Post by jinlee on Multiple WebVisu
CODESYS Forge
talk
(Post)
Hi guys, I am new to the Visualization. I am having a problem. I have multiple web-panel to use webvisu. I have my software dowwloaded into the one PFC200. There are 3 screens connected to it. I noticed that if I switch page/visualisation on one of the screens, the others will change as well. Three screens are with different URLs that I set in the software. Is there any method to make them independently ? Kind regards, Jin.
Last updated: 2024-01-25
Post by wiresplus on INT_TO_WORD function not working
CODESYS Forge
talk
(Post)
Hello, I need to take an INT input, and convert it to a WORD value. VAR DRV2Speed : WORD; //IO card takes a WORD where 16000 = full 10V output (equivalent to 50Hz) PumpFillSpeed : INT; //Users enter a value between 0 and 50 END_VAR IF <conditions> THEN DRV2Speed :=INT_TO_WORD((PumpFillSpeed/50)*16000); END_IF </conditions> According to me this should work - but it stays at 0, no matter what. What am I doing wrong?
Last updated: 2024-01-26
Post by ojz0r on INT_TO_WORD function not working
CODESYS Forge
talk
(Post)
That calculation will not work the way you expect it to. If PumpFillSpeed is limitied to 0-50 then the only whole number would be 50/50 = 1 everything else is 0.0-0.9999... and since you are using word and integer only 50 would work since there is no representation for mantissa in integer values. Declare a temporary real variable and do the calculation and then do a REAL_TO_WORD in the DRV2Speed assignment.
Last updated: 2024-01-26
Post by ofey on two different OPC clients with different privileges
CODESYS Forge
talk
(Post)
Hi! I have usually only connected one OPC client (our system) to an OPC server created in the codesys environment on a PLC. This OPC client has a lot of write privileges. A customer also want OPC access, but I want to restrict his access to only read certain values. Do you know if this is possible inside the single codesys runtime running on a controller?
Last updated: 2024-02-01
Post by jshirazi on Restore license on Raspberry Pi
CODESYS Forge
talk
(Post)
Hi, I recently got a license for Raspberry Pi, after license activation I made a backup copy of "CMLicenseNew.WibuCmRaU" file to a safe place. Things got complicated and I tried to downgrade OS for some reason after that I tried several times/ways to restore my license with no luck. the specifications are as follows: Raspberry Pi 4 Model B Rev 1.1 codesyscontrol 4.10.0.0 SDK 3.5.19.30 Logs: **** ERROR: CodeMWriteLicenseFile: 'CMLicenseNew.WibuCmRaU' failed: Container not found or Server dose not support .... So if someone know a solution for this please kindly help me. Regards
Last updated: 2024-02-03
Post by tk096 on SMC_Interpolator + SMC_controAxislbyPos
CODESYS Forge
talk
(Post)
Hi, you can define a start position for your GCode. How the start position can be defined depends on the CompileMode: For File and SMC_CNC_REF: Set the start position input of SMC_NCInterpreter (https://content.helpme-codesys.com/en/libs/SM3_CNC/Current/SM_CNC_POUs/NC2/Interpreter/SMC_NCInterpreter.html) For SMC_OutQueue: * Right-click on the CNC object in the project tree * Select Properties * Select the tab 'CNC' * Set the start position Concerning your second question: If the new set position cannot be reached with the given velocity limit (AXIS_REF_SM3.fSWMaxVelocity), SMC_controlAxisByPos will report bStopIpo and close the 'gap' with the given gap dynamics (SMC_controlAxisByPos.fGap*).
Last updated: 2024-02-07
Post by otdeveloper on IEC 61499
CODESYS Forge
talk
(Post)
It is being worked on by many companies and its even-driven function blocks seem like a natural evolution of the object oriented industrial programming I have seen Gary Pratt (author of the Book of CODESYS and much more) so expertly implement and explain. I would expect CODESYS to have this front and center on their sights and, if they do not, I would be very interested in learning why.
Last updated: 2024-02-09
Post by andrax on Prüfen ob Datei existiert wenn nicht neu erstellen
CODESYS Forge
talk
(Post)
Hi, ich ich möchte prüfen ob eine Datei existiert. Wenn diese nicht existiert, soll eine erstellt werden und dort hinein geschrieben werden. Die Datei wird im Programmlauf mehrfach geöffnet und Daten hinein geschrieben. Ich will hier die Funktion File.MODE.MAPPENDPLUS benutzen, das funktioniert aber nicht. fopen.xDone bleibt false. Hier der Code: fopen.sFileName:=sFileName; fopen.eFileMode:=File.MODE.MAPPENDPLUS; // Neu erstellen und anhängen fopen.xExclusive:=TRUE; fopen( xExecute:=TRUE); IF fopen.xDone THEN hFile:=fopen.hFile; sStringToWrite:=''; writeIndex:=0; SchrittDatenlog:=60; END_IF Wo liegt mein Fehler?
