Post by dsa28 on OPC UA subscriber not operational
CODESYS Forge
talk
(Post)
Hello All, Hopefully I can get some help configuring an OPC UA subscriber in a CODESYS runtime in a Raspberry Pi 5 that tries to retrieve data from an OPC UA publisher (in this case running in a TwinCAT system). I tried to follow the steps described in the page to implement the OPC UA subscriber: https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_opcua_pubsub.html Seems that the example provided was created with version 3.5.16.0. Now with version 3.5.20.20 is not possible to open the complete project neither convert it. Anyway, after configuring all IPs and ports used in the OPC UA connection function block but the connection state always shows DISABLED. Can someone help me to do the proper configuration of the OPC UA subscriber? Many thanks in advance.
Last updated: 2024-10-22
Post by struccc on Problem Update new version Master ethercat
CODESYS Forge
talk
(Post)
Hi, I had some issues as well migrating to the new version. What I have learnt: - Have to check all the libraries in the library manager, if they are the proper versions. - Some other parts of the application, maybe an old library referenced by another one can keep the old Ethercat libraries.... Use the "Placeholders" function on the library manager - See if there is a new version available of the slave "devices". Might just have to update them ... I had problems moving from 4.7 to with 4.8, especially with the 2nd adapter for redundancy - some devices failed to initialize properly.... So I have just downgraded those libraries now. P.
Last updated: 2024-10-28
Post by pistola on Case Function - Multiple Conditions, Is it possible?
CODESYS Forge
talk
(Post)
Looking at the help (https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_st_instruction_case.html). I don't think it is possible but I figured I'd ask. I'm looking at have a case that evaluates two variables, instead of having multiple If Else statements I was hoping I could just use a case. Example * Case Var1 & Var 2 of 10 & 10: Instruction Code 10 & 20: Instruction Code 20 & 20: Instruction Code End_Case Obviously I tried typing as noted above and Codesys threw an error. But I was wondering if there was a different way of programming to make something like this work? If not I'll just use a bunch of If Else Statements, Thanks.
Last updated: 2024-11-03
Post by trusty-squire on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
How are the servo drives controlled? EtherCAT, step/dir pulses, other? Another thought is that - if it's step/dir pulse based control - the pulses from the PLC to the drive are getting missed/lost at high frequencies? If that's the case then there would be multiple troubleshooting steps/corrections that could be investigated. You could try to create a simplified program, with all the same parameters, that only has an MC_SetPosition FB you manually trigger and see if you are still getting the same results? When you manually control the motor directly from the servo drive software at the speeds you are calling for, does it move precisely to the target position?
Last updated: 2025-01-18
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Dear people, I would like to create a TCP server in my PLC program. The TCP server needs to communicate with an external device. I have been searching the internet and found that the libraries Syssocket or CAA NetBaseSrv are two possible solutions to create a TCP server. From what I have read, CAA NetBaseSrv is more user-friendly to implement than the Syssocket variant. However, I am still struggling to actually implement this library. Foremost is my little knowledge about creating a TCP server and how to read/understand each function block, especially the outputs of some blocks and the types, e.g. server has an output CAA.Handle, but I cannot find the explanation of CAA.Handle. I tried to find a good document that can help me understand how to implement a TCP server, but I could not find it. Thank you in advance, George
Last updated: 2025-02-20
Post by trusty-squire on AXIS Rollover
CODESYS Forge
talk
(Post)
If you mean you want to shift the Origin or Zero position of your axis, you can try MC_SetPosition and set the position to 0 (if you want to take the current active position and make it the new 0. Adjust this number accordingly if/as needed). This means the servo drive keeps it's current origin position, and Codesys applies an offset to the servo drive position in the logic. You can also use the homing function of your servo drive using MC_Home and have your drive configured to set the current position as origin when it receives a homing command.
Last updated: 2025-03-11
Post by agentcousto on [Bug report] Issue with Importing XML Files Containing "POINTER TO" Variables in Codesys Platform Plugins Versions 2.7 and 2.8
CODESYS Forge
talk
(Post)
Hello, I have developed a Python script that I run to import XML files into my project. For this, I use the Python function import_xml(). Everything was working fine when I was using Codesys platform plugins version 2.6.1.2320, but since I upgraded to versions 2.7 and even 2.8, some files are no longer imported correctly. After some research, I identified that all the files containing variables of the type "POINTER TO" are affected. I have attached a screenshot of the error I am encountering. Do you know about this bug? Do you plan to fix it?
Last updated: 2025-03-26
Post by jampid on Struct Literal
CODESYS Forge
talk
(Post)
Bonjour Davidmic, Il n'est pas possible d'associer une méthode à une fonction. Cela est possible sur les Blocs fonctions. En utilisant ta DUT MyStruct, je créé une fonction avec en entrée un tableau de structure :** FUNCTION F_F3 : REAL VAR_IN_OUT // bien définir un type IN_OUT IN_ptrINT: ARRAY[*] OF MyStruct; // la taille sera définie ultérieurement/ END_VAR VAR _di: DINT; // Index de parcours du tableau pour l'écriture dans les cases ENDVAR ============== //Programme F_F3: FOR _di := LOWER_BOUND(IN_ptrINT,1) TO UPPER_BOUND(IN_ptrINT,1) DO IN_ptrINT[_di].som:=IN_ptrINT[_di].a + IN_ptrINT[_di].b; END_FOR J'utilise ensuite cette fonction dans un POU Programme : PROGRAM Test_F_Fx VAR _aiTAB9:ARRAY[0..3] OF MyStruct := [(a := 1, b := 1.2), (a := 2, b := 2.2), (a := 3, b := 3.3), (a := 4, b := 4.4)]; END_VAR ** ==========** F_F3(IN_ptrINT:=_aiTAB9 ); Voilà l'idée pour avancer. Une autre idée, est d'utiliser les pointeurs ou les références. Bon développement!
