Post by banialuk on Modbus TCP Server
CODESYS Forge
talk
(Post)
Hello, I have poroblem with define input in function block modbusFB.serverTCP 'dataModel', in my aplication I need starting Input Registers from 3000, and I must define this in 'data Model' but I dont now how exacly to do it. Anybody now somethin about this?
Last updated: 2024-10-19
Post by eschwellinger on Persistence Manager: Config File not found?
CODESYS Forge
talk
(Post)
..strange just switching of this device without graceful Linux OS shutdown? Reset orgin on the device tree and a new download of the application will bring it up and running again but sure then the persistent data are for sure lost.
Last updated: 2024-11-02
Post by andrej on Threads and TID created by CODESYSControl Win V3
CODESYS Forge
talk
(Post)
Hi all, for a deeper understanding of the Codesys RTE - I created a simple application with 3 IEC tasks (Ta,Tb,Tc) each with different priorities, and different cycle times. The application runs on Windows 10 in the Soft PLC CODESYS Control Win V3. If my understanding is correct, the RTE i.e. the Process CodesysControlService should spawn 3 threads (Th_a,Th_b,Th_c) which are executed with the defined cycle times, the priority of the threads should reflect the priority of the task set in the Codesys IDE. Does somebody have an idea, how I could identify the respective threads in Windows? Kind regards Andrej
Last updated: 2023-10-02
Post by matthew on Persistence Manager Backup
CODESYS Forge
talk
(Post)
Hi, Is there a process to restore Persistence Manager files? I have backups of persistence variables used in a machine that is currently operating and tuned and all set points adjusted. There are about 500 persistence variables, they are building another identical machine. I would like to use Persistence Manager files from the first machine in the second also. I have tried copying the files and replacing them on the new RPI but then the Persistence Manager gets errors and then they are all reset to 0 etc I have tried adjusting the times to match. Instead of replacing whole file, I tried just changing the contents inside the file, but still does not work. I may be missing something here, but surely there must be a way to load a backup. Thanks!
Last updated: 2023-10-18
Post by fabian on Sys Process Execute Command
CODESYS Forge
talk
(Post)
Hello, I have a question: Once the command is being executed, is there a way to kill it again? As the called application is running in the background, the user can't close it but it shall be closed/terminated, commanded by codesys. I have tried with "SysProcessTerminate" but I guess this is not correct as the RTE crashes when this function is called. Starting the application: IF GVL.xStrtQR THEN GVL.xStrtQR := FALSE; SysProcess.SysProcessExecuteCommand2(pszCommand:=sCmd, pszStdOut:=stdout, udiStdOutLen:= SIZEOF(stdout),pResult := ADR(GVL.pResQRTsk)); END_IF Trying to stop it again: IF GVL.xTrmQR THEN GVL.xTrmQR := FALSE; pResTerm := SysProcess.SysProcessTerminate(hProcess:=SysProcess.SysProcessGetCurrentHandle(pResult:=ADR(GVL.pResQRTsk))); END_IF Codesyscontrol Win x64, 3.5.19.10. Many thanks for any advice pointing to the correct direction.. :-) Regards, Fabian
Last updated: 2023-11-17
Post by joanm on Programmatically change the IP addresses of the Modbus TCP slave devices
CODESYS Forge
talk
(Post)
Hello all, I am working in a project in which there are multiple Modbus TCP slaves. I need to be able to change the IP addresses of those devices from the HMI and I was planning to use the process depicted here: https://faq.codesys.com/display/CDSFAQ/Modbus+TCP+Slave%3A+Dynamic+Setting+of+the+IP+Address I can see the port number is what is used to specify which slave device we want to modify the IP address of. This said, can I freely set arbitrary port numbers to each device? I mean, can I set the first device to be at port 502, the second one at port 503... Any drawback or restriction? Is there any other way to reference to the device without having to change the port numbers? Thank you all in advance.
Last updated: 2024-01-04
Post by imuser on Is it possible to use debug functions such as Step Execution while the PLC ladder is in Running?
