Post by wiresplus on Cannot get INT_TO_TIME working CODESYS Forge talk (Post)
Hello, I have a simple TON timer. It is watching prime loss for a pump. The operator can set the delay via the HMI, it is an integer (seconds) As the TON uses milliseconds, we then multiply the entry by 1000 to get seconds. Seems simple, but... VAR PrimeTimer : TON; primetime : INT; END_VAR PrimeTimer(in:=State>0 AND FlowRate<MinimumFlow,pt:=INT_TO_TIME(primetime *1000)); For an entered 15 seconds (VAR primetime:=15;) the timer reads 49d17h2m26s760ms !!!! What am I doing wrong?
Last updated: 2024-01-26

Post by fless on FB having single input but initialized with Array CODESYS Forge talk (Post)
Why will it retain the sum value from the last call? This is how PLC work. Usually variables only get initialized after a download or a reset (i.e. power loss). RETAIN variables are saved in a special kind of RAM and keep their value after a power loss. To initialize variables on every call of your FB use the VAR TEMP block. VAR_TEMP sum : INT; END_VAR
Last updated: 2024-05-07

Post by corriibme on Setting array values with JSON Utilities SL CODESYS Forge talk (Post)
I have been trying to set an array value to a JSON structure of this form: {"key": [1,2,3,4]} While I have been able to create the key and set its value to an empty array, I've not had any luck in putting any value in that array. objindex:= fb_JBuilder.SetKeyWithArray("Key6", diParentIndex := diRootIndex); objindex2:= fb_JBuilder.SetValue(value:= iValue2, diParentIndex:= objindex); iValue2: ARRAY[0..3] OF INT:= [1,2,3,4]; The two lines of code above produce {"key6": []} . The second line essentially has no effect.
Last updated: 2024-05-12

Post by wiresplus on Display minutes as hours & minutes CODESYS Forge talk (Post)
Hello, I have a counter that increments an INT value once per minute I want to display this value in Minutes until 60, then Hours/Minutes thereafter on the HMI Codesys V3.5 SP16 I can divide the minutes by 60 to get hours, but then the minutes is still more than 60. Example: a process has run for 350 Minutes. I need to display "5 Hours 50 Minutes" But if it's only been 45 Minutes, I don't want "0 Hours 45 Minutes" , just "45 Minutes"
Last updated: 2024-05-25

Post by talhaali on Create an alarm list without use of Alarm config CODESYS Forge talk (Post)
Hi, I am trying to access active alarms in code(As alarm count variable updates only when we go to to alarm table frame in visualization). I wrote following code but it is not working: VAR iCountActiveAlarms : INT; parritfActiveAlarms : POINTER TO ARRAY[0..0] OF IAlarm; itfAlarmManagerClientAll : IAlarmManagerClient; END_VAR AlarmManager.g_AlarmHandler.GetActiveAlarms( itfAlarmManagerClient :=itfAlarmManagerClientAll, iCountActiveAlarms => iCountActiveAlarms, parritfActiveAlarms => parritfActiveAlarms); The Value is always 0. Please help.
Last updated: 2024-06-06

Post by talhaali on Create an alarm list without use of Alarm config CODESYS Forge talk (Post)
Hi, I am trying to access active alarms in code(As alarm count variable updates only when we go to to alarm table frame in visualization). I wrote following code but it is not working: VAR iCountActiveAlarms : INT; parritfActiveAlarms : POINTER TO ARRAY[0..0] OF IAlarm; itfAlarmManagerClientAll : IAlarmManagerClient; END_VAR AlarmManager.g_AlarmHandler.GetActiveAlarms( itfAlarmManagerClient :=itfAlarmManagerClientAll, iCountActiveAlarms => iCountActiveAlarms, parritfActiveAlarms => parritfActiveAlarms); The Value is always 0. Please help.
Last updated: 2024-06-06

