Post by dominggus on FileDialog - OnDialogClosed not called anymore
CODESYS Forge
talk
(Post)
Hi, since the latest update it seems the OnDialogClosed is not called anymore?? using CODESYS SP20 Patch 3 with CODESYS Visualization 4.6.0.0 I am using LoadWriteRecipe to load a recipe file from disk (with some custom dialog settings), and I need to run a function (Recipes_LoadFromRecipeData()) afterwards which I execute when OnDialogClosed is closed with OK button. See attached screenshot and code below: *** OnDialogClosed : Recipes_OnLoadFileDialogClosed(pClientData): *** // the DialogManager is provided via the implicitly available VisuManager dialogMan := VisuElems.g_VisuManager.GetDialogManager(); IF dialogMan <> 0 AND pClientData <> 0 THEN FileOpenCloseDialog := dialogMan.GetDialog('VisuDialogs.FileOpenSave'); // gets the FileOpenSave dialog IF FileOpenCloseDialog <> 0 THEN result := FileOpenCloseDialog.GetResult(); // gets the result (OK, Cancel) of the dialog IF result = VisuElems.Visu_DialogResult.OK THEN Recipes_LoadFromRecipeData(); END_IF END_IF END_IF *** OnMouseClick: Execute ST-Code *** // override FileOpenSave Dialog settings // Visu_FbFileListProvider.Initialize(stDirectory, stFilter, stFileIn, stTitle, iRowCount, bBrowseDirectory, bTouch) VisuDialogs.g_FileListProvider.Initialize('./', '*.bunkerrecipe', '', 'Load recipe', 20, TRUE, FALSE); VisuDialogs.g_FileListProvider(); This used to work in CODESYS v3.5 SP20 Patch 1, but it seems it doesn't work anymore unfortunately? The OnDialogClosed just never seems to be called anymore....
Last updated: 2024-12-18
Post by timvh on When Keyboard Key is in Hold, then Webvisu is extreme slow and latent
CODESYS Forge
talk
(Post)
I'm not really sure what you are trying to do, but maybe you are referring to using the CmpCharDevice library? When you "open" the connection to a device, you can pass flags. What helped me is to set the non-blocking flag. I'm not sure if this is what you are referring to, but maybe it helps: dFlags: DINT := CmpCharDevice.ACCESS_MODE.O_RDONLY + DINT#4000; // see details for flags: http://linux.die.net/man/2/open, + DINT#4000 is for non-blocking hDevice := CmpCharDevice.CDOpen(szFilename, dFlags, Result);
Last updated: 2023-09-20
Post by andre-luis on Device diagnosis ( EtherCAT IO card )
CODESYS Forge
talk
(Post)
Hi @TimvH, In the meantime, I did some experiments and could find a way to achieve similar result. I made some tests, removing the last card from the array, seeing the change on status. PROGRAM P_IOS_STATUSES VAR devStateInput : DEVICE_STATE; devStateOutput : DEVICE_STATE; devStateEncoder : DEVICE_STATE; END_VAR devStateInput := IoConfig_Globals.EL1819.GetDeviceState(); devStateOutput := IoConfig_Globals.EL2809.GetDeviceState(); devStateEncoder := IoConfig_Globals.EL5151.GetDeviceState(); GVL.bInputCardOK := ( devStateInput = DEVICE_STATE.RUNNING ); GVL.bOutputCardOK := ( devStateOutput = DEVICE_STATE.RUNNING ); GVL.bEncoderCardOK := ( devStateEncoder = DEVICE_STATE.RUNNING ); Many thanks for your quick and extensive reply.
Last updated: 2025-02-06
Post by sandro66 on Application-based license Modbus Channels
CODESYS Forge
talk
(Post)
Hi Gatto, Using version 3.5.21.xx, it is no longer possible to use Modbus function blocks (I make extensive use of these FBs.)as shown in the example. https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_modbus_example.html The compiler detects one Modbus instance for each instance of the communication FB block. The example program above, although simple, reports 8 Modbus instances when compiled with the latest version. Codesys Support says that you must use fieldbus I/O mapping, but this will result in the loss of the ability to programmatically modify communication parameters. Sandro
Last updated: 2025-09-04
Post by amy123 on CSV Utility CANNOT_OPEN_DIRECTORY
CODESYS Forge
talk
(Post)
Hello, I tried using the CSV Utility SL Example from the CODESYS IIoT Libraries SL. No matter what path I try, I can not get the InitSave to work from CSVWRitersSTExample, line 2. It always gives the error 'CANNOT_OPEN_DIRECTORY'. I am running this on an Windows Azure VM, with Codesys Control Win V3 x64. I added a folder called 'temp' to my C: so that the default 'C:/temp' would work. However it gives CANNOT_OPEN_DIRECTORY. I tried updating to 'C:\temp' with the same result. Any help would be greatly appreciated!
