Post by baott569 on CODESYS OPC UA Security: HMI Client Not Receiving Server Certificate CODESYS Forge talk (Post)
Hello everyone, I am currently using OPC UA in CODESYS with the security mode BASIC256SHA256 – Signed and Encrypted. The OPC UA Server is running on an RTE CX device, and the HMI is running on another computer. I have reviewed many CODESYS documents and successfully established communication when the security mode is set to None with Anonymous login. However, when security is enabled, the server does not provide its certificate for the CODESYS HMI client to trust. Interestingly, the client can send its certificate to the server, and UAExpert works normally, but the CODESYS HMI client does not receive the server certificate. Can anyone help clarify what I might be missing? I have been stuck on this issue for three days. If I missed or misconfigured any step, please let me know. I believe I am stuck at step 15 in the following CODESYS guide: Encrypting the Communication of a Data Source OPC UA Client https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_encrypt_communication_data_sources_opc_ua_client.html Thank you very much.
Last updated: 2026-01-06

Post by s1ack on Wago PFC200 Ethernet / IoDrvEthernet Issue? CODESYS Forge talk (Post)
CODESYS Control for PFC200 4.13.00 CODESYS IIoT Libraries SL 1.11.0.0 Application Based License: CODESYS Control Standard M I have (2) projects with similar code base and both using Wago PFC200. On the second project I am seeing 2 things that I have not been able to resolve: 1) Errors in the log under the Ethernet Item: IoDrvEthernet: [PCI\E1Q51CE62] Could not be found on target! Please check the Ethernet settings. 2) Exception for CPU Load. "Processorload watchdog: plcload=100, maxplcload=95" I have slowed down cyclic tasks on this project, even though on the first project there is actually more code - and it does not exhibit this behavior. In looking at the CPU loading via Linux 'TOP' command there appears to be 20% idle. So plenty of headroom (my opinion). In an effort to troubleshoot I have duplicated the target hardware on my bench. It ran overnight without a CPU load exception. On the test system, I have tried (3) version of the ethernet device. 3.5.16.0 3.5.17.0 and 4.2.0.0 Presently the log does not show the error, but status says the module reports an error. I really do not know if this issue is related to the CPU load exception. The issue does not appear to effect ethernet communications (ModbusTCP or SNMP or Webvisu or PuTTy into Linux Shell). On my test bench I have ModbusTCP slave simulators for all ModbusTCP slaves, but only (1) of the (5) SNMP devices present.
Last updated: 2025-01-21

Post by jtebokkel on Access to the path *** is denied CODESYS Forge talk (Post)
I am also having this issue. It was working fine for the first 2ish months and is now throwing this error. I can just try and go online again a second time and it works. I'm wondering if there is an environmental variable or something that isn't set that is causing it to use an empty path as a temp directory. The empty path will be the location the app is running from which is that path C:\Program Files\CODESYS 3.5.19.50\CODESYS\Common. The permissions don't allow a normal user to write to that directory which causes the error. It also only seems to happen when there are changes or the build has been cleaned.
Last updated: 2024-02-14

Post by pernockham on *Exception* Async service: ServiceGroup=17, IP=0x5fa45617, Component=CmpSrv CODESYS Forge talk (Post)
*** The system may be in an inconsistent state, please reboot *** *Exception* Async service: ServiceGroup=17, IP=0x5fa45617, Component=CmpSrv Every time at the instant that I Login to the system a message that the "system may be in an inconsistent state, please reboot" is written in the log. If I logout and repeat login a new entry is set. My system is a "Control for linux SL" running on a debian linux host. Im running it on my desk without any IO attached so message might be caused from that, but I doubt i have seen it before. Rebooting makes no difference. Anyone that have a clue of how I should interpret this error message?
Last updated: 2025-09-26

Post by dhumphries on Rounding error in simple addition CODESYS Forge talk (Post)
Thanks for the response, as I've thought about this problem over the last month I began to suspect this was a problem with not being able to exactly represent .1 as a 32 bit binary number. I think I've found a work around by making the number an integer, then dividing it by 10 and storing that value as a floating point number. There is still an issue with the value not being exact somewhere in the 8th or 9th decimal place, but because I'm incrementing an integer value then dividing it, the error doesn't compound.
Last updated: 2024-05-25