Last updated: 2025-04-07
Post by andrej on Creating, using an external Function.
CODESYS Forge
talk
(Post)
Hello all, I would like to create a simple which runs directly on Control WinV3 x64 3.5.21.0 For this purpose I created a simple dll myAdder.dll in Cpp // MyAdder.cpp // cl /LD /EHsc MyAdder.cpp /Fe:MyAdder.dll #include <windows.h> extern "C" __declspec(dllexport) int __cdecl CmpMyAdder_Add(int a, int b) { return a + b; } I added the dll in the respective folder. Furthermore I "registred" the dll in the CODESYSControl.cfg. However, when I want to use the library I get the error message: Uresolved reference: *'CMPMYADDERADD' * Can you give me a hint what step I missed or where I need to declare the dll, such that the dll resp. the reference can be resolved. Many thanks and kind regards
Last updated: 2025-04-18
Post by manuknecht on Maximum dynamic limits of MC_MoveLinearAbsolute and MC_MoveLinearRelative
CODESYS Forge
talk
(Post)
Hello all I use an axis group with two linear axes in a kinematic system. Using MC_MoveLinearAbsolute and MC_MoveLinearRelative, I am trying to realise dynamic movements (set velocity: 1 m/s, set acceleration: 30 m/s^2) with the highest possible jerk, as I want to compare this with a movement with a trapezoidal velocity profile. However, my measurements show that the axes accelerate with a maximum jerk of approx. 800 m/s^3, even if the value in the function block was set to 10,000 m/s^3. I have already increased the dynamic limits of the two axes accordingly (Velocity: 5000 u/s, Acc-/Deceleration: 250'000 u/s^2, Jerk: 100'000'000 u/s^3, where 1 u = 1 mm), but this had no effect. I have checked the input parameters of the function blocks and the VelFactor, AccFactor and JerkFactor factors are all set to the maximum (value 1). Reducing the cycle time has resulted in a higher jerk, but as we are already working with a cycle time of 1 ms, there is nothing more that can be done here. The axes themselves are still a long way from drawing the maximum current, which is why I assume that this should not be a problem either. Are there other factors or parameters that influence the dynamic limits and therefore allow faster movements? The PLC I am using is a Raspberry Pi 4 and Codesys V3.5 SP20 with all libraries up to date. Thanks in advance Manuel
Last updated: 2024-05-08
Post by struccc on Inheritence of struct,
CODESYS Forge
talk
(Post)
Strangely reminds me to my struggles... Want to do something "Elegant", reusable, universal, practical... In CODESYS??? 🙃 First of all, before you get too deep into this: If you could find a way, to make a "universal" log entry object, containing the variable length data itself, you wouldn't be able to store them in an array, or access them like an array, or pass them by value as a type. (please correct me, if I'm wrong, incorrect, or not precise). Because... Basically you can't declare a type with variable memory footprint. This is a very deeply embedded characteristic of CODESYS, and all IEC 61131-3 systems, and it has many reasons behind. And yes, it is a very common trap / mistake, to forget about. So, with a log entry - I guess - it's pretty much the purpose: store data and metadata together, and then handle it in a uniform way. There are ways to handle this, really depends on what is the purpose. For example: 1. Entries with fixed length (Maybe it is not as evil as it looks for the first time. Depends on the situation, but definitely the fastest and easiest code) You can have your base object, with an internal, fixed length string or byte array variable. I would go with a string, and call it _Data.; And then you can make properties, like As_Bool, As_Int, As_Real... In the 'set' accessors, you can do like: pReal := ADR(_Data); // POINTER TO REAL As_Real := pReal^; In the 'get' accessors, evidently: pReal := ADR(_Data); // POINTER TO REAL pReal^ := AS_Real; Or, can use ANY type, if you are not obsessed with variable / property like access: 2. Fixed length, but nicer First, some disadvantage to any values: - You can only assign values with write access. No literals, constants, etc... - Can only be used as input variable of function or function_block - Therefore, stg you could reach: LogEntry.Initialize (stVariable|rVariable|iVariable|xVariable); Just a quick example (it's funny to play with ANY): Be careful it was not tested. I'm sure can be done better, please feel free to comment FUNCTION_BLOCK FB_LogEntry VAR_INPUT MsgClass : UDINT; // Like DEBUG, WARN, ERR... MsgCode : UDINT; // Like Errors.ERR_FAILED MsgTS : DT; // The timestamp END_VAR VAR _Data : STRING(80); // Our data container... _Descr : __SYSTEM.AnyType; // A standard descriptor for our data, containing TYPE_CLASS, address and size END_VAR METHOD SET_Value : BOOL VAR_INPUT anyValue : ANY; END_VAR VAR I : DINT; diSize : DINT; pStr : POINTER TO STRING; END_VAR // Check what did we receive in anyValue. diSize := anyValue.diSize; // We use constant __SYSTEM.TYPE_CLASS to identify the received data type CASE anyValue.TypeClass OF // Maybe we don't want to store references, pointers... and who knows what else... __SYSTEM.TYPE_CLASS.TYPE_REFERENCE, __SYSTEM.TYPE_CLASS.TYPE_POINTER : SET_Value := FALSE; // For the planned types we will be just fine. TYPE_CLASS.TYPE_BOOL, TYPE_CLASS.TYPE_INT, TYPE_CLASS.TYPE_REAL : SET_Value := TRUE; // Optionally string can be handled separately, maybe we have received STRING(255), but practically it is shorter than 80 bytes... TYPE_CLASS.TYPE_STRING : pStr := anyValue.pValue; diSize := MIN(anyValue.diSize, LEN(pStr^) + 1); // Get the actual size, and rewrite the received structure member diSize := MIN(SIZEOF(_Data), diSize); // Can chop down the received string to our length... SET_Value := TRUE; // Maybe want to play a little bit more here, to narrow down or convert datatypes, etc... // Or just reject any other datatype ELSE SET_Value := FALSE; RETURN; END_CASE // Fail, if the received value is still larger than our container... IF diSize > SIZEOF(_Data) THEN SET_Value := FALSE; END_IF // Here we should be ok, just set up the _DataType structure, and copy store the data IF SET_Value THEN THIS^._Descr.TypeClass := anyValue.TypeClass; // The typeclass is already filtered THIS^._Descr.diSize := diSize; // Set the (adjusted) size THIS^._Descr.pValue := ADR(_Data); // This will not change, just to be sure {IF defined (pou:SysMem.SysMemCpy)} SysMem.SysMemCpy(_DataType.pValue, anyValue.pValue, TO_UDINT(anyValue.diSize)); {ELSE} // An ugly replacement MemCpy FOR I:=0 TO diSize - 1 DO _Descr.pValue[I] := anyValue.pValue[i]; END_FOR {END_IF} // Otherwise, in case of failure maybe better set an empty value (overwrite the former data descriptor) ELSE THIS^._Descr.TypeClass := TYPE_CLASS.TYPE_NONE; THIS^._Descr.pValue := ADR(_Data); THIS^._Descr.diSize := 0; END_IF METHOD GET_Value : BOOL VAR_INPUT anyValue : ANY; END_VAR VAR I : DINT; END_VAR // We just have to serve the data, using the __System.AnyType structure received // Roughly we can say: IF anyValue.TypeClass = _Descr.TypeClass AND anyValue.pValue <> 0 // This should not be possible, already taken care of by Codesys (?) THEN {IF defined (pou:SysMem.SysMemCpy)} SysMem.SysMemCpy(anyValue.pValue, _DataType.pValue, TO_UDINT(MIN(anyValue.diSize, _Descr.diSize))); {ELSE} // An ugly replacement MemCpy FOR I:=0 TO MIN(anyValue.diSize -1, _Descr.diSize - 1) DO anyValue.pValue[I] := _Descr.pValue[I]; END_FOR {END_IF} // Just to make sure, that our string is terminated... IF anyValue.TypeClass = TYPE_CLASS.TYPE_STRING THEN anyValue.pValue[anyValue.diSize -1] := 0; END_IF GET_Value := TRUE; RETURN; END_IF // ... But can play more CASE anyValue.TypeClass OF TYPE_CLASS.TYPE_WSTRING : ; // Could do conversion TYPE_CLASS.TYPE_XSTRING : ; // Wow, I have to figure this out TYPE_CLASS.TYPE_PARAMS : ; // BTW, what is this, how to use? TYPE_CLASS.TYPE_ANYNUM : ; // ... END_CASE Be careful it was not tested. I'm sure can be done better, please feel free to comment 3. If you really want to do entries with variable size In a standard environment, it would be similar to the previous, except you dont have the container variable _Data, just use a pointer, practically _Descr.pValue At Initialize (SET_Value), you have to allocate the memory, would be easy with SysMem.SysMemAlloc - nowadays with SysMem.SysMemAllocData -, and you make sure to release it after use with SysMem.SysMemFreeData... SysMemAlloc was already hidden. The problem with this, that sooner or later your application will totally fragment the dynamic memory, and fail... So should look for some form of dynMaybe MemUtils.MemoryManager (I am not sure what is the status and the future of it). 4. You will end up by a LogEntry Factory ... 5. You could still have a look at this IEC Snippets BTW, Standard Codesys Logger is not a bad choice either. If you are really interested, I share some more code / library.
Last updated: 2025-03-09
Post by mondinmr on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
Good day, I’m writing this message out of frustration regarding the current way project files are saved as encrypted XML and single-file format in CODESYS. I find this approach to be quite tedious for several reasons: Limited Access to Structured Text: Not being able to access Structured Text (ST) externally makes it impossible to work with alternative editors like VSCode. Tools like VSCode are incredibly responsive and feature advanced systems such as GitHub Copilot, which would be a real game-changer when working with ST IEC. While CODESYS works well for small code snippets or debugging, when the codebase grows, switching to VSCode to boost productivity becomes essential, and copy-pasting between environments is a cumbersome workaround. Poor Integration with Git: This file format also makes it very difficult to integrate effectively with Git. I have tested the internal demo, but for advanced merges, it is unusable. Without properly formatted plain text, it’s impossible to leverage the vast ecosystem of external tools around Git that allow smooth merges in heterogeneous teams. File Corruption on Network Drives: I often work from multiple locations with shared network drives. When the development environment saves a file and something goes wrong midway (which can occasionally happen when using VPNs and network drives), the entire project becomes irrecoverable. There’s no way to cancel the save process, and the development environment freezes. This has happened to me at least four times over the past two weeks, and one of those incidents cost me an entire day of work. All of this is particularly disappointing because I truly believe that the libraries, runtime, and overall work done by CODESYS are exceptional. I find it fantastic that there is a platform allowing development of PLCs and control systems using OOP, which is a huge advantage in modern control engineering. I apologize for the rant, but this issue has been extremely frustrating. Best regards.
