Post by manuknecht on Opening a Dialog on a specific Client from ST
CODESYS Forge
talk
(Post)
I managed to find a solution that seems to work reliably. As the VU.Globals.CurrentClient-filter accesses the CURRENTCLIENTID or at least a similar, internal variable it can only be used if called from a certain client (e.g. from a button in a visualization). My solution works by implementing a new client filter that compares the client ID of all clients to the ID of the last client that was used. The variable containing the data of the last client is defined as: G_LastClient : VU.IVisualizationClient; // Copy of last client that detected click This last client is then updated every time a button is pressed using the Execute ST-Code input configuration of the button: G_LastClient := VU.PublicVariables.Clients.Current; Next, I created a function block that implements the client filter interface as so: FUNCTION_BLOCK FB_LastClientFilter IMPLEMENTS VU.IVisualizationClientFilter VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR END_VAR Then i added a method to the FB called IsAccepted which is used to filter out the client. When creating the method, it should automatically be filled with the according variable declaration, as it is defined in the interface: (* For every client can be desided, if it is accepted. ``TRUE``: Client is accepted*) METHOD IsAccepted : BOOL VAR_INPUT (* The client, to check*) itfClient : VU.IVisualizationClient; END_VAR Now the client can be compared to the last used client as such: // check if clientID corresponds to clientID of last recorderd client IF itfCLient.ClientId = G_LastClient.ClientId THEN IsAccepted := TRUE; ELSE IsAccepted := FALSE; END_IF To make use of this custom client filter, initialize a variable with the client filter: LastClient : FB_LastClientFilter; // Client filter to find last used client Then use this client filter when opening or closing a dialog from ST: fbOpenMyDialog(itfClientFilter:=LastClient,xExecute:=TRUE,sDialogName:='VIS_MyDialog_DLG');
Last updated: 2023-09-27
Post by dnordenberg on BOOL variable in OPC UA and modbus simultaneously
CODESYS Forge
talk
(Post)
How can I have an BOOL variable that is read/write in both modbus TCP server and from OPC UA at the same time? Variables with %MX.n %QX.n addressing which is used for BOOL/coils in modbus server is not allowed in OPC UA symbol list on Schneider M251 controllers. I have already asked on Schneiders forum but there are not a lot of codesys experts over there :( So OPC symbols can't have a address and the modbus TCP server needs a address. So how should I do it then? It seems like an impossible combination. Since I want read/write access from both ways I can't just simply make a second variable and assign it the value of another since it would be a one way assignment. I also tried using VAR_CONFIG which then makes the address syntax %Q or %M in my main variable list and that fools OPC UA Symbol Configuration to allow it and then I add the complete %MX.n address of it in the VAR_CONFIG list. This semi works, I can toggle the BOOL from modbus but the OPC UA symbol seems to be read only. It displays symbol status but nothing happens when I toogle it. I think I need another way to have the variables and symbols pointing to the same bits in memory... My plan B is to write a BOOL array compare FB that saves a history bit from previous cycle and if that does not match current status at next cycle for either the OPC symbol or the modbus variable then it copies the new status over to the other. Maybe ugly but it's like my last alternative. Kind regards David
Last updated: 2025-07-14
Post by timvh on Get Alarm status in Codesys
CODESYS Forge
talk
(Post)
