Post by timvh on Licensing info not available.
CODESYS Forge
talk
(Post)
In the VPLC configuration settings there is an entry for the IP address of the license server. In this setting fill in the IP address of your device (host IP address). Then when the virtual PLC starts up, it will get the license from the license container on the host. You can do this for all VPLC's running on your device. The VPLC will always take the smallest license which fits the required license. So if you have 2 licenses for VPLC's with small and large applications, then this will work fine if you start up one VPLC which requires the small license and the other which requires the large license. PS, personally I find it much easier, especially for testing and experimenting, to activate the licenses on a CODESYS (USB) key. This is easy to activate (on your development PC) and easier to move to another device. Addtionally you don't loose the license when you need to install a completely new image on the device.
Last updated: 2025-10-02
Post by edepalos on Text list from sd card
CODESYS Forge
talk
(Post)
Hi guys, I have a textlist in my project which is working just as expected in a drop down list. I would like to move this text list to a sd card and access it from there, because I want to ease the editing of the contents of this textlist. I'm imagining a solution like the operator shuts down the plant, takes the sd card out, edits the textlist on the card with a windows machines notepad, then reinserts the card in the PLC and restarts the plant, having the new content of the textlist populating the dropdown list. I'm sorry that I'm asking you to spoonfeed me, but I did not find anything straightforward to do this... I saw in the Project>Project settings>Visualisation a relative path thingy, but I have the plant in operation and I would not like to make 100 trial and errors right now... I'm also not interested in SysLib file read commands and stuff, I would just like to access the file from the cards part, I don't want to replace its contents dynamically or such... nor I have language files or recipes... Thank You in advance! Br, Ede
Last updated: 2024-01-16
Post by manuknecht on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hello all I am using an AxisGroup with the Gantry2 Kinematics to move a 2D-Gantry system. When creating the AxisGroup, the SoftMotion_PlanningTask is created automatically with a cycle time of 2 ms in my case. I realized that the maximum cycle time of this task can spike to very high values (up to 60 ms) at lower speeds of the motion, leading to synchronization issues and errors on the axes. The same behaviour - though not as drastic - can be observed with virtual axes too. Is this behaviour intended or to be expected? Can the cycle time or type of the SoftMotion_PlanningTask be changed to prevent these errors? Or is there another fix for this issue? I tried changing the cycle type to Freewheeling, which solved the synchronization issues, but caused an error on the AxisGroup after a while, reading SMC_CP_QUEUE_UNDERRUN. Thanks in advance and best regards Manuel
Last updated: 2024-03-07
Post by timvh on Toradex and CODESYS and licensing
CODESYS Forge
talk
(Post)
For the Virtual Control you need to use a "Network license". The Virtual Control has parameters of which one is the reference to the license server. This can be the device itself, but you need to activate the license on the host system (not in the container). For this, CODESYS has a Network License server with WBM (web based management). See for the Network License configuration: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_license_controller_linux.html If it is only for evaluation, I would advise to use a CODESYS (USB) key and activate the license on the key. Then you still have to install the CODESYS Network License server on the host, but you don't have to activate the license as soft license on the device. The benefit is that you can easily move your license to another device when needed. Off course your device must have a free USB port available to be able to do this.
Last updated: 2025-10-20
Post by programmierer on UDB Block in Codesys V2.3 implementieren um Werte an bestimmte IP-Adresse zu senden
CODESYS Forge
talk
(Post)
Hallo zusammen, ich möchte mich hiermit an euch wenden, in der Hoffnung, dass ihr mir bei meinem Problem behilflich sein könnt. Ich bin neu in der Programmierung und arbeite aktuell mit einem Wago Controller in unserem Labor, der eine Wärmepumpe steuert. Mein Ziel ist es, vier spezifische Werte an eine bestimmte IP-Adresse zu senden. Dazu habe ich versucht, in das vorhandene CODESYS-Programm der Wärmepumpe zusätzliche UDP-Blöcke einzufügen, um die Datenübertragung zu ermöglichen. Leider hat das Senden der Daten bis jetzt nicht funktioniert. Ich habe auch Bilder der Blockkonfiguration beigefügt, um einen besseren Einblick in den Aufbau zu geben. Über jegliche Hilfestellung würde ich mich sehr freuen. Vielen Dank im Voraus!
