Post by shafiq-dsc on Beckhoff EK series cannot detect but BK1120 detect
CODESYS Forge
talk
(Post)
Dear Support, I have i950 wants to connect with Beckhoff EtherCAT coupler BK1120. There are 2 GSD files for BK1120. 1. BK1120 without MDP.(EtherCAT ESI Device Description (XML)) 2. BK1120 with MDP. (EtherCAT BKxxx (MDP) configuration files) When connecting the BK1120 with i950, scanned devices detects BK1120 without MDP from ESI No1 above. But the KL1408 & KL2408 not detect because they have ELxxxx IO type. When manually insert BK1120 with MDP, the KL1xx8 is able to add manually also but the error shows and Install Missing Descriptions appears. The questions; 1. Why the error occurs? 2. Can the i950 connect with KLxxxx IO type or not? Regards, Shafiq
Last updated: 2024-10-25
Post by hardcoder on EtherCAT Mailbox Gateway
CODESYS Forge
talk
(Post)
Hi all I found that in the last Ethercat master release (4.8.0.0) the Mailbox Gateway feature has been added. This would be useful for me to connect to a specific slave in my system, since its configuration software supports this type of gateway communication. Anyway I don't find usage information or examples. At the moment I tried to enable it in the ethercat master device settings and I configured with an IP address on the subnet of the ethercat adapter (i.e. ethercat nic configured with static ip 192.168.10.100 subnet 255.255.255.0, mailbox gateway configured to 192.168.10.30). I expected it would have responded to ping commands on the address but nothing happens. I am missing something?
Last updated: 2024-12-11
Post by gseidel on Beckhoff AS1060 and EL7041 configuration
CODESYS Forge
talk
(Post)
Hi pmanuele, while I don't have firsthand experience with the EL7041 and the step motor AS1060, there are two things you can check: If you use an external encoder, please make sure you use the alternative device description calles "EL7041 1Ch. Stepper motor output stage (50V, 5A) Rev24 with external Encoder". The SoftMotion driver will set the feedback type automatically, and use the correct object for the actual position (16#6010:21 instead of 16#6010:20) If you have problems with changing the controller mode, I assume to velocity, please make sure you change the PDO mapping so that the actual velocity (16#6020:33) and set velocity (16#7010:33) are mapped by PDO. Hope this helps, Georg
Last updated: 2024-12-23
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Dear people, I would like to create a TCP server in my PLC program. The TCP server needs to communicate with an external device. I have been searching the internet and found that the libraries Syssocket or CAA NetBaseSrv are two possible solutions to create a TCP server. From what I have read, CAA NetBaseSrv is more user-friendly to implement than the Syssocket variant. However, I am still struggling to actually implement this library. Foremost is my little knowledge about creating a TCP server and how to read/understand each function block, especially the outputs of some blocks and the types, e.g. server has an output CAA.Handle, but I cannot find the explanation of CAA.Handle. I tried to find a good document that can help me understand how to implement a TCP server, but I could not find it. Thank you in advance, George
Last updated: 2025-02-20
Post by struccc on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I don't exactly recall where (I think some release notes), but I read the information that this multiple application / sub application feature is to be discontinued. Please, correct me, if I'm not right about this I am a bit sad about that - I was using that feature with more or less success. However I understand the reason behind the change: it introduces huge complexity, especially when dealing with multicore and safety support... AS I understand, it's to be replaced with the new virtual plc architecture, and standard ways for synchronizing / sharing data... So, for now the "Add application" context menu item was removed, but behind the scene it is still supported... Hint: if you still want to experiment with it, might try copy-paste things within the PLCLogic tree...
Last updated: 2025-02-28
Post by timvh on Problem Reading Registers via Modbus from non Codesys device
CODESYS Forge
talk
(Post)
According to the documentation: https://wiki.teltonika-networks.com/view/RUT956_Modbus You need to create a Channel to read 2 registers from address 143 to get the lattitude. It doesn't specify if you need to read it as a Holding Register or as an Input Register. You could try both. So in the Teltonika router, you need to enable it as being a Modbus Server. Then in CODESYS add an Ethernet Adapter, then a Modbus Client (Master) and to the Client (Master) add the Modbus Server (Slave). Set the IP address and add the Channel. The please consider that CODESYS doesn't update any variables when they are not used in the application. In the I/O mapping tab of your I/O configuration, you can set the "Always update" to enabled.
