latassan on RaspberryPi 5 gateway problem
CODESYS Forge
talk
(Post)
Hello, I'm trying to use a raspberryPi 5 as a PLC. I fixed its IP address, I can ping it. I've also installed the CODESYS Control for Raspberry Pi 64 SL runtime on it. So I've created a gateway (IP address of the Raspberry, TCP port 1217). I see the green dot next to this gateway. When I do a network scan, I can see my raspberry (see photo). When I try to connect to it, I have to define an administrator profile, which I do. On validation, I see a message: No device is responding to the scan request. I've checked that port 1217 is listening on the raspberry, I've uninstalled the runtime then installed it again, but I can't connect. Also, when I try to configure the user groups before connecting, I see that Offline mode is not supported by the device, even though I'm connected to it in the Deploy Control SL tab. When I try to refresh, I see: Gateway not configured properly. How can I connect to my Raspberry? Have I defined my gateway incorrectly?
Last updated: 2025-06-12
Post by dhumphries on Minimum system requirements for codesys control standard S
CODESYS Forge
talk
(Post)
I'm working on a low cost project and I'm considering installing the Codesys runtime on a PC running Linux Debian instead of buying a PLC with a pre-installed runtime. For my needs the Control Standard S license should be capable of running some IO over ethernet/ip, and a webvisu. The PC I am considering has a AMD GX-424CC 2.4GHz processor (4 core/4 thread) and 4GB RAM. This may compare to a raspberry pi4, but I know an X86 processor doesn't directly compare to an ARM processor, and a processor can have a high clock speed but other factors like L2/L3 cache can influence the overall performance. I can't find any published specs for the processor and RAM requirements to run the Codesys Control runtime, does anybody have a link to the minimum system requirements or experience using devices that are at or below the minimum system requirements. A raspberry pi with the control for raspberry pi SL runtime license would be the lowest cost option, but the license is not for commerical use. This restriction is somewhat vague, can anybody clarify if this means I can use a raspberry Pi runtime for in-house automation, what about if I am selling an integrated system that uses a raspberry Pi as a controller?
Last updated: 2023-12-25
Post by timvh on Toradex and CODESYS and licensing
CODESYS Forge
talk
(Post)
For the Virtual Control you need to use a "Network license". The Virtual Control has parameters of which one is the reference to the license server. This can be the device itself, but you need to activate the license on the host system (not in the container). For this, CODESYS has a Network License server with WBM (web based management). See for the Network License configuration: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_license_controller_linux.html If it is only for evaluation, I would advise to use a CODESYS (USB) key and activate the license on the key. Then you still have to install the CODESYS Network License server on the host, but you don't have to activate the license as soft license on the device. The benefit is that you can easily move your license to another device when needed. Off course your device must have a free USB port available to be able to do this.
Last updated: 2025-10-20
Post by konstantin on CAM Motion Recover after STO
CODESYS Forge
talk
(Post)
Hello Mr. Seidel, both the master and the slave axis are modulo. Basically the situation is as follows: One master cycle is 100 units. Slave's modulo length is 2000 units. In the CAM table I defined 10 master cycles on X axis - 1000 units and on the Y axis is the slave - 2000 units. Then depending on the master position 0 to 1000 units the slave's position is plotted on the Y axis - 0 to 2000 units. For example, while the master is executing the 3rd cycle i.e. above 200 units, I trigger the STO function of the slave and it stops. The master executed his cycle but the slave was stopped during the execution. How can I set the slave to continue the CAM sequence from the point where it stopped i.e. third cycle of the master? When I reset the slave error and sync again, everyrhing starts from master's 0 position. Best Regards Konstantin Kolev
Last updated: 2026-02-13
Post by kunal-pinetics on USB Communication for IP Configuration & Application Update – STM32H Series PLC
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on a PLC device based on the STM32H series MCU, running CODESYS. At the moment, I can: Change the Ethernet IP address Update/download the PLC application via Ethernet without any issues. However, I would like to implement the same functionality over USB (or Serial via USB) instead of Ethernet. My goals are: Change the device’s Ethernet IP address via USB Download/update the PLC application via USB communication Possibly use USB as a service/programming interface The hardware platform is based on STM32H series, and I am looking for guidance on: Whether CODESYS supports USB device communication for runtime download If a custom USB CDC (Virtual COM Port) implementation is required Whether a specific CODESYS runtime configuration is needed If a bootloader approach is recommended for application updates via USB If anyone has experience implementing USB communication for runtime download or device configuration on an STM32-based PLC, I would really appreciate your guidance. Thank you in advance for your help.
