Post by wollvieh on License Activation Problems
CODESYS Forge
talk
(Post)
on a raspberry pi delete the folder and its content before licensing. /var/opt/codesys/cmactlicense If you plug this SD card in another raspi ( which has another hw-serial number) you'll get a second empty softcontainer. This could lead to an unlicensed PFC (it could only handle one container) The solution is: To delete the /var/opt/codesys/cmactlicense directory and content of it and then aktivate the lizenz via WibuCmRau file and Lizenzmanager.
Last updated: 2024-06-24
Post by alimans on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hi Manuknecht, Did you manage to solve the problem? Iβm facing the same issue with Windows RTE SoftMotion β it works fine as long as nothing else is open in Windows, but as soon as I start another application, the EtherCAT DC time and max jitter values spike, and then all axes stop. Iβve already sent a support request to CODESYS, but havenβt received a response yet.
Last updated: 2025-10-23
Post by ben1 on How to stay in a method until something is finished.
CODESYS Forge
talk
(Post)
Why must you use a method? Top of my head can't you just use the button to turn on a bit and use it in a normal task? Just turn a bit on with the button, and run a TON from it in code, and turn it back off with the ton. And then just log the pressure on both the rising & falling edge?
Last updated: 2025-11-03
Post by adam on Get/Set I/O Address Mapping of DeviceObjects in python Script
CODESYS Forge
talk
(Post)
I want to cancel the automatic address allocation for all IO mappings. If I directly set the automatic_iec_address in class ScriptIoMapping to False, the address becomes None. So I reset manual_iec_address with itselfs value. It only work with the Input IOMapping . For output, it reports an error: "Invalid address: The channel type 'Output' requires address type '%Q'." I checked the description file ,both accessRight are total same. Does anyone know what causes this?
Last updated: 2025-11-14
Post by ppanchal on Add a dynamic text on One Visualization from another
CODESYS Forge
talk
(Post)
I've created a TitleBar Visualization in which I have "Logo" on the Left corner, "Screen Name" in the center and Time/ date on the right corner. I've also created a 'Menu" visualization that slides out from left to right. I have TitleBar and Menu Visualizations in the MainScreen (3rd Visualization). I want to have "Screen Name" automatically updated on TitleBar Visualization based on Menu item selected from the "Menu" visualization. Can anyone advise how can I achive this? TIA
Last updated: 2025-11-18
Post by imdatatas on SMC_ERROR.SMC_AXIS_NOT_READY_FOR_MOTION when using Drive Virtual
CODESYS Forge
talk
(Post)
@ducng, Another possible situation could be that normally there are 3 inputs for MC_Power. In your above images, I can't see the "bDriveStart" input activated. As Mr. @gseidel mentioned, you need to make sure MC_Power.Status output should be TRUE. Issuing any movement command without activating the axis would naturally result in an error. For MC_Power; You can set the Enable and bDriveStart inputs to TRUE and try turning the axis activation on and off using only the bRegulatorOn input. Regards, Imdat
Last updated: 2025-11-28
Post by gseidel on MC_Phasing state explenation
CODESYS Forge
talk
(Post)
Hi kenth1973, MC_Phasing has been improved in recent versions. I would recommend to install the latest version of SoftMotion (4.20.1.0) and test whether the problem still exists, and if so, what the error identifier is. (Also check the PLC log in this case, it might contain additional information.) Setting the internal state of the FB is not recommended, it could lead to malfunction of the FB and unintended movements of the drive. Best regards, Georg
Last updated: 2025-11-28
Post by harryc on Soft Container License issue with ARM64 Linux
CODESYS Forge
talk
(Post)
hi @eschwellinger Thanks for the hint. This is what I get with "cmu -x" There is no Dongle. I think that I'm trying to install the soft container from CODESYS development system, where I have the licensed installed in the License Repository. The development system gives me the error when I try to install the Soft Container license. # cmu -x - CodeMeter Universal Support Tool. Version 8.20 of 2024-Sep-10 (Build 6539) for Linux/ARMHF 64-Bit Copyright (C) 2007-2024 by WIBU-SYSTEMS AG. All rights reserved. #
Last updated: 2025-12-10
Post by gseidel on Scara3 kinematic robot error
CODESYS Forge
talk
(Post)
Hi aniket-b, this error has nothing to do with the scara3 kinematics, or robotics, or SoftMotion. It means that the EtherCAT bus is not synchronized. The usual cause is that the realtime of the PLC is not sufficient. See https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_basic_common_errors.html for details and ways to solve the problem. You can also check the PLC log for additional information about the error. Best regards, Georg
Last updated: 2025-12-23
Post by bertus on Axis directions in CNC editor not using right-hand rule?
