Post by dsa28 on OPC UA subscriber not operational
CODESYS Forge
talk
(Post)
Hello All, Hopefully I can get some help configuring an OPC UA subscriber in a CODESYS runtime in a Raspberry Pi 5 that tries to retrieve data from an OPC UA publisher (in this case running in a TwinCAT system). I tried to follow the steps described in the page to implement the OPC UA subscriber: https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_opcua_pubsub.html Seems that the example provided was created with version 3.5.16.0. Now with version 3.5.20.20 is not possible to open the complete project neither convert it. Anyway, after configuring all IPs and ports used in the OPC UA connection function block but the connection state always shows DISABLED. Can someone help me to do the proper configuration of the OPC UA subscriber? Many thanks in advance.
Last updated: 2024-10-22
Post by wistaro on How to use PLC_Open FBs with PROFINET servodrive (PROFIdrive layer)
CODESYS Forge
talk
(Post)
Hello, I would like to know if there is a PROFIdrive layer in CODESYS. I am already familliar with Codesys's SoftMotion on CANOpen/EtherCAT (to control PLC Open FBs), and I need the same kind of stuff for PROFINET-IO devices; In my configuration, I have a CIFX board from Hischer to enable IRT, the SoftPLC "Codesys Control RTE V3 x64", and a servo-drive from INFRANOR that implements PROFINET / PROFIdrive (with IRT) protocol. This drive works well with the Object Technology of Tia Portal, but some customers use Codesys. Do you have an idea how to do that? Thanks in advance. Regards, William ROMIGUIERES INFRANOR France
Last updated: 2024-10-29
Post by hemuv on Dialog Open
CODESYS Forge
talk
(Post)
I'm programming an HMI for a machine. I want to log all the parameter's changes (used text field for displaying and changing) for particular User levels. Created a Numpad and want to log oldvalue and Newvalue on 'ok' Button press. To retrieve the oldvalue, i check if the dialogue opened is my Numpad, Then I retrieve the dialogue interface via GetDialogInterface(ADR(myNumpad)) --> numpadData.stVariableValue which contain my oldvalue and save it locally. Problem is sometimes i retrieve the data and sometimes not. Also observed when Numpad Dialogue is Opened, VisuDlgUtil_IsDialogOpen returns False in some cycles.Attached you will find my Project. please let me know what went wrong or if there is a better approach to collect old and New Value of a textfield. Thank you.
Last updated: 2025-03-26
Post by l-lll on The plug-in is required by the current version profile but has not been installed
CODESYS Forge
talk
(Post)
Hello everyone, I meet this problem after installing Codesys SP20 Patch 5 on Windows 11 while the dialog box shows that the installation process has been successfully completed. Every time I open Codesys I get an error that says (Attached image): 'One or more issues ocurred with the current version profile. Please contact the vendor to resolve these problems. The plug-in {....} (Exactly x.x.x.x) is required by the current version profile., but has not been installed. It is highly recommended that the tools is terminated. Do you wanto to terminate now?' Can someone help me please, thanks very much!
Last updated: 2025-05-14
Post by l-lll on The plug-in is required by the current version profile but has not been installed
CODESYS Forge
talk
(Post)
Hello everyone, I meet this problem after installing Codesys SP20 Patch 5 on Windows 11 while the dialog box shows that the installation process has been successfully completed. Every time I open Codesys I get an error that says (Attached image): 'One or more issues ocurred with the current version profile. Please contact the vendor to resolve these problems. The plug-in {....} (Exactly x.x.x.x) is required by the current version profile., but has not been installed. It is highly recommended that the tools is terminated. Do you wanto to terminate now?' Can someone help me please, thanks very much!
Last updated: 2025-05-14
Post by l-lll on The plug-in is required by the current version profile but has not been installed
CODESYS Forge
talk
(Post)
Hello everyone, I meet this problem after installing Codesys SP20 Patch 5 on Windows 11 while the dialog box shows that the installation process has been successfully completed. Every time I open Codesys I get an error that says (Attached image): 'One or more issues ocurred with the current version profile. Please contact the vendor to resolve these problems. The plug-in {....} (Exactly x.x.x.x) is required by the current version profile., but has not been installed. It is highly recommended that the tools is terminated. Do you wanto to terminate now?' Can someone help me please, thanks very much!