Last updated: 2026-02-26
Post by timvh on USB Game Controller with Raspberry Pi
CODESYS Forge
talk
(Post)
I'm not sure it will work, but you could try it with the CmpCharDevice library. You could create a function block that looks something like this: As input for the filename, you have to use your Linux device, e.g.: '/dev/input/event0' '/dev/input/by-path/platform-button@23-event' Off course you must also pass the pointer to the memory where the data can be written to and the size (count in number of bytes) of the buffer. FUNCTION_BLOCK FB_CharDevice VAR_INPUT szFilename: STRING; pbyBuffer : POINTER TO BYTE; udCount : UDINT; END_VAR VAR_OUTPUT iState : INT := 0; nrBytesRead : DINT; END_VAR VAR xInit : BOOL := TRUE; dFlags: DINT := CmpCharDevice.ACCESS_MODE.O_RDONLY + DINT#4000; // see details for flags: http://linux.die.net/man/2/open, + DINT#4000 is for non-blocking hDevice: CmpCharDevice.CmpCharDevice_Implementation.RTS_IEC_HANDLE := -1; Result : CmpCharDevice.CmpCharDevice_Implementation.RTS_IEC_RESULT; END_VAR IF xInit THEN hDevice := CmpCharDevice.CDOpen(szFilename, dFlags ,Result); // if it would not succeed, the result is -1 (Invalid handle) IF hDevice <> 16#FFFFFFFF AND Result = 0 THEN iState := 5; END_IF xInit := FALSE; END_IF IF iState = 5 THEN nrBytesRead := CmpCharDevice.CDRead(hDevice, pbyBuffer, udCount, Result); ELSE nrBytesRead := 0; END_IF Make sure you close the connection properly, maybe by overwriting the default FB_Exit method of the FB: // Clean up device IF hDevice <> 16#FFFFFFFF THEN __TRY CmpCharDevice.CDClose(hDevice,Result); __CATCH ; __ENDTRY iState := 0; END_IF
Last updated: 2026-05-01
Post by raghusingh77 on $100 off Temu Coupon Code ACU934948 for new and existing customers
CODESYS Forge
talk
(Post)
The Temu coupon code ACU934948 provides a variety of discounts for both new and existing users in October 2024. Here’s a breakdown of the offers available: Flat $100 Off: New users can redeem a flat $100 discount on orders over $100 by using the code ACU934948 at checkout. 30% Additional Discount: This coupon also grants an extra 30% off on select items, making it an attractive deal for shoppers. New User Discounts: First-time users can enjoy savings of up to 75% off their initial purchase when applying the coupon. 30% Off Temu Coupons, Promo Codes + 25% Cash Back [ACU934948] Redeem Temu Coupon Code [ACU934948]. TEMU COUPON $100 OFF [ACU934948] TEMU COUPON $100 OFF FOR EXISTING CUSTOMERS [ACU934948] TEMU COUPON $100 OFF FIRST ORDER [ACU934948] TEMU COUPON $100 OFF REDDIT [ACU934948] TEMU COUPON $100 OFF FOR EXISTING CUSTOMERS REDDIT [ACU934948] TEMU COUPON $100 OFF NEW USER [ACU934948] TEMU COUPON $100 OFF FOR EXISTING CUSTOMERS 2024 [ACU934948] TEMU COUPON $100 OFF CODE [ACU934948] TEMU COUPON $100 OFF FIRST ORDER FREE SHIPPING [ACU934948] TEMU COUPON $100 OFF FOR EXISTING CUSTOMERS FREE SHIPPING USA [ACU934948] TEMU COUPON $100 OFF HOW DOES IT WORK [ACU934948] TEMU COUPON $100 OFF FOR EXISTING CUSTOMERS CANADA [ACU934948] TEMU COUPON $100 OFF 2024 [ACU934948] TEMU COUPON $100 OFF FOR NEW CUSTOMERS [ACU934948] TEMU COUPON $100 OFF CANADA [ACU934948] TEMU COUPON $100 OFF FOR EXISTING CUSTOMERS FIRST ORDER [ACU934948] TEMU 100 OFF COUPON BUNDLE [ACU934948] 100 COUPON CODES [ACU934948] 1 BUCKS TO PHP [ACU934948] IS THERE A COUPON IN THE PHILIPPINES [ACU934948] 100 BUCKS TO PHP [ACU934948] TEMU $100 OFF COUPON [ACU934948] TEMU $100 OFF CODE [ACU934948] TEMU 100 VALUE COUPON BUNDLE [ACU934948] TEMU COUPON $100 OFF FOR EXISTING CUSTOMERS FREE SHIPPING [ACU934948] TEMU 100 OFF COUPON CODE LEGIT [ACU934948] TEMU 100 OFF COUPON CODE REDDIT [ACU934948] TEMU 100 OFF COUPON CODE FOR EXISTING USERS [ACU934948] TEMU 100 OFF COUPON CODE UK [ACU934948] TEMU COUPON CODE $100 OFF FREE SHIPPING [ACU934948] TEMU COUPON CODES 100 PERCENT OFF [ACU934948] WHAT IS A HIGH COUPON RATE [ACU934948] HOW TO CALCULATE COUPON RATE WITHOUT COUPON PAYMENT [ACU934948] WHAT IS THE COUPON RATE [ACU934948] HOW TO CALCULATE COUPON VALUE [ACU934948] USING COUPONS AND REBATES TO LOWER THE PRICE OF