Post by fabiodasilveira on PLC Shell commands via ST Code CODESYS Forge talk (Post)
Hello Everybody, I have created a project for an Eaton XC303 that sends lots of data to a router via UDP. It works fine. However, when there is more than one product connected to the router, then it is necessary to change the IP address of the Ethernet port 0, from e.g. 192.168.2.11 to 192.168.2.12 (second product). It is easily done via PLC Shell (setipaddr 0 192.168.2.12), but the people in production is struggling with the PLC Shell commands and I would like to create a Visualization page that will hide that. I used the instruction: eChangeIPResult:= SysSockSetIPAddress(strEthernetPort, strIPAddress); and it works, until the PLC resets. I already read some posts and it appears that I need to stop the Ethernet 0 port and Reconfigure it, but I am really struggling to find the right way to do it. Any help will be much appreciated.
Last updated: 2025-02-28

Post by ph0010421 on How to create a stopwatch? CODESYS Forge talk (Post)
Do you need an 'hours-run' counter? And 1 second resolution is ok? I think you're over-thinking it. (The task time needs to be < 1second) Have a look at the LAD... Then, the time in seconds can be made into hh:mm:ss with this FUNction Declarations: FUNCTION funSecondsToStringTime: string VAR_INPUT InSeconds: UDINT; END_VAR VAR AsString: STRING; Minutes: UDINT; Hours: UDINT; Seconds: UDINT; MinutesAsString: STRING(2); HoursAsString: STRING(2); SecondsAsString: STRING(2); END_VAR and the code: Hours := InSeconds / 60 / 60; //Derive hours Minutes := (InSeconds - (Hours * 60 * 60)) / 60; //Derive minutes Seconds := InSeconds - ((Hours * 60 * 60) + (Minutes * 60));//Derive seconds HoursAsString := UDINT_TO_STRING(Hours); MinutesAsString := UDINT_TO_STRING(Minutes); SecondsAsString := UDINT_TO_STRING(Seconds); IF LEN(HoursAsString) = 1 THEN HoursAsString := CONCAT('0',HoursAsString); END_IF; IF LEN(MinutesAsString) = 1 THEN MinutesAsString := CONCAT('0',MinutesAsString); END_IF; IF LEN(SecondsAsString) = 1 THEN SecondsAsString := CONCAT('0',SecondsAsString); END_IF; AsString := CONCAT(HoursAsString, ':'); //assemble string AsString := CONCAT(AsString,MinutesAsString); AsString := CONCAT(AsString,':'); AsString := CONCAT(AsString, SecondsAsString); funSecondsToStringTime := AsString;
Last updated: 2023-12-08

Post by paro on Modbus Client Request Not Processed CODESYS Forge talk (Post)
Hi, Problem in your code is that you are not calling the ClientFb cyclic. Please look at the Example from CODESYS: https://forge.codesys.com/prj/codesys-example/modbus/home/Home/ Your code works if the client fb is called cyclic! IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=Ethernet.IPAddress, uiPort:=502); // configure clientSerial clientSerial(iPort:=SysCom.SYS_COMPORT2, dwBaudRate:=SysCom.SYS_BR_115200, byDataBits:=8, eParity:=SysCom.SYS_EVENPARITY, eStopBits:=SysCom.SYS_ONESTOPBIT, eRtuAscii:=ModbusFB.RtuAscii.RTU); // configure clientRequestReadCoils_1 clientRequestReadCoils_1(rClient:=clientTcp, uiUnitId:=42, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestWriteSingleRegister clientRequestWriteSingleRegister(rClient:=clientTcp, uiUnitId:=43, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadCoils_2 clientRequestReadCoils_2(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); END_IF // call the client FB's clientTcp(); clientSerial(); // call client request FB's clientRequestReadCoils_1(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_1[0])); // for more details see Example_TCP, especially ClientRequest control (xExecute, xDone, xError). IF clientRequestReadCoils_1.xDone THEN // get data from aDataCoils_1 ... END_IF clientRequestWriteSingleRegister(rClient:=clientTcp, xExecute:=TRUE, uiItem:=3, uiValue:=123); clientRequestReadCoils_2(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_2[0])); clientRequestReadInputRegisters(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=16, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-29

