Post by andrej on POU - Access to runtime
CODESYS Forge
talk
(Post)
Hello all, when creating a POU, the Codesys IDE allows the setting "Enable System Call" (in the Settings, Property -> Build), see picture. The name suggest, that runtime functionalities i.e. functions of codesyscontrol such as "stop plc" etc. can be directly called. I tried various approches without success, the following does, unsurprisingly not work. FUNCTION accessRTE: BOOL; ****************************** codesyscontrol.stop(); Can you please tell me how I can make a system call to codesyscontrol from a POU. Or could you provide me with a use case for this setting. Many thanks for your feedback and kind regards Andrej
Last updated: 2024-03-02
Post by carohe on VisuNamespace != null
CODESYS Forge
talk
(Post)
Hello, this error occured frequently over the past couple of weeks. I found out, when adding a webvisu, CODESYS added Visu libraries in the library manager. One of the libraries was the "VisuElemsAlarm" library. In my case it added this one with the version 4.3.0.0. However another library that also contained the "VisuElemsAlarm", used the "VisuElemsAlarm" with the version "4.4.0.0". After changing the Version "4.4.0.0" and uninstalling this version, the error has not occured anymore. Regards, carohe
Last updated: 2024-04-02
Post by rossanoparis on RevPi CONNECT+, CODESYS, EtherCAT master "Filedbus lost synchronicity"
CODESYS Forge
talk
(Post)
Hello @rmaas I assume, you've already verified and tuned everything regarding the EtherCAT network. In my case the problem was due to a wrong core assignement. I suggest to not use the core #0 for your EtherCAT task. The OS realtime patch, which is present on RevPi OS, uses the core #0 for its porpouses and it mustn't be used by any other task which requires realtime and deterministic features. regards Rossano
Last updated: 2024-04-11
Post by alez on CANOpen SDO to write VISIBLE STRING
CODESYS Forge
talk
(Post)
Hello, I am experiencing difficulties in configuring a CANopen device by sending SDOs. In particular I am attempting to write an Object Dictionary that has VISIBLE STRING as the Data Type. When I try to configure the sending of an SDO from Codesys to configure this parameter I am not allowed to enter a string value. In my particular case I am trying to change the Manufacturer Device Name ( Index 0x1008 ). Could it be that Codesys doesn't manage these types of variables?
Last updated: 2024-04-29
Post by gseidel on CNC - system goes to X=0 Y=0 before CNC file execution starts, how to avoid that?
CODESYS Forge
talk
(Post)
Hi peterned, the start position given in the CNC properties is only used if you use the compile mode OutQueue. With compile mode SMC_CNC_REF, you need to provide the start position in the IEC application. The function block SMC_NCInterpreter has an input piStartPosition. You can initialize it with the output of the forward kinematic transormation FB for your machine. In your case probably SMC_TRAFOF_Gantry2. Best regards, Georg
Last updated: 2024-04-30
Post by timvh on JSON
CODESYS Forge
talk
(Post)
I don't know the details of jsonArrayWriter, but the common behaviour for an xExecute input is that the FB starts on the trigger that it gets TRUE. In your case xExecute is never FALSE, so it is never triggered again to start the jsonArrayWriter. So change the condition from TRUE to a variable which you set to TRUE with the "xFirst". Then when the jsonArrayWriter is done (xDone), or has an error (xError), then set this variable to FALSE.