Last updated: 2025-05-14
Post by qkkk on Device Scan
CODESYS Forge
talk
(Post)
Hello all, I have developed a custom I/O driver in CODESYS that communicates via a Unix Domain Socket. In my DeviceDescription.xml, I have set up the following: <scan supported="true"> <scanfbinstance fbname="IOScanDevice"> The goal is to allow the user to scan for connected I/O modules from the CODESYS GUI ("Scan for Devices") and automatically populate the device tree with detected submodules.</scanfbinstance></scan> The function block IOScanDevice is implemented in the driver library and added to the main device's FB instances. However, when I initiate the scan from the GUI, nothing appears to happen the function is not executed. Is there an example project or driver (open source or from CODESYS Forge) that demonstrates a working custom scan implementation?
Last updated: 2025-05-26
Post by george32 on CSV file and string manipulation.
CODESYS Forge
talk
(Post)
Dear folks, I think I have a rather simple question but I could not find the right answer to my question: I have made with Excel a CSV file where I would like to have some general data regarding my program variables. I have made an program what let me read the file. The string I am currently get is at follows: 'IP_Adres;192.168.45.12$R$NPort_number;2000$R$NCycle_time;43$R$NStart_Standard_IO;20$R$N' Now I want to split the string in multiple part, which I later would connect to the right variable. By Google and experimenting I have reached to the following code for the first part of the splitting proces: // Splitting the BOM of the string: Received_string := FileReadString; IF LEFT(STR:=New_string,3)= '' THEN Received_string_without_BOM :=RIGHT(STR:= Received_string,SIZE:= (LEN(STR:= Received_string))-3); END_IF //Splitting the remaining string in part for later declaration. WHILE index = 0 DO index_split_part := FIND(STR1:= Received_string_without_BOM,STR2:= '$R$N'); Part_of_String[index]:=LEFT(STR:=Received_string_without_BOM, SIZE:= index_split_part); index := index + 1; END_WHILE However in the splitting proces I could not understand what is really happening. I understand that the Find() function returns the first value the $R$N in the Received_string_without_BOM. This would mean that the index_split_part := 23 I|P| _ |A |d|r|e|s|;|1_|9 |2 |. |1 |6 |8 |. |4 |5 |. |1 |2 |$ |R |$ |N |P | 1|2| 3 |4 |5|6|7|0|9|10|11|12|13|14|15|16|17|18|19|20|21|22|23|24|25|26|27| So the next part is to read the first 23 characters of the Received_string_without_BOM with the LEFT() function. I expected that the outcome the following was: 'IP_Adres;192.168.45.12$'. However the outcome is: 'IP_Adres;192.168.45.12$R'. I do not understand where the R after the $ sign comes from, because its place is 24 so it would not be added to the part_of the_string[index]. If I hard coded value 24 for the size it gives me the following return: 'IP_Adres;192.168.45.12$R$N'. I would expect everything till the R but the code adds the $N also to the string. I hope someone could explain to my what I am seeing wrong in my point of view? With kind regards, George
Last updated: 2024-09-27
Post by rossanoparis on How to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server
CODESYS Forge
talk
(Post)
Hello at all I'd like to know how to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server. In the past, I tried to ask in "Forge" about this topic, but I could find neither help nor document informations about it. Reading the file "codesyscontrol.log" I see these logs OPC UA Server Started: Hostname: NTLRPICTRL01, Port: 4840 URL: opc.tcp://NTLRPICTRL01:4840 Loopbackadapter activated. **All available networkadapters are used.** Multithreading activated. 3 workers used. My controller, which is a Linux PC, has got two network cards eth0 and eth1 I whant to use the card with name "eth0" as a server for OPCUA and keep the "eth1" free for other stuffs. Is it possible ? Best regards Rossano
Last updated: 2023-08-25
Post by jari-koivuluoma on JSON_Utilities_SL JSONFileWriter error NULL_POINTER
