Post by buczekj on About CPU Loading CODESYS Forge talk (Post)
This is a phenomenon that I have seen myself and with others. Texas instruments wrote an application note with this same issue. They noted with Codesys 3.5.19.10, that selecting CPU 1 as the EtherCAT task showed CPU spiking improvements over the performance of cores 0, 2, and 3. It appears to be linked to EtherCAT, are you configuring for use with distributed clocks? If so, I recommend choosing the 'Based on Input Reference' option. I have found it to reduce the CPU usage spike maximum slightly (see attached). See link to TI (also attached in case link breaks) https://www.ti.com/lit/an/spradh0/spradh0.pdf?ts=1723546111357
Last updated: 2025-07-01

Post by struccc on Release SP20 - Changes in behaviour? CODESYS Forge talk (Post)
Dear all, I've just started to migrate some of my ancient projects to SP20. There is one strange error (?) I have noticed so far. In a method call, depending on the circumstances I would like to return reference to an object, or an invalid reference: METHOD Add_EVT_OUT : REFERENCE TO FB_MSG VAR END_VAR IF __ISVALIDREF(refMSG_Entry) THEN Add_EVT_OUT REF= MANAGER.AddMsg_EVT_OUT( refMSG_Entry, _Get_EVT_Message(MSG_EVENT.OUT), _Get_EVT_AddCode(MSG_EVENT.OUT) )^; ELSE Add_EVT_OUT := 0; END_IF So far setting a reference variable to 0, did this. But now, the expression Add_EVT_OUT := 0; gives an error: [ERROR] DB_WTP_370: Add_EVT_ACK MSG_TRIGGER_EXT: C0032: Cannot convert type 'BIT' to type 'REFERENCE TO FB_MSG' Naturally... I can write: Add_EVT_OUT := DWORD#0; But is this the correct way? Is there any constant I could use instead, like "NULL"? Or this is totally wrong and to be avoided?
Last updated: 2024-03-24

Post by maxkemmeren on PFC200 (750-8214) high linux load average, but seems random. Possibly EtherCAT related. CODESYS Forge talk (Post)
Have you received any feedback or found any solutions to the load problem. We are running into similar issues, even without codesys running the load avarage is above 1 meaning that it is to busy already without plc code running. Hope you might have some more insight.
Last updated: 2024-07-11

Post by pafarrell on EtherCAT quick start for advanced programmers CODESYS Forge talk (Post)
It would be great if there was a thread that had some quick-start links for basic how-to. But one that advanced programmers can jump into. I found this video playlist by SoftMotion-Black, which was very, very helpful: https://www.youtube.com/playlist?list=PLkc8m2OD0r9xJyfTiCBb1vuU_d2yBhjZ_ This person has some other great vids like creating your own custom library, which is awesome for OEMS.
Last updated: 2025-05-14

Post by selim on LS ix7nh Servo drive with Codesys CODESYS Forge talk (Post)
Hello Mr./Ms., I do not find the ES driver in codesys. The setup of the project is "Rasberry PI3B>Ls ethercat I/O aps-ec-dt32k> LS ix7nh Servo drive>apmc-fbl04amk LS servo motor". How can i slove this problem. Please provide me a proper solution.
Last updated: 2025-06-02

Post by kporter on Removing <Empty> node in Device Tree CODESYS Forge talk (Post)
I initially created a SoftMotion axis for my EtherCAT CoE drive. I wanted to change it to use SoftMotionLight so I deleted the SM node, which left an <empty> node. I created the SML device, but the <empty> node remains. How can I remove that from the tree? </empty></empty>
Last updated: 2025-09-06

Post by reinier-geers on SM3 motion project CODESYS Forge talk (Post)
Hi, i try to setup a softmotion programm. Controller version 15. Ethercat, When is scan Devices then it install's the drives. 4.11 . Somehowe they have a vesion 16 libary. I tried to install new but stil problems. I tried version 19. Then i get a Visu version problem. What can i do ? Why are ther always problems with a new version ?
Last updated: 2023-12-18

Post by rmaas on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia CODESYS Forge talk (Post)
Hi, Im not sure if this is what you mean, but i do succesfully use the IoDrvEthercatLib.ETCSlave.InputData and IoDrvEthercatLib.ETCSlave.OutputData to read from and write to beckhoff DI and DO cards. Very convenient as you can make an FB with an VAR_IN_OUT of type IoDrvEthercatLib.ETCSlave and only have to pass the slave reference... So i am not using .ETCSlave_Diag but .ETCSlave...
Last updated: 2024-02-13

Post by florian on Stepper Drive with Ethercat CODESYS Forge talk (Post)
Codesys has a motion libraries (SoftMotion), but you need to buy a licence keys for them to work. the most basic one is SoftMotionLight. you just have to select your drive in the device view and add a SoftMotionLight CiA402 axis. then the library is added to your project. You can use the SML_* motion FBs and configure the axis now.
Last updated: 2024-03-22