CODESYS Forge
talk
(Post)
Hello, Coming from robotics, I'm used to coordinate systems using the right-hand rule. But when I created below small NC program in the Codesys CNC editor, I noticed that the axis triad's Z-axis is flipped (see attached screenshot), resulting in left-hand rule. Is there a setting to change this? Or am I misunderstanding something in the CNC world? N000 G00 X0 Y0 N010 G01 X100 N020 G01 Y50 N030 G01 X0 N040 G01 Y0 N050 G01 Z25
Last updated: 2026-01-02
Post by axberry on CODESYS Control for Raspberry Pi 5 - "Hardware version or firmware version not supported" on Rev 1.1, persists across multiple runtime versions and OS images
CODESYS Forge
talk
(Post)
Hi, I'm trying to run CODESYS Control for Raspberry Pi SL on a Raspberry Pi 5, and the runtime consistently fails to start with the following error when launched manually: ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-18, 0x00000BB8, 0xFFFFFFFB) Hardware: Raspberry Pi 5 Model B Rev 1.1 Revision code: d04171 CPU: aarch64, BCM2712 Serial number is correctly exposed via /proc/cpuinfo and /proc/device-tree/serial-number /proc/device-tree/model correctly reports "Raspberry Pi 5 Model B" What I've tried (all resulting in the same error): CODESYS Control for Raspberry Pi SL 4.11.0.0 (SDK 3.5.19.61) β the version that introduced Pi 5 support CODESYS Control for Raspberry Pi SL 4.21.0.0 (SDK 3.5.22.20) β latest available Raspberry Pi OS Bookworm (64-bit) with kernel 6.12.93+rpt-rpi-2712 (June 2026 build) Fresh install on Raspberry Pi OS Bookworm (64-bit) with an older image from November 24, 2025 β same error, ruling out a kernel-version regression Bootloader/EEPROM confirmed up to date (rpi-eeprom-update reports "up to date") Clean purge and reinstall of the codesyscontrol package each time (verified via dpkg -l, no leftover files) Verified /etc/codesyscontrol/3S.dat correctly symlinks to /etc/codesyscontrol/3S_aarch64.dat The service starts (systemctl status briefly shows active (running) with a real PID under /opt/codesys/bin/codesyscontrol.bin), but crashes shortly after and the process disappears β port 11740 never opens. Since this happens identically across two different runtime versions and two different OS images (5+ months apart), it doesn't seem to be a kernel/firmware timing issue. Could this be specific to the Rev 1.1 board revision, or is there a known issue with the hardware detection logic in the SL runtime that I should be aware of? Happy to provide full debug logs (-d flag output) or journalctl output if useful. Thanks in advance!
Last updated: 2026-08-10
Post by dmb-fan on From target start Win OnScreenKeyboard
CODESYS Forge
talk
(Post)
Hi ! I am get crazy.... I try to start osk.exe from Visu or PLC. From Visu I can't load it, always error (It change from programm execute always to load receipe ..!?!?) From PLC always freeze of PLC, - I allowed the win service of the PLC the data exchange between desktop and service - I allowed in ..user.cfg [SysProcess] Command=AllowAll Shutdown with SysProcessExecuteCommand works, but 'osk.exe' or the complete path always crashed the system. And like always: No documentation. Just guessing. Or know somebody more and have a link for me? THANKS !
Last updated: 2026-10-27
Post by gseidel on Axis directions in CNC editor not using right-hand rule?