Last updated: 2024-05-01
Post by rabaggett on No Visu on RasPi
CODESYS Forge
talk
(Post)
OK, I got this to work as shown above in mos89p's comment. What I did: Tools/Update Raspberry Pi. Reloading the runtime seems to have solved the web problem. I can view the visualization on the Pi and laptop using a browser as shown above. Thanks! But Isn't the visualization supposed to take over the screen of the Raspi? When I run visu projects on Windows or Wago, the visualization shows on that device's screen by default.. But this is not happening in this case
Last updated: 2024-06-20
Post by bschraud on runtime received SIGABRT
CODESYS Forge
talk
(Post)
Hallo, seit der Umstellung meines Projektes auf die aktuelle Codesys Version mit aktuellen Bibliotheken und Aktualisierung der Runtimer Version bekomme ich im Zeitraum 15min bis 1h nach Neustart des Target Systems folgende Fehlermeldung: runtime received SIGABRT - system may be in an inconsistent state Der Fehler kommt auch nach dem Start des Systems ohne eine Benutzeraktion zuverlässig, aber in unterschiedlichen Zeiträumern. Hier sind die Logs und Daten, die ich dazu ermitteln konnte: $ tail -f /var/opt/codesys/codesyscontrol.log 2025-04-03T06:54:37.659Z, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client for Extern-ID: 594337835 2025-04-03T06:54:37.660Z, 0x0000100c, 1, 0, 0, Visu_PRG: Creating Client successful for Extern-ID: 594337835 Returned IEC-ID: 0 2025-04-03T07:01:38.135Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! 2025-04-03T07:01:38.135Z, 0x00000111, 8, 260, 3, #### Exception: HANDLED EXCPT* <excpt>NonContinuable</excpt> in CH_COMM_CYCLE 2025-04-03T07:02:18.181Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! 2025-04-03T07:02:18.181Z, 0x00000111, 8, 260, 3, #### Exception: HANDLED EXCPT* <excpt>NonContinuable</excpt> in CH_COMM_CYCLE $ vmstat 1 procs -----------memory---------- ---swap-- -----io---- -system-- ------cpu----- r b swpd free buff cache si so bi bo in cs us sy id wa st 1 0 0 271120 33976 342284 0 0 135 2 2387 4751 10 7 82 1 0 1 0 0 271024 33976 342380 0 0 0 0 10163 20427 10 9 81 0 0 1 0 0 271056 33976 342380 0 0 0 0 8455 16869 9 5 86 0 0 0 0 0 271040 33976 342380 0 0 0 0 8674 17484 9 4 87 0 0 0 0 0 271072 33976 342380 0 0 0 0 10070 20350 7 7 87 0 0 1 0 0 271040 33976 342380 0 0 0 0 10354 20802 10 6 84 0 0 0 0 0 271072 33976 342380 0 0 0 0 8401 16923 8 6 86 0 0 $ vcgencmd measure_temp temp=56.9'C $ uname -a Linux PAC4 5.10.103-v7+ #1529 SMP Tue Mar 8 12:21:37 GMT 2022 armv7l GNU/Linux CODESYS V3.5 SP21 Runtime: Codesys control for Raspberry Pi MC SL V 4.13.0.0 Hinweise auf ein instabiles OS oder instabile Netzwerkverbindungen konnte ich keine finden. In dmesg und im syslog gibt es keine Auffälligkeiten. Die anderen Posts zu diesem Thema wurden nicht beantwortet. Hat jemand einen Tip, wie man an das Problem herangehen kann? Vielen Dank
Last updated: 2025-04-03
Post by clarenced on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks
CODESYS Forge
talk
(Post)
Using codesys v3.5 SP21 Patch 1. We are using Visualization to display alarms. Other then the automatically created AlarmManagerTask, there is no code written to call AlarmStorage_Prg. Any ideas why we would be seeing this error in the log? The runtime actually shutdown. Not sure if that was caused by this error or not. 2025-08-03T02:45:35.444Z, 0x00001012, 4, 0, 0, * ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks. 2025-08-03T03:48:15.294Z, 0x00001012, 4, 0, 0, * ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks. 2025-08-03T04:38:11.557Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! * 2025-08-03T04:38:11.576Z, 0x0000010f, 8, 1, 0, #### Exception: SysSemEnter - Semaphore deadlock detected - owner thread died [tid:726740] - system may be in an inconsistent state. 2025-08-03T04:38:11.576Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! 2025-08-03T04:38:11.576Z, 0x00000001, 8, 260, 3, #### Exception: HANDLED EXCPT* <excpt>NonContinuable</excpt> in CH_COMM_CYCLE 2025-08-03T04:40:12.308Z, 0x00000001, 1, 0, 35, CODESYS Control shutdown... 2025-08-03T04:40:13.436Z, 0x00000071, 1, 0, 13, Webserver stopped 2025-08-03T04:40:13.437Z, 0x00000114, 2, 1, 0, !!!! Warning: task_signalhandler_exit [MainTask] lost cycles: 14809 2025-08-03T04:40:13.497Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>IecVarAccess</cmp>, <id>0x00001007</id> <ver>3.5.3.64</ver> 2025-08-03T04:40:13.506Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>AlarmMgr</cmp>, <id>0x00001012</id> <ver>4.7.0.0</ver> 2025-08-03T04:40:13.513Z, 0x00000071, 2, 0, 14, !!!! Warning: Unbalanced calls to WebServerRequestRunning/WebServerReleaseRunning 2025-08-03T04:40:13.513Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>IECVisualization</cmp>, <id>0x0000100c</id> <ver>4.7.0.0</ver> 2025-08-03T04:40:13.611Z, 0x00000124, 1, 0, 0, Provider 'AddressSpaceFragment Provider' (version 0x3051500) unregisterd at the OPC UA server. 2025-08-03T04:40:13.611Z, 0x00000124, 1, 0, 0, Provider 'OPC UA for IEC-61131-3' (version 0x3051500) unregisterd at the OPC UA server. 2025-08-03T04:50:17.708Z, 0x00000001, 1, 0, 36, CODESYS Control shutdown done
