Post by harryc on Soft Container License issue with ARM64 Linux CODESYS Forge talk (Post)
hi @eschwellinger Thanks for the hint. This is what I get with "cmu -x" There is no Dongle. I think that I'm trying to install the soft container from CODESYS development system, where I have the licensed installed in the License Repository. The development system gives me the error when I try to install the Soft Container license. # cmu -x - CodeMeter Universal Support Tool. Version 8.20 of 2024-Sep-10 (Build 6539) for Linux/ARMHF 64-Bit Copyright (C) 2007-2024 by WIBU-SYSTEMS AG. All rights reserved. #
Last updated: 2025-12-10

Post by durallymax on VAR_INFO from inside of a FB to get info on the instance. CODESYS Forge talk (Post)
The help link appears to be broken. When I implemented something similar I had to add {attribute 'reflection} above the declaration of the FB with {attribute 'instance-path'} above the string VAR that would contain the path. Then wrote a function to trim off however much I wanted removed by searching for periods, then formatting it with spaces at the periods and removing brackets on arrays while also breaking up the PascalCase to present it a bit nicer for the end-users.
Last updated: 2025-12-12

Post by gseidel on Scara3 kinematic robot error CODESYS Forge talk (Post)
Hi aniket-b, this error has nothing to do with the scara3 kinematics, or robotics, or SoftMotion. It means that the EtherCAT bus is not synchronized. The usual cause is that the realtime of the PLC is not sufficient. See https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_basic_common_errors.html for details and ways to solve the problem. You can also check the PLC log for additional information about the error. Best regards, Georg
Last updated: 2025-12-23

Post by codegunner on how to convert library from CodeSys 2.3 to CodeSys 3.x ? CODESYS Forge talk (Post)
hello, ive tried everything and keep getting error like i have opened a file in read only so cannot save no idea what is causing it, file is not read only i cannot even open a new file i make with one variable in 2.3, get same error for read only. do you have a 2.3 file you can send me tomtry and open for a test? thanks
Last updated: 2026-04-29

Post by suyash on Device User Logon CODESYS Forge talk (Post)
Thanks for your reply @eschwellinger. Update : the is problem is resolved. It was done by renaming the User database file (/var/opt/codesys/.UserDatabase.csv) as deleting it was risky. After restart the IDE asked me to create new user. On doing that the problem got resolved. Reference for members facing similar problem/s : sudo systemctl stop codesyscontrol sudo mv /var/opt/codesys/.UserDatabase.csv_ /var/opt/codesys/.UserDatabase.csv_.old sudo systemctl start codesyscontrol
Last updated: 2026-05-14

Post by kmax365 on ModbusTCP_FunctionCode06 CODESYS Forge talk (Post)
Hey Guys, I am trying to create a ModbusTCP_FunctionCode06 which i will use as a single write register for programming a test code for Power Meter(PQM_1000) I have tried to reserach how to add it it from the libraray manager and have largely been unsuccessful. Does anyone know where I should Look? And by the way, I am i wam using Codesys V3.5 Vs 21 Patch 4 I look forward to something positive. Best, Kmax365.
Last updated: 2026-05-14

Post by kmax365 on ModbusTCP_FunctionCode06 CODESYS Forge talk (Post)
Hey Guys, I am trying to create a ModbusTCP_FunctionCode06 which i will use as a single write register for programming a test code for Power Meter(PQM_1000) I have tried to reserach how to add it it from the libraray manager and have largely been unsuccessful. Does anyone know where I should Look? And by the way, I am i wam using Codesys V3.5 Vs 21 Patch 4 I look forward to something positive. Best, Kmax365.
Last updated: 2026-05-14

Post by ph0010421 on ModbusTCP_FunctionCode06 CODESYS Forge talk (Post)
Hi You can add a channel to the standard Modbus TCP library with FC06. From the device tree, add Ethernet device, ModbusTCP master then finally a ModbusTCP slave (your power meter). You can add read/write channels (for any FC) in here. As you add these devices, the necessary libraries will be inserted for you. Alternatively, I have a ModbusTCP client/server library if your RT doesn't have Modbus (I think they all do these days?)
Last updated: 2026-05-18