Post by caprez95 on Deleting the trend recording history CODESYS Forge talk (Post)
Hallo Ich möchte eine laufende Trendaufzeichnung stoppen, den Inhalt löschen und Trend-Diagramm auf 0 zurücksetzen. Laut Codesys soll das mit dem folgenden Code möglich sein: You can insert an input element in the visualization which the operator can use to delete the previous value recording in the trend visualization at runtime. The curve displayed until then is removed and the display starts over. In the application (example: in the program PLC_PRG), implement the following code: itfTrendRecording : ITrendRecording; itfTrendStorageWriter : ITrendStorageWriter; itfTrendStorageWriter3 : ITrendStorageWriter3; sTrendRecordingName : STRING := 'TrendRecording'; itfTrendRecording := GlobalInstances.g_TrendRecordingManager.FindTrendRecording(ADR(sTrendRecordingName)); xClearHistoryTrend: BOOL; IF xClearHistoryTrend THEN itfTrendRecording := GlobalInstances.g_TrendRecordingManager.FindTrendRecording(ADR(sTrendRecordingName)); IF itfTrendRecording <> 0 THEN itfTrendStorageWriter := itfTrendRecording.GetTrendStorageWriter(); IF __QUERYINTERFACE(itfTrendStorageWriter, itfTrendStorageWriter3) THEN itfTrendStorageWriter3.ClearHistory(); END_IF END_IF In the visualization of the trend recording, add a button for deleting the previous curve. Configure its Toggle property with the variable PLC_PRG.xClearHistoryTrend. ⇒ When xClearHistoryTrend is set to TRUE, the previously recorded curve is deleted. The recording immediately starts again. Dies löscht auch die Daten vom Trend, aber das Diagramm wird nicht auf 0 zurückgesetzt, sondern läuft einfach da weiter wo man gestoppt hat. Braucht es für den Diagramm-Reset noch einen zusätzlichen Befehl? Gruss
Last updated: 2024-06-11

Post by konstantin on CAM Motion Recover after STO CODESYS Forge talk (Post)
Hello Mr. Seidel, both the master and the slave axis are modulo. Basically the situation is as follows: One master cycle is 100 units. Slave's modulo length is 2000 units. In the CAM table I defined 10 master cycles on X axis - 1000 units and on the Y axis is the slave - 2000 units. Then depending on the master position 0 to 1000 units the slave's position is plotted on the Y axis - 0 to 2000 units. For example, while the master is executing the 3rd cycle i.e. above 200 units, I trigger the STO function of the slave and it stops. The master executed his cycle but the slave was stopped during the execution. How can I set the slave to continue the CAM sequence from the point where it stopped i.e. third cycle of the master? When I reset the slave error and sync again, everyrhing starts from master's 0 position. Best Regards Konstantin Kolev
Last updated: 2026-02-13

Post by risele on Modbus connection via Qronox PCD3 M6893 CODESYS Forge talk (Post)
You are welcome. Also note, that it's valid only if you modbus-device use same real/float value representation (IEEE 754). That's true for most of systems. But some devices may have other representation, such as integer + position of the decimal point, for example 123.456 is integer = 123456 and position = 3 Also note, that, ones again, depending on endianess of each system, you may also need to swap not just words, but bytes. TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; bVal:ARRAY[0..3] OF BYTE; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE than swapping may be something as VAR A,B,C,D:BYTE; //Bytes of the real value uIn, uOut:u_Real; rVal:REAL; ModbusReg1,ModbusReg2:WORD; END_VAR uIn.rVal:=rVal; uOut.A:=uIn.D; uOut.B:=uIn.C; uOut.C:=uIn.B; uOut.D:=uIn.A; ModbusReg1:=uOut.wVal[0]; ModbusReg1:=uOut.wVal[2]; Or you even need to reorder bits... Ones again, sending float/real values is not defined by Modbus protocol itself, so it is hardware- and software-dependent. The Modbus Poll (and most of modbus tools) have configuration parameters that will properly swap bytes on their side. Ones again, that's very helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/
Last updated: 2026-02-19

Post by critcho on WebVisu Numpad dialog - Dialogtitle not accepting string variable CODESYS Forge talk (Post)
I have a WebVisu page which is re-used for multiple types of gas; it displays the alarm thresholds etc. for one gas at a time. I have an array of structures holding the set-points for each of the gasses. I'm trying to change the dialog title for the value input pop-up (VisuDialogs.Numpad). The Dialogtitle is set to Gas_Alarms.HighAlarmActivationLevelDialog, which is a string(50): When the gas type is changed (page first loaded, or prev/next buttons), METHOD Gas_Alarms.Update_Display_Variables is called, to update the strings used for the dialog titles so it shows GasName High Alarm Activation Level (EngineeringUnits), e.g. CO2 High Alarm Activation Level (PPM): HighAlarmActivationLevelDialog := Insert(' High Alarm Activation Level ()', EngineeringUnits, 30); HighAlarmActivationLevelDialog := Insert(HighAlarmActivationLevelDialog, GasName, 0); (That's not where the problem is, I'm just explaining why I'm using a variable dialogue title.) The variables used are definitely strings, but i'm always getting the error: "The type of the dialog title must be either STRING or WSTRING". I've tried moving HighAlarmActivationLevelDialog etc. to the GVL and also changing them to WSTRING, I even tried adding them to the structure array, but I always get the same error. Clearing the dialog title for that element removes the error - so I'm confident it's not a phantom error caused by something else. But I should be able to add these titles, can't just nuke them all to make it work. The MinVal and MaxVal for the Numpad are called from the array, e.g. GVL.Gas_Alarm_Configs[0].ScaledValueMIN, they are not getting an error. I am using array indexes 1 - 5 for the gasses, when I load the form or change gas, I copy the selected index to index 0 of the array, and values from Gas_Alarm_Configs[0].[ALL] are displayed on the page. When they hit save, I copy Gas_Alarm_Configs[0].[ALL] to Gas_Alarm_Configs[CurrentGasIndex].[ALL]. (ALL just means every element, I can't figure out how to display an asterix in this question... :) ) I've searched online for variable title dialog, but not found anything to help. Thanks for your help!
Last updated: 2025-05-29

