Post by vipul on Multicast udp
CODESYS Forge
talk
(Post)
Hi, Good afternoon can anybody help me with UDP Multicast code. I am not able to send or recieve data when code is dumped on linux device. Below is my code. Declaration: PROGRAM udp_multicast VAR oneTimeFlag :UINT :=0; state: INT:=0; driver: UDP.UDPDriver; //port : UDP.Port;//moved to GVL src_ipAddr_ud: UDINT; src_ipAddr_st:STRING := '192.168.127.155';//'192.168.1.155';//ipms ip address dst_ipAddr_ud:UDINT; group_ipAddr_st:STRING := '239.1.5.10'; //group_ipAddr_ud:UDINT; result: SysTypes.RTS_IEC_RESULT; //result of recieve function. bind: UDINT; //result of binding. resultCreate:SysTypes.RTS_IEC_RESULT;//result of port creation. timer:BLINK; temFlag :INT:= 0; post:INT :=0; checksumFunc:checksumXor; localStringBuf:STRING[500]; chksum:BYTE; dataBuffer:POINTER TO BYTE; checksumString:ARRAY[0..5] OF BYTE; recvSize:__XINT; errorCode:UDINT; joinGroupErrorCode:UDINT; END_VAR ************8 Implementation: IF oneTimeFlag <> 1 THEN oneTimeFlag:=1; resultCreate := driver.CreatePort(ADR(GVL.port)); src_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIPAddress:= src_ipAddr_st); GVL.group_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIpAddress:= group_ipAddr_st); GVL.port.IPAddress := src_ipAddr_ud; GVl.port.ReceivePort:= GVL.src_port;//port on which messages are expected. GVl.port.SendPort := GVL.dest_port; GVl.port.OperatingSystem := 0; //0- any system GVL.port.Socket :=3; //3- socket type is multicast bind := GVL.port.Bind(udiIPAddress:=src_ipAddr_ud,); GVl.port.JoinGroup(udiGroupAddress:= GVL.group_ipAddr_ud,udiInterfaceAddress:= src_ipAddr_ud,eLogCode=>joinGroupErrorCode); END_IF timer(ENABLE:=TRUE,TIMELOW:=T#100MS,TIMEHIGH:=T#100MS); IF timer.OUT = TRUE THEN GVL.port.Send(udiIPTo:=GVL.group_ipAddr_ud,GVL.dest_port,pbyData:=ADR(GVL.writeData),diDataSize:=SIZEOF(GVL.writeData)); ELSE SysMemSet(ADR(GVL.readData[0]),0,SIZEOF(GVL.readData)); result := GVl.port.Receive(ADR(GVL.readData),diDataSize:=SIZEOF(GVL.readData),udiIPFrom=>dst_ipAddr_ud,diRecvSize=>recvSize,eLogCode=>errorCode); SysMemMove(ADR(GVL.readDataBuf[0]),ADR(GVL.readData[0]),SIZEOF(GVL.readData)); END_IF post:=LEN(GVL.readDataBuf);
Last updated: 2024-01-14
Post by alexgooi on Codesys OPC DA server requires more then 2 GB of ram
CODESYS Forge
talk
(Post)
Dear Forum, We are currently running into a problem that the CODESYS OPC DA server is running out of RAM (larger than 2 GB). We have a setup of 10 Codesys controllers which features around 300.000 discoverable tags per controller. We are only interested in 10 percent of the tags to be communicated to the OPC-server, this is due to the fact the program consists of arrays of objects which on their part implements arrays of objects, simply reducing the number of discoverable tags is not an option The OPC-DA server loads all the discoverable tags, is it possible to: 1 let the OPC-DA server only load the tags that are requested by the SCADA/MES system. 2 let the OPC-DA server claim more memory. 3 run 2 OPC-DA servers in parallel? Thank you in advance
Last updated: 2024-01-25
Post by axilleas on SMC_Interpolator + SMC_controAxislbyPos
CODESYS Forge
talk
(Post)
dear all I am working on a very generic gantry system (virtual drives + win v3 control) reading gcode from external file. In order to stop the interpolator function from running when gaps are detected, SMC_controlAxisByPos FB has the bStopIpo output which according to the manual is connected to the Interpolator's bEmergencyStop. Lets assume that the axis are parked in position X1000 Y1000 and the initial G code movement is G00 X500 Y500. The normal behavior is to travel from the actual x1000 y1000 to G00 X500 Y500. The SMC_Interpolator always gets the X0 Y0 as the initial position, meaning that the bStopIpo is active until the axis are in X0 Y0 and the release the interpolator to set the new positions to X500 Y500. Is there a suggested method to solve this behavior? bonus question: I get a lot of bStopIpo during standard interpolation movements (not gaps). While working with virtual axis this is not a problem but when real axis are installed this will be an issue. What exactly triggers the bStopIpo output? Slow axis accelerations compare to Gcode defaults? Kind Regards
Last updated: 2024-02-05
Post by fredsta on Unable to load dynamic modules (Download failed: Application=Application)
CODESYS Forge
talk
(Post)
Hey there, I am currently trying to find a good solution for the communication between CODESYS Control on Raspberry Pi and "the rest of the world", i. e. the things apart from CODESYS on my linux. My first approach was to use the c-integration. So I created a lib, defined extern fbs, compiled the code on my Pi using the SDK and put the .so into my lib project. When I try to log into the Pi and load the program, I get the error message which you can see in the attached picture. "Die dynamischen Module der C-Integration konnten nicht auf das Laufzeitsystem geladen werden" is german and means roughly "the modules from the c-integration could not be loaded onto the runtime system." Is this normal? Am I doing something wrong? I will have a look at the unix domain socket thing next, as I am still in the process of finding the best solution for the communication.
