Post by bertcom on Converting each character to a string into ASCII
CODESYS Forge
talk
(Post)
Good afternoon, I have a project where i need to split a string and send it in ascii code to an Domino Printer. Concept: i get an String from an Zebra scanner looking like this : " R002043;5410761402862;Oil Plus 2C Comp.A - Gris Belge;1286193824;" To start is the ";" the seperator. i found some functions to delete the ";" in a string. this is okay but now i want to convert each digit in the string into ascii like this: R=82 0=48 0=48 2=50 0=48 ... This because the printer wants to receive a string like this: <esc>OQ001TE 82 48 48 50 48 ...<eot></eot></esc> Anyone who can help me with setting me on the right track with some advice?
Last updated: 2024-11-08
Post by andrax on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
Ok, here are the libraries I use. First of all, try to get the ADS1115 to run completely on its own. Without MUX or other sensors. As muxboard I use this one: https://www.digikey.de/de/products/detail/sparkfun-electronics/BOB-16784/12714950?utm_adgroup=&utm_source=google&utm_medium=cpc&utm_campaign=PMax:%20Smart%20Shopping_Product_Zombie%20SKUs&utm_term=&productid=12714950&utm_content=&utm_id=go_cmp-18521752285_adg-_ad-__dev-c_ext-_prd-12714950_sig-Cj0KCQiA88a5BhDPARIsAFj595gkPXWPT8aa-EixL97BDWjO988WDhcx-iHOVbqb_H8CLpHBcwLuJW0aAu1JEALw_wcB&gad_source=1&gclid=Cj0KCQiA88a5BhDPARIsAFj595gkPXWPT8aa-EixL97BDWjO988WDhcx-iHOVbqb_H8CLpHBcwLuJW0aAu1JEALw_wcB All other boards don't work for me either. The terminating resistor is missing Important: Before you install the drivers, remove all other device drivers. My drivers are all located in ‘Raspberry I2C MUX_11_2023’
Last updated: 2024-11-11
Post by dsa28 on OPC UA subscriber not operational
CODESYS Forge
talk
(Post)
Hi, Thanks for the reply. Please note that the information and links provided are related to OPC UA Client/Server. My problem was related to OPC UA Pub/Sub. In the end I have managed to establish OPC UA Pub/Sub communication between Codesys and TwinCAT systems. Keep in mind that OPC UA Pub/Sub example is not provided in the latest library version 1.1.0.0. The user needs to download the previous version to get the example. During the configuration I ended up with some doubts regarding the usage of IEC_ARRAY type in the dataset definition (see attachment). Can you please give more information on how to use this type? Many thanks.
Last updated: 2024-11-29
Post by ben1 on Help understanding analog in-/outputs
CODESYS Forge
talk
(Post)
Hi there mate Most PLC's have a very similar concept with AI/AO - have you used any other software before? I have not used a Wago before myself, but I assume the concept would very much be: 1. Add the analog in & out cards to your hardware config. 2. Setup the raw input scaling on the hardware (eg. 4 - 20mA = 4000 - 20000) 3. Use a built in or homemade scaling block to scale your input as needed (eg. 4000 - 20000 = -100 - 2000kPa. 4. Write code as required 5. Scale output as needed (eg. 0 - 100% = 0-10000 = 0 - 10V) Is this the information you require?
Last updated: 2024-12-15
Post by sigurdrb on Read codesys version in the codesys application
CODESYS Forge
talk
(Post)
Hi! I want to read the codesys version into the project, so I can highlight it in the SCADA system. VAR dwVersion : DWORD; END_VAR SysTarget.SysTargetGetVersion(pulVersion := ADR(dwVersion)); This gives me the value 100859909. I tried to search ths up and found som older post (https://forge.codesys.com/forge/talk/Runtime/thread/a55981ff4d/) that said each 4 bytes reads a number in the version. Example is 50662666 = 16#03050D0A which reads to V3.5.13.10 When I run this code I get the value 100859909, which I cant translate to anything meaningful. I am running it on Codesys V3.5.19.70. Help appreciated!