AN ITEM IS AN EXAMPLE OF [ACU934948] TEMU 100 DOLLAR OFF COUPON [ACU934948] DOMINOS COUPON CODE 100 OFF [ACU934948] DOMINO'S 100 RS OFF COUPON CODE [ACU934948] TEMU COUPON $100 OFF EXISTING CUSTOMERS [ACU934948] WHAT IS 10 OFF 100 DOLLARS [ACU934948] 100 OFF PROMO CODE [ACU934948] 1 CASHBACK ON 100 DOLLARS [ACU934948] IS TEMU 100 OFF COUPON LEGIT [ACU934948] TEMU COUPON $100 OFF [ACU934948] TEMU COUPON $100 OFF LEGIT [ACU934948] Temu Coupon Code $100 OFF [ACU934948] Potential for Up to 90% Off: Some promotions indicate that new users might save as much as 90% off on certain items, depending on the selection. Rewards Program for Existing Customers: Existing users can take advantage of the Temu Rewards Program, which may include additional discounts and cash-back offers when using the coupon code. Bundle Offers: The coupon may also be part of bundle deals that provide further discounts, such as up to 70% off on specific products. This combination of offers makes Temu an appealing choice for both new and returning customers looking to maximize their savings.
Last updated: 2024-10-26
Post by smeitink on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
Hi all, I'm looking for help with an issue I've come across while trying to facilitate Modbus communication between a WAGO PFC200 PLC using a 750-652 communication module and an iEM2050 Series Single Phase Energy Meter. I believe to have everything wired and setup correcty, but I keep running into a "Error time out" message, and by now I don't really know what else to try. My setup is as follows: A PFC200 Wago PLC, which has 2 750-652 Serial Interfaces extension modules connected to its field bus. I'm using one of these to talk to a Schneider iEM2050 - kWh-meter over modbus. I have connected terminal 23 (A) of the iEM2050 to connector 6 (A) on the 750-652. I have connected terminal 24 (B) of the iEM2050 to connector 2 (B) of the 750-652. I'm using 200mm of twisted together wires to connected them both, and I have placed a 120 ohm resistor between A and B at both ends. I've attached relevant pinout images to this post. I then wrote a simple program that configures the Mobus port, as per the datasheet of the iEM2050. You can find an image of the relavent page attached to this post too. This is my program: PROGRAM PLC_PRG VAR Master: FbMbMasterSerial; xIsConnected: BOOL; xError: BOOL; iIndex: INT := 1; xTrigger: BOOL; utQuery : typMbQuery := ( bUnitId := 1, // The Modbus unit or slave address bFunctionCode := 4, // Function code for reading input registers uiReadAddress := 1829, // adress for the Power on off counter uiReadQuantity := 1 // Quantity of registers to read ); iStep: INT; oStatusModbus: WagoSysErrorBase.FbResult; utResponseModbus: typMbResponse; xConnect: BOOL := FALSE; delayTimer: TON; END_VAR Master( xConnect:= xConnect, I_Port:= _750_652_24_1, udiBaudrate:= 9600, usiDataBits:= 8, eParity:= WagoTypesCom.eTTYParity.Even, eStopBits:= WagoTypesCom.eTTYStopBits.One, eHandshake:= WagoTypesCom.eTTYHandshake.None, ePhysical:= WagoTypesCom.eTTYPhysicalLayer.RS485_HalfDuplex, xIsConnected=> xIsConnected, xError=> xError, oStatus=> oStatusModbus, eFrameType:= WagoAppPlcModbus.eMbFrameType.RTU, tTimeOut:= T#5S, utQuery:= utQuery, xTrigger:= xTrigger, utResponse:= utResponseModbus); delayTimer(IN := TRUE, PT := T#3S); // Use the Q output of the timer to set xConnect after the delay IF delayTimer.Q THEN xConnect := TRUE; END_IF CASE iStep OF 0: //Wacht totdat de master de poort geopend heeft IF xIsConnected THEN iStep := 1; END_IF 1: //Stuur request naar de slave xTrigger := TRUE; iStep := 2; 2: //Wacht totdat de master klaar is met het afhandelen van de request IF NOT xTrigger THEN iStep := 3; END_IF END_CASE The TON delay before opening the port is due to a an error I encountered when opening it straight away. This seems to be a bug, as described here. However, the TON solved that particular issue. I tried reading multiple registers, but like I said, I still always end up with the "Error time out". What else can I test or try at this point?
