Post by thewizard8 on Raspberry PI4 Serial Port
CODESYS Forge
talk
(Post)
Hi All, I finally figured out how to solve it. The only away that I got it to work was to define parity to None on modbus configuration, and now works like a charm. Just for the record I'm using the GPIO port pins (8,10) and a RS485 to ttl shield that you can find online. Thanks all for the support! Regards Ricardo
Last updated: 2024-03-19
Post by cihangur on Application has invalid license metrics.
CODESYS Forge
talk
(Post)
Hi, I have a "CODESYS Control Standard L" license and I use Ethercat and Profinet in my project. The project works seamlessly with two fieldbuses. However, when I add modbus_Com (Serial) or 1 OPC Tag to the project, the program throws an exception (Application app=Application has invalid license metrics!). My license should support 10*Modbus and 512 OPC Tags. Why might this problem occur?
Last updated: 2024-03-25
Post by vformanek on Datasource OPC UA Client error ID:7012
CODESYS Forge
talk
(Post)
Hey, I am facing the same problem. Basically UA Expert and other programs work fine with the login credentials. But codesys can not use them properly. I can see the server login to it manually but when I download the program and run the datasource never runs... Currently I am facing the same Error ID: 7012 and cant get it running properly.
Last updated: 2023-11-21
Post by stiller on OPC UA RPI 4.8.0.0 Status Code / "out of range"
CODESYS Forge
talk
(Post)
Hello, I have an OPC-UA server with an information model. For many values, there is a defined range (e.g., 0 to 100). If a client enters a value outside this range (e.g., 120), the StatusCode should change to Bad. How can I accomplish this? Any help is appreciated! Thank you in advance. Best regards, Christian Stiller
Last updated: 2024-07-10
Post by damian177 on OPC UA Client
CODESYS Forge
talk
(Post)
Hi, Today I ran OPC UA Client Example in 1.1.0.0 version. I opened example visualisation and I tried connected to my OPC UA Server. In first steps looks good but connection was terminate with error OpcUa_BadLicenseLimitsExceeded. I can't test OPC UA Client witohut CODESYS OPC UA Client SL license ? Regards
Last updated: 2024-08-30
Post by dengsberg on Check Connection Status of the OPC-UA Server for Data Source Manager with OPC-UA Client
CODESYS Forge
talk
(Post)
I am using the Data Source Manager with OPC-UA Client to get data from another CodeSys application in the same Project. How can I check in the PLC_PRG structured text if the connection is ok or not?
Last updated: 2024-09-07
Post by damian177 on Problem with downloading OPC UA tags by Data Source Manager
CODESYS Forge
talk
(Post)
Unfortunately , Data Source Manager from Codesys has any problem with OPC UA Server delivered with ifix SCADA. Someone can help me add manually any tag from UaExpert to codesys ? How should be was a structure for an example of one tag ? I try like in attachement, but question is , if it a good idea ?
Last updated: 2024-09-08
Post by domebruce on Which database to use?
CODESYS Forge
talk
(Post)
We have developed a similar application few years ago with .Net and MS Sql Server. The database has about 30 tables, the more bigger tables have 2 or 3 thousands records. We can have multiple threads accessing at the same time to the DB. To garantie the data integrity we need to manage data locks and transactions. Thanks
Last updated: 2025-03-04
Post by chocojun on CODESYS WebSocket Client (IIOT Library)
CODESYS Forge
talk
(Post)
Has anyone used a library related to websocket client? I will be in charge of websocket client in CODESYS, and websocket server in python. In CODESYS, I will use WebSocketClient(FB) WebSocketRead(FB) WebSocketWrite(FB) to configure the client, Does anyone know an example of how to use it? Please help me.
Last updated: 2025-03-31
Post by chocojun on CODESYS WebSocket Client (IIOT Library)
CODESYS Forge
talk
(Post)
Has anyone used a library related to websocket client? I will be in charge of websocket client in CODESYS, and websocket server in python. In CODESYS, I will use WebSocketClient(FB) WebSocketRead(FB) WebSocketWrite(FB) to configure the client, Does anyone know an example of how to use it? Please help me.
Last updated: 2025-03-31
Post by madskaizer on Exception when OPCUA datasource disconnects from Server
CODESYS Forge
talk
(Post)
We have similar issues, with crashing PLCs, but this ranges from 3.5.16.40 to 3.5.19.70. Which log made you confirm the exception crash? I am currently looking for evidence of what causes our PLCs to crash. Network stability could be an issue with latest security roll-outs like 802.1X and segregation.
