Post by rickwot809 on Codesys Soft PLC OPC UA server CODESYS Forge talk (Post)
Enabling Anonymous Login 1. Navigate to 'Device' > 'Communication Settings' > 'Device'. 2. Next, click on 'Change Runtime Security Policy'. 3. In the new window, find and check the box for 'Allow anonymous login'. After completing these steps, you should be able to communicate with the OPC UA server.
Last updated: 2025-09-11

Post by ulad on SPI Communication CODESYS Forge talk (Post)
Hello. I created a project that uses SPI. This project is working well. I can see with an oscilloscope that the SPI pins are actually changing. But when I resave this project in the IDE and open it later in the system, I see a constant error. What do I need to fix? What am I doing wrong? Thank you.
Last updated: 2023-12-23

Post by francescoc on Access to the path *** is denied CODESYS Forge talk (Post)
Hello, I encountered similar problems, and it appears they were linked to certain add-ons. Resolving this issue turned out to be quite complex. However, we managed to find a solution by downgrading both the "CODESYS Communication" and "CODESYS Recipes" components via the CODESYS Installer, accessible under the "Tools" section.
Last updated: 2024-02-12

Post by timvh on when going online, stuck on "Syncing file "visuelemsdatetime.tl_datetime.txt" CODESYS Forge talk (Post)
I don't know the root cause... But what could help to continue when it seems to hang, is stop the CODESYS (communication) Gateway. Go to the Windows SysTray, find the icon for the Gateway and then stop it and start it again. This will interrupt the connection between CODESYS and your controller.
Last updated: 2024-03-05

Post by anlebr on Codesys Communication Manger - Required information model version exists in the model repository but is not found CODESYS Forge talk (Post)
Hi I am trying use the Codesys Communication Manager to set up an Opc ua server with a custom information model. As a start I am using the Boiler model available on Opc foundations github page. I am testing with a Wago CC100 and using Codesys V3.5 SP19 Patch 6. I get the following error: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://opcfoundation.org/UA/Boiler/ with a minimal publication date from 15/12/2023 but the device has only a model from 15/09/2021 installed. Probably the information model from 15/09/2021 is missing in the information model repository. The error message does not make sense to me. Should it not be “Probably the information model from 15/12/2023 is missing in the information model repository”? Anyway, both versions are available in the repository. How can I solve this?
Last updated: 2024-03-13

Post by nikgind on Codesys Communication Manger - Required information model version exists in the model repository but is not found CODESYS Forge talk (Post)
Hi I am trying to import a custom information model that I created using UA Modeler. I have only added two new methods and two new object types. It is possible to add the information model to the Communication Manager and the two new object types are shown in the Information Model tab. After compiling i get the following error: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://yourorganisation.org/Bsp_3.1/ with a minimal publication date from 15.12.2023 but the device has only a model from 15.09.2021 installed. Probably the information model from 15.09.2021 is missing in the information model repository. The error message does not make sense to me. Should it not be “Probably the information model from 15/12/2023 is missing in the information model repository”? Anyway I have installed the information model from 15/12/2023 but not from 15/09/2021. Which makes the error message even stranger.
Last updated: 2024-06-09

Post by mandeepahujaifm on Ethernet/IP 4.6.0 causing exceptions? CODESYS Forge talk (Post)
I have experienced the same with one of our customers after updating EIP Scanner to 4.6.0.0 and really baffled by it. The core dump simply shows error with ENIPScanner I/O task and on analyzing it says no source code available for 4.6.0.0. Contemplating to go back to 4.5.1 but 4.6.0.0 has some really nice fixes. I guess it don't matter if it crashes anways. Please keep us posted if you find anything.
Last updated: 2024-07-11

Post by totorovic on Hard shutdown: no code on device after power on CODESYS Forge talk (Post)
However, if faulty EtherCAT cables were the issue, why wouldn't the error occur during normal operation? Why would bad cables only cause problems during a hard shutdown? I don't have the answer to this question. One last question: When you encountered this behavior, did you see a similar error in your logs? i.e, an "AccessViolation" exception in the EtherCAT Task Yes. It was the exeption you can see in attached file.
Last updated: 2024-10-03

Post by trusty-squire on AXIS Rollover CODESYS Forge talk (Post)
In that case, the best thing to do might be to track the offset in a separate variable of your logic, then when you provide target positions, make your target position use the tracked offset as below: ActualTargetPosition := (TargetPosition + MyOffset) MOD 360; Although, upon further reflection, you'll still have the same cycle time issues. You might be able to break your code into multiple tasks to reduce the cycle time, or use an Event task to capture the offset position?
Last updated: 2025-03-12

Post by sturmghost on Find visualization elements that require a lot of computing time CODESYS Forge talk (Post)
I found out that the Codesys simulation mode is not good to measure performance. As soon as I upload the code onto the hardware PLC I can see that my visu-task needs around 60 ms to complete. I'm wondering if there is a possibility to find out which visualization/visualization element takes a lot of computing time? Then I would look for ways to decrease the long computing time.
Last updated: 2024-01-22

