Hello everyone! I have an PLC device that uses modem ppp connection to the internet with white IP. Device PPP connection with modem operator established, so I can connect to this device via SSH also within Codesys IDE (check version, info, etc...) BUT, I cant establish connection to this device in the device gateway options for application upload and debugging. How can I do this? Im trying set my device remote IP and port 11740, but, as I understand, it is wrong decision, because the next logic in this connection: local W10 service (Codesys Gateway) listen on 1217, then (some how) this service scanning local networks for seeking any local IP which listening on port 11740, and then connects and writes there. OR IM WRONG?:) W10 tool 'Test-NetConnection' with parameters 'ip -Port 11740' succeeded with True. Need some help, please :)
Last updated: 2024-05-21
Post by damian177 on Codesys and SMS in RPi
CODESYS Forge
talk
(Post)
Hi, I try use IIoT library to send and receive SMS by Raspbery PI and Codesys. I installed IIoT package and added the SMS library, But something is wrong, when I init communication it doesn't work, When I sniffer my communication (AT commands) beetwen RS232 RaspberryPi and my GSM modem I have only below commands: AT+CMEE=1 OK AT+CPIN? +CPIN: READY Anyone have idea what can be wrong ?
Last updated: 2023-09-28
Post by yannickasselin on Dynamically enabling/disabling Modbus slave devices in runtime (performance issue with timeouts)
CODESYS Forge
talk
(Post)
I would definitely try using the "Reconfigure" function block from "CAA Device Diagnosis@ library. https://content.helpme-codesys.com/en/libs/CAA%20Device%20Diagnosis/3.5.17.0/CAA-Device-Diagnosis/Function-Blocks/Reconfigure/Reconfigure.html#:~:text=This%20function%20block%20reads%20and,take%20effect. Although I have not tried it with Modbus, I had great success with EtherNet/IP, Profinet and EtherCAT. You can also have a look at the other functions in this library. There are useful functions to help iterate through all the nodes under a master node.
Last updated: 2025-08-12
Post by ph0010421 on ModbusTCP_FunctionCode06
CODESYS Forge
talk
(Post)
Hi You can add a channel to the standard Modbus TCP library with FC06. From the device tree, add Ethernet device, ModbusTCP master then finally a ModbusTCP slave (your power meter). You can add read/write channels (for any FC) in here. As you add these devices, the necessary libraries will be inserted for you. Alternatively, I have a ModbusTCP client/server library if your RT doesn't have Modbus (I think they all do these days?)
Last updated: 2026-05-18
Post by royw on Profinet library for C#
CODESYS Forge
talk
(Post)
Hi, I don't know if I'm in the right place or if it's even possible... I'm looking for a way to address a Profinet device with Record Read and Write from my own PC. I actually only need very few commands to configure our device. This means setting the MAC address and a serial number. We would like to do this from a C# program. Now we are looking for a library or something similar. Since you can do it from Codesys, I thought there might be a DLL or something similar that you could use for this. As I said, we don't want real-time queries of the cyclic data but only record read/write. Does anyone have any helpful hint? Thanks in advance
Last updated: 2023-12-22
Post by i-campbell on build (F11) / generate code using a python script file
CODESYS Forge
talk
(Post)
hello, please enjoy. # i-campbell 2024 import subprocess from scriptengine import * # with a project already open # save if not yet saved # check pool objects if it is a library # generate code only for the active application if it is a project # beep thanks to https://devblogs.microsoft.com/scripting/powertip-use-powershell-to-send-beep-to-console/ if projects.primary: # check project is open if projects.primary.dirty: # save projects.primary.save() if projects.primary.path.lower().endswith('.library'): projects.primary.check_all_pool_objects() # check all pool objects for lib else: projects.primary.active_application.generate_code() # generate if not lib # note, there could be more applications than the active application, # this script does not generate those else: system.write_message(Severity.Error,'no project open') ps_output = subprocess.check_output(["powershell", "-Command", "[console]::beep(500,300)"]) # beep
Last updated: 2024-04-10
Post by john-robinson on Limiting Memory Access of an Array to Within its Bounds
CODESYS Forge
talk
(Post)
Recently we had an issue regarding some simple code to calculate a rolling average. The code indexes from zero to 199 to properly store the current input into a circular buffer which then allows us to calculate a rolling average: VAR input_5s : REAL; outs_arr : ARRAY[0..199] OF REAL; i : USINT := 0; END_VAR ___ //this code runs every five seconds, calculating a rolling average outs_arr[i] := input_5s; i := i + 1; output := OSCAT_BASIC.ARRAY_AVG(ADR(outs_arr), SIZEOF(outs_arr)); IF i >= SIZEOF(outs_arr) THEN i := 0; END_IF There is a simple bug in this code where the index will be set to 0 when it has surpassed the length of the array in bytes (800 in this case) rather than larger than the number of reals in the array (200). The solution here is simple, replacing i >= SIZEOF(outs_arr) with i >= SIZEOF(outs_arr)/SIZEOF(outs_arr[0]). In this example when the index increased to 201 and the line outs_arr[201] := input_5s was called, codesys arbitrarily wrote to the address in memory that is where outs_arr[201] would be if the array was that long. I would like to find a way to wrap the codesys array inside of a wrapper class that checks if an input is within the bounds of an array before writing to that value. I know how I would implement that for a specific array, I could create a method or class that takes an input of an array of variable length, ie. ARRAY[*] OF REAL, but I don't know how to make this for any data type. I am wondering if anyone has ever done anything similar to this, or has any better suggestions to ensure that none of the programmers on this application accidentally create code that can arbitrarily write to other locations in memory.