You are right, that you can use the GetState method, but it is not that simple. You first have to get a list of (filtered) alarms from the AlarmManager. You can find an example in Forge how to do this. See https://forge.codesys.com/prj/codesys-example/alarm-manager/home/Home/ Then you can go through this list to get the state of all the (filtered) alarms. See below the code which you could use. This is all based on the example from forge. Create a program: // This example shows how to access alarms via structured text. PROGRAM PLC_PRG VAR xInit : BOOL := TRUE; udiResult : UDINT; fbAlarmFilterCriteriaAll : FB_AlarmFilterCriteriaAll; fbAlarmManagerClient : FB_AlarmManagerClient; itfAlarmManagerClient : IAlarmManagerClient := fbAlarmManagerClient; xAlarm1 : BOOL; xAlarm2 : BOOL; xWarning : BOOL; iNrOfAlarmsInAlarmList : INT; iNrOfActiveAlarmsInAlarmList : INT; paitfAlarm: POINTER TO ARRAY [0..0] OF AlarmManager.IAlarm; iAlarmIndex : INT; eAlarmState: AlarmManager.AlarmState; END_VAR IF xInit THEN xInit := FALSE; fbAlarmManagerClient.itfAlarmFilterCriteria := fbAlarmFilterCriteriaAll; // register alarm client to get updated about alarm status / changes udiResult := AlarmManager.g_AlarmHandler.RegisterClient(itfAlarmManagerClient, 0, 0); END_IF // Polling the number of alarms udiResult := AlarmManager.g_AlarmHandler.GetActiveAlarms(itfAlarmManagerClient, parritfActiveAlarms => paitfAlarm, iCountActiveAlarms => iNrOfAlarmsInAlarmList); iAlarmIndex := 0; iNrOfActiveAlarmsInAlarmList := 0; WHILE iAlarmIndex < iNrOfAlarmsInAlarmList DO eAlarmState := paitfAlarm^[iAlarmIndex].GetState(); IF eAlarmState = AlarmManager.AlarmState.Active OR eAlarmState = AlarmManager.AlarmState.ActiveAcknowledged THEN iNrOfActiveAlarmsInAlarmList := iNrOfActiveAlarmsInAlarmList + 1; END_IF iAlarmIndex := iAlarmIndex + 1; END_WHILE See below some details about the function blocks: One function block should implement the IAlarmFilterCriteria interface. This can be empty except a few methods. FUNCTION_BLOCK FB_AlarmFilterCriteriaAll IMPLEMENTS AlarmManager.IAlarmFilterCriteria Method implementation (others related to interface are empty) METHOD AreAllAlarmClassesSelected : BOOL AreAllAlarmClassesSelected := TRUE; METHOD AreAllAlarmGroupsSelected : BOOL AreAllAlarmGroupsSelected := TRUE; METHOD GetPriorityFrom : USINT GetPriorityFrom := 0; METHOD GetPriorityTo : USINT GetPriorityTo := 255; The other function block should implement IAlarmManagerClient and get a reference to the FB which implements the IAlarmFilterCriteria FUNCTION_BLOCK FB_AlarmManagerClient IMPLEMENTS AlarmManager.IAlarmManagerClient VAR_INPUT itfAlarmFilterCriteria: AlarmManager.IAlarmFilterCriteria; END_VAR Method implementation (others related to the interface are empty) METHOD GetFilterCriteria : AlarmManager.IAlarmFilterCriteria // see VAR_INPUT for filter GetFilterCriteria := itfAlarmFilterCriteria; Off course you have to add the AlarmManager to your application and add some alarms to it.
Last updated: 2025-09-02
Post by adamrobotic on llcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008
CODESYS Forge
talk
(Post)
Hi All, Recently I have been experiencing a issue in CodeSys SP16 Patch 3, with a exception which comes up after I have made several online changes. callcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008, after I experience this fault then I receive a error message for any subsequent online change "online change failed, no task gap within 10000ms". To recover either the controller needs a orgin reset, which will allow online edits thereafter until falling back into the loop. I am using a TURCK TX707 product which is controlling robot trajectory, We have hard coded the coordinate data rather than using persistence variables so hence the need to do online changes consistently. I have read on the forum other people have experienced similar issue with the online task gap, but I have no task which have same priority and also monitored the CPU usage and have not seen it go above 13%. Anyones help would be much appreciated, thankyou.
Last updated: 2023-08-18
Post by manuknecht on Persistence Manager does not save alphabetically first value
CODESYS Forge
talk
(Post)
After some more digging I realized that I get an error on the PLC Logger saying PersistenceChannel: 150 (invalid type in data: SimpleLibrary). I suppose the issue could be found in the ConfigData, which is automatically generated and which looks like this: 1 9##83 SimpleLibrary#GVL.aMoreZeros.[1]#0#64512#15#0 <[2]#0#64520#15#0 <[3]#0#64528#15#0 <[4]#0#64536#15#0 <#0#64544#15#0 <[6]#0#64552#15#0 <<lrVar#0#64560#15#0 <strVar#0#64428#16#80 <uiDummy#0#64370#11#0 Perhaps the fact that the variable is stored within a library confused the compiler? I tried changing the PersistenceChannel parameters to xCompressTags := FALSE which changed the entry in the data file from _xCompressTags BOOL:TRUE _xCompressTags BOOL:FALSE but the actual content of the data file and also the config data did not change.
