Search talk: WHERE TO FIND SHR BLOCK

 
<< < 1 .. 200 201 202 203 204 .. 243 > >> (Page 202 of 243)

Post by wollvieh on License Activation Problems CODESYS Forge talk (Post)
on a raspberry pi delete the folder and its content before licensing. /var/opt/codesys/cmactlicense If you plug this SD card in another raspi ( which has another hw-serial number) you'll get a second empty softcontainer. This could lead to an unlicensed PFC (it could only handle one container) The solution is: To delete the /var/opt/codesys/cmactlicense directory and content of it and then aktivate the lizenz via WibuCmRau file and Lizenzmanager.
Last updated: 2024-06-24

Post by alimans on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup CODESYS Forge talk (Post)
Hi Manuknecht, Did you manage to solve the problem? I’m facing the same issue with Windows RTE SoftMotion β€” it works fine as long as nothing else is open in Windows, but as soon as I start another application, the EtherCAT DC time and max jitter values spike, and then all axes stop. I’ve already sent a support request to CODESYS, but haven’t received a response yet.
Last updated: 2025-10-23

Post by ben1 on How to stay in a method until something is finished. CODESYS Forge talk (Post)
Why must you use a method? Top of my head can't you just use the button to turn on a bit and use it in a normal task? Just turn a bit on with the button, and run a TON from it in code, and turn it back off with the ton. And then just log the pressure on both the rising & falling edge?
Last updated: 2025-11-03

Post by adam on Get/Set I/O Address Mapping of DeviceObjects in python Script CODESYS Forge talk (Post)
I want to cancel the automatic address allocation for all IO mappings. If I directly set the automatic_iec_address in class ScriptIoMapping to False, the address becomes None. So I reset manual_iec_address with itselfs value. It only work with the Input IOMapping . For output, it reports an error: "Invalid address: The channel type 'Output' requires address type '%Q'." I checked the description file ,both accessRight are total same. Does anyone know what causes this?
Last updated: 2025-11-14

Post by ppanchal on Add a dynamic text on One Visualization from another CODESYS Forge talk (Post)
I've created a TitleBar Visualization in which I have "Logo" on the Left corner, "Screen Name" in the center and Time/ date on the right corner. I've also created a 'Menu" visualization that slides out from left to right. I have TitleBar and Menu Visualizations in the MainScreen (3rd Visualization). I want to have "Screen Name" automatically updated on TitleBar Visualization based on Menu item selected from the "Menu" visualization. Can anyone advise how can I achive this? TIA
Last updated: 2025-11-18

Post by imdatatas on SMC_ERROR.SMC_AXIS_NOT_READY_FOR_MOTION when using Drive Virtual CODESYS Forge talk (Post)
@ducng, Another possible situation could be that normally there are 3 inputs for MC_Power. In your above images, I can't see the "bDriveStart" input activated. As Mr. @gseidel mentioned, you need to make sure MC_Power.Status output should be TRUE. Issuing any movement command without activating the axis would naturally result in an error. For MC_Power; You can set the Enable and bDriveStart inputs to TRUE and try turning the axis activation on and off using only the bRegulatorOn input. Regards, Imdat
Last updated: 2025-11-28

Post by gseidel on MC_Phasing state explenation CODESYS Forge talk (Post)
Hi kenth1973, MC_Phasing has been improved in recent versions. I would recommend to install the latest version of SoftMotion (4.20.1.0) and test whether the problem still exists, and if so, what the error identifier is. (Also check the PLC log in this case, it might contain additional information.) Setting the internal state of the FB is not recommended, it could lead to malfunction of the FB and unintended movements of the drive. Best regards, Georg
Last updated: 2025-11-28

Post by gseidel on Scara3 kinematic robot error CODESYS Forge talk (Post)
Hi aniket-b, this error has nothing to do with the scara3 kinematics, or robotics, or SoftMotion. It means that the EtherCAT bus is not synchronized. The usual cause is that the realtime of the PLC is not sufficient. See https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_basic_common_errors.html for details and ways to solve the problem. You can also check the PLC log for additional information about the error. Best regards, Georg
Last updated: 2025-12-23

Post by bertus on Axis directions in CNC editor not using right-hand rule? CODESYS Forge talk (Post)
Hello, Coming from robotics, I'm used to coordinate systems using the right-hand rule. But when I created below small NC program in the Codesys CNC editor, I noticed that the axis triad's Z-axis is flipped (see attached screenshot), resulting in left-hand rule. Is there a setting to change this? Or am I misunderstanding something in the CNC world? N000 G00 X0 Y0 N010 G01 X100 N020 G01 Y50 N030 G01 X0 N040 G01 Y0 N050 G01 Z25
Last updated: 2026-01-02

