Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
Hi Duvan, You could make this in 1 single object (FB), Indeed don't use a function for this beacuse you need some memory to keep the old value. For i := 0 TO 200 BY 1 DO //Check if the value has been changed IF Old_Value[i] <> Value[i] THEN //Set the trigger to TRUE Trigger[i] := TRUE; Old_Value[i] := Value[i]; END_IF END_FOR If you define the Value array as an In_Out and the Trigger as an In_Out you arn't claiming any aditional memory to your system. You ofcourse then need to add some code arround it that does something with the trigger and writes it back to FALSE again. If you want more flexability you also could use pointers instead of using the IN_OUT FOR i := 0 TO 200 BY 1 DO address := address_Input + i * SIZEOF(*Put type here); IF Address^ <> Old_Value[i] THEN Trigger[i] := TRUE; Old_Value[i] := Address^; END_IF END_FOR
Last updated: 2024-04-02
Post by mxj262 on FB having single input but initialized with Array
CODESYS Forge
talk
(Post)
I am adding elements of an ARRAY using pointer to access each element inside a FOR loop and the FOR loop does not stop! What is the right way to use pointers in such case?? I have another loop that is not using pointer and it stops but the loop using pointer keep on adding. METHOD FB_Init: BOOL VAR_INPUT bInitRetains: BOOL; // TRUE: the retain variables are initialized (reset warm / reset cold) bInCopyCode: BOOL; // TRUE: the instance will be copied to the copy code afterward (online change) END_VAR VAR_IN_OUT // basically REFERENCE TO window_buffer: ARRAY [*] OF INT; // array of any size END_VAR THIS^.windowPtr := ADR(window_buffer[0]); THIS^.windowSize := UPPER_BOUND(window_buffer, 1) - LOWER_BOUND(window_buffer, 1) + 1; FUNCTION_BLOCK FB500 VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR windowPtr: POINTER TO INT; windowSize: DINT; currentIndex: UINT; element1:INT; element2:INT; i:INT; j:INT; sum:DINT:=0; END_VAR element1:=windowPtr[0]; // read the first element of the Array dynamic memorry element2:=windowPtr[1]; FOR i:=0 TO (TO_INT(windowSize-1)) BY 1 DO // this loop does not stop Sum:=sum + windowPtr[i]; END_FOR FOR j:=0 TO 5 BY 1 DO // this loop stops j:=j+1; END_FOR https://ibb.co/k3DhkZT
Last updated: 2024-05-06
Post by paro on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
Hi, Problem in your code is that you are not calling the ClientFb cyclic. Please look at the Example from CODESYS: https://forge.codesys.com/prj/codesys-example/modbus/home/Home/ Your code works if the client fb is called cyclic! IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=Ethernet.IPAddress, uiPort:=502); // configure clientSerial clientSerial(iPort:=SysCom.SYS_COMPORT2, dwBaudRate:=SysCom.SYS_BR_115200, byDataBits:=8, eParity:=SysCom.SYS_EVENPARITY, eStopBits:=SysCom.SYS_ONESTOPBIT, eRtuAscii:=ModbusFB.RtuAscii.RTU); // configure clientRequestReadCoils_1 clientRequestReadCoils_1(rClient:=clientTcp, uiUnitId:=42, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestWriteSingleRegister clientRequestWriteSingleRegister(rClient:=clientTcp, uiUnitId:=43, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadCoils_2 clientRequestReadCoils_2(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); END_IF // call the client FB's clientTcp(); clientSerial(); // call client request FB's clientRequestReadCoils_1(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_1[0])); // for more details see Example_TCP, especially ClientRequest control (xExecute, xDone, xError). IF clientRequestReadCoils_1.xDone THEN // get data from aDataCoils_1 ... END_IF clientRequestWriteSingleRegister(rClient:=clientTcp, xExecute:=TRUE, uiItem:=3, uiValue:=123); clientRequestReadCoils_2(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_2[0])); clientRequestReadInputRegisters(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=16, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-29
Post by timvh on How to implement an interface (IElement)?
