Post by kbazzett on "Sequent Microsystems" industrial automation hat raspberry pi
CODESYS Forge
talk
(Post)
Here is a complete list of the Sequent Microsystems Pi hats that work in Codesys. https://github.com/SequentMicrosystems/SM_CODESYS/tree/main/ "For easy install download the .package file and open it on your computer, Codesys installer will know what to do with it." <- This. The Multi I/O Hat fit my needs because of the Analog I/O 4-20ma and RTD. I used a Raspberry Pi 5 and 64b install. The example project is also worth the download. With the sample project open, right click on the Raspberry Pi device and update to whatever you are using (SL, MC, 64b). Enable I2C on the PI. You can jumper the hats Analog Outputs to Inputs and see it function on the Web Visualization. Very Cool! I spent quite a bit of time trying to find this solution so hopefully this update helps others. Here is the video link on how to setup a Raspberry PI as a Codesys PLC https://youtu.be/RPoPscbo3Kc?si=Th4-n-mQ6g5fdHj8
Last updated: 2024-12-05
Post by macman on Codesys 3.5 OPC UA Client to Kepware OPC UA Server
CODESYS Forge
talk
(Post)
Hi, I have problem with connecting Wago PLC WAGO 750-8212/0025-0002 configured as OPC UA client to Kepware OPC UA Server. I am using Codesys 3.5.19.70. What I did so far. To the Codesys project I added object Data Source Manager and configured connection OPC UA like below: pic 1 Then I can browse the OPC server tags in “Variables” tab after prior trust on the server side of the client certificate created in the “Communication” tab: pic 2 Additionally second certificate has been created in Codesys for runtime process in “Security screen” as well as the server certificate was approved here: pic 3 But when I compiled project, downloaded it to PLC and go to RUN I can’t read selected in “Variables” tab, OPC Server tags. I am getting such error (ID: 7001): pic 4 All two PLC certificates has been trusted in OPC server (Kepware) side: pic 5 and Kepware server configuration look like this: pic 6 I can easily connect using third party OPC UA client UaExpert to Kepware server without problem. In attachment I added also log from Kepware OPC UA server. pic # - this specifies the number of a concrete graphic from one of the collective in attachment
Last updated: 2025-04-02
Post by kurtk on Modbus TCP Server
CODESYS Forge
talk
(Post)
ditto I'm just getting my codesys wheels on and the modbus stuff is confusing. I am re-platforming an existing PLC application On that platform one could simply tag variables to register numbers and the whole shooting match could be accessed via modbus and typically holding registers and input registers were treated the same way... On codesys I see there is a modbus TCP server Device I/O mapping tab and a Modbus TCP server IEC objects tab I get the sense that one can configure the serving of variables both/either way but am unclear about the optimum/necessary path. Apparently in the IEC Objects tab one can "ADD" something or other - presumeably channels. I have created a preliminary function block but the Select Function Block window shows nothing to select WTH ? I exported the Device mapping and was surprised to see the entire Device IO map - complete with all the bit-mapped holding/input registers!! WTH!!?? Bit-mapped words are strictly a nichey special purpose application. I am targetting making a couple hundred variables available which would turn into hundreds of pages of IO/mapping Is the FUnction Block IEC objects thingy an alternative to that ? I notice that CODESYS shows the tags which the PLC used to specify the register address... are tags used in CODESYS for any specific hard-core purpose ?
Last updated: 2025-08-19
Post by xnoop on MBTCP Slave configuration
CODESYS Forge
talk
(Post)
Hello, I use Codesys 3.5 SP18 Patch 4 (64 bit) My Codesys project is composed of several dozen of Modbus TCP Slaves. I want to configure each of them by define : - Modbus TCP Slave Configuration : Name, IPAddress, port - Channels - Mapping I can't afford to configure manually and I need to find automatic way What possibilities does the Codesys offer? 1. I know it possible to use python script to create Modbus TCP Master and Slave. But I don't find anyway to create Channels and Mapping through the API 2. I 've tested to set mapping with file.csv on a Modbus Tcp Slave, but no way to import channels definition from file 3. I 've tried to use PLCOpenXml file. For example I 've create a project with an Ethernet device. I've exported it in PlcOpenXml file. After delete the Ethernet device, I've imported the PlcOpenXml file without success. I've tried the same by creating Modbus TCP Slave. Could you help me to find to good way ? Thanks
Last updated: 2024-06-19
Post by eoahe on Problem Reading Registers via Modbus from non Codesys device
CODESYS Forge
talk
(Post)
Hey Guys :) I have the following Problem using Modbus via Codesys: I'm trying to implement a Modbus Device into my codesys project. The device is a Router from Teltonika (RUT956) and it can communicate via Modbus. Currently I'm trying to implement it into my codesys prject as a slave and I'm using my windows computer as master. As it is not a codesys device (the codesys application is not uploaded to device as it has its own software) I'm having problems requesting and reading registers from the router. I've set up my windows computer as Master and implemented the router as slave. When I go online on my master device it sais that it has established a connection to the slave (router)(So I'm thinking this could work as there is a connection?). The goal is to read the GPS (latitude and longitude) data and on the homepage of teltonika you can find the register address and number of registers (adress 143 for latitude and 145 for longitude; both have a number of two registers). I've found tutorials how to read specific registers via their register address with other modbus programs (like modbus-cli), but as my entire project is established in codesys I was hoping to read these specific registers via codesys so that I can show the GPS data on my dashboard. I've tried establishing slave channels but that hasn't been working. I tried read input register channels of the length 4 but it's not possible to define specific register addresses to read via codesys so that didn't work (I jsut get a slaves device failure) and I've also tried establishing 516 (total number of registers the router sends I think?) read inputregister channels but that has the samle failure... So i guess the problem I'm having is establishing slave channels to read these specific registers. Does anyone know how to tackle this problem and has maybe had the same problem? Or maybe someone knows a workaround? I'm quite new to codesys so maybe I'm also lacking expertise...
