Post by struccc on Problem Reading Registers via Modbus from non Codesys device CODESYS Forge talk (Post)
Hi, Might be a good idea first to try out the connection and the device with some handy software, like Modbus Poll. There you can see better, what's really going on... - Is it really connected? - What error code does it return? - Can it read from the register address? - Maybe try Input registers and Holding Registers - can make a difference - Sometimes register addresses are messed up: shifted +-1 (mixing of 2 standards) - Sometimes register addresses start with offset 30000, 40000 ... - Are you using the right protocol? - Is it RTU or TCP? Maybe ASCII? - Can even have a look at the data packets, etc... All this is easier to figure out first with some modbus utility... and then to set it up in CODESYS should not be an issue. P.
Last updated: 2025-03-09

Post by hemuv on Dialog Open CODESYS Forge talk (Post)
I'm programming an HMI for a machine. I want to log all the parameter's changes (used text field for displaying and changing) for particular User levels. Created a Numpad and want to log oldvalue and Newvalue on 'ok' Button press. To retrieve the oldvalue, i check if the dialogue opened is my Numpad, Then I retrieve the dialogue interface via GetDialogInterface(ADR(myNumpad)) --> numpadData.stVariableValue which contain my oldvalue and save it locally. Problem is sometimes i retrieve the data and sometimes not. Also observed when Numpad Dialogue is Opened, VisuDlgUtil_IsDialogOpen returns False in some cycles.Attached you will find my Project. please let me know what went wrong or if there is a better approach to collect old and New Value of a textfield. Thank you.
Last updated: 2025-03-26

Post by imdatatas on Programmatically change Tappet on a cam CODESYS Forge talk (Post)
Yes, There is. As explained "Manual creation of CAM structure" on below section. Likewise tappet structure also can be create manual and value of the switching point can be change during IEC program running. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_basic_cam_programmatic_creation.html Just create a cam table and define some tapped points as sample for your project. Then on project compile, the created cam tapped data is converted internally into a global variable list. By clicking "Display generated code" in the "cam editor", you can display the automatically created global variables for both cam & tappets. Regards, Imdat
Last updated: 2025-04-02

Post by elsmart on How to create custom visualisation components (widgets)? CODESYS Forge talk (Post)
Hello I'm currently working on a project where I need to implement visualisation in Codesys on Raspberry Pi via web browser. I'm uing Codesys IDE V. 3.5 and I was able to successfully run my program and visualisation using generic elements provided by Codesys on Raspberry Pi Compute Module 4. However I am dissatisifed by the limiations and looks of generic elements. I would like to create my own components for this specific task (like cyclic buffer with messege boxes or matrix of data structures). How do people develop their own visualisation components in Codesys and how to implement them in a project?
Last updated: 2025-05-27

Post by timvh on Codesys 3.5.18.60 – Application Loss and Persistent Data Corruption CODESYS Forge talk (Post)
Which device do you use? Does this have persistent memory (e.g. NVRAM) available? Maybe first ask your PLC vendor about the possibilities and how they advice to use persistent variables? If you have no NVRAM available, CODESYS will store the variables in a file when the device gracefully shuts down. But on an abrupt power failure, this is not possible. If you have no NVRAM and you want to use persistent variables, then consider using a UPS. In this case when the power is lost, the UPS can keep the power on the PLC which then can gracefully shut down. Alternatively use the Persistence Manager to store the variable values in a file e.g. only on change. See: https://content.helpme-codesys.com/en/CODESYS%20Application%20Composer/ac_pm_overview.html
Last updated: 2025-08-26

Post by jzhvymetal77 on VarAccGetAddress does not return the correct address for TYPE_ARRAY or TYPE_USERDEF. CODESYS Forge talk (Post)
VarAccGetAddress does not return the correct address for TYPE_ARRAY or TYPE_USERDEF. When you use VarAccGetNode, it returns a proper IBaseTreeNode if you provide the full path of an array element or structure element, and it even provides the correct data type. The problem is that with TYPE_ARRAY, it returns the start address of the array rather than the indexed element. With TYPE_USERDEF, it only returns the offset of the element instead of the actual address. This causes many issues with nested structures or arrays of structures, since it requires manually calculating the address based on the parent IBaseTreeNode. See attached image and example.
Last updated: 2025-08-28

