Post by manuknecht on Creating softmotion axis dynamically CODESYS Forge talk (Post)
Hi I was wondering the same thing. I managed to dynamically add an EtherCat Slave but I could not find out how to add a softmotion axis to it. Does anyone have an answer to this? Thanks in advance!
Last updated: 2024-02-21

Post by eschwellinger on CODESYS Automation Server Connector for 3.5 SP11 CODESYS Forge talk (Post)
https://store.codesys.com/en/codesys-automation-server-connector.html Programming System CODESYS Development System V3.5.15.0 or higher
Last updated: 2023-08-30

Post by eschwellinger on CODESYS Installer does't open CODESYS Forge talk (Post)
please check the windows event log for errors. Try to install it again from the CODESYS store. stanalone setup CODESYS installer
Last updated: 2025-04-01

Post by fugtwad on Automation Builder V2.5 EtherCAT CM579 Master Scan for devices - >No gateway selected CODESYS Forge talk (Post)
ABB Automation Builder v2.5.0.22 Premium CodeSys 2.3.9.62 Running on Win 10 VM x64 Goal: I have an EtherCAT topology issue which normally a "Scan for devices.." on the EtherCAT master would shed some light on. Issue: Upon trying such I get a "No gateway selected" error. Question: How might I point the the "scanner" at a gateway? What is working: Gateway is running in system tray. I can go online to PLC. A scan from the "Diagnostics live" tab of the EtherCAT master gives slave status. What I have tried: Restarting gateway in system tray. Exiting system tray gateway and reloading it. Turning off firewall. Contacting ABB support multiple times. Any help appreciated.
Last updated: 2024-05-20

Post by msirotkin on EtherCAT status errors CODESYS Forge talk (Post)
Hello, I'm trying to understand the reason for the many errors on the EtherCAT master status page. If we set the cycletime to 1ms we see a lot of rxerrors and lostframes, but the send and recive times are quite good (see attachement). And the status of the EtherCAT bus is good (no other errors, all is green, slave has no errors) But when we set 2ms cycletime the lostframe errors are gone, but periodically increses rxerror counter (see attachement). The questions is, what do these errors actually mean and what we can do to get gid of them? Linux RT, imx8, Codesys runtime for ARM 3.5.21.10, Ethercat 4.10 Thanks
Last updated: 2025-11-25

Post by reinier-geers on Ping By Name CODESYS Forge talk (Post)
To bad. Controller uses Version 9.2 But i dont see a lower version of net bas Service. Maybe i can try a linux command.
Last updated: 2023-08-29

Post by chir on SMC_REGULATOR_OR_START_NOT_SET issue CODESYS Forge talk (Post)
Hello everyone! I faced the error SMC_REGULATOR_OR_START_NOT_SET using InoProShop (Inovance IDE). This error occured then I enable MC_Power block. The output BUSY is TRUE constantly.. The description of this error in documentation - "Controller enable not done or brake applied". Maybe someone know how to solve this problem
Last updated: 2024-04-19

Post by reinier-geers on SYSDIR 3.5.17.0 CODESYS Forge talk (Post)
I had a funcioning Directory read wit SYSDIR. Now ive got a new controller with Linux. and now i get only ordners Names. NO file Names !! WHY ? It workt already on a other with linux. But that was i think version 14
Last updated: 2026-01-06

Post by reinier-geers on SYSDIR 3.5.17.0 CODESYS Forge talk (Post)
I had a funcioning Directory read wit SYSDIR. Now ive got a new controller with Linux. and now i get only ordners Names. NO file Names !! WHY ? It workt already on a other with linux. But that was i think version 14
Last updated: 2026-01-06