Post by bertus on Can't get SMC_SmoothPath to work CODESYS Forge talk (Post)
Hello all, I am trying to run a XY trajectory from a static G-Code file. Everything works except the smoothing/blending of the corners. My setup: Codesys v3.5sp18 Raspberry Pi 4 CODESYS Control for Raspberry Pi SL, using demo license. Zero axes (only using the interpolator). The order of processing for my decoding is: SMC_NCDecoder (ok) SMC_SmoothMerge (ok) SMC_SmoothPath (not ok) SMC_LimitDynamics SMC_CheckVelocities I created following instances and buffers: fbNCDecoder: SMC_NCDecoder; fbSmoothMerge: SMC_SmoothMerge; fbSmoothPath: SMC_SmoothPath; fbLimitDynamics: SMC_LimitDynamics; fbCheckVelocities: SMC_CheckVelocities; aNCDecoderBuffer: ARRAY[0..49] OF SMC_GeoInfo; // buffer stage 1 (fbNCDecoder) aSmoothMergeBuffer: ARRAY[0..19] OF SMC_GeoInfo; // buffer stage 2 (fbSmoothMerge) aSmoothPathBuffer: ARRAY[0..99] OF SMC_GeoInfo; // buffer stage 3 (fbSmoothPath) aLimitDynamicsBuffer: ARRAY[0..39] OF SMC_GeoInfo; // buffer stage 4 (fbLimitDynamics) My original G-Code file has a lot of short G1 elements but this example, I reduced it to a simple square: N000 G51 D10 N010 G38 O1 N020 G00 X0 Y0 F50 E1000 E-1000 N030 G01 X0 Y-37.5 N040 G01 X-75 Y-37.5 N050 G01 X-75 Y37.5 N060 G01 X0 Y37.5 N070 G01 X0 Y0 N080 G50 N090 G39 O1 In the Codesys CNC settings, I have these instances activated: SMC_SmoothMerge SMC_SmoothPath SMC_LimitDynamics SMC_CheckVelocities And with those settings (and the path-preprocessing button actived), the G-Code viewer shows the square with nicely blended corners (see attached picture). However, when running it on the PLC, it doesn't blend the corners at all. Below the relevant part of my code. The process is started with bDecode. // stage 1: decoding G-code fbNCDecoder( ncprog := square, bExecute:= bDecode, bAbort:= NOT bDecode, nSizeOutQueue := SIZEOF(aNCDecoderBuffer), pbyBufferOutQueue := ADR(aNCDecoderBuffer) ); // stage 2: merge short linear segments fbSmoothMerge( bExecute := bDecode, poqDataIn := fbNCDecoder.poqDataOut, nSizeOutQueue := SIZEOF(aSmoothMergeBuffer), pbyBufferOutQueue := ADR(aSmoothMergeBuffer), piMaxDifference := PI_MAX_DIFFERENCE, usiMaxDegree := 5, wFeatureFlag := 1, wAdditionalParamNumber := 0, dMinimumCurvatureRadius := D_MIN_CURVATURE_RADIUS ); // stage 3: smooth corners fbSmoothPath( bExecute := bDecode, bAbort := NOT bDecode, poqDataIn := fbSmoothMerge.poqDataOut, eMode := SMC_SMOOTHPATHMODE.SP_SPLINE5_MIN_CURVATURE, eAddAxMode := SMC_SMOOTHPATHADDAXMODE.SPAA_NONE, nSizeOutQueue := SIZEOF(aSmoothPathBuffer), pbyBufferOutQueue := ADR(aSmoothPathBuffer), dAngleTol := D_ANGLE_TOL, bSymmetricalDistances := TRUE, bImprovedSymmetricCuts := TRUE ); // stage 4: keep acc/dec and velocity within limits fbLimitDynamics( bExecute := bDecode, bAbort := NOT bDecode, poqDataIn := fbSmoothPath.poqDataOut, wAxis := 16#07, nSizeOutQueue := SIZEOF(aLimitDynamicsBuffer), pbyBufferOutQueue := ADR(aLimitDynamicsBuffer), bIncludePathSettings := TRUE, dMaxVel := 2500, dMaxAccDec := 10000 ); // stage 5: check the path speed fbCheckVelocities( bExecute := bDecode, bAbort := NOT bDecode, poqDataIn := fbLimitDynamics.poqDataOut, dAngleTol := D_ANGLE_TOL); pathQueue := fbCheckVelocities.poqDataOut; // repeat until MaxDuration ... Any idea what I'm doing wrong? Is smooth path supposed to work at all when using a demo license? Thanks.
Last updated: 2025-12-17