Post by sumit on Remote Ethernet/ip Adapter communication with scanner running on codesys CODESYS Forge talk (Post)
Hello there, I have my ethernet/ip adapter (from Texas Instrument) running on Texas Instrument Board and I have configured the scanner on codesys. I have mapped the I/Os and I can see (on wireshark) the frames coming from adapter but I don't see my input variables in scanner get updated, they just stay at 0. I wanted to see the real data that has been sent from adapter to scanner on codesys. I am not sure if the problem is in I/O mapping or there is a step/s that I have missed. I have attached the screenshot of my project for your ref. Thank you, Sumit
Last updated: 2023-12-15

Post by sumit on Remote Ethernet/ip Adapter communication with scanner running on codesys CODESYS Forge talk (Post)
Hello there, I have my ethernet/ip adapter (from Texas Instrument) running on Texas Instrument Board and I have configured the scanner on codesys. I have mapped the I/Os and I can see (on wireshark) the frames coming from adapter but I don't see my input variables in scanner get updated, they just stay at 0. I wanted to see the real data that has been sent from adapter to scanner on codesys. I am not sure if the problem is in I/O mapping or there is a step/s that I have missed. I have attached the screenshot of my project for your ref. Thank you, Sumit
Last updated: 2023-12-15

Post by royw on Profinet library for C# CODESYS Forge talk (Post)
Hi, I don't know if I'm in the right place or if it's even possible... I'm looking for a way to address a Profinet device with Record Read and Write from my own PC. I actually only need very few commands to configure our device. This means setting the MAC address and a serial number. We would like to do this from a C# program. Now we are looking for a library or something similar. Since you can do it from Codesys, I thought there might be a DLL or something similar that you could use for this. As I said, we don't want real-time queries of the cyclic data but only record read/write. Does anyone have any helpful hint? Thanks in advance
Last updated: 2023-12-22

Post by askjong on Update variables when OPC UA Client updates. Error ID: 268468277 BadAttributeIdInvalid CODESYS Forge talk (Post)
Hi, I'm connecting to a OPC UA Server using the Data Soruce Manager OPC UA Client. This works well until the OPC UA Server updates and the OPC UA list doesn't match up when i did last clicked the "Update variables" to add variables. All the variables are still the exists and none are removed from the server, but more are added during the engineering process. The error message i get in CODESYS is "Error in OPC UA call BadAttributeIdInvalid, Error ID: 268468277". The issues is fixed when i press the "Update variables" button and just press ok without adding or removing any variables in the list. Is there a way to either automatically update the browsepath if it fails or on startup, or to trigger it by code?
Last updated: 2024-01-08

Post by comingback4u on Memory Address Overlap CODESYS Forge talk (Post)
Hello, We use a controller that comes with a bunch of predefined faults. These faults are considered active and historic. They are a 32 byte array but only take up 26 bytes of data. Because of this the historic faults start at address 26 instead of 31. Active faults variable take up address location 0 to 31. Historic faults variable take up address location 26 to 57. Because of this overlap I get an error that these overlap and it wont allow me to download to my controller. This isn't an issue in 3.5.5.4 but becomes an issue in newer version. Is there a way to turn this off? If I change the address location, the historic faults then become broken without doing some manipulation in the code. The software will build just fine. Thank you for your time.
Last updated: 2024-03-07

Post by dhumphries on How to determine code size CODESYS Forge talk (Post)
I'm trying to determine which Codesys Control license I need, the Control Standard S has all the features I think I'll need, but the code size is limited to 3mb, I created a simple program with only 1 line of ladder logic and a simple visualization with a button and an indicator. When I generate code I get some messages, one indicates that the total allocated memory size for code and data is 2.1mb. Is this metric the correct size of the code? I question the size because it exceeds the allowable code size for the Basic S and Basic M licenses and consumes 2/3 of the available memory for the Basic L or Standard S license. What tool can I use to estimate the size of code as it relates to the runtime license limit?
Last updated: 2024-04-05