CODESYS Forge
talk
(Post)
See: https://forge.codesys.com/prj/codesys-example/element-collect/home/Home/ This contains an application "OnlineChangeSafeLinkedListExample". What you should do is create a new interface which has your "Priority" property. Then your FB should extend the base element function block and implement your own interface: E.g. FUNCTION_BLOCK MyElement EXTENDS COL.LinkedListElementBase IMPLEMENTS I_MyInterface Then the __QUERYINTERFACE does the magic to check if your "element" also implements your interface. Something like this: // Compares this element with itfElement. // Returns 0 if the elements are equal, < 0 if the element is less than itfElement, // > 0 if the element is greater than itfElement. // This method will be called from sorted collections (e.g. |COL.SortedList|) to sort the elements. // IMPORTANT: The underlying value to be compared with MUST NOT be changed during the lifecycle of the object. METHOD ElementCompareTo : INT VAR_INPUT (* The element to compare*) itfElement : COL.IElement; END_VAR VAR itfIntElement : I_MyInterface; xResult : BOOL; END_VAR // We use integer iInt1 for sorting. xResult := __QUERYINTERFACE(itfElement, itfIntElement); IF xResult THEN IF iInt1 < itfIntElement.Priority THEN ElementCompareTo := -1; ELSIF iInt1 > itfIntElement.Priority THEN ElementCompareTo := 1; ELSE ElementCompareTo := 0; END_IF ELSE ElementCompareTo := -1; END_IF
Last updated: 2024-07-22
Post by mecmag on gear over gear (2 masters,1 slave) - how to do it?
CODESYS Forge
talk
(Post)
Hello, i need to create an application that uses 2 masters, with 2 different ratios, and it outputs in one single slave. I explain better: Imagine axis A, B and C. -Axis A is the slave. -Axis B is master of A, with a specific ratio. -Axis C is master of A, with a specific ratio. the result motion from B and C should be executed by A, proportionally in position and ratios from B and C. With standard softmotion libraries (MC_...) it is not possible (i couldn't) because it is allowed only one master with its ratio. I have made a similiar application in past, using MoveOverGear in order to synch gears before engage. Instead this time, i need to do a gear over gear application, using 2 different masters. The position have to be the sum of both masters (considering their ratios). Any clue about how to do it? Or were to find some FB that can do it?
Last updated: 2024-08-16
Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
I have found a very interesting solution using: IoConfigTaskMap IoConfigConnectorMap IoConfigChannelMap The first is the list of IO tasks. The second is the connector for each IO module in the IOMap. The third is the individual input or output on the IOMap. One of the properties of the connector is another pointer to a connector, which corresponds with the connector of the EtherCAT slave. Through this information, it is possible to understand to which EtherCAT slave an IO connectormap corresponds. I am attaching an FB that allows for the construction of an IO map and finding the pointer to the actual IOs in the IOMap based on the bitoffset. FUNCTION_BLOCK IOExplorer VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR inputChannels: COL.LinkedList; outputChannels: COL.LinkedList; ulintFactory: COL.UlintElementFactory; END_VAR METHOD inputAtBitOffsetOfConnector : POINTER TO BYTE VAR_INPUT conn: POINTER TO IoConfigConnectorMap; bitOffset: UDINT; END_VAR VAR it: COL.LinkedListIterator; itf: COL.IElement; elem: COL.iUlintElement; channelInfo: POINTER TO ADVChannelInfo; bitOffsetR: UDINT; END_VAR inputChannels.ElementIterator(it); WHILE it.HasNext() DO it.Next(itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} channelInfo := TO___UXINT(elem.UlintValue); {warning restire C0033} IF channelInfo^.connectorField = conn THEN IF bitOffsetR = bitOffset THEN inputAtBitOffsetOfConnector := channelInfo^.addr; RETURN; END_IF bitOffsetR := bitOffsetR + channelInfo^.size; ELSE bitOffsetR := 0; END_IF END_WHILE inputAtBitOffsetOfConnector := 0; END_METHOD METHOD outputAtBitOffsetOfConnector : POINTER TO BYTE VAR_INPUT conn: POINTER TO IoConfigConnectorMap; bitOffset: UDINT; END_VAR VAR it: COL.LinkedListIterator; itf: COL.IElement; elem: COL.iUlintElement; channelInfo: POINTER TO ADVChannelInfo; bitOffsetR: UDINT; END_VAR outputChannels.ElementIterator(it); WHILE it.HasNext() DO it.Next(itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} channelInfo := TO___UXINT(elem.UlintValue); {warning restire C0033} IF channelInfo^.connectorField = conn THEN IF bitOffsetR = bitOffset THEN outputAtBitOffsetOfConnector := channelInfo^.addr; RETURN; END_IF bitOffsetR := bitOffsetR + channelInfo^.size; ELSE bitOffsetR := 0; END_IF END_WHILE outputAtBitOffsetOfConnector := 0; END_METHOD METHOD scanIO VAR_INPUT END_VAR VAR numTasks: DINT := IoConfig_Globals.nIoConfigTaskMapCount; tType: WORD; ioTask: POINTER TO IoConfigTaskMap; numCon: WORD; connector: POINTER TO IoConfigConnectorMap; numCh: DWORD; channelInfo: POINTER TO ADVChannelInfo; iTsk: DINT; iCon: WORD; iCh: DWORD; i: DINT; _tmpConnList: COL.IList; elem: COL.IUlintElement; itf: COL.IElement; tmpCh: POINTER TO ADVChannelInfo; lastE: DINT; e: COL.COLLECTION_ERROR; e1: Error; END_VAR VAR_INST lF: COL.ListFactory; END_VAR IF outputChannels.CountElements() > 0 OR inputChannels.CountElements() > 0 THEN RETURN; END_IF _tmpConnList := lF.CreateDynamicList(16, 16); //Iterate through all IO tasks FOR iTsk := 0 TO numTasks - 1 DO ioTask := ADR(IoConfig_Globals.pIoConfigTaskMap[iTsk]); //Store the type of the task (Input or Output) tType := ioTask^.wType; numCon := ioTask^.wNumOfConnectorMap; //Iterate through all connectors of the task FOR iCon := 0 TO numCon - 1 DO connector := ADR(ioTask^.pConnectorMapList[iCon]); numCh := connector^.dwNumOfChannels; //Iterate through all channels of the connector FOR iCh := 0 TO numCh - 1 DO //Create a new channel info object and fill it with the address, connector and size of the channel //Connectors is address of field connector in this case like EtherCAT slave //Address is the address of the IOMap //Size is the size of channel data in bits in IOMap channelInfo := __NEW(ADVChannelInfo); channelInfo^.addr := connector^.pChannelMapList[iCh].pbyIecAddress; channelInfo^.connectorField := connector^.pConnector; channelInfo^.size := connector^.pChannelMapList[iCh].wSize; //We put the channel info a temporary ordered list //Order is based on the address of IOMap lastE := TO_DINT(_tmpConnList.CountElements()) - 1; FOR i := 0 TO lastE DO _tmpConnList.GetElementAt(udiPosition := TO_UDINT(i), itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} tmpCh := TO___UXINT(elem.UlintValue); {warning restire C0033} //If the address of the channel is smaller than the address of the channel in the list IF tmpCh^.addr > channelInfo^.addr THEN //Insert the channel in the list at the current position _tmpConnList.InsertElementAt(TO_UDINT(i), ulintFactory.Create(TO_ULINT(channelInfo))); //Clear the channel info pointer channelInfo := 0; //Exit the loop i := lastE + 1; END_IF END_FOR //If the channel info is not 0, it means that the channel was not inserted in the list IF channelInfo <> 0 THEN //Add the channel to the end of the list elem := ulintFactory.Create(TO_ULINT(channelInfo)); _tmpConnList.AddElement(elem); END_IF END_FOR //Iterate temporary list and add the channels to the input or output list lastE := TO_DINT(_tmpConnList.CountElements()) - 1; FOR i := 0 TO lastE DO _tmpConnList.GetElementAt(udiPosition := TO_UDINT(i), itfElement => itf); __QUERYINTERFACE(itf, elem); {warning disable C0033} tmpCh := TO___UXINT(elem.UlintValue); {warning restire C0033} //If type is input, add the channel to the input list IF tType = TaskMapTypes.TMT_INPUTS THEN e := inputChannels.AddElement(ulintFactory.Create(TO_ULINT(tmpCh))); //If type is output, add the channel to the output list ELSIF tType = TaskMapTypes.TMT_OUTPUTS THEN e := outputChannels.AddElement(ulintFactory.Create(TO_ULINT(tmpCh))); ELSE __DELETE(tmpCh); END_IF END_FOR //Clear the temporary list _tmpConnList.RemoveAllElements(); END_FOR END_FOR END_METHOD
Last updated: 2024-02-13
Post by t-probst on Strong Private Key Protection for Encryption Certificates
CODESYS Forge
talk
(Post)