Last updated: 2024-10-15
Post by r-niedermayer on OPC UA subscriber not operational
CODESYS Forge
talk
(Post)
Hi. As far as projects in "old version"s are concerned, these can be upgraded to newer versions at any time. To do this, the device must be updated accordingly and the copilers and library versions must be adapted. You can find instructions on how to proceed in the online help/FAQ: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_changing_compiler_version.html https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_cmd_update_device.html See also 4.3.22.4 "How to open an Example Project" within the following pdf for more details on the single steps: https://forge.codesys.com/lib/counit/tickets/_discuss/thread/3e991befbc/ca97/attachment/Public%20FAQ-v13-20240610_075228.pdf Regaring your OPCUA connection state always showing just "DISABLED", without knowing both sides of the assembly in detail, one can only approach the problem theoretically. We can give a chekclist on how to proceed: Fist, please recheck the communication settings in the OPC UA connection function block to ensure that the server URL, endpoint URL, and other settings are correct and match the configuration of the OPC UA server. Verify that the OPC UA server is running and accessible. -You can try to connect to the OPC UA server using a separate client, such as UAExpert, to ensure that the issue is not related to the OPC UA server itself. Test the security settings in the OPC UA connection function block to ensure that the correct security policy and certificate are selected. If you are using a dynamic connection to the OPC UA server, probe that the connection settings are correctly configured and that the OPC UA client is able to establish a connection to the OPC UA server. Also, please loock into the log files for any errors related to the OPC UA connection function block, these should be listet there. The log files may also provide additional information about the issue and help you to further troubleshoot the problem. FYI - Please see https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_obj_data_source_communication_opc_ua_server.html: Her you can finde the Communication settings via OPC UA Server -> layout Browse Live Server: The client connects to the server and detects the existing variables and types. From Information Model The client reads the data structure (layout) of the OPC UA Server from the information model set here and as a result receives the information about available variables and types. A connection to the server is not required. The list contains the information models installed in the OPC UA Information Model Repository. "Read Connection" Settings from IEC Variable (option set): - The connection settings used by the device are not read here from the dialog, but at runtime from the IEC variable specified here. - For this possibility, please see the Using a Dynamic Connection to an OPC UA Server (https://content.helpme-codesys.com/en/CODESYS%20Communication/_comm_use_dynamic_opc_ua_server_comm_settings.html) The settings for the communication of a Client-data source to an OPC UA Server can also be dynamically configured from the IEC code and can also be changed at runtime. For such a purpose, a structure is available in the DatasourceOpcUAServer library (For a description of the OPC UA Server, there is one included in the standard installation of CODESYS, https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_encrypt_communication_data_sources_opc_ua_client.html)
Last updated: 2024-11-04
Post by mubeta on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
How are the servo drives controlled? EtherCAT, step/dir pulses, other? CANOpen, 1 Mb/s, bus load 35%, cycle time 2ms. Another thought is that - if it's step/dir pulse based control - the pulses from the PLC to the drive are getting missed/lost at high frequencies? If that's the case then there would be multiple troubleshooting steps/corrections that could be investigated. Here, it seems to me that we are getting completely off track with the observed problem. You could try to create a simplified program I had already written this elsewhere. The program before being brought into machines was exhaustively tested in SW emulation and the problem did not occur. However, in emulation I was interested in checking other aspects of the process, not this specific one which is for real a correction made necessary after the fact. The part of the program that does this correction with the function mentioned in the topic, came up from its origins, but I didn't know or didn't think it was really useful. A scruple that later turned out to be necessary. However, for now I do not think I will spend any more time on this verification, already lacking any to do my normal. I remain amazed, however, that a function intended to correct the axis position with the motor in motion and that it should not interfere with this, in fact instead changes behavior as the motor speed changes. Mah! When you manually control the motor directly from the servo drive software at the speeds you are calling for, does it move precisely to the target position? The drive and motor have been working fine for about 10 years. In replacing the machine control system, I opted for CoDeSys where before there was something else. But this is not the subject of the problem. What I need to resolve is the fact that a clutch specially placed at a certain point can slip and, therefore, I have the undeniable need to phase the 'prime mover' to the mechanical position of the machine, detected by a cam for each turn, in order to properly stop at its optimum point. Which for now I have ruled out doing. In fact, if I really have to say, since we have now gone brutally OT, I originally thought that this clutch should only come into action in cases of extreme necessity, as happens in most trials. But this one, the way it is made, slips more easily than I could estimate and the servo-controlled 'prime mover,' and the machine, get out of phase, maybe by a little, but frequently, and when the machine work at it's high speed, (in fact all of the time), I can't adjust properly the 'prime mover' position at fly.
