Post by installwhat on Panasonic servo Softmotion project
CODESYS Forge
talk
(Post)
There are examples installed when you install codesys. they are located in C:\Program Files\CODESYS 3.5.19.50\CODESYS\CODESYS SoftMotion\Examples The examples won't be specific to your drive, though you haven't specified the exact drive. After you add the device to the ethercat master you can click on it and set pdo etc
Last updated: 2024-06-13
Post by mucleus on What is the solution for "Application stopped on recovery switch request"?
CODESYS Forge
talk
(Post)
Hi, everyone. I am using CODESYS RTE and Profinet I/O or EtherCAT I/O. Occasionally (once every 1-2 months) the attached image occurs and the program stops. I want to know why this phenomenon occurs and how to solve it. I attached log. Please help me. Thanks.
Last updated: 2024-07-05
Post by charleskentyfz on (no subject)
CODESYS Forge
talk
(Post)
I have created an EtherCAT slave code and fixed two slaves (IDs written in the 0xF050 object dictionary). The module IDs are 0x1 and 0x101, respectively. It can be scanned normally in TwinCAT, but when scanning in CODESYS, it reports an error. Why is this happening?text in the second pic means 'device cannot be found in repository'
Last updated: 2024-07-07
Post by maxkemmeren on PFC200 (750-8214) high linux load average, but seems random. Possibly EtherCAT related.
CODESYS Forge
talk
(Post)
Have you received any feedback or found any solutions to the load problem. We are running into similar issues, even without codesys running the load avarage is above 1 meaning that it is to busy already without plc code running. Hope you might have some more insight.
Last updated: 2024-07-11
Post by rajankkrs on Ethercat master softmotion lost connection
CODESYS Forge
talk
(Post)
Dear Edwin, we are also facing similar problem of communication failure, FB3 error in servo drives. we tried all the suggestion by Kim but still we couldn't solve the issue. we uses Codesys 3.5 sp18 patch2, servotronix servo drives CDHD and crevis GN-9483. Any suggestion / input to solve the issue please. is anyway in codesys to reset the FB3 error? -Rajan
Last updated: 2024-10-07
Post by giackanto on Eoe issues with Windows and Linux
CODESYS Forge
talk
(Post)
Hello, I've been trying to use EoE for communication between a Windows PC and an M753 drive from Control Technique. Despite following some online guides (https://content.helpme-codesys.com/en/libs/EtherCATStack/4.3.0.0/Ethernet_over_EtherCAT/fld-Ethernet_over_EtherCAT.html) I haven’t had any success. Both are connected to a Debian device where RTE is running: The PC is connected via the Ethernet port. The drive is connected via the EtherCAT port. I'm unable to ping the drive from my Windows PC. Here is my configuration: On Debian: (See attachments 1, 2, 3) enp1s0 = Ethernet port enp2s0 = EtherCAT port tap2 = TAP device IP forwarding and routes are both configured. On Windows: (See attachments 4, 5) On Codesys: (See attachments 6, 7) Version: Windows 11 Debian GNU/Linux 11 Codesys 3.5.17 Control for Linux SL 4.7.0 EtherCAT 4.4.0 With this configuration, I can ping the TAP device, but not the drive (See attachment 8). Could someone explain how to properly configure all these settings? Thank you, GA
Last updated: 2023-12-19
Post by wehling-h on PI Input value
CODESYS Forge
talk
(Post)
Hi geoweil, have you tried to save changed values to remanent area or using a VAR RETAIN? After restart you have to initialize Counter with last remanent value. Depending on changes per cycle and the possibilitiy of your control unit to write remanent storage. Otherwise you need a buffering system to ensure save backup of last PI_Counter value. May you could read this Thread to get further help: https://forge.codesys.com/forge/talk/Engineering/thread/31e1c8349e/#bf48
Last updated: 2024-01-12
Post by sturmghost on Visualization using methods and cyclic ST-calls
CODESYS Forge
talk
(Post)
I found a way to do it: You can use, for example, the text variable property of any visualization element and call a function in it. Example: Write a test POU as a function (FUN), like MyTestFun which need a boolean Variable as an input value. Now write into the text variable property: MyTestFun(bBooleanValue) Thats it. The function is called at each visu_task cycle.
Last updated: 2024-01-22
Post by installwhat on Initialization of POUs (FB_Init)
CODESYS Forge
talk
(Post)
Hi I was wondering if there's a pattern I can employ to acheive what you're doing but with a "reference to" and also allowing for online changes? Someone told me that the new beckhoff keeps references safe during online changes but all the documentation I've found suggests that's not the case. The easiest thing is to use fb_init for normal vars and pointers and references can be added in the function body every cycle and this allows for method calls after so far as I can tell.