Post by axberry on CODESYS Control for Raspberry Pi 5 - "Hardware version or firmware version not supported" on Rev 1.1, persists across multiple runtime versions and OS images CODESYS Forge talk (Post)
Hi, I'm trying to run CODESYS Control for Raspberry Pi SL on a Raspberry Pi 5, and the runtime consistently fails to start with the following error when launched manually: ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-18, 0x00000BB8, 0xFFFFFFFB) Hardware: Raspberry Pi 5 Model B Rev 1.1 Revision code: d04171 CPU: aarch64, BCM2712 Serial number is correctly exposed via /proc/cpuinfo and /proc/device-tree/serial-number /proc/device-tree/model correctly reports "Raspberry Pi 5 Model B" What I've tried (all resulting in the same error): CODESYS Control for Raspberry Pi SL 4.11.0.0 (SDK 3.5.19.61) β€” the version that introduced Pi 5 support CODESYS Control for Raspberry Pi SL 4.21.0.0 (SDK 3.5.22.20) β€” latest available Raspberry Pi OS Bookworm (64-bit) with kernel 6.12.93+rpt-rpi-2712 (June 2026 build) Fresh install on Raspberry Pi OS Bookworm (64-bit) with an older image from November 24, 2025 β€” same error, ruling out a kernel-version regression Bootloader/EEPROM confirmed up to date (rpi-eeprom-update reports "up to date") Clean purge and reinstall of the codesyscontrol package each time (verified via dpkg -l, no leftover files) Verified /etc/codesyscontrol/3S.dat correctly symlinks to /etc/codesyscontrol/3S_aarch64.dat The service starts (systemctl status briefly shows active (running) with a real PID under /opt/codesys/bin/codesyscontrol.bin), but crashes shortly after and the process disappears β€” port 11740 never opens. Since this happens identically across two different runtime versions and two different OS images (5+ months apart), it doesn't seem to be a kernel/firmware timing issue. Could this be specific to the Rev 1.1 board revision, or is there a known issue with the hardware detection logic in the SL runtime that I should be aware of? Happy to provide full debug logs (-d flag output) or journalctl output if useful. Thanks in advance!
Last updated: 2026-08-10

Post by dmb-fan on From target start Win OnScreenKeyboard CODESYS Forge talk (Post)
Hi ! I am get crazy.... I try to start osk.exe from Visu or PLC. From Visu I can't load it, always error (It change from programm execute always to load receipe ..!?!?) From PLC always freeze of PLC, - I allowed the win service of the PLC the data exchange between desktop and service - I allowed in ..user.cfg [SysProcess] Command=AllowAll Shutdown with SysProcessExecuteCommand works, but 'osk.exe' or the complete path always crashed the system. And like always: No documentation. Just guessing. Or know somebody more and have a link for me? THANKS !
Last updated: 2026-10-27

Post by gseidel on Axis directions in CNC editor not using right-hand rule? CODESYS Forge talk (Post)
Hi bertus, the coordinate systems used in SoftMotion CNC are all right-handed. The CNC editor uses isometric projection. This can be confusing, as in your example. The y-axis seems to point into the screen, away from the viewer. However, this is just an optical effect. If you turn on the (experimental) perspective projection (must be added to the CNC tool bar using tools->customize), you can see that the coordinate system is in fact right-handed. Best regards, Georg
Last updated: 2026-01-07

Post by codegunner on how to convert library from CodeSys 2.3 to CodeSys 3.x ? CODESYS Forge talk (Post)
hello, ive tried everything and keep getting error like i have opened a file in read only so cannot save no idea what is causing it, file is not read only i cannot even open a new file i make with one variable in 2.3, get same error for read only. do you have a 2.3 file you can send me tomtry and open for a test? thanks
Last updated: 2026-04-29

Post by srinidhi on Pilz PBRT Robot with CoDeSys CODESYS Forge talk (Post)
If anyone here are working with robots and using Codesys to control it and implement tasks, Please let me know. I am currently in my Master thesis and i need some advice on this. We have Pilz Robot with Codesys and I am trying to proceed with certain tasks but have no documentation for it. Would be helpful if anyone of you can suggest and help connect with the right people.
Last updated: 2026-05-10

Post by dhumphries on Codesys Installation problem CODESYS Forge talk (Post)
Installing codesys has been the biggest point of frustration for me and is the reason I'm currently working on building a VM just for the codesys engineering software so once I get a working installation I can copy the VM to new workstations instead of fighting with the installer every time I get a workstation upgrade. The best advice I've gotten in the past is to uninstall everything and start over, this is successful 50% of the time. Also don't install the latest version it's usually less stable than an older one ironically.
Last updated: 2026-08-10

