I don't know if this is where I should ask this, but I'm trying to get a Codesys OPC UA Client set up with a Kepware OPC UA Server
CODESYS Forge
talk
(Thread)
I don't know if this is where I should ask this, but I'm trying to get a Codesys OPC UA Client set up with a Kepware OPC UA Server
Last updated: 2023-10-19
Post by romrot on I don't know if this is where I should ask this, but I'm trying to get a Codesys OPC UA Client set up with a Kepware OPC UA Server
CODESYS Forge
talk
(Post)
Trying to create a Data Source under Data source manager, but I'm having issues with security. I get "BadUserAcessDenied" I don't know if there is something special I need to do on the Kepware server to make this work or what.
Last updated: 2023-10-19
Post by leon78 on Codesys 3.5 SP17 Patch 2 CheckBounds (POUs for Implicit Checks)
CODESYS Forge
talk
(Post)
Hello! I use CheckBounds (POUs for Implicit Checks). But I have a problem. I use an array as an VAR_IN_OUT of Function Block. If I try to monitor the array of variable length ([* ]), its does't work. The CheckBounds POU isn't called. If I use the array of fixed lenght ([lower..upper]), the CheckBounds POU is called. Why?
Last updated: 2023-11-14
Post by leon78 on Codesys 3.5 SP17 Patch 2 CheckBounds (POUs for Implicit Checks)
CODESYS Forge
talk
(Post)
Hello! I use CheckBounds (POUs for Implicit Checks). But I have a problem. I use an array as an VAR_IN_OUT of Function Block. If I try to monitor the array of variable length ([* ]), its does't work. The CheckBounds POU isn't called. If I use the array of fixed lenght ([lower..upper]), the CheckBounds POU is called. Why?
Last updated: 2023-11-14
Post by scarter on Import/Export PLCOpen xml Task Configuration
CODESYS Forge
talk
(Post)
I'm Having the same issue. If I highlight PLC Logic and import it erases everything else and replaces the Task config. If I highlight the Application I get the same result. Simple manual fix is click and drag the task config onto the origional Application, and delete the second one. Easy fix but not the expected result of importing task config.
Last updated: 2024-01-17
Post by alexgooi on How to protect library project?
CODESYS Forge
talk
(Post)
Hi aniket-b, If you save the library as a compiled library you are not able to see the source code. When the end user tries to view inside the object, CODESYS will give a notification that the source code is missing, see attachment. In short if you don't send the source code, it will not show.
Last updated: 2024-01-25
Post by ferrim on IEC 61499
CODESYS Forge
talk
(Post)
Hello otdeveloper, I am very interested in this topic. I have been dedicated to IEC 61499 for some time and I would like to understand if the time has come to adopt it in the real world of automation or if it will continue to fill up research papers only.
Last updated: 2024-02-09
Post by manuknecht on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hi, thanks a lot for the response. I did check all these parameters, but if the PlanningTask takes up to 60 ms, I can't increase the Buffer to such values. I contacted the Codesys support with a projectarchive. Let's see if they can help. Thanks again for your great support!