Last updated: 2024-02-14
Post by androidzz on Json Builder problem?
CODESYS Forge
talk
(Post)
Dear reader, I am using the codesys JSON utilities SL, 1.9.0.0 library. And then specifically the FB JSONBuilder. I need to create a main object with at least 2 objects in it. The first object is no problem, but I cannot insert the second object into the main object. See attached my code and the result I get. I am assuming that I am doing something wrong with the parent index but have tried a lot and can't get it done. Kind regards, Rob
Last updated: 2024-03-11
Post by superjojo2002 on Licensing info not available.
CODESYS Forge
talk
(Post)
I checked it using the very same docker container version like colleague moon and the command returned root@nt0001c02c5533:/# cmu -x cmu - CodeMeter Universal Support Tool. Version 7.60c of 2023-Aug-09 (Build 5625) for Linux/ARMHF 64-Bit Copyright (C) 2007-2023 by WIBU-SYSTEMS AG. All rights reserved. Result: 0 CmContainer(s) listed. (CodeMeter not running) Please consider that we intend to license a codesys ARM64 SL in a docker container.
Last updated: 2024-03-20
Post by imdatatas on SMC_ERROR.SMC_AXIS_NOT_READY_FOR_MOTION when using Drive Virtual
CODESYS Forge
talk
(Post)
@ducng, Another possible situation could be that normally there are 3 inputs for MC_Power. In your above images, I can't see the "bDriveStart" input activated. As Mr. @gseidel mentioned, you need to make sure MC_Power.Status output should be TRUE. Issuing any movement command without activating the axis would naturally result in an error. For MC_Power; You can set the Enable and bDriveStart inputs to TRUE and try turning the axis activation on and off using only the bRegulatorOn input. Regards, Imdat
Last updated: 2025-11-28
Post by rtlman on Scan devices hangs CODESYS
CODESYS Forge
talk
(Post)
Hello, I have a problem that randomly appeared today. When trying to scan a network adapter in "Deploy Control SL" the whole program hangs and needs to be restarted. I have been running "CODESYS v3.5 SP21 Patch 3" for a while and it has worked without any issues until now. I've tried upgrading to "CODESYS v3.5 SP21 Patch 4" with the same result. I've not made any system settings recently that im aware of which could cause this. Has anybody had similar a issue?
Last updated: 2025-12-12
Post by ryusoup on JSONByteArrayWriter problem?
CODESYS Forge
talk
(Post)
Hello, I am trying to implement a FB to make JSON formatted WSTRING type message using JSON Utilities 1.9.0.0 included in the IIoT library. In my case, I want to set some objects or arrays and set values to them later. But when I wrote as the sample below, // init builder builder(pJsonData:=pJsonData, diRootObj=>diRootObj); // set the 1st key to root diKey1 := builder.SetKeyWithArray(wsKey:="key1", diParentIndex:=diRootObj, eError=>eError); // set a value to the 1st key wsValue:="value01"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set the 2nd key to root diKey2 := builder.SetKeyWithArray(wsKey:="key2", diParentIndex:=diRootObj, eError=>eError); // set a value to the 2nd key wsValue:="value02"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // set a value to the 1st key again wsValue:="value03"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set a value to the 2nd key again wsValue:="value04"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // write build result writer(xExecute:=TRUE, pwData:=ADR(wsResult), udiSize:=SIZEOF(wsResult), xAsyncMode:=FALSE, jsonData:=pJsonData^); the result was: { "key1": ["value01"], "key2": ["value02", "value03", "value04"] } while my expection was: { "key1": ["value01", "value03"], "key2": ["value02", "value04"] } Inspecting pJsonData^, JSONData itself seems to be ok, so I believe the issue is something caused by the writer FB. Does anyone know how to fix it? Thanks,
Last updated: 2023-10-04
Post by otbeka on CmpCrypto CryptoGenerateHash Not Outputting
CODESYS Forge
talk
(Post)