Post by dhumphries on Codesys Installation problem CODESYS Forge talk (Post)
Installing codesys has been the biggest point of frustration for me and is the reason I'm currently working on building a VM just for the codesys engineering software so once I get a working installation I can copy the VM to new workstations instead of fighting with the installer every time I get a workstation upgrade. The best advice I've gotten in the past is to uninstall everything and start over, this is successful 50% of the time. Also don't install the latest version it's usually less stable than an older one ironically.
Last updated: 2026-08-10

Post by alexgooi on No Bootproject possible CODESYS Forge talk (Post)
Dear Forum, When using a online-change I often get the following message: No Bootproject possible in this state: application out of memory. Perform full download first. I'm using Codesys virtual control for linux SL running on a docker server with plenty of memory available, therefore I’m not expecting a hardware limitation. Is there a setting available to for example reserve more memory, so the controller is not that quick out of memory? thank you in advance. Alex
Last updated: 2026-03-27

Post by eschwellinger on cannot connect ot linux runtime: device does not answer the scanrequest CODESYS Forge talk (Post)
for me looks like you do not use latest CODESYS IDE version, there is a known bug if you use a newer runtime your are forced to use a more complex password as user for the login. The old IDE version does not show this problem on login. so either update CODESYS or use a pw which meet the complexity requirements.
Last updated: 2026-06-11

Post by darwin03 on Mismatch between coordinate monitor and actual motion using SMC_GroupJog2, MC_MoveLinearAbsolute (6DOF) CODESYS Forge talk (Post)
Hi Georg, Thanks for your previous suggestion. I was able to resolve the issue! I'm now trying to build the 6DOF robot again, but I'm not sure why this is happening. Even when I simulate it in RoboDK using the joint angles from my code, the robot's motion still seems abnormal. Do you have any ideas what might be causing this? Thank you for taking the time to look into my question! Best regards, darwin03 Video link: https://drive.google.com/file/d/1PBqS4yIY2R_CZ3celSKz-BXVRk8pCHKz/view?usp=sharing
Last updated: 2026-10-09

