Post by marlutec on [ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0
CODESYS Forge
talk
(Post)
Hello every one. Now i'm instaling a Weintek cMT2108x2(v2) with IR-ETN40R. When I start to import the archive content the code of I/O remote IR-ETN40R, ocurred this error. [ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0 Can someone help me? Marcos Gentil, from Brazil.
Last updated: 2024-02-15
Post by adam on Get/Set I/O Address Mapping of DeviceObjects in python Script
CODESYS Forge
talk
(Post)
I want to cancel the automatic address allocation for all IO mappings. If I directly set the automatic_iec_address in class ScriptIoMapping to False, the address becomes None. So I reset manual_iec_address with itselfs value. It only work with the Input IOMapping . For output, it reports an error: "Invalid address: The channel type 'Output' requires address type '%Q'." I checked the description file ,both accessRight are total same. Does anyone know what causes this?
Last updated: 2025-11-14
Post by bjarne-pagaard on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20)
CODESYS Forge
talk
(Post)
Hi, I would like to divide a project into multiple applications - as a minimum: one handling visualization and Alarm Manager, one handling I/O and plant control logic. But how to exchange variables between the applications? What have you done to get such a solution? In versions 3.5.19 and earlier, you can have Child applications, where the children can access a GVL in the Parent application. Children apps is no longer possible in 3.5.20 - but you can have 'sibling' apps - Several apps directly under PLC Logic, that is. But how do they best communicate? The Communication Manager / Data Sources Manager is sort of possible via OPC UA, but it seems like overkill and with some limitations - for example no ARRAY OF STRUCT possible this way. If you have separate devices in your project, you can exchange data via 'CODESYS ApplicationV3', but not other applications in the same device (see attachment Datasources.png). You can do it via 'Select the project type'->'Other Project' and select the same project file, but this leads to crashing the Development system when working with the variables afterwards. It would be great to hear your thoughts / experiences on this topic - Bjarne
Last updated: 2024-09-27
Post by duvanmoreno24 on Modbus writing on value change
CODESYS Forge
talk
(Post)
Hi all, I want to know if someone has an idea of how I can write on value change in Modbus Codesys. I have a Wago PLC and I was used to work with E-cockpit which it was quite easy to do that without the necessity to trigger any value when there was a change in the variable ( I will put how easy is ). how you can see just changing the trigger in "On value Change" will do that channel writing automatically when It detects a change in those arrays. On the other hand, in Codesys if I enable the rising edge in Codesys It ask me to put a bool variable and if triggers is going to write that value. That is making me that I have to create a function or a logic to detect the change, the problem I have is that doing that is very tedious. I first approach I got it was to create a Function who returns a bool when the value change, but I tried to keep the old value but what is happening is that in Functions all the data is erased every cycle so I can not keep any Old value. so in the Main program the trigger is going to be TRUE all the time due, the old value is cero every cycle. The second approach I got it was using a function Block (POU_1) and it works but I dont want to instance that function for every Channel or value that I want to check if the value change, Basically if I have 200 values to write trhough modbus I have to create 200 instances of that function which I think it is not practicall at all. It should be a better way to implement this as e-Cockpit from Wago Does. However, I haven't been able to know how.
