Post by clarenced on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks CODESYS Forge talk (Post)
Using codesys v3.5 SP21 Patch 1. We are using Visualization to display alarms. Other then the automatically created AlarmManagerTask, there is no code written to call AlarmStorage_Prg. Any ideas why we would be seeing this error in the log? The runtime actually shutdown. Not sure if that was caused by this error or not. 2025-08-03T02:45:35.444Z, 0x00001012, 4, 0, 0, * ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks. 2025-08-03T03:48:15.294Z, 0x00001012, 4, 0, 0, * ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks. 2025-08-03T04:38:11.557Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! * 2025-08-03T04:38:11.576Z, 0x0000010f, 8, 1, 0, #### Exception: SysSemEnter - Semaphore deadlock detected - owner thread died [tid:726740] - system may be in an inconsistent state. 2025-08-03T04:38:11.576Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! 2025-08-03T04:38:11.576Z, 0x00000001, 8, 260, 3, #### Exception: HANDLED EXCPT* <excpt>NonContinuable</excpt> in CH_COMM_CYCLE 2025-08-03T04:40:12.308Z, 0x00000001, 1, 0, 35, CODESYS Control shutdown... 2025-08-03T04:40:13.436Z, 0x00000071, 1, 0, 13, Webserver stopped 2025-08-03T04:40:13.437Z, 0x00000114, 2, 1, 0, !!!! Warning: task_signalhandler_exit [MainTask] lost cycles: 14809 2025-08-03T04:40:13.497Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>IecVarAccess</cmp>, <id>0x00001007</id> <ver>3.5.3.64</ver> 2025-08-03T04:40:13.506Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>AlarmMgr</cmp>, <id>0x00001012</id> <ver>4.7.0.0</ver> 2025-08-03T04:40:13.513Z, 0x00000071, 2, 0, 14, !!!! Warning: Unbalanced calls to WebServerRequestRunning/WebServerReleaseRunning 2025-08-03T04:40:13.513Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>IECVisualization</cmp>, <id>0x0000100c</id> <ver>4.7.0.0</ver> 2025-08-03T04:40:13.611Z, 0x00000124, 1, 0, 0, Provider 'AddressSpaceFragment Provider' (version 0x3051500) unregisterd at the OPC UA server. 2025-08-03T04:40:13.611Z, 0x00000124, 1, 0, 0, Provider 'OPC UA for IEC-61131-3' (version 0x3051500) unregisterd at the OPC UA server. 2025-08-03T04:50:17.708Z, 0x00000001, 1, 0, 36, CODESYS Control shutdown done
Last updated: 2025-08-04

Post by leafy on Use third party actuator with IO-Link Master (IFM) CODESYS Forge talk (Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16

Post by leafy on Use third party actuator with IO-Link Master (IFM) CODESYS Forge talk (Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16

Post by andrebrandt on FB string and naming CODESYS Forge talk (Post)
Thank you so much. This worked. Waht im trying to do here is to automatically tag each sensors, valves and so on. There is a preatty nasty tag system i working on. "_320" is not alloved. I can have a tag "+4f=320.004-RT001V" In codesys I want to build the FB in folders. -4f | --320 | --001 This is the system structure. Inside here is all of the sensors and so on. But with Codesys, I cannot tag this like this. So what I'm trying to do now is to Make a folder for the building "4f" and one for the system "320", and a POU _001. Is there a way in init to get folder names?
Last updated: 2024-10-01

Post by fugtwad on Automation Builder V2.5 EtherCAT CM579 Master Scan for devices - >No gateway selected CODESYS Forge talk (Post)
ABB Automation Builder v2.5.0.22 Premium CodeSys 2.3.9.62 Running on Win 10 VM x64 Goal: I have an EtherCAT topology issue which normally a "Scan for devices.." on the EtherCAT master would shed some light on. Issue: Upon trying such I get a "No gateway selected" error. Question: How might I point the the "scanner" at a gateway? What is working: Gateway is running in system tray. I can go online to PLC. A scan from the "Diagnostics live" tab of the EtherCAT master gives slave status. What I have tried: Restarting gateway in system tray. Exiting system tray gateway and reloading it. Turning off firewall. Contacting ABB support multiple times. Any help appreciated.
Last updated: 2024-05-20

Post by lucaver89 on Raspberry pi 3 and runtime 4.9.0.0 CODESYS Forge talk (Post)
Good morning, I'm using a raspberry pi3 as plc with the runtime 4.9.0.0. My program has many of retrain variables but when an update is performed the retrain variables comes back to default values. Is the a way to backups the retrain variables n a csv file? Is still the way to restore them from the csv? Thank you for helping Luca
Last updated: 2023-09-23