Last updated: 2024-03-22
Post by hanoues on Holding brake release
CODESYS Forge
talk
(Post)
I've tried using the SMC3_BrakeControl function block to control the brake, but unfortunately, it's not functioning as expected. Despite setting the appropriate parameters and inputs, the brake control does not operate correctly. Any insights or suggestions on resolving this issue would be greatly appreciated. STATE_MANUAL.UNLOCK_BRAKE: IF Button_release_brake THEN GVL.drum1_Control_Brake:=TRUE; FBA.T11_ContBrake.bExecute := TRUE; GVL.manual_state := STATE_MANUAL.WAIT_FOR_BRAKE_RELEASE; END_IF STATE_MANUAL.WAIT_FOR_BRAKE_RELEASE: IF FBA.T11_ContBrake.bDone THEN FBA.T11_ContBrake.bExecute := FALSE; GVL.manual_state := STATE_MANUAL.WAIT_START_BUTTON; END_IF
Last updated: 2024-04-08
Post by timvh on Change the Opening Position of the Dialog using VU.FbOpenDialog
CODESYS Forge
talk
(Post)
Probably best to call the FB continuously. So something like this could solve it: IF xOpenLatchSettingDialog THEN xOpenLatchSettingDialog := FALSE; fbOpenLatchSettingsDialog.xExecute := TRUE; END_IF IF fbOpenLatchSettingsDialog.xDone OR fbOpenLatchSettingsDialog.xError THEN fbOpenLatchSettingsDialog.xExecute := FALSE; END_IF TopLeftDialog.iX := 100; TopLeftDialog.iY := 23; fbOpenLatchSettingsDialog( itfClientFilter:= VU.Globals.OnlyTargetVisu, sDialogName:= 'visu_AlarmLatchSettings', xModal:= TRUE, pTopLeftPosition:= ADR(TopLeftDialog) );
Last updated: 2024-05-09
Post by rajesh008 on i can't declear the address in GVL - codesys SP19 Patch5
CODESYS Forge
talk
(Post)
The β_AB AT %IW0:word; β if i called the value then im getting this error. like below "the declartion of the variable with an address assignment cannot be used in a PRG or GVL with the attribute 'subsequent'" This is happening when the GVL is selected in Redundancy Configuration. if i un-select the address declaration is working fine
Last updated: 2024-05-13
Post by oymyakon on Modbus Lockup
CODESYS Forge
talk
(Post)
Hi i have a project where i am communicating with many modbus devices using TCP to serial. This is all working extremely well except when i turn one of the remote devices off. If i leave the auto reconnect on it still doesn't talk to the rmianing devices and if i turn Auto reconnect off it locks up. Any help would be appreciated. Paul.
Last updated: 2024-08-07
Post by oymyakon on Modbus Lockup
CODESYS Forge
talk
(Post)
Hi i have a project where i am communicating with many modbus devices using TCP to serial. This is all working extremely well except when i turn one of the remote devices off. If i leave the auto reconnect on it still doesn't talk to the rmianing devices and if i turn Auto reconnect off it locks up. Any help would be appreciated. Paul.
Last updated: 2024-08-07
Post by davidbo on Modbus: Is there a way to get the channel index from the channel name?
CODESYS Forge
talk
(Post)
When I use the FUNCTION_BLOCK ModbusChannel I have to sepcify the integer iChannelIndex It can easily go wrong if one has many channels. It would be better if one could use the name. Is that possible? Attached a snippet of the channel name and the channel index to the left.
Last updated: 2024-10-21
Post by lsislsis on SIGABRT Error
CODESYS Forge
talk
(Post)
After many tests i see that problem comes when serial communication established for modbus rtu. If the slave device not connected we don't see the exception. If the slave device connected at serial port then we have exception about 1 hour after startup and every 10 or 15 minutes. Any suggestion?
Last updated: 2024-11-08
Post by timvh on Leitungsverzweigung mit einem existierenden Block (z.B. AND-Glied) zu verbinden
CODESYS Forge
talk
(Post)
If you are really happy with PLCnext engineer, then just use that. There is probably also something in CODESYS that cannot be done in PLCnext engineer. But if you are forced to make something like this in CODESYS, then maybe just use CFC instead of FBD.
Last updated: 5 days ago
Post by timvh on How to implement an interface (IElement)?
