Post by gseidel on Discontinuity of A/B/C axis movement. CODESYS Forge talk (Post)
Hi jonasz, you already solved it, I'm answering here for the sake of others with a similar question. You can provide the slope of the A/B/C axis with the U/V/W word. See example 3 here: https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_cnc_din66025_additional_axis.html If you don't want to change the G-Code, the function block SMC_RecomputeABCSlopes can compute the slopes automatically. https://content.helpme-codesys.com/en/libs/SM3_CNC/Current/SM_CNC_POUs/SoftMotion-CNC/SoftMotion-Function-Blocks/SMC_RecomputeABCSlopes.html Best regards, Georg
Last updated: 2024-04-30

Post by gseidel on CNC - system goes to X=0 Y=0 before CNC file execution starts, how to avoid that? CODESYS Forge talk (Post)
Hi peterned, the start position given in the CNC properties is only used if you use the compile mode OutQueue. With compile mode SMC_CNC_REF, you need to provide the start position in the IEC application. The function block SMC_NCInterpreter has an input piStartPosition. You can initialize it with the output of the forward kinematic transormation FB for your machine. In your case probably SMC_TRAFOF_Gantry2. Best regards, Georg
Last updated: 2024-04-30

Post by corriibme on Setting array values with JSON Utilities SL CODESYS Forge talk (Post)
It turns out that you can build JSON structures without ever calling the JSONBuilder function block directly. Instead, create a pointer to JSON.JSONData and invoke the necessary methods on its dereference. The parent object has a parent index of -1 (and an index of 0). EVERY other item (including keys, values, empty arrays and sub-objects) created by the setX methods needs the index to increase by 1. Then use the JSONByteArrayWriter FB to generate your JSON string
Last updated: 2024-05-23

Post by swe-hob on call of a method of a function block in another program CODESYS Forge talk (Post)
Hi, Let's assume following: PRG_1 fb_1 : fbExample1; fb_1.method_1 do something... PRG_2 fb_2 : fbExample2; fb_2.method_2 if xTest then PRG_1.fb_1.method_1(); end_if; Is there a reason why runtime hangs when I call the method_1 in PRG_1 from a method in PRG_2? Both programs run in the same task. No chance that any other program calls the method. What I practically do there is that in the program PRG_2 I add a structed object into a buffer. In PRG_1 I just process the items in the buffer.
Last updated: 2024-06-03

Post by swe-hob on call of a method of a function block in another program CODESYS Forge talk (Post)
Hi, Let's assume following: PRG_1 fb_1 : fbExample1; fb_1.method_1 do something... PRG_2 fb_2 : fbExample2; fb_2.method_2 if xTest then PRG_1.fb_1.method_1(); end_if; Is there a reason why runtime hangs when I call the method_1 in PRG_1 from a method in PRG_2? Both programs run in the same task. No chance that any other program calls the method. What I practically do there is that in the program PRG_2 I add a structed object into a buffer. In PRG_1 I just process the items in the buffer.
Last updated: 2024-06-03

Post by jgalaska on SMC_Trafo 6DOF Config Error CODESYS Forge talk (Post)
Hello, Recently I was trying to run 6DOF robot in codesys via SMC_Trafo_ArticulatedRobot_6DOF, unfortunately no matter what parameters I tried, it always outputs InvalidConfig Error. I saw the same issue in a topic: https://forge.codesys.com/forge/talk/Motion/thread/16e1f0327f/ But if I understand correctly, the user solved it by developing his own version of this block. I wanted to know if it is a bug in the library (SM3_CNC 4.20.0.0) or am I doing something wrong? Can anyone confirm that they can use the FB without it reporing the Error? Kind regards,
Last updated: 2026-01-21