Last updated: 2025-03-01
Post by xcqt on Oop best practice
CODESYS Forge
talk
(Post)
Hi all, I’m currently trying to improve my OOP structure in CODESYS and I’m looking for some input on how others approach this. I understand the basics like inheritance, interfaces, abstract FBs, methods, and properties, but I still struggle a bit with the overall architecture and what’s considered clean or scalable in bigger projects. As an example, I’m working on two different energy meter function blocks: FB_EnergyMeter_MQTT reads data from MQTT (strings) FB_EnergyMeter_Modbus reads data from Modbus (words) Both have their own Update() method and implement the same interface (something like IF_EnergyMeter). Later on, I’ll probably add more meter types, but they should all behave the same from the controller’s point of view. Now, there’s a FB_GridControl block that needs power data from these meters. I see two options here: Define the meter blocks inside FB_GridControl and call them directly (for example fbModbusMeter.UpdateModbus()). Keep the meter blocks outside and pass them into FB_GridControl as interface references, so the control block doesn’t know which specific type of meter it’s dealing with. Option 2 feels cleaner and more flexible to me, but I’m not entirely sure how to handle the data flow in that case. Should I pass the meter instance through an interface reference (REFERENCE TO IF_EnergyMeter)? Or is there a better way to link the external FBs to the control block? I’d like to hear how you structure this kind of setup or see an example from someone who has done something similar. EDIT: I think i need to do something like this fbModbusUpdateInput(wInput:= wWordValue); fbMqttUpdateInput(strInput:= strStringValue); IF bUseMqtt THEN Meter REF = fbMqttUpdateInput; ELSE Meter REF = fbModbusUpdateInput; END_IF fbControl.SetMeter(UsedMeter := Meter); Or am i thinking wrong? Thanks, Thomas
Last updated: 2025-10-16
Post by nico01 on Integer with comma in visualization
CODESYS Forge
talk
(Post)
Hello everyone, I created a visualization with a lot of REAL, with one or two digits after the decimal point. This causes me problems in terms of rounding and memory... is it possible to display an integer with a comma, like with PROFACE or SIEMENS? It's just an "abuse" of display, the comma is just on the visualization. This limits the memory (16 versus 64 bytes) and rounding is easier to manage... See print screen on proface software THANKS
Last updated: 2023-09-20
Post by timvh on Management of a PLC network from a remote station
CODESYS Forge
talk
(Post)
Maybe the CODESYS HMI is a good solution. https://store.codesys.com/en/codesys-hmi-sl-bundle.html Run this on the remote main control station. In the HMI application you can add the data source manager and to this manager you can add Data sources. A data source has a reference to the PLC you want to connect to and can get access to the variables of the PLC application. You can then use these variables in the visualization of the HMI application.
Last updated: 2023-12-04
Post by mmoncada on Dinamically loading recipes
CODESYS Forge
talk
(Post)
I'm having trouble with the initial loading of recipes. I can create them and load one or the other, but when the program restarts the recipes are not listed. I'm calling: RecipeManCommands.ReloadRecipes and then RecipeManCommands.GetRecipeCount which returns 0 recipes. None of the methods returns error and if i call them again after RecipeManCommands.CreateRecipe RecipeManCommands.ReadAndSaveRecipe getRecipeCount returns the number of recipes created. When i restart the system, once again they are not listed even though the recipe files are there. Any ideas? Martin Btw, Codesys 3.5 SP 16 Path 9
Last updated: 2023-12-06
Post by xabier on Problem Update new version Master ethercat
CODESYS Forge
talk
(Post)
Hi, I have a project in Codesys...and i need update a new version of amster ehtercat and i have a problem. The origianl version with create of project was 3.5.13.10 I can change version to Master Ethercat 3.5.13.10 to 3.5.16.70 but i can´t update the last version 4.4.0.0 (I attached the screen "Version Master OK-NO OK"). In the moment update to the last version appear a lot of error("Version Master NO OK") Can anyone help me please?