Post by paulg on RasPi CAA Serial example - unexpected behavior during debug CODESYS Forge talk (Post)
I've trimmed down the CAA Serial Codesys example to only listen on one port but, when stepping through the Case structure in debug mode, it jumps out of the structure during a specific point in every scan (I'll point it out below after describing the setup and listing the code). I'm using a Pi 4 Model B, and I have an Arduino Nano Every plugged in via USB which is streaming the following serial message at 1 Hz: Time since opening connection: 1 s Time since opening connection: 2 s ...and so on. The Pi shows the Nano at /dev/ttyACM0 so I edited CODESYSControl_User.cfg to read: Linux.Devicefile=/dev/ttyACM The code in my PLC_PRG is (ignore some of the comments, I hadn't deleted them out from the original example): PROGRAM PLC_PRG VAR xStartTest : BOOL:= TRUE; iState : INT; xTestDone : BOOL;(* True, when the test was done succesfully *) (* Settings to communicate with the COM Port *) aCom1Params : ARRAY [1..7] OF COM.PARAMETER; como1 : COM.Open; comc1 : COM.Close; comw1 : COM.Write; comr1 : COM.Read; //sWrite : STRING := 'Test String!'; sRead : STRING(25); szRead : CAA.SIZE; xCom1OpenError : BOOL; xCom1CloseError : BOOL; xCom1WriteError : BOOL; xCom1ReadError : BOOL; END_VAR //This example shows the communication of two COM Ports with each other. //The first one writes a string of characters, which is read by the second one. //After successful execution, the two COM Ports are closed and the test is done. IF xStartTest THEN CASE iState OF 0: //The parameters are set for the COM Port aCom1Params[1].udiParameterId := COM.CAA_Parameter_Constants.udiPort; aCom1Params[1].udiValue := 1; // the correct Port should be adapted aCom1Params[2].udiParameterId := COM.CAA_Parameter_Constants.udiBaudrate; aCom1Params[2].udiValue := 115200; aCom1Params[3].udiParameterId := COM.CAA_Parameter_Constants.udiParity; aCom1Params[3].udiValue := INT_TO_UDINT(COM.PARITY.NONE); aCom1Params[4].udiParameterId := COM.CAA_Parameter_Constants.udiStopBits; aCom1Params[4].udiValue := INT_TO_UDINT(COM.STOPBIT.ONESTOPBIT); aCom1Params[5].udiParameterId := COM.CAA_Parameter_Constants.udiTimeout; aCom1Params[5].udiValue := 0; aCom1Params[6].udiParameterId := COM.CAA_Parameter_Constants.udiByteSize; aCom1Params[6].udiValue := 8; aCom1Params[7].udiParameterId := COM.CAA_Parameter_Constants.udiBinary; aCom1Params[7].udiValue := 0; //The first Port is opened with the given parameters como1(xExecute := TRUE, usiListLength:=SIZEOF(aCom1Params)/SIZEOF(COM.PARAMETER),pParameterList:= ADR(aCom1Params)); IF como1.xError THEN xCom1OpenError := TRUE; iState := 1000; END_IF //After a successful opening, the next state is reached IF como1.xDone THEN iState := 15; END_IF 15: // the reading process is started comr1(xExecute := TRUE,hCom:= como1.hCom, pBuffer:= ADR(sRead), szBuffer:= SIZEOF(sRead)); IF comr1.xError THEN xCom1ReadError := TRUE; END_IF //After completion the size of the written bytes are saved IF comr1.xDone OR comr1.xError THEN szRead := comr1.szSize; iState := 20; END_IF 20: // If everything was successful the ports are closed and the handles are released comc1(xExecute := TRUE,hCom:= como1.hCom); IF comc1.xError THEN xCom1CloseError := TRUE; END_IF IF comc1.xDone OR comc1.xError THEN iState := 25; END_IF 25: // The first port is closed and the used handle released xTestDone := TRUE; xStartTest := FALSE; iState := 0; como1(xExecute := FALSE); comw1(xExecute := FALSE); comc1(xExecute := FALSE); ELSE iState := 0; END_CASE END_IF I realize as I write this that the .udiPort should be 0 and not 1, but that shouldn't be causing the issue I'm seeing. I'm forcing xStartTest:=TRUE every scan so that I can step into each line and observe what's happening. What I see is that the port parameters are set and the port is opened with no errors, but the code jumps out of the case structure to the last line every time it reaches (and I step into) the iState:=15 line (at the end of the iState:=0 block). So every scan cycle it goes through the block for iState=0 and jumps out at the same spot. I'm a little new to PLC programming so I may be misunderstanding the flow, but shouldn't this case structure keep moving down in the same scan? If it only handles one case per scan, why doesn't the value of iState persist? Thanks! Update: I restarted the Codesys control today and I was then able to see an error for como1.eError of "WRONG_PARAMETER". I tried doing some digging and another post made me think I should add another line to CODESYSControl_User.cfg, so I now have: [SysCom] Linux.Devicefile=/dev/ttyACM portnum := COM.SysCom.SYS_COMPORT1 So now when I set .udiPort to 1, I get "NO_ERROR" but I also don't read anything from the port (i.e. szRead = 0 always). If I try setting the port to 0 (which I'm confused about, because I added a COMPORT1 line but the device shows on the Pi as ACM0), I get the "WRONG_PARAMETER" error again. Is there an easier way to troubleshoot the Pi and view what ports the Codesys runtime is actually able to see while the Pi is running?
Last updated: 2024-06-06