Post by steven-schalm on Github Actions CI/CD tasks - development topic CODESYS Forge talk (Post)
hello kevinrn, I've been looking for a solution to the CI/CD issue for a long time. Briefly about me... I am 32 and software architect for Codesys V3 and fullstack dev for web (VueJS, NestJS) in a small company in Erfurt (Germany). https://www.rex-at.de/. Through my web part, we already have CI/CD running well via GitLab (YAML-based configuration file (.gitlab-ci.yml), which defines which pipelines and jobs are executed when certain events occur) with everything you know. Stages for npm packages - prepare (GitVersion, npm install or whatever) - build (vite, tsc or whatever) - testing (vitest, jest or whatever) - deploy (npm packages) And similar for monorepo's or backend services (in NestJS) as DockerImages. For Codesys we have been building an OOP framework for years (~50 libraries now), which is currently managed via SVN and a specially written Svn-Watcher (in Python) gets commits and runs and builds everything together and deploys it to an FTP server and network drive. Why do we still have SVN? Because we are unfortunately still tied to the safety integration of Codesys and can therefore only go to SP15 at most with our controller/Eckelmann. But soon there will be an update and there will be no more obstacles to using Git. Hence my questions: 1. the basic idea is to run a local Windows Runner on some machine? 2. install Codesys on the machine where the runner is running? 3. powershell & python scripts are then used to execute builds (compile, build, sign libraries) & deploys? 4. can the Github action also be used in GitLab? ChatGPT has already told me that it's not the same, but it doesn't hurt to ask. Do you have any ideas on this? Greetings :D
Last updated: 2024-08-20

codesys-->opc ua-->codesys CODESYS Forge talk (Thread)
codesys-->opc ua-->codesys
Last updated: 2021-08-11

Post by simotion on Codesys Softmotion Win V3 x64 CODESYS Forge talk (Post)
I have a project in Codesys v3.5 sp19 patch2 that contains softmotion virtual axes. I want to simulation the code (softmotion) on the simulated plc on the pc. The controller in the project is a Codesys Softmotion Win V3 x64. I have started up the Codesys Softmotion Win 64 on the pc. However it seems a 3.5 sp14 controller. When trying to download the project, I get a message that target system is different from connected system (3.5.19 vs 3.5.14). How do I set the connected system to 3.5.20 (there seems no way to set the target system to 3.5.14
Last updated: 2023-10-04

Post by antonz on CoDeSys v3.5: creating libraries for both 32-bit and 64-bit controllers CODESYS Forge talk (Post)
Follow up question: in the Project Settings, under Library Development, there is an option related to this: Check all Pool Objects -> Pointer size to use Options are: * 32 Bit * 64 Bit * 32 and 64 Bit The descriptions and online help suggest to me this is only relevant for checking and showing any incorrect pointer types as an error in the IDE. E.g. using a DWORD to store a pointer value on a 64-bit controller. It would not control the creation of either 32-bit or 64-bit compiled libraries. Is that correct?
Last updated: 2025-09-01

Post by drbuzz on Communication Error (#0) for IFM controller CODESYS Forge talk (Post)
Hi Folks, Every time I use an IFM controller I always seem to run into a problem connecting to it. I get the Communications Error (#0). So I thought I would share some tips and tricks. Once the CANfox Cable (EC2112) cable driver is installed, you can use the yellow app in the sys tray to blink the lights on the cable. Confirm the cable works in the IFM maintenance software by connecting to the controller and reading the information on it. Make sure to download an OS into the controller (the light will go from a fast blink to solid green). In Codesys V2.3, the communication settings for the CR0401 is 250kBaud by default and Node ID 127. What got me, was I needed to reboot the computer after the cable driver install. Also if your application has canbus settings in it which are changed from default, after the controller is power cycled, the new Node ID and Baud will be in effect. I made a handy guide because too much time has been wasted on this. Programming IFM CR0401 Serial/Can Programming Cable • Connect IFM EC2112 CanFox programming cable with connector adapter. • Make sure cable is linked to VM (if using VM). • Install drivers for cable if not installed. o Download from IFM EC2112 site. https://www.ifm.com/ca/en/product/EC2112 • Once Installed, reboot computer. • In system tray, there should be a yellow icon that you can open and check on programming cable. Select the cable in the list and flash the lights to confirm it is working. Maintenance Software • Install IFM Maintenance Tool Software. o Download from IFM Site. https://www.ifm.com/ca/en/download/eco100_MaintenanceTool • Open IFM Maintenance software • Select Basic System • Select CAN cable • It will tell you if you don’t have a cable connected. • Use Wizard if needed. • Read Channel Parameter on the Settings page, or get Identity in the System Information > Identity. • Default Node is 127 on a new unit. Baud is 250kBaud (bits/sec) • Controller information should populate. • Controller green light should be blinking at 5hz (meaning OK but no OS, just bootloader). • Click Software > Load. • Open the OS file. Should match Codesys version selection (for CR0401 this is version 3). o Download OS file from IFM Website. https://www.ifm.com/ca/en/product/CR0401 o It is located at the top of the download under “software for CR0401”. o Select the file and load it… this will take a minute. • Once completed the unit should now have a solid green light o Solid green means the controller has an OS but no application is running. Codesys V2.3 Application • Codesys needs to be downloaded and installed from the IFM website as it has the IFM libraries and license to use the software. o Download from the IFM CR0401 page. o https://www.ifm.com/ca/en/product/CR0401 • Create new application with the correct IFM controller or Open Codesys application. • Keep in mind that the PLC Configuration on the Resources tab can be changed for the CAN communication interface… so changes to node and baud will take effect after the first download and reboot of the controller. • Go to “Online” in the top menu and change “Communication Parameters” o The Local dropdown shows the last configuration used. All other interfaces will show below it and need to be updated when changed or used. o Confirm Node ID is 127 for the first download.  The NodeID will change to whatever the program has after (in my case 125).  Node Send Offset should be default at 1536  Node Recv Offset should be default at 1408  Can bus Baudrate should be 250 kbaud.  Yes to Motorola Byte Order  Block Transfer should be false and note used (60 is default setting).  Can Card Driver should match the systray item which is Sie_USB. • If the system populated the other one, just update and relay the communication parameters. The software will usually bring up the available cable and driver. • Go to “Online” and Login to download. o Press Yes to Download Application. I hope this helps!
Last updated: 2025-03-21