Hi, I have been trying to use CryptoGenerateHash from the CmpCrypto Implementation library. My code is taken almost directly from the CryptoDemo.project example provided on Codesys Forge, yet the CryptoGenerateHash function does not write to the address listed in pHash. RTS_IEC_RESULT is OK, but I am getting nothing out of the function. No errors either, all my libraries are up to date. Any help would be appreicated! PROGRAM PLC_PRG VAR sMessage : MESSAGE := 'The red fox runs across the ice'; abyHashCode : HASH_CODE := [ 16#52, 16#ED, 16#87, 16#9E, 16#70, 16#F7, 16#1D, 16#92, 16#6E, 16#B6, 16#95, 16#70, 16#08, 16#E0, 16#3C, 16#E4, 16#CA, 16#69, 16#45, 16#D3 ]; xMessageOK : BOOL; END_VAR xMessageOK := CheckMessage(sMessage, abyHashCode); FUNCTION CheckMessage : BOOL VAR_INPUT sMessage : REFERENCE TO MESSAGE; abyHashCode : REFERENCE TO HASH_CODE; END_VAR VAR _hHASH : RTS_IEC_HANDLE := CryptoGetAlgorithmById(ui32CryptoID:=RtsCryptoID.HASH_SHA1, pResult:=0); Result : RTS_IEC_RESULT; bsMessage : RtsByteString := (ui32MaxLen:=SIZEOF(sMessage), pByData:=ADR(sMessage), ui32Len:=TO_UDINT(LEN(sMessage))); abyNewHashCode : HASH_CODE; bsNewHashCode : RtsByteString := (ui32MaxLen:=SIZEOF(abyNewHashCode), pByData:=ADR(abyNewHashCode)); diCmpResult : DINT; END_VAR Result := CryptoGenerateHash(hAlgo:=_hHASH, pData:=ADR(bsMessage), pHash:=ADR(bsNewHashCode)); diCmpResult := SysMemCmp(pBuffer1:=ADR(abyHashCode), pBuffer2:=ADR(abyNewHashCode), udiCount:=SIZEOF(HASH_CODE)); CheckMessage := diCmpResult = 0;
Last updated: 2024-09-06
Post by ojz0r on Assignment Efficiency - Repetitive Assignment vs IF statement
CODESYS Forge
talk
(Post)
Its important that you know the difference between the two. Example 1: Coils[0] := Coils[0] OR (Buttons[0] AND Sensors[0] > 6); In this case the statements will be evaluated every scan and result in either true or false for Coils[0]. Example 2: IF NOT Coils[0] AND Buttons[0] AND (Sensors[0] > 6) THEN Coils[0] := TRUE; END_IF In this example Coils[0] will latch the result in a true evaluation, if you want it to behave the same way as example 1 then you need to do it like example 3 below: IF NOT Coils[0] AND Buttons[0] AND (Sensors[0] > 6) THEN Coils[0] := TRUE; ELSE Coils[0] := FALSE; END_IF However back to the real question. There is no problem using either example 1 or example 3, if im not requiring a latch i usually go with example 1 as it is more compact.
Last updated: 2025-03-07
Post by dtamm on How to read string from CharBufferPtr?
CODESYS Forge
talk
(Post)
I am trying to implement a mechanism to send alarm SMS. For this, I have created an Alarm Class with a Notification Action which calls a POU. This POU implements IAlarmNotifiable making it selectable in the Alarm Class configuration. IAlarmNotifiable has an Execute method which is called by the alarm class. Now, I want to extract the alarm message of the triggered alarm. The Execute method comes with a VAR_INPUT itfAlarm: AlarmManager.IAlarm which supplies a method called GetMessage. The help text says: Returns the message text, that has been configured for the alarm. The result is a pointer to the buffer, where the message text is stored The type of the result is CharBufferPtr, and at some place I read that it can be interpreted as a pointer to string. But I cannot manage to extract the alarm message, all I get are numbers. I have tried the following: psAlarmText := itfAlarm.GetMessage(__SYSTEM.TYPE_CLASS.TYPE_STRING)^; sAlarmText := TO_STRING( itfAlarm.GetMessage(__SYSTEM.TYPE_CLASS.TYPE_STRING)^ ); So how do I get access to the alarm message as clear text? (In this case, "Larm 1")
Last updated: 2024-02-21
Post by francescoc on Custom log CmpLog
CODESYS Forge
talk
(Post)
Hi, I am trying to create a log in my application. Since I cannot find any documentation regarding modifying the codesys configuration file to be able to log in ms, i tried to create a new log via CmpLog.LogCreate. Below is the part of the code where I create the logger and write a test string. In the log tab of codesys I actually see the new log that was created, but it is empty, and in the folder I cannot find any files. I can't find any detailed documentation. Can you guys give me support? Are there any examples? Thank you IF NOT FirstCycle THEN LogName:= 'LOGS/TestLog'; LogOptions.bEnable:= 1; LogOptions.iMaxEntries:= 5000; LogOptions.iMaxFiles:= 100; LogOptions.iMaxFileSize:= 5000; LogOptions.szName:= LogName; LogOptions.uiType:= CmpLog.LogTypes.LT_TIMESTAMP_RTC_HIGHRES; LogOptions.uiFilter:= CmpLog.LogClass.LOG_ALL; LogHandle:= CmpLog.LogCreate(pOptions := ADR(LogOptions), pResult:= ADR(Result)); LogHandle:= CmpLog.LogOpen(pszName:= LogName, pResult:= Result); Component_Manager.CMAddComponent2('TestLogNEW', 16#00000001, ADR(udiCmpIdNEW), 0); CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Logger started...'); END_IF IF TestWrite THEN TestWrite:= FALSE; CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Write test'); END_IF