Last updated: 2025-01-17
Post by pedegani on "Do you really want to perform" dialog boxes
CODESYS Forge
talk
(Post)
I have the same annoying problem. The confirmation prompt for every single action appeared recently after an update from CODESYS 3.5 SP20 Patch 3 to Patch4, but I don't think it's due to this. Having to confirm every operation while debugging an application is a considerable waste of time and does not help at all to concentrate on development, not to mention that many times you miss the long-awaited event because you are busy looking for the 'yes' button to resume debugging or force a variable. Does anyone know how to disable the confirmation messages?
Last updated: 2025-02-14
Post by tmarmy1 on Redundancy for RTE x64 - stuck in standalone
CODESYS Forge
talk
(Post)
Sorry if this has been asked before, but I can't seem to locate a thread that leads me answers. I am running two RTE x64 softPLCs, one on the host machine and a second via a VM. I have managed to finally get both to a position that they see each other, but they are in standalone mode instead of an active/passive state for failover (image attached). Every attempt to sync via the button fails. There is probably some step or option that I have missed in my bumbling through this learning process, but for the life of me I can't seem to figure it out. Anyone got any suggestions what I need to look at to get this into an active/passive redundancy state?
Last updated: 2025-02-20
Post by rshabsh on Using Latch Variable in Alarm as input from text list
CODESYS Forge
talk
(Post)
I am currently utilizing Alarm Manager’s Latch Variable 1 to display additional information related to alarms. However, instead of mapping this latch variable to a fixed PLC variable, I would like to dynamically update its text content based on the selected language in the system. To achieve this, I am considering using a text list that corresponds to different languages rather than directly linking Latch Variable 1 to a PLC variable. This approach would allow the displayed alarm information to be automatically translated according to the active language setting. Could you please confirm if this method is feasible within the Alarm Manager configuration? Additionally, if there are specific steps or best practices to follow when implementing this functionality, I would appreciate any guidance you can provide. Looking forward to your insights.
Last updated: 2025-02-26
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by struccc on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I don't exactly recall where (I think some release notes), but I read the information that this multiple application / sub application feature is to be discontinued. Please, correct me, if I'm not right about this I am a bit sad about that - I was using that feature with more or less success. However I understand the reason behind the change: it introduces huge complexity, especially when dealing with multicore and safety support... AS I understand, it's to be replaced with the new virtual plc architecture, and standard ways for synchronizing / sharing data... So, for now the "Add application" context menu item was removed, but behind the scene it is still supported... Hint: if you still want to experiment with it, might try copy-paste things within the PLCLogic tree...
Last updated: 2025-02-28
Post by peterkcontrols on Copying 2 byte word to output
CODESYS Forge
talk
(Post)
Hello. I am using codesys 3.5. I would like to know if it is possible to set a variable to an output without declaring in. I have defined a STRUCT and within this struct I have a Struct for inputs called I and a struct for outputs called O. I have declared a variable of the type of this Struct, I would like to set or alias the value in this variable to an input/output value of an IO block that has a module on the ethernet tree. Is it possible to copy the contents of %IW0 -> STRUCT.I ? The size of both of these is 2 bytes. I understand that I can declare a variable with the input like Input01 AT %IX0.0 : BOOL; However how can I make STRUCT.I.D00 AT %IX0.0? Is this possible? Thanks
Last updated: 2025-03-03
Post by mehakfatima on Need Help Configuring Energy Analyzers via Modbus TCP & RTU (RS-485) in CODESYS 3.5
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on reading data from energy analyzers using Modbus TCP and RTU (RS-485). In my previous software, I used the following method to add slave devices (i have attached the image) and configure registers: Add the Modbus slave device. Configure the communication parameters (baud rate, parity, etc.). Define the registers and their addresses for data retrieval. Now, I am trying to achieve the same in CODESYS 3.5, but I am not sure how to configure the Modbus master, add slave devices, and set up the registers properly. If anyone has experience with Modbus TCP/RTU setup in CODESYS 3.5, I would really appreciate your guidance! A step-by-step explanation or any references/tutorials would be extremely helpful.