Last updated: 2025-03-31
Post by programmer on 3.5 P20 hangs - no response
CODESYS Forge
talk
(Post)
hi imdatatas, thanks for your suggestion! I added the process execution to be sure. In the meantime I reïnstall Windows but it dind't help directly. Finally I deleted CodeMeter Runtime Server after Codesys installation. Because this Service was not able to start. And it works (for now) :)!
Last updated: 2025-06-25
Post by vincentd on Datasource OPC UA Client error ID:7012
CODESYS Forge
talk
(Post)
I have not used this client / server OPC UA combination since. We were only making some kind of proof of concept. I did understand that there could be some kind of bug. I do not know if the supposed bug has been resoved since. Perhaps you could try what piautomation is suggesting
Last updated: 2024-04-05
Post by stiller on OPC-UA ApplicationUri / ProductUri
CODESYS Forge
talk
(Post)
Thank you for your answer! I'm not sure, but it seems this is not what I am looking for. I attached three pictures. The first one is from the Codesys IDE. I use an Information Model to generate an OPC-UA server. I connected via UA-Expert, and there I see the URIs I would like to change.
Last updated: 2024-05-10
Post by tomast on Codesys and Siemens SINAMICS 20 modbus RTU "Response CRC Fail"
CODESYS Forge
talk
(Post)
Hi everyone, I'm currently working on a project involving the control of 5 VFDs via Modbus RTU, this time using the WAGO 750-8212 CPU. So far, I've managed to make progress, but I've encountered an issue. While I can successfully read and write to all the registers I need, I consistently encounter a "Response CRC Fail" error when attempting to write the value 1151 to the STW register at address 40100. I'm able to set the frequency via register 40101 and adjust all other parameters using different registers. Setting STW to 1150 results in the drive ready boolean from the ZSW-bit being received instantly. However, the moment I attempt to send 1151 to register 40100, I immediately receive the "Response CRC Fail" error for all channels. I've also attempted to use combined control, employing Modbus for frequency control and starting from a digital input. Everything seems to function properly until I send the start command to the VFD. Interestingly, I consistently encounter the same error the moment I send the start command, regardless of whether I use register 40006 (high) or 40100 (1151). Could someone please assist me in resolving this issue?
Last updated: 2024-03-21
Post by andrea199403 on Assigning Modbus addresses to a structure in a dynamic way
CODESYS Forge
talk
(Post)
Hello everyone, I am new to this forum and I am also new to Codesys programming. My problem is this: I have a STRUCT of 64 bool and 30 real, this STRUCT is assigned in the programme 9 times. Now I need to communicate with an HMI via Modbus and I have defined the slave device and created the holding registers for communication. I would like to declare the first call of the STRUCT on the Modbus registers %QX2000.0 to %QX2007.7 for the booleans and on the registers %QW1004 to %QW1034 for the real registers. That said, I would like to change an index and set an offset of 100 bytes for the calls of the other 8 assignments, so that the result is: %QX2100.0 to %QX2107.7 for the booleans and on the %QW1104 to %QW1134 registers for the Real registers, etc. Is there a way to declare this? Thank you very much.
Last updated: 2025-10-21
Post by mm-sceg on Runtime geht sporadisch in Störung -> RaspiPi4 reagiert nicht mehr
CODESYS Forge
talk
(Post)
Guten Tag, ich hab seit längerem das Problem, dass mein Raspberry Pi4 durch die PLC in Störung geht. Auf dem Raspi läuft eine einfache Software mit OPC UA server, InfluxDB und ein NodeRed-Server. (Und MQTT-Server) Daten werden von der PLC über OPC-UA an NodeRed übergeben. Es kann sein, dass der Raspi 2 Wochen läuft, dann geht die PLC in Stopp. Manchmal nur 2-3 Tage. Ein Neustart über Spannung aus & wieder an schafft Abhilfe. NodeRed wirft extrem viele Fehlermeldungen in kurzer Zeit. Wenn die PLC in Störung ist, kann man sich nicht mal mehr über SSH beim Raspi einloggen. Der Raspi ist aktiv gekühlt und im Normalbetrieb nicht überlastet. Ich hab einige logfiles mit vielen Einträgen die mir nichts sagen, eventuell hat hier jemand eine Idee wie ich dem Problem Herr werden kann :) Der letzte Datenbankeintrag von der SPS war am 11.11.2023 um 5:55:50 Uhr. D.h. danach muss die SPS gestorben sein. Siehe Raspi-Log im Anhang. Das LogFile von Codesys startet leider erst um 11 Uhr, weshalb weiß ich leider nicht. Vielen Dank schonmal
Last updated: 2023-11-11
Post by timvh on Toradex and CODESYS and licensing
CODESYS Forge
talk
(Post)
For the Virtual Control you need to use a "Network license". The Virtual Control has parameters of which one is the reference to the license server. This can be the device itself, but you need to activate the license on the host system (not in the container). For this, CODESYS has a Network License server with WBM (web based management). See for the Network License configuration: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_license_controller_linux.html If it is only for evaluation, I would advise to use a CODESYS (USB) key and activate the license on the key. Then you still have to install the CODESYS Network License server on the host, but you don't have to activate the license as soft license on the device. The benefit is that you can easily move your license to another device when needed. Off course your device must have a free USB port available to be able to do this.
