Post by tk096 on Fieldbus has lost synchronicity
CODESYS Forge
talk
(Post)
Hi, a few suggestions on how to tackle the problem: - it might help to increase the cycle time of the ethercat task - increase the value of the ethercat parameter DCInSyncWindow (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/DCInSyncWindow.html) (see attached image) - enable FrameAtTaskStart (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/FrameAtTaskStart.html) in the ethercat master (see attached image) - if the drives can handle the synchronization problems, checking of the synchronization can be deactivated using SMC_Set_ETC_DCSyncSupervision (https://content.helpme-codesys.com/en/libs/SM3_Drive_ETC/Current/SMC_Set_ETC_DCSyncSupervision.html).
Last updated: 2024-04-11
Post by toby on Ethernet/IP communication with Omron NX1P2
CODESYS Forge
talk
(Post)
Hey guys, I'm very much a noob with networking, it's my achillies heel, and this is my first networking project using Ethernet/IP. Any help offered is GREATLY appreciated. I'm trying to network a Codesys Project with an Omron NX1P2 PLC. I'm using EIP due to hardware restrains. I've added the fieldbus, EIP scanner (as the master), and made a Network Variable List. On the Sysmac Studio end, I've made the variables and set them to network inputs/outputs, registered them in EIP settings, but when I try to set the target device (the Codesys project), I suspect I need to import an EDS file for the EIP mapping. Back in the Codesys project, I'm not sure how to: - Make an EDS file to share with Sysmac Studio - How to link the target device (Omron PLC) to the EIP fieldbus - How to map the inputs from the Omron PLC. Im sorry for my very open request for help, i'm kind of lost looking through the various forums/video/tutorials as many of them dont match what im trying to do. Any help, or sample programs would be so so greatly appreciated. If you need any further clarifications, please feel free to ask. Thanks in advance, Toby
Last updated: 2024-01-24
Post by totorovic on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
I think that the .err file is the .app file renamed by Codesys, so it is compiled. We met this behaviour one time, it was because the runtime goes in exception due to bad Ethercat cables.
Last updated: 2024-10-03
Post by gatto on library ModbusTCP Slave 4.1.0.0 - function block ModbusServer
CODESYS Forge
talk
(Post)
Hi, again after spending a lot of time finding more information with no results, by chance I changed the device ID from 1 to 255 and the transmission works. Unfortunately the documentation is very very poor.
Last updated: 2024-11-28
Post by sumit on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
Yes, green icon is there, this time I tried by enabling the device to always update variables but results are the same. I have attached the screenshot and eds file I am using.
Last updated: 2024-03-06
Post by davidbo on *EXCEPTION* [ProsessorLoadWatchdog] codesys 3.5.11.40
CODESYS Forge
talk
(Post)
Under Application->"Task Configuration" you can find your task double click on that and you will see a fane to the right. You find the watchdog enable switch it off or increase the time
Last updated: 2025-11-17
Post by nz-dave on Ethernet/IP Scanner Exception
CODESYS Forge
talk
(Post)
Hi Trusty-Squire, just seen you post , thanks for the reply. I was out on site the other day as it had done it again and changed a few things like cycle time etc. plc load is only 7% at its highest. I took a few screenshots while i was there to add to this post. its been up for about a week now but seems to happen at random every couple of weeks. fingers crossed!
Last updated: 2025-03-19
Post by yannickasselin on display values with frames
CODESYS Forge
talk
(Post)
Put %f in the "text" field and rValue in the "Text variable" field. You could also have a look at the possible placeholders: https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_placeholder_with_formatting_sequence_in_a_string.html
Last updated: 2025-08-17
Post by gurkan on OPCUA array max length?