Post by xnoop on MBTCP Slave configuration CODESYS Forge talk (Post)
Hello, I use Codesys 3.5 SP18 Patch 4 (64 bit) My Codesys project is composed of several dozen of Modbus TCP Slaves. I want to configure each of them by define : - Modbus TCP Slave Configuration : Name, IPAddress, port - Channels - Mapping I can't afford to configure manually and I need to find automatic way What possibilities does the Codesys offer? 1. I know it possible to use python script to create Modbus TCP Master and Slave. But I don't find anyway to create Channels and Mapping through the API 2. I 've tested to set mapping with file.csv on a Modbus Tcp Slave, but no way to import channels definition from file 3. I 've tried to use PLCOpenXml file. For example I 've create a project with an Ethernet device. I've exported it in PlcOpenXml file. After delete the Ethernet device, I've imported the PlcOpenXml file without success. I've tried the same by creating Modbus TCP Slave. Could you help me to find to good way ? Thanks
Last updated: 2024-06-19

Post by nano on conformation about the CODESYS Extends SL and CODESYS SDK CODESYS Forge talk (Post)
as an oem i can tell you, extension sl isn't the sdk. its more an hard restricted part of it with much missing parts. why u may ask this?
Last updated: 2025-11-11

Post by zatalian on Beckhoff EL7037 softmotion CODESYS Forge talk (Post)
Hi, Is the Beckhoff EL7037 supported by codesys with softmotion? Where can I find a device descriptor that includes the drive object for the EL7037?
Last updated: 2024-11-25

Post by imdatatas on The default ramp type selection in SoftMotion V4.18.0.0 is Quadratic CODESYS Forge talk (Post)
Unfortunately, The same behaviour still exist with SoftMotion V4.19.0.0 too. (default ramp type is quadratic instead trapezoid for new created axis object) For your information.
Last updated: 2025-09-04

Post by taywinkel on Virtual Keyboard Support on Login Page CODESYS Forge talk (Post)
I am in the process of getting a visualization to work with the codesys keyboard. I created a custom keyboard which works fantastic for all input fields in the main visualization. I created a user management for my runtime, which gave me the standard blue login page. The codesys keyboard does not show up when trying to enter the usernam or password. I have tried every setting: changing the keyboard back to the standard codesys keyboard, and changing various settings on the visualization manager with no success. I can only use a physical keyboard connected to the device to enter the password. I did try removing the keyboard to no success either. I even tried creating my own login page so I could guarantee the keyboard showed up. This ended in disaster as I could not figure out the very complicated VisuUserManagement and VisuUserManagementDialog library, and documentation is contradictory or lacking. I imagine that an on screen keyboard is essential for many people's projects when using touchscreen panels, so I am wondering what others are doing. I would rather not use an external virtual keyboard (external to codesys) because this causes its own complications (I am working on a linux build with high securities).
Last updated: 2026-03-22

Post by gseidel on MC_MoveAbsolute: C0138: No matching 'FB_Init' method found for instantiation of SMC_MoveAbsRelPerformerImpl [ERROR] CODESYS Forge talk (Post)
Hi imdatatas, sorry to hear this issue caused so much overhead for you. Frankly, I'd expect a project created with an older version to compile without errors after opening > it with the latest Codesys version and updating all libraries. Yes, that is a reasonable expectation. I tried a few times but could not reproduce the problem. In case you run into the problem again, we can investigate the issue if you send a project archive. Best regards, Georg
Last updated: 2025-10-02

Post by rodberna on Library for arrays CODESYS Forge talk (Post)
Hi, I'm creating a program where I need to handle arrays, like: - Declare lenght variable arrays - [array(1..var) of "sometype"]. This is not possible in pure codesys, right? - Know array lenght, min, max, avg values in runtime - append/delete itens in an array - and so on Is there a library know for this in codesys. Is it possible to build our own libraries using some high level language like python or java script?
Last updated: 2024-01-10

Post by r-niedermayer on C0564 Warning Message CODESYS Forge talk (Post)
Please see or Online Help on how to initialize variable before using them: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_pragma_attribute_global_init_slot.html Regarding the Attribute global_init_slot: You can use this pragma to influence the order in which signatures are processed during global initialization. It can only be applied to signatures. By default, the initialization sequence for variables from global variable lists is undefined! However, if, for example, variables from one list depend on variables from another list, it is necessary to initialize one before the other. (Aee OLH and Syntax) The placeholder <slot> must be replaced by an integer value that defines the position in the initialization sequence.</slot> The default value is 50000. A lower value causes an earlier initialization! If several signatures have the same value for the 'global_init_slot' attribute, the order of their initialization remains undefined! Cautious application should therefore be considered! Example: The project contains f.e. two global variable lists GVL_1 and GVL_2. The global variable "A" is part of the global variable list GVL_1: {attribute 'global_init_slot' := '300'} VAR_GLOBAL A : INT:=1000; END_VAR The initialization values of the variables "B" and "C" of GVL_2 are dependent on the variable "A". {attribute 'global_init_slot' := '350'} VAR_GLOBAL B : INT:=A+1; C : INT:=A-1; END_VAR So if you set the 'global_init_slot' attribute of the global variable list GVL_1 to 300, i.e. to the lowest initialization value in the example, then it is ensured that the expression "A+1" is well-defined at the time of initialization of "B".
Last updated: 2024-01-30