Last updated: 2024-03-05
Post by kunal-pinetics on USB Communication for IP Configuration & Application Update β STM32H Series PLC
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on a PLC device based on the STM32H series MCU, running CODESYS. At the moment, I can: Change the Ethernet IP address Update/download the PLC application via Ethernet without any issues. However, I would like to implement the same functionality over USB (or Serial via USB) instead of Ethernet. My goals are: Change the deviceβs Ethernet IP address via USB Download/update the PLC application via USB communication Possibly use USB as a service/programming interface The hardware platform is based on STM32H series, and I am looking for guidance on: Whether CODESYS supports USB device communication for runtime download If a custom USB CDC (Virtual COM Port) implementation is required Whether a specific CODESYS runtime configuration is needed If a bootloader approach is recommended for application updates via USB If anyone has experience implementing USB communication for runtime download or device configuration on an STM32-based PLC, I would really appreciate your guidance. Thank you in advance for your help.
Last updated: 2026-02-26
Post by eschwellinger on Persistence Manager Backup
CODESYS Forge
talk
(Post)
you need at them moment a download once (for the configuration files generated including addresses) then stop the plc - exchange the persistence file ( without the config file) This will be improved to 3.5.18.6 and 3.5.20.0. (possible then to generate offline bootproject including full persistenmanager files) - this is if you have not 100% the same bootapplication on the devices. In case you copy the whole Application (PLCLogic) directory it should work out of the box - but only with 100% same bootprojects as mentioned above. By the CODESYS Automation Server would help solve this too.
Last updated: 2023-10-19
Post by struccc on Application failing to boot after system reboot
CODESYS Forge
talk
(Post)
I started to experience the same issue, after upgrading to 3.5.19 , and still persists with 3.5.20.3 , using CodesysControlWinV3 x64 on Windows. Unfortunately, this is a live application, normally it is running for months without interruption - so it was a surprise at the last cold start... It was not possible to go online with the original version, so I couldn't see the application, or system status, just the log message. First time I manually clean the Application from the PlcLogic directory (there was no coredump file in there), then I could start the runtime service, and do a fresh download, and set the bootproject. I could not try a cold system reboot - it's in a 24/7 production environment, and I was under heavy pressure to start... What I did, I have created a backup from the * complete * runtime directory, from the failed, and fixed version - before and after download. This directory in my case C:\ProgramData\CODESYS\CODESYSControlWinV3x64\55096128 - At the next shutdown, it was sufficient to copy back this backup completely, and could start the runtime service afterwards. Ugly, but local staff with some skills can do it without programming tool... I don't store any live data, configuration, log files, persistent data in this directory - the only reason I need this is to edit the CodesysControl... .cfg file.... And to see the logfiles in emergencies like this. The application concerned doesn't use any retain area. - exactly for these reasons - Maybe that is causing the problem with the newer runtime versions As far as I see, this problem occurs only if the power of the Windows PLC is interrupted without a proper shutdown. Unfortunately, this can happen sometimes. The newer versions, seems tp modify CodesysControl.cfg on the fly, and register the applications, and bootproject information after download. (I don't really see CodesysControl.cfg a proper location for this... but that's just my feeling) So now I had a look at CodesysCotrol.cfg on my laptop and I found: [CmpRetain] ;Retain.SRAM.Size=0x200200 ;Retain.SRAM.Address=0xFA3C5776 ;SimulateSRAM=1 [CmpApp] ;Bootproject.CreateOnDownload=0 ;Bootproject.StoreOnlyOnDownload=0 ;Bootproject.InvalidateByRename=1 ;Bootproject.InvalidateBySetting=1 ;Bootproject.InvalidateNever=0 ;PersistentForce=0 ;RetainType.Applications=InSRAM ;RetainType.Applications=OnPowerfail ;RetainType.Applications=None ;Exception.Hardware.GlobalStop=1 Application.1=MyTestAppNoRetain The last line appeared after download and boot project creation. Maybe... Should set RetainType.Applications=None? I wonder about all these settings, but... Will write separately about it. I hope this helps a little...