Post by artplc on 3.5 P20 hangs - no response CODESYS Forge talk (Post)
Subject: Solution: CODESYS Freezes Linked to Large Symbol Configuration (OPC UA) Hello everyone, I was experiencing the same problem as many here: CODESYS (v3.5 SP20+) freezing during compilation and download, especially on projects that use OPC UA for SCADA. The only workaround was to run Build > Clean all before every download. I believe I have found the root cause and a permanent solution. The Problem: The issue is directly related to a large Symbol Configuration. In my project, I only need about 700 tags for OPC UA, but the Symbol Configuration list was showing over 250,000 tags. This is because it automatically includes all variables from Global Variable Lists (GVLs) and other memory areas. When any static variable is changed, the IDE tries to rebuild this enormous list, causing it to freeze for several minutes. The Solution: Instead of letting CODESYS export every variable by default, you can use a pragma to tell it which variables or GVLs to exclude from the symbol export process. Place the following pragma at the top of any GVL or data structure that you do not want to be part of the symbol configuration: 1 {attribute 'symbol' := 'none'} 2 VAR_GLOBAL 3 // All variables in this GVL will now be excluded from the 4 // Symbol Configuration by default. 5 InternalVariable1 : INT; 6 InternalVariable2 : BOOL; 7 END_VAR After adding this pragma to all the GVLs that were not needed for OPC UA, the number of tags in my Symbol Configuration dropped to the correct amount. The compilation and download process is now fast again, with no freezing. This method is much more efficient than manually managing the symbol list in the editor. I hope this helps others who are facing this frustrating issue. Best regards.
Last updated: 2025-08-10

Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug? CODESYS Forge talk (Post)
Hallo, I have a strange problem with the recipe manager. ISSUE: When using RecipeManCommands not all values are loaded correctly. Saving a recipe with CreateRecipe(), ReadAndSaveRecipe() or ReadAndSaveRecipeAs() works without any problems. BUT: LoadRecipe(), WriteRecipe() or LoadFromAndWriteRecipe() do not load the data correctly. It is Interesting that we have a different error pattern with LoadRecipe() than with WriteRecipe() or LoadFromAndWriteRecipe(). LoadRecipe() does not load all data and WriteRecipe() or LoadFromAndWriteRecipe() overwrites some data or assigns it incorrectly. And it is also strange that LoadRecipe() writes the values to the PLC. Normally it doesn’t do it. It makes no difference whether the memory type is textual or binary. I have an object consisting of STRUCTs which is inserted in the recipe definition. Environment: Codesys V3.5 SP19 Patch 4 (64Bit), Recipe Management 4.2.0.0 *Add a project (reduced to the problem)
Last updated: 2023-11-15

Post by hazarath on How extract JSONElement containing Array data CODESYS Forge talk (Post)
I want to extract each element of an Array. Can someone help me with this. When I use JSONElementToString (part of JSON Utilities SL), I am seeing output as "ARRAY" instead of actual data. Here is the JSON content that I want to read : { "value1Unit": { "units": "M" }, "data": { "stepSize": 300.23, "points": [6,8] } } I would like to read each item of the element "points" i.e. 6 and 8. Here is the code I used, // Reading the content as JSON reader ( xExecute := execute , pwData := ADR ( converted_value ), jsonData := jsonDataStorage ); // Get the JSON Element jsonDataStorage.FindFirstValueByKey( wsKey := fidKeyVar, diStartIndex := searchElem, jsonElement => jsonElement ); JSON.JSONElementToString ( element := jsonElement , wsResult := valueWstring ); The content of the output of valueWstring is shown as "ARRAY" instead of the array items i.e. 6 and 8 Please can someone help me.
Last updated: 2024-07-30

Post by damian177 on Problem with downloading OPC UA tags by Data Source Manager CODESYS Forge talk (Post)
Hi, In Codesys V3.5 SP20, using Data Source Manager I am trying to connect to the OPC UA server and receive tags from it. The connection is ok, but the Codesys have a problem with downloading Tags group. The window (downloadingTags.jpg in attachement) never stop. After waiting for a while, I disconnect the connection and only the Server group remains downloaded, with OPC UA server diagnostic data (and this is read in Codesys). Of course, I tried connected via another OPC UA client : UaExpert , and everything works as it should, all tags are downloaded (Uaexpert.jpg screen). Has anyone on the forum encountered the OPC UA client configuration in Codesys? Is it possible to manually request the appropriate tags from the OPC server for reading in Codesys?
Last updated: 2024-09-03