Last updated: 2025-03-08
Post by mehakfatima on Need Help Configuring Energy Analyzers via Modbus TCP & RTU (RS-485) in CODESYS 3.5
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on reading data from energy analyzers using Modbus TCP and RTU (RS-485). In my previous software, I used the following method to add slave devices (i have attached the image) and configure registers: Add the Modbus slave device. Configure the communication parameters (baud rate, parity, etc.). Define the registers and their addresses for data retrieval. Now, I am trying to achieve the same in CODESYS 3.5, but I am not sure how to configure the Modbus master, add slave devices, and set up the registers properly. If anyone has experience with Modbus TCP/RTU setup in CODESYS 3.5, I would really appreciate your guidance! A step-by-step explanation or any references/tutorials would be extremely helpful.
Last updated: 2025-03-13
Post by bjarne-pagaard on Global Variables
CODESYS Forge
talk
(Post)
Old thread, I know - but it still has good answers. I would like to add a bit of info to it, as I was having a problem that lead me to this thread, but didn't give an exact answer. I am porting a project to a different PLC architecture. (Wago PFC300) A GVL named 'GVL' in the POUs section of my project was shadowed by a PLC-specific library in the Application->Library Manager. So all the existing references in the device specific code to 'GVL.something' would not resolve. Right-clicking the GVL in the code and 'Go to definition' would point me to the library in the Application Library Manager. All I had to do from there, was right-click the library, and set the property 'Only allow qualified access to all identifiers' in the library.
Last updated: 2025-04-11
Post by rer-code on Codesys 3.5.18.60 – Application Loss and Persistent Data Corruption
CODESYS Forge
talk
(Post)
Hi, I’m currently managing over 50 PLCs running Codesys version 3.5.18.60. At seemingly random intervals, some of these devices experience a failure where: All persistent variables are lost. Attempting to log in results in the message: “The application does not exist on device. Do you want to create it and proceed with download?” The log shows: “Loading retain-data/bootproject failed.” From what I’ve gathered, this may be due to a corrupted persistent data file, but I’m not entirely sure how to confirm or resolve this issue. If anyone has encountered something similar or has suggestions for troubleshooting or preventing this, I would greatly appreciate your input. Best regards
Last updated: 2025-08-19
Post by ranadheer on Implementation of IEC-104
CODESYS Forge
talk
(Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14
Post by ranadheer on Implementation IEC-104
CODESYS Forge
talk
(Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14
Post by imuser on Is it possible to use debug functions such as Step Execution while the PLC ladder is in Running?
CODESYS Forge
talk
(Post)
Hello, I am a student learning CODSIS. Lately, I've been curious about something. During the actual PLC run, that is, Assume that the I/O is connected to a physical device and the analog value is updated in real time. Is it possible to use a feature like Codesys’ Debug-Step Over-Step IN? If possible..... How do I process the values of analog values (pressure sensor, temperature, current, etc.) that are being updated in real time? To step over, the ladder must stop at the breakpoint. If that happens, the PLC will actually stop, right??
Last updated: 2024-01-16
Post by gallusrrr on usb2can in Codeysy 3.5 Can Gateway
CODESYS Forge
talk
(Post)
Hallo Forum das ist mein erster Post bei euch also bitte seit nachsichtig :) ich habe mir den: USB zu CAN Konverter Kable for Raspberry Pi4/Pi3B+/Pi3/Pi Zero(W)/Jetson Nano/Tinker Board and Any Single Board Computer Support Windows Linux and Mac OS (USB2CAN-C) Gekauft da er in Linux arbeiten soll dachte ich man kann den so in codesys einbinden da es auf einen Rasperry Pi lauft. Erkannt wird der Adapter als Bus 001 Device 004: ID 1d50:606f OpenMoko, Inc. Geschwister Schneider CAN adapter Wie bekomme ich den in Codesys mit einen Rasperry pi eingebunden. (Im Internet habe ich nichts gefunden.) ich bedanke mich. euer Martin
Last updated: 2024-01-16
Post by dhumphries on Ethernet/IP Issue
CODESYS Forge
talk
(Post)
Make sure the O->T and T->O bytes required by the remote device match the configuration in Codesys. Most of the EDS files I've imported have not worked by default. See the attached images for the connections and assemblies tabs. Note that the connections are in Bytes and the assemblies are in bits, you have to have enough bits to equal the bytes. Either mismatch will give a red/orange triangle. Page 343 of the manual (assuming the STF10-IP is an applied motion microstep driver) has some recommended connection settings, you should be able to confirm the input and output bits somehow, some devices have a web GUI, some require a software tool.