Post by wbj0t on one variable signed to modbus tcp server device and modbus serial device CODESYS Forge talk (Post)
Hi. Raspberry pi 4 runtime. Runtime version 4.16, IDE version 3.5.21. Is it possible write new value for variable via modbus tcp or serial devices when both enabled? As I see - not. What can I do? It is terrible restriction.
Last updated: 2025-07-17

Post by peter-skokanek on Rpi install runtime licence on SP13 CODESYS Forge talk (Post)
Hi, I have an older project which has been running for years. Unfortunately I have to replace current Raspberry. I repplaced it by new rpi 3 with newest 32 bit Raspberry OS. I oredered a new runtime licence. When I try to activate it, the connection to target is interrupted immediatelly after press next button in the last step of instalation.
Last updated: 2024-01-08

Post by paho on Linux runtime mit init-functions CODESYS Forge talk (Post)
Hallo, ich habe eine Frage zu den init-functions: kann man irgendwie verhindern, dass bei einer Installation der Runtime (normal Update per CODESYS Linux Dialog) die init-functions unter /opt/codesys/scripts/init-functions immer überschrieben werden? Dort habe ich einige CPU/IRQ Anweisungen die ausgeführt werden müssen, aber nach jedem Runtime Update ist die Datei wieder auf Werkseinstellung. Danke!
Last updated: 2024-04-30

Post by nano on Cant login to Rpi4 but can see it in codesys communications settings. CODESYS Forge talk (Post)
which ports in detail are configured. the search of the rts works via broadcast-messages, programming with tcp-port on p2p-connection woth port-hopping, handled by runtime after siccesfully handshake. look at this entry on forge https://forge.codesys.com/forge/talk/Runtime/thread/4078a2ed28/
Last updated: 2024-06-23

Post by vtec35 on search runtime 4.9.0.0 for pi 3 CODESYS Forge talk (Post)
Hello everyone, following corrupted data on the SD card of our Pi3B+ provided with a machine, we reinstalled a CODESYS image for Raspberry Pi, but we cannot find the 4.9.0.0 runtime that is compatible with the project. Currently, the machine is on 4.1.0.0, and we tried a more recent version 4.13.0.0, but there are error messages. Thanks in advance.
Last updated: 2025-10-24

Post by wbj0t on Raspberry Pi CM4. CoDeSyS files corrupted after hard reset. CODESYS Forge talk (Post)
Hello everyone. Raspberry Pi CM4 after some 1 week of work was hard reset mannualy several times and after these hard resets User Management file was missed (when click login button, enter login/password, error: User Management File missed). Also programm can not open file via SysFile library, but this file exists and size of him is 0 bytes, but must be more any way (I keep some kind of archive via this lib). What happens, how files corrupted? Where do I need try to find this error of the codesys or system whole? In the log files of codesys nothing interesting about this happens. Thanks for reading Is this enough hold PlcLogic and SysFileMap.cfg as reserve copy in another place for restoring the programm? And how automate restoring actions if programm files corrupted?
Last updated: 2024-09-16

Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20) CODESYS Forge talk (Post)
If you have a Windows system (RTE), then why not run the CODESYS HMI as separate controller. This could easily be moved to another PC if required. In the HMI you could also still use the Symbolic Var access as part of the Data Source Manager, although maybe OPC is the preferred way to make it more future proof. Or what about the Remote Target Visu. Then you can reduce the load of the main controller, while still only having to create one application including Visualization. This is now also supported for Linux systems. See: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_target_visu_for_linux.html https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_execute_remote_target_visu.html
Last updated: 2024-09-28

Post by dsa28 on OPC UA subscriber not operational CODESYS Forge talk (Post)
Hello All, Hopefully I can get some help configuring an OPC UA subscriber in a CODESYS runtime in a Raspberry Pi 5 that tries to retrieve data from an OPC UA publisher (in this case running in a TwinCAT system). I tried to follow the steps described in the page to implement the OPC UA subscriber: https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_opcua_pubsub.html Seems that the example provided was created with version 3.5.16.0. Now with version 3.5.20.20 is not possible to open the complete project neither convert it. Anyway, after configuring all IPs and ports used in the OPC UA connection function block but the connection state always shows DISABLED. Can someone help me to do the proper configuration of the OPC UA subscriber? Many thanks in advance.
Last updated: 2024-10-22

