Post by remlab on WebClient result empty
CODESYS Forge
talk
(Post)
Hello, I try to read into a IPX800v4 (this is a PLC for domotic application) with a WebClient fonction I use as url http://192.168.0.250:50543/api/xdevices.json?key=XXX&Get=C XXX is replace by the correct key for sure The status code is 200, it should works correctly But the result is '{' that's my problem When I try the same url with a web browser the result is correct like { "product": "IPX800_V4", "status": "Success", "C1": 16, "C2": 2, "C3": 0, "C4": 0, "C5": 0, "C6": 0, "C7": 0, "C8": 0, "C9": 0, "C10": 0, "C11": 0, "C12": 0, "C13": 0, "C14": 0, "C15": 0, "C16": 0 } When i replace the url by a web site like google for exemple it works Can you help me please ?
Last updated: 2026-03-04
Post by struccc on Application failing to boot after system reboot
CODESYS Forge
talk
(Post)
I started to experience the same issue, after upgrading to 3.5.19 , and still persists with 3.5.20.3 , using CodesysControlWinV3 x64 on Windows. Unfortunately, this is a live application, normally it is running for months without interruption - so it was a surprise at the last cold start... It was not possible to go online with the original version, so I couldn't see the application, or system status, just the log message. First time I manually clean the Application from the PlcLogic directory (there was no coredump file in there), then I could start the runtime service, and do a fresh download, and set the bootproject. I could not try a cold system reboot - it's in a 24/7 production environment, and I was under heavy pressure to start... What I did, I have created a backup from the * complete * runtime directory, from the failed, and fixed version - before and after download. This directory in my case C:\ProgramData\CODESYS\CODESYSControlWinV3x64\55096128 - At the next shutdown, it was sufficient to copy back this backup completely, and could start the runtime service afterwards. Ugly, but local staff with some skills can do it without programming tool... I don't store any live data, configuration, log files, persistent data in this directory - the only reason I need this is to edit the CodesysControl... .cfg file.... And to see the logfiles in emergencies like this. The application concerned doesn't use any retain area. - exactly for these reasons - Maybe that is causing the problem with the newer runtime versions As far as I see, this problem occurs only if the power of the Windows PLC is interrupted without a proper shutdown. Unfortunately, this can happen sometimes. The newer versions, seems tp modify CodesysControl.cfg on the fly, and register the applications, and bootproject information after download. (I don't really see CodesysControl.cfg a proper location for this... but that's just my feeling) So now I had a look at CodesysCotrol.cfg on my laptop and I found: [CmpRetain] ;Retain.SRAM.Size=0x200200 ;Retain.SRAM.Address=0xFA3C5776 ;SimulateSRAM=1 [CmpApp] ;Bootproject.CreateOnDownload=0 ;Bootproject.StoreOnlyOnDownload=0 ;Bootproject.InvalidateByRename=1 ;Bootproject.InvalidateBySetting=1 ;Bootproject.InvalidateNever=0 ;PersistentForce=0 ;RetainType.Applications=InSRAM ;RetainType.Applications=OnPowerfail ;RetainType.Applications=None ;Exception.Hardware.GlobalStop=1 Application.1=MyTestAppNoRetain The last line appeared after download and boot project creation. Maybe... Should set RetainType.Applications=None? I wonder about all these settings, but... Will write separately about it. I hope this helps a little...
Last updated: 2024-11-21
Post by moksan on Unconnected_Send Explicit message with Route Path
CODESYS Forge
talk
(Post)
I have been trying out Unconnected_Send Explicit Message with route path.(The Unconnected_Send service shall use the Connection Manager object in each router to forward the message and to remember the return path. Vol 1.3 / 3-5.6.7) However, I could not see the correct path on Wireshark. I want to see the Unconnected_Send Message Service Code as 0x52 and also the last of the message should have the route path. I want to ask some questions about this topic. The IIoDrvEIPAcylicServices Interface has the IoDrvSendUnconnectedMessage Method. And there is a struct (EIP_SendUnconnectedMessage) for this service. But there is no information about how to implement to project, and if it is successful, does it send a message with 0x52 Unconnected_Send Service Code or not? If that is not a solution, how can I set the Unconnected_Send Explicit Message struct on Codesys? Also how can I send explicit message with route path?
