Post by felipemsgarcia on Axis EtherCAT address
CODESYS Forge
talk
(Post)
Hello, Thank you for your answer. I'm afraid I was not clear on what I was trying to achieve. I'm trying to change parameters and command axes from inside a function block and the first thing that came to my mind was pass both the EtherCAT slave and axis to the function block (as image attached). But, I believe it's worse than just pass directly the EtherCAT slave address to the function block (is it???). However I was wondering if there was a way to get the EtherCAT address directly from the axis, so I don't need to pass the EtherCAT slave nor the EtherCAT address to the function block. Thank you again!
Last updated: 2025-03-07
Post by milosfejgl on Codesys Licenses - How to reload them after updating the Raspberry Pi OS
CODESYS Forge
talk
(Post)
We use several control units running on Raspberry Pi, programmed using Codesys software, with multiple licenses stored as soft containers. We are planning to update the SD card image of the Raspberry Pi to a newer OS version. However, we are concerned that this process might result in the loss of our soft container licenses. Is there a way to temporarily deactivate the license so that it can be reactivated on the updated system? Alternatively, what would be the best method to preserve the licenses during the update? Thank you in advance for any responses!
Last updated: 2025-03-13
Post by madskaizer on ModbusTCP Slave Device, maximum uiClientConnections?
CODESYS Forge
talk
(Post)
I got a Wago PFC200V2, running Codesys 3.5.16.40, 100ms scan cycle, consumes about 20ms. It will randomly crash the runtime every 10 minutes to a few hours. We suspect an overloaded ModbusTCP Slave Device, as this is work done by a 3rd party contractor, but we can not find anything in the help files or documentation, that mentions a hard limit on maximum number of clients connections. This PLC currently has 44 client connections to the Slave Device and 29 slaves configured for its own Master Device. This topic metnions a hard limit of maximum 16 connections, but where is this written? https://forge.codesys.com/forge/talk/Engineering/thread/bd95b9d6d2/
Last updated: 2025-03-26
Post by bjarne-pagaard on Global Variables
CODESYS Forge
talk
(Post)
Old thread, I know - but it still has good answers. I would like to add a bit of info to it, as I was having a problem that lead me to this thread, but didn't give an exact answer. I am porting a project to a different PLC architecture. (Wago PFC300) A GVL named 'GVL' in the POUs section of my project was shadowed by a PLC-specific library in the Application->Library Manager. So all the existing references in the device specific code to 'GVL.something' would not resolve. Right-clicking the GVL in the code and 'Go to definition' would point me to the library in the Application Library Manager. All I had to do from there, was right-click the library, and set the property 'Only allow qualified access to all identifiers' in the library.
Last updated: 2025-04-11
Post by rossanoparis on Internal Error (ARM): Unsupported conversion! With new version v3.5 SP21
CODESYS Forge
talk
(Post)
I have updated CODESYS development tool to the version v3.5 SP21 (64bit) The previous version was v3.5.20.40 Compiling an existing application with the new evelopment tool I get the following error. kunbusiodrvrevpibridge, 1.4.1.0 (kunbus gmbh): IoDrvScanModules [IoDrvRevPiBridge](Line 51, Column 1 (Impl)): Internal Error (ARM): Unsupported conversion! This error was not reported in the previous compiler version and is now highlighted in a third-party library, which I cannot change or modify. The error is due to the following conversion: m_udiError := TO_UDINT(excCode); . The excCode variable is a system type, declared as shown below, and should be converted to a UDINT excCode : __SYSTEM.ExceptionCode; m_udiError: UDINT; . I would appreciate it if someone could provide feedback on this issue.
