Search talk: CONVERSION DATA TYPE

 
<< < 1 .. 19 20 21 22 23 .. 27 > >> (Page 21 of 27)

Post by maxsus on Visu Frame-configuration___text will not work CODESYS Forge talk (Post)
Hello I have a problem with the Frame-configuration. In the picture below you can see that I set the Editor Type to variable. If it would be text it would work, but it wasnt variable anymore. Thanks for your time. Sorry, my codesys is in German.
Last updated: 2024-08-20

Post by timvh on Configuring a 2's compliment CODESYS Forge talk (Post)
You could create a DUT of the Type Union and add an array of 2 bytes + an Int. Then write the byte values in the array of the Union and read the Int. Or VAR iInt : INT; byHigh : BYTE := 2#1111_1111; byLow : BYTE := 2#1111_1111; END_VAR iInt := TO_INT(byHigh*16#100 + byLow);
Last updated: 2024-09-28

Post by marek71 on Ambiguous use of name - CO136 CODESYS Forge talk (Post)
My PLC is WAGO PFC200 Firmware Revision 26. target After updating WAGO_Devices_and_Libraries with newer Firmware 27, CODESYS wants to update all libraries to new versions. I will only add that I did not update the Firmware in the PLC. After compiling the program, I received the following errors: ------ Build started: Application: Device.Application ------- Typify code... [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): FbSerialInterface_internal: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): FbSerialInterface_internal: C0136: Ambiguous use of name 'RTS_IEC_RESULT' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0032: Cannot convert type 'Unknown type: 'RTS_INVALID_HANDLE'' to type 'POINTER TO BYTE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0136: Ambiguous use of name 'RTS_INVALID_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): Initialize [FbSerialInterface_internal]: C0046: Identifier 'RTS_INVALID_HANDLE' not defined [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_is_tx_empty: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_get_line_state: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_is_line_available: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): COMSW_SET_MODE: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' [ERROR] wagosyscom_internal_pfc, 1.0.2.5 (wago): comextra_set_line_state: C0136: Ambiguous use of name 'RTS_IEC_HANDLE' Compile complete -- 10 errors, 0 warnings Build complete -- 10 errors, 0 warnings : No download possible The problem was caused by the WagoSysPlainMem(WAGO) library in the original version 1.5.3.0 after updating to 1.5.3.1. After returning to version 1.5.3.0, the problems disappeared. Probably the version number of this library is responsible for supporting the appropriate Firmware Revision. Can anyone confirm or deny my suspicions?
Last updated: 2024-07-06

Post by alexgooi on Function Blocks and arrays of function blocks CODESYS Forge talk (Post)
Hi Jack, I think you have to look at a FB in a different way. A Function block (Class) can contain its own data. In other words don't define loose data in your GVL, but define a instance of a FB (Object) in your GVL: Example: Function_Block Basic_Class VAR_INPUT Open_Command: BOOL; END_VAR VAR_OUTPUT Opened: BOOL; END_VAR if Open_Command then Opened := TRUE; ELSE Opened := FALSE; END_IF Global Variables Objects: ARRAY[1..100] OF Basic_Class; //Here you ar defining you objects END_VAR In your code you can directly acces the data and couple it to the IO: GVL.Objects[1].Open_Command := %IX0.0; %QX0.0 := GVL.Objects[1].Opened; //To call the code itself use: GVL.Objects[1](); If you want to take this a step further you are also able to add methods and properties to the FB/Class end thereby creating a OOIP program
Last updated: 2024-02-15

Post by dhumphries on Not able to see input data coming from eip adapter on codesys CODESYS Forge talk (Post)
Does the device have a green icon next to it when the PLC is running? If not you have some kind of communication problem, wireshark may be picking up some data but the scanner may not be configured correctly to receive the data. Check the T>O and O>T bytes and make sure they match on both the scanner and adapter. I've had very little success loading a .eds file and having the configuration work without some manual configuration. If you have a green icon, have you enabled the device to always update variables?
Last updated: 2024-03-02

Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together CODESYS Forge talk (Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18

Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together CODESYS Forge talk (Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18

Post by hazarath on How extract JSONElement containing Array data CODESYS Forge talk (Post)
I want to extract each element of an Array. Can someone help me with this. When I use JSONElementToString (part of JSON Utilities SL), I am seeing output as "ARRAY" instead of actual data. Here is the JSON content that I want to read : { "value1Unit": { "units": "M" }, "data": { "stepSize": 300.23, "points": [6,8] } } I would like to read each item of the element "points" i.e. 6 and 8. Here is the code I used, // Reading the content as JSON reader ( xExecute := execute , pwData := ADR ( converted_value ), jsonData := jsonDataStorage ); // Get the JSON Element jsonDataStorage.FindFirstValueByKey( wsKey := fidKeyVar, diStartIndex := searchElem, jsonElement => jsonElement ); JSON.JSONElementToString ( element := jsonElement , wsResult := valueWstring ); The content of the output of valueWstring is shown as "ARRAY" instead of the array items i.e. 6 and 8 Please can someone help me.
Last updated: 2024-07-30