Last updated: 2023-10-17
Post by climblinne on Calling OPC UA Methods from UaExpert
CODESYS Forge
talk
(Post)
Hello, I hope someone could help me. I installed the newest Codesys 3.5 SP 20 Patch 1. When loading the demo files from @i-campbell I can upgrade them to the latest version and everthing works on the OPC-UA client side as expected (object "a" is visible, I can use the "ExampleMethod"). Now I * remove the "Information Model", * delete the "OPC_UA_Symbols Objects", * Add "Information Model" again * add "TestRootObjectType" again and "Generate IEC declarations" * and search for mapped instances (to get instance "a" again) Very good still working as expected. Now I delete the OPC_UA_Symbols and add it again referring to the "objecttest" from 16.9.2020. Also I redo the steps from above. The result is now, that I can't see the "a" object in the "Root/Objects" folder. Why ist this and how can I make it running? I think, it could may be a different version of the UA configuration file. I tried to build my own model definition files and got the same problem (but I am really not an expert). When someone has a actual model, which is also running in the actual Codesys I would be very grateful. Or even better, how to make the correct model in e.g. UA Modeler SW (I followed the description https://documentation.unified-automation.com/uamodeler/1.6.0/html/howprojnet_sec.html).
Last updated: 2024-07-01
Post by ahuckphin on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
I have a DFRobot RS485 temperature & humidity sensor (SEN0438) connected to my Raspberry Pi via a USB to RS485 adapter. I am able to connect and read the sensor data when running a python code locally. However in Codesys, I encounter this error "A bus error has occurred." and "There was no response in time". Could this be because of Modbus Server Channel and Modbus Server Init configuration on my part? Admittedly I am new to Codesys. To get to this stage, I: 1. added some lines to CODESYSControl_User.cfg 2. added "Modbus_COM" in Codesys and set "Serial Port Configuration" under "General" 3. added "Modbus_Master_COM_Port" in Codesys and checked transmission mode is set to "RTU" 4. added "Modbus_Slave_COM_Port" in Codesys and checked server address is set to 1 (also set 1 in my sensor) 5. added 1 channel and 1 init for "Modbus_Slave_COM_Port" under "Modbus Server Channel" and "Modbus Server Init"
Last updated: 2024-07-10
Post by latassan on RaspberryPi 5 gateway problem
CODESYS Forge
talk
(Post)
Hello, I'm trying to use a raspberryPi 5 as a PLC. I fixed its IP address, I can ping it. I've also installed the CODESYS Control for Raspberry Pi 64 SL runtime on it. So I've created a gateway (IP address of the Raspberry, TCP port 1217). I see the green dot next to this gateway. When I do a network scan, I can see my raspberry (see photo). When I try to connect to it, I have to define an administrator profile, which I do. On validation, I see a message: No device is responding to the scan request. I've checked that port 1217 is listening on the raspberry, I've uninstalled the runtime then installed it again, but I can't connect. Also, when I try to configure the user groups before connecting, I see that Offline mode is not supported by the device, even though I'm connected to it in the Deploy Control SL tab. When I try to refresh, I see: Gateway not configured properly. How can I connect to my Raspberry? Have I defined my gateway incorrectly?
Last updated: 2025-06-12
Post by alexgooi on Licensing info not available.
CODESYS Forge
talk
(Post)
Sorry for the question, but I'm not completely getting the idea here, could you be more specific, maybe give an example? I'm now in a state where I don't have a softcontainer on my license server anymore (even after reinstalling from the Codesys-IDE). I tried reaching the webserver of Codemeter but when I do that I get redirected to http://"IP":22352 This is not reachable, afterwards I installed lynx on my Debian machine (command line only). From here I could reach the webserver and toggle the network server setting, but unfortunately this did not help. I also tried to changed the remote read setting to 1 (in the Server.ini file). But after a Codemeter reboot this is overwritten to 0. I have the feeling that it should be much easier to get a license to work, am I missing some checkbox somewhere? Is there a tutorial (or manual) that explains the licensing sequence step by step, because I'm pretty stuck.