CODESYS Forge
talk
(Post)
Hello, I am a student learning CODSIS. Lately, I've been curious about something. During the actual PLC run, that is, Assume that the I/O is connected to a physical device and the analog value is updated in real time. Is it possible to use a feature like Codesys’ Debug-Step Over-Step IN? If possible..... How do I process the values of analog values (pressure sensor, temperature, current, etc.) that are being updated in real time? To step over, the ladder must stop at the breakpoint. If that happens, the PLC will actually stop, right??
Last updated: 2024-01-16
Post by nilesh on Request for Assistance with Online Logic Changes in PLC System using Codesys
CODESYS Forge
talk
(Post)
Dear Sir, We are writing to seek guidance regarding our current situation with the Opto 22 Groov EPIC PR1 PLC system. Over the past year, we have successfully downloaded and implemented logic using Codesys, and the PLC has been operational without issues. However, we now require minor modifications to the logic. Despite attempting to upload the modified logic, we are unable to see the "online change" option, prompting us to consider a direct logic download. Our concern is that during this process, certain digital outputs or analog outputs might momentarily disrupt operations, which is unacceptable given the system's continuous 24x7 operation. We have explored online changes in other PLC systems, but due to the absence of the last downloaded backup, we are unable to proceed confidently.
Last updated: 2024-03-01
Post by sachem on Problem retain values Weidmuller UC20-WL2000
CODESYS Forge
talk
(Post)
Good afternoon. I am working with a weidmuller uc20-wl2000 controller, using a codesys license. We made a ladder code to control a process, and it works well, but we want some variables to remain stored even when the controller is turned off. We tried to use retain variables, but at the time of loading the program, when we went offline from the controller, the program was deleted, it did not remain in the controller, and in the same way if we turned off the controller. In addition to this, when we tried to program it again, the program would not stay loaded and began to present errors with the opc-ua communication. What could be causing this problem? How can we maintain the values of the variables without damaging the program or affecting the controller? thank you
Last updated: 2024-04-10
Post by ppix on Establishing TLS Connection with MQTT Broker using MQTT Client SL Package
CODESYS Forge
talk
(Post)
For anyone confused with the process visit this link (the bottom section about creating a .pfx file) https://content.helpme-codesys.com/en/LibDevSummary/certificate.html#import-of-client-certificates-with-private-key. I solved this problem by creating a .pfx file and importing it into the security store under 'Own Certificates'(must have SP18 or newer to import .pfx). I used a gitbash shell to enter the openssl command that created the .pfx file. Once you import the file, in your TLS context, set your 'sUseCaseName' to be the same as the name listed in the 'Information' column of your imported certificate. This did it for me
Last updated: 2024-06-20
Post by shrikantp007 on help to get codesys understand
CODESYS Forge
talk
(Post)
Hello , I need some help on how to start with , 1) how to get test license to test codesys , 2) how to take a configuration backup or running process back and post file on fourm so people can understand and deploy same file and get idea what is missing or configure wrong 3) where i can get pdf for codesys admin or programmer 4) what is hardware recommand ,i am running on windows guest on kvm server .is it ok ? 5) i am trying to get ardunio porject working ,using ardunio board as a modbus slave but its not working some how https://forge.codesys.com/forge/talk/Engineering/thread/bf832569b8/ Thanks in advance . shrikant pune -india
Last updated: 2024-07-22
Post by jnoyau on Visualisaion while in simulation
CODESYS Forge
talk
(Post)
Hi all, Im new to Codesys 3.5, and am in the process fo making a visualisation i'd eventually export towards a Wago device. The issue I'm having currently is that when I compile and connect to the simulated program, my simulation won't launch. On the Visualisation tab, all I get is a text message (where previously there was my prepared visualisation) that says "The visualisation awaits a connection. Start the application" One thing to note: I work with Codesys 3.5 in french, so this is a rough translation. And a second: I'm not getting any errors nor warnings about the visualisation tab itself upon compiling Is there a step i'm missing after launching my simulation? Or would it be some really specific issue caused by the way I've set up my program? Thanks, J
Last updated: 2024-07-31
Post by vassilis91 on EtherCat-Rexroth Drive lost connection or no?