CODESYS Forge
talk
(Post)
Hi bertus, the coordinate systems used in SoftMotion CNC are all right-handed. The CNC editor uses isometric projection. This can be confusing, as in your example. The y-axis seems to point into the screen, away from the viewer. However, this is just an optical effect. If you turn on the (experimental) perspective projection (must be added to the CNC tool bar using tools->customize), you can see that the coordinate system is in fact right-handed. Best regards, Georg
Last updated: 2026-01-07
Post by codegunner on how to convert library from CodeSys 2.3 to CodeSys 3.x ?
CODESYS Forge
talk
(Post)
hello, ive tried everything and keep getting error like i have opened a file in read only so cannot save no idea what is causing it, file is not read only i cannot even open a new file i make with one variable in 2.3, get same error for read only. do you have a 2.3 file you can send me tomtry and open for a test? thanks
Last updated: 2026-04-29
Post by srinidhi on Pilz PBRT Robot with CoDeSys
CODESYS Forge
talk
(Post)
If anyone here are working with robots and using Codesys to control it and implement tasks, Please let me know. I am currently in my Master thesis and i need some advice on this. We have Pilz Robot with Codesys and I am trying to proceed with certain tasks but have no documentation for it. Would be helpful if anyone of you can suggest and help connect with the right people.
Last updated: 2026-05-10
Post by baltzer on ICertificateVerifier.VerifyCertificate doesn't appear to override an ERR_CERT_HAS_EXPIRED rejection in TCP_Client.Upgrade()
CODESYS Forge
talk
(Post)
Follow-up: working workaround found (routing TLS outside CODESYS) For anyone finding this thread later with the same problem (a third-party device presenting a self-signed and/or expired certificate that ICertificateVerifier/udiVerificationMode won't let you connect through) - we never got a working fix within NBS itself, but found a practical workaround worth sharing. Approach: run a local TLS-terminating proxy on the same host as the CODESYS runtime, and have CODESYS talk plain, unencrypted TCP to it instead of connecting to the remote device directly over TLS: CODESYS --plain TCP--> 127.0.0.1:<port> --stunnel/TLS--> <remote device>:<port> We used stunnel (client mode), with certificate verification explicitly disabled at that layer (verifyChain = no, verifyPeer = no) - a simple, well-documented one-line option, unlike anything we could get working inside NBS. Running it as a systemd service with Restart=always means it survives reboots and recovers automatically if the proxy or the remote device drops. On the CODESYS side, this required no changes beyond pointing TCP_Client at 127.0.0.1 instead of the device's real IP, and removing the TLSContext/ICertificateVerifier code entirely - the rest of our application-layer logic (framing, checksums, etc.) was completely unaffected, since none of that ever depended on where the TLS termination happened. Confirmed working end-to-end against a real device with an expired self-signed certificate, running on CODESYS Control for Raspberry Pi SL (Linux). We haven't yet set this up on Windows - stunnel does have Windows builds available, so the same general approach should be possible there too, but that combination isn't tested or confirmed by us at this point. Caveat: this only makes sense when the proxy and the CODESYS runtime are on the same trusted host (in our case, both on the same Raspberry Pi) - don't expose the proxy's plaintext side on a reachable network interface, since that would create an unauthenticated plaintext path to the device. The original question - whether there's a supported way to override an ERR_CERT_HAS_EXPIRED/self-signed rejection from within NBS's own TLSContext/ICertificateVerifier - remains open as far as we know. Still happy to hear from anyone who's solved that particular piece, since the workaround above is a practical detour rather than an actual answer to the original question.
Last updated: 2026-08-06
Post by dhumphries on Codesys Installation problem
CODESYS Forge
talk
(Post)
Installing codesys has been the biggest point of frustration for me and is the reason I'm currently working on building a VM just for the codesys engineering software so once I get a working installation I can copy the VM to new workstations instead of fighting with the installer every time I get a workstation upgrade. The best advice I've gotten in the past is to uninstall everything and start over, this is successful 50% of the time. Also don't install the latest version it's usually less stable than an older one ironically.