CODESYS Forge
talk
(Post)
2000 works. When testing with UA Expert there is a timeout from the OPCUA Server when trying to subscribe to the variable CPU do not seems to be to affected. The memory(RAM) however is building up
Last updated: 2024-02-19
Post by liamb on Converting CANbus to Decimal from signed 2's complement
CODESYS Forge
talk
(Post)
I need to combine two 8 bit CANbus messages to 16 bits signed int then convert to decimal Decimal from signed 2's complement. I've been using the below code to read for new messages, combine them then assign them to a variable What is the best way to do this for from signed 2's complement? fbRxMessage351(Data := RxMessage351Data); IF fbRxMessage351.NewMessage THEN ChargeVoltage := (WORD_TO_REAL((RxMessage351Data[0]) + ((RxMessage351Data[1]) * 256))) * 0.1; END_IF
Last updated: 2024-08-16
Post by nano on How to access to variable value through symbolic string name
CODESYS Forge
talk
(Post)
i know, this is the reason for us either. PLC-Handler is to big, and only available with additional Contracts/Costs. OPC-UA is to slow for us. As described, there is a solution available, but im not allowed to post them here. i would prefer you send a message at codesys store by "have a question" or similar called. Not sure. Or, if an Codesys-Official Member allows to share that informations, i can give you the right hints.
Last updated: 2024-06-15
Post by gerdkoch on OPCUA Datasource, can not login...
CODESYS Forge
talk
(Post)
Hi, please share your codesys ide version and the version of the communication addon. Do you use encrypted communication? Did the browsing in the ide work? Did you create the certificate for the client in the security screen? BR
Last updated: 2023-11-27
Post by mos89p on how to use UseDataExpanding() in datasource
CODESYS Forge
talk
(Post)
Hi I need to update by software some structures in my datasource, i found this example: https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_update_data_interface.html it seems that because i use complex variable structure i need to use UseDataExpanding() instead of use data, the question is how to get an instance of IDatasourcesMgr3 i have the global variable g_Datasources is instantiated automatically
Last updated: 2024-06-18
Post by elsmart on Sequential read and triggering of Modbs RTU channels in application
CODESYS Forge
talk
(Post)
Hello I need some help understanding how to use Modbus RTU (COM port) in Codesys enviroment. I defined a Modbus Server device (slave) in device tree and added some channels to read from (function 3). Also I set trigering mode to Application. I have a POU in which I want to trigger each channel one after the other something like this (C code for better visualisation): for (int i = 0; i < channelsCount; i++) { triggerChannel(channelsArray[i]); // Start transmission while(channel.xBusy); // Wait for transmission to complete } I have found ModbusChannel function block documentation but examples are scarce. I don't understand how rising edge triggering works. What would be the best solution for achieving sequntial channel triggering? What is the common way to read multiple Modbus channels once every time a specified POU is executed?
Last updated: 2025-05-16
Post by royw on Profinet library for C#
CODESYS Forge
talk
(Post)
Hi, I don't know if I'm in the right place or if it's even possible... I'm looking for a way to address a Profinet device with Record Read and Write from my own PC. I actually only need very few commands to configure our device. This means setting the MAC address and a serial number. We would like to do this from a C# program. Now we are looking for a library or something similar. Since you can do it from Codesys, I thought there might be a DLL or something similar that you could use for this. As I said, we don't want real-time queries of the cyclic data but only record read/write. Does anyone have any helpful hint? Thanks in advance
Last updated: 2023-12-22
Post by csu-chris on No file found
CODESYS Forge
talk
(Post)
I'm having trouble getting started with the SysFile library. I tried copying and running the code found here: https://forge.codesys.com/forge/talk/Engineering/thread/f17c3d0e64/ Every time I try to run the file handle pointer returns: 16#FFFFFFFFFFFFFFFF <dereference of="" invalid="" pointer=""></dereference> I can see the file when I look in the Device -> Files window Any idea what I'm doing wrong?
Last updated: 2024-10-15
Post by domebruce on Which database to use?