Post by paulg on RasPi CAA Serial example - unexpected behavior during debug CODESYS Forge talk (Post)
I've trimmed down the CAA Serial Codesys example to only listen on one port but, when stepping through the Case structure in debug mode, it jumps out of the structure during a specific point in every scan (I'll point it out below after describing the setup and listing the code). I'm using a Pi 4 Model B, and I have an Arduino Nano Every plugged in via USB which is streaming the following serial message at 1 Hz: Time since opening connection: 1 s Time since opening connection: 2 s ...and so on. The Pi shows the Nano at /dev/ttyACM0 so I edited CODESYSControl_User.cfg to read: Linux.Devicefile=/dev/ttyACM The code in my PLC_PRG is (ignore some of the comments, I hadn't deleted them out from the original example): PROGRAM PLC_PRG VAR xStartTest : BOOL:= TRUE; iState : INT; xTestDone : BOOL;(* True, when the test was done succesfully *) (* Settings to communicate with the COM Port *) aCom1Params : ARRAY [1..7] OF COM.PARAMETER; como1 : COM.Open; comc1 : COM.Close; comw1 : COM.Write; comr1 : COM.Read; //sWrite : STRING := 'Test String!'; sRead : STRING(25); szRead : CAA.SIZE; xCom1OpenError : BOOL; xCom1CloseError : BOOL; xCom1WriteError : BOOL; xCom1ReadError : BOOL; END_VAR //This example shows the communication of two COM Ports with each other. //The first one writes a string of characters, which is read by the second one. //After successful execution, the two COM Ports are closed and the test is done. IF xStartTest THEN CASE iState OF 0: //The parameters are set for the COM Port aCom1Params[1].udiParameterId := COM.CAA_Parameter_Constants.udiPort; aCom1Params[1].udiValue := 1; // the correct Port should be adapted aCom1Params[2].udiParameterId := COM.CAA_Parameter_Constants.udiBaudrate; aCom1Params[2].udiValue := 115200; aCom1Params[3].udiParameterId := COM.CAA_Parameter_Constants.udiParity; aCom1Params[3].udiValue := INT_TO_UDINT(COM.PARITY.NONE); aCom1Params[4].udiParameterId := COM.CAA_Parameter_Constants.udiStopBits; aCom1Params[4].udiValue := INT_TO_UDINT(COM.STOPBIT.ONESTOPBIT); aCom1Params[5].udiParameterId := COM.CAA_Parameter_Constants.udiTimeout; aCom1Params[5].udiValue := 0; aCom1Params[6].udiParameterId := COM.CAA_Parameter_Constants.udiByteSize; aCom1Params[6].udiValue := 8; aCom1Params[7].udiParameterId := COM.CAA_Parameter_Constants.udiBinary; aCom1Params[7].udiValue := 0; //The first Port is opened with the given parameters como1(xExecute := TRUE, usiListLength:=SIZEOF(aCom1Params)/SIZEOF(COM.PARAMETER),pParameterList:= ADR(aCom1Params)); IF como1.xError THEN xCom1OpenError := TRUE; iState := 1000; END_IF //After a successful opening, the next state is reached IF como1.xDone THEN iState := 15; END_IF 15: // the reading process is started comr1(xExecute := TRUE,hCom:= como1.hCom, pBuffer:= ADR(sRead), szBuffer:= SIZEOF(sRead)); IF comr1.xError THEN xCom1ReadError := TRUE; END_IF //After completion the size of the written bytes are saved IF comr1.xDone OR comr1.xError THEN szRead := comr1.szSize; iState := 20; END_IF 20: // If everything was successful the ports are closed and the handles are released comc1(xExecute := TRUE,hCom:= como1.hCom); IF comc1.xError THEN xCom1CloseError := TRUE; END_IF IF comc1.xDone OR comc1.xError THEN iState := 25; END_IF 25: // The first port is closed and the used handle released xTestDone := TRUE; xStartTest := FALSE; iState := 0; como1(xExecute := FALSE); comw1(xExecute := FALSE); comc1(xExecute := FALSE); ELSE iState := 0; END_CASE END_IF I realize as I write this that the .udiPort should be 0 and not 1, but that shouldn't be causing the issue I'm seeing. I'm forcing xStartTest:=TRUE every scan so that I can step into each line and observe what's happening. What I see is that the port parameters are set and the port is opened with no errors, but the code jumps out of the case structure to the last line every time it reaches (and I step into) the iState:=15 line (at the end of the iState:=0 block). So every scan cycle it goes through the block for iState=0 and jumps out at the same spot. I'm a little new to PLC programming so I may be misunderstanding the flow, but shouldn't this case structure keep moving down in the same scan? If it only handles one case per scan, why doesn't the value of iState persist? Thanks! Update: I restarted the Codesys control today and I was then able to see an error for como1.eError of "WRONG_PARAMETER". I tried doing some digging and another post made me think I should add another line to CODESYSControl_User.cfg, so I now have: [SysCom] Linux.Devicefile=/dev/ttyACM portnum := COM.SysCom.SYS_COMPORT1 So now when I set .udiPort to 1, I get "NO_ERROR" but I also don't read anything from the port (i.e. szRead = 0 always). If I try setting the port to 0 (which I'm confused about, because I added a COMPORT1 line but the device shows on the Pi as ACM0), I get the "WRONG_PARAMETER" error again. Is there an easier way to troubleshoot the Pi and view what ports the Codesys runtime is actually able to see while the Pi is running?
Last updated: 2024-06-06