Post by damian177 on Problem with downloading OPC UA tags by Data Source Manager CODESYS Forge talk (Post)
Hi, In Codesys V3.5 SP20, using Data Source Manager I am trying to connect to the OPC UA server and receive tags from it. The connection is ok, but the Codesys have a problem with downloading Tags group. The window (downloadingTags.jpg in attachement) never stop. After waiting for a while, I disconnect the connection and only the Server group remains downloaded, with OPC UA server diagnostic data (and this is read in Codesys). Of course, I tried connected via another OPC UA client : UaExpert , and everything works as it should, all tags are downloaded (Uaexpert.jpg screen). Has anyone on the forum encountered the OPC UA client configuration in Codesys? Is it possible to manually request the appropriate tags from the OPC server for reading in Codesys?
Last updated: 2024-09-03

Post by shabroz-gill on Exception when OPCUA datasource disconnects from Server CODESYS Forge talk (Post)
If i loose the network and the opcua data source suddenly looses connection with the server, i get an exception and my application stops working. I am using the latest version of the communication add v4.5.2.0 Is this a known issue? This makes the datasource unusable because it is inevitable that we will loose connectivity at some point, and the datasource crashing everything due to that seems to be a deal breaker. I can provide more details is someone from codesys is reading this. You can recreate is by just shutting off the Opc server after the codesys data source is connected and reading data from it. The codesys app does not crash everytime and sometimes it is able to reconnect without crashing, so you may have to try this a few times to see the exception. Best regards
Last updated: 2024-09-16

Post by taqamert on CANopen PDO Issue with Pressure Sensor in Codesys CODESYS Forge talk (Post)
Hello everyone, I am using an IFM CR0303 model PLC, which has a tilt sensor and a pressure sensor connected via CANopen. Both sensors are from the same brand (ATEK). I can read data from the tilt sensor without any issues, but I am unable to read data from the pressure sensor. I have added the EDS file in the PLC configuration and adjusted the node-ID settings. When I check with the PCAN-View application, I can see that the selected PDOs are coming through, but the data is not reaching the Codesys side. What could be the issue, and what can I try to resolve it? Can anyone help me?
Last updated: 2024-10-22

Post by usacodesysuser on How to connect serial devices ? CODESYS Forge talk (Post)
@eschwellinger do you have any examples of using a USB barcode scanner? I have read through the forums here and I am unable to find how to get the barcode data to populate in a text field without having to first click into the text field to activate it. Is there a library that allows you to access the barcode data? I am really new to this in general any help is greatly appreciated, hopefully you have a pretty clear example
Last updated: 2024-01-06

Post by hoatran on Use third party actuator with IO-Link Master (IFM) CODESYS Forge talk (Post)
The generic sensor FB is for controlling the sensor via its cyclic input (PDI) and output (PDO). In this case, ifm raw cyclic input and output data are WORDs (16 bits total) The PDO data from the Buerkert unit are SINT (8 bits) In this case, I would use the unpackword fb from the CAA memory library to unpack the valve feed back value into the appropriate location.
Last updated: 2024-04-23

Post by yannickasselin on How to sort JSON object in codesys CODESYS Forge talk (Post)
Just adding: sSubscriberdata := ''; Right before your memcopy should fix the extra characters. It is because your are copying 36 characters into a string which can contain more than 36 characters and there is garbage left in the extra characters. Regarding the parsing of json, I usually build a structure that mirrors the json data and use the available methods in the IIoT library to parse the data and fill the structure.
Last updated: 2024-05-08

Post by veneto on OPC UA Client CODESYS Forge talk (Post)
Ciao damian177, provo a chiederti un'informazione. Sul mio progetto Codesys(ver.3.5 SP17) non Γ¨ visibile l'oggetto "Data Source Manager". Il PC con il progetto Codesys(client) Γ¨ collegato via rete TCP ad un PLC Siemens1200(server). Sul PC con Codesys ho installato UAexpert(client) e riesco a vedere le variabili del PLC1200. Riesci ad aiutarmi a capire come mai non Γ¨ visibile l'oggetto "Data Source Manager"? Molte grazie
Last updated: 2024-09-06

