Post by jaspergain on Non-existing identifiers
CODESYS Forge
talk
(Post)
Hello, I got a bit of a weird issue going on which is kind of annoying. So recently we switched a lot of Modbus IO to EtherCAT, as we were having issues with stability. All works fine, which is great. But sometimes when I change the program I get errors claiming that identifiers are not defined. Meaning I can't go online. See the picture below. I believe this is because some of these identifiers were used with Modbus, and they weren't properly removed/deleted? A clean all temporary fixes the issue, but it comes back again after a while of changing the code, and building. Any way to fix these non-existing required identifiers, or even find out where they are required? Thanks for the help in advance. Jasper.
Last updated: 2024-05-29
Post by paro on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
Hi, works in my case if I increase the timeout! to_udint(t#100ms) -> 100 -> 100us.. FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; uistart: UINT := 100; udiTimeout1: UDINT; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=1000000); // 1sec END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=uistart, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-30
Post by jens on Modbus tcp - channel
CODESYS Forge
talk
(Post)
Help wanted This is the first time i'm doing a Modbus Tcp project. I have some VLT with a extension module MCA-122. i'm currently unable to write to the VLT slave, but i can read from status word parameter=1603 and address := 16029 where the address is calculated from parameter is ((id x 10)-1). in the manual the functions that are supported are 3 hex, 6 hex, 10 hex, b hex and 11 hex. read holdin registers, write single register, write multiple registers, get comm. event counter, report slave id. i'm only using the Modbus Slave Channel is this wrong when trying to write to the vlt ?
Last updated: 2024-06-13
Post by gatto on Modbus tcp - channel
CODESYS Forge
talk
(Post)
Hi can you give more details? Are you talking about a danfoss? wich model? Can post the configuration of channel' I used, on the past, serial modbus with danfoss fc280 I remember ((id x 10)-1) I remember that you couldn't use continuous reading/writing of the directors but you had to use them one at a time. it seemed that reading empty registers (caused by x10) was not accepted by danfoss. So I had created a scan that used just one register, then the next etc etc with a timed interval. But this was for the serial, I don't know if it's the same thing with ethernet. I currently use Ethernet TCP/IP interface with FC280.
Last updated: 2024-06-13
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together
CODESYS Forge
talk
(Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18
Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together
CODESYS Forge
talk
(Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18
Post by ppix on Establishing TLS Connection with MQTT Broker using MQTT Client SL Package
CODESYS Forge
talk
(Post)
For anyone confused with the process visit this link (the bottom section about creating a .pfx file) https://content.helpme-codesys.com/en/LibDevSummary/certificate.html#import-of-client-certificates-with-private-key. I solved this problem by creating a .pfx file and importing it into the security store under 'Own Certificates'(must have SP18 or newer to import .pfx). I used a gitbash shell to enter the openssl command that created the .pfx file. Once you import the file, in your TLS context, set your 'sUseCaseName' to be the same as the name listed in the 'Information' column of your imported certificate. This did it for me
Last updated: 2024-06-20
Post by tayhim on WAGO HMI Device not found
CODESYS Forge
talk
(Post)
Hello, I'm trying to connect with a Wago TP600 HMI but without success. I'm using codysis 3.5 SP19 patch 7 (SP20 block all the time) and the official wago package is installed. However, when I scan and select my device, I get a message saying that the device doesn't match the project's device object with the possibility to update the device (as shown in the attached picture). however, after choosing to update i got a message that the device is not found. I've tried with a new empty project but the same results. do you have any ideas? Thanks.
Last updated: 2024-06-25
Post by uluking on CodeSys2.3 Modbus 64-Bit Double Read Problem
CODESYS Forge
talk
(Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I am reading data from a Siemens PAC3220 energy analyzer using Modbus with Wago-8202. However, the device's energy indices are given as doubles. Since a double variable is 64-bit, it is not possible to read it directly. I have been struggling for days, I have written many conversion functions but I have not been able to get results. I would appreciate your help. I read 4 word variables and processed them. I am converting them according to IEEE-754, but I can't seem to read the correct data. I would appreciate your help.