Last updated: 2025-08-04
Post by bahrt on Mapping GPIO and adding GPIO configurations
CODESYS Forge
talk
(Post)
Hi I am about to configure ALL GPIOs on a Raspberry Pi 3 model B V1.2. It seems that I have limited understanding of why not all the IO’s become available with the corresponding mapped IO’s – the 'dwInUse' contains mapping of the inputs from GPIO0 to GPIO27. But 'dwInputs' are only showing GPIO0 to GPIO8 and GPIO15 as available inputs. These mentioned inputs work fine You will be able to watch the limited mapped IO activity here: https://drive.google.com/file/d/1zz4PBNBfRZBF2YkiJ2VQxw6L9MBVji7R/view?usp=sharing Can you please bring your best idea on why GPIO09 to GPIO14 and GPIO16 to GPIO27 state are zero in the dwInputs register? Thanks in advance. Best regards Andreas Bahrt
Last updated: 2023-11-16
Post by trent on Automation server - trends stop recording - need to manually reconnect
CODESYS Forge
talk
(Post)
Hi All, I use the analysis page in automation server to capture historical trends from my PLC - i only sample one point per hour but it does the job (for now) One issue I have is I often log on to analysis page to find the system has stopped recording trends from my PLC. To fix this, I need to choose "state information" in the "List view" under PLC and click "Reconnect" When I do this I see my variables listed under "parameters" under "PLC Details" start updating again and the trend in Data analyzer continues to update. My Question, Why do I need to manually reconnect? Is there a way to get automation server to automatically reconnect to the PLC so I continue to capture data from the PLC? Regards, Trent
Last updated: 2024-10-22
Post by eozupek on File Transfer Error 4
CODESYS Forge
talk
(Post)
I couldn't exactly solve the file transfer when I wanted to do multiple transfers while the compiler was open in a way that I couldn't understand. Notification from target: runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! * details of the target component that sent this notification: [CmpName=SysExcept, CmpId=0x00000103, ClassID=0X0001008, ErrorID=0X00000001, InfoID= 0X0000000j] I see the warning. I couldn't find out why error code 4 is coming or what kind of measures I need to take to prevent it from coming within the application. Can you help me? regards Emre OZUPEK
Last updated: 2024-11-24
Post by tyleretn on Codesys 3.5 SP18 P4 Freezing on Library Update
CODESYS Forge
talk
(Post)
I have created a library with both code and visualizations to be used in multiple other projects. After I update the library version into the library repository, I have much difficulty updating the version into the main project. I can always update the library version in the Library Manager just fine. My issue, is sometimes Codesys will freeze when opening the visualization that uses the library visualizations. Sometimes it opens, but freezes when I try to access the library visualizations from the Visualization Toolbox. I try letting Codesys run for upwards of 4+ hours and it is stuck in this state. On very rare cases I have no issues and can continue with my work. I haven't found a consistent reason or work around. Has anyone else had this happen?
Last updated: 2025-02-27
Post by budd7566 on Text size suddenly changed
CODESYS Forge
talk
(Post)
Iv been working with a Deep Sea Electronics DSE840 for about 6 months. I have a development version of my program working with a state machine and a basic gui interface. I went to implement CAN and suddenly the text on the gui on the controller is much larger than before. I could flash old versions of my project and the text was the correct size, but if i renamed the project file, the text displayed would be large. The visualization in CODESYS always shows the expected size, but not the controller. I did a fresh install of CODESYS and even a new project with only one text box, I cant get the text size on the controller to match what is displayed in codesys to match. Any advice?
Last updated: 2023-12-09
Post by sawicpx on CANbus Remapping PDOs During Runtime
CODESYS Forge
talk
(Post)
Hello, I am working on an application where I need to remap PDOs to a different CANopen object during runtime depending on what value is at a specific register. I have gotten to the point where I put the device into Preoperational State using the CIA405.NMT function. I then reconfigure the PDO 180x and 1a0x obejcts usings SDOs to point to a new canopen object on the device however when I go to restart the Device from PREOP to OP using the CIA405.NMT function the device is reset back to the original configuration as per the initial setup. I am wondering is there any way to change the PDOs at runtime is there some more functionaility I can access to do this. Any direction is appreciated!