Last updated: 2024-02-03
Post by sumit on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
dhumphries, I changed the datatype this time from BYTE to USINT (because that's what my adapter is sending: array of uint8_t). The text "New Help String" you saw in previous screenshots is just the description of the input/s (it can be anything). I also looked into the logs (see attached) for that ! sign next to the device, I found that connection is being timeout. I tried some suggestions from online such as increase the RPI but still got connection timeout issue, also by changing the datatype, I still don't see incoming data from the adapter, although its visible on wireshark. thanks,
Last updated: 2024-03-07
Post by phoward131 on Text List Fallback Value
CODESYS Forge
talk
(Post)
I am relatively new to Codesys and I'm trying to develop an HMI that displays what mode a particular device is in based on an integer value. I am currently using dynamic texts with a text list which works fine but I am looking for a way to display a particular string (ie 'Unknown') when the index doesn't match any of of the indices in the text list. I can enter 'Unknown' in the text property of the text field element which works as expected but it displays the single quotes on the visualization. How can I escape these quotes to simply display the word Unknown? Thanks!
Last updated: 2024-03-22
Post by danwoodlock on Rpi zero w lost license after 4.11 update
CODESYS Forge
talk
(Post)
Hello all, Encountered an issue with my zero which seems to have happened after the 4.11 update. It now runs in demo mode (2hr) and I am trying to see what the appropriate steps are prior to contacting codesys directly. Background: I recently did a fresh install of w11 on my pc, so it seems "c:\ProgramData\CODESYS\Licenses\" only has information related to my pi5, which I licensed just this past Friday. I have all my license documentation about my rpi zero as far as the emails received, but when I try to claim using the ticket number it says its already been used, or something to that effect, which it was. Currently trying to perform device license reader, which is taking some time.
Last updated: 2024-04-14
Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20
CODESYS Forge
talk
(Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20
Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20
CODESYS Forge
talk
(Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20
Post by robpqs on Program from one PLC to other WAGO 750-8204
CODESYS Forge
talk
(Post)
Hello, You use the WAGOUpload tool. You can download it on the download center of WAGO. Make a backup and restore it on the new device. (if can check the remanent data to copy the persistent variables if necessary) You can also use a SD card, go to the WBM copy it the image to the SD card and restart the other controller on the SD card. In the WBM, copy it back to the internal flash. If you contact your local Wago office, they will more than probably help you. There is also a WAGO forum. RP,
Last updated: 2024-05-27
Post by etalp on Eaton XC303 firmware update via USB
CODESYS Forge
talk
(Post)
Hi, I'm struggling with updating my xc303 to firmware 3.5.17. It is possible only via USB port. I've installed proper update files on the USB then plug it into the PLC's USB port and restarted the device. Shortly after LED's on the PLC started to blink, so updating process has started. But after 10 minutes the PLC LED turned off and after all I could't serach for this PLC in Codesys, but could ping it. Could someone eplain to me proper procedure of updating the fimrware in XC303 via USB? Is it neccesary to STOP the PLC switch after pluging the USB?
Last updated: 2025-10-15
Post by clarenced on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I am looking for an example of how to run 2 applications on 1 device that would have global variables shared between the two apps. In this case what I am trying to do is to have the main program logic run as one application and then have the visualization run as a second application. I find this https://us.store.codesys.com/media/n98_media_assets/files/000013-F/0/Multiple%20Applications_en.pdf, that talks about exactly what I want to do, but I can't find the download. The main reason I want to do this is for download speed. Right now it takes at least a minute to download our application to the PLC. A simple program downloads to the PLC in a very short time, but add visualization and the download time gets much longer. If I could download the program separately from the visualization I think that a simple program change would take very little time to download. I have tried create a GVL in the POUs view. This partly works in that both applications can see the GVL, but they each create their own instance of it and the variables are not shared between the two apps. There are ideas of using OPCUA but this raises problems with licensing and having to move any variable that needs to be shared into the Symbol Configuration. This adds a lot of management to keep this up to date. Any ideas would be appreciated thanks.