Last updated: 2023-10-17
Post by psychoengineer on Cannot Save CSV File on Windows Computer Using CODESYS and Control Win
CODESYS Forge
talk
(Post)
I am currently working on a project using CODESYS and Control Win on a Windows computer. I've encountered an issue where I am unable to save a CSV file. I have followed the standard procedures and used the appropriate file handling functions, but the file is not being created or saved as expected. IF xStartTest THEN sFileName := '\logs.txt'; sFileName := CONCAT(gvl.g_sMainDirectory, sFileName); sFileNameCopy := '\CAAFileCopy.txt'; sFileNameCopy := CONCAT(gvl.g_sMainDirectory, sFileNameCopy); //eWriteState := FILE_OPEN_TRIGGER; xTestDone := FALSE; xError := FALSE; xStartTest := FALSE; END_IF VAR_GLOBAL g_sMainDirectory : STRING := 'C:\LogFiles'; // file path for CSV file END_VAR Despite this, the file does not appear in the specified directory, and no error messages are being generated. I've checked the directory permissions and ensured that the path is correct. Has anyone else experienced a similar issue or have any suggestions on how to resolve this? Any help would be greatly appreciated. Thank you!
Last updated: 2024-07-04
Post by berto on Opening PDF in Web Browser in Target Visu HMI
CODESYS Forge
talk
(Post)
Hi everybody, I've been facing problems with the PDF visualization in Web Browser. I am trying to open a pdf file called 'sample.pdf' which I manually saved inside PlcLogic/visu folder. I am setting the web browser URL as: 'http://127.0.0.1:8080/sample.pdf' but I get 'refused connection'. I got a similar error trying to open https sites and I discovered that I can only open http websites. Opening 'http://de.wikipedia.org' everything works fine. I also tried to check using code whether the sample.pdf is present in the directory. Unfortunately, when I try to read directories of 'PlcLogic' I get file FILE_OPERATION_DENIED (I am using File.DirList). I would like to be able to open PDF files in web browser. Possibly to move new PDF files in the folder as my customer wants to display different pdf manuals on the hmi. Here you find some screenshots and my .project. I am using Codesys 3.5.19.70. Best regards, Berto
Last updated: 2024-07-11
Post by faceplant on CmpDynamicText unresolved references
CODESYS Forge
talk
(Post)
Hello! I am new to codesys so I am sorry if this is not the right place to ask this question. I am using codesys V3.5 SP20 Patch 1 + (64-bit) and a Groov EPIC PLC (GRV-EPIC-PR2). I am trying to build and deploy my application to the PLC, but when I log in I get 6 errors (codesys_error.png). It seems that the errors have to do with the CmpDynamicText system library which I have as version 3.5.20.0. I have tried to add CmpDynamicText to the ComponentManager section in the PLC's CODESYSControl.cfg file as described in this forum post and still hit the same error. I noticed that the library is grayed out in the library manager, which I think might be the issue. However I don't remember if it was grayed out before I encountered this issue. Please let me know if I can provide anymore info. Thank you!!!
Last updated: 2024-07-19
Post by denkihitsuji on Content update through Data URI on Web Brower on Visualization Toolbox
CODESYS Forge
talk
(Post)
Objective: I want to dynamically update the content with strings and JPEG images received from a TCP/IP socket. For this purpose, I am exploring the possibility of utilizing the Web Browser feature of the Visualization toolbox. Example: In a standard web browser, entering data:text/plain;charset=utf-8;base64,SGVsbG8gc3RyYW5nZXI= in the URL window will display "Hello stranger" on the webpage. Issue: When attempting to use this method in the Web Browser of the Visualization toolbox, the content does not display as expected. Instead, it shows the error:'Navigation to the webpage was canceled.'. Request: I seek guidance on how to resolve this issue so that the Web Browser in the Visualization toolbox correctly interprets and displays the data URI content. Alternative Solution Welcomed: Or, if it is possible to directly use Codesys Structured Text (ST) variables within an HTML page, this approach would also meet my requirements. Thank you for your attention.