Last updated: 2023-12-22
Post by ph0010421 on Stepper Drive with Ethercat
CODESYS Forge
talk
(Post)
Hello That's certainly CiA402. I'll attach a part of the manual for my servos, but the state diagram should be the same at yours. To be sure, get one from your manufacturer. Look at the bits in the StatusWord to see where you are in the diagram, then twiddle the bits in the ControlWord to get you to the next step. Then there are other bits in the StatusWord to tell you 'InPosition' and things like that. From the screenshot, as it mentions only 'PositionProfile' the driver will create the motion profile. So you need to put a target position in here - there should be profile velocity somewhere? Possibly, you need to write these with SDO's? At the minimum, you need to write a value to 0x6081, 0x6083 and 0x6084 (velocity, accel, decel)
Last updated: 2024-03-22
Post by lzml on Safety
CODESYS Forge
talk
(Post)
I have a problem with a project that uses EtherCAT Safety. The project is developed with CODESYS version 3.5.19.20, runtime 3.5.18.30, safety CPU EL6900 4.3.1.0, TCEL6900FBS 3.5.1.10, IODrvEL6900 4.3.1.0, IODrvEtherCAT 4.1.0.0. The safety project works correctly, but when I download the PLC project for modifications, the ESM objects are no longer aligned with the states inside the safety program. Specifically, inside the safety program, they are seen as true, while outside the safety program, the state is reported as false, but not for all ESMs, only some. I have already tried to completely redo the safety from scratch, but nothing has changed. Any solutions? Thanks
Last updated: 2024-05-24
Post by alimans on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
For anyone still experiencing this issue, here’s how I managed to solve it: Symptoms: 1. Sometimes, on the first start of CODESYS Runtime, the modules fail to run. 2. After disconnecting and reconnecting the communication cable, the drive does not start again. 3. MC_Reset cannot clear the fault. Solution (what worked for me): 1. Check the axis communication using the SMC_CheckAxisCommunication function block (FB). 2. If CheckAxisCommunication.eComState of the axis is equal to or higher than SMC_CommunicationState.SMC_COMSTATE_BASE_COM_INITIALIZATION, then 3. Use the SMC3_ReinitDrive function block to reset the drive — and it works. For more information, refer to the official CODESYS documentation: 👉 https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/DriveInterface/AXIS_REF/SMC3_ReinitDrive.html
Last updated: 2025-10-23
Post by imdatatas on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
Dear @alimans, Additionally, As far as I know since starting from Softmotion V4.18.0.0 automatic restart behaviour for an axis has been changed for this issue. See below explanation from release notes. "With CODESYS SoftMotion 4.18.0.0, the behavior of SoftMotion axes after a loss of communication to the servo drive has changed. Now, an automatic reinitialization is performed as soon as the communication is established again. Before, an explicit call to SMC3_ReinitDrive had to be performed. An example for a loss of communication is that the cable to one of the drives is unplugged." Regards, imdatatas
Last updated: 2025-10-23
Post by msegon on OPC UA Client failed to connect
CODESYS Forge
talk
(Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I'm trying to read data from Tridium Niagara 4.15 OPC UA Server, but I get the error BadCertificateInvalid. As far as I understand, you need to add a CA certificate somewhere to establish a secure connection, but I don't know where. 2025-10-27T09:06:43.247Z, 0x0000008d, 4, 0, 0, * ERROR: OpcUa_Channel_BeginConnect: Cannot create secure channel without certificates! 2025-10-27T09:06:43.247Z, 0x00001090, 4, 0, 0, * ERROR: Datasource: Error Failed (268468242) in state Connecting I tried communicating without encryption, but it doesn't find the point. Has anyone managed to establish encrypted OPC UA communication?
Last updated: 2025-10-28
Post by dekelec on Codesys 2.3 & Peak PCAN
CODESYS Forge
talk
(Post)
I use Peak USB adapter daily to download from CoDeSys 2.3 and 3.5 to IFM, EPEC and other controllers. The process: - First you need to install the appropriate driver. Link: https://www.peak-system.com/Drivers.523.0.html?&L=1 - Restart the computer - Start the CoDeSys application - Change the name of the adapter in Communication parameters, as mentioned in previous comment. Write the name exactly as written "Peak_USB", as it could also be case sensitive (defines which .dll file to use). If this doesn't work I would contact the vendor of the controller to find out the procedure. In the attachment I've added a FAQ document from IFM regarding using PCAN USB. P.S. I've noticed in your picture of communication parameters a channel via TCP/IP is mentioned. In this case a USB to CAN connection is not being used. First you should change the channel/gateway to connect via CANbus or connect using an Ethernet cable.