Post by dkugler on build (F11) / generate code using a python script file CODESYS Forge talk (Post)
thank you very much! I found the generate_code methode, but struggled with the primary and active_application. With this expample I will be able to play around. If the code generation takes a minute or more I often switch to other programs and don't notify the process is finished. So now I'll get an alert and will switch back immediately. My next little project will be, to beep different if there are errors and a seperate script to do the download incl. the user management data base without stopping at the dialogs asking for onlinechange/complete download and overwriting an existing database and as goody, play a beep/sound again.
Last updated: 2024-04-11

Post by mbmik on IoDrvModbusTCP_Diag not defined when using MODBUS CODESYS Forge talk (Post)
Hi Im trying to setup a WeidmΓΌller WL2000 to run with MODBUS, to get some data from a server. Codesys V3.5 SP20. The issue is, that whenever i attach an ethernet port and add MODBUS Master und also a Slave, codesys will compile the project, but there always seem to be some remaining errors, which or only visible, when setting the messages window to "Pre-Compiled". I tried a lot of stuff to get rid of these errors, but cant find to seem the reason. New installation of codesys, cleaned project, setup completely empty new project, manually adding libs. Nothing helps. Any help is apreciated. Maybe we are doing something wrong.. Example Project is available, if somebodey wants to take a look. Greetings and thanks alot
Last updated: 2024-04-15

Post by alexgooi on FB_INIT in library CODESYS Forge talk (Post)
Dear Forum, I currently have a challenge. I have a library with some communication classes. These communication classes need to be linked to an interface like this: Devices_and_controllers.Comm_Frame.Modbus_GVL_Link.KNX_TCP[Interface_Index] := THIS^; This is executed via a FB_Init() method. When I try to do this in a program this works fine. But when I declare the FB_Init() in the library the FB_Init() method is being called but the link is not made (interface still has the value 0000000000). The Objects and interfaces are defined in the library (GVL), so I’m assuming the data should be there. When I call the FB_Init method explicitly in the program it also works fine. Whys is this not working when it is all defined in the library? And is it even possible to create a structure like this in Codesys? Kind regards Alex
Last updated: 2024-05-22

Post by robpqs on Program from one PLC to other WAGO 750-8204 CODESYS Forge talk (Post)
Hello, You use the WAGOUpload tool. You can download it on the download center of WAGO. Make a backup and restore it on the new device. (if can check the remanent data to copy the persistent variables if necessary) You can also use a SD card, go to the WBM copy it the image to the SD card and restart the other controller on the SD card. In the WBM, copy it back to the internal flash. If you contact your local Wago office, they will more than probably help you. There is also a WAGO forum. RP,
Last updated: 2024-05-27

Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device CODESYS Forge talk (Post)
Hello, CODESYS Control is running on my RevPi, and my system communicates over a CANbus with a master using the ConnectCan module (Slave - CANopen Device). The communication works perfectly fine so far. However, as soon as I call a Python script with "SysProcessExecuteCommand2" that creates a CSV file and executes without errors, the master does not adopt any changes to the Transmission Process Data Objects (TPDOs). I don't quite understand what one has to do with the other, and perhaps someone can help me with this. Here is my script call: SysProcess.SysProcessExecuteCommand2(pszCommand:='python /home/pi/test.py', pszStdOut:=sCMDOutput, udiStdOutLen:= SIZEOF(sCMDOutput), pResult := ADR(eResult)); Thank you in advance! Best regards, Stefan
Last updated: 2024-06-20

Post by msegon on OPC UA Client failed to connect CODESYS Forge talk (Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I'm trying to read data from Tridium Niagara 4.15 OPC UA Server, but I get the error BadCertificateInvalid. As far as I understand, you need to add a CA certificate somewhere to establish a secure connection, but I don't know where. 2025-10-27T09:06:43.247Z, 0x0000008d, 4, 0, 0, * ERROR: OpcUa_Channel_BeginConnect: Cannot create secure channel without certificates! 2025-10-27T09:06:43.247Z, 0x00001090, 4, 0, 0, * ERROR: Datasource: Error Failed (268468242) in state Connecting I tried communicating without encryption, but it doesn't find the point. Has anyone managed to establish encrypted OPC UA communication?
Last updated: 2025-10-28

