Post by gseidel on MC_Phasing state explenation
CODESYS Forge
talk
(Post)
Hi kenth1973, it is not a matter of who created the function block. It is just that we don't have, and don't provide, documentation about internal implementation details... Hope you can understand that, Georg
Last updated: 2025-12-17
Post by siscu on Raspberry i2c master device
CODESYS Forge
talk
(Post)
I want to implement an extended I2C master for Raspberry Pi Control. I was hoping for it to be as easy as creating a library with a FB that extends i2cMaster and associating it with a device following the forge drivers documentation, but I haven't managed to make it work as the driver behaves only as an i2c slave. I'm thinking this is because the forge forum only talks about extending i2c, and the master portion is omitted since most users won't want to add a custom one. I'd like to know if I'm doing something wrong. Is it really possible to make an I2C master extension device? If so, are there public examples we can check out? Any info on this topic will be appreciated.
Last updated: 2024-10-16
Post by madskaizer on ModbusTCP Slave Device, maximum uiClientConnections?
CODESYS Forge
talk
(Post)
I got a Wago PFC200V2, running Codesys 3.5.16.40, 100ms scan cycle, consumes about 20ms. It will randomly crash the runtime every 10 minutes to a few hours. We suspect an overloaded ModbusTCP Slave Device, as this is work done by a 3rd party contractor, but we can not find anything in the help files or documentation, that mentions a hard limit on maximum number of clients connections. This PLC currently has 44 client connections to the Slave Device and 29 slaves configured for its own Master Device. This topic metnions a hard limit of maximum 16 connections, but where is this written? https://forge.codesys.com/forge/talk/Engineering/thread/bd95b9d6d2/
Last updated: 2025-03-26
Post by alimans on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
For anyone still experiencing this issue, here’s how I managed to solve it: Symptoms: 1. Sometimes, on the first start of CODESYS Runtime, the modules fail to run. 2. After disconnecting and reconnecting the communication cable, the drive does not start again. 3. MC_Reset cannot clear the fault. Solution (what worked for me): 1. Check the axis communication using the SMC_CheckAxisCommunication function block (FB). 2. If CheckAxisCommunication.eComState of the axis is equal to or higher than SMC_CommunicationState.SMC_COMSTATE_BASE_COM_INITIALIZATION, then 3. Use the SMC3_ReinitDrive function block to reset the drive — and it works. For more information, refer to the official CODESYS documentation: 👉 https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/DriveInterface/AXIS_REF/SMC3_ReinitDrive.html
Last updated: 2025-10-23
Post by paulpotat on cm4 runtime problem
CODESYS Forge
talk
(Post)
It looks like it works with 4.13.0.0 indeed. However when installing the runtime, it's not possible to select the multicore option (see attachment). But once the 4.13.0.0 runtime is installed, the logs seems to indicate that the runtime is running in multicore mode. Looking at "htop" output, it seems like it actually is running on multiple CPU. This is very misleading, is it normal or is this a bug ? Thank you for your answer @eschwellinger, BR
Last updated: 2024-09-02
Post by zatalian on Codesys Control for Raspberry Pi 4.10.0.0 - Raspberry Pi OS > 2023-12-05
CODESYS Forge
talk
(Post)
There seem to be problems with the latest version of raspberry pi os 64bit (I used the lite version). The codesys control runtime crashes after a few seconds. The same runtime works on the raspberry pi image from 2023-10-10 When starting the runtime from the commandline, i get the following error: ooops... this runtime was build for RASPBERRYPI. Hardware version or firmware version not supported! (and yes, I'm running this on a raspberry pi :-)
Last updated: 2023-12-11
Post by edson-bueno on SysProcess Execute Command unable to run commands with special characters
CODESYS Forge
talk
(Post)