Last updated: 2025-10-27
Post by msegon on OPC UA Client failed to connect
CODESYS Forge
talk
(Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I'm trying to read data from Tridium Niagara 4.15 OPC UA Server, but I get the error BadCertificateInvalid. As far as I understand, you need to add a CA certificate somewhere to establish a secure connection, but I don't know where. 2025-10-27T09:06:43.247Z, 0x0000008d, 4, 0, 0, * ERROR: OpcUa_Channel_BeginConnect: Cannot create secure channel without certificates! 2025-10-27T09:06:43.247Z, 0x00001090, 4, 0, 0, * ERROR: Datasource: Error Failed (268468242) in state Connecting I tried communicating without encryption, but it doesn't find the point. Has anyone managed to establish encrypted OPC UA communication?
Last updated: 2025-10-28
Post by wchin on Passing EtheNetIP adapter device into a Function Block to access it's IO
CODESYS Forge
talk
(Post)
We are creating helper function blocks for our VFD(EtherNetIP). How should I set it up so that I can pass the device into and out of the Function Block so that ideally I can access the IO of the device by devicename.channelname. So something like for example we have a VFD with a start bit that is in the ControlWord channel and a SetVelocity that is a channel. And we want to create a Function Block called StartVFD. So I declare something like: FUNCTION_BLOCK StartVFD VAR_IN_OUT device: ioDrvEthernetIP.RemoteAdapter; END_VAR VAR_INPUT velocity : REAL; So in the code it would look something like device.SetVelocity := velocity; device.ControlWord.6 := True; We have a pretty basic eds file for our VFD and can update it if necessary. Thanks in advance.
Last updated: 2025-10-28
Post by wchin on Passing EtheNetIP adapter device into a Function Block to access it's IO
CODESYS Forge
talk
(Post)
We are creating helper function blocks for our VFD(EtherNetIP). How should I set it up so that I can pass the device into and out of the Function Block so that ideally I can access the IO of the device by devicename.channelname. So something like for example we have a VFD with a start bit that is in the ControlWord channel and a SetVelocity that is a channel. And we want to create a Function Block called StartVFD. So I declare something like: FUNCTION_BLOCK StartVFD VAR_IN_OUT device: ioDrvEthernetIP.RemoteAdapter; END_VAR VAR_INPUT velocity : REAL; So in the code it would look something like device.SetVelocity := velocity; device.ControlWord.6 := True; We have a pretty basic eds file for our VFD and can update it if necessary. Thanks in advance.
Last updated: 2025-10-28
Post by wchin on Passing EtheNetIP adapter device into a Function Block to access it's IO
CODESYS Forge
talk
(Post)
We are creating helper function blocks for our VFD(EtherNetIP). How should I set it up so that I can pass the device into and out of the Function Block so that ideally I can access the IO of the device by devicename.channelname. So something like for example we have a VFD with a start bit that is in the ControlWord channel and a SetVelocity that is a channel. And we want to create a Function Block called StartVFD. So I declare something like: FUNCTION_BLOCK StartVFD VAR_IN_OUT device: ioDrvEthernetIP.RemoteAdapter; END_VAR VAR_INPUT velocity : REAL; So in the code it would look something like device.SetVelocity := velocity; device.ControlWord.6 := True; We have a pretty basic eds file for our VFD and can update it if necessary. Thanks in advance.