Last updated: 2024-03-26
Post by jari-koivuluoma on Problem trying Net Base Services 3.5.15.0 TCP connection
CODESYS Forge
talk
(Post)
I have a need to send messages between 2 PLCs and I cant use network variables (because of size limit) so I tried writing this simple test program. This seems to work fine. I can send messages back and forth when a first "Start server" and then "Connect client". See the attached image. However, if I disconnect the client by setting ClientConnect to false and try to re-connect then the TCP_Client just gives me TIMEOUT error. When I stop and start the server again, then Im able to reconnect. How is this supposed to work? Why reconnecting wont work. There is not other way of disconnecting the client than setting xEnable of the TCP_Client to false. This is just a testing program and I will try it on 2 seperate devices once this works. PROGRAM PLC_PRG VAR CONSTANT mySize : UDINT := 255; END_VAR VAR Server: NBS.TCP_Server; ServerIpStr: STRING := '127.0.0.1'; ServerIP: NBS.IP_ADDR; ServerPort: UINT := 50000; ServerConnection: NBS.TCP_Connection; Client: NBS.TCP_Client; ServerRead: NBS.TCP_Read; ServerWrite: NBS.TCP_Write; ServerSend: STRING(mySize); ServerReceive: STRING(mySize); ServerConnect: BOOL; bServerSend: BOOL; IP: NBS.INADDR; ConnectedClientIP: STRING; ClientPort: UINT := 50000; ClientIpStr: STRING := '192.168.1.49'; ClientIP: NBS.IP_ADDR; ClientRead: NBS.TCP_Read; ClientWrite: NBS.TCP_Write; ClientSend: STRING(mySize); ClientReceive: STRING(mySize); ClientConnect: BOOL; bClientSend: BOOL; Error: BOOL; Message: BOOL; END_VAR // Server ServerIP.sAddr := ServerIpStr; Server( ipAddr := ServerIP, uiPort := ServerPort ); ServerConnection( xEnable := Server.xEnable, hServer := Server.hServer, ); IP := ServerConnection.IPAddress; ConnectedClientIP := F_Concat7( BYTE_TO_STRING(IP.S_un_b.s_b1),'.', BYTE_TO_STRING(IP.S_un_b.s_b2),'.', BYTE_TO_STRING(IP.S_un_b.s_b3),'.', BYTE_TO_STRING(IP.S_un_b.s_b4)); ServerRead( xEnable := ServerConnection.xActive, hConnection := ServerConnection.hConnection, szSize := SIZEOF(ServerReceive), pData := ADR(ServerReceive) ); IF ServerRead.xReady AND ServerRead.szCount > 0 THEN Message := TRUE; END_IF IF ServerRead.eError > 0 THEN Error := TRUE; END_IF ServerWrite( xExecute := ServerConnection.xActive AND bServerSend, hConnection := ServerConnection.hConnection, szSize := LEN(ServerSend)+1, pData := ADR(ServerSend) ); IF ServerWrite.xDone THEN bServerSend := FALSE; END_IF IF ServerWrite.eError > 0 THEN Error := TRUE; END_IF // Client ClientIP.sAddr := ClientIpStr; Client( xEnable := ClientConnect, ipAddr := ClientIP, uiPort := ServerPort, udiTimeOut := 10000000 ); ClientRead( xEnable := Client.xActive, hConnection := Client.hConnection, szSize := SIZEOF(ClientReceive), pData := ADR(ClientReceive) ); IF ClientRead.xReady AND ClientRead.szCount > 0 THEN Message := TRUE; END_IF IF ClientRead.eError > 0 THEN Error := TRUE; END_IF ClientWrite( xExecute := Client.xActive AND bClientSend, hConnection := Client.hConnection, szSize := LEN(ClientSend)+1, pData := ADR(ClientSend) ); IF ClientWrite.xDone THEN bClientSend := FALSE; END_IF IF ClientWrite.eError > 0 THEN Error := TRUE; END_IF
Last updated: 2024-10-03
Post by timvh on Management of a PLC network from a remote station
CODESYS Forge
talk
(Post)
Maybe the CODESYS HMI is a good solution. https://store.codesys.com/en/codesys-hmi-sl-bundle.html Run this on the remote main control station. In the HMI application you can add the data source manager and to this manager you can add Data sources. A data source has a reference to the PLC you want to connect to and can get access to the variables of the PLC application. You can then use these variables in the visualization of the HMI application.