Last updated: 2025-10-20
Post by tjacks on Opc UA Data Source Client Browse Error in Codesys HMI
CODESYS Forge
talk
(Post)
Codesys V3.5 SP21 Patch 3 Codesys HMI 3.5.21.30 I'm trying to connect to an OPC UA server on a Kuka robot controller using Codesys HMI's data source manager. I get through the login phase and the client browses most of the data structure on the server but errors out toward the end with a generic: Error while browsing the client, Failed with service result: BadUnexpectedError. If I complete the data source setup and try to update variables, I get the attached stack trace for the error. I've tried several different endpoint and security options. Most get me through the login but all error out while browsing. UA Expert happily connects and browses with the same configuration. I've connected this same version of Codesys to TwinCAT OPC UA servers and Siemens PLC OPC UA servers. Any ideas on what may be causing the generic BadUnexpectedError during OPC UA server browse?
Last updated: 2025-11-17
Post by dantheman on Connecting to SoftPLC Only Works By Turning Off Modbus Ethernet Port
CODESYS Forge
talk
(Post)
I have an IPC with 2 ethernet ports and 1 Wi-Fi. I'm using ModbusTCP with the ethernet port named "enp2s0" connected to my remote I/O. This works fine when testing with Python and also works with CODESYS, but CODESYS is only able to scan for the Linux SoftPLC when I turn off the "enp2s0" interface. In other words, I can't get online with the IDE if I want my ModbusTCP comms to run with CODESYS. I'm using a Linux SoftPLC that has the following entry in CODESYSControl.cfg, hoping that this will allow me to connect with "enp1s0" or "wlp3s0", and leave "enp2s0" for field comms, but this seems to only make the source IP of the ModbusTCP comms to be bound to "enp2s0". That last point is the case only if I don't restart the service, but if I do restart the service after changing the config file, the source IP for the ModbusTCP comms then becomes the one for "enp1s0", which is very confusing to me: [SysSocket] Adapter.0.Name="enp2s0" Adapter.0.EnableSetIpAndMask=1 On the device list, I only have "enp2s0" given as the ethernet device that has the ModbusTCP master & slave beneath it, shown in Screenshot 1. On the IPC, I can ping the ModbusTCP client (remote I/O) from "enp2s0", and I've attached a Wireshark capture of running ModbusTCP from the CODESYS runtime as Screenshot 2, 3 & 4 (again, I can't get online when this is running, I have to turn off "enp2s0" to connect even when it's idle and I don't have an active TCP session with my Python tests). Like I explained above, the source IP is "enp1s0", even though the ethernet device on the project is "enp2s0". I was lucky to catch the red message that showed the source IP that makes sense to me (the one for "enp2s0"), but for some reason that connection was reset and I never saw that packet again. I've also tried this with Auto-reconnect both enabled & disabled, for the ModbusTCP Master device. I also have to turn off "enp1s0" and then turn it on, just so that I can have the ModbusTCP comms running from "enp2s0" (which is not intuitive in any way to me, I'd love some help understanding that phenomenon as well) in the weird manner that I've described above. I would be very appreciative if someone can help me figure out this pickle. I'd love to just connect to CODESYS through my Wi-Fi interface and leave my ethernet ports for field comms.