Last updated: 2024-07-09
Post by jrsantab on Remote connection to ifm PLC & HMI
CODESYS Forge
talk
(Post)
We have finally solved the problem. The version of the Gateway in the computer that worked (3.5.11.0) and the one that didn't (3.5.17.30) was different. We have three different Codesys 3.5 versions installed because we work with different controllers. I believe that, depending on the sequence you follow to install the versions you get a different Gateway version. To solve the problem you first have to disable the "obsolete" services. Open services, serach for (in our case) CODESYS Gateway V3 Version 3.5.11.0 CODESYS ServiceControl Version 3.5.11.0 I stopped the services and changed to Manual Start. Then you have to create the new services. In our case, from a Command Prompt session (cmd): SC CREATE "Codesys GatewayService Rigual" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\GatewayService.exe" and then SC CREATE "CODESYS ServiceControl Version 3.5.17.30" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\CODESYSControlService.exe" remember also to set them as Automatic Start!
Last updated: 2024-04-22
Post by gallusrrr on usb2can in Codeysy 3.5 Can Gateway
CODESYS Forge
talk
(Post)
Hallo und guten Morgen, Ich danke für die Rückmeldung. ich habe das oben geschriebene durchgeführt und auch festgestellt das mit die Commandos für die Can befehle noch fehlen. (Google angeschmissen und geschaut auch gefunden) sudo apt-get install can-utils (damit auch jemanden anders der Post hilft) Anschließend habe ich das CAN System komplett aufgebaut so das ich mit einen anderen CAN Adapter schauen konnte ob die Nachricht auch ankommt. die Nachricht kommt an :) danach habe ich follgende Ausgabe: pi@Codesys:~ $ sudo ip -s -d link show can0 3: can0: <noarp,up,lower_up,echo> mtu 16 qdisc pfifo_fast state UP mode DEFAULT group default qlen 10 link/can promiscuity 0 allmulti 0 minmtu 0 maxmtu 0 can state ERROR-ACTIVE restart-ms 0 bitrate 250000 sample-point 0.875 tq 250 prop-seg 6 phase-seg1 7 phase-seg2 2 sjw 1 brp 12 gs_usb: tseg1 1..16 tseg2 1..8 sjw 1..4 brp 1..1024 brp_inc 1 clock 48000000 re-started bus-errors arbit-lost error-warn error-pass bus-off 0 0 0 0 0 0 numtxqueues 1 numrxqueues 1 gso_max_size 65536 gso_max_segs 65535 tso_max_size 65536 tso_max_segs 65535 gro_max_size 65536 parentbus usb parentdev 1-1.4:1.0 RX: bytes packets errors dropped missed mcast 3549 819 0 0 0 0 TX: bytes packets errors dropped carrier collsns 32 4 0 0 0 0</noarp,up,lower_up,echo> (Sorry habe kein Speicherplatz im Web um Bilder anzuzeigen..) man kan sehen das die Nachricht abgeht und auch 32 Byte Empfangen worden sind. Die nachricht ist auch am anderen CAN Adapter sichtbar gewesen. Wie bekomem ich den einrichteten Adapter in Codesys rein? das ich den Befehl sudo ip link set can0 up type can bitrate 500000 das ich die Einrichtungs des Can Adapters noch in die Rasperry Start rutine nehmen muss ist mir klar. Ich bedanke mich .
Last updated: 2024-01-18
Post by alez on CANopen safety , SRDO error behavior
CODESYS Forge
talk
(Post)
I have a project in which there is a Safety device in CANopen, and the PLC interfaces with it as Master. I would like to understand if it is possible to set the behavior in case one of the SRDOs that I receive from the slave is no longer received. From what I have seen, if the SRDOs are not received, the CANopen safety status becomes "Not in progress" and the mapped variables freeze at the last value detected. I want to understand if it was possible to set the variables connected to the SRDOs to take a default value (e.g. zero) in the event of a CANOpen error during reception.
Last updated: 2024-07-15
Post by mubeta on parker servo and position
CODESYS Forge
talk
(Post)
Reading between the lines of what you did not specify, it therefore seems to appear that in the programme, at the end of the movement order, there is an order to remove power and switch off the pulse modulation. if this is the case, it is obvious that the motor then remains free. If the position is to be maintained at the end of the movement, the motor current modulator, which on the PLC side is controlled via the MC_Power method, must not be interrupted. Another possibility is that in the motor drive settings, the standstill torque current is set very low or zero and without position monitoring. You have to check this via the servo motor drive.
Last updated: 2024-08-05