Last updated: 2025-04-15
Post by kut69 on Retain / Persistent Variables in Codesys for Raspberry Pi
CODESYS Forge
talk
(Post)
Hi, I am interested in details about the .ret file in the filesystem. I have already a project where the file is used (write on demand, read by start) and I want to share it as 'default input' for test devices using the identical application. Opening the .ret file content in a hex editor (I only use a single string retain var) I asked myself what the meaning of the first 24 bytes is. It neither contains a handle to the application nor a reference to the variable. Is this maybe a timestamp? Or a CRC/checksum? Regards, Thomas
Last updated: 2025-05-19
Post by abuckie on Getting raw value as full resolution for ADS1115
CODESYS Forge
talk
(Post)
I just found this and I am getting a value larger than 16 bit, around 81000 something. I am reading a 5 volt value and I am using level shifters for the i2c bus. This is how I have the channel configured: ADS1115.usiAddress := 16#48; ADS1115.ChannelConfigs[0].Active := TRUE; ADS1115.ChannelConfigs[0].PGA := FSR_6144mV; ADS1115.ChannelConfigs[0].InputMux := Single_0; RawAnalogValue := ADS1115.Channels[0].Value; It looks like every value is a multiple of 3. Any idea where to look to fix this? I think i found what I want to change in UpdateChannels Channels[FChannelNo].Value := INT_TO_REAL(WORD_TO_INT(LValue) * GetFullScaleRange(ChannelConfigs[FChannelNo].PGA)) / 2048.0; I try to edit it but I can't, sorry if this is a basic question, I am new to CODESYS.
Last updated: 2025-05-22
Post by rockallsue on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
Some developers export ST code manually and edit it in VSCode, then copy it back. However, a more practical approach might be using automation scripts (PowerShell, Python) to extract and inject code into the CODESYS project. You could also check if CODESYS Automation Server or CODESYS API allows better ST access for external tools. https://www.codesys.com/the-system/releases-updates-lifecycle/release-plan-roadmap.html Network drive issues are particularly painful. As a mitigation, you could try using local project storage with periodic cloud sync instead of directly saving to a network drive. Using Rsync or Syncthing for automatic but safe synchronization might reduce risks of file corruption.
Last updated: 2025-06-03
Post by durallymax on Dynamical scaling of bar graph without the bar itself
CODESYS Forge
talk
(Post)
I'm a fan of the analog indicators from ISA101. To recreate these, I use a number of rectangles that are dynamically sized and colored based on the input configuration. To keep it standard and easy, everything is built around 100px height. Then when instantiated in a frame, it can be resized as needed with the math remaining the same. The math logic is in a METHOD called by the rear most rectangle. These indicators do not use a "filling" bar graph, rather a fixed bar graph with a carrot to track the current value.
Last updated: 2025-06-06
Post by kareem-pt on Velocity is too low even though correct value is reported
CODESYS Forge
talk
(Post)
Hello, I'm playing around with a single axis. I've setup scaling and set the drive to move 360 degrees in the commissioning tab. The axis does move 360 degrees, but it moves much slower than the 360 degrees per second that I set for the velocity. It seems to be about 3 times slower (taking about 3 seconds instead of 1). This is despite the set and actual velocity both being displayed as 360. The acceleration, deceleration and jerk are all set to very high values. I'm just running this on my PC, using demo mode (no license purchased yet). I've attached a video showing the problem. Does anyone know what the problem could be? Thanks
Last updated: 2025-06-06
Post by levih on FbHTTPs_Get how to get data from a website and use it in codesys
CODESYS Forge
talk
(Post)
You get an array of DWORD into your receive buffer. You need to process this into usable data, before you can fit it into your DUT. I've made it work using FbWrite_ToIEC_ByRule in stead of Fb_JSON_ParseAndModify. I've attached images of the code. You receive the data into ARRAY[0..1023] OF DWORD. Then you use that array as the input for fbWrite_ToIEC_ByRule. To get the output from this you define a rule to fit the expected data structure including nesting levels. The you feed the rule into FbWrite_ToIEC_ByRule and then you can set the output to be of your DUT type.