Post by luca03 on OPC UA information model into the Communication Manager CODESYS Forge talk (Post)
Hello, unfortunately I am unable to load an OPC UA information model as a NodeSet2.xml file into the CODESYS Communication Manager. Importing via Tools -> OPC UA Information Model Repository still works, but when I try to load the model explicitly, CODESYS crashes without displaying an error message. Has anyone else encountered this problem, or does anyone have any suggestions? Thanks in advance
Last updated: 2026-08-22

Post by zeljko2212 on Seeking a Code-Based Solution for EtherCAT Slave Dropout or Master Errors in Production (Beyond Software Hot Reset) CODESYS Forge talk (Post)
PROGRAM RES_ECAT VAR xMP1: INT; xRESTART: BOOL; xFinish: BOOL; xStop: BOOL; pSlave: POINTER TO ETCSlave; TP1 : TP; STS11: WORD; pSlave6: POINTER TO IoDrvEthercatDriverLib.ETCSlave; MP1: INT; TON1 : TON; xSTAT: BOOL; TP_1 :standard.TP; END_VAR TON1(IN:= NOT TON1.Q, PT:= T#300mS ); TP_1(IN:= ton1.Q, PT:= t#2s ); EtherCAT_Master.xRestart := xRESTART; EtherCAT_Master(); EtherCAT_Master(); xFinish := EtherCAT_Master.xConfigFinished; EtherCAT_Master.xStopBus := xSTOP; EtherCAT_Master(); pSlave := EtherCAT_Master.FirstSlave; WHILE pSlave <> 0 DO pSlave^(); IF pSlave^.wState = ETC_SLAVE_STATE.ETC_SLAVE_OPERATIONAL THEN xRESTART := FALSE; ELSE xRESTART := TP_1.Q; END_IF pSlave := pSlave^.NextInstance; END_WHILE
Last updated: 2026-02-14

Post by aapostolidis on _NEW when used with classes and interfaces. Interface shows "Hidden Instance" in watch. CODESYS Forge talk (Post)
Hello, im using dynamic memory allocation with the NEW()-operator. When i instanciate a class with the NEW()-operator and want to debug/watch the interface of the class, the watch is only showing "Hidden Instance" (See attached screenshot). Is there any possibility to debug the interface data ? The interface is working properly but the debugging by the watch is not possible, what is a big disadvantage. Thank you. Best Regards, Alexander
Last updated: 2026-03-24

Post by lofty on CODESYS Download Issue CODESYS Forge talk (Post)
I am attempting to install CODESYS 3.5.22.20 and the installer gets stuck at "Install Package CODESYS Compatibility Package 3.5.17.20" every single time. I've tried reinstalling the software multiple times and the same issue persists. I've tried running the installer as an administrator and even turned off my virus protection and the same issue persists. I've attached a photo for reference. Has anyone run into this issue before or have any idea what I can do to complete the install?
Last updated: 2026-05-26

Post by dmb-fan on Attemp Convert old V2.3 projects : Error HRESULT: 0x80010105 (RPC_E_SERVERFAULT)) CODESYS Forge talk (Post)
I had runnig this already. Then I updated to SP22 patch3. After that I got always this error: ===== Project importieren: XXXXnameYYYYYY ===== *[FATALER FEHLER] Fehler beim Import des Projekts: Ausnahmefehler des Servers. * [FATAL ERROR] Error importing the project: Server exception. (Exception to HRESULT: 0x80010105 (RPC_E_SERVERFAULT)) I delete the version and installed again. Same. I uninstalled all CoDeSys on the PC and installed the old SP22 patch2 new. Same error by opening old projects. Immediatly, not by converting. Convert V3.5.17 was always installed. What is happening or what can I do?
Last updated: 2026-08-11

Post by tarek on How to add/Scan devicenet Master/Slave CODESYS Forge talk (Post)
Hello, i have a similar problem with this. Im using an EL6752 from Beckhoff DeviceNet Master and i dont have an EDS for the comms with the slave (EVO GT II Valve). In CODESYS they dont let me put a digital slave. My question, how can i add a slave in the EL6752 the Process data mapping to see values. I cant add a DeviceNet slave in the tree, thanks
Last updated: 2026-09-14