CODESYS Forge
talk
(Post)
See: https://forge.codesys.com/prj/codesys-example/element-collect/home/Home/ This contains an application "OnlineChangeSafeLinkedListExample". What you should do is create a new interface which has your "Priority" property. Then your FB should extend the base element function block and implement your own interface: E.g. FUNCTION_BLOCK MyElement EXTENDS COL.LinkedListElementBase IMPLEMENTS I_MyInterface Then the __QUERYINTERFACE does the magic to check if your "element" also implements your interface. Something like this: // Compares this element with itfElement. // Returns 0 if the elements are equal, < 0 if the element is less than itfElement, // > 0 if the element is greater than itfElement. // This method will be called from sorted collections (e.g. |COL.SortedList|) to sort the elements. // IMPORTANT: The underlying value to be compared with MUST NOT be changed during the lifecycle of the object. METHOD ElementCompareTo : INT VAR_INPUT (* The element to compare*) itfElement : COL.IElement; END_VAR VAR itfIntElement : I_MyInterface; xResult : BOOL; END_VAR // We use integer iInt1 for sorting. xResult := __QUERYINTERFACE(itfElement, itfIntElement); IF xResult THEN IF iInt1 < itfIntElement.Priority THEN ElementCompareTo := -1; ELSIF iInt1 > itfIntElement.Priority THEN ElementCompareTo := 1; ELSE ElementCompareTo := 0; END_IF ELSE ElementCompareTo := -1; END_IF
Last updated: 2024-07-22
Post by jari-koivuluoma on Problem trying Net Base Services 3.5.15.0 TCP connection
CODESYS Forge
talk
(Post)
I have a need to send messages between 2 PLCs and I cant use network variables (because of size limit) so I tried writing this simple test program. This seems to work fine. I can send messages back and forth when a first "Start server" and then "Connect client". See the attached image. However, if I disconnect the client by setting ClientConnect to false and try to re-connect then the TCP_Client just gives me TIMEOUT error. When I stop and start the server again, then Im able to reconnect. How is this supposed to work? Why reconnecting wont work. There is not other way of disconnecting the client than setting xEnable of the TCP_Client to false. This is just a testing program and I will try it on 2 seperate devices once this works. PROGRAM PLC_PRG VAR CONSTANT mySize : UDINT := 255; END_VAR VAR Server: NBS.TCP_Server; ServerIpStr: STRING := '127.0.0.1'; ServerIP: NBS.IP_ADDR; ServerPort: UINT := 50000; ServerConnection: NBS.TCP_Connection; Client: NBS.TCP_Client; ServerRead: NBS.TCP_Read; ServerWrite: NBS.TCP_Write; ServerSend: STRING(mySize); ServerReceive: STRING(mySize); ServerConnect: BOOL; bServerSend: BOOL; IP: NBS.INADDR; ConnectedClientIP: STRING; ClientPort: UINT := 50000; ClientIpStr: STRING := '192.168.1.49'; ClientIP: NBS.IP_ADDR; ClientRead: NBS.TCP_Read; ClientWrite: NBS.TCP_Write; ClientSend: STRING(mySize); ClientReceive: STRING(mySize); ClientConnect: BOOL; bClientSend: BOOL; Error: BOOL; Message: BOOL; END_VAR // Server ServerIP.sAddr := ServerIpStr; Server( ipAddr := ServerIP, uiPort := ServerPort ); ServerConnection( xEnable := Server.xEnable, hServer := Server.hServer, ); IP := ServerConnection.IPAddress; ConnectedClientIP := F_Concat7( BYTE_TO_STRING(IP.S_un_b.s_b1),'.', BYTE_TO_STRING(IP.S_un_b.s_b2),'.', BYTE_TO_STRING(IP.S_un_b.s_b3),'.', BYTE_TO_STRING(IP.S_un_b.s_b4)); ServerRead( xEnable := ServerConnection.xActive, hConnection := ServerConnection.hConnection, szSize := SIZEOF(ServerReceive), pData := ADR(ServerReceive) ); IF ServerRead.xReady AND ServerRead.szCount > 0 THEN Message := TRUE; END_IF IF ServerRead.eError > 0 THEN Error := TRUE; END_IF ServerWrite( xExecute := ServerConnection.xActive AND bServerSend, hConnection := ServerConnection.hConnection, szSize := LEN(ServerSend)+1, pData := ADR(ServerSend) ); IF ServerWrite.xDone THEN bServerSend := FALSE; END_IF IF ServerWrite.eError > 0 THEN Error := TRUE; END_IF // Client ClientIP.sAddr := ClientIpStr; Client( xEnable := ClientConnect, ipAddr := ClientIP, uiPort := ServerPort, udiTimeOut := 10000000 ); ClientRead( xEnable := Client.xActive, hConnection := Client.hConnection, szSize := SIZEOF(ClientReceive), pData := ADR(ClientReceive) ); IF ClientRead.xReady AND ClientRead.szCount > 0 THEN Message := TRUE; END_IF IF ClientRead.eError > 0 THEN Error := TRUE; END_IF ClientWrite( xExecute := Client.xActive AND bClientSend, hConnection := Client.hConnection, szSize := LEN(ClientSend)+1, pData := ADR(ClientSend) ); IF ClientWrite.xDone THEN bClientSend := FALSE; END_IF IF ClientWrite.eError > 0 THEN Error := TRUE; END_IF