Post by riccardo on VisuElems.CurrentUserGroupId is not stable CODESYS Forge talk (Post)
Goodmorning TimvH, Thanks for the reply. I don't know if your solution solve my trouble yet, I am going to see the link you sent me. In the mean time I try to explane better what I need to do. I have a turbine system that get in alarm under some condition (E.g low speed of turbine) and block the itself. When the system is stoped there is no speed turbine and the system cannot start. To give to the operetor the possibility to bypass the alarms, there is an acknoledgement alarm pushbutton. This bypass must not work for everyone but only for those client that perform the login by (User Management). Furthermore, if the user perform the (manual or automatic) logout in alarm conditions, the acknowlegment must be annulled and block the system again. To do this, I need to know if an operator is logged in the page and is working to fix the problem; otherwise the syste must autoturn off again. Now I go to study your solution, if I have explaned better and you have another idea tell me please.
Last updated: 2023-11-16

Post by mikek10 on HTTP Client TCP Init Error CODESYS Forge talk (Post)
Hi, I tried posting in the discussion for the HTTP Client example but perhaps that is not monitored? I have been using http client successfully for approximately 12 months, however in recent weeks I have begun to get TCP_INIT_ERROR when attempting to communicate. The only resolution seems to be power cycling and then the connection begins to work again for a time. I am not aware of any changes to code or libraries between working ok and now. Cold reset does not resolve, only power cycle. It seems the error from NBS.TCP_Client is 6002 which I think is invalid_addr However the address is the same when working and not working?
Last updated: 2024-07-04

Post by rcanfield on Code Coverage and Test Manager CODESYS Forge talk (Post)
I am exploring the possibility of measuring test coverage using the Test Manager and Profiler tools. It appears there are some significant limitations. Has anyone been successful trying to use these tools? Here are my observed limitations. Am I misunderstanding anything? * Profiler only works for one "run cycle". Even warm resets will clear the coverage calculations. Thus, all tests would have to manually reset values when complete to prevent contamination to other tests. * It is not possible to see which statements were/weren't executed. One would have to use the flow control tool which cannot be used in conjunction with the Profiler, and must be viewed in realtime. * The profiler control cannot be automated and therefore must be executed through a manual procedure. Thank you!
Last updated: 2024-07-11

Post by rcanfield on Code Coverage and Test Manager CODESYS Forge talk (Post)
I am exploring the possibility of measuring test coverage using the Test Manager and Profiler tools. It appears there are some significant limitations. Has anyone been successful trying to use these tools? Here are my observed limitations. Am I misunderstanding anything? * Profiler only works for one "run cycle". Even warm resets will clear the coverage calculations. Thus, all tests would have to manually reset values when complete to prevent contamination to other tests. * It is not possible to see which statements were/weren't executed. One would have to use the flow control tool which cannot be used in conjunction with the Profiler, and must be viewed in realtime. * The profiler control cannot be automated and therefore must be executed through a manual procedure. Thank you!
Last updated: 2024-07-11

Post by hyys12 on How to use/create SOTU in LD program CODESYS Forge talk (Post)
I am trying to make a LD program for an existing installation with a motor. Here an inductive sensor is used to give an input, as a check to verify the conveyor is actually running. Here the plan was to use a TOF timer which gets constantly reset when the sensor input gets detected. The problem is, that if the conveyor is stuck, and the sensor sends a continous signal, the timer will never do what it is supposed to do. Therefor I need some help on how I can convert the input to a pulse, with the help of something like a SOTU. I just cannot find this in codesys anywhere.
Last updated: 2024-07-11

Post by milan-svarny on ModbusFB.ClientSerial Problem with Reply Timeout CODESYS Forge talk (Post)
Hi All, I have problem with ModbusFB.ClientSerial. I'm using 4 different port for Modbus communication. After some time of running program ClientSerial stops to receive data to reply buffer and all request finish with Reply Timeout. The Device sent reply correctly,that it is visible on oscilloscope and it is possible to see that data( reply )are in the device. If the usbtty device is read over external app. then it is possible to see all data which were not taken by ModbusFB.ClientSerial. The stack does not overflow or something , program runs correctly forward and no exceptions or something. The main problem it is that when the error occur than it is not possible to reset port or something or maybe i'm doing it wrong way. please help me with this issue. Thank you for any help in advice Milan
Last updated: 2025-05-23

Post by rafa on MODBUS TCP SERVER DONT AUTO-STARTUP CODESYS Forge talk (Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically?
Last updated: 2025-07-15

Post by rafa on MODBUS TCP SERVER DON'T AUTOMATIC STARTUP CODESYS Forge talk (Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically? Um using Codesys Version 3.5.20.30 Patch 3+ My CPU is a Weintek Cmtx Built-int - ( CMT3092x )
Last updated: 2025-07-15