Last updated: 2025-01-18
Post by ara32 on CODESYS 4 Linux:
CODESYS Forge
talk
(Post)
Hello! I managed to correctly launch CODESYS Developer Studio 3.5.17, almost all functionality works. The only issue remaining is that when connecting to a device and obtaining its public key, the NCryptEncrypt function is called, which is not fully implemented in the DLL source code, resulting in the connection not being established. Currently, the code of this function in the Wine repository looks like this: SECURITY_STATUS WINAPI NCryptEncrypt(NCRYPT_KEY_HANDLE key, BYTE *input, DWORD insize, void *padding, BYTE *output, DWORD outsize, DWORD *result, DWORD flags) { struct object *key_object = (struct object *)key; TRACE("(%#Ix, %p, %lu, %p, %p, %lu, %p, %#lx)\n", key, input, insize, padding, output, outsize, result, flags); if (flags & ~(NCRYPT_NO_PADDING_FLAG | NCRYPT_PAD_OAEP_FLAG | NCRYPT_PAD_PKCS1_FLAG | NCRYPT_SILENT_FLAG)) { FIXME("Flags %lx not supported\n", flags); return NTE_BAD_FLAGS; } if (flags & NCRYPT_NO_PADDING_FLAG || flags & NCRYPT_PAD_OAEP_FLAG) { FIXME("No padding and oaep padding not supported\n"); return NTE_NOT_SUPPORTED; } if (key_object->type != KEY) return NTE_INVALID_HANDLE; return map_ntstatus(BCryptEncrypt(key_object->key.bcrypt_key, input, insize, padding, NULL, 0, output, outsize, result, flags)); } The program crashes due to the NCRYPT_PAD_OAEP_FLAG flag. I'm not proficient in C++, but I attempted to add handling myself, and here's the result: SECURITY_STATUS WINAPI NCryptEncrypt(NCRYPT_KEY_HANDLE key, BYTE *input, DWORD insize, void *padding, BYTE *output, DWORD outsize, DWORD *result, DWORD flags) { struct object *key_object = (struct object *)key; TRACE("(%#Ix, %p, %lu, %p, %p, %lu, %p, %#lx)\n", key, input, insize, padding, output, outsize, result, flags); if (flags & ~(NCRYPT_NO_PADDING_FLAG | NCRYPT_PAD_OAEP_FLAG | NCRYPT_PAD_PKCS1_FLAG | NCRYPT_SILENT_FLAG)) { FIXME("Flags %lx not supported\n", flags); return NTE_BAD_FLAGS; } if (flags & NCRYPT_NO_PADDING_FLAG) { FIXME("No padding not supported\n"); return NTE_NOT_SUPPORTED; } BCRYPT_OAEP_PADDING_INFO oaepInfo = { 0 }; oaepInfo.pszAlgId = BCRYPT_SHA1_ALGORITHM; NTSTATUS status = BCryptEncrypt(key_object->key.bcrypt_key, input, insize, &oaepInfo, NULL, 0, output, outsize, result, flags); if (key_object->type != KEY) return NTE_INVALID_HANDLE; return map_ntstatus(BCryptEncrypt(key_object->key.bcrypt_key, input, insize, padding, NULL, 0, output, outsize, result, flags)); } Now, when calling the connection, it crashes with the error "bcrypt:BCryptEncrypt flags 0x4 not implemented." Can anyone help with enhancing this functionality or at least point me in the right direction?
Last updated: 2024-03-22
Post by george32 on CSV file and string manipulation.
CODESYS Forge
talk
(Post)
Dear folks, I think I have a rather simple question but I could not find the right answer to my question: I have made with Excel a CSV file where I would like to have some general data regarding my program variables. I have made an program what let me read the file. The string I am currently get is at follows: 'IP_Adres;192.168.45.12$R$NPort_number;2000$R$NCycle_time;43$R$NStart_Standard_IO;20$R$N' Now I want to split the string in multiple part, which I later would connect to the right variable. By Google and experimenting I have reached to the following code for the first part of the splitting proces: // Splitting the BOM of the string: Received_string := FileReadString; IF LEFT(STR:=New_string,3)= '' THEN Received_string_without_BOM :=RIGHT(STR:= Received_string,SIZE:= (LEN(STR:= Received_string))-3); END_IF //Splitting the remaining string in part for later declaration. WHILE index = 0 DO index_split_part := FIND(STR1:= Received_string_without_BOM,STR2:= '$R$N'); Part_of_String[index]:=LEFT(STR:=Received_string_without_BOM, SIZE:= index_split_part); index := index + 1; END_WHILE However in the splitting proces I could not understand what is really happening. I understand that the Find() function returns the first value the $R$N in the Received_string_without_BOM. This would mean that the index_split_part := 23 I|P| _ |A |d|r|e|s|;|1_|9 |2 |. |1 |6 |8 |. |4 |5 |. |1 |2 |$ |R |$ |N |P | 1|2| 3 |4 |5|6|7|0|9|10|11|12|13|14|15|16|17|18|19|20|21|22|23|24|25|26|27| So the next part is to read the first 23 characters of the Received_string_without_BOM with the LEFT() function. I expected that the outcome the following was: 'IP_Adres;192.168.45.12$'. However the outcome is: 'IP_Adres;192.168.45.12$R'. I do not understand where the R after the $ sign comes from, because its place is 24 so it would not be added to the part_of the_string[index]. If I hard coded value 24 for the size it gives me the following return: 'IP_Adres;192.168.45.12$R$N'. I would expect everything till the R but the code adds the $N also to the string. I hope someone could explain to my what I am seeing wrong in my point of view? With kind regards, George
Last updated: 2024-09-27
Post by mogam on Internal error:System.NullReferenceException: The object reference was not set to an object instance.