Last updated: 2023-12-04
Post by lsislsis on Alarms Placeholder
CODESYS Forge
talk
(Post)
Hello. When i put placeholders at "/etc/codesyscontrol/CODESYSControl.cfg" : [SysFile] FilePath.1=/etc/codesyscontrol/, 3S.dat IecFilePath.1=/proc/, cpuinfo IecFilePath.2=/proc/, iomem PlaceholderFilePath.1=/sys/devices/w1_bus_master1, $OneWire$ PlcLogicPrefix=1 PlaceholderFilePath.2=/data/persistence, $ac_persistence$ PlaceholderFilePath.2.Volatile=1 PlaceholderFilePath.2.View=1 PlaceholderFilePath.3=/data/alarms, $alarms$ PlaceholderFilePath.3.Volatile=1 PlaceholderFilePath.3.View=1 Where "Data" are my USB Flash. I take these attachment errors at run time. What i am doing wrong.
Last updated: 2024-10-15
Post by respl on IFM EXOR Network variable Error
CODESYS Forge
talk
(Post)
We are connected IFM CR711S to Exor EX710. We are exchanging data using network variables. Both devices are configured on same project so no need to use file source. When tested application it works fine. But after 3 months same application not working. We are able to send data from CR711 to EX710 but data from Ex710 to CR711s works only for one scan when we cold reset CR 711S. Can somebody help to find out error.
Last updated: 2025-03-17
Post by nha451 on EIP Scanner not receiving data from adapter
CODESYS Forge
talk
(Post)
Hello, I have an EtherNet IP adapter (GoPxL) running with a virtual PLC. I have successfully connected the adapter with green icons next to it. On WireShark I can see the data coming from GoPxL but on CODESYS it shows up as all 0. My firewall is turned off and I have enabled the device to always update variables. I tested my set up with Profinet and I can receive the data. Please let me know if you have any suggestions!
Last updated: 2025-09-12
Post by dekelec on Codesys 2.3 & Peak PCAN
CODESYS Forge
talk
(Post)
IF you have an USB interface type in "Peak_USB" for CAN card driver (Name of CAN card driver). No need to add libraries for communication via CoDeSys Gateway. For other card types contact PEAK support and they will help you. Regards,
Last updated: 2024-07-08
Post by dennisyhli on Ethernet IP Connection timeout
CODESYS Forge
talk
(Post)
I use ethernet ip scanner and the connection type is set to multicast. After running the PLC, the ethernet IP will have a connection timeout every 10 seconds. What is the reason for this error?
Last updated: 2024-08-16
Post by ph0010421 on How to manage variable types larger than 64 bits - Ethernet/IP
CODESYS Forge
talk
(Post)
So it's currently mapped to an array of BYTES? Can you create a UNION? TYPE sBytesString : UNION AsBytes: ARRAY[0..127] OF BYTE; AsString: STRING(128); END_UNION END_TYPE Map it to the bytes, read it in the STRING!
Last updated: 2024-09-23
Post by opineiro on How to manage variable types larger than 64 bits - Ethernet/IP
CODESYS Forge
talk
(Post)
Thanks, that's what I thought initially. The point is that I can't select a String type variable. See the attached image
Last updated: 2024-09-23
Post by timvh on Readable IO names
CODESYS Forge
talk
(Post)
IF you create an ENUM {attribute 'qualified_only'} {attribute 'strict'} TYPE E_IO : ( FIRST := 0, SECOND := 1 ); END_TYPE You should be able to access the array items like: IOCard_OUTPUT[E_IO.FIRST]
Last updated: 2024-09-28
Post by tmo21 on Automation server - trends stop recording - need to manually reconnect
CODESYS Forge
talk
(Post)
Hi Edwin, Thanks for your message. Edge controller Version: 4.4.0.0 based on 3.5.17.30 PLC version: Device Identification Name CODESYS Control for Raspberry Pi MC SL Vendor 3S - Smart Software Solutions GmbH Device type Softmotion3S Firmware version 4.4.0.0
Last updated: 2024-10-23
Post by nonstop-cat on Problem of assigning physical addresses to variables of type ARRAY OF ARRAY as MW and QW
CODESYS Forge
talk
(Post)
Array writing method error,,,<arrayname>: ARRAY [<ll1>..<ul1>, <ll2>..<ul2>, <ll3>..<ul3>]</ul3></ll3></ul2></ll2></ul1></ll1> OF <basedatatype></basedatatype></arrayname>
Last updated: 2025-03-31
Post by nonstop-cat on Problem of assigning physical addresses to variables of type ARRAY OF ARRAY as MW and QW
CODESYS Forge
talk
(Post)
Array writing method error,,,<arrayname>: ARRAY [<ll1>..<ul1>, <ll2>..<ul2>, <ll3>..<ul3>]</ul3></ll3></ul2></ll2></ul1></ll1> OF <basedatatype></basedatatype></arrayname>
Last updated: 2025-03-31
Post by eschwellinger on RaspberryPi 5 gateway problem
CODESYS Forge
talk
(Post)
Do you use the same type Raspberry PI64 SL in the device tree? Which version of the Pi package / Runtime do you use? 4.16.0.0?