CODESYS Forge
talk
(Post)
Hi all, i am encounter a mystery problem with a build with rexroth drives at my work. At my company we are make a machine with two Rexroth Indradrives . The two drives are goes by ethercat protocol . To be more specific i am going from my plc to the Beckoff El1100 coupler and after to the first drive and from the first drive to the second. The second drive works with no problem but the first(motor) sometimes without any pattern start to make a mysterious noise like stop and suddenly goes on again. If i couldn't hear the noise from the motor i couldn't Imagine that this happen. After a lot of research i see that sometime i have some strange zeros from the drive to the plc? Really i am in a deadlock and I don't know how to continue. From the other side the values on the other drive(second)are stable . The problem maybe: https://youtube.com/shorts/g7PCFLUaDUI?si=eiq0F2IzhQZax2e2
Last updated: 2023-10-25
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Problem mit control runtime V3 und profinet
CODESYS Forge
talk
(Post)
Ich habe einen brandneuen Beckhoff-Panel-PC mit einer Codesys Control Runtime V3 eingerichtet. Ich habe es zusammen mit 2 Profinet-Feldgeräten konfiguriert: einem 16in/16out IO-Modul von Turck und einem MTS-Linearencoder. Die Maschine funktioniert einwandfrei, bis plötzlich die Kommunikation abbricht und die Profinet-Teilnehmer nicht mehr erreichbar sind. Zu diesem Zeitpunkt kann ich das Gerät noch anpingen, aber der Profinet-Master findet sie nicht mehr: Wenn ich einen Scan durchführe, werden sie nicht gefunden. Wenn ich einen Kaltstart durchführe, wird der Profinet-Master wieder aktiv und die Geräte werden wieder gefunden. Im Protokoll erhalte ich den Ethercat-Paketempfangsfehler: sysethernet. Ich bin etwas verwirrt, es gibt kein Ethercat-Gerät im Gerätebaum. Ich habe den Sendetakt und das Untersetzungsverhältnis bereits auf höhere Werte eingestellt, jedoch ohne Ergebnis. Kann Codesys so konfiguriert werden, dass die Kommunikation ohne Kalt-Reset wiederhergestellt wird? Das ist sehr ärgerlich und verursacht viele Produktionsausfälle. Grüße Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by mondinmr on First IO address of a CAADiagDeviceDefault.
CODESYS Forge
talk
(Post)
I have a device CAADiagDeviceDefault: IoConfig_Globals.Axis_A In our library, we perform introspection of the Etc_SlaveDiag. In that case, we have connectors, and by searching for them by address, I can find them in the IO mapping using the offset and size provided by EtherCAT. However, a Lenze i700 drive, instead of placing the IO mapping in the Etc_SlaveDiag device, places it in a sub-device CAADiagDeviceDefault. So, when I perform introspection, I cannot find the IO correspondences. Yet, in the CAADiagDeviceDefault, I do not find the connectors and cannot do the matching. Is there a way with a pointer or reference to a CAADiagDeviceDefault to obtain the address of the first input and the address of the first output? This is because we have our own motion library with many EtherCAT devices that automatically configure the mappings, but I can't manage to do so with the Lenze i700.
Last updated: 2024-08-22
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
This explanation aligns with the issues we’re experiencing with our machines. The scenario I described is happening with one of them (let’s call it Machine A). This machine is identical to another one (Machine B), except for some custom code that facilitates communication with an external Beckhoff PLC for MES integration in the production line. Machine B has been powered on and off daily for at least three months and has never had this problem. Given that, I highly doubt the MES custom code is the cause of the code corruption. This being said, your explanation does seem plausible. However, if faulty EtherCAT cables were the issue, why wouldn't the error occur during normal operation? Why would bad cables only cause problems during a hard shutdown? One last question: When you encountered this behavior, did you see a similar error in your logs? i.e, an "AccessViolation" exception in the EtherCAT Task?