Last updated: 2024-02-11
Post by nmcc on Toggling Visualizations using HMI Physical Buttons
CODESYS Forge
talk
(Post)
Hey thank you for the reply dkugler. I am sorry if this seems like a stupid question. I have the use current visuvariable checkbox enabled. I can see the string names of all my visualizations. I am trying to use ladder logic to be the anser to the button press using "VisuElems.CurrentVisu := 'MainScreen';. This returns an error. Any idea what I am doing wrong or could you point me in the right direction for fixing this. Thanks,
Last updated: 2024-02-13
Post by nmcc on Toggling Visualizations using HMI Physical Buttons
CODESYS Forge
talk
(Post)
Hey thank you for the reply dkugler. I am sorry if this seems like a stupid question. I have the use current visuvariable checkbox enabled. I can see the string names of all my visualizations. I am trying to use ladder logic to be the anser to the button press using "VisuElems.CurrentVisu := 'MainScreen';. This returns an error. Any idea what I am doing wrong or could you point me in the right direction for fixing this. Thanks,
Last updated: 2024-02-13
Post by martincapd on EWON
CODESYS Forge
talk
(Post)
I have the same problem in that I can connect to the eWon and ping the controller IP Address, however I cant connect through CodeSys. I'm using Gateway-1 which is configured to use "IP-Address: localhost" and "Port: 1217". Rather than scanning the network for devices, I enter the IP Address of the device, codesys returns a "No Device is repsonding..." message. See attached. I'm wondering if the IP-Address used Gateway-1 should be "localhost" or the WAN/LAN IP of the eWon? Thanks for the help MC
Last updated: 2024-02-21
Post by aniket-b on Multiple function blocks are not executing at the same time in ladder logic
CODESYS Forge
talk
(Post)
I have two ethernet Ip drives and created Function Blocks for different motions tasks. I am using same FB for both the drives. When I try to execute the relative move start command on FB for both the drives it is not working. However, if I add 1ms second delay between the execution of each drive it is working. Also when I change the rung order it is working for the first drive in the rung. what could be the wrong here?
Last updated: 2024-03-12
Post by stuartjr on Disabling forcing of specific variables
CODESYS Forge
talk
(Post)
OK.. so maybe I miss understood for how the forcing order works. It seems that the force list is applied at the beginning of every task call (I'm assuming this based on what I am seeing). If I force my variable FALSE and then write it TRUE in a task, then it stays TRUE for that task, but then in the next task it will go back to FALSE.
Last updated: 2024-03-15
Post by mp9876 on Device User Logon
CODESYS Forge
talk
(Post)
Just adding some info regarding the issue above. Logged onto the project using dev3og5 user (see screenshots); appeared to be ok although when attempting to logon to the device message says 'currently not authorized to perform this operation on the device' (screenshot). If user dev3og5 has same permissions as Owner user; why would it not be authorized. I am at a loss; any assistance would greatly be appreciated. Thank you Mike
Last updated: 2024-03-16
Post by timvh on Device logon problem following fresh install
CODESYS Forge
talk
(Post)
In your project you selected the "CODESYS Control Win V3" as device, but the device you want to connect to is a "CODESYS Control Win V3 x64". Those are not the same. If you double click on the device during the network scan, you will get information that these are not the same, but that you can change the type in your project to the x64 bit type. Another option is to "right-click" on the device in the device tree of your project and select "update device" then select the x64 type.
Last updated: 2024-03-19
Post by mimodia1 on I do not have any reedings in RUN MODE from MPU6050........
CODESYS Forge
talk
(Post)
Good morning, mecke96. Exactly the same thing happens to me, although I have not done the part of executing a .py file. It only reads the temperature and the counter, but the other values are zero as in your image "no readings". I have tested the MPU6050 device on an Arduino and it works. Could you tell me if you solved it?