Post by tk096 on Fieldbus has lost synchronicity CODESYS Forge talk (Post)
Hi, a few suggestions on how to tackle the problem: - it might help to increase the cycle time of the ethercat task - increase the value of the ethercat parameter DCInSyncWindow (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/DCInSyncWindow.html) (see attached image) - enable FrameAtTaskStart (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/FrameAtTaskStart.html) in the ethercat master (see attached image) - if the drives can handle the synchronization problems, checking of the synchronization can be deactivated using SMC_Set_ETC_DCSyncSupervision (https://content.helpme-codesys.com/en/libs/SM3_Drive_ETC/Current/SMC_Set_ETC_DCSyncSupervision.html).
Last updated: 2024-04-11

Post by yofi on Raspberry Pi 4 POU not running CODESYS Forge talk (Post)
I have this error where the pou doesn't run even for simple programs like contact and a coil if i remove the pou from the task and put another one it works for one run then it stops working again in the photo we can see a contact is on but the coil connected to it is still not on and the device is in run mode I had this issue again and again any help
Last updated: 2024-06-02

Post by yofi on Raspberry Pi 4 POU not running CODESYS Forge talk (Post)
I have this error where the pou doesn't run even for simple programs like contact and a coil if i remove the pou from the task and put another one it works for one run then it stops working again in the photo we can see a contact is on but the coil connected to it is still not on and the device is in run mode I had this issue again and again any help
Last updated: 2024-06-02

Post by swe-hob on call of a method of a function block in another program CODESYS Forge talk (Post)
Hi, Let's assume following: PRG_1 fb_1 : fbExample1; fb_1.method_1 do something... PRG_2 fb_2 : fbExample2; fb_2.method_2 if xTest then PRG_1.fb_1.method_1(); end_if; Is there a reason why runtime hangs when I call the method_1 in PRG_1 from a method in PRG_2? Both programs run in the same task. No chance that any other program calls the method. What I practically do there is that in the program PRG_2 I add a structed object into a buffer. In PRG_1 I just process the items in the buffer.
Last updated: 2024-06-03

Post by swe-hob on call of a method of a function block in another program CODESYS Forge talk (Post)
Hi, Let's assume following: PRG_1 fb_1 : fbExample1; fb_1.method_1 do something... PRG_2 fb_2 : fbExample2; fb_2.method_2 if xTest then PRG_1.fb_1.method_1(); end_if; Is there a reason why runtime hangs when I call the method_1 in PRG_1 from a method in PRG_2? Both programs run in the same task. No chance that any other program calls the method. What I practically do there is that in the program PRG_2 I add a structed object into a buffer. In PRG_1 I just process the items in the buffer.
Last updated: 2024-06-03

Post by ben1 on How to stay in a method until something is finished. CODESYS Forge talk (Post)
Why must you use a method? Top of my head can't you just use the button to turn on a bit and use it in a normal task? Just turn a bit on with the button, and run a TON from it in code, and turn it back off with the ton. And then just log the pressure on both the rising & falling edge?
Last updated: 2025-11-03

Post by gorditron on I2C Communication with CODESYS Forge talk (Post)
Hello, I have problems with the I2C communication to an ADS7828 AD converter. I don't get any value back from the chip. I use a Kontron chip (ARM 32SC) with Linux as the operating system. I also use the CmpCharDevice library. ADS7828 parameters Address: A1 = 0 / A0 = 0 = SD = 1 = Single End C2 = 0 / C1= 0 / C0= 0 / Channel 0 PD1 = Internal Reference and PD0 = AD Converter ON Here is my code: VAR b_i2cAdr : BYTE := 16#48; (* Standard I2C-Adresse des ADS7828 *) x_Init: BOOL;(* Flag für die Initialisierung *) b_config_byte: BYTE;(* Konfigurationsbyte für den ADS7828 *) ab_cmd_buffer : ARRAY [0..0] OF BYTE; (* Buffer für den Befehl *) ab_data_buffer : ARRAY [0..1] OF BYTE; (* Buffer für die empfangenen Daten *) ui_adc_value_1 : UINT; (* Ausgelesener ADC-Wert *) I2C_Handle: RTS_IEC_HANDLE; (* Handle für das I2C-Device *) di_result_open: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_adr: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_wr_cmd: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_rd_cmd: DINT;(* Ergebnis der Funktionsaufrufe *) di_result_close: DINT;(* Ergebnis der Funktionsaufrufe *) END_VAR //*** Init from the I2C communication port *** IF NOT x_Init THEN I2C_Handle := CDOpen(szFile:= '/dev/i2c-0', dFlags:= O_RDWR, pResult:= ADR(di_result_open)); //* I2C opening * //*** set of the I2C address *** CDIoctl(hFile:=I2C_Handle , dRequest:=1795 , dParameter:=b_i2cAdr , pResult:=ADR(di_result_adr) ); x_Init := TRUE; END_IF (* Hauptlogik *) IF I2C_Handle <> 0 THEN (* Konfigurationsbyte setzen: Single-Ended Kanal 0, interne Referenz *) b_config_byte := 16#8C; (* 10001100b: AIN0, interne Referenz, Single-Ended *) ab_cmd_buffer[0] := b_config_byte; (* Schreiboperation zum Konfigurieren des Chips *) CDWrite(hFile:= I2C_Handle, pbyBuffer:= ADR(ab_cmd_buffer), udCount:= SIZEOF(ab_cmd_buffer), pResult:= ADR(di_result_wr_cmd)); IF di_result_wr_cmd = 0 THEN (* Leseoperation, um den ADC-Wert zu erhalten *) CDRead(hFile:= I2C_Handle, pbyBuffer:= ADR(ab_data_buffer), udCount:= SIZEOF(ab_data_buffer), pResult:= ADR(di_result_rd_cmd)); IF di_result_rd_cmd = 0 THEN (* ADC-Wert aus den Daten extrahieren *) ui_adc_value_1 := SHL(TO_UINT(ab_data_buffer[0]), 8) OR TO_UINT(ab_data_buffer[1]); ELSE (* Fehler beim Lesen der Daten *) ui_adc_value_1 := 0; (* ADC-Wert auf 0 setzen *) END_IF ELSE (* Fehler beim Schreiben der Konfiguration *) ui_adc_value_1 := 0; END_IF END_IF
Last updated: 2024-12-13