Last updated: 2024-07-30
Post by mubeta on parker servo and position
CODESYS Forge
talk
(Post)
In general, drives have parameter sets to adjust behaviour in such cases: position recovery, adaptation with resistant torque, out-of-position window failure, etc. (Much depends on the type of configuration set for the axis: positioner, speed controller, torque controller, etc.). I have used that type of drive very little, in only two cases and a long time ago. To tell you what is normal is impossible. I know by reputation they are very simple objects, without too many pretensions and adjustments possible. Try running traces by monitoring actual position, motor current, torque and following error. These are the most sensible curves to understand what is going on. Maybe by fine tuning the motor tuning, the current controller or the speed controller you will get something closer to what you want. For example, from DS, the motor has a standstill torque of 3 Nm. Observe with traces whether this is effective: motor current trend. And afterwards, when you have your own accurate picture of the situation, you can also hear from the product's local support to see if you can steal a few more things from it performance-wise.
Last updated: 2024-08-05
Post by mainak on Opaque NodeId in the OPC UA server
CODESYS Forge
talk
(Post)
Hello all, I am using the OPC UA server with my custom information model. I have used the communication manager to add my information model under my application and created instances from OPC UA types. I see that the created instances in the OPC UA server has some opaque nodeid (attached screenshot) and I want to change that. Therefore I have the following questions: 1. Is there a way to configure the NodeIds of instances in the OPC UA server? I tried to edit it using the UaExpert client but got error "BadNotWriteable". is it possible to configure it somewhere so that the nodeids can be changed using an external client? 2. Is there a way to define the rule for creating instance nodeids within the codesys IDE? 3. Is it possible to create the instances before e.g. using a modelling tool like UaModeler and import them as part of the information model and use them later? Using the communication manager, I can only create instances from types. I couldn't find a way to map my existing instances to plc tags from my application. It would be nice if someone could help me with these issues. Thanks in advance. :)
Last updated: 2024-10-19
Post by koerbejm on Probleme beim aktivieren von Lizenzen
CODESYS Forge
talk
(Post)
Liebe Codesys-Gemeinde, ich habe folgendes Problem und bitte um Hilfe: Um eine auf meinem dem Raspberry Pi laufende Steuerung ohne große Mühe duplizieren zu können, habe ich mir ein Image der SD Karte mit Win32 Diskimager erstellt. Dieses konnte ich bisher ohne weitere Probleme auf eine weitere Micro-SD karte ausrollen. Anschließend habe ich mich via Putty auf den PI geschaltet, die vorherige Lizenz (die ja für den vorheringen PI zulässig war) gelöscht über - sudo su - rm -r /var/opt/codesys/cmact_licenses/ - reboot Um dann via Codesys 3.5 SP16 Patch 4 eine neue Lizenznummer ">>Tools>Lizenzmanager>Lizenz aktivieren" zu aktivieren und das wars. Durch die Umstellung des Lizensierungsverfahrens klappt diese Variante nun nicht mehr. Ich habe mir neue Lizenzen von Codesys gekauf, doch sobald ich diese in die Ticket-ID eintrage und aktivieren möchte bekomme ich folgende Fehlermeldung: ReturnCode: 403046401, An internal error has occured. Please try it again later. (siehe Bild im Anhang "Fehler_Codesys3.5V16.png") Ich habe dann meine Codesys-Version auf Version 3.5 SP20 geupdated und das selbe versucht mit dem Resultat, dass ich nun folgende Fehlermeldung erhalte: "Der ausgewählte Container "...." paßt nicht zu Ihrem Ticket. Bitte wählen Sie einen passenden aus." --> Siehe Bild im Anhang "Fehler_Codesys3.5V120.png" Was genau kann/muss ich tun, damit ich einfach wie bisher meine Steuerungen duplizieren kann? Verwendete Hardware: Raspberry Pi 3 Model B+ Verwendete Lizenz: Codesys Control Basic L Viele Grüße und Danke, Jan
Last updated: 2024-10-23
Post by edvard-munch on How I can get "Done flag" for "Modbus Slave Channel"?