Post by scoob on ModbusFB - Slow Response Time CODESYS Forge talk (Post)
Hello, I have been trying to use the ModbusFB functions so I can put some code into libraries, but it seems to be very slow for me. I have a Modbus device with 100ms registers. I previously setup 10 channels in the 'traditional' Modbus Slave with channels and mappings - and set a cyclic trigger at 100ms - this worked fine. I then tried the ModbusFB example, and setup reading the same 10 blocks of modbus addresses, copying the example and putting all of the requests into an array and triggering the requests sequentially. I timed how long the requests are taking to get round to each one, and it is around 1s 450ms. How do I speed this up to match the cyclic time? IF NOT(init) THEN init := TRUE; // Set the required IP address: ipAddress[0] := 192; ipAddress[1] := 168; ipAddress[2] := 1; ipAddress[3] := 10; // Pass the required IP address to the clinet FB: client_NetworkSwitch.aIPaddr := ipAddress; client_NetworkSwitch.udiLogOptions := (ModbusFB.LoggingOptions.ClientConnectDisconnect OR ModbusFB.LoggingOptions.ClientReceivedValidReplies); // Try to connect the client client_NetworkSwitch(xConnect:=TRUE); // Configure all the channels to read connecting them to the client: portStatus_Request(rClient := client_NetworkSwitch, uiStartItem := 4096, uiQuantity := 32, pData := ADR(portStatus), udiReplyTimeout := udiReplyTimeout); portSpeed_Request(rClient := client_NetworkSwitch, uiStartItem := 4352, uiQuantity := 32, pData := ADR(portSpeed)); flowControl_Request(rClient := client_NetworkSwitch, uiStartItem := 4608, uiQuantity := 32, pData := ADR(flowControl)); linkUpCounter_Request(rClient := client_NetworkSwitch, uiStartItem := 5888, uiQuantity := 32, pData := ADR(linkUpCounter)); txPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8192, uiQuantity := 100, pData := ADR(txPacketCounter1)); txPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8292, uiQuantity := 28, pData := ADR(txPacketCounter2)); rxPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8448, uiQuantity := 100, pData := ADR(rxPacketCounter1)); rxPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8548, uiQuantity := 28, pData := ADR(rxPacketCounter2)); txErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8704, uiQuantity := 64, pData := ADR(txErrors)); rxErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8960, uiQuantity := 64, pData := ADR(rxErrors)); // Trigger all client requests initially FOR clientRequestsCnt := 0 TO (SIZEOF(clientRequests)/SIZEOF(clientRequests[0]))-1 DO pClientRequest := clientRequests[clientRequestsCnt]; pClientRequest^.xExecute := TRUE; END_FOR // Prepare sequential trigger / control of client requests. clientRequestsCnt := 0; pClientRequest := clientRequests[clientRequestsCnt]; END_IF // Call the client to do request processing: client_NetworkSwitch(); // Now we trigger client request sequentially ... IF NOT pClientRequest^.xExecute AND NOT pClientRequest^.xDone AND run AND client_NetworkSwitch.xConnected THEN pClientRequest^.xExecute := TRUE; END_IF // .. and check result/error IF pClientRequest^.xExecute AND run AND client_NetworkSwitch.xConnected THEN IF pClientRequest^.xDone THEN // Prepare next trigger of client request (a rising edge of xExecute) pClientRequest^.xExecute := FALSE; IF clientRequestsCnt < SIZEOF(clientRequests)/SIZEOF(clientRequests[0])-1 THEN // next client request clientRequestsCnt := clientRequestsCnt + 1; ELSE clientRequestsIterationCounter := clientRequestsIterationCounter + 1; clientRequestsCnt := 0; END_IF pClientRequest := clientRequests[clientRequestsCnt]; END_IF END_IF I did try a semi-coded way using the IoDrvModbusTCP library, and setting the slave com settings, then 10 commands and 10 requests, then using a TP on xDone as a pause, before triggering another request - this is time the delay is around 120ms - so the device is fine with the speed, just something I am doing wrong in the ModbusFB method I am sure.
Last updated: 2024-04-26