Post by paulg on RasPi CAA Serial example - unexpected behavior during debug CODESYS Forge talk (Post)
I've trimmed down the CAA Serial Codesys example to only listen on one port but, when stepping through the Case structure in debug mode, it jumps out of the structure during a specific point in every scan (I'll point it out below after describing the setup and listing the code). I'm using a Pi 4 Model B, and I have an Arduino Nano Every plugged in via USB which is streaming the following serial message at 1 Hz: Time since opening connection: 1 s Time since opening connection: 2 s ...and so on. The Pi shows the Nano at /dev/ttyACM0 so I edited CODESYSControl_User.cfg to read: Linux.Devicefile=/dev/ttyACM The code in my PLC_PRG is (ignore some of the comments, I hadn't deleted them out from the original example): PROGRAM PLC_PRG VAR xStartTest : BOOL:= TRUE; iState : INT; xTestDone : BOOL;(* True, when the test was done succesfully *) (* Settings to communicate with the COM Port *) aCom1Params : ARRAY [1..7] OF COM.PARAMETER; como1 : COM.Open; comc1 : COM.Close; comw1 : COM.Write; comr1 : COM.Read; //sWrite : STRING := 'Test String!'; sRead : STRING(25); szRead : CAA.SIZE; xCom1OpenError : BOOL; xCom1CloseError : BOOL; xCom1WriteError : BOOL; xCom1ReadError : BOOL; END_VAR //This example shows the communication of two COM Ports with each other. //The first one writes a string of characters, which is read by the second one. //After successful execution, the two COM Ports are closed and the test is done. IF xStartTest THEN CASE iState OF 0: //The parameters are set for the COM Port aCom1Params[1].udiParameterId := COM.CAA_Parameter_Constants.udiPort; aCom1Params[1].udiValue := 1; // the correct Port should be adapted aCom1Params[2].udiParameterId := COM.CAA_Parameter_Constants.udiBaudrate; aCom1Params[2].udiValue := 115200; aCom1Params[3].udiParameterId := COM.CAA_Parameter_Constants.udiParity; aCom1Params[3].udiValue := INT_TO_UDINT(COM.PARITY.NONE); aCom1Params[4].udiParameterId := COM.CAA_Parameter_Constants.udiStopBits; aCom1Params[4].udiValue := INT_TO_UDINT(COM.STOPBIT.ONESTOPBIT); aCom1Params[5].udiParameterId := COM.CAA_Parameter_Constants.udiTimeout; aCom1Params[5].udiValue := 0; aCom1Params[6].udiParameterId := COM.CAA_Parameter_Constants.udiByteSize; aCom1Params[6].udiValue := 8; aCom1Params[7].udiParameterId := COM.CAA_Parameter_Constants.udiBinary; aCom1Params[7].udiValue := 0; //The first Port is opened with the given parameters como1(xExecute := TRUE, usiListLength:=SIZEOF(aCom1Params)/SIZEOF(COM.PARAMETER),pParameterList:= ADR(aCom1Params)); IF como1.xError THEN xCom1OpenError := TRUE; iState := 1000; END_IF //After a successful opening, the next state is reached IF como1.xDone THEN iState := 15; END_IF 15: // the reading process is started comr1(xExecute := TRUE,hCom:= como1.hCom, pBuffer:= ADR(sRead), szBuffer:= SIZEOF(sRead)); IF comr1.xError THEN xCom1ReadError := TRUE; END_IF //After completion the size of the written bytes are saved IF comr1.xDone OR comr1.xError THEN szRead := comr1.szSize; iState := 20; END_IF 20: // If everything was successful the ports are closed and the handles are released comc1(xExecute := TRUE,hCom:= como1.hCom); IF comc1.xError THEN xCom1CloseError := TRUE; END_IF IF comc1.xDone OR comc1.xError THEN iState := 25; END_IF 25: // The first port is closed and the used handle released xTestDone := TRUE; xStartTest := FALSE; iState := 0; como1(xExecute := FALSE); comw1(xExecute := FALSE); comc1(xExecute := FALSE); ELSE iState := 0; END_CASE END_IF I realize as I write this that the .udiPort should be 0 and not 1, but that shouldn't be causing the issue I'm seeing. I'm forcing xStartTest:=TRUE every scan so that I can step into each line and observe what's happening. What I see is that the port parameters are set and the port is opened with no errors, but the code jumps out of the case structure to the last line every time it reaches (and I step into) the iState:=15 line (at the end of the iState:=0 block). So every scan cycle it goes through the block for iState=0 and jumps out at the same spot. I'm a little new to PLC programming so I may be misunderstanding the flow, but shouldn't this case structure keep moving down in the same scan? If it only handles one case per scan, why doesn't the value of iState persist? Thanks! Update: I restarted the Codesys control today and I was then able to see an error for como1.eError of "WRONG_PARAMETER". I tried doing some digging and another post made me think I should add another line to CODESYSControl_User.cfg, so I now have: [SysCom] Linux.Devicefile=/dev/ttyACM portnum := COM.SysCom.SYS_COMPORT1 So now when I set .udiPort to 1, I get "NO_ERROR" but I also don't read anything from the port (i.e. szRead = 0 always). If I try setting the port to 0 (which I'm confused about, because I added a COMPORT1 line but the device shows on the Pi as ACM0), I get the "WRONG_PARAMETER" error again. Is there an easier way to troubleshoot the Pi and view what ports the Codesys runtime is actually able to see while the Pi is running?
Last updated: 2024-06-06

Post by kevinrn on Github Actions CI/CD tasks - development topic CODESYS Forge talk (Post)
Hello community, I just want to inform you about our plans and the current status of automating the build process for CODESYS libraries. So it might be helpful for some people who are in the same situation. Background story: I am a software engineer at powerIO GmbH, normally I use high level languages for the products we develop and offer. Sometimes I work with my team on CODESYS libraries, which can also be found in the CODESYS store. Most of the time I spend with them on architecture tasks and tasks that are not directly related to our products. Every time I see the manual processes for releasing a library etc., I am very surprised about this time intensive process. Current situation: I know there has been a scripting interface for years. CODESYS Git was released a few years ago, but the scripting interface was only released a few months (weeks?) ago. We developed a pseudo-automated solution a few months ago, but it was all very hacky. So now there is a better Git implementation and also more modularization and installation options. For example, the CODESYS installer has a full CLI, which makes it very convenient to install CODESYS installations headless. Plans: I think it's the right time to develop a better automation solution. Most of our software projects are hosted on Github and we use Github actions very intensively for other software projects. Therefore, we have decided to use Github for our CODESYS library projects as well. Following tasks should be implemented in automation for CI/CD tasks: - Automated setup of CODESYS installation (Already released: https://github.com/marketplace/actions/setup-codesys-installation) - Checkout CODESYS libraries - Execute tests scripts - Sign CODESYS libraries - Extract Library documentation - Create CODESYS package - Sign CODESYS package Side Note: - This is mainly a side project, and we do not provide support for the CI/CD part. - This topic is here to help and also to get help from other software engineers. - This project and idea is not prioritized as I am currently the only one working on it and I hope it will help us and also others and increase productivity. - We are putting this out there as an organization, but priorities can change quickly and the CI/CD tasks I am developing are mostly done in my spare time. So please don't expect this to happen in a short time or even be fully completed. I would be very happy if some ppl will join the development process and might be open to discuss some technical details for this. I hope this topic is not to off-topic, but I think the CI/CD part is very important today and it can increase a lot of quality and push productivity. Thanks :)
Last updated: 2024-03-28