Last updated: 2024-02-24
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
I'm getting closer to the error. The combination of STRUCT and ARRAY probably causes the strange behavior. As soon as the ARRAY is followed by a variable, the problem arises. Examples: X: ARRAY[1..2] OF INT; // okay Y: ARRAY[1..2] OF STRUCT; // problem Z: STRUCT; Z.ArrayOfInt[1]; // okay Z.ArrayOfStruct[1].Variable // problem // *update - array of array also causes the error A: ARRAY[1..2] OF ARRAY[1..4] OF BOOL; // problem I can't be the only one who has this problem. Or? Maybe there is a solution. Anyone? Or is it a bug after all?
Last updated: 2023-11-17
Post by trusty-squire on parker servo and position
CODESYS Forge
talk
(Post)
@gepert, When you say "I do not turn off power", are you saying you don't power off the drive, or you don't turn of the MC_POWER function block? I read your statement as you don't kill actual electrical power. MC_POWER should stay enabled. @Gustavo, not related to problem at all, but when you say 1.6 Nm is only enough torque to unscrew a loose bottle cap, I think that's a bit low. A quick mental math I use is 1 Nm is almost the same force as 1kG applied to a 10cm wrench. So 1.6kG applied to a 10cm wrench is still not a huge force, but more than enough to be felt if trying to turn the shaft by hand.
Last updated: 2024-08-06
Post by cihangur on OpC UA server on Raspberry Pi 64 SL runtime
CODESYS Forge
talk
(Post)
After my tests, I noticed two issues. 1- WinCC disconnects the connection after receiving the GetEndPointResponse message from CoDeSys. (I found it with UAExpert and Wireshark.) 2- It establishes a connection despite waiting for a while on the network with DNS. As a result of this information: I solved the problem by adding the line "193.193.193.150 t9pac" to the C:\Windows\System32\Drivers\etc\hosts file and making Windows accept messages coming from the IP number 193.193.193.150 as coming from t9pac. (t9pac is the name of my PLC running CoDeSys.) If there is a setting that will allow CoDeSys OPC UA to respond to GetEndPointRequest with its IP address, this problem will not occur.
Last updated: 2024-12-12
Post by pernockham on Slider instance value when accessed through "execute ST-code"
CODESYS Forge
talk
(Post)
I have a time which I want to modify with a slider. I have confirmed it is possible to set the value of the slider by to_real(time) (I can see that the slider changes according to 'my_time_value's value). Slider variable: to_real(my_time_value); However I fail to access the current slider instance value when I want to write back the value as time (write to a variable will not work as I need a type-conversion before assignment). my_time_value := to_time(slider-instance-value); I tried with this^.? but could not see anything interesting and also THIS^.GEN_Instance.? but nothing resemble what could be the sliders value. Anyone that knows? Thanks!
Last updated: 2025-02-06
Post by pernockham on Inheritence of struct,
CODESYS Forge
talk
(Post)
Apparently my construction will not work as any of the sub-types are not be able to accept any (further) value-initiation. Ie: string_item : log_data_base := (string_value := 'test', val_type := STRING_); is not eq to (the string_value will not be assigned): string_item_2 : log_data_string := (string_value := 'test'); Because effectively for the compiler this is eq. to a "double" assignment where the compiler sees only the first assignment (my guess). string_item_2 : log_data_base := (val_type := STRING_) := (string_value := 'test'); Im not sure this should be treated as a bug, but it would surely be nice to be able to use this construction (compiler is 3.5.20.40). Anyone see any other alternative for solution (other than 4 complete STRUCTS with all fields individually defined)?
Last updated: 2025-03-07
Post by mark on IO link on IFM AL133x only single digital input on a channel
CODESYS Forge
talk
(Post)
I have a problem with the CODESYS IO-Link SL software. When I insert a IO link master AL1332 and plug a discrete digital input to a channel it reads only 1 of the 2 available inputs on that channel. Is there anyone who sorted out if the second input is also usable? When we configure the module without the CODESYS IO-Link SL software then the second input on the channel can be used. At the moment we use some channels on a module as IO-link port, and some as discrete IO. It would be very nice if we can use both inputs on a channel with the use of CODESYS IO-Link SL.
Last updated: 2023-12-18
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
Hello, according to Codesys, the problem should be solved with version 4.3.0.0. After the update to version 4.3.0.0 I had the problem that the recipes weren’t saved correctly, but loading was okay. Return to the version 4.2.0.0 didn’t change the behavior. Strange… So I uninstalled the update, cleaned the project and built it new. The known behavior of version 4.2.0.0 was back. Update to version 4.3.0.0, clean and build it new, it works. Even with version 4.2.0.0. Strange, but okay. Notice: ManCommands.LoadRecipe() no longer writes into the PLC. Just as it should be. As of now, I can use the new version.