Post by jeffg on ERROR: GetNetLinkSockAndInfoByMac(): could not open netlink socket: Too many open files CODESYS Forge talk (Post)
I just installed codesys runtime on a raspberry pi Cortex-A72 (ARM v8) 64-bit SoC @ 1.5GHz (Compute Module 4) I am running on Codesys control for raspberry pi 64 SL ver 4.13.0 and I keep getting a crash after about five to ten minutes. This program was running fine on a 32bit system with runtime 4.8 previously but they upgraded the panel PC cause it got smashed. Looking at the logs I see this error "ERROR: GetNetLinkSockAndInfoByMac(): could not open netlink socket: Too many open files" at the time of crash. I do have a UDP socket open for a serial to ethernet adapter and im wondering if maybe its opening a bunch of sockets and while receiving messages, Im not sending anything to the device only receiving. Below is the code used for the UDP VAR // Scale Comm fbPeerServer : NBS.UDP_Peer; ipAddress : NBS.IPv4Address; fbReceive : NBS.UDP_Receive; xPeerActiv : BOOL := TRUE; abyReceive : ARRAY [0..255] OF BYTE; sLastValidReceive : STRING(255); udiIndex : UDINT; END_VAR IF xPeerActiv AND NOT fbPeerServer.xBusy THEN ipAddress.SetInitialValue(ipAddress := gvlSettings.sIPAddres); fbPeerServer(xEnable := TRUE, itfIPAddress := ipAddress, uiPort := gvlSettings.uiPort); END_IF fbPeerServer(); fbReceive(xEnable := fbPeerServer.xBusy, itfPeer := fbPeerServer, pData := ADR(abyReceive), udiSize := SIZEOF(abyReceive)); IF fbReceive.udiCount > 0 THEN IF fbReceive.udiCount < SIZEOF(sLastValidReceive) THEN SysMem.SysMemCpy(pDest := ADR(sLastValidReceive), pSrc := ADR(abyReceive), udiCount := fbReceive.udiCount); // Set End of String sLastValidReceive[fbReceive.udiCount] := 0; END_IF END_IF If anyone as seen this I could really use some help figuring it out. I included the Log report
Last updated: 2024-09-19

Post by mondinmr on Why SysPipeWindows is not implemented in RTE? CODESYS Forge talk (Post)
This library would be very useful for IPC communications. Using a UDP socket on localhost is unpredictable, as with slightly loaded machines it does not even guarantee packet delivery locally. Using TCP creates a lot of overhead. Message named pipes would be an excellent solution for Windows RTE. On Linux, since the release of the extension package, there is no issue, as it is sufficient to develop a component. However, although now 90% of our clients understand that Linux runtimes are better in every way compared to Windows RTE, especially from the security aspect (Not in kernel space) and the issues with Windows updates, 10% stubbornly insist (sometimes for trivial commercial reasons) on using Windows. Managing IPC with circular buffers in shared memory is quite ugly, or rather really ugly and unaesthetic. In the manuals, I saw the SysPipeWindows libraries, so I decided to test them, but unfortunately, I noticed that they are not implemented for RTE devices. Technically, I could try to open them as regular files, but SysFileOpen returns 16#27 or 16#39 depending on how I set the name (direction of the slashes). Here is the code to create shared memory and named pipes. Shared memory work great, named pipes no! #ifdef Q_OS_WIN32 SECURITY_ATTRIBUTES sa; SECURITY_DESCRIPTOR sd; InitializeSecurityDescriptor(&sd, SECURITY_DESCRIPTOR_REVISION); SetSecurityDescriptorDacl(&sd, TRUE, NULL, FALSE); sa.nLength = sizeof(SECURITY_ATTRIBUTES); sa.lpSecurityDescriptor = &sd; sa.bInheritHandle = FALSE; const wchar_t* name = L"Global\\ShmTest"; HANDLE hMapFile = CreateFileMapping( INVALID_HANDLE_VALUE, NULL, PAGE_READWRITE, 0, sizeof(SharedData), name); if (hMapFile == NULL) { qCritical("Error creating shared memory"); return 1; } data = static_cast<SharedData*>(MapViewOfFile(hMapFile, FILE_MAP_ALL_ACCESS, 0, 0, sizeof(SharedData))); if (data == NULL) { qCritical("Error mapping shared memory"); return 1; } HANDLE hPipe = CreateNamedPipe( TEXT("\\\\.\\pipe\\MyPipe"), PIPE_ACCESS_DUPLEX, PIPE_TYPE_MESSAGE | PIPE_READMODE_MESSAGE | PIPE_WAIT, PIPE_UNLIMITED_INSTANCES, 1024 * 1024, 1024 * 1024, NMPWAIT_USE_DEFAULT_WAIT, &sa); if (hPipe == INVALID_HANDLE_VALUE) { qCritical("Error creating named pipe"); return -1; } if (!ConnectNamedPipe(hPipe, NULL)) { qCritical("Error connecting to named pipe"); return -1; } checkPipe(hPipe); #endif
Last updated: 2024-02-02