CODESYS Forge
talk
(Post)
Hi everyone, I have a my App that reads values from a shared memory than 2 variables x,y were calculated. here as you can see in my code: PROGRAM PLC_PRG VAR szName : STRING := '/SM'; ( Name of the shared memory.) uxiSize : __UXINT := 646 * 2 * SIZEOF(REAL); ( Size of the shared memory. ) hShm : RTS_IEC_HANDLE; ( Handle to the shared memory ) pStart : POINTER TO REAL; ( Pointer to the first element in the memory ) pData : POINTER TO REAL; ( Pointer, which is incremented until the last sign in the memory is reached. ) shared_data :ARRAY[0..645, 0..1] OF REAL; velocity : ARRAY[0..2] OF REAL; ( Velocity array ) position : ARRAY[0..2] OF REAL; ( Position array ) angleDepth : ARRAY[0..645, 0..1] OF REAL; ( Angle and depth array ) xEndOfMemory : BOOL; x : ARRAY[0..645] OF REAL := 1.0; y : ARRAY[0..645] OF REAL := 1.0; (* Result of actions at the memory. *) OpenResult : RTS_IEC_RESULT; ReadResult : RTS_IEC_RESULT; PointerResult : RTS_IEC_RESULT; DeleteResult : RTS_IEC_RESULT; CloseResult : RTS_IEC_RESULT; i : INT; END_VAR ( Open the shared memory ) hShm := SysSharedMemoryOpen2(szName, 0, ADR(uxiSize), ADR(OpenResult)); IF hShm <> RTS_INVALID_HANDLE THEN (* Read the entire shared memory table *) SysSharedMemoryRead(hShm:= hShm, ulOffset:= 0, pbyData:= ADR(shared_data), ulSize:= uxiSize, pResult:= ADR(ReadResult)); (* Fetch the pointer from the shared memory. The pointer is pointing to the first element address *) //pStart := SysSharedMemoryGetPointer(hShm, ADR(PointerResult)); (* Close the shared memory *) //CloseResult := SysSharedMemoryClose(hShm := hShm); (* Read velocity and position data from the shared memory *) FOR i := 0 TO 2 DO velocity[i] := shared_data[i, 0]; position[i] := shared_data[i, 1]; END_FOR; (* Read angle and depth data from the shared memory *) FOR i := 0 TO 645 DO angleDepth[i, 0] := shared_data[(i + 6), 0]; angleDepth[i, 1] := shared_data[(i + 6), 1]; END_FOR; FOR i := 0 TO 645 DO x[i] := angleDepth[i, 1]*COS(angleDepth[i, 0]); y[i] := angleDepth[i, 1]*SIN(angleDepth[i, 0]); END_FOR; END_IF For these values an XY-CHART needs to be done and when i create a visualisation and set the x data and y data when i try to compile, i recieve this error: ------ Übersetzungslauf gestartet: Applikation: Device.Read_App ------- Code typisieren ... [FEHLER] Internal error:System.NullReferenceException: Der Objektverweis wurde nicht auf eine Objektinstanz festgelegt. bei _3S.CoDeSys.LanguageModelManager.LDateType.Accept(ITypeVisitor typvis) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IArrayType ) bei ..(_IPointerType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IPointerType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IPointerType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei _3S.CoDeSys.Compiler35140.Compiler.(_ICompileContext , _IPreCompileContext , _ICompileContext , IProgressCallback ) bei _3S.CoDeSys.Compiler35140.Compiler.(_ICompileContext , Boolean , Boolean , _IPreCompileContext , _IPreCompileContext , _ICompileContext , Boolean , Boolean& , IProgressCallback ) bei _3S.CoDeSys.Compiler35140.Compiler.(Guid , Boolean , Boolean , Boolean , Boolean& , _ICompileContext& , _ICompileContext& , IProgressCallback , Boolean , Boolean ) Kompilierung abgeschlossen -- 1 Fehler, 0 Warnungen Übersetzung abgeschlossen -- 1 Fehler, 0 Warnungen : Kein Download möglich!
Last updated: 2024-05-24
Post by mogam on Internal error:System.NullReferenceException: The object reference was not set to an object instance.
CODESYS Forge
talk
(Post)
Hi everyone, I have a my App that reads values from a shared memory than 2 variables x,y were calculated. here as you can see in my code: PROGRAM PLC_PRG VAR szName : STRING := '/SM'; ( Name of the shared memory.) uxiSize : __UXINT := 646 * 2 * SIZEOF(REAL); ( Size of the shared memory. ) hShm : RTS_IEC_HANDLE; ( Handle to the shared memory ) pStart : POINTER TO REAL; ( Pointer to the first element in the memory ) pData : POINTER TO REAL; ( Pointer, which is incremented until the last sign in the memory is reached. ) shared_data :ARRAY[0..645, 0..1] OF REAL; velocity : ARRAY[0..2] OF REAL; ( Velocity array ) position : ARRAY[0..2] OF REAL; ( Position array ) angleDepth : ARRAY[0..645, 0..1] OF REAL; ( Angle and depth array ) xEndOfMemory : BOOL; x : ARRAY[0..645] OF REAL := 1.0; y : ARRAY[0..645] OF REAL := 1.0; (* Result of actions at the memory. *) OpenResult : RTS_IEC_RESULT; ReadResult : RTS_IEC_RESULT; PointerResult : RTS_IEC_RESULT; DeleteResult : RTS_IEC_RESULT; CloseResult : RTS_IEC_RESULT; i : INT; END_VAR ( Open the shared memory ) hShm := SysSharedMemoryOpen2(szName, 0, ADR(uxiSize), ADR(OpenResult)); IF hShm <> RTS_INVALID_HANDLE THEN (* Read the entire shared memory table *) SysSharedMemoryRead(hShm:= hShm, ulOffset:= 0, pbyData:= ADR(shared_data), ulSize:= uxiSize, pResult:= ADR(ReadResult)); (* Fetch the pointer from the shared memory. The pointer is pointing to the first element address *) //pStart := SysSharedMemoryGetPointer(hShm, ADR(PointerResult)); (* Close the shared memory *) //CloseResult := SysSharedMemoryClose(hShm := hShm); (* Read velocity and position data from the shared memory *) FOR i := 0 TO 2 DO velocity[i] := shared_data[i, 0]; position[i] := shared_data[i, 1]; END_FOR; (* Read angle and depth data from the shared memory *) FOR i := 0 TO 645 DO angleDepth[i, 0] := shared_data[(i + 6), 0]; angleDepth[i, 1] := shared_data[(i + 6), 1]; END_FOR; FOR i := 0 TO 645 DO x[i] := angleDepth[i, 1]*COS(angleDepth[i, 0]); y[i] := angleDepth[i, 1]*SIN(angleDepth[i, 0]); END_FOR; END_IF For these values an XY-CHART needs to be done and when i create a visualisation and set the x data and y data when i try to compile, i recieve this error: ------ Übersetzungslauf gestartet: Applikation: Device.Read_App ------- Code typisieren ... [FEHLER] Internal error:System.NullReferenceException: Der Objektverweis wurde nicht auf eine Objektinstanz festgelegt. bei _3S.CoDeSys.LanguageModelManager.LDateType.Accept(ITypeVisitor typvis) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IArrayType ) bei ..(_IPointerType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IPointerType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IPointerType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei ..(_ISignature , _IPreCompileContext ) bei ..( ) bei ..(String ) bei ..(String , IVariable[]& , ISignature[]& ) bei ..(String , IVariable[]& , ISignature[]& , IScope& ) bei ..visit(_IVariableExpression , AccessFlag ) bei ..(_IUserdefType ) bei ..(_IVariable , IScope5 , _ICompileContext , _ISignature ) bei ..(_ISignature , IScope5 , _ICompileContext ) bei _3S.CoDeSys.Compiler35140.Compiler.(_ICompileContext , _IPreCompileContext , _ICompileContext , IProgressCallback ) bei _3S.CoDeSys.Compiler35140.Compiler.(_ICompileContext , Boolean , Boolean , _IPreCompileContext , _IPreCompileContext , _ICompileContext , Boolean , Boolean& , IProgressCallback ) bei _3S.CoDeSys.Compiler35140.Compiler.(Guid , Boolean , Boolean , Boolean , Boolean& , _ICompileContext& , _ICompileContext& , IProgressCallback , Boolean , Boolean ) Kompilierung abgeschlossen -- 1 Fehler, 0 Warnungen Übersetzung abgeschlossen -- 1 Fehler, 0 Warnungen : Kein Download möglich!