Last updated: 2024-07-19
Post by andrebrandt on FB string and naming
CODESYS Forge
talk
(Post)
Hi Tim. Not quite correct. What i'd like, is when you place the FB in prog, i choose a block NTC10k, and name this RT401. What i'm trying to do, is to get the name RT401 automaticly into the FB, so i can put this into the string i pass in a struct. So in var in POU, i saw this a place i could do this, RT401: NTC10k(Tag:='RT401'), but i can't get this to work. I shurly must have had something like this in FB: FUNCTION_BLOCK NTC10k String TAG But it's here where I'm stuck...
Last updated: 2024-09-30
Post by ben1 on Help understanding analog in-/outputs
CODESYS Forge
talk
(Post)
Hi there mate Most PLC's have a very similar concept with AI/AO - have you used any other software before? I have not used a Wago before myself, but I assume the concept would very much be: 1. Add the analog in & out cards to your hardware config. 2. Setup the raw input scaling on the hardware (eg. 4 - 20mA = 4000 - 20000) 3. Use a built in or homemade scaling block to scale your input as needed (eg. 4000 - 20000 = -100 - 2000kPa. 4. Write code as required 5. Scale output as needed (eg. 0 - 100% = 0-10000 = 0 - 10V) Is this the information you require?
Last updated: 2024-12-15
Post by peterkcontrols on Copying 2 byte word to output
CODESYS Forge
talk
(Post)
Hello. I am using codesys 3.5. I would like to know if it is possible to set a variable to an output without declaring in. I have defined a STRUCT and within this struct I have a Struct for inputs called I and a struct for outputs called O. I have declared a variable of the type of this Struct, I would like to set or alias the value in this variable to an input/output value of an IO block that has a module on the ethernet tree. Is it possible to copy the contents of %IW0 -> STRUCT.I ? The size of both of these is 2 bytes. I understand that I can declare a variable with the input like Input01 AT %IX0.0 : BOOL; However how can I make STRUCT.I.D00 AT %IX0.0? Is this possible? Thanks
Last updated: 2025-03-03
Post by amy123 on codesys mqtt publish serialization
CODESYS Forge
talk
(Post)
Hello, I am using the CODESYS IIoT Libraries SL MQTT Publish. Does this publish block only support publishing STRINGS as a readable format? I can publish ENUM, STRUCT, BOOL; however, MQTT Explorer will only display strings. When I use Wireshark, I can see that it is publishing something, but it looks to be publishing a serialized version which is a bunch of 0s or random text. If so, is there any way to deserialize this information back into a readable format? See pictures, where I have a BOOL TRUE that gets published as 001. Then see where I publish a STRUCT and it's an incomprehensible combination of 0s - only the string variable is displayed. Or, is it expected that you convert everything to a string before publishing? Any help is greatly appreciated! :)
Last updated: 2024-02-16
Post by esave on OPC UA Server with on Codesys + OPC UA Client on Labview
CODESYS Forge
talk
(Post)
Hello everyone I want a communication between my PLC as an OPC UA Server and Labview on my PC as the OPC UA Client. I have an Festo CPX-E-CEC-C1-PN PLC and I have the OPC UA Toolkit from Labview. I created some Variables for testing (see picture 1) on Codesys. I tried to use this Labview block diagram (see picture 2) but I cant connect the PLC to it. What do I have to type in the Server Endpoint URL and what in the Node ID? Is this a good way for communication with a PLC to a PC? If not is there another way?
Last updated: 2024-04-12
Post by tayhim on WAGO HMI Device not found
CODESYS Forge
talk
(Post)
Hello, I'm trying to connect with a Wago TP600 HMI but without success. I'm using codysis 3.5 SP19 patch 7 (SP20 block all the time) and the official wago package is installed. However, when I scan and select my device, I get a message saying that the device doesn't match the project's device object with the possibility to update the device (as shown in the attached picture). however, after choosing to update i got a message that the device is not found. I've tried with a new empty project but the same results. do you have any ideas? Thanks.