Post by mondinmr on COL.IMap2 and HashTableFactory cause frequent Access Violation CODESYS Forge talk (Post)
Good morning, I’ve been using the Collection library for a long time, mostly with Stack, LinkedList, and List. From your examples I was able to manage the different factories, even for custom elements. Now I need a hashtable, but with this object I’m running into a lot of random access violations. If I append something inside FB_Init after constructing the hashtable, it crashes, even though the list was already created. If I only create the hashtable in FB_Init and append afterwards, it usually works. I don’t understand the meaning of the dispose call in this code: pSlave := ADR(slave); uSlave := TO_ULINT(pSlave); iKey := fKey.Create(uSlave); IF hash.CountKeys() = 0 THEN Service.logger.appendLog('Filling hashtable', 'HashManager', AdvLogType.AdvDebugMsg); ok := FALSE; ELSE eError := hash.ContainsKey(iKey, xResult => ok); END_IF IF NOT ok THEN pI := __NEW(UINT); iVal := fKey.Create(TO_ULINT(pI)); Service.logger.appendLog(CONCAT('New slave', TO_STRING(uSlave)), 'HashManager', AdvLogType.AdvDebugMsg); hash.AddKeyValuePair(iKey, iVal); appendNewSlave := pI; ELSE eError := hash.GetElementByKey(iKey, itfValue => iElem); xResult := __QUERYINTERFACE(iKey, itfIInstance); IF xResult THEN itfIInstance.Dispose(); END_IF IF eError <> COL.COLLECTION_ERROR.NO_ERROR THEN Service.logger.appendLog(CONCAT('ERROR ', TO_STRING(eError)), 'HashManager', AdvLogType.AdvCriticalMsg); appendNewSlave := nullptr; RETURN; END_IF __QUERYINTERFACE(iElem, iVal); {warning disable C0033} pI := TO___UXINT(iVal.UlintValue); {warning restore C0033} appendNewSlave := pI; END_IF Without the dispose call, every second cold reset crashes immediately when I try to access iVal, even if eError doesn’t report any error. With the dispose call, the cold reset issue disappears, but I get other problems: a) If I start the runtime using systemctl start codesyscontrol, it crashes at IF hash.CountKeys() = 0 THEN b) If I delete the files in PlcLogic and download again, it works and survives multiple cold resets. But as soon as I run systemctl restart codesyscontrol, everything gets corrupted again and it starts crashing at that point. FUNCTION_BLOCK SlaveMapCounter VAR hash : COL.IMap2; eError : COL.COLLECTION_ERROR; END_VAR In its FB_Init I create it: METHOD FB_Init: BOOL VAR_INPUT bInitRetains: BOOL; // TRUE: retain variables are initialized (reset warm / reset cold) bInCopyCode: BOOL; // TRUE: the instance will be copied to the copy code afterward (online change) END_VAR VAR hF : COL.HashTableFactory; END_VAR hash := hF.Create(256); In another FB I instantiate it statically: FUNCTION_BLOCK ABSTRACT AbstractServoEthercatController EXTENDS AbstractServoController VAR_STAT hashSlaves : SlaveMapCounter; END_VAR VAR field : REFERENCE TO ADVAbstractFieldUnitEthercatCia402; initCnt : REFERENCE TO UINT; END_VAR The append method is the one shown above, and I call it after the runtime has started. The accesses are performed by a single task, and in any case I’m working on an isolated single core. I’ve tried everything, moving the create, the instances, and all the rest several times, but nothing seems to work. I’d like to point out that these FBs are part of our own library, which is used in many applications.
Last updated: 2025-09-11

Post by sawicpx on CANbus Remapping PDOs During Runtime CODESYS Forge talk (Post)
Hello, I am working on an application where I need to remap PDOs to a different CANopen object during runtime depending on what value is at a specific register. I have gotten to the point where I put the device into Preoperational State using the CIA405.NMT function. I then reconfigure the PDO 180x and 1a0x obejcts usings SDOs to point to a new canopen object on the device however when I go to restart the Device from PREOP to OP using the CIA405.NMT function the device is reset back to the original configuration as per the initial setup. I am wondering is there any way to change the PDOs at runtime is there some more functionaility I can access to do this. Any direction is appreciated!
Last updated: 2023-12-22

Post by timvh on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28

Post by timvh on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28

Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications CODESYS Forge talk (Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14

Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications CODESYS Forge talk (Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14

Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications CODESYS Forge talk (Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14

Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications CODESYS Forge talk (Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14

Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications CODESYS Forge talk (Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14

Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications CODESYS Forge talk (Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14