Last updated: 2024-02-15
Post by alex00 on DCS / Central Engineering with Codesys support
CODESYS Forge
talk
(Post)
Hello together I'm currently investing in possibilities to have a central engineering software / system for Codesys based controllers. Something like a DCS / SCADA depending on where you see the functionality. We plan to use more or less vanilla codesys. The tool should support the following: - Connect to multiple PLC's in a project to see its variables and debug it. - Central Engineering capabilities (for example shared libraries in a project). - Download the new code / binaries to the plc. - Maybe have functionality to combine visualization elements and logic together. - See the live status variables on all the systems (crosscommunication). I see that codesys theoretically supports engineering of multiple PLC's, but I couldnt find to much functionality for a DCS type of operation, but that could be lack of knowledge. Any tips from you? Is Codesys good enough for this and maybe there are some manufacturers which build around it? Or are there good tools on the market with Codesys support (and the engineering is separate, but download to codesys possible). The use case is distributed energy installations like Heating pumps, Photovoltaics, etc. All these installations should have a PLC with codesys installed and run in one larger network, the PLC's are connected via VPN. Thanks for your inputs Greetings
Last updated: 2024-02-19
Post by alex00 on DCS / Central Engineering for Codesys
CODESYS Forge
talk
(Post)
Hello together I'm currently investing in possibilities to have a central engineering software / system for Codesys based controllers. Something like a DCS / SCADA depending on where you see the functionality. We plan to use more or less vanilla codesys. The tool should support the following: - Connect to multiple PLC's in a project to see its variables and debug it. - Central Engineering capabilities (for example shared libraries in a project). - Download the new code / binaries to the plc. - Maybe have functionality to combine visualization elements and logic together. - See the live status variables on all the systems (crosscommunication). I see that codesys theoretically supports engineering of multiple PLC's, but I couldnt find to much functionality for a DCS type of operation, but that could be lack of knowledge. Any tips from you? Is Codesys good enough for this and maybe there are some manufacturers which build around it? Or are there good tools on the market with Codesys support (and the engineering is separate, but download to codesys possible). The use case is distributed energy installations like Heating pumps, Photovoltaics, etc. All these installations should have a PLC with codesys installed and run in one larger network, the PLC's are connected via VPN. Thanks for your inputs Greetings
Last updated: 2024-02-19
Post by brell on Automatic xExecute NBS.TCP_write
CODESYS Forge
talk
(Post)
I've recently started experimenting with CODESYS for a project and am fairly new to it. I'm currently working with Function Block Diagrams (FBD) to set up TCP communication between a server and a client, where the client is implemented as a Python script. Once the communication is established, my connection status changes to True, which is the expected behavior. My challenge arises with the TCP write module, which requires the xEnable_write flag to toggle between True and False. If xEnable_write remains True, the module only performs a single write operation. To address this, I introduced a falling edge trigger (F_TRIG), expecting it to help in toggling xEnable_write and it does, However, I've encountered an issue where in the beginning after connxion established I need to manually set xEnable_write to True for the system to work as intended. I'm looking for a way to automate this process so that xEnable_write becomes True automatically upon establishing a connection . Initially, I tried setting xEnable_write to True from the start, but this approach didn't work well since it left the flag permanently True, preventing further toggling. I also experimented with using a TON timer, but I faced similar issues. I am seeking a solution that automatically toggles xEnable_write between True and False after a connection is established, ensuring continuous write operations without manual intervention. Any advice or guidance on how to achieve this would be greatly appreciated."