Last updated: 2024-05-24
Post by rcaponi on Codesys Control RTE V3. Remote Control
CODESYS Forge
talk
(Post)
Hello, I would like to have, if possible, some clarification on this function. That is, I would like to understand if it is useful for managing, fom my development PC, the RTE runtime executed on a remote control. This is what the help says: Remote PLC: Opens the Remote Configuration dialog. By enabling or disabling the Control remote PC, not local option, you determine whether a PLC is used that is on a remote or local PC. Accordingly, the menu commands Start PLC, Stop PLC, and PLC Configuration refer to the local PC or a PC reached on the network. For the remote PC, specify the Target PC address, Port number, and a Timeout value (in ms) for the connection (Remote Timeout [ms]). But does this mean that I also need to install the RTE runtime on my development PC? Is it possible to have some more information? Best regards Roberto Caponi
Last updated: 2023-09-22
Post by timvh on VisuElems.CurrentUserGroupId is not stable
CODESYS Forge
talk
(Post)
I'm not sure what you are trying to do, but getting the CurrentUserGroupID like this will not work, because there could be multiple Visualization Clients and each can have a different user that is logged in. Also when you go online with CODESYS and open an Visualization, this is counted as a client. Probably this is the reason you see it changing. What you can to is "iterate" over all clients and then see which user is logged in on which visualization Client. For this you need to add the Visu Utils library to the project and call the FbIterateClients. See https://content.helpme-codesys.com/en/libs/Visu%20Utils/4.4.0.0/VisuUtils/VisuActionUtilities/Function-Blocks/FbIterateClients.html fbClientIteration( xExecute := x_Execute, itfClientFilter := VU.Globals.AllClients, itfIterationCallback := fbIterator, xDone => x_Done, xBusy => x_Busy, xError => x_Error, eError => e_Error); The fbIterator, in the example above, should be an instance of an FB which you have created yourself and this must implement VU.IVisualizationClientIteration. For example: FUNCTION_BLOCK FB_ITERATOR IMPLEMENTS VU.IVisualizationClientIteration Then automatically the corresponding methods will be called. In the HandleClient Method, you will get an interface to the client(s) and then you can get the current user through this interface: itfClient.UserGroupId You can also get the UserName: itfClient.UserName
Last updated: 2023-11-14
Post by user3000 on Can't find an Extended Pulse Timer (TP and LTP)
CODESYS Forge
talk
(Post)
Hello, For my program I need an extended pulse timer, which can be referred to as a retriggerable pulse timer. Where every rising edge of the input resets the elapsed time zero, extending the lenght of the output pulse. The Codesys pulse timer (TP) is a one-shot timer and only resets the elapsed time with the falling edge of the input. There is also a pulse timer (LTP) in codesys, but in my simulation it was also functioning as a one-shot even though the description sounds like LTP should be retriggerable. I have uploaded some timing plots from another PLC program for reference. I am looking for a timer equivalent to the "TEP" diagram. Is there an Extended Pulse Timer in Codesys? Maybe there is a way to manipulate the input so it resets the elapsed time outside the function block?
Last updated: 2023-12-06
Post by ragarcia on Error while using UpdateConfiguredIPSettings to change IP address
CODESYS Forge
talk
(Post)
Hello everyone, I am trying to change dynamically by code the IP address of a Weidmuller controller. So I am basically using IoDrvEthernet library to use UpdateConfiguredIPSettings function but I am getting constantly the 'INVALID_STATE' error. Even though I am following a procedure it should work: * First I added on the config file of codesys the following: [SysSocket] Adapter.0.Name="eth0" Adapter.0.EnableSetIpAndMask=1 Adapter.1.Name="eth1" Adapter.1.EnableSetIpAndMask=1 * Secondly I am first disabling the ethernet interface by using Ethernet_0.Enable = FALSE and then executing DED.Reconfigure. After that, I run the Ethernet_1.updateConfiguredIPSettings Code: Ethernet_1.Enable:= EnableDisable; Reconfigure(xExecute:= TRUE, itfNode:= Ethernet_1, xError=> ErrorReconfigure, eError=> ErrorCodeReconfigure); IF Reconfigure.xDone THEN ErrorCodeIP:= Ethernet_1.UpdateConfiguredIPSettings(IPAddress:= newIP, SubnetMask:= newMask, Gateway:= newGW); END_IF IF Reconfigure.xDone OR Reconfigure.xError THEN Reconfigure(xExecute:= FALSE); END_IF Ethernet_1.Enable:= TRUE; Reconfigure(xExecute:= TRUE, itfNode:= Ethernet_1); IF Reconfigure.xDone OR Reconfigure.xError THEN Reconfigure(xExecute:= FALSE); END_IF Can someone help me? Thank you. All I am trying is to find a way to change dynamically with code, the IP addresses of my controller (2 ethernet ports).