Post by john-ronald on Communication error (#0), logout performed,please check if plc is connected CODESYS Forge talk (Post)
Hi, I have the same problem. However I am using ethernet connection not USB. I can ping the PLC and also connect to it via Wago ethernet settings, but I cannot upload using the Codesys 2.3. My PLC is Wago 750-862. The detailed error is - " connect: Connection refused Write attempt from invalid socket. " Any help would be appreciated.
Last updated: 2023-09-11

Post by timvh on ernesto881124 CODESYS Forge talk (Post)
You will need a USB to RS485 converter to connect the PC to the Modbus RTU Slave Device. In Windows this converter will be recognized as Serial COM poort (e.g. COM2, or COM3, see the windows device manager to find this out). Select this port in your CODESYS application. On the PC you need to use the CODESYS Control Win (SoftPLC) to run your application. It will not work in simulation mode, because then the Modbus Communication will not be activated.
Last updated: 2023-09-14

Post by nikgind on Codesys Communication Manger - Required information model version exists in the model repository but is not found CODESYS Forge talk (Post)
Hi, yes i did solve it. You have to change the namespace 0 model in the UaModeler. Open the modeler --> Settings --> Edit Settings --> scroll down to the last option "External Model Support" --> Check "Allow replacing built-in..." Now create a new project in the UaModeler. If you have to choose your base models, you can see the option "Find another Opc.Ua.NodeSet2". I have attached the .xml i am using.
Last updated: 2024-06-28

Post by timvh on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
If your Control Win is the Modbus "Master" then your configuration should be something like: Modbus_COM (Serial port) - Modbus Master (this is the Control Win SoftPLC actively setting up the communication) - Modbus Slave (this is then your WAGO 750-315) You need to add channels to the Modbus Slave configuration to inform the master which variables to read/write from the Wago module. The way you configured it now, the Control Win is also a slave. PS, don't forget to put the PLC (Control Win) in Run.
Last updated: 2024-09-03

Post by thn-power on Codesys Communication Manger - Required information model version exists in the model repository but is not found CODESYS Forge talk (Post)
Hi. Thanks for the answer. I think I found your post on the Wago forum. I have tried installing all different nodeset versions of the opcfoundation.org/UA but neither work. Though I could not find the nodeset version called 15.09.2021 anywhere online. The opcfoundation repository only goes back to version 1.04.11 2022-03-29. Also wondering how I can generate a custom information model that only refrences the latest version of nodesets?
Last updated: 2024-09-19

Post by mani-i4point0 on Codesys (Ethernet IP Scanner ) and Python (Ethernet IP Adapter) CODESYS Forge talk (Post)
Hi, I am currently developing the software to establish the communication and data transfer between Python Module as a Ethernet IP - Adapter coding is running my laptop and Codesys as a Ethernet IP scanner in the resperry PI hardware. I am trying to look for some available recourses online, Can anyone suggest me to develop this function in Codesys and Python ? Best Regards, Mani
Last updated: 2024-09-24

Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20) CODESYS Forge talk (Post)
The RTE will take the RTE license. The HMI will take the HMI license. For the Application Based Licenses, the Runtime will take the smallest which is required. So if you have an application running EtherCAT and no visualization, only the Control with support for EtherCAT is used. If you have another runtime which requires the visualization, it will take the smallest Control license which is required and available + the smallest visualization license which is required.
Last updated: 2024-10-01

Post by mini-developer on Profinet Exor connection drop CODESYS Forge talk (Post)
Hello, I have a Exor HMI with 2 seperatred ETH interface's. It is Configured as PN Master on ETH interface 1 and the IO's are working, as long as the development PC is connected to the ETH 0 interface. When the PC is disconnected, the PN communication drops and a reconnection is started. I installed the newest device description for Codesys and Firmware for the Panel. The IO Gateway is from Weidmueller What could cause the Problem?