Post by shrikantp007 on new to codesys help on modbus with ardunio modbus rtu CODESYS Forge talk (Post)
Hello , I am new to codesys ,working with it for just 15-17 days so ,i think i am able to installed it and configure it ,not i want to use ardunio program (smart dustbin ,college project using motor and Ultrasonic Module HC-SR04 and servo motor). i use ardunio program to write code with chatgpt to work ardunio as a modbus rtu as i dont have ethernet or wifi shild ,i wrote program in ariduno but now don have idea what change i have to make in codesys to comunicate as modbus slave it give error with bus error ,where i can get all errors ? Thanks in advance :)
Last updated: 2024-07-21

Post by shrikantp007 on help to get codesys understand CODESYS Forge talk (Post)
Hello , I need some help on how to start with , 1) how to get test license to test codesys , 2) how to take a configuration backup or running process back and post file on fourm so people can understand and deploy same file and get idea what is missing or configure wrong 3) where i can get pdf for codesys admin or programmer 4) what is hardware recommand ,i am running on windows guest on kvm server .is it ok ? 5) i am trying to get ardunio porject working ,using ardunio board as a modbus slave but its not working some how https://forge.codesys.com/forge/talk/Engineering/thread/bf832569b8/ Thanks in advance . shrikant pune -india
Last updated: 2024-07-22

Post by joanm on Programmatically change the IP addresses of the Modbus TCP slave devices CODESYS Forge talk (Post)
Hello all, I am working in a project in which there are multiple Modbus TCP slaves. I need to be able to change the IP addresses of those devices from the HMI and I was planning to use the process depicted here: https://faq.codesys.com/display/CDSFAQ/Modbus+TCP+Slave%3A+Dynamic+Setting+of+the+IP+Address I can see the port number is what is used to specify which slave device we want to modify the IP address of. This said, can I freely set arbitrary port numbers to each device? I mean, can I set the first device to be at port 502, the second one at port 503... Any drawback or restriction? Is there any other way to reference to the device without having to change the port numbers? Thank you all in advance.
Last updated: 2024-01-04

Post by yang123 on EtherCAT Can't reconnect to servo drive CODESYS Forge talk (Post)
I am using Ethercat Master 4.6.0.0 and have use the automatic restart slaves feature. But we found of after the Ethercat communication normal and slave drive power-off and power-on the slave can't reconnect sucess. The PLC Log show the drive was al status "6#34 : Invalid DC Timeout Error" and its was reconnection sucess first but seconced later the drive will show the "16#2C : Fatal Sync error" and then drive will can't reconnection. Other slave are reconnect sucess which was link after the can't reconnect's drive the drive was OMRON R88D-1SN
Last updated: 2024-01-23

Post by jens on Modbus tcp - channel CODESYS Forge talk (Post)
Help wanted This is the first time i'm doing a Modbus Tcp project. I have some VLT with a extension module MCA-122. i'm currently unable to write to the VLT slave, but i can read from status word parameter=1603 and address := 16029 where the address is calculated from parameter is ((id x 10)-1). in the manual the functions that are supported are 3 hex, 6 hex, 10 hex, b hex and 11 hex. read holdin registers, write single register, write multiple registers, get comm. event counter, report slave id. i'm only using the Modbus Slave Channel is this wrong when trying to write to the vlt ?
Last updated: 2024-06-13