Post by miltos on licensing question CODESYS Forge talk (Post)
Greetings to all, I'm working on a webvisu project on control win V3 x64 runtime, and have purchased 3 licenses for my application. -Codesys Control Standard M -Codesys Visualization L -Codesys Communication M I have them installed on a Codesys usb dongle When I try to download the program, a login error window appears with the message "No valid license found for the webvisualization". The control win v3 communicates with 3 plc, and have enabled communication over codesys V3 communication by adding one datasource for every plc in the datamanager. If I remove the data manager from the project, the rest of the visualisation can be downloaded normally. Do I need to purchase another License and which one? Please find attached the software metrics and the error screen.
Last updated: 2025-10-31

Post by mattkaree on Mapping values with etherCAT mailbox communication CODESYS Forge talk (Post)
I am using a WAGO PFC200 PLC as an etherCAT master and a Keyence IV3-G120 with DL-EC1A attached as an etherCAT slave. I am using CODESYS V3.5 SP21 Patch 3. I was able to set up mailbox communication and can see values changing accordingly, but I want to know how I can map these values and reference them in my program. I am able to map the process data objects in the 'EtherCAT I/O Mapping' tab, but there is no where to map the mailbox values in the 'CoE Online' tab. Is there a way I can reference one of these values in my code?
Last updated: 2026-01-27

Post by timvh on EXCEPTION [watchdog] how to find position cause CODESYS Forge talk (Post)
Monitor what your current cycle time is (in the Task Configuration when you are online). If this is sometimes close to 200ms, then change your code (e.g. limit the loops, or prevent copying a lot of data between objects). Or just set the Watchdog time (or sensitivity) higher if you don't care that it sometimes takes longer than 200ms. If you want to find out which objects in your application consume the most time, then buy a PDE (Professional Developer Edition) license. With this you get a license for the Profiler. This can help you a lot to find the root cause, because it will create a nice overview of all objects, their calls and the time (percentage) it takes to execute it.
Last updated: 2026-02-09

Post by dvmaris on Control for Linux ARM64-User Management issue CODESYS Forge talk (Post)
I'm trying to work with Codesys Control for Linux ARM64 SL 4.18.0.0 on a Toradex Verdin NXP iMX8MP. I have the runtime installed and operational as well as Codemeter lite 8.40.7141.503 (arm64). I'm running 3.5.20.60 and when "Scan Network" I see the Verdin popup. When I try to connect to it, the "mandatory use of the user management" popup shows...which makes sense. I click YES and enter user information and click OK. It immediately displays a "No device is responding to the scan request" popup. The IDE can see the Verdin in the scan...so this popup does not make sense to me. I thought maybe it was a read only issue but I've made all partitions and paths RW. Has anyone experienced this? Can anyone tell me where it is trying to write user data?
Last updated: 2026-02-11