Last updated: 2025-10-01
Post by spiessli on Softmotion axis to CANopen Maxon IDX drive
CODESYS Forge
talk
(Post)
Thanks for the advise, indeed, this was somewhat, what my intention was. I tried around again with EDSes and DCFs, anyway. It appears that the DCFs end up in a subfolder in the attach device dialog. Astonishingly, when attaching the DCF version I get a device in the device tree, where I can add a SoftMotion axis, whereas when I attach the device not in the subfolder, then I cannot. Further astonishingly, when looking in the CANopen parameters in supported profiles, "402" is listed in the case of the DCF variant, whereas in the EDS variant "0" is shown. Comparing EDS and DCF files I cannot guess, where the difference is coming from. I cannot tell either why I have always attached the EDS variant and apparantly never the DCF variant. As I am not in the lab right now, I cannot test if the connection actually is working. Thanks again, spiessli
Last updated: 2024-01-07
Post by thewizard8 on Raspberry PI4 Serial Port
CODESYS Forge
talk
(Post)
Hi Dear All, I'm using my raspberry PI4 as a CoDeSyS PLC (Build from scratch with custom electronics). I was able to implement all fieldbuses with the exception of Modbus Serial. I'm using the internal Port (GPIO) and I configured it in /etc/Codesyscontrol_user.cfg the following away: [SysCom] Linux.Devicefile.1=/dev/ttyUSB0 Linux.Devicefile.2=/dev/ttyS0 I'm using COM2 on Master configuration. I'm using a interface board from TTL/RS485 (bidirectional board), and it's works perfectly with other devices but not in CoDeSyS. I'm able to send data with python script and read it on my pc using putty, but when I use a modbus slave simulator to interface with codesys I always get red icons on master and slave. (Please find image attached). I'm pretty shure that this might be a bad parameter on my CoDeSyS runtime configurstion file. Can someone help me? I'm stuck and this is for my master degree certification.
Last updated: 2024-03-18
Post by fontrap on cmDongle Raspberry Pi issue
CODESYS Forge
talk
(Post)
Hello mates, I'm working with CODESYS V3.5 SP20 on a Raspberry Pi and I use "Raspberry Pi MC SL" as device on the project. I've installed the Control Standard L (multicore) license on a Wibu System usb-Dongle (cmStick/4.50) that already had another license from another vendor. I follow the online activation procedure from CODESYS documentation. Raspberry Pi has already CodeMeter installed for the other license. When I plugin the dongle on Raspberry and start the Runtime from Raspberry Pi Update in CODESYS I receive the message that I'm on Demo mode because the license is missing. I double checked that the license is activated in the dongle, through the WebAdmin of CodeMeter and the second license runs properly without any issue. I have already try to change the dongle from HID to MSD device and backward but the the Runtime cannot recognize the Dongle. I have also try to stop and start the Runtime through CODESYS without success. Is there anything else I can do to fix this issue?
Last updated: 2024-04-22
Post by jrsantab on Remote connection to ifm PLC & HMI
CODESYS Forge
talk
(Post)
We have finally solved the problem. The version of the Gateway in the computer that worked (3.5.11.0) and the one that didn't (3.5.17.30) was different. We have three different Codesys 3.5 versions installed because we work with different controllers. I believe that, depending on the sequence you follow to install the versions you get a different Gateway version. To solve the problem you first have to disable the "obsolete" services. Open services, serach for (in our case) CODESYS Gateway V3 Version 3.5.11.0 CODESYS ServiceControl Version 3.5.11.0 I stopped the services and changed to Manual Start. Then you have to create the new services. In our case, from a Command Prompt session (cmd): SC CREATE "Codesys GatewayService Rigual" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\GatewayService.exe" and then SC CREATE "CODESYS ServiceControl Version 3.5.17.30" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\CODESYSControlService.exe" remember also to set them as Automatic Start!
Last updated: 2024-04-22
Post by tortilla on J1939 connection between two devices
CODESYS Forge
talk
(Post)
Hey, I'm pretty new to CoDeSys so I don't know a lot of things yet. I have to create a connection between two devices (CANbus - J1939 connection). The idea for now is to send a message from one to another (one operates on 3.5 SP11 the other one on 2.3) I watched a few videos, worked with the documentation and worked with chatGPT 4o and was able to build the attached file. This part is about the device on 3.5.11: I'm using the J1939LocalECUDiag, TransmitParameterGroup, TransmissionTrigger Function blocks to send the message but my TransmitPG.xBusy / .xDone never turns to True and therefore my message is not sent while TransmitPG.xExcecute is True. I added the two devices in the CANbus in the J1939Manager and addapted the options like I've seen in the documentation. Can anyone explain what's wrong with my code in this casse or give me advices how to properly create a connection between my two devices? Thanks in advance!