CODESYS Forge
talk
(Post)
We have developed a similar application few years ago with .Net and MS Sql Server. The database has about 30 tables, the more bigger tables have 2 or 3 thousands records. We can have multiple threads accessing at the same time to the DB. To garantie the data integrity we need to manage data locks and transactions. Thanks
Last updated: 2025-03-04
Post by tomast on Codesys and Siemens SINAMICS 20 modbus RTU "Response CRC Fail"
CODESYS Forge
talk
(Post)
Hi everyone, I'm currently working on a project involving the control of 5 VFDs via Modbus RTU, this time using the WAGO 750-8212 CPU. So far, I've managed to make progress, but I've encountered an issue. While I can successfully read and write to all the registers I need, I consistently encounter a "Response CRC Fail" error when attempting to write the value 1151 to the STW register at address 40100. I'm able to set the frequency via register 40101 and adjust all other parameters using different registers. Setting STW to 1150 results in the drive ready boolean from the ZSW-bit being received instantly. However, the moment I attempt to send 1151 to register 40100, I immediately receive the "Response CRC Fail" error for all channels. I've also attempted to use combined control, employing Modbus for frequency control and starting from a digital input. Everything seems to function properly until I send the start command to the VFD. Interestingly, I consistently encounter the same error the moment I send the start command, regardless of whether I use register 40006 (high) or 40100 (1151). Could someone please assist me in resolving this issue?
Last updated: 2024-03-21
Post by macros8 on Alarm Management - latched variable represented as Text list
CODESYS Forge
talk
(Post)
Hi all, in Alarm management you can latch some variable to show value within the alarm msg. It´s very useful sometime. But I´m wondering whether there is any possibility to represent that value as Text list. It´s quite common in other HMI tools and this is very useful in case of using some ErrorID for detail specification of error. Unfortunately I could not find any way how to do it but I believe that exists :) Thanks a lot. M.
Last updated: 2023-09-06
Post by ewi04 on How to upload application file to remote controller (offline) ?
CODESYS Forge
talk
(Post)
Thank you very much for your time and replay! Sounds like a good idea. Unfortunately, I have no other option to run the code from the running plc. So, I can’t stop any services. If anyone has the same problem, I've gotten a little closer to understanding it: Sometimes the copied files are empty after the restart. The update code checks if there are any empty files. Before I turn off the device, everything is okay. But after starting, some files are suddenly empty and that cause the problems. I don't know why this happens.
Last updated: 2024-02-16
Post by mwandy on Codesys Project Protection
CODESYS Forge
talk
(Post)
I'm having trouble finding clear answers on this. I'm looking for a way to make a Codesys project password protected so that if the project is distributed it can be used to log into a controller to view and debug logic. At this same time I want to prevent the project from being saved as well as edits being downloaded to the controller. Basically I want to make a whole project view-only. What is the beat way to achieve this? I have had minor success with access rights, which solves the problem with trying to login if the project doesn't match what is in the controller. However with this solution, edits can still be made and saved, possibly corrupting the core project, preventing future logins. Any suggestions?