Hi, I found the same issue, and I fixed with this steps: 1st go to codesys .cfg file. sudo nano CODESYSControl.cfg Then insert this: [SysProcess] BasePriority=Realtime Command=AllowAll Now we need to grant codesys root rights on Linux. Step 1: Create or edit the systemd override configuration: sudo systemctl edit codesyscontrol In the editor that opens, insert: [Service] User=root Save and exit: Press Ctrl+O to save Press Ctrl+X to exit Step 2: Reload systemd and reboot To apply the override: sudo systemctl daemon-reexec sudo systemctl daemon-reload sudo reboot Step 3: Confirm CODESYS is running as root After reboot, open the terminal and run: ps aux | grep codesyscontrol You should see something like: root 1234 ... /opt/codesys/bin/codesyscontrol.bin ... If instead it shows admin or another user, the override was not applied correctly. Step 4: (Optional) Confirm from within CODESYS In your CODESYS project, insert this test code to run the Linux command whoami: Make sure the lib SysProcessImplementation, SysTypes, and CmpErrors is on the project. VAR sCommand : STRING := '/usr/bin/whoami'; sOutput : STRING(255); refCommand : REFERENCE TO STRING; refOutput : REFERENCE TO STRING; resultCmd : UDINT; END_VAR refCommand REF= sCommand; refOutput REF= sOutput; SysProcessExecuteCommand2( pszCommand := refCommand, pszStdOut := refOutput, udiStdOutLen := SIZEOF(sOutput), pResult := ADR(resultCmd) ); Notes & Warnings This method gives full system access to the CODESYS runtime — do not expose this system to the public network without protection. Do not use sudo in commands inside CODESYS when the runtime is already running as root. @tomas111, in case you want to read the temperatur, use this command: sCommand:STRING:='/usr/bin/vcgencmd measure_temp';
Last updated: 2025-05-20
Post by clarenced on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks
CODESYS Forge
talk
(Post)
Using codesys v3.5 SP21 Patch 1. We are using Visualization to display alarms. Other then the automatically created AlarmManagerTask, there is no code written to call AlarmStorage_Prg. Any ideas why we would be seeing this error in the log? The runtime actually shutdown. Not sure if that was caused by this error or not. 2025-08-03T02:45:35.444Z, 0x00001012, 4, 0, 0, * ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks. 2025-08-03T03:48:15.294Z, 0x00001012, 4, 0, 0, * ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks. 2025-08-03T04:38:11.557Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! * 2025-08-03T04:38:11.576Z, 0x0000010f, 8, 1, 0, #### Exception: SysSemEnter - Semaphore deadlock detected - owner thread died [tid:726740] - system may be in an inconsistent state. 2025-08-03T04:38:11.576Z, 0x00000103, 65544, 1, 0, runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! 2025-08-03T04:38:11.576Z, 0x00000001, 8, 260, 3, #### Exception: HANDLED EXCPT* <excpt>NonContinuable</excpt> in CH_COMM_CYCLE 2025-08-03T04:40:12.308Z, 0x00000001, 1, 0, 35, CODESYS Control shutdown... 2025-08-03T04:40:13.436Z, 0x00000071, 1, 0, 13, Webserver stopped 2025-08-03T04:40:13.437Z, 0x00000114, 2, 1, 0, !!!! Warning: task_signalhandler_exit [MainTask] lost cycles: 14809 2025-08-03T04:40:13.497Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>IecVarAccess</cmp>, <id>0x00001007</id> <ver>3.5.3.64</ver> 2025-08-03T04:40:13.506Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>AlarmMgr</cmp>, <id>0x00001012</id> <ver>4.7.0.0</ver> 2025-08-03T04:40:13.513Z, 0x00000071, 2, 0, 14, !!!! Warning: Unbalanced calls to WebServerRequestRunning/WebServerReleaseRunning 2025-08-03T04:40:13.513Z, 0x00000001, 1, 0, 10, [UNLOADED] IEC|Dynamic: <cmp>IECVisualization</cmp>, <id>0x0000100c</id> <ver>4.7.0.0</ver> 2025-08-03T04:40:13.611Z, 0x00000124, 1, 0, 0, Provider 'AddressSpaceFragment Provider' (version 0x3051500) unregisterd at the OPC UA server. 2025-08-03T04:40:13.611Z, 0x00000124, 1, 0, 0, Provider 'OPC UA for IEC-61131-3' (version 0x3051500) unregisterd at the OPC UA server. 2025-08-03T04:50:17.708Z, 0x00000001, 1, 0, 36, CODESYS Control shutdown done
Last updated: 2025-08-04
Post by leafy on Use third party actuator with IO-Link Master (IFM)
CODESYS Forge
talk
(Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16
Post by leafy on Use third party actuator with IO-Link Master (IFM)
CODESYS Forge
talk
(Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16
Post by andrebrandt on FB string and naming
CODESYS Forge
talk
(Post)
Thank you so much. This worked. Waht im trying to do here is to automatically tag each sensors, valves and so on. There is a preatty nasty tag system i working on. "_320" is not alloved. I can have a tag "+4f=320.004-RT001V" In codesys I want to build the FB in folders. -4f | --320 | --001 This is the system structure. Inside here is all of the sensors and so on. But with Codesys, I cannot tag this like this. So what I'm trying to do now is to Make a folder for the building "4f" and one for the system "320", and a POU _001. Is there a way in init to get folder names?