Last updated: 2025-06-12
Post by timvh on Unable to select VisuDialogs.Numpad in Open Dialog input configuration
CODESYS Forge
talk
(Post)
You should not use the "open dialog" to change the value. Instead use the input configuration "Write Variable" to change a variable value in the visualization. in the setting of this input command, you can choose the Input type (select dialog).
Last updated: 2025-07-23
Post by gseidel on The default ramp type selection in SoftMotion V4.18.0.0 is Quadratic
CODESYS Forge
talk
(Post)
Hi imdatatas, thanks for your detailed and thoughtful feedback. We will discuss the topic in our team. Best regards, Georg
Last updated: 2025-10-02
Post by eschwellinger on WAGO PFC200 FW25 unable to connect
CODESYS Forge
talk
(Post)
please double check if you have in the project the same plc type like online available. (untag the " Hide non matching device filter.."
Last updated: 2023-12-09
Post by jdjennings1962 on Trouble accessing Math functions in OSCAT library
CODESYS Forge
talk
(Post)
Thank you seoerr for your suggestion. When I implement that line, I get this error: ** [ERROR] 'OSCAT_BASIC.ARRAY_SDV' is of type FUNCTION and cannot be instantiated** Any other thoughts about instantiating these sections of the library which seem to be provided as source only?
Last updated: 2024-01-16
Post by eschwellinger on How to Connect / Go Online without re-downloading the project
CODESYS Forge
talk
(Post)
Which plc type is it: Either use Automationserver to do this or save the project archives instead of projects or use the source dowload function and reopen the application from plc. So you need to chose one of them.
Last updated: 2024-04-13
Post by rabaggett on CODESYS control for Raspberry Pi 64 SL errors
CODESYS Forge
talk
(Post)
Hi, I am trying to create a project using a raspberry pi, I have added the modules for the Pi and MCP3008. I have encountered som errors that I don't know how to track down. 1. The GPIOs give preprocessor errors, but I read that this does not prevent compiling. This seems to be true. I can build the empty project with no errors. 2. After adding a SPI master and MCP3008, the preprocessor errors double, but seem similar and the project again builds with no errors. 3. I add a DUT and GVL, with a function, and I get the following errors. They remain even if I delete these things. ------ Build started: Application: Device.Application ------- Typify code... [ERROR] crr: C0032: Cannot convert type 'Unknown type: 'ADR(GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7.Io_17160064_c083_41f8_9e53_208be7537753_HPS_7)'' to type 'POINTER TO IoConfigParameter' [ERROR] crr: C0077: Unknown type: 'GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7.Io_17160064_c083_41f8_9e53_208be7537753_HPS_7' [ERROR] crr: C0046: Identifier 'GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7' not defined Compile complete -- 3 errors, 0 warnings I attach the project. What am I doing wrong? Thanks!
Last updated: 2024-05-02
Post by gcodejedi on The element of type 'VisuFbElemImage' could not be updated. Reason: Index was outside the bounds of the array.
CODESYS Forge
talk
(Post)
Hello, I am experiencing this exact same issue. Were you able to get yours resolved? If so, would you mind sharing the solution you discovered? Thanks!
Last updated: 2025-11-03