CODESYS Forge
talk
(Post)
FB jsonFileWriter gives a NULL_POINTER error, why? JSONByteArrayWriter works fine so the JSONData FB should be fine. The device is CODESYS Control Win V3 x64 in simulation mode. Codesys version is V3.5 SP16 Patch 5 JSON_Utilities_SL version is 1.3.0.0 Src: ST_TestStruct1a; TXT: WSTRING(10000); MakeJSON : BOOL := TRUE; SrcJSONData: JSON.JSONData; jsonFileWriter : JSON.JSONFileWriter; IF MakeJSON THEN MakeJSON := FALSE; // Struct data to JSONData FB F_TestStructToJSON(ADR(Src),ADR(SrcJSONData)); // Writing to file jsonFileWriter( xExecute := TRUE, sFileName := 'c:\JSONTEST\JSON.txt', eEncoding := JSON.Encoding.UTF_16, xAsyncMode := TRUE, jsonData := SrcJSONData ); // Waiting to finish WHILE jsonFileWriter.xBusy DO ; END_WHILE // To text jsonArrayWriter( xExecute := TRUE, pwData := ADR(TXT), udiSize := SIZEOF(TXT), jsonData := SrcJSONData, xAsyncMode := FALSE, ); END_IF
Last updated: 2023-09-08
Post by ggarcia94 on CANOPEN SDO configuration
CODESYS Forge
talk
(Post)
Hello, I´m connected to two drives via CANOPEN. The connection seems to be ok. However, I´m not able to get the PDOs to work even tho they are configured as in the manual of the drives. Looking at the SDOs I´ve seen that for each PDO there is a "Disable PDO" SDO that does not exist in the manual or in the EDS file of the drives. This "Disable PDO" signal has the same Index and Subindex as another SDO used to set and enable the COB-ID of the PDO. I´m assuming this is normal but why is Codesys creating a "Disable PDO" SDO for each PDO and could that be the reason the PDOs are not working?
Last updated: 2023-09-25
Post by bahrt on Mapping GPIO and adding GPIO configurations
CODESYS Forge
talk
(Post)
Hi I am about to configure ALL GPIOs on a Raspberry Pi 3 model B V1.2. It seems that I have limited understanding of why not all the IO’s become available with the corresponding mapped IO’s – the 'dwInUse' contains mapping of the inputs from GPIO0 to GPIO27. But 'dwInputs' are only showing GPIO0 to GPIO8 and GPIO15 as available inputs. These mentioned inputs work fine You will be able to watch the limited mapped IO activity here: https://drive.google.com/file/d/1zz4PBNBfRZBF2YkiJ2VQxw6L9MBVji7R/view?usp=sharing Can you please bring your best idea on why GPIO09 to GPIO14 and GPIO16 to GPIO27 state are zero in the dwInputs register? Thanks in advance. Best regards Andreas Bahrt
Last updated: 2023-11-16
Post by bahrt on Raspberry Pi GPIO mapping
CODESYS Forge
talk
(Post)
Hi I am about to configure ALL GPIOs on a Raspberry Pi 3 model B V1.2. It seems that I have limited understanding of why not all the IO’s become available with the corresponding mapped IO’s – the 'dwInUse' contains mapping of the inputs from GPIO0 to GPIO27. But 'dwInputs' are only showing GPIO0 to GPIO8 and GPIO15 as available inputs. These mentioned inputs work fine You will be able to watch the limited mapped IO activity here: https://drive.google.com/file/d/1zz4PBNBfRZBF2YkiJ2VQxw6L9MBVji7R/view?usp=sharing Can you please bring your best idea on why GPIO09 to GPIO14 and GPIO16 to GPIO27 state are not active (at a fixed zero state) in the dwInputs register? Thanks in advance. Best regards Andreas Bahrt
Last updated: 2023-11-21
Post by budd7566 on Text size suddenly changed
CODESYS Forge
talk
(Post)
Iv been working with a Deep Sea Electronics DSE840 for about 6 months. I have a development version of my program working with a state machine and a basic gui interface. I went to implement CAN and suddenly the text on the gui on the controller is much larger than before. I could flash old versions of my project and the text was the correct size, but if i renamed the project file, the text displayed would be large. The visualization in CODESYS always shows the expected size, but not the controller. I did a fresh install of CODESYS and even a new project with only one text box, I cant get the text size on the controller to match what is displayed in codesys to match. Any advice?