Post by john-robinson on Limiting Memory Access of an Array to Within its Bounds CODESYS Forge talk (Post)
Recently we had an issue regarding some simple code to calculate a rolling average. The code indexes from zero to 199 to properly store the current input into a circular buffer which then allows us to calculate a rolling average: VAR input_5s : REAL; outs_arr : ARRAY[0..199] OF REAL; i : USINT := 0; END_VAR ___ //this code runs every five seconds, calculating a rolling average outs_arr[i] := input_5s; i := i + 1; output := OSCAT_BASIC.ARRAY_AVG(ADR(outs_arr), SIZEOF(outs_arr)); IF i >= SIZEOF(outs_arr) THEN i := 0; END_IF There is a simple bug in this code where the index will be set to 0 when it has surpassed the length of the array in bytes (800 in this case) rather than larger than the number of reals in the array (200). The solution here is simple, replacing i >= SIZEOF(outs_arr) with i >= SIZEOF(outs_arr)/SIZEOF(outs_arr[0]). In this example when the index increased to 201 and the line outs_arr[201] := input_5s was called, codesys arbitrarily wrote to the address in memory that is where outs_arr[201] would be if the array was that long. I would like to find a way to wrap the codesys array inside of a wrapper class that checks if an input is within the bounds of an array before writing to that value. I know how I would implement that for a specific array, I could create a method or class that takes an input of an array of variable length, ie. ARRAY[*] OF REAL, but I don't know how to make this for any data type. I am wondering if anyone has ever done anything similar to this, or has any better suggestions to ensure that none of the programmers on this application accidentally create code that can arbitrarily write to other locations in memory.
Last updated: 2024-03-05

Post by reinier-geers on Softmotion general CODESYS Forge talk (Post)
Hi, Im busy using softmotion. But its reading data , but no respons on the commands. Most examples has Softmotion General exis pool. How can get that?
Last updated: 2023-12-19

Post by kislov on Visu Plugin 4.5.0.0, "Visu, Webvisu: Improve diagnosis" CODESYS Forge talk (Post)
Hi. I have question about new feature in Visu Plugin 4.5.0.0: https://www.codesys.com/fileadmin/data/Images/System/Releaseinformation/Release-Notes-CODESYS-Visualization-4500.html VIS-3409 Improvement Visu, Webvisu: Improve diagnosis (legacy) Please tell me how I can activate this diagnosis feature.
Last updated: 2023-12-20

Post by naidureginald on creating a visualization table CODESYS Forge talk (Post)
hi all im trying to create a visualisation table for a axis alarms list. upon entering the data array, i recieve a message as attached. any help would be much appreciated.
Last updated: 2024-01-03

Post by hclai on Table Content with Multilanguage CODESYS Forge talk (Post)
I have an data structure which intend to list in a table and let user to add the content to the table. How can we able to support for displaying different language in the content of the table? which is dynamic to the user input.
Last updated: 2024-01-10

Post by smartcoco on Bit / Bool data types in function parameters CODESYS Forge talk (Post)
Memory addressing is measured in bytes, with BOOL occupying one byte. BIT is quite unique as it occupies one bit. So, try not to use BIT in the program. You can use the Unpack function to solve your problem.
Last updated: 2024-01-18

Post by ewi04 on Git - User identification data is lost when codesys is closed CODESYS Forge talk (Post)
With git 1.4.0.0 it has gotten even worse. Now i have to enter the information every commit. Great.. Doesn't that bother anyone?
Last updated: 2024-01-26

Post by davidbo on I2c write is BeforeWriteOutputs needed? CODESYS Forge talk (Post)
I have made an I2C library where writing happens by calling write8 I now see that I do not call BeforeWriteOutputs at all, however it seems to work data are sent at least for an hour. So is BeforeWriteOutputs needed
Last updated: 2024-02-07

Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia CODESYS Forge talk (Post)
Using SDO, I can read the EtherCAT mappings and offsets from various registers like 0x1c12, 0x1c13, etc. When I obtain registers mapped in the PDOs and various offsets, I could technically access directly to the statusword, controlword, etc., if they are mapped. I have noticed that on IoDrvEthercatLib.ETCSlave_Diag I can find pointers to the input and output buffers. However, although the input buffer can be easily read by referring to what has been obtained from the SDOs, it is not possible to write to the output buffer, as it is overwritten in each cycle by the data from the IOMapping task. Is there a way, knowing an instance of IoDrvEthercatLib.ETCSlave_Diag, to obtain the pointer to the first data in the IOMapping? The offsets are identical to those of the PDOs, but obviously the data is a copy. For me, the cleanest thing would be to access the pointers on IOMapping, for DS402a devices to retrieve the key data and point them to internal references. I need to know this as, having developed our own motion library, I would like to simplify the initial setup by eliminating unnecessary and nonsensical mappings that can lead users to unnecessary errors. In the current version that we have been using for years, we have to map everything manually. I would like to pass only the slave reference to the FB_init constructors and eliminate the mapping.
Last updated: 2024-02-12

Post by paro on OPCUA array max length? CODESYS Forge talk (Post)
I think the amount of data is already relatively high and maybe it has something to do with that? Maybe also the CPU load of your device? an array with string(5000)? and have you tested with how many array elements it still works?
Last updated: 2024-02-17

<< < 1 .. 19 20 21 22 23 .. 27 > >> (Page 21 of 27)

Showing results of 672

Sort by relevance or date