Post by cihangur on Application has invalid license metrics. CODESYS Forge talk (Post)
Hi, I have a "CODESYS Control Standard L" license and I use Ethercat and Profinet in my project. The project works seamlessly with two fieldbuses. However, when I add modbus_Com (Serial) or 1 OPC Tag to the project, the program throws an exception (Application app=Application has invalid license metrics!). My license should support 10*Modbus and 512 OPC Tags. Why might this problem occur?
Last updated: 2024-03-25

Post by timvh on CODESYS: Combining Master Redundancy with EtherCAT Ring Topology – Is it Supported? CODESYS Forge talk (Post)
Yes, this works (at least we have it running with Wago PLC and Beckhoff I/O), but the concept works. You need 2 PLC's with at leat 3 network interfaces. And 2 switches (can be unmanaged). See the attached simple diagram for the solution.
Last updated: 2026-02-05

Post by mrkm-dic on CODESYS: Combining Master Redundancy with EtherCAT Ring Topology – Is it Supported? CODESYS Forge talk (Post)
Hi! thanks for reply. We tested the configuration you proposed as well; however, when the cable between the controller and the switch was disconnected, the Active and Standby roles were swapped. Did you observe the same behavior in your configuration using WAGO and Beckhoff?
Last updated: 2026-02-06

OPC-UA Server, Symbol Set: Raise an error: Object reference not set to an instance of an object. CODESYS Forge talk (Thread)
OPC-UA Server, Symbol Set: Raise an error: Object reference not set to an instance of an object.
Last updated: 2024-08-08

[Error when Install Codesys for Beaglebone black ver4.0.0] cannot access '/sys/bus/i2c/devices/0-0050/at24-0/nvmem': No such file or directory CODESYS Forge talk (Thread)
[Error when Install Codesys for Beaglebone black ver4.0.0] cannot access '/sys/bus/i2c/devices/0-0050/at24-0/nvmem': No such file or directory
Last updated: 2021-11-21

【Solved】Error 4355, 4370, 4371--A transition may not have any side effects; Superfluous lines; Invalid characters CODESYS Forge talk (Thread)
【Solved】Error 4355, 4370, 4371--A transition may not have any side effects; Superfluous lines; Invalid characters
Last updated: 2023-06-30

Python Scripting: How to detect and handle "Object reference not set to an instance of an object" error CODESYS Forge talk (Thread)
Python Scripting: How to detect and handle "Object reference not set to an instance of an object" error
Last updated: 2023-08-16

[ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0 CODESYS Forge talk (Thread)
[ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0
Last updated: 2024-02-15

Post by eschwellinger on CSVReaderInit returns error : INVALID_HANDLE CODESYS Forge talk (Post)
this is a security issue not to read/write in the plc allowed path I would recommend to update and change the path in the application were the files are😏
Last updated: 2023-08-30

Post by roundex on CSVReaderInit returns error : INVALID_HANDLE CODESYS Forge talk (Post)
Could you please give me an example where to select new path in plc. Right now my csv files are placed into /home/user/csvfiles
Last updated: 2023-08-30

Post by totorovic on CSVReaderInit returns error : INVALID_HANDLE CODESYS Forge talk (Post)
Thank you for the return. The path targets to a CFast card. User has R/W access to it. We will try to change it.
Last updated: 2023-08-31

Post by marekxc on Error C0521 - unknow compiler CODESYS Forge talk (Post)
Select in tree "DEVICE", right-click and select "Update Device" Select "Library manager" and Change the version of the Library (down manualy). Samoetimes "Try reload Library". If you open a project version 3.5.19 in version 3.5.16, there are difficulties.
Last updated: 2023-09-02

Post by nyee on Project compiling error in Simulation mode CODESYS Forge talk (Post)
Hi, I have a similar issue - we have been using codesys V3.5.16.20 Do you have any suggestions or confirmation that this will work with a different version of codesys and Pi extension
Last updated: 2023-09-07

Post by fleaplc on FILE_OPERATION_DENIED CODESYS Forge talk (Post)
By using the CAA FILE library (FB FILE.Open) (raspberry pi, codesys 3.5.19.0) I always get the error FILE_OPERATION_DENIED The file exist, it has r/w/x access and path is correct... Some idea to fix it?
Last updated: 2023-09-25

Post by simond on The required device description is not installed.. CODESYS Forge talk (Post)
Hi folks, can someone please tell me how to go about fixing this issue? I am getting this error when I implement an instance of the J1939_Manager. Thanks Simon
Last updated: 2023-10-03

Post by tomas111 on Help with error C0142 CODESYS Forge talk (Post)
There was an exact mistake. I did as they wrote. I created a visualization and transferred it from the old one and everything works. CS 3.5 SP 19. Thank you.