Last updated: 2024-03-29
Post by alessandro on SysMemCmp SysMemCpy
CODESYS Forge
talk
(Post)
VAR Data1:ARRAY[1..10] OF SINT ; Data2:ARRAY[1..10] OF SINT ; Data3:ARRAY[1..10] OF SINT ; Data4:ARRAY[1..10] OF SINT ; ex_1 : BOOL ; ex_2 : BOOL ; enable : BOOL :=0 ; END_VAR // PROGRAM // The scope of this example is compare and copy the values of two ARRAY only if some value is different using SysMemCmp and SysMemCpy. // In this 2 example we don't use a FOR cicle for do this, and pBuffer1 and pBuffer2 is just a pointer to ARRAY. See details in Library util.SysMem of Codesys // The compare funcion util.SysMem.SysMemCmp is bidirectional if Data1 chanege respect Data2 ex_1 go to 1 and if Data2 change respect Data1 also // but the copy function util.SysMem.SysMemCpy work only from source ARRAY pSrc:=ADR(Data1) to destination ARRAY pDest:=ADR(Data2) // Example 1 Full ARRAY compare and copy // This compare 2 different equal ARRAY and if there is some difference ex_1 go to 1 and if you give enable he copy Data1 in Data2 ex_1 := TO_BOOL(util.SysMem.SysMemCmp(pBuffer1:=ADR(Data1), pBuffer2:=ADR(Data2), udiCount:=SIZEOF(Data1))); IF ex_1 AND enable THEN util.SysMem.SysMemCpy(pDest:=ADR(Data2), pSrc:=ADR(Data1), udiCount:=SIZEOF(Data1)); END_IF // Example 2 Only selected area of the ARRAY compare and copy // This compare 2 different equal ARRAY starting from position number [3] for 4 byte in this case start at position [3] and finish at position number [6] // and if there is some difference only in area [3..6] of the ARRAY ex_2 go to 1 if you give enalbe he copy Data3[3..6] in Data4[3..6] // if something change in other array position[0..2] or [7..10] are ingnored ex_2 := TO_BOOL(util.SysMem.SysMemCmp(pBuffer1:=ADR(Data3[3]), pBuffer2:=ADR(Data4[3]), udiCount:=4)); IF ex_2 AND enable THEN util.SysMem.SysMemCpy(pDest:=ADR(Data4[3]), pSrc:=ADR(Data3[3]), udiCount:=4); END_IF // Attention udiCount input is intended in <byte> in the example 1 I pass to udiCount:=SIZEOF(Data1) for compare and copy the intere ARRAY and // SIZEOF pass the size of intere ARRAY in byte to the function input, in this 2 examples I used variable type SINT each one occupie 1 byte and one position in the ARRAY // and in the example 2 I pass udiCount:=4 for compare and copy only 4 position of Data3/4[3..6] if you want to extend this example and use it for an ARRAY OF WORD // remember that each WORD will occupe 2 byte (16 bit) and you will have to pass udiCount:=SIZEOF(Data1) if you need to compare intere ARRAY example 1 // but need udiCount:=(42) for the example 2 because need to compare and copy 4 word each occupie 2 byte (16 bit). // For REAL (32 bit) need udiCount:=SIZEOF(44) for LREAL or (64 bit) need udiCount:=SIZEOF(416) // a good rule is calculate the dimension of the ARRAY in byte without empty space at the end, multiple of data type number for variable bigger then 8 bit // Example : If you want to create an ARRAY for 5 REAL (32 bit) each occupie 4 byte the correct size is ARRAY[0..19] OF REAL 54=20 position. // NOTE : In the example the position of compare function util.SysMem.SysMemCmp is first and the copy function util.SysMem.SysMemCpy inside the IF is after // in one cycle of the program the two array is compared and if there is some difference and enable are copied. // If you move util.SysMem.SysMemCmp after the IF cycle he will copare the ARRAY in the current cycle but the copy of the value will do in the next cycle.</byte>
Last updated: 2025-10-24
Post by matt-purcell on Which Lib to use, connect to a socket with URL instead of IP address
CODESYS Forge
talk
(Post)
Hello, I have a new project and I need to connect to a TCP socket using the URL instead of an explicit IP address, myendpoint@mydomain.com Which library is best suited for this? This is for a new enterprise project, the endpoint is a server in a datacenter running some real time application. We have big IP, it will automatically reassign the IP address to the backup server if a crash occurs so an explicit IP won't work for me. I've done this in RS logix, working now to migrate that code over to codesys. Thanks in advance!
Last updated: 2024-06-17
How to intercept a variation in the RetainPerstist variables (for saving to file)
CODESYS Forge
talk
(Thread)
How to intercept a variation in the RetainPerstist variables (for saving to file)
Last updated: 2018-08-03
RPI How to login for a copy of the SD image
CODESYS Forge
talk
(Thread)
RPI How to login for a copy of the SD image
Last updated: 2023-10-18