Last updated: 2024-03-05
Post by manuknecht on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hello all I am using an AxisGroup with the Gantry2 Kinematics to move a 2D-Gantry system. When creating the AxisGroup, the SoftMotion_PlanningTask is created automatically with a cycle time of 2 ms in my case. I realized that the maximum cycle time of this task can spike to very high values (up to 60 ms) at lower speeds of the motion, leading to synchronization issues and errors on the axes. The same behaviour - though not as drastic - can be observed with virtual axes too. Is this behaviour intended or to be expected? Can the cycle time or type of the SoftMotion_PlanningTask be changed to prevent these errors? Or is there another fix for this issue? I tried changing the cycle type to Freewheeling, which solved the synchronization issues, but caused an error on the AxisGroup after a while, reading SMC_CP_QUEUE_UNDERRUN. Thanks in advance and best regards Manuel
Last updated: 2024-03-07
Post by acc00 on Main Task cycle too long leading to PLC Fail
CODESYS Forge
talk
(Post)
I have 2 Wago PFC200 PLC, running with Runtime SP19 Patch 5, with the Redundant application. The PLC communicates as Modbus Master with at this moment 15 Modbus Slaves -later there will be 28 in total- (Drives, Power management units,...). These devices are connected in 2 rings (1 ring of Drives, 1 ring of Power Management units), with 2 Managed Moxa Switches being part of the ring. Each PLC is connected to one of these switches. The issue I'm encountering is that the Cycle time of the Active PLC goes very high when I'm closing the Drive ring (simulating an issue on one Cabinet supply, resulting in that one Drive shut down, which can happen on field quite often). As a result of this long cycle, the PLC fails and goes to Exception, and the Passive PLC does not take control of the system. A normal cycle is around 30ms for the Main task, and a few ms for the Ethercat task. When I monitor with Profiler, I see that in this Maximum Cycle, the main Task is only taking 13ms, so I'm not sure where the PLC is hanging for so long. Is the remaining cycle time the Redundant management/sync or something else? Thank you in advance.
Last updated: 2024-03-08
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via CmpApp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by danieldiaz on Problem with FB execution
CODESYS Forge
talk
(Post)
Hello everyone, I've been working on a system which needs an error function, with this purpose I've created a FB programmed in LD, after debugging I run the simulation. It seems that the variable linked to a coil doesn't change the value when the contacts are associated to input variables. When I use internal variables the logic works properly. I don't know if the problem is related to the variables definition or with the logic program. As you can see in the image, I1 and I2 are variables declared on the FB, the rest are input variables. If I force the eStop and Reset signals to TRUE the coil value should change, but it doesn't. However in the second network if I1 is TRUE the coil change to TRUE as it has to be. To sum up, my doubt is why that coil doesn't change its value? I would like someone to shed a light on this. Thanks!