Post by eschwellinger on communication CODESYS Forge talk (Post)
depends on if you use PFC200 SL from CODESYS store or the Wago target for the PFC. If you use the SL product you need to setup the interface by a plcshell command...
Last updated: 2023-08-19

Post by rossanoparis on After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working CODESYS Forge talk (Post)
Hello at all. After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working. I'm not able to read or write files from the PLC application. Before this upgrade all worked fine. I've read this thread [ https://forge.codesys.com/forge/talk/Engineering/thread/3da9ded84e/ ] Despite I followed that indications I couldn't get my code working again. Perhaps I'm missing something or I didn't understand how to use placeholders at all. Is there a different syntax to use for "SysFileOpen" in order to use placeholders? Thanks in advance for your help. Information Compiler: CODESYS V3.5 SP19 Patch 2 Runtime: codesyscontrol 4.9.0 HW: KUNBUS RevPi Connect S Below the paths I want to access (The entire CODESYSControl_User.cfg file is attached) [SysFile] PlaceholderFilePath.1=/home/pi/hpca/bin, $hpcabin$ PlaceholderFilePath.2=/home/pi/hpca/cfg, $hpcacfg$ PlaceholderFilePath.3=/home/pi/hpca/logs, $hpcalogs$ PlaceholderFilePath.4=/home/pi/hpca/resources, $hpcares$
Last updated: 2023-08-22

Post by eschwellinger on Connection to device closed CODESYS Forge talk (Post)
is there a way to check the plclog on Opus A3 by using cmd line under Linux? This log is what you need to check for the disconnection problem
Last updated: 2023-08-24

Post by rohitk on CoDeSys libraries for BECKHOFF EL7332/EL7342 CODESYS Forge talk (Post)
Hi, step 1 : go to beckhoff website, go to required IO card, go to download option in that, go to XML donlowad and download the file Step2 : Go to codesys software, go to tools - deviceRepository - install that downloaded file.
Last updated: 2023-08-24

Post by eschwellinger on How to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server CODESYS Forge talk (Post)
check this faq section here: https://faq.codesys.com/plugins/servlet/mobile?contentId=102137886#content/view/102137886
Last updated: 2023-08-25

Post by totorovic on CSVReaderInit returns error : INVALID_HANDLE CODESYS Forge talk (Post)
Thank you for the return. The path targets to a CFast card. User has R/W access to it. We will try to change it.
Last updated: 2023-08-31

Post by felipemsgarcia on EtherCAT - Force Control Word CODESYS Forge talk (Post)
What worked for me: Use SMC_SetControllerMode and set the nControllerMode to SMC_nocontrol. With that, you can control the drive via Modes of Operation(16#6060) and Controlword(16#6040) directly. Hope that helps, Cheers!
Last updated: 2023-08-31

Post by tvm on Ranges, Lambdas, on Fixed arrays of structs CODESYS Forge talk (Post)
Have you looked at this? https://forge.codesys.com/prj/codesys-example/element-collect/home/Home/ It's not exactly what you're looking for, but I've been able to make some things work more efficiently using this library.
Last updated: 2023-08-31

Post by eschwellinger on Ethercat scan for devices not picking up EL7041 as a softmotion axis CODESYS Forge talk (Post)
Add existing version (with SM drive) - without scan - disable under expert settings in the slave the revision check.
Last updated: 2023-09-03