Last updated: 2024-10-03
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
I have found a very interesting solution using: IoConfigTaskMap IoConfigConnectorMap IoConfigChannelMap The first is the list of IO tasks. The second is the connector for each IO module in the IOMap. The third is the individual input or output on the IOMap. One of the properties of the connector is another pointer to a connector, which corresponds with the connector of the EtherCAT slave. Through this information, it is possible to understand to which EtherCAT slave an IO connectormap corresponds. I am attaching an FB that allows for the construction of an IO map and finding the pointer to the actual IOs in the IOMap based on the bitoffset. FUNCTION_BLOCK IOExplorer VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR inputChannels: COL.LinkedList; outputChannels: COL.LinkedList; ulintFactory: COL.UlintElementFactory; END_VAR METHOD inputAtBitOffsetOfConnector : POINTER TO BYTE VAR_INPUT conn: POINTER TO IoConfigConnectorMap; bitOffset: UDINT; END_VAR VAR it: COL.LinkedListIterator; itf: COL.IElement; elem: COL.iUlintElement; channelInfo: POINTER TO ADVChannelInfo; bitOffsetR: UDINT; END_VAR inputChannels.ElementIterator(it); WHILE it.HasNext() DO it.Next(itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} channelInfo := TO___UXINT(elem.UlintValue); {warning restire C0033} IF channelInfo^.connectorField = conn THEN IF bitOffsetR = bitOffset THEN inputAtBitOffsetOfConnector := channelInfo^.addr; RETURN; END_IF bitOffsetR := bitOffsetR + channelInfo^.size; ELSE bitOffsetR := 0; END_IF END_WHILE inputAtBitOffsetOfConnector := 0; END_METHOD METHOD outputAtBitOffsetOfConnector : POINTER TO BYTE VAR_INPUT conn: POINTER TO IoConfigConnectorMap; bitOffset: UDINT; END_VAR VAR it: COL.LinkedListIterator; itf: COL.IElement; elem: COL.iUlintElement; channelInfo: POINTER TO ADVChannelInfo; bitOffsetR: UDINT; END_VAR outputChannels.ElementIterator(it); WHILE it.HasNext() DO it.Next(itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} channelInfo := TO___UXINT(elem.UlintValue); {warning restire C0033} IF channelInfo^.connectorField = conn THEN IF bitOffsetR = bitOffset THEN outputAtBitOffsetOfConnector := channelInfo^.addr; RETURN; END_IF bitOffsetR := bitOffsetR + channelInfo^.size; ELSE bitOffsetR := 0; END_IF END_WHILE outputAtBitOffsetOfConnector := 0; END_METHOD METHOD scanIO VAR_INPUT END_VAR VAR numTasks: DINT := IoConfig_Globals.nIoConfigTaskMapCount; tType: WORD; ioTask: POINTER TO IoConfigTaskMap; numCon: WORD; connector: POINTER TO IoConfigConnectorMap; numCh: DWORD; channelInfo: POINTER TO ADVChannelInfo; iTsk: DINT; iCon: WORD; iCh: DWORD; i: DINT; _tmpConnList: COL.IList; elem: COL.IUlintElement; itf: COL.IElement; tmpCh: POINTER TO ADVChannelInfo; lastE: DINT; e: COL.COLLECTION_ERROR; e1: Error; END_VAR VAR_INST lF: COL.ListFactory; END_VAR IF outputChannels.CountElements() > 0 OR inputChannels.CountElements() > 0 THEN RETURN; END_IF _tmpConnList := lF.CreateDynamicList(16, 16); //Iterate through all IO tasks FOR iTsk := 0 TO numTasks - 1 DO ioTask := ADR(IoConfig_Globals.pIoConfigTaskMap[iTsk]); //Store the type of the task (Input or Output) tType := ioTask^.wType; numCon := ioTask^.wNumOfConnectorMap; //Iterate through all connectors of the task FOR iCon := 0 TO numCon - 1 DO connector := ADR(ioTask^.pConnectorMapList[iCon]); numCh := connector^.dwNumOfChannels; //Iterate through all channels of the connector FOR iCh := 0 TO numCh - 1 DO //Create a new channel info object and fill it with the address, connector and size of the channel //Connectors is address of field connector in this case like EtherCAT slave //Address is the address of the IOMap //Size is the size of channel data in bits in IOMap channelInfo := __NEW(ADVChannelInfo); channelInfo^.addr := connector^.pChannelMapList[iCh].pbyIecAddress; channelInfo^.connectorField := connector^.pConnector; channelInfo^.size := connector^.pChannelMapList[iCh].wSize; //We put the channel info a temporary ordered list //Order is based on the address of IOMap lastE := TO_DINT(_tmpConnList.CountElements()) - 