Last updated: 2024-06-25
Post by rossanoparis on After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working
CODESYS Forge
talk
(Post)
Hello at all. After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working. I'm not able to read or write files from the PLC application. Before this upgrade all worked fine. I've read this thread [ https://forge.codesys.com/forge/talk/Engineering/thread/3da9ded84e/ ] Despite I followed that indications I couldn't get my code working again. Perhaps I'm missing something or I didn't understand how to use placeholders at all. Is there a different syntax to use for "SysFileOpen" in order to use placeholders? Thanks in advance for your help. Information Compiler: CODESYS V3.5 SP19 Patch 2 Runtime: codesyscontrol 4.9.0 HW: KUNBUS RevPi Connect S Below the paths I want to access (The entire CODESYSControl_User.cfg file is attached) [SysFile] PlaceholderFilePath.1=/home/pi/hpca/bin, $hpcabin$ PlaceholderFilePath.2=/home/pi/hpca/cfg, $hpcacfg$ PlaceholderFilePath.3=/home/pi/hpca/logs, $hpcalogs$ PlaceholderFilePath.4=/home/pi/hpca/resources, $hpcares$
Last updated: 2023-08-22
Post by sturmghost on Visualization using methods and cyclic ST-calls
CODESYS Forge
talk
(Post)
Im looking for a way to implement ST-code into the visualization element without creating a helper POU or method in my device/application tree. Like visualization properties are evaluated at each VISU_TASK cycle I want to be able to create own ST code which interacts with the visualization interface variables. To be more specific I want to have a property which executes user defined ST-code at each VISU_TASK cycle exactly like its already possible for Input Configuration on various mouse and dialog events. Also a property for initialization (so only executed once) and a timed property would be nice. With the situation right now I'll have to create a POU function which handles the ST-code and misuse a property, like the text variable, to execute this POU function at each VISU_TASK cycle. Or does it exist and I don't know it?
Last updated: 2023-10-02
Post by julianramirez on ModbusFB write update
CODESYS Forge
talk
(Post)
Hello everyone, I am testing the ModbusFB library tcp server and so far I am able to create holding registers successfully, however, I am trying to identify after each write which registers got updated (i.e. function code, write value). I can even see the var udiNumWriteRequests, which increases with every write. I noticed that there is logging with the LogStatusInfo method. After I call it I am able to read in the console stuff that I want. Nevertheless, this is only available at the logs and is not easy to decode because it consists on several messages, I would like to know if there is a way for me to retrieve this information from the function itself with pointers or if there is any way to copy the logs messages (assuming that I can filter them with the LoggingOptions to only show what I need) inside the runtime code and not in the console. Thanks for your help :)
Last updated: 2024-09-16
Post by trusty-squire on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
Here, it seems to me that we are getting completely off track with the observed problem. If questions clarifying the details of the installation are problematic, it's best to include those details in the original question then... I had already written this elsewhere. The program before being brought into machines was exhaustively tested in SW emulation and the problem did not occur. Testing the full program in emulation is entirely different from creating a simplified program to isolate the function causing problems in the real world. I would recommend trying it to isolate the issue. The drive and motor have been working fine for about 10 years. In replacing the machine control system, I opted for CoDeSys where before there was something else. But this is not the subject of the problem A simple "yes" is the correct answer to my question here... Anyways, you seem to be a very knowledgeable expert, good luck on your problem!
Last updated: 2025-01-18
Post by atcprojectteam on Modbus Function Code 15, writing multiple coils
CODESYS Forge
talk
(Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26
Post by atcprojectteam on Modbus Function Code 15, writing multiple coils
CODESYS Forge
talk
(Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26
Post by ph0010421 on How to create a stopwatch?