CODESYS Forge
talk
(Post)
This is from 10 years ago, I know. But I have been using (SLAVE_DEVICE.iChannelIndex = CHANNEL_NUMBER) AND (SLAVE_DEVICE.xDone) I suppose that it shows xDone for the channel that shows up in the iChannelIndex at the same cycle? It seems to be working properly for two devices that I have been using it before But now I have another device and using two write channels, for one register each. One channel works properly and returns DONE flag When another channel is triggered, I see that it shows up in iChannelIndex, but flag DONE not received, but no Error for the channel. Also, when i check the register in the device it's evident that data has been transferred. Is this could happen sometimes with CODESYS, so DONE flag not received? Or this is a problem with a given device? With this certain register
Last updated: 2024-12-19
Post by atcprojectteam on Modbus Function Code 15, writing multiple coils
CODESYS Forge
talk
(Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26
Post by atcprojectteam on Modbus Function Code 15, writing multiple coils
CODESYS Forge
talk
(Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26
Post by macman on Codesys 3.5 OPC UA Client to Kepware OPC UA Server
CODESYS Forge
talk
(Post)
Hi, I have problem with connecting Wago PLC WAGO 750-8212/0025-0002 configured as OPC UA client to Kepware OPC UA Server. I am using Codesys 3.5.19.70. What I did so far. To the Codesys project I added object Data Source Manager and configured connection OPC UA like below: pic 1 Then I can browse the OPC server tags in “Variables” tab after prior trust on the server side of the client certificate created in the “Communication” tab: pic 2 Additionally second certificate has been created in Codesys for runtime process in “Security screen” as well as the server certificate was approved here: pic 3 But when I compiled project, downloaded it to PLC and go to RUN I can’t read selected in “Variables” tab, OPC Server tags. I am getting such error (ID: 7001): pic 4 All two PLC certificates has been trusted in OPC server (Kepware) side: pic 5 and Kepware server configuration look like this: pic 6 I can easily connect using third party OPC UA client UaExpert to Kepware server without problem. In attachment I added also log from Kepware OPC UA server. pic # - this specifies the number of a concrete graphic from one of the collective in attachment
Last updated: 2025-04-02
Post by jeroenaero on Problem with CodeSys Control SL Deploy Tool 4.15.0.0
CODESYS Forge
talk
(Post)
Hello, We just installed the new version of CodeSys Control SL Deploy Tool 4.15.0.0 but we get the following error when we try to add a VPLC. Can someone of the CodeSys team fix this issue? the object reference is not set to an instance of the object Zie het einde van dit bericht voor meer informatie over het aanroepen van JIT-foutopsporing (Just In Time) in plaats van dit dialoogvenster. ** Tekst van uitzondering ** System.NullReferenceException: De objectverwijzing is niet op een exemplaar van een object ingesteld. bij _3S.CoDeSys.RuntimeDeployTool.Views.AddNewInstanceForm.ShowAllImages() bij _3S.CoDeSys.RuntimeDeployTool.Views.AddNewInstanceForm..ctor(List1 virtualControls, List1 existingNames) bij _3S.CoDeSys.RuntimeDeployTool.Views.MainEditorTab_Operation.OnAddInstanceClick() bij _3S.CoDeSys.RuntimeDeployTool.Views.MainEditorTab_Operation.bt_add_Click(Object sender, EventArgs e) bij System.Windows.Forms.ToolStripItem.RaiseEvent(Object key, EventArgs e) bij System.Windows.Forms.ToolStripButton.OnClick(EventArgs e) bij System.Windows.Forms.ToolStripItem.HandleClick(EventArgs e) bij System.Windows.Forms.ToolStripItem.HandleMouseUp(MouseEventArgs e) bij System.Windows.Forms.ToolStripItem.FireEventInteractive(EventArgs e, ToolStripItemEventType met) bij System.Windows.Forms.ToolStripItem.FireEvent(EventArgs e, ToolStripItemEventType met) bij System.Windows.Forms.ToolStrip.OnMouseUp(MouseEventArgs mea) bij System.Windows.Forms.Control.WmMouseUp(Message& m, MouseButtons button, Int32 clicks) bij System.Windows.Forms.Control.WndProc(Message& m) bij System.Windows.Forms.ScrollableControl.WndProc(Message& m) bij System.Windows.Forms.ToolStrip.WndProc(Message& m) bij System.Windows.Forms.Control.ControlNativeWindow.OnMessage(Message& m) bij System.Windows.Forms.Control.ControlNativeWindow.WndProc(Message& m) bij System.Windows.Forms.NativeWindow.Callback(IntPtr hWnd, Int32 msg, IntPtr wparam, IntPtr lparam) ** Geladen assembly's ** mscorlib Assembly-versie: 4.0.0.0 Win32-versie: 4.8.9300.0 built by: NET481REL1LAST_C
Last updated: 2025-04-24
Post by bmatlove on Variable Length Array - Cannot mix variable and fixed length dimensions?