Last updated: 2023-12-11
Post by vipul on Multicast udp
CODESYS Forge
talk
(Post)
Hi, Good afternoon can anybody help me with UDP Multicast code. I am not able to send or recieve data when code is dumped on linux device. Below is my code. Declaration: PROGRAM udp_multicast VAR oneTimeFlag :UINT :=0; state: INT:=0; driver: UDP.UDPDriver; //port : UDP.Port;//moved to GVL src_ipAddr_ud: UDINT; src_ipAddr_st:STRING := '192.168.127.155';//'192.168.1.155';//ipms ip address dst_ipAddr_ud:UDINT; group_ipAddr_st:STRING := '239.1.5.10'; //group_ipAddr_ud:UDINT; result: SysTypes.RTS_IEC_RESULT; //result of recieve function. bind: UDINT; //result of binding. resultCreate:SysTypes.RTS_IEC_RESULT;//result of port creation. timer:BLINK; temFlag :INT:= 0; post:INT :=0; checksumFunc:checksumXor; localStringBuf:STRING[500]; chksum:BYTE; dataBuffer:POINTER TO BYTE; checksumString:ARRAY[0..5] OF BYTE; recvSize:__XINT; errorCode:UDINT; joinGroupErrorCode:UDINT; END_VAR ************8 Implementation: IF oneTimeFlag <> 1 THEN oneTimeFlag:=1; resultCreate := driver.CreatePort(ADR(GVL.port)); src_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIPAddress:= src_ipAddr_st); GVL.group_ipAddr_ud := UDP.IPSTRING_TO_UDINT(sIpAddress:= group_ipAddr_st); GVL.port.IPAddress := src_ipAddr_ud; GVl.port.ReceivePort:= GVL.src_port;//port on which messages are expected. GVl.port.SendPort := GVL.dest_port; GVl.port.OperatingSystem := 0; //0- any system GVL.port.Socket :=3; //3- socket type is multicast bind := GVL.port.Bind(udiIPAddress:=src_ipAddr_ud,); GVl.port.JoinGroup(udiGroupAddress:= GVL.group_ipAddr_ud,udiInterfaceAddress:= src_ipAddr_ud,eLogCode=>joinGroupErrorCode); END_IF timer(ENABLE:=TRUE,TIMELOW:=T#100MS,TIMEHIGH:=T#100MS); IF timer.OUT = TRUE THEN GVL.port.Send(udiIPTo:=GVL.group_ipAddr_ud,GVL.dest_port,pbyData:=ADR(GVL.writeData),diDataSize:=SIZEOF(GVL.writeData)); ELSE SysMemSet(ADR(GVL.readData[0]),0,SIZEOF(GVL.readData)); result := GVl.port.Receive(ADR(GVL.readData),diDataSize:=SIZEOF(GVL.readData),udiIPFrom=>dst_ipAddr_ud,diRecvSize=>recvSize,eLogCode=>errorCode); SysMemMove(ADR(GVL.readDataBuf[0]),ADR(GVL.readData[0]),SIZEOF(GVL.readData)); END_IF post:=LEN(GVL.readDataBuf);
Last updated: 2024-01-14
Post by axilleas on SMC_Interpolator + SMC_controAxislbyPos
CODESYS Forge
talk
(Post)
dear all I am working on a very generic gantry system (virtual drives + win v3 control) reading gcode from external file. In order to stop the interpolator function from running when gaps are detected, SMC_controlAxisByPos FB has the bStopIpo output which according to the manual is connected to the Interpolator's bEmergencyStop. Lets assume that the axis are parked in position X1000 Y1000 and the initial G code movement is G00 X500 Y500. The normal behavior is to travel from the actual x1000 y1000 to G00 X500 Y500. The SMC_Interpolator always gets the X0 Y0 as the initial position, meaning that the bStopIpo is active until the axis are in X0 Y0 and the release the interpolator to set the new positions to X500 Y500. Is there a suggested method to solve this behavior? bonus question: I get a lot of bStopIpo during standard interpolation movements (not gaps). While working with virtual axis this is not a problem but when real axis are installed this will be an issue. What exactly triggers the bStopIpo output? Slow axis accelerations compare to Gcode defaults? Kind Regards
Last updated: 2024-02-05
Post by brell on Automatic xExecute NBS.TCP_write
CODESYS Forge
talk
(Post)
I've recently started experimenting with CODESYS for a project and am fairly new to it. I'm currently working with Function Block Diagrams (FBD) to set up TCP communication between a server and a client, where the client is implemented as a Python script. Once the communication is established, my connection status changes to True, which is the expected behavior. My challenge arises with the TCP write module, which requires the xEnable_write flag to toggle between True and False. If xEnable_write remains True, the module only performs a single write operation. To address this, I introduced a falling edge trigger (F_TRIG), expecting it to help in toggling xEnable_write and it does, However, I've encountered an issue where in the beginning after connxion established I need to manually set xEnable_write to True for the system to work as intended. I'm looking for a way to automate this process so that xEnable_write becomes True automatically upon establishing a connection . Initially, I tried setting xEnable_write to True from the start, but this approach didn't work well since it left the flag permanently True, preventing further toggling. I also experimented with using a TON timer, but I faced similar issues. I am seeking a solution that automatically toggles xEnable_write between True and False after a connection is established, ensuring continuous write operations without manual intervention. Any advice or guidance on how to achieve this would be greatly appreciated."