Post by thewizard8 on Raspberry PI4 Serial Port CODESYS Forge talk (Post)
Hi Dear All, I'm using my raspberry PI4 as a CoDeSyS PLC (Build from scratch with custom electronics). I was able to implement all fieldbuses with the exception of Modbus Serial. I'm using the internal Port (GPIO) and I configured it in /etc/Codesyscontrol_user.cfg the following away: [SysCom] Linux.Devicefile.1=/dev/ttyUSB0 Linux.Devicefile.2=/dev/ttyS0 I'm using COM2 on Master configuration. I'm using a interface board from TTL/RS485 (bidirectional board), and it's works perfectly with other devices but not in CoDeSyS. I'm able to send data with python script and read it on my pc using putty, but when I use a modbus slave simulator to interface with codesys I always get red icons on master and slave. (Please find image attached). I'm pretty shure that this might be a bad parameter on my CoDeSyS runtime configurstion file. Can someone help me? I'm stuck and this is for my master degree certification.
Last updated: 2024-03-18

Post by lsislsis on SIGABRT Error CODESYS Forge talk (Post)
2024-11-08T13:39:07.354Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state* We recommend a reboot of the controller now! 2024-11-08T13:39:07.354Z, 0x00000111, 8, 260, 3, #### Exception: More than 2 exceptions in CH_COMM_CYCLE: Stop logging 2024-11-08T14:36:33.126Z, 0x0000100d, 1, 0, 0, Demo mode expired. 2024-11-08T15:35:49.253Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state We recommend a reboot of the controller now! 2024-11-08T15:42:54.664Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state We recommend a reboot of the controller now! *
Last updated: 2024-11-08

Post by markus-huber on CodeSys SVN doesn't work CODESYS Forge talk (Post)
I installed CodeSys V3.5 SP9 for HY-eVision2 1.18.0.0 and activated the License Keys for SVN and noticed that the "SVN" doesn't pop up when i go on Menu - Project. For some reason the SVN works on CodeSys SP10. I already deinstalled all CodeSys Applications and installed them again but it's the same. Maybe the problem already occurred and someone could help me.
Last updated: 2024-02-20

Post by davidbo on Toradex and CODESYS and licensing CODESYS Forge talk (Post)
I am evaluating a Toradex product for use with CODESYS. Toradex and CODESYS are partners, but using "CODESYS Virtual Control for Linux ARM64 SL" together with a carrier board "Verdin mallow" However it doesn't seem to be a soft container for licenses. So how do I install a license
Last updated: 2025-10-20

Post by konstantin on Lenze i950 Servo and WAGO PFC200 CODESYS Forge talk (Post)
Hello, In our workshop we have a Lenze i950 servo drive that has an EtherCAT bus and CiA402 compatibility. The WAGO is PFC200 750-8212 and as per documentation it has built-in license for SoftMotion Light functionality. It is not capable of supporting the full SoftMotion functionality like gearing and synchronizing. I added the EtherCAT esi files from Lenze and the EtherCAT master does see the drive, then I added a SoftMotion Light Axis object. The problem is that I can only energize the axis, I cannot execute any other commands. I set the positive and negative torque limits from the PDOs to 200% and when I try to move the axis by force it does not move back to its original position. I use the SML function blocks from the PLCOpen library and the error from the function blocks is that the op mode cannot be changed. Then I tried using a standard SoftMotion axis object and everything works fine, except the MC_Home function block. The axis moves back to its position when forced out of it. I follow this guide from Lenze - Lenze i950 CODESYS V3 What could cause this issue with the SoftMotion Light axis object? Best Regards Konstantin Kolev
Last updated: 2026-02-11

Post by em1681 on Modbus RTU over 750-652 CODESYS Forge talk (Post)
Hi, It's my first time operating in Codesys 2.3, but I have done a good amount of Codesys programming, so I'm a little familiar. I haven't done a lot of RTU, but a lot of Modbus TCP. I don't have the PLC in my reach at the moment, but I'm trying to be a little ahead. We're adding the 750-652 module to read energy from a flowmeter over RTU. There will only be 1 slave. I attached pictures of my current hardware, PLC code, the register datasheet from the slave and the only modbus serial library I seem to have available. I'm uncertain if this will work. Any help or clarification on how things work will be greatly appreciated. Thanks in advance.