Last updated: 2024-10-03
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
Hi Duvan, You could make this in 1 single object (FB), Indeed don't use a function for this beacuse you need some memory to keep the old value. For i := 0 TO 200 BY 1 DO //Check if the value has been changed IF Old_Value[i] <> Value[i] THEN //Set the trigger to TRUE Trigger[i] := TRUE; Old_Value[i] := Value[i]; END_IF END_FOR If you define the Value array as an In_Out and the Trigger as an In_Out you arn't claiming any aditional memory to your system. You ofcourse then need to add some code arround it that does something with the trigger and writes it back to FALSE again. If you want more flexability you also could use pointers instead of using the IN_OUT FOR i := 0 TO 200 BY 1 DO address := address_Input + i * SIZEOF(*Put type here); IF Address^ <> Old_Value[i] THEN Trigger[i] := TRUE; Old_Value[i] := Address^; END_IF END_FOR
Last updated: 2024-04-02
Post by riccardo on Codesys SP19 patch 4
CODESYS Forge
talk
(Post)
Hallo everyone, I am working on new PLC of Weidmueller that uses Codesys SP19. I made the upgrade at the Patch 4 coming from patch 0. Unce made the upgrade everything is working well in the progect except the web visu user menagent. In the new version, when I perfom the login, I cannot use the keyboard of the device; the window where to digit the user name and password opens, the buttons "OK" and "Cancel" work but the system doesn't allow to put input from the device keybord, the mouse behaves as it is an image. If I active the virtual keypad or numpad it works otherwise nothing. I am wondering if it is a bug of the new package or if I must set something else. Thanks in advance, Riccardo.
Last updated: 2023-11-27
Post by ton on How to create a stopwatch?
CODESYS Forge
talk
(Post)
One i wrote this to measure elepse time When xMeasure is true is starts en when false it stops and time is messured. FUNCTION_BLOCK FB_ElapseTime VAR_INPUT xMeasure: BOOL; END_VAR VAR_OUTPUT xRisingEdge: BOOL; xFallingEdge: BOOL; tElapsed: TIME; ltElapsed: LTIME; ltPrev_Elapsed: LTIME; ltElapsedMax: LTIME; END_VAR VAR xLastValue: BOOL; LTIMEStart: LTIME; LTIMEEnd: LTIME; tonReset: TON:= (IN:= TRUE, PT:= TIME#30S0MS); END_VAR ------------------------------------------- xRisingEdge:= (xLastValue XOR xMeasure) AND xMeasure; xFallingEdge:= (xLastValue XOR xMeasure) AND NOT xMeasure; IF xRisingEdge THEN ltPrev_Elapsed:= ltElapsed; LTIMEStart:= LTIME(); END_IF IF xMeasure OR xFallingEdge THEN LTIMEEnd:= LTIME(); END_IF ltElapsed:= LTIMEEnd - LTIMEStart; ltElapsedMax:= MAX(ltElapsedMax, ltElapsed); tElapsed:= LTIME_TO_TIME(ltElapsed); xLastValue:= xMeasure; tonReset(); IF tonReset.Q THEN tonReset.IN:= FALSE; ltElapsedMax:= LTIME#0NS; END_IF Meaby this will help.
Last updated: 2023-12-09
Post by i-campbell on What does CODESYS expect to do when I get such an error message
CODESYS Forge
talk
(Post)
you need to get the addons that the person that programmed it used. I always store an .installation-config file alongside the project. If you have lost that, then it gets a bit of a headache: I think even with SP18 you can hit yes to open it anyway, and it will suggest which addons it thinks are missing, if you double click the yellow "missing-addons" in the status bar. If you know you have the right addons, you can do a "Save As.." and it will write your current addon list to the file, and you wont get the error next time.
Last updated: 2024-01-08
Post by mondinmr on Shared Memory Access Issues
CODESYS Forge
talk
(Post)
In Windows I need create shared memory in PC software and connect from CODESYS. If shm is not GLOBAL doesn't work due different users between runtime and PC software. PC software need admin privileges. Name need "Global\\" before key. Very unsafe!!! If CODESYS create shared I cannot find key PC side. In Linux I can create shared memory as standard user, bind in the runtime docker, use keys without any "Global\\". Much more safe!!! If CODESYS create shared you need play with permissions to use app as standard user. I prefer create form PC software as standard user.
Last updated: 2024-01-30
Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28
Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND
or OR
.