Last updated: 2025-10-28
Post by tali on Configuration of disabled/deactivated visu elements
CODESYS Forge
talk
(Post)
would be great to have such fucntionality. Sometimes it is not clear for user which elemetns are blocked and which are not - the greyed out eleemtns are not so different for low resolution / low quality screeens. What I have in my mind as well is to have a possibility to detect the visu Element clicked on and get its Access Rights. If it is blocked/deactivated, the dialog can be rised with INFO 'please login first with proper rights'. It is possible now to have a Mose event Handler ( Examples -> EventHandler) and rise the dialog out of ST (Exapmpals -> ST Dialogs). I am struggling still with getting the separate Visu Element under the mouse and its structure info
Last updated: 2025-12-05
Post by gseidel on Can't get SMC_SmoothPath to work
CODESYS Forge
talk
(Post)
Hi bertus, I cannot see any problem in the code you posted. Just some ideas: What is the value of D_ANGLE_TOL? - Do you need the assignment bAbort := NOT bDecoder? Does it help to leave it out? Any errors (e.g. SMC_SmoothPath.Error/ErrorID) or PLC log messages? What if you comment out SMC_SmoothMerge and SMC_LimtiDynamics, is corner smoothing still not working? Is bDecode written from a different task (e.g. visu)? Then I would recommend to assign to a local variable (bDecodeLocal := bDecode) and use that for all FBs. Otherwise, FBs might see different values of bDecode in a single cycle, which will cause problems. Regards, Georg
Last updated: 2025-12-17
Post by pernockham on Unable to deploy "Control for Linux SL 4.18.0.0"
CODESYS Forge
talk
(Post)
The option to update "Control for Linux SL" is not shown in the "deploy control SL tool", I can see and update the gateway but not the control (3.5.21 SP4). Has the way to update control SL changed? In the process of fault finding I removed the control SL entirely from my target, then I had to revert to version 3.5.21.0 SP 1 to re-install "Control SL 4.17.0.0". So I thought it was just a matter of using SP1 to update also to 4.18.0.0, but after installing the files for 4.18.0.0 in the SP1-version, the behavior was identical to SP4, ie no Control for Linux SL shown in the deploy tool.. See screenshots.
Last updated: 2025-12-19
Post by reinier-geers on wEBCLIENT Post data api
CODESYS Forge
talk
(Post)
Ive got the webclient axample. If i put https://reversed.notion.site/Marktprijzen-API-89ce600a88ac4abe8c2ad89d3167a83e example to https://reqbin.com/post-online then i get data. If i do the same in Webclient example i get " not a valid graphql request. Why ? sUrl := 'https://graphql.frankenergie.nl/' Request_type_post Contenttype = 1 (json ) Postvalue := '{"query":{"query":"query MarketPrices {\n marketPrices(date:\"2025-12-25\") {\n electricityPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n gasPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n }\n}' I tranfer the postvalue from String to WSTRING
Last updated: 3 days ago
Post by thommy54 on CODESYSControl_User cfg richtig konfigurieren
CODESYS Forge
talk
(Post)
Hallo, nach Erwerb eines neueren Raspberry pi 4 (V1.5) musste ich zwangsläufig von Codesys 3.5.16 hochwechseln - ich habe auf 3.5.20.1 geupdated. Da schlugen mir plötzlich ne Menge Einschränkungen entgegen, deren Behebung einige Zeit dauerte. Eine davon ist, das ein SysFile.SysFileOpen nicht mehr funktioniert. Ich habe das Problem mit Einträgen in der /etc/CODESYSControl.cfg behoben: [SysFile] FilePath.1=/etc/, 3S.dat IecFilePath.1=/proc/, cpuinfo IecFilePath.2=/proc/, iomem PlaceholderFilePath.1=/sys/devices/w1_bus_master1, $OneWire$ PlcLogicPrefix=1 ; ; ---------------------- ; selbst eingefügt PlaceholderFilePath.2=/home/root, $my_home_root$ PlaceholderFilePath.3=/etc/init.d, $my_conf$ PlaceholderFilePath.4=/var/lib/mpd, $my_music$ PlaceholderFilePath.5=/root/Rasp_SPS_Filesystem, $my_Rasp$ Ob die Einträge sich etwas überlappen, kann mir gern jemand sagen, das ist aber nicht das Problem. Ich habe bei den vielen Versuchen, das Teil zum Laufen zu bringen, bemerkt, daß die Einträge auch ganz schnell mal verschwinden. Das ist ja auch so beschrieben, wenn die nächste Version kommt, sind meine Einträge weg. Da ich ähnliche Probleme mit dem Funktionieren von "SysProcessExecuteCommand2()" hatte, die ich ebenfalls mit Einträgen in die /etc/CODESYSControl.cfg hätte beheben können, habe ich gelesen, das man "private" Einträge lieber in die Datei /etc/CODESYSControl_User.cfg machen soll. Gesagt getan und "SysProcessExecuteCommand2()" lief: [SysProcess] Command=AllowAll Command.0=shutdown Aber auch irgendwo stand, das so ein Beteichner wie [SysFile] oder [SysProcess] nur einmal in den beiden Files /etc/CODESYSControl.cfg oder(!) /etc/CODESYSControl_User.cfg vorkommen darf. Das ist nun die eigentliche Frage! Ist das so ? Bei [SysProcess] ist das kein Problem, das gibt es in /etc/CODESYSControl.cfg nicht. Aber bei [SysFile] sieht das anders aus. Da sind 5 Zeilen schon in /etc/CODESYSControl.cfg drin. Würde ich diese in die User-Datei rüberschieben, könnte beim nächsten Update was fehlen oder, oder... Lasse ich es so wie es ist, sind meine Einträge beim Update weg - das sollte ja verhindert werden. Kann da jemand genaue Auskunft geben ?? Vielen Dank Thomas
Last updated: 2024-06-28
Post by thommy54 on Raspi-Cam: CameraStream.project nicht zum Laufen zu bringen
CODESYS Forge
talk
(Post)
Hallo, Ich bringe das CameraStream.project nicht zum Laufen. Ich sehe die Ursache darin, das das Beispielprogramm sehr sparsam mit Programm-Kommentaren umgeht (von der Hilfe gar nicht zu reden). Ich habe beide Varianten bei der zu ändernden Zielvariable getestet: //copy video.htm to the webserver; //the location of the webserver depends on the used Apache version as mentioned in online help hDirHtmlTest:=SysDirOpen( szDir:='/var/www', pDirInfo:= ADR(dirInfo), diMaxDirEntry:=iMaxDirEntry, szDirEntry:=szDirEntry, pResult:=ADR(iDirHtmlError)); IF (iDirHtmlError = 0) THEN SysDirClose(hDir:=hDirHtmlTest); SysFileCopy('/var/www/video.htm', '$$PlcLogic$$/Application/video.htm', ADR(dwCopySize)); ELSE .... als auch hDirHtmlTest:=SysDirOpen( szDir:='/var/www/html', pDirInfo:= ADR(dirInfo), diMaxDirEntry:=iMaxDirEntry, szDirEntry:=szDirEntry, pResult:=ADR(iDirHtmlError)); IF (iDirHtmlError = 0) THEN SysDirClose(hDir:=hDirHtmlTest); SysFileCopy('/var/www/html/video.htm', '$$PlcLogic$$/Application/video.htm', ADR(dwCopySize)); ELSE .... Die Url-Streams habe ich gelassen wie sie vorgegeben waren: urlStream := CONCAT('http://', CONCAT(sIPAddress, '/video.htm')); urlPicture := CONCAT('http://', CONCAT(sIPAddress, '/cam_pic.php')); In der Webvisu im Browser komme ich maximal dahin wie im Screeshot Video_Visu_1 zu sehen. Also scheint der Link zu video.htm zu klappen. Das der zu cam_pic.php nicht klappt, wundert mich nicht, denn es existiert nicht und wird auch nicht evtl. am rechten Ort angelegt. Ich bin mir vollkommen im Unklaren: muss da was auf dem Raspberry Pi im Hintergrund laufen , z.B. raspivid . Welcher Programmteil bedient die Cam ? Ich erkenne auch nicht, wo ein einzelnes picture entstehen soll. Wäre dankbar, wenn ich hier etwas Hilfe bekommen könnte. Evtl. gibt es Probleme mit der von mir verwendeten Codesys-Version 3.5.20.1 ? Ich benutze einen Raspberry 4 Rev.1.2. Grüße Thomas
Last updated: 2024-07-04