Post by dmb-fan on From target start Win OnScreenKeyboard CODESYS Forge talk (Post)
Hi ! I am get crazy.... I try to start osk.exe from Visu or PLC. From Visu I can't load it, always error (It change from programm execute always to load receipe ..!?!?) From PLC always freeze of PLC, - I allowed the win service of the PLC the data exchange between desktop and service - I allowed in ..user.cfg [SysProcess] Command=AllowAll Shutdown with SysProcessExecuteCommand works, but 'osk.exe' or the complete path always crashed the system. And like always: No documentation. Just guessing. Or know somebody more and have a link for me? THANKS !
Last updated: 2026-10-27

Post by scoob on ModbusFB - Slow Response Time CODESYS Forge talk (Post)
Hello, I have been trying to use the ModbusFB functions so I can put some code into libraries, but it seems to be very slow for me. I have a Modbus device with 100ms registers. I previously setup 10 channels in the 'traditional' Modbus Slave with channels and mappings - and set a cyclic trigger at 100ms - this worked fine. I then tried the ModbusFB example, and setup reading the same 10 blocks of modbus addresses, copying the example and putting all of the requests into an array and triggering the requests sequentially. I timed how long the requests are taking to get round to each one, and it is around 1s 450ms. How do I speed this up to match the cyclic time? IF NOT(init) THEN init := TRUE; // Set the required IP address: ipAddress[0] := 192; ipAddress[1] := 168; ipAddress[2] := 1; ipAddress[3] := 10; // Pass the required IP address to the clinet FB: client_NetworkSwitch.aIPaddr := ipAddress; client_NetworkSwitch.udiLogOptions := (ModbusFB.LoggingOptions.ClientConnectDisconnect OR ModbusFB.LoggingOptions.ClientReceivedValidReplies); // Try to connect the client client_NetworkSwitch(xConnect:=TRUE); // Configure all the channels to read connecting them to the client: portStatus_Request(rClient := client_NetworkSwitch, uiStartItem := 4096, uiQuantity := 32, pData := ADR(portStatus), udiReplyTimeout := udiReplyTimeout); portSpeed_Request(rClient := client_NetworkSwitch, uiStartItem := 4352, uiQuantity := 32, pData := ADR(portSpeed)); flowControl_Request(rClient := client_NetworkSwitch, uiStartItem := 4608, uiQuantity := 32, pData := ADR(flowControl)); linkUpCounter_Request(rClient := client_NetworkSwitch, uiStartItem := 5888, uiQuantity := 32, pData := ADR(linkUpCounter)); txPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8192, uiQuantity := 100, pData := ADR(txPacketCounter1)); txPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8292, uiQuantity := 28, pData := ADR(txPacketCounter2)); rxPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8448, uiQuantity := 100, pData := ADR(rxPacketCounter1)); rxPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8548, uiQuantity := 28, pData := ADR(rxPacketCounter2)); txErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8704, uiQuantity := 64, pData := ADR(txErrors)); rxErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8960, uiQuantity := 64, pData := ADR(rxErrors)); // Trigger all client requests initially FOR clientRequestsCnt := 0 TO (SIZEOF(clientRequests)/SIZEOF(clientRequests[0]))-1 DO pClientRequest := clientRequests[clientRequestsCnt]; pClientRequest^.xExecute := TRUE; END_FOR // Prepare sequential trigger / control of client requests. clientRequestsCnt := 0; pClientRequest := clientRequests[clientRequestsCnt]; END_IF // Call the client to do request processing: client_NetworkSwitch(); // Now we trigger client request sequentially ... IF NOT pClientRequest^.xExecute AND NOT pClientRequest^.xDone AND run AND client_NetworkSwitch.xConnected THEN pClientRequest^.xExecute := TRUE; END_IF // .. and check result/error IF pClientRequest^.xExecute AND run AND client_NetworkSwitch.xConnected THEN IF pClientRequest^.xDone THEN // Prepare next trigger of client request (a rising edge of xExecute) pClientRequest^.xExecute := FALSE; IF clientRequestsCnt < SIZEOF(clientRequests)/SIZEOF(clientRequests[0])-1 THEN // next client request clientRequestsCnt := clientRequestsCnt + 1; ELSE clientRequestsIterationCounter := clientRequestsIterationCounter + 1; clientRequestsCnt := 0; END_IF pClientRequest := clientRequests[clientRequestsCnt]; END_IF END_IF I did try a semi-coded way using the IoDrvModbusTCP library, and setting the slave com settings, then 10 commands and 10 requests, then using a TP on xDone as a pause, before triggering another request - this is time the delay is around 120ms - so the device is fine with the speed, just something I am doing wrong in the ModbusFB method I am sure.
Last updated: 2024-04-26

<< < 1 .. 200 201 202 203 204 .. 243 > >> (Page 202 of 243)

Showing results of 6055

Sort by relevance or date