Last updated: 2025-02-20
Post by paulpotat on cm4 runtime problem
CODESYS Forge
talk
(Post)
Hello, I have exactly the same issue, with the following configuration : Hardware version >>> cat /proc/cpuinfo processor : 0 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 1 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 2 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 3 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 Hardware : BCM2711 Revision : a03141 Serial : 10000000d5be5b5f Model : Raspberry Pi Compute Module 4 Rev 1.1 Kernel version >>> uname -a Linux raspberrypi 6.1.21-v7l+ #1642 SMP Mon Apr 3 17:22:30 BST 2023 armv7l GNU/Linux OS Version >>> cat /etc/os-release PRETTY_NAME="Raspbian GNU/Linux 11 (bullseye)" NAME="Raspbian GNU/Linux" VERSION_ID="11" VERSION="11 (bullseye)" VERSION_CODENAME=bullseye ID=raspbian ID_LIKE=debian HOME_URL="http://www.raspbian.org/" SUPPORT_URL="http://www.raspbian.org/RaspbianForums" BUG_REPORT_URL="http://www.raspbian.org/RaspbianBugs" /boot/config.txt I added the following line : arm_64bit=0 CodeSys runtime version 4.10 Were you able to solve the issue @michelebianchi ? Any help with this would be appreciated... BR
Last updated: 2024-08-28
Post by edson-bueno on SysProcess Execute Command unable to run commands with special characters
CODESYS Forge
talk
(Post)
Hi, I found the same issue, and I fixed with this steps: 1st go to codesys .cfg file. sudo nano CODESYSControl.cfg Then insert this: [SysProcess] BasePriority=Realtime Command=AllowAll Now we need to grant codesys root rights on Linux. Step 1: Create or edit the systemd override configuration: sudo systemctl edit codesyscontrol In the editor that opens, insert: [Service] User=root Save and exit: Press Ctrl+O to save Press Ctrl+X to exit Step 2: Reload systemd and reboot To apply the override: sudo systemctl daemon-reexec sudo systemctl daemon-reload sudo reboot Step 3: Confirm CODESYS is running as root After reboot, open the terminal and run: ps aux | grep codesyscontrol You should see something like: root 1234 ... /opt/codesys/bin/codesyscontrol.bin ... If instead it shows admin or another user, the override was not applied correctly. Step 4: (Optional) Confirm from within CODESYS In your CODESYS project, insert this test code to run the Linux command whoami: Make sure the lib SysProcessImplementation, SysTypes, and CmpErrors is on the project. VAR sCommand : STRING := '/usr/bin/whoami'; sOutput : STRING(255); refCommand : REFERENCE TO STRING; refOutput : REFERENCE TO STRING; resultCmd : UDINT; END_VAR refCommand REF= sCommand; refOutput REF= sOutput; SysProcessExecuteCommand2( pszCommand := refCommand, pszStdOut := refOutput, udiStdOutLen := SIZEOF(sOutput), pResult := ADR(resultCmd) ); Notes & Warnings This method gives full system access to the CODESYS runtime — do not expose this system to the public network without protection. Do not use sudo in commands inside CODESYS when the runtime is already running as root. @tomas111, in case you want to read the temperatur, use this command: sCommand:STRING:='/usr/bin/vcgencmd measure_temp';
Last updated: 2025-05-20
Post by gerdkoch on Dynamic I/Os Mapping
CODESYS Forge
talk
(Post)
Hi, I assume that you have a Pfc200 G2 or something and work with the original WAGO runtime. Then I would recommend the WagoSysDynamicIoMapping. Here in the example projects there is a PDF file for the library: https://downloadcenter.wago.com/learning-material/details/ll0w3pmdunzvem83g1 There is a global functional component in a GVL of the library. I think it's called DynKbusIoManager or something. The active terminals are registered there. Then there are filter Fb's for e.g. the first clamp with a specific article number. Everything is in the PDF.
Last updated: 2023-08-18