Last updated: 2025-06-16
Post by buczekj on About CPU Loading
CODESYS Forge
talk
(Post)
This is a phenomenon that I have seen myself and with others. Texas instruments wrote an application note with this same issue. They noted with Codesys 3.5.19.10, that selecting CPU 1 as the EtherCAT task showed CPU spiking improvements over the performance of cores 0, 2, and 3. It appears to be linked to EtherCAT, are you configuring for use with distributed clocks? If so, I recommend choosing the 'Based on Input Reference' option. I have found it to reduce the CPU usage spike maximum slightly (see attached). See link to TI (also attached in case link breaks) https://www.ti.com/lit/an/spradh0/spradh0.pdf?ts=1723546111357
Last updated: 2025-07-01
Post by manuknecht on Using an Axis of an Axis Group in Torque Conctrol
CODESYS Forge
talk
(Post)
I don't seem to be able to use an axis, which is part of an Axis Group in torque control mode. I call the SMC_SetControllerMode FB to switch from position to torque control mode, followed by the SMC_SetTorque FB to set the desired torque. This works flawlessly for most axes, however if an axis is part of an axis group, switching the controller mode seems to work without any issues, but the desired torque is never set. SMC_SetTorque does not return an error, but fSetTorque of the axis is never changed. Disabling the axis group before does not change anything, but if I use MC_UngroupAllAxes before changing the controller mode, it all works as it should. Is there no way to control a single axis in torque control, if it is part of an axis group?
Last updated: 2025-07-17
Post by andrej on Signing of Boot Application for Raspberry Pi
CODESYS Forge
talk
(Post)
Hello all, I would like to sign my boot application for my Raspberry PI. I generated the X509 Certificate and loaded it to the raspberry. It is successfully displayed as trusted certificate. However, I cannot download and start the Application to the Rasperry, due to a signature mismatch.The error message is rather clear, but I still donβt see how I can fix the issue, since the certificates on the Controller seem to mach the certificate in the user profile. Could you tell me where the error is or which step I am missing. Many thanks and kind regards Andreas
Last updated: 2025-07-17
Post by andrej on Signing of Boot Application for Raspberry Pi
CODESYS Forge
talk
(Post)
Hello all, I would like to sign my boot application for my Raspberry PI. I generated the X509 Certificate and loaded it to the raspberry. It is successfully displayed as trusted certificate. However, I cannot download and start the Application to the Rasperry, due to a signature mismatch.The error message is rather clear, but I still donβt see how I can fix the issue, since the certificates on the Controller seem to mach the certificate in the user profile. Could you tell me where the error is or which step I am missing. Many thanks and kind regards Andreas
Last updated: 2025-07-17
Post by andrej on Signing of Boot Application for Raspberry Pi
CODESYS Forge
talk
(Post)
Hello all, I would like to sign my boot application for my Raspberry PI. I generated the X509 Certificate and loaded it to the raspberry. It is successfully displayed as trusted certificate. However, I cannot download and start the Application to the Rasperry, due to a signature mismatch.The error message is rather clear, but I still donβt see how I can fix the issue, since the certificates on the Controller seem to mach the certificate in the user profile. Could you tell me where the error is or which step I am missing. Many thanks and kind regards Andreas
Last updated: 2025-07-17
Post by fedex03 on Read Global Variable from an IoT Device
CODESYS Forge
talk
(Post)
Hello everyone, I am new to the forum, and to programming with CodeSys. I am dealing with IoT device for industry and I should check if a device is able to read/write global variables in an EtherNet/IP Master. Since I do not have an EtherNet/IP PLC, I thought of using CodeSys as a softPLC. I created a program with a set of global variables (GVL) and a task that increments them. I would like to know if I need to enable any options so that the global variables can be read by IoT devices. My device supports Class 2 Class (Explicit Messaging Connection) communication. Thank you in advance for your help.
Last updated: 2025-07-22
Post by antonz on CoDeSys v3.5: creating libraries for both 32-bit and 64-bit controllers
CODESYS Forge
talk
(Post)
Follow up question: in the Project Settings, under Library Development, there is an option related to this: Check all Pool Objects -> Pointer size to use Options are: * 32 Bit * 64 Bit * 32 and 64 Bit The descriptions and online help suggest to me this is only relevant for checking and showing any incorrect pointer types as an error in the IDE. E.g. using a DWORD to store a pointer value on a 64-bit controller. It would not control the creation of either 32-bit or 64-bit compiled libraries. Is that correct?