Last updated: 2024-05-23
Post by svenkaro on Codesyscontrol.service stoppt nach 30s
CODESYS Forge
talk
(Post)
Wie Du schon vermutet hast, es meint, die Hardware/Firmware sei nicht kompatibel ... ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-18, 0x00000BB8, 0xFFFFFFFB) Architecture: aarch64 Byte Order: Little Endian CPU(s): 4 On-line CPU(s) list: 0-3 Vendor ID: ARM Model name: Cortex-A72 Model: 3 Thread(s) per core: 1 Core(s) per cluster: 4 Socket(s): - Cluster(s): 1 Stepping: r0p3 CPU(s) scaling MHz: 40% CPU max MHz: 1500.0000 CPU min MHz: 600.0000 BogoMIPS: 108.00 Flags: fp asimd evtstrm crc32 cpuid Caches (sum of all): L1d: 128 KiB (4 instances) L1i: 192 KiB (4 instances) L2: 1 MiB (1 instance) Vulnerabilities: Gather data sampling: Not affected Itlb multihit: Not affected L1tf: Not affected Mds: Not affected Meltdown: Not affected Mmio stale data: Not affected Retbleed: Not affected Spec rstack overflow: Not affected Spec store bypass: Vulnerable Spectre v1: Mitigation; __user pointer sanitization Spectre v2: Vulnerable Srbds: Not affected Tsx async abort: Not affected Allerdings habe ich schon reichlich Firmware versionen getestet.
Last updated: 2024-06-21
Post by valenting on License problem with Raspberry Pi
CODESYS Forge
talk
(Post)
Hello, I have a raspberry pi with a license installed, but Codesys stops after 2 hours, and when I start it manually I have the following message: pszInfo=!!!! no runtime license - running in demo mode(~2 hours) I tried using License Manager, and got the following message: Licensing info not available. There is no dongle attached to the device. I have this message frequently, and usually removing the content of /var/opt/codesys/.cmact_license makes it work. After doing it and restarting Codesys, I have an empty Softcontainer without my License. I tried using "Install license" using the .WibuCmRau file for the corresponding license and got the following message: Licensing info not available. The device does not support this service. I also tried using Additional Functions > Restore Licenses with the Ticket ID and got the following message: This device does not support automatic license backup. How can I reinstall the license to this Raspberry Pi?
Last updated: 2025-11-28
Post by risele on Modbus connection via Qronox PCD3 M6893
CODESYS Forge
talk
(Post)
First, if you don't need to change conversion rules in runtime, take a look at "Unit conversion" module (Application -> add object -> UnitConversion). You can specify there biderectional conversion with different units, limits and so on. Second, since MODBUS don't have "real" types but only general 16-bit registers and Real is 32-bit, generally you need a byte-was conversion Real <> two Words. Note, that depending on the devices on both sides, there are two options: Real-> Word1, Word2 or Real-> Word2, Word1, where Word1 is minor register in Modbus register pair and Word2 is major. You can use simple union: TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE and convert it as following: VAR myUnion:u_Real; rValue_TO_SEND:REAL; rValue_TO_GET:REAL; END_VAR myUnion.rVal:=rValue_TO_SEND; rValue_TO_GET:=myUnion.rVal; Note, that WORD-order should be properly set in MODBUS registers, otherwise you will get strange values. This tool is helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/ Alternative, you can use functions as REAL_TO_DW and DW_TO_REAL from OSCAT_BASIC, for example.
Last updated: 2026-02-19
Post by lukasz on Unresolved reference when trying to upload to Codesys Runtime V3
CODESYS Forge
talk
(Post)
Hello! I'm working with Codesys SP21 Patch 4. The project builds without any errors. When trying to upload my project to Codesys Runtime V3 x64 I get a lot of Unresolved Reference errors, all with FU- at the start and then -CLOSELAYER2, -GETBUSINFO, -GETFRAME etc. I also get a error pop-up that I should 'update device' in the project but it's not specified to which version or anything useful really.There's also not much to choose from. When I check Runtime version in the systray I get 3.5.21.40 and it's the same as I have set up in the project as the device. All information I get is that it should be clear from the errors but no useful information is provided in the errors. Do I need to install some library? I checked other posts and for different reference error and this was the answer. Thanks in advance!