Last updated: 2024-03-16
Post by ilya-vah on Table element issues
CODESYS Forge
talk
(Post)
Hello, First post here. I would like to clarify whether the following behavior is known or if it is a bugs. Issue 1 β First row not displayed when using Maximum array index with 1-based arrays Description: When displaying data from an array that is indexed starting from 1 (e.g., ARRAY[1..N]), and the number of displayed rows is limited using the Maximum array index property, the first row of the array is not shown in the visualization. Steps to reproduce: Create an array indexed from 1 (e.g., ARRAY[1..N]). Bind the array to a Table element. Limit the number of displayed rows using the Maximum array index property. Run the visualization. Actual result: The first array element (index 1) is not displayed in the table. Issue 2 β Tooltip string placeholder cannot be bound to string variable from array Description: It is not possible to use a string placeholder in the tooltip that is bound to a string variable from the array. Steps to reproduce: Use a table bound to an array containing string variables. Configure a tooltip using a string placeholder referencing a string field from the array. Run the visualization. Actual result: Tooltip doesn't show any text. A test project demonstrating both issues is attached. Thank you for your time and support.
Last updated: 2026-02-16
Post by eschwellinger on Editor FIND highlight color
CODESYS Forge
talk
(Post)
To change the color of search result markings (the "find color") in the CODESYS Text Editor using Themes, follow these steps: Go to the menu: Tools β Options. In the Options dialog, select the Text editor category. Switch to the Theme tab. Here, you can select your desired color theme for the text editor. The available color schemes (themes) are stored in the installation directory in the Themes folder. To specifically adjust the color for search result markings, go to the Text Area tab within the Text editor options. Here, you can customize the Selection color β Inactive parameter, which determines the color used to highlight search results. Changing the theme will apply a new set of color settings, including those for selections and search highlights. If you want further customization, you can manually edit or create your own theme files in the Themes folder of your installation directory Example "c:\Program Files\CODESYS 3.5.21.50\CODESYS\Themes\myDefault.editortheme" https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_dlg_options_text_editor.html
Last updated: 2026-03-12
Post by danielbeers on Automation Server + Pi Gateway + PLC w/ CAN
CODESYS Forge
talk
(Post)
Hello, I have a project using some EPEC PLC's. Some of them are programmable using Ethernet and some use CAN. We currently have a Raspberry Pi that is acting as a gateway to the Codesys Automation Server and is successfully working for the PLC's communicating over ethernet. I am trying to achieve a similar result for the PLC's that have only CAN access. I have PEAKCan drivers on the Pi, and can successfully send/receive messages. But the Gateway does not recognise the PLC when scanned from the Automation server online. Is there a library or service that exists to translate the CAN messaging, to the Edge Gateway, and be able to achieve remote access with the Automation Server? Or is this not possible without creating something custom? Cheers, Daniel
Last updated: 2024-09-22
Post by cihangur on OpC UA server on Raspberry Pi 64 SL runtime
CODESYS Forge
talk
(Post)
After my tests, I noticed two issues. 1- WinCC disconnects the connection after receiving the GetEndPointResponse message from CoDeSys. (I found it with UAExpert and Wireshark.) 2- It establishes a connection despite waiting for a while on the network with DNS. As a result of this information: I solved the problem by adding the line "193.193.193.150 t9pac" to the C:\Windows\System32\Drivers\etc\hosts file and making Windows accept messages coming from the IP number 193.193.193.150 as coming from t9pac. (t9pac is the name of my PLC running CoDeSys.) If there is a setting that will allow CoDeSys OPC UA to respond to GetEndPointRequest with its IP address, this problem will not occur.