Last updated: 2024-10-01
Post by fugtwad on Automation Builder V2.5 EtherCAT CM579 Master Scan for devices - >No gateway selected
CODESYS Forge
talk
(Post)
ABB Automation Builder v2.5.0.22 Premium CodeSys 2.3.9.62 Running on Win 10 VM x64 Goal: I have an EtherCAT topology issue which normally a "Scan for devices.." on the EtherCAT master would shed some light on. Issue: Upon trying such I get a "No gateway selected" error. Question: How might I point the the "scanner" at a gateway? What is working: Gateway is running in system tray. I can go online to PLC. A scan from the "Diagnostics live" tab of the EtherCAT master gives slave status. What I have tried: Restarting gateway in system tray. Exiting system tray gateway and reloading it. Turning off firewall. Contacting ABB support multiple times. Any help appreciated.
Last updated: 2024-05-20
Post by lucaver89 on Raspberry pi 3 and runtime 4.9.0.0
CODESYS Forge
talk
(Post)
Good morning, I'm using a raspberry pi3 as plc with the runtime 4.9.0.0. My program has many of retrain variables but when an update is performed the retrain variables comes back to default values. Is the a way to backups the retrain variables n a csv file? Is still the way to restore them from the csv? Thank you for helping Luca
Last updated: 2023-09-23
Post by wbj0t on one variable signed to modbus tcp server device and modbus serial device
CODESYS Forge
talk
(Post)
Hi. Raspberry pi 4 runtime. Runtime version 4.16, IDE version 3.5.21. Is it possible write new value for variable via modbus tcp or serial devices when both enabled? As I see - not. What can I do? It is terrible restriction.
Last updated: 2025-07-17
Post by peter-skokanek on Rpi install runtime licence on SP13
CODESYS Forge
talk
(Post)
Hi, I have an older project which has been running for years. Unfortunately I have to replace current Raspberry. I repplaced it by new rpi 3 with newest 32 bit Raspberry OS. I oredered a new runtime licence. When I try to activate it, the connection to target is interrupted immediatelly after press next button in the last step of instalation.
Last updated: 2024-01-08
Post by paho on Linux runtime mit init-functions
CODESYS Forge
talk
(Post)
Hallo, ich habe eine Frage zu den init-functions: kann man irgendwie verhindern, dass bei einer Installation der Runtime (normal Update per CODESYS Linux Dialog) die init-functions unter /opt/codesys/scripts/init-functions immer überschrieben werden? Dort habe ich einige CPU/IRQ Anweisungen die ausgeführt werden müssen, aber nach jedem Runtime Update ist die Datei wieder auf Werkseinstellung. Danke!
Last updated: 2024-04-30
Post by nano on Cant login to Rpi4 but can see it in codesys communications settings.
CODESYS Forge
talk
(Post)
which ports in detail are configured. the search of the rts works via broadcast-messages, programming with tcp-port on p2p-connection woth port-hopping, handled by runtime after siccesfully handshake. look at this entry on forge https://forge.codesys.com/forge/talk/Runtime/thread/4078a2ed28/
Last updated: 2024-06-23
Post by vtec35 on search runtime 4.9.0.0 for pi 3
CODESYS Forge
talk
(Post)
Hello everyone, following corrupted data on the SD card of our Pi3B+ provided with a machine, we reinstalled a CODESYS image for Raspberry Pi, but we cannot find the 4.9.0.0 runtime that is compatible with the project. Currently, the machine is on 4.1.0.0, and we tried a more recent version 4.13.0.0, but there are error messages. Thanks in advance.