CODESYS Forge
talk
(Post)
Do you need an 'hours-run' counter? And 1 second resolution is ok? I think you're over-thinking it. (The task time needs to be < 1second) Have a look at the LAD... Then, the time in seconds can be made into hh:mm:ss with this FUNction Declarations: FUNCTION funSecondsToStringTime: string VAR_INPUT InSeconds: UDINT; END_VAR VAR AsString: STRING; Minutes: UDINT; Hours: UDINT; Seconds: UDINT; MinutesAsString: STRING(2); HoursAsString: STRING(2); SecondsAsString: STRING(2); END_VAR and the code: Hours := InSeconds / 60 / 60; //Derive hours Minutes := (InSeconds - (Hours * 60 * 60)) / 60; //Derive minutes Seconds := InSeconds - ((Hours * 60 * 60) + (Minutes * 60));//Derive seconds HoursAsString := UDINT_TO_STRING(Hours); MinutesAsString := UDINT_TO_STRING(Minutes); SecondsAsString := UDINT_TO_STRING(Seconds); IF LEN(HoursAsString) = 1 THEN HoursAsString := CONCAT('0',HoursAsString); END_IF; IF LEN(MinutesAsString) = 1 THEN MinutesAsString := CONCAT('0',MinutesAsString); END_IF; IF LEN(SecondsAsString) = 1 THEN SecondsAsString := CONCAT('0',SecondsAsString); END_IF; AsString := CONCAT(HoursAsString, ':'); //assemble string AsString := CONCAT(AsString,MinutesAsString); AsString := CONCAT(AsString,':'); AsString := CONCAT(AsString, SecondsAsString); funSecondsToStringTime := AsString;
Last updated: 2023-12-08
Post by wbj0t on mobus tcp slave device. read/write holdings with 2 variables.
CODESYS Forge
talk
(Post)
Hi there. I have an issue to read and set time for the controller. In the issue many registers described as writable by 6/16 functions, and, in this time, also(!) readable! For example: I have time registers: min, hour, day, mon, year. By specifications it is possible check time (so I need always update these varibles in loop) and set time by writing these same registers, BUT how to set, if they will immediatle updated by current time after writing? So, I need to separate one address at two variables. I have seen option mark: Overlay of the process image by the holding and input register. I understand this so: When I READ by function 3, I will get variable that connected with the same INPUT address and when I WRITE by 6/16 this will change second variable that connected with HOLDING address. BUT, this mark doesnt work, when I write 6/16 and try to get by function 3, I will get written value instead INPUT variable. So, what to do?
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via CmpApp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by sanacfu on looking for v2.3 libraries on v3.5.19
CODESYS Forge
talk
(Post)
Hi all, I'm new to Codesys and Wago but well versed in Rockwell. I've been tasked with upgrading old Wago 750-880 PLCs that run Codesys v2.3. All I was giving is the original PLC program in v2.3 and the currently running machine. I've spec out to what I believe is a suitable upgrade, the PFC100 2ndGen, 750-8111. As I'm rewriting this code on the Codesys I can't find the same library functions blocks for ethernet settings PLC functions. Currently I'm working on code to get/set the PLC ethernet IP address and HMI IP addresses from the HMI screen. One other function I'm looking for is a warm reset function to the PLC. When googling for this stuff I see a lot of code not in ladder logic. Are these functions now not available to implement in ladder logic? Where can I get more information on finding and implementing this functions? Do I have to buy a license from Codesys to use these functions? The PLC I ordered should be arriving in 2-3 weeks.
Last updated: 2024-03-25
Post by duvanmoreno24 on Modbus writing on value change
CODESYS Forge
talk
(Post)
Yes, I tried to do what you put in the first code. However, I have a problem with that and that is that the inputs must be declared with the type. I have many data types running in my code (real, int, uint, bool) and I can't put them in the same function, another thing is that I need to instantiate that function for everything I want to write to the slave. You put a for to 200 but it means that it has to be the same data type and inside the array, but I want to get them individually. I'm struggling to do it in a good and efficient way like wago's E-cockpit does. in the first screenshot you can see, you simply type in value, change the package of things you want to write in value change and it does everything by itself automatically, without comparing any old and new values and even less having the need to activate a bool. , it is perfect.
Last updated: 2024-04-03
Post by aris on Modbus write via FB failure
CODESYS Forge
talk
(Post)
Hi all, I am using CoDeSys V3.5 and a soft controller Win V3x64. I am trying to read a modbus slave via Function Blocks and not via the channels of the hardware tree for the Slave. I created some requests of type ModbusRequest and I notice that I can read Input Registers and Coils but I can not write Holding Registers and Coils. I am using the library IoDrvModbusTCP 4.1.0.0. When i just use a single modbus request with FC06 (or FC16), there is no request sent to the slave and although the xExecute takes its true value from a pulse of 2 seconds duration, I take almost every 3 minutes an error "TCP_COMMUNICATION_ERROR - 16#A5 - TCP Port. error. Request was not sent". My code is ok because if i change the function code for reading registers, everything works fine. Did anyone have this issue in the past? Thank you in advance.
Last updated: 2025-11-06
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.