Hello, We are trying to implement an automated method of adding of a certificate and private key to the Windows certificate store for encrypting CODESYS projects. We want to do this so that users do not have to deal with details of certificates at all and to prevent user error. We are keen on enforcing strong private key protection since it ensures that a password is required for the certificate to be used to decrypt a CODESYS project. When we add a certificate to the certificate store and enable strong key protection using the Microsoft Management Console Certificates snap-in, it works as expected. However, through this method the user may mistakenly not enable strong private key protection. For the certificates we create programmatically (using Microsoft’s Cryptography Next Generation API in .Net 7) bag attributes are added to the certificate and key by the API. These bag attributes are as follows: Bag Attributes localKeyID: 01 00 00 00 subject=C = xx, ST = xxx, O = xxx, OU = xxx, CN = xxx issuer=C = xx, ST = xxx, L = xxx, O = xxx, OU = xxx, CN = xxx -----BEGIN CERTIFICATE----- [encoded certificate] -----END CERTIFICATE----- After using this certificate with bag attributes to encrypt a CODESYS project, it can’t be decrypted, showing this error: "The specified project could not be loaded. Possible reasons might be: - The project file is corrupted or invalid - The project has been saved with a newer version of the programming system. If this is the case, you can open the project in the corresponding version. Choose "Save as..." with the appropriate storage version, and retry again. - You may not have the necessary permissions to lad the project" We know that the bag attributes are causing the issue because if we manually edit the certificate file to remove them before using the certificate to encrypt a project, the project can be decrypted as expected. However, we are unable to automatically enforce strong key protection using this method. Here is a link to a StackOverFlow question that we have posted recently for this issue: https://stackoverflow.com/questions/76922355/enforcing-strong-private-key-protection-for-x509certificate2-objects-in-net-mod Any help is greatly appreciated.
Last updated: 2023-08-22
Post by alex-at-xana on EThercat Dynamic configuration
CODESYS Forge
talk
(Post)
Hi Everyone, For a fast monitoring system I am using Ethercat oversampling and timestamping inputs. As the customers has a lot of different configurations out in the field, we went for a dynamic Ethercat configuration. Already got the whole detection chain working but now I am stuck since two days in debugging the configuration. Here are my quesitons: I extended the dynamic config example for the EL3632 16#0E303052: //EL3632 pSlave^.SetDCSettings(TRUE,TRUE,80,80,TRUE,4000,0,0); pSlave^.AddSyncManager(16#1000,128,16#26,TRUE,3); pSlave^.AddSyncManager(16#1080,128,16#22,TRUE,2); pSlave^.AddSyncManager(16#1100,0,16#4,TRUE,1); pSlave^.AddSyncManager(16#1110,214,16#20,TRUE,0); pSlave^.AddFMMU(0,214,0,7,16#1110,0,1,1); pSlave^.AddFMMU(0,1,0,0,16#80D,0,1,1); xKnown := TRUE; This leads to a PLL Error for these devices. I double and triple checked the configuraton, but cannot find the issue. There seems to be one difference: the config dialog creates a startup parameter: 16#10F3:16#05, Name: Command_0, Value:0. Bitlen: 16, Stop on fault: false, jumpt at fault: false: next line: 0 a) I do not find information on how to set this in my code. Can you help me there? b) Without trying to set the value, I get a PLL error for these devices in the master log. Is the config wrong? c) Do I need to set the Master to Autoconfigure or Manual? I used autoconfigure for my tests. The stack creates input data addresses for the slaves input data range (pSlaves[i].InputData) which are different from those created when I use the Engineering tools dialogs to configure Ethercat. Specifically, the addresses seem to be aligned at 16 byte boundaries when they are created using the engineering tool, but may appear at uneven addresses when I use the script in dynamic config. I did not try to access ULINT at uneven addresses yet, but I am suspecting this may be a problem. Do I need to manually align the addresses ? Any help is appreciated...