Last updated: 2024-04-02
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
Hi Duvan, You could make this in 1 single object (FB), Indeed don't use a function for this beacuse you need some memory to keep the old value. For i := 0 TO 200 BY 1 DO //Check if the value has been changed IF Old_Value[i] <> Value[i] THEN //Set the trigger to TRUE Trigger[i] := TRUE; Old_Value[i] := Value[i]; END_IF END_FOR If you define the Value array as an In_Out and the Trigger as an In_Out you arn't claiming any aditional memory to your system. You ofcourse then need to add some code arround it that does something with the trigger and writes it back to FALSE again. If you want more flexability you also could use pointers instead of using the IN_OUT FOR i := 0 TO 200 BY 1 DO address := address_Input + i * SIZEOF(*Put type here); IF Address^ <> Old_Value[i] THEN Trigger[i] := TRUE; Old_Value[i] := Address^; END_IF END_FOR
Last updated: 2024-04-02
Post by rmaas on Fieldbus has lost synchronicity
CODESYS Forge
talk
(Post)
Hi, On a gantry system with 2 axis i am getting the following error: SMC_DI_FIELDBUS_LOST_SYNCRONICITY This happens random, sometimes it happens every 5 minutes and sometimes no error for 2 hours... The Setup: - Using codesys 3.5 SP20 with all latest libs... - Kontron AL Pi-Tron CM4 with Preempt realtime patch (Raspberry Pi 4) - Codesys runtime 4.11.0.0 (single core) - CODESYS Control for Raspberry Pi SL licensed - Softmotion + CNC + Robotics licensed - 2x Leadshine EL8-EC400 servo drives - Axis group for a 2-axis T-Gantry Ethercat network wiring: Ethercat master softmotion -> Beckhoff EK1100 -> Servo drive #1 -> Servo drive #2 Ethercat Cycle time = 4ms Max Jitter = 140~150 What i have tried so far: - changed the sync offset from 20% to 30% - changed ethercat task priority from 1 to 0 Running tasks: - Ethercat tast: Prio = 0, Interval = 4ms - Main task: Prio = 1, Interval = 8ms - Visu task: Prio = 31, Interval = 100ms - Softmotion planning task: Prio = 15, Freewheeling - 3 other default tasks that were created by AC_Persist Motion fb's are called in the ethercat task... Does anyone have an idea how to fix this? Any help is greatly appreciated!
Last updated: 2024-04-11
Post by leafy on Use third party actuator with IO-Link Master (IFM)
CODESYS Forge
talk
(Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16
Post by leafy on Use third party actuator with IO-Link Master (IFM)
CODESYS Forge
talk
(Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16
Post by fontrap on cmDongle Raspberry Pi issue
CODESYS Forge
talk
(Post)
Hello mates, I'm working with CODESYS V3.5 SP20 on a Raspberry Pi and I use "Raspberry Pi MC SL" as device on the project. I've installed the Control Standard L (multicore) license on a Wibu System usb-Dongle (cmStick/4.50) that already had another license from another vendor. I follow the online activation procedure from CODESYS documentation. Raspberry Pi has already CodeMeter installed for the other license. When I plugin the dongle on Raspberry and start the Runtime from Raspberry Pi Update in CODESYS I receive the message that I'm on Demo mode because the license is missing. I double checked that the license is activated in the dongle, through the WebAdmin of CodeMeter and the second license runs properly without any issue. I have already try to change the dongle from HID to MSD device and backward but the the Runtime cannot recognize the Dongle. I have also try to stop and start the Runtime through CODESYS without success. Is there anything else I can do to fix this issue?
Last updated: 2024-04-22
Post by timvh on Toradex and CODESYS and licensing
CODESYS Forge
talk
(Post)
For the Virtual Control you need to use a "Network license". The Virtual Control has parameters of which one is the reference to the license server. This can be the device itself, but you need to activate the license on the host system (not in the container). For this, CODESYS has a Network License server with WBM (web based management). See for the Network License configuration: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_license_controller_linux.html If it is only for evaluation, I would advise to use a CODESYS (USB) key and activate the license on the key. Then you still have to install the CODESYS Network License server on the host, but you don't have to activate the license as soft license on the device. The benefit is that you can easily move your license to another device when needed. Off course your device must have a free USB port available to be able to do this.