Last updated: 2023-12-09
Post by dhumphries on No source code available
CODESYS Forge
talk
(Post)
Try using an Ethernet/IP scanner instead of an adapter, I'm guessing the 2 devices you're trying to communicate with are adapters, you have to have a scanner somewhere and Codesys should be a scanner. I don't know why you're getting the error, you should be able to use your Ethernet port as an EthernetIP adapter (although I've never had a reason to try,) but it's probably not what you wanted to do, unless you're connecting to another PLC that is a scanner. Good luck configuring the devices you're trying to connect to, it will be a lot easier if you have an .EDS file instead of starting with a generic module, even with an .EDS it can be tricky getting the communication working.
Last updated: 2024-02-03
Post by ewi04 on How to upload application file to remote controller (offline) ?
CODESYS Forge
talk
(Post)
Hi, I am looking for a good way to update a decice remotely. The devices are distributed worldwide and have normally no connection to the internet. The CODESYS Automation Server can't help here. So I want to update the decices via USB stick. I have written my own code* to update the files that are created with ‘Create boot application’. But sometimes strange things happen: visu elements are present, but are not found the application is no longer registered and therefore no longer starts I have not yet found out why these errors occur. Has anyone had similar problems or found a better way? Is there perhaps a CODESYS library or something else? Many thanks! *the code deletes the directories on the device and copies the new directories from the USB stick while the system is running (goes without saying)
Last updated: 2024-02-05
Post by ewi04 on How to upload application file to remote controller (offline) ?
CODESYS Forge
talk
(Post)
Thank you very much for your time and replay! Sounds like a good idea. Unfortunately, I have no other option to run the code from the running plc. So, I can’t stop any services. If anyone has the same problem, I've gotten a little closer to understanding it: Sometimes the copied files are empty after the restart. The update code checks if there are any empty files. Before I turn off the device, everything is okay. But after starting, some files are suddenly empty and that cause the problems. I don't know why this happens.
Last updated: 2024-02-16
Post by nmcc on Viewing PDF in WebBrowser Visual Element
CODESYS Forge
talk
(Post)
I am trying to show a PDF in a WebBrowser element. I have the file saved to the drive of the HMI/PLC. I am linking it in the URL parameter of the WebBrowser using the following directory link. 'http://localhost:8080/$$sdcard$$/FileName.pdf'. This allows for the program to download without any errors. When I navigate to that screen it is just a white box and nothing shows. I attempted putting the same link in the show parameter and I get a loading icon on my cursor when monitoring the HMI with my PC. Any help is appreciated. Thank you.
Last updated: 2024-02-29
Post by rost on Rezeptur speichern
CODESYS Forge
talk
(Post)
Servus beianand, eine kurze Vorstellung, da ich hier neu bin Wohne und Arbeite in Bayern seit 27 Jahren als Programmierer. Mit Codesys arbeite ich seit 4 Jahren. Für mein Projekt hab ich die einfache Rezepturverwaltung verwendet. Bis jetzt alles unproblematisch, hab aber jetzt ein wenig um- und aufgeräumt, prinzipiell aber nicht verändert. Ich kann Rezepturen mit neuem Namen speichern, wenn ich aber den gleichen Namen verwende, öffnete sich bisher ein Dialogfenster mit "File already exists..." Neu öffnet sich aber der Dialog mit kryptischen Zeichen ohne Eingabemöglichkeit und ohne das Fenster wieder schließen zu können. Dann kann ich nur noch aus und wieder einschalten. Hat jemand eine Idee?
Last updated: 2024-03-01
Post by rost on Rezeptur speichern
CODESYS Forge
talk
(Post)
Servus beianand, eine kurze Vorstellung, da ich hier neu bin Wohne und Arbeite in Bayern seit 27 Jahren als Programmierer. Mit Codesys arbeite ich seit 4 Jahren. Für mein Projekt hab ich die einfache Rezepturverwaltung verwendet. Bis jetzt alles unproblematisch, hab aber jetzt ein wenig um- und aufgeräumt, prinzipiell aber nicht verändert. Ich kann Rezepturen mit neuem Namen speichern, wenn ich aber den gleichen Namen verwende, öffnete sich bisher ein Dialogfenster mit "File already exists..." Neu öffnet sich aber der Dialog mit kryptischen Zeichen ohne Eingabemöglichkeit und ohne das Fenster wieder schließen zu können. Dann kann ich nur noch aus und wieder einschalten. Hat jemand eine Idee?