Last updated: 2024-03-29
Post by amy123 on Alarm Manager Project Doesn't Open Successfully
CODESYS Forge
talk
(Post)
Hello, when I download AlarmManager.project from https://forge.codesys.com/prj/codesys-example/alarm-manager/home/Home/, it gives an error when I open it. If I ignore the warning and continue to open, the alarms are missing. ** Exception Text ** System.ArgumentNullException: Value cannot be null. Parameter name: first at _3S.CoDeSys.ControlsContrib.Utilities.WeakMulticastDelegate.Invoke(Object[] args) at _3S.CoDeSys.ControlsContrib.Controls.WizardControl.OnFinishClick(EventArgs e) at System.Windows.Forms.Control.OnClick(EventArgs e) at System.Windows.Forms.Button.OnMouseUp(MouseEventArgs mevent) at System.Windows.Forms.Control.WmMouseUp(Message& m, MouseButtons button, Int32 clicks) at System.Windows.Forms.Control.WndProc(Message& m) at System.Windows.Forms.ButtonBase.WndProc(Message& m) at System.Windows.Forms.Button.WndProc(Message& m) at System.Windows.Forms.NativeWindow.Callback(IntPtr hWnd, Int32 msg, IntPtr wparam, IntPtr lparam)
Last updated: 2024-04-04
Post by tk096 on Fieldbus has lost synchronicity
CODESYS Forge
talk
(Post)
Hi, a few suggestions on how to tackle the problem: - it might help to increase the cycle time of the ethercat task - increase the value of the ethercat parameter DCInSyncWindow (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/DCInSyncWindow.html) (see attached image) - enable FrameAtTaskStart (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/FrameAtTaskStart.html) in the ethercat master (see attached image) - if the drives can handle the synchronization problems, checking of the synchronization can be deactivated using SMC_Set_ETC_DCSyncSupervision (https://content.helpme-codesys.com/en/libs/SM3_Drive_ETC/Current/SMC_Set_ETC_DCSyncSupervision.html).
Last updated: 2024-04-11
Post by installwhat on raspistepper error after install
CODESYS Forge
talk
(Post)
I've had issues getting the raspistepper installed, all due to errors upon installation. The closest I get is the pictured error. The functions are in the sm3_shared library. I can add this library but that leaves 2 issues. I don't actually know, and I really want to understand this, why the required dependencies haven't been installed correctly. If I add the library it's only available with through the namespace. What can I do to both understand and resolve this? Thanks edit codesys 64 3.5.20.0 - same error on other versions too sm3 raspi stepper 0.0.0.5
Last updated: 2024-04-20
Post by dkugler on Alarm State Icon
CODESYS Forge
talk
(Post)
thank you for pointing me to this "bug"!! I haven't recognized, the bit is reset after the first alarm is gone. I use this only for warnings, so it's not a drama, but was not correct in the past. I solved it now simply stupid by counting up a variable every time an alarm appears and decreasing it if an alarm is gone. The "warning lamp" is activated by checking the counter is > 0 The nice side effect, i'm able to show the number of active alarms in the state line now.
Last updated: 2024-04-24
Post by dkugler on Codesys SVN
CODESYS Forge
talk
(Post)
Don't set on SVN. The service phase has started in March 2024 and will be discontinued in 2027. We actually use SVN and have to switch to GIT in the future. As I informed, there is no way of getting a single SVN or GIT licence. I' dont understand, why Codesys forces us customers to pay for an expensive Professional Edition paket from year to year using only one part of it! If you find a way to buy a single licence, let me know.
Last updated: 2024-04-29
Post by gseidel on Discontinuity of A/B/C axis movement.
CODESYS Forge
talk
(Post)
Hi jonasz, you already solved it, I'm answering here for the sake of others with a similar question. You can provide the slope of the A/B/C axis with the U/V/W word. See example 3 here: https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_cnc_din66025_additional_axis.html If you don't want to change the G-Code, the function block SMC_RecomputeABCSlopes can compute the slopes automatically. https://content.helpme-codesys.com/en/libs/SM3_CNC/Current/SM_CNC_POUs/SoftMotion-CNC/SoftMotion-Function-Blocks/SMC_RecomputeABCSlopes.html Best regards, Georg
Last updated: 2024-04-30
Post by gseidel on CNC - system goes to X=0 Y=0 before CNC file execution starts, how to avoid that?
CODESYS Forge
talk
(Post)
Hi peterned, the start position given in the CNC properties is only used if you use the compile mode OutQueue. With compile mode SMC_CNC_REF, you need to provide the start position in the IEC application. The function block SMC_NCInterpreter has an input piStartPosition. You can initialize it with the output of the forward kinematic transormation FB for your machine. In your case probably SMC_TRAFOF_Gantry2. Best regards, Georg
Last updated: 2024-04-30
Post by totorovic on Softmotion not working with simulation mode
CODESYS Forge
talk
(Post)
Good morning, I think that the mode Simulation does not support the Softmotion functionnality because it runs the CODESYS process with normal priority wich is not a good thing for real-time behavior. If you want to test your PLC project, please use a Codesys Control Softmotion (and your computer must have the Ethercat driver installed) or much easier, download your code into the C6 Smart. BR
Last updated: 2024-05-13
Post by tomas111 on OPC UA Client API
CODESYS Forge
talk
(Post)
I ran into a problem. Uploaded an example (https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_uacapi_example.html) After launch. on the emulator. I see that I am having problems: - UaExpert does not connect. There are many servers but no connection. - I can’t transfer the certificate from quarantine to trusted ones. There is some problem with creating the certificate. CS 19.2. If anyone has had similar problems, please give me advice. Thank you.
Last updated: 2024-05-20