Last updated: 2024-09-10
Post by manuknecht on Opening a Dialog on a specific Client from ST
CODESYS Forge
talk
(Post)
I managed to find a solution that seems to work reliably. As the VU.Globals.CurrentClient-filter accesses the CURRENTCLIENTID or at least a similar, internal variable it can only be used if called from a certain client (e.g. from a button in a visualization). My solution works by implementing a new client filter that compares the client ID of all clients to the ID of the last client that was used. The variable containing the data of the last client is defined as: G_LastClient : VU.IVisualizationClient; // Copy of last client that detected click This last client is then updated every time a button is pressed using the Execute ST-Code input configuration of the button: G_LastClient := VU.PublicVariables.Clients.Current; Next, I created a function block that implements the client filter interface as so: FUNCTION_BLOCK FB_LastClientFilter IMPLEMENTS VU.IVisualizationClientFilter VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR END_VAR Then i added a method to the FB called IsAccepted which is used to filter out the client. When creating the method, it should automatically be filled with the according variable declaration, as it is defined in the interface: (* For every client can be desided, if it is accepted. ``TRUE``: Client is accepted*) METHOD IsAccepted : BOOL VAR_INPUT (* The client, to check*) itfClient : VU.IVisualizationClient; END_VAR Now the client can be compared to the last used client as such: // check if clientID corresponds to clientID of last recorderd client IF itfCLient.ClientId = G_LastClient.ClientId THEN IsAccepted := TRUE; ELSE IsAccepted := FALSE; END_IF To make use of this custom client filter, initialize a variable with the client filter: LastClient : FB_LastClientFilter; // Client filter to find last used client Then use this client filter when opening or closing a dialog from ST: fbOpenMyDialog(itfClientFilter:=LastClient,xExecute:=TRUE,sDialogName:='VIS_MyDialog_DLG');
Last updated: 2023-09-27
Post by adamrobotic on llcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008
CODESYS Forge
talk
(Post)
Hi All, Recently I have been experiencing a issue in CodeSys SP16 Patch 3, with a exception which comes up after I have made several online changes. callcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008, after I experience this fault then I receive a error message for any subsequent online change "online change failed, no task gap within 10000ms". To recover either the controller needs a orgin reset, which will allow online edits thereafter until falling back into the loop. I am using a TURCK TX707 product which is controlling robot trajectory, We have hard coded the coordinate data rather than using persistence variables so hence the need to do online changes consistently. I have read on the forum other people have experienced similar issue with the online task gap, but I have no task which have same priority and also monitored the CPU usage and have not seen it go above 13%. Anyones help would be much appreciated, thankyou.
Last updated: 2023-08-18
Post by manuknecht on Persistence Manager does not save alphabetically first value
CODESYS Forge
talk
(Post)
After some more digging I realized that I get an error on the PLC Logger saying PersistenceChannel: 150 (invalid type in data: SimpleLibrary). I suppose the issue could be found in the ConfigData, which is automatically generated and which looks like this: 1 9##83 SimpleLibrary#GVL.aMoreZeros.[1]#0#64512#15#0 <[2]#0#64520#15#0 <[3]#0#64528#15#0 <[4]#0#64536#15#0 <#0#64544#15#0 <[6]#0#64552#15#0 <<lrVar#0#64560#15#0 <strVar#0#64428#16#80 <uiDummy#0#64370#11#0 Perhaps the fact that the variable is stored within a library confused the compiler? I tried changing the PersistenceChannel parameters to xCompressTags := FALSE which changed the entry in the data file from _xCompressTags BOOL:TRUE _xCompressTags BOOL:FALSE but the actual content of the data file and also the config data did not change.
Last updated: 2023-10-17
Post by forest on SM Drive license error
CODESYS Forge
talk
(Post)
Hi, when it comes about license, I used INVTmatic Studio, which uses Codesys, for programming INVT plc. I bought Codesys Modbus license, it was not expensive, and then realised that INVT didn't have License Manager option (greyed out in program) which is needed for using of Codesys License. I contacted support from INVT, but developers told me that option is still not available. So depending on environment for programming Codesys, you can or not use Modbus license. Good thing about this version of Modbus TCP it works both direction. I could send commands and receive feedbacks from drive. But communication stops after 30 mins. So I used simple version of ethernet modbus which is somewhere in INVT or Condesys library (I can check tomorrow) which works only one way. I could send cmd to drive, and control it, but didn't have any feedback, like some readings back in PLC. which is bad, but at least I could start it and it didn't fail after 30 mins.