Last updated: 2024-07-29
Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time
CODESYS Forge
talk
(Post)
CODESYS Control for Raspberry Pi MC SL v4.4.0.0 CANopen_Manager 4.2.0.0 I did not call rm directly from my TASK-i2c, it was trough the attached python script. It is not always a problem happens, but sometimes a rm takes a long time. I reduced the amount of calls to logi2c.py but I don't understand why TASK-i2c sometimes can cause problems for TASK-CAN
Last updated: 2024-09-27
Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time
CODESYS Forge
talk
(Post)
CODESYS Control for Raspberry Pi MC SL v4.4.0.0 CANopen_Manager 4.2.0.0 I did not call rm directly from my TASK-i2c, it was trough the attached python script. It is not always a problem happens, but sometimes a rm takes a long time. I reduced the amount of calls to logi2c.py but I don't understand why TASK-i2c sometimes can cause problems for TASK-CAN
Last updated: 2024-09-27
Post by albertisa on GPIO Konfiguration auf SK-AM64B
CODESYS Forge
talk
(Post)
Hallo, seit einigen Tagen versuche ich erfolglos eine Ansteuerung der GPIOs des SK-AM64B Entwicklungsboards (Texas Instruments) über Codesys zu bewerkstelligen. Bei dem Versuch GPIOs anzusteuern, ohne die devdesc.xml bzw. den iodriver anzupassen, wird mir von Codesys die Fehlermeldung "Bus läuft nicht" (siehe Screenshot) angezeigt. Welche Vorgehensweise wird zur Konfiguration der IO empfohlen? Ist eine Anpassung der devdesc.xml und des IOdrivers notwendig? Wie wird am besten bei der Anpassung der genannten Dateien vorgegangen? Folgende Dokumentation ist mir bekannt, hat mir aber noch nicht weitergeholfen: https://forge.codesys.com/drv/io-drivers/doc/Generic/
Last updated: 2023-09-19
Post by vincentger on using ADS1115
CODESYS Forge
talk
(Post)
Any reason the ADS1115 wouldnt work with SP20.1 and Runtime 10.0.0.0 on the Raspberry Pi . Using Bullseye or Buster i run into the same issue: Libary and integration works in general as described above BUT i am seeing "bleeding" between the analog inputs . Specifically consecutive ones: So sometimes the raw from AI1 shows on AI2, AI2 on AI3, .. AI4 on AI1. Even with filtering i cant smoothen that out properly and i feel like something is wrong. Almost like the bus is stumbling over itself, or the request from Codesys to the device.
Last updated: 2024-10-28
Post by sukrit on What licenses are required for runtime on raspberry pi cm4
CODESYS Forge
talk
(Post)
We have developed a project for 2 servo motors using raspberry pi computemodule 4 on ethercat master. we are using web visualization for display different screens. project is running well in demo. we want to implement it in production envoirment. being new still wondering which licences i need. Can We get this information in codesys devlopment software. code size is approx 5 mb, 1 instance of etharcat master and aproox 100 variables in visaualization.
Last updated: 2023-10-17
Post by totorovic on Softmotion not working with simulation mode
CODESYS Forge
talk
(Post)
Good morning, I think that the mode Simulation does not support the Softmotion functionnality because it runs the CODESYS process with normal priority wich is not a good thing for real-time behavior. If you want to test your PLC project, please use a Codesys Control Softmotion (and your computer must have the Ethercat driver installed) or much easier, download your code into the C6 Smart. BR
Last updated: 2024-05-13
Post by esave on Softmotion Axis Controll
CODESYS Forge
talk
(Post)
Hello everybody I have two of these EtherCat CiA402 stepper driver from Leadshine: https://www.leadshine.com/product-detail/EM3E-556E.html I want to controll them. I already have implemented them in Codesys with Softmotion. I see the position, the velocity and the status word so I can read everything. See picture 1. But when I want to write something like MC_Power or MC_MoveAbsolut with the SM3_Basic library it wont work and with the MC_Reset POU it shows: "SMC_R_DRIVE_DOESNT_ANSWER". See picture 2. Can somebody help me? Thanks a lot esave
Last updated: 2024-05-24
Post by installwhat on C0077 on one machine but not another
CODESYS Forge
talk
(Post)
https://forge.codesys.com/forge/talk/Engineering/thread/92c913bf7c/ Solved by changing the ethercat master version after reading the thread linked above. I think I need to read up on why this happened. I understand that placeholders should point to a particular version for obvious reasons however what has occurred in this instance is different. The example project was released as a "project archive" but it seems to load differently based on what I've got installed in my repositories. I'm going to dig into that tomorrow but any advice is welcome.