Post by leandroct on Error reading files after runtime update from 4.0.0.0 to 4.8.0.0 CODESYS Forge talk (Post)
Since version 19 they changed how file access is handle. There are two solutions: 1. You change where the file is stored (need to go to: /PlcLogic/) 2. You can, if you don´t want to store at PlcLogic, add the following line in the CODESYSControl.cfg under [SysFile]: ForceIecFilePath=0 The CodesysControl.cfg is at C:\ProgramData\CODESYS\CODESYSControlWinV3x64\xxPROJECT_NUMBERxx\ Here the email they sent me: "with the 3.5.19 Version we changed how files are handled. See following issue: CDS-81506 - CODESYS Control SysFile system file access vulnerability. There are two solutions: 1. You change where the file is stored (need to go to: /PlcLogic/) 2. You can, if you don´t want to store at PlcLogic, add the following line in the CODESYSControl.cfg under [SysFile]: ForceIecFilePath=0 Here is the official release-note: [[COMPATIBILITY_INFORMATION]] With the activation of ForceIecFilePath the file access from IEC is now restricted to the configured paths only (file sandbox)! [SysFile] ForceIecFilePath=1 (new default) The standard path is the current directory, the PlcLogic subfolder or a configured path. Every file access outside of this path is configured via PlaceholderFilePath, for example access to temporary files or removable media: [SysFile] PlaceholderFilePath.1=/tmp, $TMP$ PlaceholderFilePath.2=/media/usb, $USB$ PlaceholderFilePath.2.Volatile=1 For more information see our tutorial FilePath & Placeholders. To restore the old behavior ForceIecFilePath may be configured as follows: [SysFile] ForceIecFilePath=0 BUT WE HIGHLY RECOMMEND TO LEAVE THIS SETTING AT ITS NEW DEFAULT VALUE! "
Last updated: 2024-05-07

Post by john-ronald on Communication error (#0), logout performed,please check if plc is connected CODESYS Forge talk (Post)
Hi, I have the same problem. However I am using ethernet connection not USB. I can ping the PLC and also connect to it via Wago ethernet settings, but I cannot upload using the Codesys 2.3. My PLC is Wago 750-862. The detailed error is - " connect: Connection refused Write attempt from invalid socket. " Any help would be appreciated.
Last updated: 2023-09-11

Post by damian177 on Codesys MQTT subscribe CODESYS Forge talk (Post)
Hi, In my project I have MQTT Client like below: //mqtt client mqttClient( xEnable:=connect_to_broker, sHostname :=sHostname, uiPort:= uiPort, xUseTLS:=FALSE, wsUsername:="", wsPassword:="", xCleanSession:=TRUE, sClientId:='694d45587761676f4b6f6e74656e6572', pbWillMessage := ADR(sWillMessage), uiWillMessageSize:=DINT_TO_UINT(Stu.StrLenA(ADR(sWillMessage))), xWillRetain:=FALSE, udiTimeOut:= 10000000); And ten subscriber's , one of those is below: //subscribe a topic1 mqttSubscriber_S1(xEnable:=subscribe, eSubscribeQoS := 0, pbPayload:=ADR(sSubscribeMessage_S1), udiMaxPayloadSize :=SIZEOF(sSubscribeMessage_S1), mqttClient:=mqttClient, wsTopicFilter:=wsSubcribeTopic_S1); TerminateString(ADR(sSubscribeMessage_S1), mqttSubscriber_S1.udiPayloadSize); After connected to broker I set subscribe to TRUE in alls subscribers and my mqttclient recive error : ACKNOWLEDGE_TIMEOUT what can be wrong ?
Last updated: 2023-10-11

Post by tehthoams on Library Search not working CODESYS Forge talk (Post)
Hello All! Having a strange issue. When adding a library, I'm unable to search. Each time a window pops up 'creating the search index' and then has 0 results. I have the same behavior when using the library repository and pressing the 'Find' button. I wonder if there is a way to reset or fix this issue? It is making it very difficult to search and find proper libraries to add to my project. Much appreciated.
Last updated: 2023-10-17

Post by mmoncada on Dinamically loading recipes CODESYS Forge talk (Post)
I'm having trouble with the initial loading of recipes. I can create them and load one or the other, but when the program restarts the recipes are not listed. I'm calling: RecipeManCommands.ReloadRecipes and then RecipeManCommands.GetRecipeCount which returns 0 recipes. None of the methods returns error and if i call them again after RecipeManCommands.CreateRecipe RecipeManCommands.ReadAndSaveRecipe getRecipeCount returns the number of recipes created. When i restart the system, once again they are not listed even though the recipe files are there. Any ideas? Martin Btw, Codesys 3.5 SP 16 Path 9
Last updated: 2023-12-06

Post by nikgind on Codesys Communication Manger - Required information model version exists in the model repository but is not found CODESYS Forge talk (Post)
Hi, yes i did solve it. You have to change the namespace 0 model in the UaModeler. Open the modeler --> Settings --> Edit Settings --> scroll down to the last option "External Model Support" --> Check "Allow replacing built-in..." Now create a new project in the UaModeler. If you have to choose your base models, you can see the option "Find another Opc.Ua.NodeSet2". I have attached the .xml i am using.
Last updated: 2024-06-28