CODESYS Forge
talk
(Post)
Using Codesys 3.5.18.30 I am trying to work with an array of variable length in one dimension, but known in the other dimension. For example, using an array that represents a list of items, each with an attribute profile. I do not know how many items will be in the list, but I know that every item has 5 attributes, like size, weight, etc. Codesys does not seem to be able to accept this. I have referenced Data Type: ARRAY OF documentation page, which is not explicit if variable & fixed length array dimensions can be mixed. In the VAR_IN_OUT scope, I initially tried MY_ARRAY : ARRAY [*, *] OF REAL; which was no problem, of course. I then modified it to MY_ARRAY : ARRAY [*, 1..5] OF REAL; which throws C0006: ', or ]' expected instead of '..' among consequent downstream errors. I then used the Auto Declare -> Array Wizard, which accepted (asterisk)-(asterisk) and 1-5 for 2-dimensional lower and upper bounds. It output: MY_ARRAY: ARRAY[*..*, 1..6] OF INT; which throws the same error stream. What's the deal here? Is this possible?
Last updated: 2025-05-23
Post by laurits on Max lines of code, codesys CNC ?
CODESYS Forge
talk
(Post)
Hi, okay here's the project, it's a modified version of "CNC Example 10: Programming Dynamic CNC Paths", no need for G Code text file (i have also tried with G code text file, same problem) in "PROGRAM PLC_PRG" you can set bStart to true, and the program should start running, go to "PROGRAM CNC" and you can see axis moving. lrXpos := IoConfig_Globals.XAixs.fSetPosition; lrYpos := IoConfig_Globals.YAxis.fSetPosition; Now you can can change the number of movements in the the "PROGRAM PLC_PRG" From this number of movements in "program PLC_PRG" BUF : ARRAY[0..32010] OF SMC_GEOINFO; xp : ARRAY[1..32000] OF REAL; yp : ARRAY[1..32000] OF REAL; to this number to this number of movements BUF : ARRAY[0..132010] OF SMC_GEOINFO; xp : ARRAY[1..132000] OF REAL; yp : ARRAY[1..132000] OF REAL; Now if you start the program again you should see an error in the "sMC_Interpolator: SM3_CNC.SMC_Interpolator;" function block Let me know if you can not get it running.
Last updated: 2025-06-03
Post by pouyavakili on Execute Codesys Tests with python
CODESYS Forge
talk
(Post)
❓ Issue: TestManager Not Available in Python Script (AttributeError) 🙏 Question: Why does project.get_testmanager() not work in scripting, even though Test Manager is installed and licensed, and the script runs in GUI mode? Is there a way to ensure the Test Manager interface is loaded or accessible from the scripting environment? 🧠 Summary: I'm trying to automate test execution using the CODESYS scripting engine (Python) via a script that opens a project, builds the application, and runs tests from a TestRepository.xml. Although the Test Manager works manually in the IDE, it fails when accessed via script with the following error: AttributeError: 'ScriptObject' object has no attribute 'testmanager' 🧪 Test Setup: CODESYS version: 3.5.21.10 Test Manager: Installed and licensed (works in the IDE manually) Project: Contains a test repository, which can be executed via the GUI Script execution method: powershell Start-Process -FilePath "C:\Program Files\CODESYS 3.5.21.10\CODESYS\Common\CODESYS.exe" ` -ArgumentList @( '--profile="CODESYS V3.5 SP21 Patch 1"', '--runscript="C:\Scripts\run_tests.py"' ) -Wait 📜 Script Summary: python project = projects.open(project_path) application = project.active_application application.build() This fails: testmanager = project.get_testmanager() ❗ Problem: Calling project.get_testmanager() or application.testmanager throws an AttributeError, even though the same project and test repository work in the GUI.
