Post by etalp on Eaton XC303 firmware update via USB
CODESYS Forge
talk
(Post)
Hi, I'm struggling with updating my xc303 to firmware 3.5.17. It is possible only via USB port. I've installed proper update files on the USB then plug it into the PLC's USB port and restarted the device. Shortly after LED's on the PLC started to blink, so updating process has started. But after 10 minutes the PLC LED turned off and after all I could't serach for this PLC in Codesys, but could ping it. Could someone eplain to me proper procedure of updating the fimrware in XC303 via USB? Is it neccesary to STOP the PLC switch after pluging the USB?
Last updated: 2025-10-15
Post by s1mon on Two OneWireMaster on one Raspberry PI 5
CODESYS Forge
talk
(Post)
I don't know why the EtherCat fails, but what happens is: First I have only one 1WireMaster running on my Raspberry Pi and EtherCat is running fine. Then I'd like to add a 2nd 1WireMaster. Therefore I enable a 2nd GPIO Pin on the raspberry in the file "/boot/firmware/config.txt". dtoverlay=w1-gpio,gpiopin=4,pullup=0 dtoverlay=w1-gpio,gpiopin=23,pullup=0 To be able to use this 2nd 1WireMaster in Codesys Runtime I Adjust the CODESYScontrol.cfg file and add there: PlaceholderFilePath.2=/sys/devices/w1_bus_master2, $OneWire2$ After a reboot the EtherCat Master is not working any more. I didn't even add a 2nd OneWire Master in Codesys, but still if I do the EtherCat does not work. Do you have an idea why?
Last updated: 2025-10-21
Post by alimans on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
For anyone still experiencing this issue, here’s how I managed to solve it: Symptoms: 1. Sometimes, on the first start of CODESYS Runtime, the modules fail to run. 2. After disconnecting and reconnecting the communication cable, the drive does not start again. 3. MC_Reset cannot clear the fault. Solution (what worked for me): 1. Check the axis communication using the SMC_CheckAxisCommunication function block (FB). 2. If CheckAxisCommunication.eComState of the axis is equal to or higher than SMC_CommunicationState.SMC_COMSTATE_BASE_COM_INITIALIZATION, then 3. Use the SMC3_ReinitDrive function block to reset the drive — and it works. For more information, refer to the official CODESYS documentation: 👉 https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/DriveInterface/AXIS_REF/SMC3_ReinitDrive.html
Last updated: 2025-10-23
Post by malte on OPC UA multiple Endpoints
CODESYS Forge
talk
(Post)
My CODESYS OPC UA server provides endpoints using both the hostname and the IP address. Connecting via the IP address works fine, but connecting via the hostname does not. The endpoint list shows both opc.tcp://<hostname>:4840 and opc.tcp://<ip>:4840. When using the hostname, the OPC UA client (UA Expert) fails to connect. Using the IP address connects without issues. Main goal is to conect via Python but opcua-asyncio seems to prefer the hostname. How can I configure CODESYS or my system so that the OPC UA connection via hostname also works properly or disable it completly? Running Codesys for PFC200 sl 4.18.0.0
Last updated: 2025-10-28
Post by bitor-leao on *EXCEPTION* [ProsessorLoadWatchdog] codesys 3.5.11.40
CODESYS Forge
talk
(Post)
Good night. I am having a problem with CODESYS 3.5.11.40, which gives the exception EXCEPTION [ProcessorLoadWatchdog]. I followed some forum posts and tried to modify the CODESYSControl.cfg file, but it shows: [SysFile] Windows.WorkingDirectory=C:\ProgramData\CODESYS\CODESYSControlWinV3\D5050FE1 Then I go to this directory and try to modify CODESYSControl.cfg according to the forums, but it doesn’t work: [CmpSchedule] ;EnableLogger=0 ProcessorLoad.Maximum=80 ;Timeslicing.Mode=Internal ;Timeslicing.PlcSlicePercent=80 ;Timeslicing.PlcSliceUs=4000 ;Timeslicing.StartOnProcessorLoad=1 ;SchedulerPriority=5 ;SchedulerInterval=1000 I tried to change ProcessorLoad.Maximum to 0 or 100, but it doesn’t compile when I try. I really don’t know what to do,
Last updated: 2025-11-16
Post by bitor-leao on *EXCEPTION* [ProsessorLoadWatchdog] codesys 3.5.11.40
CODESYS Forge
talk
(Post)
Good night. I am having a problem with CODESYS 3.5.11.40, which gives the exception EXCEPTION [ProcessorLoadWatchdog]. I followed some forum posts and tried to modify the CODESYSControl.cfg file, but it shows: [SysFile] Windows.WorkingDirectory=C:\ProgramData\CODESYS\CODESYSControlWinV3\D5050FE1 Then I go to this directory and try to modify CODESYSControl.cfg according to the forums, but it doesn’t work: [CmpSchedule] ;EnableLogger=0 ProcessorLoad.Maximum=80 ;Timeslicing.Mode=Internal ;Timeslicing.PlcSlicePercent=80 ;Timeslicing.PlcSliceUs=4000 ;Timeslicing.StartOnProcessorLoad=1 ;SchedulerPriority=5 ;SchedulerInterval=1000 I tried to change ProcessorLoad.Maximum to 0 or 100, but it doesn’t compile when I try. I really don’t know what to do,
Last updated: 2025-11-16
Post by davidbo on RETAIN PERSISTENT only stored at gracefully shutdown?