1; FOR i := 0 TO lastE DO _tmpConnList.GetElementAt(udiPosition := TO_UDINT(i), itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} tmpCh := TO___UXINT(elem.UlintValue); {warning restire C0033} //If the address of the channel is smaller than the address of the channel in the list IF tmpCh^.addr > channelInfo^.addr THEN //Insert the channel in the list at the current position _tmpConnList.InsertElementAt(TO_UDINT(i), ulintFactory.Create(TO_ULINT(channelInfo))); //Clear the channel info pointer channelInfo := 0; //Exit the loop i := lastE + 1; END_IF END_FOR //If the channel info is not 0, it means that the channel was not inserted in the list IF channelInfo <> 0 THEN //Add the channel to the end of the list elem := ulintFactory.Create(TO_ULINT(channelInfo)); _tmpConnList.AddElement(elem); END_IF END_FOR //Iterate temporary list and add the channels to the input or output list lastE := TO_DINT(_tmpConnList.CountElements()) - 1; FOR i := 0 TO lastE DO _tmpConnList.GetElementAt(udiPosition := TO_UDINT(i), itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} tmpCh := TO___UXINT(elem.UlintValue); {warning restire C0033} //If type is input, add the channel to the input list IF tType = TaskMapTypes.TMT_INPUTS THEN e := inputChannels.AddElement(ulintFactory.Create(TO_ULINT(tmpCh))); //If type is output, add the channel to the output list ELSIF tType = TaskMapTypes.TMT_OUTPUTS THEN e := outputChannels.AddElement(ulintFactory.Create(TO_ULINT(tmpCh))); ELSE __DELETE(tmpCh); END_IF END_FOR //Clear the temporary list _tmpConnList.RemoveAllElements(); END_FOR END_FOR END_METHOD
Last updated: 2024-02-13
Post by imdatatas on MC_CamIn did not work properly with SMC_FreeEncoder on SoftMotion 4.17.0.0
CODESYS Forge
talk
(Post)
Hello, I am facing a problem with the new Softmotion 4.17.0.0 version. Has anyone encountered a similar problem, what is the solution? I would be happy if you could share it. Problem description: -- "SMC_FreeEncoder" encoder axis is the master, -- The motor of the servo driver on the EtherCAT bus is the slave axis. -- When the MC_CamIn block executed, the InSync output is activated. However, although the master encoder axis position value changes, there is no movement in the slave servo axis! Test steps: 1-) EtherCAT servo axis installed, configured and motion test was performed with MC_Jog. No problem. 2-) Softmotion general axis pool > SMC_FreeEncoder was added and pulse amount configuration was performed. No problem. 3-) Incremental encoder actual count value was transferred to the "SMC_FreeEncoder.diEncoderPosition" variable as DINT under the ethercat task in every cycle and the encoder axis position value was observed. No problem. 4-) A simple CAM table with a 1:1 ratio was created under the project tree. (For example: Simply, when the encoder rotates 1 turn, the motor will rotate 1 turn.) 5-) The SMC_FreeEncoder axis enabled with MC_Power and brought to the StandStill state. 6-) The MC_CamTableSelect block was run with default input values ​​(all absolute) and only the Cam table name was specified. The Done output was seen successfully. No problem. 7-) The MC_CamIn block was activated with default input values ​​(absolute) and only the master encoder axis name, slave servo axis name, CamTableID input pins was specified and then "Execute" input set to TRUE. 8-) The InSync output information of the MC_CamIn block observed as TRUE. However, although the encoder axis value changed, the position value of the slave axis did not change at all, it did not move. It always remained at 0.0mm. 9-) When I repeated the same steps above, only changing the master axis to SM_Drive_Virtual instead of FreeEncoder and gave movement to the virtual axis, this time the slave axis moved successfully. However, when the same steps and operations are performed with the same IDE just downgrade SoftMotion version from 4.17.0.0 to 4.10.0.0, everything works normally and without problems as expected in MC_CamIn block with FreeEncoder master. (By the way, The used IDE version is Codesys V3.5 SP20patch3.) Best Regards Imdat