Last updated: 2024-12-12
Post by milosfejgl on Codesys Licenses - How to reload them after updating the Raspberry Pi OS
CODESYS Forge
talk
(Post)
We use several control units running on Raspberry Pi, programmed using Codesys software, with multiple licenses stored as soft containers. We are planning to update the SD card image of the Raspberry Pi to a newer OS version. However, we are concerned that this process might result in the loss of our soft container licenses. Is there a way to temporarily deactivate the license so that it can be reactivated on the updated system? Alternatively, what would be the best method to preserve the licenses during the update? Thank you in advance for any responses!
Last updated: 2025-03-13
Post by benemenn on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
so from what i've learned. Codesys OPCUA Server can only provide OPC UA Methods, when they are created in an XML Model beforehand. So you have to create the XML Model with OPC UA Methods. Then load that model into codesys and create the IEC Blocks. This is automated Code and will create all the variables and Methods from your XML Model. Then they will be displayed on discovery with an OPC UA Client. As far as I understood. There is no way for Methods to be shown in OPC UA when not using an external XML Informationmodel. Codesys can not yet create the informationmodel on itself. Regards
Last updated: 2025-04-02
Post by benemenn on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
so from what i've learned. Codesys OPCUA Server can only provide OPC UA Methods, when they are created in an XML Model beforehand. So you have to create the XML Model with OPC UA Methods. Then load that model into codesys and create the IEC Blocks. This is automated Code and will create all the variables and Methods from your XML Model. Then they will be displayed on discovery with an OPC UA Client. As far as I understood. There is no way for Methods to be shown in OPC UA when not using an external XML Informationmodel. Codesys can not yet create the informationmodel on itself. Regards
Last updated: 2025-04-02
Post by pernockham on Control for linux SL, 4.14.0.0 -> 4.15.0.0 breaks web page access. URL requires authentication
CODESYS Forge
talk
(Post)
I have a problem which I have identified with a device-update from 4.14.0.0 to (4.15.0.0-4.17.0.0) where the newer versions will stop any local access to the internal web page with the browser responding "The requested URL requires authentication". Setting the device back to 4.14.0.0. the web page will respond. Access to web page through Automation server is possible also for the newer version, but not "local" access. Runtime (Codesys control for linux SL) is on 4.17.0.0. I have tried to manipulate settings for 'Access-Control-Allow-Origin' '*' always; through nginx (normally a proxy_pass to localhost:8080). Also tested bypassing nginx by accessing 8080 directly with the same result.
Last updated: 2025-09-08
Post by fdmartello on Unable to compare projects containing alarm manager 4.5.0.0
CODESYS Forge
talk
(Post)
Hello. In Codesys version 3.5.19.50 when comparing two projects that have an "Alarm Configuration" obj from the Alarm Manager library vers. 4.5.0.0 the attached error pops up. This originally happened with two projects that I converted from vers. 3.5.17.30 so, thinking it was some conversion issue, I created two clean projects directly in 3.5.19.50 using the Standard Project template and only added the Alarm Configuration objects in them. The result is the same and the only way I found that allowed me to compare them is by deleting the incriminated object in one of the two projects. Has anyone else encountered this issue? Best regards
Last updated: 2024-01-19
Post by alexgooi on Is it possible in the log to see previous shutdown
CODESYS Forge
talk
(Post)
Hi DavidBo, In general Codesys is used to control equipment and an exception is the worst thing that can happen in your installation. If you cannot prevent the exception from triggering, you could implement a Try catch statement, with this solution your controller keeps on running and you are able to handle the exception. __TRY //This statement will trigger an exception Result := 4/0; __CATCH(exc) //Handle the exception HandleException(exc, strExceptionText => strExceptionText); // From the Codesys help file //Create a log file //-------------------------------------------------------- __ENDTRY What you also could do is implement implicit checks, these functions cover most of the exceptions (like dividing by zero) See picture But in general avoid a complete controller shutdown!
Last updated: 2024-02-09
Post by arundara on OPC UA Server Stops after 5 consecutive disconnections of ethernet port
CODESYS Forge
talk
(Post)
Hello Every one, During testing of OPC UA communication between UA Expert software and the CODESYS SoftPLC on a Linux environment, an observation was made. When the Ethernet cable was disconnected and reconnected with 2-minute intervals, on the 5th attempt, the OPC UA connection failed to establish in UA Expert software. At this juncture, restarting the CODESYS SoftPLC enabled the reestablishment of OPC UA communication. The same result was obtained when testing on a Raspberry Pi SoftPLC. What is the reason behind this phenomenon? and whether there are settings to stop this behavior? Please help. Thanks & Regards.
Last updated: 2024-02-13