CODESYS Forge
talk
(Post)
I have {attribute 'checksumnoinit_override' := '2629838988'} {attribute 'init_related_code' := '5c6efcf8-e0f4-4166-a9fa-17eadd8908df'} VAR_GLOBAL RETAIN PERSISTENT {attribute 'order_in_persistent_editor' := '0'} segmentValue: ARRAY[0..49] OF REAL; {attribute 'order_in_persistent_editor' := '1'} segmentTime: ARRAY[0..49] OF REAL; // Generated instance path of persistent variable PRG.test: INT; // Generated instance path of persistent variable PRG.nw_storage: SysSocket_Implementation.SysSocket_Interfaces.SOCK_ADAPTER_INFORMATION2; END_VAR When I have changed PRG.nw_storage it will not be stored at a power off, but if I do a: sudo systemctl restart codesycontrol and then a power off it will be stored. Is there a way to store persistent variables without a restart of codesyscontrol? Can anyone explain how and when CODESYS store persistent variables?
Last updated: 2025-11-17
Post by mr-ege on Error: C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr
CODESYS Forge
talk
(Post)
Hi all! I'm trying to learn PLC Programing. Today I was making a simple PLC program, as you can see. When I compile the program without the visualization, there are no errors. However, when I add the visualization and then compile it, I get this error. I don’t know how to solve the problem. I have tried the following solutions: rebooting the PC and updating the software. Error Code: C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr Compile complete -- 1 errors, 0 warnings Build complete -- 1 errors, 0 warnings : No download possible Version: CODESYS V3.5 SP21 Patch 3
Last updated: 2025-11-25
Post by gseidel on Can't get SMC_SmoothPath to work
CODESYS Forge
talk
(Post)
Hi bertus, I cannot see any problem in the code you posted. Just some ideas: What is the value of D_ANGLE_TOL? - Do you need the assignment bAbort := NOT bDecoder? Does it help to leave it out? Any errors (e.g. SMC_SmoothPath.Error/ErrorID) or PLC log messages? What if you comment out SMC_SmoothMerge and SMC_LimtiDynamics, is corner smoothing still not working? Is bDecode written from a different task (e.g. visu)? Then I would recommend to assign to a local variable (bDecodeLocal := bDecode) and use that for all FBs. Otherwise, FBs might see different values of bDecode in a single cycle, which will cause problems. Regards, Georg
Last updated: 2025-12-17
Post by mait-tim on Drive communication errors
CODESYS Forge
talk
(Post)
With a machine I'm working with i get a communication error when I'm updating some softstop limits. As soon as I update the code the drives do not want to operate. Using the MC_readStatus I'm receiving errors as soon as i want to start a movement. Using MC_ReadAxisError i see that i receive error 131, no response. With a SMC3_ETC_ReadParameter_CoE i do not recieve any driver errors. Does anyone know how i can figure out what the error is and how to solve it. When i go back to the old software no errors occur. Im working with a legacy machine running a Beijer PLC with some Mitsubishi drives. running on Codesys 3.5 SP10. the runtime version is probably 3.5.3. The drives are all Ethercat Drives (CoE). All using the SM3_drive_ETC libary and the SM3_basic library.
Last updated: 2025-12-22
Post by timvh on Codesys complains about matching versions
CODESYS Forge
talk
(Post)
Open the CODESYS Installer. Create an export file from your current PC from your current version. Then on the other PC Open the installer and install a new version based on the same essentials version, but additionally select the export file which you have created on the first PC. Or just install (import) it within the already existing version. For the installer, you can install it from: https://store.codesys.com/en/codesys-installer.html For help see: https://content.helpme-codesys.com/en/CODESYS%20Installer/_inst_install_setups_and_addons.html On PC 1, save the project as projectarchive (which will then include all the libraries and devices). Then extract this projectarchive on PC 2.
Last updated: 2025-12-15
Post by fless on No source code available for profinet library
CODESYS Forge
talk
(Post)
looks like you are running in a bug in the newest version 4.4.0 of the profinet library or the new library triggers a bug in your code. did you update your profinet device too? you could try to downgrade to an older version of the library. via library manager - placeholders, double click Profinet 4.4.0 in the library column and choose an older version.
Last updated: 2023-08-23
Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
Ohhh OK. Yeah this seems to be timing like you said. Yeah I read through that document and came to the same conclusion. I haven't tried setting them both to 200ms. Maybe I'll give it a shot. Thanks so much for your input. Its greatly apreciated.