Last updated: 2025-10-24
Post by noah on "Invalid Value" for Variables at Runtime
CODESYS Forge
talk
(Post)
Hello, I also have the problem that suddenly all variables in my project were invalid and shown as "???" during runtime. Could you manage to fix the problem in the last 4,5 years ;) ? Because I tried everythin to fix it but nothing worked. I feel like maybe this is a bug. Thank you.
Last updated: 2026-03-09
Post by noah on "Invalid Value" for Variables at Runtime
CODESYS Forge
talk
(Post)
Hello, I also have the problem that suddenly all variables in my project were invalid and shown as "???" during runtime. Could you manage to fix the problem in the last 4,5 years ;) ? Because I tried everythin to fix it but nothing worked. I feel like maybe this is a bug. Thank you.
Last updated: 2026-03-09
Post by wbj0t on Raspberry Pi CM4. CoDeSyS files corrupted after hard reset.
CODESYS Forge
talk
(Post)
Hello everyone. Raspberry Pi CM4 after some 1 week of work was hard reset mannualy several times and after these hard resets User Management file was missed (when click login button, enter login/password, error: User Management File missed). Also programm can not open file via SysFile library, but this file exists and size of him is 0 bytes, but must be more any way (I keep some kind of archive via this lib). What happens, how files corrupted? Where do I need try to find this error of the codesys or system whole? In the log files of codesys nothing interesting about this happens. Thanks for reading Is this enough hold PlcLogic and SysFileMap.cfg as reserve copy in another place for restoring the programm? And how automate restoring actions if programm files corrupted?
Last updated: 2024-09-16
Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20)
CODESYS Forge
talk
(Post)
If you have a Windows system (RTE), then why not run the CODESYS HMI as separate controller. This could easily be moved to another PC if required. In the HMI you could also still use the Symbolic Var access as part of the Data Source Manager, although maybe OPC is the preferred way to make it more future proof. Or what about the Remote Target Visu. Then you can reduce the load of the main controller, while still only having to create one application including Visualization. This is now also supported for Linux systems. See: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_target_visu_for_linux.html https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_execute_remote_target_visu.html
Last updated: 2024-09-28
Post by dsa28 on OPC UA subscriber not operational
CODESYS Forge
talk
(Post)
Hello All, Hopefully I can get some help configuring an OPC UA subscriber in a CODESYS runtime in a Raspberry Pi 5 that tries to retrieve data from an OPC UA publisher (in this case running in a TwinCAT system). I tried to follow the steps described in the page to implement the OPC UA subscriber: https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_opcua_pubsub.html Seems that the example provided was created with version 3.5.16.0. Now with version 3.5.20.20 is not possible to open the complete project neither convert it. Anyway, after configuring all IPs and ports used in the OPC UA connection function block but the connection state always shows DISABLED. Can someone help me to do the proper configuration of the OPC UA subscriber? Many thanks in advance.
Last updated: 2024-10-22
Post by eozupek on File Transfer Error 4
CODESYS Forge
talk
(Post)
I couldn't exactly solve the file transfer when I wanted to do multiple transfers while the compiler was open in a way that I couldn't understand. Notification from target: runtime received SIGABRT - system may be in an inconsistent state * We recommend a reboot of the controller now! * details of the target component that sent this notification: [CmpName=SysExcept, CmpId=0x00000103, ClassID=0X0001008, ErrorID=0X00000001, InfoID= 0X0000000j] I see the warning. I couldn't find out why error code 4 is coming or what kind of measures I need to take to prevent it from coming within the application. Can you help me? regards Emre OZUPEK
Last updated: 2024-11-24
Post by sigurdrb on Read codesys version in the codesys application
CODESYS Forge
talk
(Post)
Hi! I want to read the codesys version into the project, so I can highlight it in the SCADA system. VAR dwVersion : DWORD; END_VAR SysTarget.SysTargetGetVersion(pulVersion := ADR(dwVersion)); This gives me the value 100859909. I tried to search ths up and found som older post (https://forge.codesys.com/forge/talk/Runtime/thread/a55981ff4d/) that said each 4 bytes reads a number in the version. Example is 50662666 = 16#03050D0A which reads to V3.5.13.10 When I run this code I get the value 100859909, which I cant translate to anything meaningful. I am running it on Codesys V3.5.19.70. Help appreciated!