Post by alexgooi on OPC-UA Boolean format CODESYS Forge talk (Post)
Dear Forum, We are currently making the switch from OPC-DA (Codesys server) to OPC-UA (Running on a Codesys controller). We are using Codesys version 3.5 SP 20. Our Scada system is expecting Boolean's to be represented as a 0/1 (True Boolean) but the OPC-UA server is representing a boolean as False/True This indeed matches the OPC-UA standard, but is there a way to configure the OPC-UA server's boolean representation? Thank you in advance
Last updated: 2024-08-06

Post by liamb on Converting CANbus to Decimal from signed 2's complement CODESYS Forge talk (Post)
I need to combine two 8 bit CANbus messages to 16 bits signed int then convert to decimal Decimal from signed 2's complement. I've been using the below code to read for new messages, combine them then assign them to a variable What is the best way to do this for from signed 2's complement? fbRxMessage351(Data := RxMessage351Data); IF fbRxMessage351.NewMessage THEN ChargeVoltage := (WORD_TO_REAL((RxMessage351Data[0]) + ((RxMessage351Data[1]) * 256))) * 0.1; END_IF
Last updated: 2024-08-16

Post by c3po on Visualisierung wechseln über SPS Variable Codesys 3.5 CODESYS Forge talk (Post)
Sì senor: https://www.helpme-codesys.com/help-sp17-lower.html Abgeschaltet! Peinlich! Ah ich liebe es in Foren nachfragen zu müssen, weil der Support NULL funktioniert. Dieser freundliche Ton immer ô.0 Da bitte, meine Suche: https://www.helpme-codesys.com/search.html?L=1&id=888&tx_solr%5Bq%5D=current+visu 1. Link angeklick: https://content.helpme-codesys.com/en/libs/VisuElemBase/Current/Private-Implementation/pou-Visu_PRG/DoCurrentVisuHandling.html (2. und 3. Link haben mir auch nicht groß weiter geholfen, also habe ich dieses Forum kontaktiert) thx for your help!
Last updated: 2024-08-27

Post by agilename on J1939 manager DM1 message reading CODESYS Forge talk (Post)
https://content.helpme-codesys.com/en/CODESYS%20CANbus/_can_f_j1939_diagnosis_application.html you need this : VAR J1939_ECU:j1939.J1939RemoteECUDiag; DM1_ :j1939.DM1_Read; DTCliste : J1939.idtchandlerList; DTCWriter : j1939.DTCBufferWriter; arDTC:ARRAY[0..MaxDTC]OF j1939.DTC; END_VAR VAR CONSTANT MaxDTC:UDINT :=100; END_VAR DM1_( xEnable:=TRUE, xDone=> , xBusy=> , xError=> , itfSourceECU:= J1939_ECU, //My CAN J1939 ECU itfDTCHandlerList=> DTCListe , udiDTCCount=> , MalfunctionIndicatorLamp=> , RedStopLamp=> , AmberWarningLamp=> , ProtectLamp=> , xReceived=> , eError=> ); DTCWriter( xEnable:= TRUE, itfDTCHandlerList:=DM1_, eError=> , pDTCBuffer:=ADR(arDTC) , udiDTCBufferCount:=MaxDTC , udiDTCReceiveCount=> , udiDTCLostCount=> , xReceived=> );
Last updated: 2024-09-05

Post by naps on Welchen I-Port benötige ich? CODESYS Forge talk (Post)
Hallo, ich versuche eine 750-653(konfiguriert per iocheck) über die Wago Modbus Lib einzusetzen. Ich scheitere im moment an dem Korrekten I-Port. Ich habe es mit 75x_653 und IoConfig_Globals.75x653 versucht, jedoch bekomme ich folgenden fehler: ------ Übersetzungslauf gestartet: Applikation: Device.Application ------- Code typisieren... Code erzeugen... [FEHLER] Unbenannt7: POU_1 Device: SPS-Logik: Application: C0032: Typ 'DED.CAADiagDeviceDefault(caa device diagnosis, 3.5.20.0 (caa technical workgroup))' kann nicht in Typ 'WagoTypesCom.I_WagoSysComBase(wagotypescom, 1.6.2.3 (wago))' konvertiert werden Übersetzung abgeschlossen -- 1 Fehler, 0 Warnungen : Kein Download möglich Wie kann ich den die Karte benutzen?
Last updated: 2024-10-01

Post by balazska2 on Position values with integer variables CODESYS Forge talk (Post)
Hello guys! https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_elem_label.html My question: Could I give an integer variable to the Position records (in the Element list => Position => width / height)? If yes, how? I defined a TEST integer variable with 300 value. I tried to add this variable to the width record (.TEST or only TEST), but if I saved, the value jumps back to 0. Thanks for your help! :)
Last updated: 2024-10-03

Post by mini-developer on Profinet Exor connection drop CODESYS Forge talk (Post)
Hello, I have a Exor HMI with 2 seperatred ETH interface's. It is Configured as PN Master on ETH interface 1 and the IO's are working, as long as the development PC is connected to the ETH 0 interface. When the PC is disconnected, the PN communication drops and a reconnection is started. I installed the newest device description for Codesys and Firmware for the Panel. The IO Gateway is from Weidmueller What could cause the Problem?
Last updated: 2024-10-16