Last updated: 2023-09-06
Post by martinlithlith on Device User Logon and No device is responding.. Pi4b codesys 3.5 SP19 2 + (64-bit)
CODESYS Forge
talk
(Post)
Hi, Thank you for your reply! What should be the version 4.9.0.0? I have a user named pi on the pi, thats what i´m using as credientials to be able to for example update/install runtime. Or do i need another user? once agin, thank for the reply! Martin
Last updated: 2023-09-11
Post by transmin01 on EL6751 Canopen_Manager issue
CODESYS Forge
talk
(Post)
Hi, I have a Beckhoff EL6751 EtherCAT / CANopen gateway which fails on the Canbus when the CANopen_Manager is added. Currently no devices are connected to the EL6751. If I add a device, I get the same issue. If I add a device and connect the bus, I get the same issue. Is there something I am doing wrong? Regards Trevor
Last updated: 2023-09-12
Post by spareparts on SPI Master not running/MCP3008 Missing driver.
CODESYS Forge
talk
(Post)
I believe I have installed the correct device descriptions and library, in an attempt to use the MCP3008 in conjunction with RPI; when project runs the MCP3008 is unable to find the correct driver. Is there anything I'm missing? Very new to this so any help is apprecated!
Last updated: 2023-09-12
Post by transmin01 on EtherCat Master cannot open network adaptor on Win10x64 target
CODESYS Forge
talk
(Post)
Hi, If I utilise an EtherCat master with a Beckhoff EK1100 coupler on a Win10x64 target I get a "Network Adaptor could not be opened" error. I have tried this on both a VM and a physical PC. Has anyone experienced this issue? Regards Trevor
Last updated: 2023-09-14
Post by snhatton on Alarm Management - latched variable represented as Text list
CODESYS Forge
talk
(Post)
Hi There, For my understanding: are you trying to display the contents of a text list in an alarm message based on the id? For example, you could maintain a text list of common alarm messages, and then display based on which message is true?
Last updated: 2023-09-18
Post by lucaver89 on Raspberry pi 3 and runtime 4.9.0.0
CODESYS Forge
talk
(Post)
Good morning, I'm using a raspberry pi3 as plc with the runtime 4.9.0.0. My program has many of retrain variables but when an update is performed the retrain variables comes back to default values. Is the a way to backups the retrain variables n a csv file? Is still the way to restore them from the csv? Thank you for helping Luca
Last updated: 2023-09-23
Post by derpaul on Official MQTT-Client: MAX_RECEIVE_BUFFER_SIZE_EXCEEDED
CODESYS Forge
talk
(Post)
I've post the Versions in the Attachments. It seems with htop, that there is a very high CPU Load. In the Log I can see nothing, as mentioned above I've to restart the PLC with Power off/on and the log in codesys was deleted. Or what do you mean with plclogger?
Last updated: 2023-09-23
Post by sivakov on CoDeSys Exception EIP Adapter
CODESYS Forge
talk
(Post)
Hi, Got same problem, appeared after 4.3.1.0 update. Prabably problem is in performance. I am using virtual machine, so adding one more core and several GB to RAM still not solved, but atleast did system more stable. Try optimise your main program or set less task interval. Regards, I will be your mate in solving this mistery =)
Last updated: 2023-09-28
Post by ltrinta on AWS IoT Core connection using AWS certificates
CODESYS Forge
talk
(Post)
Hi there I want to know if there is possibility to connect a CODESYS application to AWS IoT Core using the certificates owneds by AWS. In the examples of CODESYS using AWS IoT Core library, we need to generate a local certificate and update it to AWS IoT Core. I want to use AWS IoT Core certificates. Regards, Leonardo
Last updated: 2023-09-28
Post by dgrard on Camera RTSP Feed
CODESYS Forge
talk
(Post)
Hello Is it possible to view a camera RTSP feed in a visualization? It seems as though the browser element doesn't support this and we are trying to replicate an example using the ActivX element with no luck. We are using the Windows Control Win x64 device with a camera connected via LAN. If it is possible, can you provide some instructions please. Thank you
Last updated: 2023-10-17
Post by mawaloc on creationg on dynamic widgets
CODESYS Forge
talk
(Post)
Hello, Is there is any way to create a different dynamic widget than what can be found on codesys. I would like to create similar with adding things like limits etcc. in codesys I just see 180 deg or 360 deg. and shape are differents Any tutorial on it. ThankYou
Last updated: 2023-10-20
Post by timvh on Send file from codesys to...... ftp, cloud, etc
CODESYS Forge
talk
(Post)
You can use the (open source) FTP client in Forge. This works on 64 bit systems. See: https://forge.codesys.com/prj/ftp-client/code/HEAD/tree/ As this is open, the idea is that when you use it and make improvements to the source code, that you also commit this in a branch so others can also benefit from it.