Last updated: 2024-01-10
Post by wbj0t on System libs and I/O Drivers
CODESYS Forge
talk
(Post)
Hi everyone. My question about: where I can learn (read or watch) an info about codesys workflow through the system IO libs? I want to know how to implement I/O drivers by my self. In the system libs I see many interfaces, methods etc... But there is no explanation about them, just names of methods and fields of the FBs. I know about this page: https://forge.codesys.com/drv/io-drivers/doc/Generic/ There is so BIG the device description file and not so clear explaining of the attributes and elements, also some elements or attributes missed at it all. Yes, there are code examples on this page, but, so shortly and, for example, code about Modbus drivers is absent. And even if I try to add the IoDrvFB with lib, I get and error, something like: "failed to load IoDrvFB driver". And what about the book of codesys that written by Gary Pratt? Is there information about system libs and drivers in this book more clearly? Thank you :)
Last updated: 2024-02-02
Post by fredsta on Unable to load dynamic modules (Download failed: Application=Application)
CODESYS Forge
talk
(Post)
Hey there, I am currently trying to find a good solution for the communication between CODESYS Control on Raspberry Pi and "the rest of the world", i. e. the things apart from CODESYS on my linux. My first approach was to use the c-integration. So I created a lib, defined extern fbs, compiled the code on my Pi using the SDK and put the .so into my lib project. When I try to log into the Pi and load the program, I get the error message which you can see in the attached picture. "Die dynamischen Module der C-Integration konnten nicht auf das Laufzeitsystem geladen werden" is german and means roughly "the modules from the c-integration could not be loaded onto the runtime system." Is this normal? Am I doing something wrong? I will have a look at the unix domain socket thing next, as I am still in the process of finding the best solution for the communication.
Last updated: 2024-02-15
Post by mtho on JSON Utilities - JSON file written with invalid structure
CODESYS Forge
talk
(Post)
I'm using the JSON Utilities SL library to write configurations in my program to a file. I'm generating the JSON data using the builder function block and all appears to work correctly. When I write the jsondata to file, I'm finding that some of the JSON elements are not being written in the right location in the file. Rather than writing they keys under the parent object, they get written outside the root JSON object at the end of the file. If I then try to read the file back into the program, I get an invalid_structure error. I don't get any errors when populating the JSON data or when writing the file. I attached an example of the JSON writer output. The problems begin with key P200. Each P200 should go under MBR1 through MBR3. Among the rest of the keys, they are supposed to be under different parent objects. I am using default values for wsLineBreak and encoding.
Last updated: 2024-03-06
Post by manuknecht on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hello all I am using an AxisGroup with the Gantry2 Kinematics to move a 2D-Gantry system. When creating the AxisGroup, the SoftMotion_PlanningTask is created automatically with a cycle time of 2 ms in my case. I realized that the maximum cycle time of this task can spike to very high values (up to 60 ms) at lower speeds of the motion, leading to synchronization issues and errors on the axes. The same behaviour - though not as drastic - can be observed with virtual axes too. Is this behaviour intended or to be expected? Can the cycle time or type of the SoftMotion_PlanningTask be changed to prevent these errors? Or is there another fix for this issue? I tried changing the cycle type to Freewheeling, which solved the synchronization issues, but caused an error on the AxisGroup after a while, reading SMC_CP_QUEUE_UNDERRUN. Thanks in advance and best regards Manuel
Last updated: 2024-03-07
Post by umdee on Error when monitoring LAD programs
CODESYS Forge
talk
(Post)
System Information from the computer being used: OS Name Microsoft Windows 11 Pro Version 10.0.22631 Build 22631 Other OS Description Not Available OS Manufacturer Microsoft Corporation System Manufacturer Dell Inc. System Model Latitude 5500 System Type x64-based PC System SKU 08B9 Processor Intel(R) Core(TM) i7-8665U CPU @ 1.90GHz, 2112 Mhz, 4 Core(s), 8 Logical Processor(s) BIOS Version/Date Dell Inc. 1.3.11, 6/11/2019 SMBIOS Version 3.2 Embedded Controller Version 255.255 BIOS Mode UEFI BaseBoard Manufacturer Dell Inc. BaseBoard Product 0M14W7 BaseBoard Version A00 Platform Role Mobile Secure Boot State On PCR7 Configuration Elevation Required to View Windows Directory C:\WINDOWS System Directory C:\WINDOWS\system32 Boot Device \Device\HarddiskVolume1 Locale United States Hardware Abstraction Layer Version = "10.0.22621.2506" User Name CARDASSIA-IX\Engineer Time Zone Eastern Daylight Time Installed Physical Memory (RAM) 16.0 GB Total Physical Memory 15.8 GB Available Physical Memory 4.67 GB Total Virtual Memory 18.5 GB Available Virtual Memory 2.52 GB Page File Space 2.63 GB Page File C:\pagefile.sys Kernel DMA Protection Off Virtualization-based security Not enabled Windows Defender Application Control policy Enforced Windows Defender Application Control user mode policy Off Device Encryption Support Elevation Required to View Hyper-V - VM Monitor Mode Extensions Yes Hyper-V - Second Level Address Translation Extensions Yes Hyper-V - Virtualization Enabled in Firmware Yes Hyper-V - Data Execution Protection Yes