Last updated: 2026-08-10
Post by luca03 on OPC UA information model into the Communication Manager
CODESYS Forge
talk
(Post)
Hello, unfortunately I am unable to load an OPC UA information model as a NodeSet2.xml file into the CODESYS Communication Manager. Importing via Tools -> OPC UA Information Model Repository still works, but when I try to load the model explicitly, CODESYS crashes without displaying an error message. Has anyone else encountered this problem, or does anyone have any suggestions? Thanks in advance
Last updated: 2026-08-22
Post by jgalaska on SMC_Trafo 6DOF Config Error
CODESYS Forge
talk
(Post)
Hello, Recently I was trying to run 6DOF robot in codesys via SMC_Trafo_ArticulatedRobot_6DOF, unfortunately no matter what parameters I tried, it always outputs InvalidConfig Error. I saw the same issue in a topic: https://forge.codesys.com/forge/talk/Motion/thread/16e1f0327f/ But if I understand correctly, the user solved it by developing his own version of this block. I wanted to know if it is a bug in the library (SM3_CNC 4.20.0.0) or am I doing something wrong? Can anyone confirm that they can use the FB without it reporing the Error? Kind regards,
Last updated: 2026-01-21
Post by aapostolidis on _NEW when used with classes and interfaces. Interface shows "Hidden Instance" in watch.
CODESYS Forge
talk
(Post)
Hello, im using dynamic memory allocation with the NEW()-operator. When i instanciate a class with the NEW()-operator and want to debug/watch the interface of the class, the watch is only showing "Hidden Instance" (See attached screenshot). Is there any possibility to debug the interface data ? The interface is working properly but the debugging by the watch is not possible, what is a big disadvantage. Thank you. Best Regards, Alexander
Last updated: 2026-03-24
Post by lofty on CODESYS Download Issue
CODESYS Forge
talk
(Post)
I am attempting to install CODESYS 3.5.22.20 and the installer gets stuck at "Install Package CODESYS Compatibility Package 3.5.17.20" every single time. I've tried reinstalling the software multiple times and the same issue persists. I've tried running the installer as an administrator and even turned off my virus protection and the same issue persists. I've attached a photo for reference. Has anyone run into this issue before or have any idea what I can do to complete the install?
Last updated: 2026-05-26
Post by dmb-fan on Attemp Convert old V2.3 projects : Error HRESULT: 0x80010105 (RPC_E_SERVERFAULT))
CODESYS Forge
talk
(Post)
I had runnig this already. Then I updated to SP22 patch3. After that I got always this error: ===== Project importieren: XXXXnameYYYYYY ===== *[FATALER FEHLER] Fehler beim Import des Projekts: Ausnahmefehler des Servers. * [FATAL ERROR] Error importing the project: Server exception. (Exception to HRESULT: 0x80010105 (RPC_E_SERVERFAULT)) I delete the version and installed again. Same. I uninstalled all CoDeSys on the PC and installed the old SP22 patch2 new. Same error by opening old projects. Immediatly, not by converting. Convert V3.5.17 was always installed. What is happening or what can I do?
Last updated: 2026-08-11
Post by tarek on How to add/Scan devicenet Master/Slave
CODESYS Forge
talk
(Post)
Hello, i have a similar problem with this. Im using an EL6752 from Beckhoff DeviceNet Master and i dont have an EDS for the comms with the slave (EVO GT II Valve). In CODESYS they dont let me put a digital slave. My question, how can i add a slave in the EL6752 the Process data mapping to see values. I cant add a DeviceNet slave in the tree, thanks
Last updated: 2026-09-14
Post by dmb-fan on From target start Win OnScreenKeyboard
CODESYS Forge
talk
(Post)
Hi ! I am get crazy.... I try to start osk.exe from Visu or PLC. From Visu I can't load it, always error (It change from programm execute always to load receipe ..!?!?) From PLC always freeze of PLC, - I allowed the win service of the PLC the data exchange between desktop and service - I allowed in ..user.cfg [SysProcess] Command=AllowAll Shutdown with SysProcessExecuteCommand works, but 'osk.exe' or the complete path always crashed the system. And like always: No documentation. Just guessing. Or know somebody more and have a link for me? THANKS !
Last updated: 2026-10-27
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.