Last updated: 2024-10-25
Post by trusty-squire on Display Units/Scale on Path3D visualization
CODESYS Forge
talk
(Post)
Hi, Is it possible to display the units along the X,Y axis of the Path3D element? It correctly shows the CNC path to be followed, but there's no indication of scale or size of what's being displayed. I looked at the documentation and my first inclination is that this is not possible, and the option option would be to somehow recreate the Path3D functionality into the XY Chart visu element - which is not ideal. Any suggestions or pointers would be appreciated!
Last updated: 2024-11-08
Post by nz-dave on FAILURE TO OPEN PROJECT ON ANOTHER COMPUTER
CODESYS Forge
talk
(Post)
Hi All Not sure what im missing here but i seem to have a lot of issues when i start a project say at home then try to open it at work the next day on another pc, using same version of Codesys. I try the build option when opening the project but still get loads of placeholder,library and some random errors i'm not to sure about. have tied project Archive, which is better, but not perfect. Can someone tell me what im doing wrong!. Cheers
Last updated: 2025-01-20
Post by hismoon on Inheritence of struct,
CODESYS Forge
talk
(Post)
Using a UNION instead of a STRUCT alone should give you that flexibility and only occupy memory once. And if you want to be really elegant, you could use an FB, which only holds PUBLIC VAR. Because a POU can use "EXTENDS"/inheritance. In CODESYS V3, an FB has a lot in common with C++ classes. Using ANY or ALIAS is rarely a good idea. It neither won't be pretty, nor have good readability and requires you to create a lot of error-prone things around it.
Last updated: 2025-03-14
Post by installwhat on Ethercat and profinet on together
CODESYS Forge
talk
(Post)
I'm curious about the impact of having profinet and Ethercat (specifically softmotion so frame at start of task?) running together. Since it's advised to access the data from the bus task should have both profinet io and ethercat on the same task? Are there any implications around this one should be aware of especially since the frame at task start is just, so far as I'm aware, an ethercat thing? Thanks
Last updated: 2025-04-08
Post by wbj0t on Update project from SP20 to SP21
CODESYS Forge
talk
(Post)
Hello everyone. I have a problem: I installed new version of codesys IDE. When I try open project in this new version, I have many errors about Visu: rectalnge/button/frame/etc does not exist. How update properly project? 20+ pages of visu pages from 100+ frames and all visu elems looks like "Error image". It is not problem of SP20->SP21. Any update has problems from visu side.
Last updated: 2025-06-09
Post by otdeveloper on IEC 61499
CODESYS Forge
talk
(Post)
It is being worked on by many companies and its even-driven function blocks seem like a natural evolution of the object oriented industrial programming I have seen Gary Pratt (author of the Book of CODESYS and much more) so expertly implement and explain. I would expect CODESYS to have this front and center on their sights and, if they do not, I would be very interested in learning why.
Last updated: 2024-02-09
Post by matthew on New Ladder Diagram conversion does not work due to missing features
CODESYS Forge
talk
(Post)
Hi @eschwellinger, I have been trying out v1.0 of the new ladder and have a few questions. I have warnings Expression or part of it has no effect I can't get rid of them, what do they exactly mean? Using the ST_Block, is there a way when online to open the ST_Block and view the running code? Thanks!