Last updated: 2026-03-25
Post by timvh on When Keyboard Key is in Hold, then Webvisu is extreme slow and latent
CODESYS Forge
talk
(Post)
I'm not really sure what you are trying to do, but maybe you are referring to using the CmpCharDevice library? When you "open" the connection to a device, you can pass flags. What helped me is to set the non-blocking flag. I'm not sure if this is what you are referring to, but maybe it helps: dFlags: DINT := CmpCharDevice.ACCESS_MODE.O_RDONLY + DINT#4000; // see details for flags: http://linux.die.net/man/2/open, + DINT#4000 is for non-blocking hDevice := CmpCharDevice.CDOpen(szFilename, dFlags, Result);
Last updated: 2023-09-20
Post by fred on Rasperry Control Debian 12
CODESYS Forge
talk
(Post)
Hi, I have Proxmox running on a Rasperry 4 and have debian 12 ARM installed here. I wanted to install Codesys Control for Raspberry on it. According to the messages, the runtime environment and the gateway were installed successfully, but I can't find a device to downplay a program. The sudo service codesys start command fails. (see image) Does somebody has any idea? Thank you for your help! Greetings Fred
Last updated: 2023-11-22
Post by gepert on parker servo and position
CODESYS Forge
talk
(Post)
Hello, Thank you for your response. In my application i use ethercat and while work i do not turn off power. After relative move motor is in standstill. As you suggest I suppose that problem is in drive setting but i do not see any option about increase standstill torque. Below i posted some photos from drive setting manager - PSD Servomanager Do you see any settings responsible for standstill torque? thank you
Last updated: 2024-08-05
Post by trusty-squire on How to adapt Codesys Control SL to custom board
CODESYS Forge
talk
(Post)
For general usage, these links might help you out. If you are looking at using I2C interfaces, examples from the Raspberry Pi will probably be useful, even if your board isn't a Raspberry Pi. https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_rts_serial_com.html https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_raspberry.html If you're developing your own drivers, I can't help you there, although the link you provided will help. If you drill in deeper, the I2C page for example shows function block and method usage, etc. Good luck!
Last updated: 2024-08-09
Post by ralfki on User management
CODESYS Forge
talk
(Post)
Hello eschwellinger, at first thank you for your answer. So the only ways to activate the user management are CodeSys delevelopment enviroment and the Codesys Automation Server. So there is no function to activate the user management via code? Do you have an idea how to get back the users when somebody replaced the PLC. Our customers have only our own developed visualization and they also don't want to install further softwares. Do you maybe have a solution for this
Last updated: 2024-09-04
Post by dkugler on EThercat Dynamic configuration
CODESYS Forge
talk
(Post)
I can confirm that at my 4ms EtherCAT Master the frames per second is equal at round about 500 with Codesys SP19. The same program at SP16 it was at 380-430 f/sec. for me it will be interesting too, whats the reason is for this high frame count/sec? I havn't had the time to use a paket sniffer and analyse all the frames. I can't help with your other questions, sorry.
Last updated: 2024-09-19
Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20)
CODESYS Forge
talk
(Post)
The RTE will take the RTE license. The HMI will take the HMI license. For the Application Based Licenses, the Runtime will take the smallest which is required. So if you have an application running EtherCAT and no visualization, only the Control with support for EtherCAT is used. If you have another runtime which requires the visualization, it will take the smallest Control license which is required and available + the smallest visualization license which is required.
Last updated: 2024-10-01
Post by paulpotat on Can't open license manager with raspberry CM4
CODESYS Forge
talk
(Post)
Hello, I have a problem when opening the license manager for my raspberry pi (CM4 model) with runtime 4.13.0.0. I select "Device" --> "Soft Container" and click on my device in the scan window but I get this error message : Licensing info not available. There is no dongle attached to this device. I can't install licenses anymore, and I don't understand why is CodeSys looking for a dongle when I specified I wanted to use a Soft Container. Can somebody help me please ? Best regards
Last updated: 2024-10-04
Post by mini-developer on Profinet Exor connection drop
CODESYS Forge
talk
(Post)
Hello, I have a Exor HMI with 2 seperatred ETH interface's. It is Configured as PN Master on ETH interface 1 and the IO's are working, as long as the development PC is connected to the ETH 0 interface. When the PC is disconnected, the PN communication drops and a reconnection is started. I installed the newest device description for Codesys and Firmware for the Panel. The IO Gateway is from Weidmueller What could cause the Problem?
Last updated: 2024-10-16