Last updated: 2024-08-01
Post by duvanmoreno24 on Modbus writing on value change
CODESYS Forge
talk
(Post)
Hi all, I want to know if someone has an idea of how I can write on value change in Modbus Codesys. I have a Wago PLC and I was used to work with E-cockpit which it was quite easy to do that without the necessity to trigger any value when there was a change in the variable ( I will put how easy is ). how you can see just changing the trigger in "On value Change" will do that channel writing automatically when It detects a change in those arrays. On the other hand, in Codesys if I enable the rising edge in Codesys It ask me to put a bool variable and if triggers is going to write that value. That is making me that I have to create a function or a logic to detect the change, the problem I have is that doing that is very tedious. I first approach I got it was to create a Function who returns a bool when the value change, but I tried to keep the old value but what is happening is that in Functions all the data is erased every cycle so I can not keep any Old value. so in the Main program the trigger is going to be TRUE all the time due, the old value is cero every cycle. The second approach I got it was using a function Block (POU_1) and it works but I dont want to instance that function for every Channel or value that I want to check if the value change, Basically if I have 200 values to write trhough modbus I have to create 200 instances of that function which I think it is not practicall at all. It should be a better way to implement this as e-Cockpit from Wago Does. However, I haven't been able to know how.
Last updated: 2024-03-26
Post by abinvest579 on TCP Client
CODESYS Forge
talk
(Post)
Hi All, I am using codesys based plc to read and control magna power DC supply over LXI protocol using SCPI command. To connect device required socket programming for that i am using Net base service library function block TCP_Client to establish connection over TCP/IP , TCP_Write to write SCPI commands and TCP_Read to read data from Magna power DC supply. I have attached screenshot for logic developed. I am able to connect and write commands to device but i not receiving any information from device. For writing Commands i also tried various end of line character like \n,<nl>, A, D, 10, 13, 0x0A, 0x0D but not received any status from device. For testing purpose i am using simple command '*IDN?' to read data. Also if tried to check on hercules software what data actually plc read, first it read correct data after that is read wrong data as see in screen shot. 'Hello World' was correct read and after that Codesys in replaced with 'Codesysorld' that is not correct way. Same issue also appeared for send data. Any one have face same issue how i can read data directly from device correctly and send data please suggest solution on this.</nl>
Last updated: 2024-07-01
Post by josul on Web Client HTTPS Communication Issue
CODESYS Forge
talk
(Post)
Web Client Library Documentation Company: 3S - Smart Software Solutions GmbH Title: Web Client Version: 1.0.1.7 Categories: Application|Utils Namespace: WEB_CLIENT Author: 3S - Smart Software Solutions GmbH Placeholder: WebClient I encountered an issue using this library above. Note it is now part of Codesys IIoT Libraries SL in the form of Web Client SL, but I am not using this version. I was sending Content-Type: application/json, HTTP POST using a HTTPS URL. No issue observed initially, successful operation. At some point operation stopped and the codesyscontrol.log file started to accumulate errors: ERROR: TlsCreateContext2: Failed to save context. An application reset failed to resume operation and I was unable observe any TCP connection forming to a destination port 443. The error appeared as a TCP_INIT error. I can find no details as to what may have happened or why a reset of the PLC application did not resume operation. Testing with a curl operation proved to be successful, so I am confident there was no fundamental networking issue preventing a TCP connection forming. The solution was to reboot the hardware itself, but this is not satisfactory in the long term. Is there any description of the TLS error I received? Is there any suggestion here that there might be an issue with certificates? Any advice or information is appreciated.
Last updated: 2025-06-05
Post by ernesto881124 on ernesto881124
CODESYS Forge
talk
(Post)
Hello good morning everyone I would like to ask a question, is it possible to directly connect a device that only contains modbus RTU communication through an R-45 connector, directly to the PC? Or would you need an intermediate device to achieve communication? It would be of great help to me because I cannot achieve communication between the Codesys simulator plc and a Fuji Frenic mini VFD, please help me if anyone has had the same experience. Thank you so much
Last updated: 2023-09-13
Post by jeffgamsby on Accessing ModbusTCP addresses from python
CODESYS Forge
talk
(Post)
Hi, I am new to modbusTCP and I am trying to access Input registers from codesys (3.5.SP13). The offset is 16#0000 and I am trying to access Channel 1[24] %IW24 to pull analog values. I am using pyModbusTCP and I need to supply a modbus address and the number of registers to read. What does 16#0000 mean in terms of the actual offset, how do I translate this number plus the channel to access this info via python? Any help would be appreciated, thank you.
Last updated: 2023-09-20