Post by mondinmr on Why SysPipeWindows is not implemented in RTE? CODESYS Forge talk (Post)
This library would be very useful for IPC communications. Using a UDP socket on localhost is unpredictable, as with slightly loaded machines it does not even guarantee packet delivery locally. Using TCP creates a lot of overhead. Message named pipes would be an excellent solution for Windows RTE. On Linux, since the release of the extension package, there is no issue, as it is sufficient to develop a component. However, although now 90% of our clients understand that Linux runtimes are better in every way compared to Windows RTE, especially from the security aspect (Not in kernel space) and the issues with Windows updates, 10% stubbornly insist (sometimes for trivial commercial reasons) on using Windows. Managing IPC with circular buffers in shared memory is quite ugly, or rather really ugly and unaesthetic. In the manuals, I saw the SysPipeWindows libraries, so I decided to test them, but unfortunately, I noticed that they are not implemented for RTE devices. Technically, I could try to open them as regular files, but SysFileOpen returns 16#27 or 16#39 depending on how I set the name (direction of the slashes). Here is the code to create shared memory and named pipes. Shared memory work great, named pipes no! #ifdef Q_OS_WIN32 SECURITY_ATTRIBUTES sa; SECURITY_DESCRIPTOR sd; InitializeSecurityDescriptor(&sd, SECURITY_DESCRIPTOR_REVISION); SetSecurityDescriptorDacl(&sd, TRUE, NULL, FALSE); sa.nLength = sizeof(SECURITY_ATTRIBUTES); sa.lpSecurityDescriptor = &sd; sa.bInheritHandle = FALSE; const wchar_t* name = L"Global\\ShmTest"; HANDLE hMapFile = CreateFileMapping( INVALID_HANDLE_VALUE, NULL, PAGE_READWRITE, 0, sizeof(SharedData), name); if (hMapFile == NULL) { qCritical("Error creating shared memory"); return 1; } data = static_cast<SharedData*>(MapViewOfFile(hMapFile, FILE_MAP_ALL_ACCESS, 0, 0, sizeof(SharedData))); if (data == NULL) { qCritical("Error mapping shared memory"); return 1; } HANDLE hPipe = CreateNamedPipe( TEXT("\\\\.\\pipe\\MyPipe"), PIPE_ACCESS_DUPLEX, PIPE_TYPE_MESSAGE | PIPE_READMODE_MESSAGE | PIPE_WAIT, PIPE_UNLIMITED_INSTANCES, 1024 * 1024, 1024 * 1024, NMPWAIT_USE_DEFAULT_WAIT, &sa); if (hPipe == INVALID_HANDLE_VALUE) { qCritical("Error creating named pipe"); return -1; } if (!ConnectNamedPipe(hPipe, NULL)) { qCritical("Error connecting to named pipe"); return -1; } checkPipe(hPipe); #endif
Last updated: 2024-02-02

Post by struccc on Wish: CODESYSControl.cfg - again CODESYS Forge talk (Post)
Before creating this topic, I was browsing the search results for CodesysControl.cfg - many results, and I remember very well, it's a problematic issue for a long time. To summarize: there were many requests for documentation on this file - the most comprehensive reply is: https://forge.codesys.com/forge/talk/Runtime/thread/ebbf851a3d/#eb85 Hi, not really, this is covered by the manual which you get if you use a runtime toolkit which is not free of charge. Maybe we need to extract the config file part from that documentation if that is possible. BR Edwin I am not sure how much is this relevant, since we buy SL License directly from CODESYS... I think it is a reasonable demand, to get documentation on the configuration entries affecting the documented behaviour of the runtime system and it's components The actual reason I bring up this issue again can be read here: https://forge.codesys.com/forge/talk/Runtime/thread/febad3cc40/#0e12 but mostly my frustration about noticing some new, unknown and undocumented entries in my configuration file. Again. And this happens a lot recently. Just some examples: Changes with SysFile - and mandatory use of IEC path Introduction of Mandatory user management File transfer service now disabled by default SysProcess - allowed commands The above mentioned CmpApp parameters... And finally (Regaridng windows install): With the newer versions, the installation directory (together with the configuration file) tends to hide itself to some super silly location under the roaming profile data of local system account. I am not sure if this change was documented somewhere, but was a very unpleasant one. Someone could please explain the reason and the concept of the introduction of this release specific directories (I am sure, there is a good reason) - how to use them properly? - How to re-introduce user configuration (to preserve configuration data between versions)? - How to do version - to version migrations properly? - How to keep old version of runtime available and ready to start with it's original configuration and application? - ... Therefore, the lack a regularly updated description of CodesysControl .cfg , including all the configuration entries, together with their default values for different runtime versions is really a big deficiency.* This should be done for all components storing or just seeking data from this file... (Maybe there is such thing but I failed to find???) It is regularly causing trouble when introducing a new version (together with the long awaited bug fixes and enhancements), what has changed it's default behaviour for security or other practical reasons. I agree this is very important, and it is logical to change the default options: But it must be documented historically, and make it easily available, so we can prepare better for the upgrade of the runtime. Forge talk is a great source, but not very practical for this kind of documentation purposes... Thanks in advance for CODESYS staff πŸ™πŸ™πŸ™ (Ps.: It would look rather silly, if some members of the user community prepares this documentation on a Forge Wiki page... Or??? Should we?)
Last updated: 2024-11-21