Last updated: 2025-07-23
Post by nicetuxedo on Can not activate license on Raspberry pi
CODESYS Forge
talk
(Post)
Hello everyone, I'm hoping for some assistance with a license activation issue: a software crash has left my license in a strange state. Here is the sequence of events: I purchased a new license for the Raspberry PI from the official CODESYS web store. I opened the CODESYS and started the online activation process using the ticket number I received. During the activation, the CODESYS software threw an exception and crashed. I was not able to see if the activation completed. After restarting CODESYS, I attempted to run the activation process again with the same ticket number. The License Manager now gives me an error stating that the ticket has already been activated/used. I am now stuck because my installation is not licensed, but the activation server believes my ticket has been consumed. Has anyone encountered this before? Is there a way to have the ticket status reset?
Last updated: 2025-10-08
Post by forest on SM Drive license error
CODESYS Forge
talk
(Post)
Hi, when it comes about license, I used INVTmatic Studio, which uses Codesys, for programming INVT plc. I bought Codesys Modbus license, it was not expensive, and then realised that INVT didn't have License Manager option (greyed out in program) which is needed for using of Codesys License. I contacted support from INVT, but developers told me that option is still not available. So depending on environment for programming Codesys, you can or not use Modbus license. Good thing about this version of Modbus TCP it works both direction. I could send commands and receive feedbacks from drive. But communication stops after 30 mins. So I used simple version of ethernet modbus which is somewhere in INVT or Condesys library (I can check tomorrow) which works only one way. I could send cmd to drive, and control it, but didn't have any feedback, like some readings back in PLC. which is bad, but at least I could start it and it didn't fail after 30 mins.
Last updated: 2024-01-10
Post by wbj0t on System libs and I/O Drivers
CODESYS Forge
talk
(Post)
Hi everyone. My question about: where I can learn (read or watch) an info about codesys workflow through the system IO libs? I want to know how to implement I/O drivers by my self. In the system libs I see many interfaces, methods etc... But there is no explanation about them, just names of methods and fields of the FBs. I know about this page: https://forge.codesys.com/drv/io-drivers/doc/Generic/ There is so BIG the device description file and not so clear explaining of the attributes and elements, also some elements or attributes missed at it all. Yes, there are code examples on this page, but, so shortly and, for example, code about Modbus drivers is absent. And even if I try to add the IoDrvFB with lib, I get and error, something like: "failed to load IoDrvFB driver". And what about the book of codesys that written by Gary Pratt? Is there information about system libs and drivers in this book more clearly? Thank you :)
Last updated: 2024-02-02
Post by fredsta on Unable to load dynamic modules (Download failed: Application=Application)
CODESYS Forge
talk
(Post)
Hey there, I am currently trying to find a good solution for the communication between CODESYS Control on Raspberry Pi and "the rest of the world", i. e. the things apart from CODESYS on my linux. My first approach was to use the c-integration. So I created a lib, defined extern fbs, compiled the code on my Pi using the SDK and put the .so into my lib project. When I try to log into the Pi and load the program, I get the error message which you can see in the attached picture. "Die dynamischen Module der C-Integration konnten nicht auf das Laufzeitsystem geladen werden" is german and means roughly "the modules from the c-integration could not be loaded onto the runtime system." Is this normal? Am I doing something wrong? I will have a look at the unix domain socket thing next, as I am still in the process of finding the best solution for the communication.
Last updated: 2024-02-15
Post by mtho on JSON Utilities - JSON file written with invalid structure
CODESYS Forge
talk
(Post)
I'm using the JSON Utilities SL library to write configurations in my program to a file. I'm generating the JSON data using the builder function block and all appears to work correctly. When I write the jsondata to file, I'm finding that some of the JSON elements are not being written in the right location in the file. Rather than writing they keys under the parent object, they get written outside the root JSON object at the end of the file. If I then try to read the file back into the program, I get an invalid_structure error. I don't get any errors when populating the JSON data or when writing the file. I attached an example of the JSON writer output. The problems begin with key P200. Each P200 should go under MBR1 through MBR3. Among the rest of the keys, they are supposed to be under different parent objects. I am using default values for wsLineBreak and encoding.
Last updated: 2024-03-06