Last updated: 2024-03-19
Post by squiggleypuff on Can't Add New Version of Modbus TCP Master
CODESYS Forge
talk
(Post)
I'm having a tough time trying to get Modbus working on a Festo CPX-E PLC; it throws these pre-compiler errors as soon as I add in my Modbus TCP Master 3.5.12.30 to my project: I'm confused about the C0046 error, as I have IODrvModbusTCP 4.3.0.0 Library installed. So I thought maybe I needed to use the newest Modbus TCP Master 4.3.0.0, which is in my device repository: However, whenever I go to add this underneath the Ethernet adapter (which is version 4.2.0.0), the only TCP Master version available is the old 3.5.12.30 one, even if I have Display all versions checked.: I even went so far as to delete the old version, but then there were no options to add a Modbus TCP Master under my Ethernet adapter. What needs to be done to use the newest Modbus TCP Master? Or are these pre-compiler errors unrelated and I'm missing something? Any help greatly appreciated.
Last updated: 2024-04-04
Post by william-blandon on RecipeManCommands.ReloadRecipes
CODESYS Forge
talk
(Post)
Hi Dave. Thanks for your answer. I still struggling with this. I have done everything according with the Codesys help even I have looked in detail at the example. I have double checked the recipe manager configuration and the use of all the methods. There are two methods that do not work as expected. I'm using Codesys 3.5.19.20 and recipe management 4.4.0.0 .CreateRecipe just create a recipe in the recipe definition but do not create the file. This have a walk around just giving a .ReadAndSaveRecipe afterwards. .ReloadRecipes do nothing but do not generate any error as well. After calling it I call the .GetRecipeCount and the number is always 0. When I create a new recipe (using the function block methods) then the number changes. Looks like this method is looking to the wrong directory finding nothing. I don't know if there is a missing configuration in the CODESYSControl.cfg file. I'm thinking in a walk around for this but I need to create a strings array with the recipe names as retentive and making all the management when deleting and adding recipes. Have had some one the same problem?
Last updated: 2024-05-23
Post by fajean on CODESYS control on RPi starts, shortly runs, then exits
CODESYS Forge
talk
(Post)
I have a Raspberry Pi 4 we have been using for years to run CODESYS for development purposes. I recently have had to re-install the OS (Raspberry OS lite). The only change to the default configuration is not creating the "pi" user during install. I (apparently successfully) installed the 4.10.0.0 control on the Raspberry Pi. We have licences on a dongle. I am able to start the control. systemctl status shows it as running for a little while (exactly, precisely 30 seconds as per my tests, every time), then it becomes exited. I can restart the control, and the same thing happens again. Every time. In the brief moments it is running, I can log in to the PLC. Working fast and restarting the control many times, I have been able to configure users. I have been able to download my application. I have been able to run the application, and stop on a breakpoint. I have been able to connect with the licence manager and confirm the dongle is detected and licences are listed as OK. I see nothing wrong until the service just exits. I have found nothing in the logs. It is like the runtime just terminates with no error code or message after exactly 30 seconds. Any help would be appreciated.
Last updated: 2024-06-13
Post by psychoengineer on Cannot Save CSV File on Windows Computer Using CODESYS and Control Win
CODESYS Forge
talk
(Post)
I am currently working on a project using CODESYS and Control Win on a Windows computer. I've encountered an issue where I am unable to save a CSV file. I have followed the standard procedures and used the appropriate file handling functions, but the file is not being created or saved as expected. IF xStartTest THEN sFileName := '\logs.txt'; sFileName := CONCAT(gvl.g_sMainDirectory, sFileName); sFileNameCopy := '\CAAFileCopy.txt'; sFileNameCopy := CONCAT(gvl.g_sMainDirectory, sFileNameCopy); //eWriteState := FILE_OPEN_TRIGGER; xTestDone := FALSE; xError := FALSE; xStartTest := FALSE; END_IF VAR_GLOBAL g_sMainDirectory : STRING := 'C:\LogFiles'; // file path for CSV file END_VAR Despite this, the file does not appear in the specified directory, and no error messages are being generated. I've checked the directory permissions and ensured that the path is correct. Has anyone else experienced a similar issue or have any suggestions on how to resolve this? Any help would be greatly appreciated. Thank you!