Last updated: 2024-02-09
Post by alexgooi on Disable OPC-UA server
CODESYS Forge
talk
(Post)
Dear Forum, I recently updated to the newest Codesys IDE (3.5 SP19 patch 5) The program wouldn't download cause of the amount of OPC-UA server tags (see picture) I'm not planning on using the OPC-UA server and therefore I unchecked the "Support OPC-UA features" checkbox in the symbol configuration. But this didn’t solve the issue of the OPC-UA server exceeding its license. How can I disable the OPC-UA server while still maintaining the symbol configuration. Thank you in advance Alex
Last updated: 2024-03-01
Post by i-campbell on Publish a JSON payload via MQTT Publish (using IIot Libraries)
CODESYS Forge
talk
(Post)
your are sending as a WSTRING which is UTF16, but your receiver is interpriting as UTF8. Change the receiver to use UTF16, or better change your sender to convert to UTF8. You publish the entire storage space (SIZEOF) Instead of the number of bytes of actual text (StrLenA) try using utf8JsonData : STRING(2000); JSON.Stu.ConvertUTF16toUTF8( ADR(wsJsonData), ADR(utf8JsonData), SIZEOF(utf8JsonData) ); and change your publish to mqttPublish( mqttClient:=mqttClient, pbPayload:=ADR(utf8JsonData), udiPayloadSize:=To_UDINT(JSON.Stu.StrLenA(ADR(utr8JsonData))), wsTopicName:=topic, mQTTPublishProperties:=mqttPublishProperties );
Last updated: 2024-04-10
Post by robpqs on Visual error with cut/shredded texts
CODESYS Forge
talk
(Post)
Hello, This is an old topic but it might help. This can/should be solved by either of the solution below 1. disabling the "Support client animations and overlay of native elements" option in the visualization Manager (which is handy) 2. disabling the "Hardware acceleration" of the browser. Saw it happening on some clients/PC and on other it works fine with the same webvisu... (Version 3.5.19.20 with visu package 4.4.0.0) Hopefully it will be fixed it in a next release. I haven't tested the 4.5.0.0 visu packages yet. RP,
Last updated: 2024-05-27
Post by arcadium on TargetVisu element stacking on top of each other
CODESYS Forge
talk
(Post)
Hello, I'm new here so if I do something wrong please bare with me. I am using raspberry pi touchscreen made by comfile (CPi-C070WR4C). I also have a window 11 pc where I would like to have a second visualisation, but when I run a TargetVisu with it, all elements of the visualisation end up in the top left corner stacked on top of each other. I have same results running targetVisu on my laptop. Maybe someone had same issues and know the solution? Simas
Last updated: 2024-06-17
Post by hyplcmotion on The element of type 'VisuFbElemImage' could not be updated. Reason: Index was outside the bounds of the array.
CODESYS Forge
talk
(Post)
Hello, I’m encountering the same issue. I only receive these errors when downloading to the PLC—there are no errors during the build—after upgrading to CODESYS 3.5.21.10. Is there any known fix or recommended solution? Visualization seems running ok, no PLC log error. Visualization: Error: The element of type 'VisuFbLabel' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemSimple' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemSimple' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemImage' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemSimple' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemSimple' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemImage' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemButton' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemButton' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds. Visualization: Error: The element of type 'VisuFbElemSimple' could not be updated. Reason: Source array was not long enough. Check srcIndex and length, and the array's lower bounds.
Last updated: 2026-01-26
Post by e13740e on Сalling the context menu from the keyboard
CODESYS Forge
talk
(Post)
Hello. I have a question for you, perhaps you have an answer to it. Regarding calling the Context menu from the keyboard in Devices, specifically calling the context menu window from the keyboard via an assigned combination. Goal: to have the ability to navigationally add internal Objects (Methods, Properties) to Function Blocks from the keyboard without using the mouse. The Codesys environment interface does not allow Windows access to this via Shift+F10. Externally (outside the Codesys environment), the hotkey call for the context menu (Shift+F10) from the keyboard works in various environments, but at the same time, in Codesys it does not (it doesn't work). I have already tried various options on my own to achieve this (but unsuccessfully): Tools\Customize\Keyboard\Objects (the set combination does not give the desired result) Tools\Customize\Keyboard\Objects... (the set combination is extremely useful as it provides access to adding objects directly to Devices but does not provide the ability to add an internal object (Method/Property) to a Function Block). Thank you in advance for your help!!! P.S. I have already started trying to implement a script-based solution to call the context menu via AutoHotkey - by relocating the mouse cursor to the area of the navigational selection with a subsequent call of the context menu on it and relocating the mouse cursor back to its initial position. And in order not to "reinvent the wheel," I am writing this request to you!!!
Last updated: 2025-10-05
Post by e13740e on Сalling the context menu from the keyboard
CODESYS Forge
talk
(Post)
Hello. I have a question for you, perhaps you have an answer to it. Regarding calling the Context menu from the keyboard in Devices, specifically calling the context menu window from the keyboard via an assigned combination. Goal: to have the ability to navigationally add internal Objects (Methods, Properties) to Function Blocks from the keyboard without using the mouse. The Codesys environment interface does not allow Windows access to this via Shift+F10. Externally (outside the Codesys environment), the hotkey call for the context menu (Shift+F10) from the keyboard works in various environments, but at the same time, in Codesys it does not (it doesn't work). I have already tried various options on my own to achieve this (but unsuccessfully): Tools\Customize\Keyboard\Objects (the set combination does not give the desired result) Tools\Customize\Keyboard\Objects... (the set combination is extremely useful as it provides access to adding objects directly to Devices but does not provide the ability to add an internal object (Method/Property) to a Function Block). Thank you in advance for your help!!! P.S. I have already started trying to implement a script-based solution to call the context menu via AutoHotkey - by relocating the mouse cursor to the area of the navigational selection with a subsequent call of the context menu on it and relocating the mouse cursor back to its initial position. And in order not to "reinvent the wheel," I am writing this request to you!!!
Last updated: 2025-10-05
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15