Last updated: 2025-10-20
Post by animesh on SoftPLC (CODESYS Control x86 RTE V3 x64) OPC UA binds only to 127.0.0.1 β Not binding to LAN IP
CODESYS Forge
talk
(Post)
Hello everyone, I am facing a persistent issue with the OPC UA Server on Advantech Soft PLC with hard realtime for Win64 (V3_5_2010_3) and need help from the community. Device Information Name: Advantech Control x86 RTE V3 x64 Vendor: Advantech Co., Ltd. Categories: PLCs Version: 3.5.20.10 Description: Advantech Soft PLC with hard realtime for Win64 (V3_5_2010_3) Problem Summary The OPC UA Server works perfectly when accessed via: opc.tcp://localhost:4842 opc.tcp://<hostname>:4842</hostname> But it does NOT work when using the LAN IP: opc.tcp://192.168.0.XX:4842 In UAExpert I get: Discovery FindServers on opc.tcp://192.168.0.XX:4842 failed (BadCommunicationError) Port is LISTENING in windows Firewall.. Tried with turning off the firewall completely. System Information Windows 10 x64 Advantech CODESYS RTE Soft-PLC (hard real-time) Network IP: 192.168.0.XX Hostname: WINDOWS-XXXXX Need your Support
Last updated: 2025-11-24
Post by fredashbolt on Dynamically Update JSON Payload
CODESYS Forge
talk
(Post)
I am trying to generate a JSON payload populated with a value that updates for use with a telemetry system, the payload is to be published by MQTT. I have established the MQTT client and can publish a working JSON payload but I can't get the payload to update as the value (iValue) changes. I am using a timer to trigger the .SetValue function periodically, but the JSON will only give the value as it is when it is first initialized using xFirst IF statement. Any suggestions? Thanks VAR pJsonData : POINTER TO JSON.JSONData := factory.Create(); fb_JBuilder : JSON.JSONBuilder; diRootIndex, diObject1Index : DINT; iValue : INT := 10 ; jsonArrayWriter : JSON.JSONByteArrayWriter; wsJsonData : WSTRING(1000); xFirst : BOOL := TRUE; utf8JsonData : STRING(2000); diTempVal : DINT ; PublishTimer : TON ; END_VAR IF xFirst = TRUE THEN fb_JBuilder ( pJsonData := pJsonData , diRootObj => diRootIndex ) ; diObject1Index := fb_Jbuilder.SetKeyWithObject ( "Device" , diParentIndex := diRootIndex ) ; diTempVal := fb_Jbuilder.SetKeyWithValue ( "Temp" , iValue , diParentIndex := diObject1Index ) ; xFirst := FALSE ; END_IF PublishTimer ( IN := PublishTimer.Q = 0 , PT := T#5S ) ; IF PublishTimer.Q THEN fb_JBuilder.SetValue ( iValue , diTempVal ) ; END_IF jsonArrayWriter( xExecute := PublishTimer.Q , pwData := ADR(wsJsonData), udiSize := SIZEOF(wsJsonData), jsonData := pJsonData^, xAsyncMode := FALSE ) ; JSON.Stu.ConvertUTF16toUTF8( ADR ( wsJsonData ) , ADR ( utf8JsonData ) , SIZEOF ( utf8JsonData ) , bStrictConversion := TRUE ) ;
Last updated: 2026-03-10
Post by pernockham on Gateway in China - "Gateway not connected"
CODESYS Forge
talk
(Post)
Some new test. Now I cannot connect from Automation server to my gateway in any way also from my office setup with my unit directly connected to my router by dhcp. I can use the IDE and the tool "Connect Edge Gateway" and successfully connect to my server/link to my Automation server account. However no PLC will respond from Automation server "Network scan". I guess the traffic should be initiated by the gateway towards automation server? Any tips on how I can diagnose my problem? Ports to be opened etc? Thing is that this has been working previously but not now (base system has been updated from debian 12 to debian 13, but I dont know at which point it has stopped working). Setup as before. A "Codesys Control for Linux SL" running on a debian 13 installation. Any help/tips appreciated! Per Update. Found the error. Had a wrong gateway-setting. Which meant the PLC could not reach internet. Checked by "ping google.com" from the PLC.