Last updated: 2025-09-01
Post by voffi on projects.open not working for file based storage project
CODESYS Forge
talk
(Post)
Hello! Opening a project from a python script given at the CODESYS command line does not work for me with a file based storage project. Example: Running projects.open("test.project", primary = True) works but converting the project to a file based storage project and then give the folder name as an argument to project.open Running projects.open("test.fbsproj", primary = True) does not work. We decided to work with file based storage for the project. Is there a scripting API for file-based storage to e.g. convert it while running the script back or how to open file based storage project with projects.open? Thank you! voffi
Last updated: 2025-09-05
Post by bbmussatto on Connetion with Topcon Opus B3 ECO Full display
CODESYS Forge
talk
(Post)
I have a Topcon Opus B3 ECO Full display and i wanna program it with codesys, but i cant connect it to the display. After creating a new project, i choose the device "Opus B3-B4-B6-3.5.19.50" that is already available in my version of codesys, but i think the problem is that my version of codesys or something else is not the same as the codesys runtime version running on my display. Can anyone tell me how i can see the codesys runtime version on my display? i tried looking in the settings (Daemon > CDS) on the display, but all i see is "N/A" for "Customer Number", "Customer Part Number" and "Customer Serial Number". Can anyone help me make this connection?
Last updated: 2025-10-07
Post by ouzago on ERROR C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr
CODESYS Forge
talk
(Post)
When I created a new project in CODESYS using the "Standard Project" template and then added a Visualization, I was receiving the C0138 error during compilation. This issue persisted even with a new, completely empty project. A Quick and Effective Solution (My Method): After many attempts, I solved the problem as follows: From the File -> New Project menu, I selected the "HMI Project" template directly, instead of the "Standard Project" template. After creating the project with this template, I added my POUs, Tasks, and programs (e.g., Ladder, ST). Using this method, the project compiled successfully without any errors. So, my question is: are there any other solutions besides this method?
Last updated: 2025-10-07
Post by reinier-geers on Web client
CODESYS Forge
talk
(Post)
Hi, ive got the webclient example. So now i want to use it. Ive got an example. but thats some JSON type. As far i know is JSONe som kind of structure. But thats new for me. I think its posible with get. Can someone help me? This is the link witch explains what to do https://reversed.notion.site/Marktprijzen-API-89ce600a88ac4abe8c2ad89d3167a83e i tried this : sURL : STRING(1024) := 'https://graphql.frankenergie.nl/get/ {"query":"query MarketPrices {\n marketPrices(date:\"2022-01-01\") {\n electricityPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n gasPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n }\n}\n"}'; // URL But thats a bad request
Last updated: 2025-10-08
Post by kevinl on RevPi Connect RS485
CODESYS Forge
talk
(Post)
I figured this out on my own with this logic: usually the Serial port on a Raspberry pi is on /dev/ttyUSB0 then you need to set linux.DeviceFile=/dev/ttyUSB in codesys you then must set com port to 1 so i assumed codesys subtracts 1 from the number and adds this to the filename... (in code it would look like this: var comPort : byte := '1'; linuxDevice : string := '/dev/ttyUSB'; filename : string; end_var filename := concat(linuxDevice, (to_string(comPort-1)); filaname then is /dev/ttyUSB0 RevPi uses ttyRS485 as Serial port so you must remove the last number from the name and set the com port to this number +1 i hope this is understandable ;-)
Last updated: 2023-12-11
Post by sawicpx on CANbus Remapping PDOs During Runtime
CODESYS Forge
talk
(Post)
Hello, I am working on an application where I need to remap PDOs to a different CANopen object during runtime depending on what value is at a specific register. I have gotten to the point where I put the device into Preoperational State using the CIA405.NMT function. I then reconfigure the PDO 180x and 1a0x obejcts usings SDOs to point to a new canopen object on the device however when I go to restart the Device from PREOP to OP using the CIA405.NMT function the device is reset back to the original configuration as per the initial setup. I am wondering is there any way to change the PDOs at runtime is there some more functionaility I can access to do this. Any direction is appreciated!
Last updated: 2023-12-22
Post by davidbo on Does the new license policy means I have to upgrade everything?
CODESYS Forge
talk
(Post)
We have several old project written with 3.5.17 and 3.5.18 and also some older Until now when a customer ordered a product from us. We just installed (we have a tested image) and added a license Now the license policy has changed and we have to buy a License Control Basic S or M However it only works with CODESYS Development System Version 3.5.19.10 or higher Does that mean we have to upgrade all our old products? That is not a simple task as a previous post has explained with weird error messages from CODESYS V3.5. Next we have to do rigorous testing of our applications afterwards. It is very expensive