Last updated: 2024-06-11
Post by gepert on parker servo and position
CODESYS Forge
talk
(Post)
Hello, Thank you for your response. In my application i use ethercat and while work i do not turn off power. After relative move motor is in standstill. As you suggest I suppose that problem is in drive setting but i do not see any option about increase standstill torque. Below i posted some photos from drive setting manager - PSD Servomanager Do you see any settings responsible for standstill torque? thank you
Last updated: 2024-08-05
Post by alex-at-xana on EThercat Dynamic configuration
CODESYS Forge
talk
(Post)
Hi Everyone, For a fast monitoring system I am using Ethercat oversampling and timestamping inputs. As the customers has a lot of different configurations out in the field, we went for a dynamic Ethercat configuration. Already got the whole detection chain working but now I am stuck since two days in debugging the configuration. Here are my quesitons: I extended the dynamic config example for the EL3632 16#0E303052: //EL3632 pSlave^.SetDCSettings(TRUE,TRUE,80,80,TRUE,4000,0,0); pSlave^.AddSyncManager(16#1000,128,16#26,TRUE,3); pSlave^.AddSyncManager(16#1080,128,16#22,TRUE,2); pSlave^.AddSyncManager(16#1100,0,16#4,TRUE,1); pSlave^.AddSyncManager(16#1110,214,16#20,TRUE,0); pSlave^.AddFMMU(0,214,0,7,16#1110,0,1,1); pSlave^.AddFMMU(0,1,0,0,16#80D,0,1,1); xKnown := TRUE; This leads to a PLL Error for these devices. I double and triple checked the configuraton, but cannot find the issue. There seems to be one difference: the config dialog creates a startup parameter: 16#10F3:16#05, Name: Command_0, Value:0. Bitlen: 16, Stop on fault: false, jumpt at fault: false: next line: 0 a) I do not find information on how to set this in my code. Can you help me there? b) Without trying to set the value, I get a PLL error for these devices in the master log. Is the config wrong? c) Do I need to set the Master to Autoconfigure or Manual? I used autoconfigure for my tests. The stack creates input data addresses for the slaves input data range (pSlaves[i].InputData) which are different from those created when I use the Engineering tools dialogs to configure Ethercat. Specifically, the addresses seem to be aligned at 16 byte boundaries when they are created using the engineering tool, but may appear at uneven addresses when I use the script in dynamic config. I did not try to access ULINT at uneven addresses yet, but I am suspecting this may be a problem. Do I need to manually align the addresses ? Any help is appreciated...
Last updated: 2024-09-10
Post by tvm on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
ok, that's different than our issue then. We're using Schneider Electric M262 PLCs, and we've had it where certain web browsers cause the web server to only allow https connections, but it's not recoverable with a refresh. It usually requires a power cycle or even a full firmware flash. Your issue might have more to do with the timing. I don't know if it helps you, but we normally run our visu task at 200mS, with an update rate of 200mS. Seems to work. I went through this: https://faq.codesys.com/pages/viewpage.action?pageId=112525371 but it really seems like trial and error.
Last updated: 2023-09-06
Post by jegerjon on Testing of Codesys program
CODESYS Forge
talk
(Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07
Post by jegerjon on Testing of Codesys program
CODESYS Forge
talk
(Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07
Post by niloufar on Execution Order of Function Blocks
CODESYS Forge
talk
(Post)
Hi, Our program incorporates various function blocks and programs written in different languages such as St and SFC. They implement numerous actions and methods using different languages from their function blocks. My question is whether the execution order of function blocks is associated with the programming languages used. I understand that cycle time can be configured in the task configuration, but I'm curious if there is a specific sequence order of execution for function blocks written in different languages. For example, all function blocks in (ST) are executed first, followed by the execution of (SFC). Specifically, when the function is written in (ST) and the action is implemented in (SFC). I modified all function blocks in the main PLC program and configured a task configuration for the main program.
Last updated: 2023-12-13
Post by cedriclee on RaspberryPI reconnection error
CODESYS Forge
talk
(Post)
"Hello, I'm Cedric Lee, a PLC engineer based in Korea. I'm reaching out about an ongoing issue with the connection when attempting to control Beckhoff modules using Raspberry Pi with CODESYS for the first time. I use CODESYS to target the Raspberry Pi's IP, install version 4.10.0.0 of the CODESYS Runtime Package, and upon pressing Start in the Runtime, the target connects to the Raspberry Pi. However, within about a minute, an error window appears, stating 'no connection to the device. please rescan your network,' leading to the disconnection of the target. This cycle repeats. I've attached some pictures for your reference. I'm using CODESYS Development System V3, Raspberry Pi 4 Model B (installed as 64-bit), and Beckhoff EK1100 modules. If anyone has a solution to this issue, please help. Your assistance is greatly appreciated."
Last updated: 2024-01-11
Post by timvh on Is it possible to use debug functions such as Step Execution while the PLC ladder is in Running?
CODESYS Forge
talk
(Post)
Yes, it is possible to set breakpoints and use step into / step over (also in Ladder diagram). Yes, the PLC will actually stop, so be carefull with this. How a PLC works is that at the start of the execution of the Task, the Inputs are read, then the code is being executed and then the outputs are written. So if you set a breakpoint, you will not see your analog inputs changing, because the task cycle is interrupted and the inputs and outputs are not refreshed. For detailed information, see: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_using_breakpoints.html
Last updated: 2024-01-16