Last updated: 2026-02-12
Post by risele on Modbus connection via Qronox PCD3 M6893
CODESYS Forge
talk
(Post)
You are welcome. Also note, that it's valid only if you modbus-device use same real/float value representation (IEEE 754). That's true for most of systems. But some devices may have other representation, such as integer + position of the decimal point, for example 123.456 is integer = 123456 and position = 3 Also note, that, ones again, depending on endianess of each system, you may also need to swap not just words, but bytes. TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; bVal:ARRAY[0..3] OF BYTE; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE than swapping may be something as VAR A,B,C,D:BYTE; //Bytes of the real value uIn, uOut:u_Real; rVal:REAL; ModbusReg1,ModbusReg2:WORD; END_VAR uIn.rVal:=rVal; uOut.A:=uIn.D; uOut.B:=uIn.C; uOut.C:=uIn.B; uOut.D:=uIn.A; ModbusReg1:=uOut.wVal[0]; ModbusReg1:=uOut.wVal[2]; Or you even need to reorder bits... Ones again, sending float/real values is not defined by Modbus protocol itself, so it is hardware- and software-dependent. The Modbus Poll (and most of modbus tools) have configuration parameters that will properly swap bytes on their side. Ones again, that's very helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/
Last updated: 2026-02-19
Post by struccc on Wish: CODESYSControl.cfg - again
CODESYS Forge
talk
(Post)
Before creating this topic, I was browsing the search results for CodesysControl.cfg - many results, and I remember very well, it's a problematic issue for a long time. To summarize: there were many requests for documentation on this file - the most comprehensive reply is: https://forge.codesys.com/forge/talk/Runtime/thread/ebbf851a3d/#eb85 Hi, not really, this is covered by the manual which you get if you use a runtime toolkit which is not free of charge. Maybe we need to extract the config file part from that documentation if that is possible. BR Edwin I am not sure how much is this relevant, since we buy SL License directly from CODESYS... I think it is a reasonable demand, to get documentation on the configuration entries affecting the documented behaviour of the runtime system and it's components The actual reason I bring up this issue again can be read here: https://forge.codesys.com/forge/talk/Runtime/thread/febad3cc40/#0e12 but mostly my frustration about noticing some new, unknown and undocumented entries in my configuration file. Again. And this happens a lot recently. Just some examples: Changes with SysFile - and mandatory use of IEC path Introduction of Mandatory user management File transfer service now disabled by default SysProcess - allowed commands The above mentioned CmpApp parameters... And finally (Regaridng windows install): With the newer versions, the installation directory (together with the configuration file) tends to hide itself to some super silly location under the roaming profile data of local system account. I am not sure if this change was documented somewhere, but was a very unpleasant one. Someone could please explain the reason and the concept of the introduction of this release specific directories (I am sure, there is a good reason) - how to use them properly? - How to re-introduce user configuration (to preserve configuration data between versions)? - How to do version - to version migrations properly? - How to keep old version of runtime available and ready to start with it's original configuration and application? - ... Therefore, the lack a regularly updated description of CodesysControl .cfg , including all the configuration entries, together with their default values for different runtime versions is really a big deficiency.* This should be done for all components storing or just seeking data from this file... (Maybe there is such thing but I failed to find???) It is regularly causing trouble when introducing a new version (together with the long awaited bug fixes and enhancements), what has changed it's default behaviour for security or other practical reasons. I agree this is very important, and it is logical to change the default options: But it must be documented historically, and make it easily available, so we can prepare better for the upgrade of the runtime. Forge talk is a great source, but not very practical for this kind of documentation purposes... Thanks in advance for CODESYS staff πππ (Ps.: It would look rather silly, if some members of the user community prepares this documentation on a Forge Wiki page... Or??? Should we?)
Last updated: 2024-11-21
Post by maldus512 on How to adapt Codesys Control SL to custom board
CODESYS Forge
talk
(Post)
Hello everyone, I have been given the task to develop I/O drivers for a custom made, Linux based board to allow for Codesys applications to run and control the hardware. I have successfully installed Codesys Control SL for ARM/Linux and tested it with a simple demo application. Now I should start interfacing the runtime to the actual hardware; I should be able to interact with 2 RS485 serial ports, a few GPIOs and an I2C port, all of which already have the corresponding /dev/ interface in the Linux system. I am having trouble understanding how it should be approached. I have found sporadic references that fail to lead to a really comprehensive documentation. For example: The store page (https://store.codesys.com/en/codesys-control-for-linux-arm-sl-1.html#options) mentions a "runtime package" that should allow "Integration of existing C code" and "Usage of local I/Os", which seems exactly what I need to interact with custom peripherals. I have found no further reference to Codesys-C interpop. The Codesys Help page for the runtime package has a page on the "Development of Drivers" (https://content.helpme-codesys.com/en/CODESYS%20Control/rtsllinuxrbpdriverdevelopment.html) that suggests to either "Implement a function block" or "Implement I/O drivers". Those in turn lead to this page (https://forge.codesys.com/drv/io-drivers/doc/Generic/) which describes briefly an XML schema to describe new devices; unfortunately, it doesn't mention what to do with such a description (i.e. how does the runtime know about it) or how it is in any way connected to the actual hardware. Could anyone give me some pointers? I should also mention I have no prior experience with Codesys, so maybe I'm missing an obvious answer.
Last updated: 2024-08-09
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.