Last updated: 2025-03-13
Post by madskaizer on ModbusTCP Slave Device, maximum uiClientConnections?
CODESYS Forge
talk
(Post)
I got a Wago PFC200V2, running Codesys 3.5.16.40, 100ms scan cycle, consumes about 20ms. It will randomly crash the runtime every 10 minutes to a few hours. We suspect an overloaded ModbusTCP Slave Device, as this is work done by a 3rd party contractor, but we can not find anything in the help files or documentation, that mentions a hard limit on maximum number of clients connections. This PLC currently has 44 client connections to the Slave Device and 29 slaves configured for its own Master Device. This topic metnions a hard limit of maximum 16 connections, but where is this written? https://forge.codesys.com/forge/talk/Engineering/thread/bd95b9d6d2/
Last updated: 2025-03-26
Post by hemuv on Dialog Open
CODESYS Forge
talk
(Post)
I'm programming an HMI for a machine. I want to log all the parameter's changes (used text field for displaying and changing) for particular User levels. Created a Numpad and want to log oldvalue and Newvalue on 'ok' Button press. To retrieve the oldvalue, i check if the dialogue opened is my Numpad, Then I retrieve the dialogue interface via GetDialogInterface(ADR(myNumpad)) --> numpadData.stVariableValue which contain my oldvalue and save it locally. Problem is sometimes i retrieve the data and sometimes not. Also observed when Numpad Dialogue is Opened, VisuDlgUtil_IsDialogOpen returns False in some cycles.Attached you will find my Project. please let me know what went wrong or if there is a better approach to collect old and New Value of a textfield. Thank you.
Last updated: 2025-03-26
Post by anlebr on Alarm group template - Is it not possible with several instances?
CODESYS Forge
talk
(Post)
Hi In the POU section of my project I have created a Fan function block and defined an alarm group template for this FB with one alarm (Motor fault). In the PLC program I define two instances of the fan function block. When going to the alarm configuration and pressing "Create or update alarm instances", I get two alarms listed. So far so good. However, when I start my program and check the alarm table in the visualization I only see one alarm, even if both are active. Am I doing something wrong, or is it not possible to define alarms on a function block level and get one set of alarms per instance of the function block?
Last updated: 2025-04-01
Post by timvh on How to manage soft container licenses for (remote) multi units?
CODESYS Forge
talk
(Post)
You need to activate an individual license (ticket number) for each device. THe hardware of each device is unique, so you cannot copy a soft container from one device to another. This license can be installed in a local (wibu - codemeter) soft container, or you could optionally activate it on a hardware (USB) key. The benefit of the key is that you can easily move it to another device, nor does it get lost when you replace parts of the hardware of the device or completely overwrite the image. See: https://store.codesys.com/en/codesys-key.html
Last updated: 2025-04-08
Post by ulvis on CFC Pages Cut&Paste is not working at its best
CODESYS Forge
talk
(Post)
In the CFC page oriendted editor, if I copy some elements consisting of an input connector, some connected logic and an output connector and then paste this on a another page then the pasted elements get inserted with an offset to the right so that the rightmost connector falls outside of the page, in the grey hatched area. So far so good. Then I mark all the elements and try to drag them into the correct placement, collectively. THIS IS NOT POSSIBLE! I only get the "forbidden" icon tooltip. One has to drag & drop the INDIVIDUAL elements to move the elements around. What am I doing wrong?
Last updated: 2025-05-15
Post by ulvis on CFC Pages Cut&Paste is not working at its best
CODESYS Forge
talk
(Post)
In the CFC page oriendted editor, if I copy some elements consisting of an input connector, some connected logic and an output connector and then paste this on a another page then the pasted elements get inserted with an offset to the right so that the rightmost connector falls outside of the page, in the grey hatched area. So far so good. Then I mark all the elements and try to drag them into the correct placement, collectively. THIS IS NOT POSSIBLE! I only get the "forbidden" icon tooltip. One has to drag & drop the INDIVIDUAL elements to move the elements around. What am I doing wrong?