Post by yannickasselin on Lenze i950 Servo and WAGO PFC200 CODESYS Forge talk (Post)
In order to use SoftMotion Light, a servo drive needs to support CiA 402 operating modes: Profile Position (PP), Profile Velocity (PV) and Homing Mode (HM). https://content.helpme-codesys.com/en/CODESYS%20SoftMotion%20Light/_sm_light_requirements.html According to the Lenze i950 documentation you linked in your post, none of these modes are supported. Not even Homing Mode which explains why MC_Home does not work even with the full SoftMotion. The full SoftMotion uses Cyclic Synchronous Position Mode (CSP) but still uses Homing Mode (HM) when using MC_Home. You can monitor PDO 0x6060 (Mode of Operation). When using SoftMotion Light you will see it set to 1 (PP) for a MC_MoveAbsolute_SML and MC_MoveRelative_SML and to 3 (PV) for MC_MoveVelocity_SML and to 6 (HM) for MC_Home_SML. When using the SoftMotion instructions, it will pretty much always be set to 8 (CSP) except when using MC_Home, then it will be set to 6 (HM).
Last updated: 2026-02-13

Post by nz-dave on Custom library, ethernet/ip adaptor CODESYS Forge talk (Post)
Im Putting alot of my custom functions blocks into a library I have a EthernetIP VSD FB that i would like to get Status from the adaptor. EthernetIP_remote_adaptor.estate is one what i want to get. so anyone know how to point that to my function block? when i use the block i just want to have an input "Drive" that would point to the adaptor. like in softmotion when you just put the axis name in the FB to point the FB to a certain axis. Hope that makes sense, cheers
Last updated: 2025-05-21

Post by jickisticki on Witch library? CODESYS Forge talk (Post)
Crafting my Fellowship Personal Statement was like weaving the threads of my aspirations into a tapestry of words. Each sentence became a brushstroke, painting a vivid portrait of my journey and ambitions. Beyond being just a document, it became a mirror reflecting the depth of my experiences. Like a conductor guiding an orchestra, my personal statement was composed to resonate with my unique voice. In the realm of specialized opportunities, this statement serves as a compass, guiding me toward the next chapter of my professional growth. With each word, I felt the guidance of mentors shaping my story into an eloquent narrative.
Last updated: 2023-08-17

Post by timvh on Is it possible to use debug functions such as Step Execution while the PLC ladder is in Running? CODESYS Forge talk (Post)
Yes, it is possible to set breakpoints and use step into / step over (also in Ladder diagram). Yes, the PLC will actually stop, so be carefull with this. How a PLC works is that at the start of the execution of the Task, the Inputs are read, then the code is being executed and then the outputs are written. So if you set a breakpoint, you will not see your analog inputs changing, because the task cycle is interrupted and the inputs and outputs are not refreshed. For detailed information, see: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_using_breakpoints.html
Last updated: 2024-01-16

Post by micik on How to generate an "ENI" file CODESYS Forge talk (Post)
That really depends on this third party software you want to use. It is possible that .xml file generated with "Generate EtherCAT XML" will not be recognized as valid ENI file. Anyway, "Generate EtherCAT XML" command is not available through standard menus and needs to be added via Tools->Customize and then Add Command. You'll find it under "Devices" section. If you provide more info, we might be able to help you further.
Last updated: 2024-08-09

Post by yannickasselin on MQTT QoS 1 & 2 CODESYS Forge talk (Post)
Using Wireshark, I can see that the broker sends the QoS 1 or 2 messages when Codesys MQTT client reconnects but they are just discarded and not acknowledged by Codesys MQTT Client. So the broker holds on to them and tries to send them back to Codesys every time the client reconnects but they are always discarded by Codesys. There really seems to be an issue with QoS 1 & 2 in Codesys. It really does not behaves like it should.
Last updated: 2024-10-31

Post by kleeswi on SysFileOpen does not work after update to V3.5 SP19 Patch 5 CODESYS Forge talk (Post)
I use the function SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_WRITE, pErrorFileOpen); to open and write a file. Since the update from Codesys V3.5 SP17 to V3.5 SP19 Patch 5 it does not work anymore. I first had SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_APPEND_PLUS, pErrorFileOpen); in both versions. hFile_Test is a pointer to byte. It gives an exceptional error when dereferencing the hFile_Test pointer. Edit: I use Codesys on a Raspberry pi
Last updated: 2024-02-19