Last updated: 2024-03-01
Post by rost on Rezeptur speichern
CODESYS Forge
talk
(Post)
Servus beianand, eine kurze Vorstellung, da ich hier neu bin Wohne und Arbeite in Bayern seit 27 Jahren als Programmierer. Mit Codesys arbeite ich seit 4 Jahren. Für mein Projekt hab ich die einfache Rezepturverwaltung verwendet. Bis jetzt alles unproblematisch, hab aber jetzt ein wenig um- und aufgeräumt, prinzipiell aber nicht verändert. Ich kann Rezepturen mit neuem Namen speichern, wenn ich aber den gleichen Namen verwende, öffnete sich bisher ein Dialogfenster mit "File already exists..." Neu öffnet sich aber der Dialog mit kryptischen Zeichen ohne Eingabemöglichkeit und ohne das Fenster wieder schließen zu können. Dann kann ich nur noch aus und wieder einschalten. Hat jemand eine Idee?
Last updated: 2024-03-01
Post by dhumphries on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
Does the device have a green icon next to it when the PLC is running? If not you have some kind of communication problem, wireshark may be picking up some data but the scanner may not be configured correctly to receive the data. Check the T>O and O>T bytes and make sure they match on both the scanner and adapter. I've had very little success loading a .eds file and having the configuration work without some manual configuration. If you have a green icon, have you enabled the device to always update variables?
Last updated: 2024-03-02
Post by eschwellinger on Zielsystem stimmt nicht mit dem verbundenen Gerät überein
CODESYS Forge
talk
(Post)
na ja es gibt halt einfach die Möglichkeiten: 1. Man installiert Raspberry PI OS 32Bit -> dann geht PI SL und PI MC Multicore als Target 2. Man installiert Raspberry PI OS 64Bit dann muss es PI64Bit sein falls der Übersetzungsfehler nicht in einer Bibliothek ist (die du vielleicht nicht ändern kannst) https://faq.codesys.com/pages/viewpage.action?pageId=128253958 Hier der Hinweis was man tun muss das dein IEC Code für 32Bit als auch 64Bit Targets funktioniert Also entweder zurück auf Raspberry PI OS 32 Bit: nur zur Info noch was im Config file steht für welche Plattform/Produkt [CmpRasPi] Architecture=aarch64 (-> 64Bit PI) oder Architecture=armv7l (-> PI MC Multicore) oder Architecture=armv6l (-> PI SL Single Core)
Last updated: 2024-03-11
Post by esave on Stepper Drive with Ethercat
CODESYS Forge
talk
(Post)
Hello everybody I am new into Codesys. I have a stepper driver (EM3E-556E) from Leadshine. I want to controll the stepper driver via EtherCat to a ST programm but I dont have any function block or anything that i can use. I only have the XML-File wich I loaded. With it I implemented the drive as a Ethercat slave and now I see these variables. (See picture) I dont know how to controll the stepper drive. And the manufacturer doesnt provide support for me. Can anybody help me or atleast tell me how they would do it?
Last updated: 2024-03-14
Post by bschraud on Unerwünschte Username- und Passwortabfrage im Browserfenster
CODESYS Forge
talk
(Post)
Hallo, die Option CallVisuServicesDirectly=1 verändert das Verhalten leider nicht. In Codesys gibt es noch in den Einstellungen der Webvisu den Eintrag unter Login-Visualisierung. Das Löschen dieses Eintrages ergibt aber auch keine Änderung. Evtl. wird bei der neuen Codesys Version für die Webvisu eine https Verbindung vorausgesetzt. Zu dem Thema bin ich im Thread https://forge.codesys.com/forge/talk/Visualization/thread/5767230df2/ auf die Beschreibung im Installationsverzeichnis unter file:///C:/Program%20Files/CODESYS%203.5.20.0/GatewayPLC/Documentation/WebServerSSL_de.pdf gestoßen. Allerdings gibt es dort Diskrepanzen zwischen der Verzeichnisstruktur auf meinem Gerät und in der Beschreibung. Also werde ich in dieser Richtung weiterforschen. Vielleicht hat noch jemand einen Tip, wie die Webvisu schnell auf https umgestellt werden kann. Vielen Dank!
Last updated: 2024-04-10