Post by eozupek on File Transfer Error 4 CODESYS Forge talk (Post)
I couldn't exactly solve the file transfer when I wanted to do multiple transfers while the compiler was open in a way that I couldn't understand. Notification from target: runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! * details of the target component that sent this notification: [CmpName=SysExcept, CmpId=0x00000103, ClassID=0X0001008, ErrorID=0X00000001, InfoID= 0X0000000j] I see the warning. I couldn't find out why error code 4 is coming or what kind of measures I need to take to prevent it from coming within the application. Can you help me? regards Emre OZUPEK
Last updated: 2024-11-24

Post by sigurdrb on Read codesys version in the codesys application CODESYS Forge talk (Post)
Hi! I want to read the codesys version into the project, so I can highlight it in the SCADA system. VAR dwVersion : DWORD; END_VAR SysTarget.SysTargetGetVersion(pulVersion := ADR(dwVersion)); This gives me the value 100859909. I tried to search ths up and found som older post (https://forge.codesys.com/forge/talk/Runtime/thread/a55981ff4d/) that said each 4 bytes reads a number in the version. Example is 50662666 = 16#03050D0A which reads to V3.5.13.10 When I run this code I get the value 100859909, which I cant translate to anything meaningful. I am running it on Codesys V3.5.19.70. Help appreciated!
Last updated: 2025-01-17

Post by ewi04 on How to upload application file to remote controller (offline) ? CODESYS Forge talk (Post)
Hi, I am looking for a good way to update a decice remotely. The devices are distributed worldwide and have normally no connection to the internet. The CODESYS Automation Server can't help here. So I want to update the decices via USB stick. I have written my own code* to update the files that are created with ‘Create boot application’. But sometimes strange things happen: visu elements are present, but are not found the application is no longer registered and therefore no longer starts I have not yet found out why these errors occur. Has anyone had similar problems or found a better way? Is there perhaps a CODESYS library or something else? Many thanks! *the code deletes the directories on the device and copies the new directories from the USB stick while the system is running (goes without saying)
Last updated: 2024-02-05

Post by superjojo2002 on Licensing info not available. CODESYS Forge talk (Post)
I recognized that I have to start the two services "/etc/init.d/codemeter" and "/etc/init.d/codemeter-webadmin" in the docker container as well. If I do so, then the command "cmu -x" returns root@sensoredge-field-netfield-produktmanagment:/# cmu -x cmu - CodeMeter Universal Support Tool. Version 7.60c of 2023-Aug-09 (Build 5625) for Linux/ARMHF 64-Bit Copyright (C) 2007-2023 by WIBU-SYSTEMS AG. All rights reserved. So this time there is no indication any more that "Codemeter is not running". But still we are getting the error when using the license manager in CODESYS development system.
Last updated: 2024-03-21

Post by fajean on CODESYS control on RPi starts, shortly runs, then exits CODESYS Forge talk (Post)
4.11 appears to solve the problem. Thanks for your help. I had first installed the 64-bit version of RPiOS, but looking at various posts and the product's page on the store which only lists 32-bit compatibility, I downgraded to the 32-bit version. I did this before trying 4.11, and it did not solve the problem. Thus my working system is 32-bit, and I am wondering if I can go back to 64-bit or not. An 64-bit OS is not listed as compatible on the store's web page, but when installing there actually is a 64-bit version listed (automatically chosen when installing on 64-bit, but otherwise greyed out). Is 64-bit supported and the website is out-of-date, or is that some kind of work-in-progress?
Last updated: 2024-06-13

Profinet Device keeps abort connection with AR alarm.ind(err) CODESYS Forge talk (Thread)
Profinet Device keeps abort connection with AR alarm.ind(err)
Last updated: 2023-08-21

No source code available for profinet library CODESYS Forge talk (Thread)
No source code available for profinet library
Last updated: 2023-08-23

Stop raspberry from executing a plc program CODESYS Forge talk (Thread)
Stop raspberry from executing a plc program
Last updated: 2023-08-24

Raspberry Pi Control SL MC - Restoring License not working anymore! CODESYS Forge talk (Thread)
Raspberry Pi Control SL MC - Restoring License not working anymore!
Last updated: 2023-08-24

Relay board / relays for raspberry pi 3 b+ CODESYS Forge talk (Thread)
Relay board / relays for raspberry pi 3 b+
Last updated: 2023-09-03

Post by kumareasu on Code Size CODESYS Forge talk (Post)
Is this "Application Based Licence" is applicable for CODESYS Control RTE SL
Last updated: 2023-09-08