Post by shabroz-gill on Exception when OPCUA datasource disconnects from Server CODESYS Forge talk (Post)
If i loose the network and the opcua data source suddenly looses connection with the server, i get an exception and my application stops working. I am using the latest version of the communication add v4.5.2.0 Is this a known issue? This makes the datasource unusable because it is inevitable that we will loose connectivity at some point, and the datasource crashing everything due to that seems to be a deal breaker. I can provide more details is someone from codesys is reading this. You can recreate is by just shutting off the Opc server after the codesys data source is connected and reading data from it. The codesys app does not crash everytime and sometimes it is able to reconnect without crashing, so you may have to try this a few times to see the exception. Best regards
Last updated: 2024-09-16

Post by taqamert on CANopen PDO Issue with Pressure Sensor in Codesys CODESYS Forge talk (Post)
Hello everyone, I am using an IFM CR0303 model PLC, which has a tilt sensor and a pressure sensor connected via CANopen. Both sensors are from the same brand (ATEK). I can read data from the tilt sensor without any issues, but I am unable to read data from the pressure sensor. I have added the EDS file in the PLC configuration and adjusted the node-ID settings. When I check with the PCAN-View application, I can see that the selected PDOs are coming through, but the data is not reaching the Codesys side. What could be the issue, and what can I try to resolve it? Can anyone help me?
Last updated: 2024-10-22

Post by milan-svarny on ModbusFB.ClientSerial Problem with Reply Timeout CODESYS Forge talk (Post)
Hi All, I have problem with ModbusFB.ClientSerial. I'm using 4 different port for Modbus communication. After some time of running program ClientSerial stops to receive data to reply buffer and all request finish with Reply Timeout. The Device sent reply correctly,that it is visible on oscilloscope and it is possible to see that data( reply )are in the device. If the usbtty device is read over external app. then it is possible to see all data which were not taken by ModbusFB.ClientSerial. The stack does not overflow or something , program runs correctly forward and no exceptions or something. The main problem it is that when the error occur than it is not possible to reset port or something or maybe i'm doing it wrong way. please help me with this issue. Thank you for any help in advice Milan
Last updated: 2025-05-23

Post by rer-code on Codesys 3.5.18.60 – Application Loss and Persistent Data Corruption CODESYS Forge talk (Post)
Hi, I’m currently managing over 50 PLCs running Codesys version 3.5.18.60. At seemingly random intervals, some of these devices experience a failure where: All persistent variables are lost. Attempting to log in results in the message: “The application does not exist on device. Do you want to create it and proceed with download?” The log shows: “Loading retain-data/bootproject failed.” From what I’ve gathered, this may be due to a corrupted persistent data file, but I’m not entirely sure how to confirm or resolve this issue. If anyone has encountered something similar or has suggestions for troubleshooting or preventing this, I would greatly appreciate your input. Best regards
Last updated: 2025-08-19

Post by ranadheer on Implementation of IEC-104 CODESYS Forge talk (Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14

Post by ranadheer on Implementation IEC-104 CODESYS Forge talk (Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14

Post by alexgooi on Function Blocks and arrays of function blocks CODESYS Forge talk (Post)
Hi Jack, I think you have to look at a FB in a different way. A Function block (Class) can contain its own data. In other words don't define loose data in your GVL, but define a instance of a FB (Object) in your GVL: Example: Function_Block Basic_Class VAR_INPUT Open_Command: BOOL; END_VAR VAR_OUTPUT Opened: BOOL; END_VAR if Open_Command then Opened := TRUE; ELSE Opened := FALSE; END_IF Global Variables Objects: ARRAY[1..100] OF Basic_Class; //Here you ar defining you objects END_VAR In your code you can directly acces the data and couple it to the IO: GVL.Objects[1].Open_Command := %IX0.0; %QX0.0 := GVL.Objects[1].Opened; //To call the code itself use: GVL.Objects[1](); If you want to take this a step further you are also able to add methods and properties to the FB/Class end thereby creating a OOIP program
Last updated: 2024-02-15

Post by dhumphries on Not able to see input data coming from eip adapter on codesys CODESYS Forge talk (Post)
Does the device have a green icon next to it when the PLC is running? If not you have some kind of communication problem, wireshark may be picking up some data but the scanner may not be configured correctly to receive the data. Check the T>O and O>T bytes and make sure they match on both the scanner and adapter. I've had very little success loading a .eds file and having the configuration work without some manual configuration. If you have a green icon, have you enabled the device to always update variables?
Last updated: 2024-03-02

Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together CODESYS Forge talk (Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18

Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together CODESYS Forge talk (Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18

Post by aria13 on Has anyone fed ESP32 sensor data into CODESYS (via MQTT/Modbus)? CODESYS Forge talk (Post)
Has anyone tried sending live sensor data from an ESP32 into a CODESYS runtime (for example via MQTT gateway or a Modbus bridge) to trigger PLC logic? I was reading an ESP32 → MQTT tutorial (https://www.theengineeringprojects.com/2021/11/esp32-mqtt.html) that shows how easy it is to publish sensor data from an ESP32, and I’m wondering how practical that is when tying the stream into industrial control software like CODESYS. I’ve also seen Arduino forum threads where people relay sensor streams to MQTT brokers and Raspberry Pi projects that bridge MQTT→Modbus, so I’m mainly curious about real-world issues: reliability, message latency, and simple patterns you’d recommend for safe PLC integration. Any tips, examples, or gotchas from folks who’ve done this?
Last updated: 2025-10-29

Post by pernockham on Trend legend naming and access/config to/of trend/legend-variables CODESYS Forge talk (Post)
Trying the web-version of trend-data. This seems to be a impressive tool, but I lack/cant find a number of what I would think are important parts. There does not seem to be a way to get away from the dot.notated variable naming in the legend.. A developer might want the dot-notation but an end-customer will surely not. For instance I want to display 12 temperatures, instead of t1, t2 etc.. they will be named. gvl_io.unit[1].trend.temps.t1_a gvl_io.unit[1].trend.temps.t1_b gvl_io.unit[1].trend.temps.t1_c gvl_io.unit[1].trend.temps.t2_a .. gvl_io.unit[1].trend.temps.t4_b.. gvl_io.unit[1].trend.temps.t4_c.. Quite a lot of unnecessary text/data taking space from the actual trend => Is there a way to access/interface the legend-data programmatically so I can change the presentation/naming?
Last updated: 2025-12-16

Post by installwhat on IDialogOpenedListener CODESYS Forge talk (Post)
Why do you develop things like this? The workflow should be highly dependent on autocomplete, then if that's not super obvious browse to definition and everything is made clear possibly with the checking of a few types. The nature of how things are done makes me think these libraries aren't developed for general use and are actually internal or for partners. The example projects include objects that don't appear in autocomplete and then lead nowhere obvious when browsing. Do you consider developer workflow when creating these libraries? Are some libraries really for public use such as Visu Utils and others not? If so which? It's really hard to tell.
Last updated: 2024-08-06

Post by george32 on TCP Server CODESYS Forge talk (Post)
Dear people, I would like to create a TCP server in my PLC program. The TCP server needs to communicate with an external device. I have been searching the internet and found that the libraries Syssocket or CAA NetBaseSrv are two possible solutions to create a TCP server. From what I have read, CAA NetBaseSrv is more user-friendly to implement than the Syssocket variant. However, I am still struggling to actually implement this library. Foremost is my little knowledge about creating a TCP server and how to read/understand each function block, especially the outputs of some blocks and the types, e.g. server has an output CAA.Handle, but I cannot find the explanation of CAA.Handle. I tried to find a good document that can help me understand how to implement a TCP server, but I could not find it. Thank you in advance, George
Last updated: 2025-02-20

Post by pernockham on Inheritence of struct, CODESYS Forge talk (Post)
Apparently my construction will not work as any of the sub-types are not be able to accept any (further) value-initiation. Ie: string_item : log_data_base := (string_value := 'test', val_type := STRING_); is not eq to (the string_value will not be assigned): string_item_2 : log_data_string := (string_value := 'test'); Because effectively for the compiler this is eq. to a "double" assignment where the compiler sees only the first assignment (my guess). string_item_2 : log_data_base := (val_type := STRING_) := (string_value := 'test'); Im not sure this should be treated as a bug, but it would surely be nice to be able to use this construction (compiler is 3.5.20.40). Anyone see any other alternative for solution (other than 4 complete STRUCTS with all fields individually defined)?
Last updated: 2025-03-07