Last updated: 2024-07-04
Post by berto on Opening PDF in Web Browser in Target Visu HMI
CODESYS Forge
talk
(Post)
Hi everybody, I've been facing problems with the PDF visualization in Web Browser. I am trying to open a pdf file called 'sample.pdf' which I manually saved inside PlcLogic/visu folder. I am setting the web browser URL as: 'http://127.0.0.1:8080/sample.pdf' but I get 'refused connection'. I got a similar error trying to open https sites and I discovered that I can only open http websites. Opening 'http://de.wikipedia.org' everything works fine. I also tried to check using code whether the sample.pdf is present in the directory. Unfortunately, when I try to read directories of 'PlcLogic' I get file FILE_OPERATION_DENIED (I am using File.DirList). I would like to be able to open PDF files in web browser. Possibly to move new PDF files in the folder as my customer wants to display different pdf manuals on the hmi. Here you find some screenshots and my .project. I am using Codesys 3.5.19.70. Best regards, Berto
Last updated: 2024-07-11
Post by faceplant on CmpDynamicText unresolved references
CODESYS Forge
talk
(Post)
Hello! I am new to codesys so I am sorry if this is not the right place to ask this question. I am using codesys V3.5 SP20 Patch 1 + (64-bit) and a Groov EPIC PLC (GRV-EPIC-PR2). I am trying to build and deploy my application to the PLC, but when I log in I get 6 errors (codesys_error.png). It seems that the errors have to do with the CmpDynamicText system library which I have as version 3.5.20.0. I have tried to add CmpDynamicText to the ComponentManager section in the PLC's CODESYSControl.cfg file as described in this forum post and still hit the same error. I noticed that the library is grayed out in the library manager, which I think might be the issue. However I don't remember if it was grayed out before I encountered this issue. Please let me know if I can provide anymore info. Thank you!!!
Last updated: 2024-07-19
Post by denkihitsuji on Content update through Data URI on Web Brower on Visualization Toolbox
CODESYS Forge
talk
(Post)
Objective: I want to dynamically update the content with strings and JPEG images received from a TCP/IP socket. For this purpose, I am exploring the possibility of utilizing the Web Browser feature of the Visualization toolbox. Example: In a standard web browser, entering data:text/plain;charset=utf-8;base64,SGVsbG8gc3RyYW5nZXI= in the URL window will display "Hello stranger" on the webpage. Issue: When attempting to use this method in the Web Browser of the Visualization toolbox, the content does not display as expected. Instead, it shows the error:'Navigation to the webpage was canceled.'. Request: I seek guidance on how to resolve this issue so that the Web Browser in the Visualization toolbox correctly interprets and displays the data URI content. Alternative Solution Welcomed: Or, if it is possible to directly use Codesys Structured Text (ST) variables within an HTML page, this approach would also meet my requirements. Thank you for your attention.
Last updated: 2024-07-30
Post by mubeta on parker servo and position
CODESYS Forge
talk
(Post)
In general, drives have parameter sets to adjust behaviour in such cases: position recovery, adaptation with resistant torque, out-of-position window failure, etc. (Much depends on the type of configuration set for the axis: positioner, speed controller, torque controller, etc.). I have used that type of drive very little, in only two cases and a long time ago. To tell you what is normal is impossible. I know by reputation they are very simple objects, without too many pretensions and adjustments possible. Try running traces by monitoring actual position, motor current, torque and following error. These are the most sensible curves to understand what is going on. Maybe by fine tuning the motor tuning, the current controller or the speed controller you will get something closer to what you want. For example, from DS, the motor has a standstill torque of 3 Nm. Observe with traces whether this is effective: motor current trend. And afterwards, when you have your own accurate picture of the situation, you can also hear from the product's local support to see if you can steal a few more things from it performance-wise.