Post by mgabryel on Problems with CAN 2.0 comunication on Wago PLC (Codesys 3.5) CODESYS Forge talk (Post)
Hello, I am trying to program CAN Bus comunication on WAGO PLC (more precisely on WAGO Touch Monitor model TP600). I am using for this purpose library "WagoAppCanLayer2" from Wago company. My IDE for programming this device is CODESYS V3.5 SP19 Patch 2 + (64-bit). My program is written in Structured text using function blocks from previously mentioned library. Here is code of this program: 1) Variables declarations: PROGRAM PLC_PRG VAR oOpenInterface : WagoAppCanLayer2.FbCanL2Open :=( udiBaudrate := 125000 ); xInterfaceIsOpen : BOOL; sInterfaceInfo : STRING; oReceive : WagoAppCanLayer2.FbCanRx29BitFrame :=( xBufferMode := FALSE, wCanId := 16#181 ); xRecv : BOOL; sReceiveInfo : STRING; oSend : WagoAppCanLayer2.FbCanTx29BitFrame :=( dwCanId := 16#100, //was 16#201 xRtrFrame := FALSE ); xSend : BOOL; sSendInfo : STRING; oCanDiag : WagoAppCanLayer2.FbCanErrorInfo; xRst : BOOL; aSendData : ARRAY [1..8] OF BYTE; bSendLen : BYTE; TON_0 : TON; TON_1 : TON; END_VAR 2) Program body: oOpenInterface( xEnable := NOT xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE ); sInterfaceInfo := oOpenInterface.oStatus.GetDescription(); xInterfaceIsOpen S= oOpenInterface.xValid AND NOT oOpenInterface.xError; oReceive( xEnable := xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, xRxTrigger := xRecv ); sReceiveInfo := oReceive.oStatus.GetDescription(); IF NOT xRecv THEN IF oReceive.bRxNBytes > 0 THEN oReceive.aRxBuffer[1]; oReceive.aRxBuffer[2]; oReceive.aRxBuffer[3]; oReceive.aRxBuffer[4]; oReceive.aRxBuffer[5]; oReceive.aRxBuffer[6]; oReceive.aRxBuffer[7]; oReceive.aRxBuffer[8]; END_IF xRecv := TRUE; END_IF aSendData[1] := 224; aSendData[2] := 13; aSendData[3] := 14; aSendData[4] := 15; aSendData[5] := 222; aSendData[6] := 13; aSendData[7] := 14; aSendData[8] := 15; bSendLen := 8; TON_0(IN:= NOT TON_1.Q, PT:= T#2S , Q=>xSend, ET=> ); TON_1(IN:= TON_0.Q, PT:= T#2S , Q=>, ET=> ); oSend( xEnable := xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, aTxBuffer := aSendData, bTxNBytes := bSendLen, xTxTrigger := xSend ); sSendInfo := oSend.oStatus.GetDescription(); oCanDiag( xEnable := TRUE, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, xTriggerResetCounter := xRst, xValid=> , xError=> , oStatus=> , wBusState=> , wBusDiag=> , uiRxOverflowsL2=> , uiTxOverflowsL2=> , uiRxOverflows=> , uiMsgTimeouts=> , uiBusOffs=> , uiBusWarnings=> ); Program first opens comunication on CAN 2 device and then periodically try send one CAN data frame. After starting program CAN 2 interface is properly open. The xSend variable is toggling with period 2s. When program sends data an "Tx overflow" error appears. When I am watching CAN_H line on DSub 9 socket i am not able to see proper CAN frames - see screenshot attached to this message. Could somebody help me determine what is wrong with this program. Best regards
Last updated: 2024-08-02