Last updated: 2025-05-15
Post by ulvis on CFC Pages Cut&Paste is not working at its best
CODESYS Forge
talk
(Post)
In the CFC page oriendted editor, if I copy some elements consisting of an input connector, some connected logic and an output connector and then paste this on a another page then the pasted elements get inserted with an offset to the right so that the rightmost connector falls outside of the page, in the grey hatched area. So far so good. Then I mark all the elements and try to drag them into the correct placement, collectively. THIS IS NOT POSSIBLE! I only get the "forbidden" icon tooltip. One has to drag & drop the INDIVIDUAL elements to move the elements around. What am I doing wrong?
Last updated: 2025-05-15
Post by ulvis on CFC Cut & Paste not working at its best.
CODESYS Forge
talk
(Post)
In the CFC page oriendted editor, if I copy some elements consisting of an input connector, some connected logic and an output connector and then paste this on a another page then the pasted elements get inserted with an offset to the right so that the rightmost connector falls outside of the page, in the grey hatched area. So far so good. Then I mark all the elements and try to drag them into the correct placement, collectively. THIS IS NOT POSSIBLE! I only get the "forbidden" icon tooltip. One has to drag & drop the INDIVIDUAL elements to move the elements around. What am I doing wrong?
Last updated: 2025-05-15
Post by kut69 on Retain / Persistent Variables in Codesys for Raspberry Pi
CODESYS Forge
talk
(Post)
Hi, I am interested in details about the .ret file in the filesystem. I have already a project where the file is used (write on demand, read by start) and I want to share it as 'default input' for test devices using the identical application. Opening the .ret file content in a hex editor (I only use a single string retain var) I asked myself what the meaning of the first 24 bytes is. It neither contains a handle to the application nor a reference to the variable. Is this maybe a timestamp? Or a CRC/checksum? Regards, Thomas
Last updated: 2025-05-19
Post by edson-bueno on IFM Controller Connection Issue
CODESYS Forge
talk
(Post)
Hi, Could you please send an print of your ethernet adapter info? Ip addr Subnet Mask Default Gateway Also, check if the gateway service is active in your windows. Win+R > services.msc > Look in the list CODESYS Control Win V3 x64 Gateway OR CODESYS Gateway V3 Hook up the M12 code D into the ETH port, supply the controller, it should apperars to you. Make sure when you try to connect with the controller, the target of your project has to match with the controller. Otherwise, click on the device in the devices tree > Communications Settings tab > Device > Options > And disable "Filter Network Scans by Target ID". Good luck.
Last updated: 2025-05-29
Post by rockallsue on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
Some developers export ST code manually and edit it in VSCode, then copy it back. However, a more practical approach might be using automation scripts (PowerShell, Python) to extract and inject code into the CODESYS project. You could also check if CODESYS Automation Server or CODESYS API allows better ST access for external tools. https://www.codesys.com/the-system/releases-updates-lifecycle/release-plan-roadmap.html Network drive issues are particularly painful. As a mitigation, you could try using local project storage with periodic cloud sync instead of directly saving to a network drive. Using Rsync or Syncthing for automatic but safe synchronization might reduce risks of file corruption.
Last updated: 2025-06-03
Post by durallymax on Dynamical scaling of bar graph without the bar itself
CODESYS Forge
talk
(Post)
I'm a fan of the analog indicators from ISA101. To recreate these, I use a number of rectangles that are dynamically sized and colored based on the input configuration. To keep it standard and easy, everything is built around 100px height. Then when instantiated in a frame, it can be resized as needed with the math remaining the same. The math logic is in a METHOD called by the rear most rectangle. These indicators do not use a "filling" bar graph, rather a fixed bar graph with a carrot to track the current value.
Last updated: 2025-06-06