Post by baltzer on ICertificateVerifier.VerifyCertificate doesn't appear to override an ERR_CERT_HAS_EXPIRED rejection in TCP_Client.Upgrade() CODESYS Forge talk (Post)
Follow-up: working workaround found (routing TLS outside CODESYS) For anyone finding this thread later with the same problem (a third-party device presenting a self-signed and/or expired certificate that ICertificateVerifier/udiVerificationMode won't let you connect through) - we never got a working fix within NBS itself, but found a practical workaround worth sharing. Approach: run a local TLS-terminating proxy on the same host as the CODESYS runtime, and have CODESYS talk plain, unencrypted TCP to it instead of connecting to the remote device directly over TLS: CODESYS --plain TCP--> 127.0.0.1:<port> --stunnel/TLS--> <remote device>:<port> We used stunnel (client mode), with certificate verification explicitly disabled at that layer (verifyChain = no, verifyPeer = no) - a simple, well-documented one-line option, unlike anything we could get working inside NBS. Running it as a systemd service with Restart=always means it survives reboots and recovers automatically if the proxy or the remote device drops. On the CODESYS side, this required no changes beyond pointing TCP_Client at 127.0.0.1 instead of the device's real IP, and removing the TLSContext/ICertificateVerifier code entirely - the rest of our application-layer logic (framing, checksums, etc.) was completely unaffected, since none of that ever depended on where the TLS termination happened. Confirmed working end-to-end against a real device with an expired self-signed certificate, running on CODESYS Control for Raspberry Pi SL (Linux). We haven't yet set this up on Windows - stunnel does have Windows builds available, so the same general approach should be possible there too, but that combination isn't tested or confirmed by us at this point. Caveat: this only makes sense when the proxy and the CODESYS runtime are on the same trusted host (in our case, both on the same Raspberry Pi) - don't expose the proxy's plaintext side on a reachable network interface, since that would create an unauthenticated plaintext path to the device. The original question - whether there's a supported way to override an ERR_CERT_HAS_EXPIRED/self-signed rejection from within NBS's own TLSContext/ICertificateVerifier - remains open as far as we know. Still happy to hear from anyone who's solved that particular piece, since the workaround above is a practical detour rather than an actual answer to the original question.
Last updated: 2026-08-06

Post by vformanek on irq-set piority is not working in plc-shell CODESYS Forge talk (Post)
Hello, I am currently having issues on CODESYS Control for linux SL with DTH expiring. I have followed several tutorials of creating a proper RT linux. Then I further configured the linux based on this tutorial: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_performance_optimization.html Currently I am getting DHT expires in the communication and I am trying to increase of the priority of the network task which manages the PROFINET network adapter. I am following this tutorial: https://content.helpme-codesys.com/en/CODESYS%20PROFINET/_pnio_trouble_connection_failure.html But the irq-set is not changing the priority. See the image bellow....
Last updated: 2024-01-05

Post by mainak on Opaque NodeId in the OPC UA server CODESYS Forge talk (Post)
Hello all, I am using the OPC UA server with my custom information model. I have used the communication manager to add my information model under my application and created instances from OPC UA types. I see that the created instances in the OPC UA server has some opaque nodeid (attached screenshot) and I want to change that. Therefore I have the following questions: 1. Is there a way to configure the NodeIds of instances in the OPC UA server? I tried to edit it using the UaExpert client but got error "BadNotWriteable". is it possible to configure it somewhere so that the nodeids can be changed using an external client? 2. Is there a way to define the rule for creating instance nodeids within the codesys IDE? 3. Is it possible to create the instances before e.g. using a modelling tool like UaModeler and import them as part of the information model and use them later? Using the communication manager, I can only create instances from types. I couldn't find a way to map my existing instances to plc tags from my application. It would be nice if someone could help me with these issues. Thanks in advance. :)
Last updated: 2024-10-19

Post by atone on Change IO-Link Device Interface connected to a Profinet-Slave at Runtime CODESYS Forge talk (Post)
OK, I figured out that I can simply define all the sensors as 16 bytes IN/OUT, even if they are not all used. EDIT: The negative effect is that each bit is taken into account as an I/O for the license, even if not used.
Last updated: 2025-04-28

Post by andrej on Creating, using an external Function. CODESYS Forge talk (Post)
One step closer Hello finally the SoftPlc starts to load the dll on start up, however it is not successfull. I create a new minimal example Lib_XMATH.dll. Could please give me a hint, why the dll is not succesully loaded yet. Inputs would be highly appreciated. Many thanks.
Last updated: 2025-04-30