Last updated: 2024-11-21
Post by nz-dave on FAILURE TO OPEN PROJECT ON ANOTHER COMPUTER
CODESYS Forge
talk
(Post)
just now i have tried loading the achive file from today at work. using 3.5.20.4 same as at work. when i open the project it says " prject inspection, this project has been saved with a different version(codesys v3.5 sp20 patch 4).? one option in the above "project inspection" window just wants to download that same version again. the other option leads no where as it say the required add ons cant be resolved. just end up going around in circles.
Last updated: 2025-01-22
Post by jaspergain on Access to the path *** is denied
CODESYS Forge
talk
(Post)
Hello, Recently I upgraded to 3.5.19.50 and have been having errors/issues when doing a download/online change. The message as seen in the attachment pops up. The file in the path is different every time. However when I login again afterwards all works fine. This issue does not happen on older versions. Any clue what the issue could be? I did an reinstall/repair but the issue reappeared again... Thanks in advance!
Last updated: 2024-01-25
Post by yannick on Raspberry PI 5 not working
CODESYS Forge
talk
(Post)
Hello I'm using Codesys V3.5 SP19 Patch 6 and a Raspberry PI 5 4GB Bookworm 32bit with the Runtime 4.11.0.0 SL. I can install the runtime and download the software completly but after a few seconds the connection disconnects with the message no connection to device. Please scan network again. And the object reference was not set to an object instance. See screenshot. Can somebody help me with that? Thanks
Last updated: 2024-04-28
Post by lofty on CODESYS Download Issue
CODESYS Forge
talk
(Post)
I am attempting to install CODESYS 3.5.22.20 and the installer gets stuck at "Install Package CODESYS Compatibility Package 3.5.17.20" every single time. I've tried reinstalling the software multiple times and the same issue persists. I've tried running the installer as an administrator and even turned off my virus protection and the same issue persists. I've attached a photo for reference. Has anyone run into this issue before or have any idea what I can do to complete the install?
Last updated: 2026-05-26
Post by damian177 on RPi, Codesys , RS232
CODESYS Forge
talk
(Post)
Hi, so far I have only used one com port - built-in interface in RPi - RS232 (dev/serial0) as COM1 in Codesys, and my CODESYControl_User.cfg have congiuration like below: [SysCom] Linux.Devicefile=/dev/serial portnum := COM.SysCom.SYS_COMPORT1 Actually I added to my Rpi Hat with 2xRS232 (SPI). - /dev/spidev0.0 and /dev/spidev0.1 How I should change my CODESYControl_User.cfg file to use added porta as COM2 and COM3 in Codesys ?
Last updated: 2023-10-05
Post by sean-barton on FILE_OPERATION_DENIED
CODESYS Forge
talk
(Post)
I have code written since version 3.5.16 to access the USB drive, how can I do that now the file access has been taken away? I have tried adding a sybolic link to the usb drive in the following directories: /var/opt/codesys/PlcLogic/ /var/opt/CODESYS/PlcLogic/ /opt/CODESYS/PlcLogic/ I still recieve a "FILE_OPERATION_DENIED" response when accessing the USB drive.
Last updated: 2023-10-13
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by mucleus on What is the solution for "Application stopped on recovery switch request"?
CODESYS Forge
talk
(Post)
Hi, everyone. I am using CODESYS RTE and Profinet I/O or EtherCAT I/O. Occasionally (once every 1-2 months) the attached image occurs and the program stops. I want to know why this phenomenon occurs and how to solve it. I attached log. Please help me. Thanks.
Last updated: 2024-07-05
Post by stiller on OPC UA RPI 4.8.0.0 Status Code / "out of range"
CODESYS Forge
talk
(Post)
Hello, I have an OPC-UA server with an information model. For many values, there is a defined range (e.g., 0 to 100). If a client enters a value outside this range (e.g., 120), the StatusCode should change to Bad. How can I accomplish this? Any help is appreciated! Thank you in advance. Best regards, Christian Stiller
Last updated: 2024-07-10
Post by tk096 on gear over gear (2 masters,1 slave) - how to do it?
CODESYS Forge
talk
(Post)
Hi, you could calculate the position/dynamics of the slave axis yourself and use one of the function blocks SMC_FollowPosition/SMC_FollowSetValues to move the slave axis. https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/POUs/Movement/Direct/SMC_FollowPosition.html https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/POUs/Movement/Direct/SMC_FollowSetValues.html
Last updated: 2024-08-19